Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Troubleshooting advice requested, because the LED blinking
constantly supposedly indicates that the heater is wired in reverse (which really isn't very likely, so I must be misinterpreting something obvious). Heater worked last year (AFAIK). It just started getting cold in California, so, the heater power was turned on, and ... and ... and ... uh ... um ... no heat. https://c4.staticflickr.com/8/7508/1...4311f464_k.jpg Thermostat batteries are good: https://c1.staticflickr.com/9/8595/1...3c98abbd_k.jpg Heater power is on and the blower blows but the red led blinks at a steady pace forever. https://c4.staticflickr.com/8/7513/1...4a54e186_c.jpg Checked that the switches inside were all on: https://c4.staticflickr.com/8/7510/1...c399d625_b.jpg Checked that the fuse on the circuit board was good: https://c1.staticflickr.com/9/8672/1...4a6d21f8_c.jpg The sticker says constant flashes indicates reverse wiring: https://c4.staticflickr.com/8/7505/1...4f42e6c5_c.jpg But, there's no way the wiring was changed between last year & now. https://c4.staticflickr.com/8/7540/1...2d8775fe_c.jpg Here's what it looks like inside: https://c4.staticflickr.com/8/7561/1...7f78bee3_b.jpg https://c1.staticflickr.com/9/8561/1...7cc1f787_b.jpg I don't know where the model number is, so, I don't have a manual yet. Debugging suggestions are requested, and very helpful. Thanks! |
#2
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/19/2014 6:56 PM, Danny D. wrote:
Troubleshooting advice requested, because the LED blinking constantly supposedly indicates that the heater is wired in reverse (which really isn't very likely, so I must be misinterpreting something obvious). Heater worked last year (AFAIK). It just started getting cold in California, so, the heater power was turned on, and ... and ... and ... uh ... um ... no heat. https://c4.staticflickr.com/8/7508/1...4311f464_k.jpg Thermostat batteries are good: https://c1.staticflickr.com/9/8595/1...3c98abbd_k.jpg Heater power is on and the blower blows but the red led blinks at a steady pace forever. https://c4.staticflickr.com/8/7513/1...4a54e186_c.jpg Checked that the switches inside were all on: https://c4.staticflickr.com/8/7510/1...c399d625_b.jpg Checked that the fuse on the circuit board was good: https://c1.staticflickr.com/9/8672/1...4a6d21f8_c.jpg The sticker says constant flashes indicates reverse wiring: https://c4.staticflickr.com/8/7505/1...4f42e6c5_c.jpg But, there's no way the wiring was changed between last year & now. https://c4.staticflickr.com/8/7540/1...2d8775fe_c.jpg Here's what it looks like inside: https://c4.staticflickr.com/8/7561/1...7f78bee3_b.jpg https://c1.staticflickr.com/9/8561/1...7cc1f787_b.jpg I don't know where the model number is, so, I don't have a manual yet. Debugging suggestions are requested, and very helpful. Thanks! Model number inside the case, in your machine probably on the inner ceiling. As to reverse polarity, you'd have to use a VOM to confirm the black is hot, white is neutral. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#3
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Friday, December 19, 2014 6:57:23 PM UTC-5, Danny D. wrote:
Troubleshooting advice requested, because the LED blinking constantly supposedly indicates that the heater is wired in reverse (which really isn't very likely, so I must be misinterpreting something obvious). Heater worked last year (AFAIK). It just started getting cold in California, so, the heater power was turned on, and ... and ... and ... uh ... um ... no heat. https://c4.staticflickr.com/8/7508/1...4311f464_k.jpg Thermostat batteries are good: https://c1.staticflickr.com/9/8595/1...3c98abbd_k.jpg Heater power is on and the blower blows but the red led blinks at a steady pace forever. https://c4.staticflickr.com/8/7513/1...4a54e186_c.jpg Checked that the switches inside were all on: https://c4.staticflickr.com/8/7510/1...c399d625_b.jpg Checked that the fuse on the circuit board was good: https://c1.staticflickr.com/9/8672/1...4a6d21f8_c.jpg The sticker says constant flashes indicates reverse wiring: https://c4.staticflickr.com/8/7505/1...4f42e6c5_c.jpg But, there's no way the wiring was changed between last year & now. https://c4.staticflickr.com/8/7540/1...2d8775fe_c.jpg Here's what it looks like inside: https://c4.staticflickr.com/8/7561/1...7f78bee3_b.jpg https://c1.staticflickr.com/9/8561/1...7cc1f787_b.jpg I don't know where the model number is, so, I don't have a manual yet. Debugging suggestions are requested, and very helpful. Thanks! According to that secret decoder table, it tells you what's wrong by blinking short blinks, followed by long blinks. Those continue indefinitely, in a pattern. So, are you saying it's not doing that, but instead it's giving you no pattern, just rapid flashes, which the table says is reversed polarity? If so, best guess would be that the oontroller board is kaput. Did you have that flakey generator running it? |
#4
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Fri, 19 Dec 2014 16:14:54 -0800:
According to that secret decoder table, it tells you what's wrong by blinking short blinks, followed by long blinks. Those continue indefinitely, in a pattern. So, are you saying it's not doing that, but instead it's giving you no pattern, just rapid flashes, which the table says is reversed polarity? Here is exactly what the blinking is doing with the cover off and me pressing on the door switch manually: https://www.flickr.com/photos/98287134@N02/15438398234/ This is the secret decoder ring in a full-size JPEG file: https://c4.staticflickr.com/8/7484/1...5d624fe0_c.jpg What do you make of those blinks with the cover off the unit? |
#5
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Fri, 19 Dec 2014 19:13:20 -0500:
Model number inside the case, in your machine probably on the inner ceiling. As to reverse polarity, you'd have to use a VOM to confirm the black is hot, white is neutral. Thanks for that advice. I can check the polarity, but, really, there's no way it changed. So, I must be interpreting the flashes incorrectly. Here is the full-size secret decoder ring: https://c4.staticflickr.com/8/7484/1...5d624fe0_c.jpg Given that, what do folks make of these flashes in this 30-second video while the cover was still on the unit? https://www.flickr.com/photos/98287134@N02/16060716735/ |
#6
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/19/2014 10:21 PM, Danny D. wrote:
Here is exactly what the blinking is doing with the cover off and me pressing on the door switch manually: https://www.flickr.com/photos/98287134@N02/15438398234/ This is the secret decoder ring in a full-size JPEG file: https://c4.staticflickr.com/8/7484/1...5d624fe0_c.jpg What do you make of those blinks with the cover off the unit? I could not tell if it was continuous, or blinking 11. In any case, and open ground can some times give a fault code. I'd get out the VOM, and check for polarity and also check for open ground. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#7
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Sat, 20 Dec 2014 06:01:41 -0500:
I could not tell if it was continuous, or blinking 11. If it's 11, then that corresponds to the following (which I don't understand). 11: NO PREVIOUS CODE - Stored status codes are erased when power (115V or 24V) to control is interrupted or 48 hours after each fault is cleared What does that mean? |
#8
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Sat, 20 Dec 2014 06:01:41 -0500:
I could not tell if it was continuous, or blinking 11. If it's continuous, that corresponds to: RAPID FLASHING - Line voltage (115V) polarity reversed. If twinned, refer to twinning kit instructions. What does "twinned" mean? |
#9
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Saturday, December 20, 2014 6:01:47 AM UTC-5, Stormin Mormon wrote:
On 12/19/2014 10:21 PM, Danny D. wrote: Here is exactly what the blinking is doing with the cover off and me pressing on the door switch manually: https://www.flickr.com/photos/98287134@N02/15438398234/ This is the secret decoder ring in a full-size JPEG file: https://c4.staticflickr.com/8/7484/1...5d624fe0_c.jpg What do you make of those blinks with the cover off the unit? I could not tell if it was continuous, or blinking 11. In any case, and open ground can some times give a fault code. I'd get out the VOM, and check for polarity and also check for open ground. The video wouldn't play in Internet Explorer, just sound. In Chrome it played for me and clearly it shows 1 long flash, 5 short flashes, followed by continuous flashes. The other video, with the door on, just shows it flashing continously, no patterm. Two problems. First the table says the codes are given by the number of long flashes and short flashes, which would lead you to believe the long flashes should come first, not the other way around. Second, no matter, there is no table entry for 1-5 or 5-1. The continous flashing with the cover on, in the other video, I would agree looks like line polarity reversed. Which for a previously installed furnace would appear to be virtually impossible. Another possibility would be that the control board was replaced previously with a different type that has different codes. So, I agree, I'd check with a VOM to make sure AC is in order. After that, IDK. We don't know the sequence of what comes before those videos. If the furnace winds up with that constant blinking in the first video right after power has been removed, then turned back on, I'd say it's most likely the control board. If the light is just on steady, which I think is normal condition, and then when it goes to *fire*, he gets the 1 -5 sequence, then I'd say it's more likely something else, ie that it's detecting something wrong, like pressure, when purging. But why it's not in the list, the blinks seem backward, I guess that's just par for the course with the stuff at D's house. |
#10
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Sat, 20 Dec 2014 05:19:01 -0800:
The video wouldn't play in Internet Explorer, just sound. In Chrome it played for me and clearly it shows 1 long flash, 5 short flashes, followed by continuous flashes. The other video, with the door on, just shows it flashing continously, no patterm. Thanks for taking a look at it, because I saw exactly the same thing. The video with the door on was taken after it was running for ten or fifteen minutes, but with no heat, so I crawled into the crawlspace where the heater was and taped the flashing. There was nothing whatsoever done with the line voltage of this furnace, at least not on purpose. No electricians came to the house. And nothing was done on the furnace whatsoever. So, for the line voltage to reverse, that would be odd. Two problems. First the table says the codes are given by the number of long flashes and short flashes, which would lead you to believe the long flashes should come first, not the other way around. I can't tell if the continuous flashes are long or short. Second, no matter, there is no table entry for 1-5 or 5-1. I did see, as you saw, that the first few seconds of flashes were not the same as the rest of the flashes. I didn't know what to make of it, but you discerned a 1-5, which makes your timing better than mine. Another possibility would be that the control board was replaced previously with a different type that has different codes. Ah. I understand what you're saying. If the control board doesn't match the cover secret decoder ring, then that might explain a lot. We don't know the sequence of what comes before those videos. I'll snap a new "reboot" video today, with the power turned off to the furnace, for a few hours, and then turned back on and started right up so we get the "initial" sequence of flashes. |
#11
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Saturday, December 20, 2014 8:27:16 AM UTC-5, Danny D. wrote:
trader_4 wrote, on Sat, 20 Dec 2014 05:19:01 -0800: The video wouldn't play in Internet Explorer, just sound. In Chrome it played for me and clearly it shows 1 long flash, 5 short flashes, followed by continuous flashes. The other video, with the door on, just shows it flashing continously, no patterm. Thanks for taking a look at it, because I saw exactly the same thing. The video with the door on was taken after it was running for ten or fifteen minutes, but with no heat, so I crawled into the crawlspace where the heater was and taped the flashing. There was nothing whatsoever done with the line voltage of this furnace, at least not on purpose. No electricians came to the house. And nothing was done on the furnace whatsoever. So, for the line voltage to reverse, that would be odd. Two problems. First the table says the codes are given by the number of long flashes and short flashes, which would lead you to believe the long flashes should come first, not the other way around. I can't tell if the continuous flashes are long or short. Second, no matter, there is no table entry for 1-5 or 5-1. I did see, as you saw, that the first few seconds of flashes were not the same as the rest of the flashes. I didn't know what to make of it, but you discerned a 1-5, which makes your timing better than mine. Another possibility would be that the control board was replaced previously with a different type that has different codes. Ah. I understand what you're saying. If the control board doesn't match the cover secret decoder ring, then that might explain a lot. We don't know the sequence of what comes before those videos. I'll snap a new "reboot" video today, with the power turned off to the furnace, for a few hours, and then turned back on and started right up so we get the "initial" sequence of flashes. It doesn't have to be turned off for a few hours, just turned off and back on. Record what it does when power comes back on without a call for heat. If it shows normal, stays that way for a few mins, then turn up the thermostat and see what happens. Another thing, you're not operating the furnace normally. You have the cover off, furnace powered up and you're depressing the door safety switch to initite it. For all we know that 1 -5 sequence could mean "detected door switch open". Power it up with the door switch closed, either with the door on, tape over it, etc. |
#12
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
"Danny D." wrote in news:m73ter$o70$1@dont-
email.me: Second, no matter, there is no table entry for 1-5 or 5-1. The way I see it is that you may need a new controler. |
#13
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/20/2014 7:51 AM, Danny D. wrote:
Stormin Mormon wrote, on Sat, 20 Dec 2014 06:01:41 -0500: I could not tell if it was continuous, or blinking 11. If it's 11, then that corresponds to the following (which I don't understand). 11: NO PREVIOUS CODE - Stored status codes are erased when power (115V or 24V) to control is interrupted or 48 hours after each fault is cleared What does that mean? Means that either someone turned off the power (so the unit lost its memory kind of like a VCR blinking 12:00) or that the fault was so long ago, that the unit lost its memory. In any case, please try shutting off the power for 30 seconds or so, and turn it back on. Some times that handles nussiance trips. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#14
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
Zak W wrote:
"Danny D." wrote in news:m73ter$o70$1@dont- email.me: Second, no matter, there is no table entry for 1-5 or 5-1. The way I see it is that you may need a new controler. He might try blowing the control board off with compressed air . Dust , if damp , can short circuit those miniscule signals ... as I found out after buying a new board for my Goodman furnace . Now I have a spare . -- Snag |
#15
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed(red LED blinks constantly)
Danny D. wrote:
trader_4 wrote, on Fri, 19 Dec 2014 16:14:54 -0800: According to that secret decoder table, it tells you what's wrong by blinking short blinks, followed by long blinks. Those continue indefinitely, in a pattern. So, are you saying it's not doing that, but instead it's giving you no pattern, just rapid flashes, which the table says is reversed polarity? Here is exactly what the blinking is doing with the cover off and me pressing on the door switch manually: https://www.flickr.com/photos/98287134@N02/15438398234/ This is the secret decoder ring in a full-size JPEG file: https://c4.staticflickr.com/8/7484/1...5d624fe0_c.jpg What do you make of those blinks with the cover off the unit? Hi, I believe it is code 33. I am pretty sure. |
#16
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Tony Hwang wrote, on Sat, 20 Dec 2014 19:41:51 -0700:
I believe it is code 33. I am pretty sure. Thanks for looking as it's really hard to tell what the blinking indicates. If it's 33, then that corresponds to: LIMIT OR FLAME ROLL-OUT SWITCH IS OPEN- If open longer than three minutes, code changes to #13. Check for: - Defective blower motor or start capacitor - Loose blower wheel - Inadequate combustion air supply flame roll-out switch or fuse link - Open flame roll-out switch, or fuse link. Manual reset or replace. - Dirty filter or restricted duct system - Defective switch or connections I'm not sure I understand all of those, but some are easy, e.g., I'll look for whereever the filter is (which has never been cleaned to my knowledge). |
#17
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Some of these controllers sense the small electrical conductivity of a fire as a flame sensor. Since the fire is grounded, the flame sense ciccuot senses to earth ground. To do that, the conntroller needs a good earth ground and it gets that through the ac connection. All 3 wires of the ac connection have to be correct. The black has to be hot. The white neutral and the green or bare ground. Check that these 3 connections are correct, including the ground connection. Also chech that these is no sign of water on the electronics. Also chcck the flame sensorrobe wire is not shorted or has water.
Mark |
#18
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
makolber wrote, on Sun, 21 Dec 2014 04:53:55 -0800:
Some of these controllers sense the small electrical conductivity of a fire as a flame sensor. Since the fire is grounded, the flame sense ciccuot senses to earth ground. To do that, the conntroller needs a good earth ground and it gets that through the ac connection. All 3 wires of the ac connection have to be correct. The black has to be hot. The white neutral and the green or bare ground. Check that these 3 connections are correct, including the ground connection. Also chech that these is no sign of water on the electronics. Also chcck the flame sensorrobe wire is not shorted or has water. The area is in a crawlspace that is *above* the house, so, it's pretty dry. At least, I don't see any moisture anywhere, even though it has been raining (thank God) outside. |
#19
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/21/2014 2:51 AM, Danny D. wrote:
Tony Hwang wrote, on Sat, 20 Dec 2014 19:41:51 -0700: I believe it is code 33. I am pretty sure. Thanks for looking as it's really hard to tell what the blinking indicates. If it's 33, then that corresponds to: LIMIT OR FLAME ROLL-OUT SWITCH IS OPEN- If open longer than three minutes, code changes to #13. Check for: - Defective blower motor or start capacitor - Loose blower wheel - Inadequate combustion air supply flame roll-out switch or fuse link - Open flame roll-out switch, or fuse link. Manual reset or replace. - Dirty filter or restricted duct system - Defective switch or connections I'm not sure I understand all of those, but some are easy, e.g., I'll look for whereever the filter is (which has never been cleaned to my knowledge). If this is the trouble code, you most likely have not enough air flow through the furnace, and the furnace is over heating. You might also have a clogged flue. First step is to seek for the air filter, and replace it. Also see if the blower wheel spins while the furnace is on, and calling for heat. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#20
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Sun, 21 Dec 2014 18:39:15 -0500:
First step is to seek for the air filter, and replace it. I opened up all the vents, and removed all the filters. https://c4.staticflickr.com/8/7576/1...eb92f0c2_b.jpg Also see if the blower wheel spins while the furnace is on, and calling for heat. Is this the "blower wheel"? https://c4.staticflickr.com/8/7471/1...173421dd_b.jpg It spins freely manually (but never turns when the blower is running). I also replaced the batteries, in the controller, even though they had tested at 1.4VDC open circuit (the new ones are 1.6 volts open circuit). https://c4.staticflickr.com/8/7534/1...12b21a95_b.jpg |
#21
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Sat, 20 Dec 2014 09:45:08 -0500:
In any case, please try shutting off the power for 30 seconds or so, and turn it back on. Some times that handles nussiance trips. I turned the power off and then after a few minutes, back on. Nothing changed. I tried to check voltages, but I don't know what to test: https://c4.staticflickr.com/8/7550/1...abb172d6_b.jpg The model is Bryant 373LAV024070, input 69,000BTU, output 66,000 BTU: https://c4.staticflickr.com/8/7568/1...8fa24051_b.jpg |
#22
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Sat, 20 Dec 2014 05:37:54 -0800:
It doesn't have to be turned off for a few hours, just turned off and back on. Record what it does when power comes back on without a call for heat. If it shows normal, stays that way for a few mins, then turn up the thermostat and see what happens. I turned off the power. Put the covers back on. Turned the power back on. Waited about 20 minutes. Turned it off for a few minutes. Turned it back on. Set the heat to HOLD at 80 degrees. The blinking lights don't seem to have changed. Here is the latest blinking light - which is odd as it stumbles at 24 seconds, but I don't know what to make of that anomaly. https://www.flickr.com/photos/98287134@N02/15889437369/ |
#23
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Tony Hwang wrote, on Sat, 20 Dec 2014 19:41:51 -0700:
I believe it is code 33. I am pretty sure. I found where to get manuals but I can't find the exact model: http://www.bryant.com/apps/finddocs/form.jsp?b=b The model is a Bryant 373LAV024070 (AGJA). https://c4.staticflickr.com/8/7568/1...8fa24051_b.jpg The closest Bryant PDF manual I can find is: 373LAV 376CAV Downflow/Horizontal and 383KAV 395CAV Upflow Gas Furnace http://dms.hvacpartners.com//docs/10...0B/OM04-35.pdf 383KAV Upflow Gas Furnace 373LAV Downflow Horizontal Gas Furnace http://dms.hvacpartners.com//docs/10...83_373-005.pdf I'll call Bryant on Monday to figure out why I can't find the exact model in the lists of documents: 800-428-4326 from 5:00am-2:00pm (Pacific) weekdays. |
#24
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Instead of making it fire, what does it do/flash if you just power it up with no call for heat?
|
#25
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
You have the model. The last numbers are the specific size and output. 24 may be width, 70k btus?
|
#26
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Sun, 21 Dec 2014 22:40:38 -0800:
Instead of making it fire, what does it do/flash if you just power it up with no call for heat? It appears to do the same thing, but I need to test further. |
#27
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Monday, December 22, 2014 6:32:55 AM UTC-5, Danny D. wrote:
trader_4 wrote, on Sun, 21 Dec 2014 22:40:38 -0800: Instead of making it fire, what does it do/flash if you just power it up with no call for heat? It appears to do the same thing, but I need to test further. Then it's nothing to do with it failing to ignite, overheating, gas supply, etc. It;'s detecting something wrong with just the application of power, without it even having a call for heat, trying to fire, etc. Could be some sensor input is lacking, but then you'd think it would be flashing a code that was in the table. Given what it's doing, my first suspicion would be that it's a bad control board. Did you put a meter on it when power is first applied, verified that it has 120V, ground is OK, etc? |
#28
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/21/2014 7:41 PM, Danny D. wrote:
Stormin Mormon wrote, on Sun, 21 Dec 2014 18:39:15 -0500: First step is to seek for the air filter, and replace it. I opened up all the vents, and removed all the filters. https://c4.staticflickr.com/8/7576/1...eb92f0c2_b.jpg CY: Yow, that's cruddy. And it looks like the air flow is blocked. Should be open. Is it possible some one walled off the air vent? Also see if the blower wheel spins while the furnace is on, and calling for heat. Is this the "blower wheel"? https://c4.staticflickr.com/8/7471/1...173421dd_b.jpg CY: That indicated item is the inducer fan. I meant the blower which should be about a foot diameter, and about a foot long. Hope this picture arrives: http://www.meci.com/ebay1/7350905-0510.jpg If the air handler blower isn't running, the furnace will over heat. It spins freely manually (but never turns when the blower is running). CY: Spins freely is good. The black six inch diameter counter weight should run when the furnace is calling for heat. It moves air through the combustion chamber. The six inch blower has to spin up to speed before the gas valve opens. I also replaced the batteries, in the controller, even though they had tested at 1.4VDC open circuit (the new ones are 1.6 volts open circuit). https://c4.staticflickr.com/8/7534/1...12b21a95_b.jpg CY: New batteries is a good idea. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#29
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/21/2014 7:45 PM, Danny D. wrote:
Stormin Mormon wrote, on Sat, 20 Dec 2014 09:45:08 -0500: In any case, please try shutting off the power for 30 seconds or so, and turn it back on. Some times that handles nussiance trips. I turned the power off and then after a few minutes, back on. Nothing changed. I tried to check voltages, but I don't know what to test: https://c4.staticflickr.com/8/7550/1...abb172d6_b.jpg The model is Bryant 373LAV024070, input 69,000BTU, output 66,000 BTU: https://c4.staticflickr.com/8/7568/1...8fa24051_b.jpg If you're safe with a VOM, here's the technique: Where the BX cable comes in on top (right over the inducer fan), it ties into the furnace inside the small box inside the case of the furnace. You can get into the small box, and check for polarity and if the ground is connected. I hesitate to suggest people open up safety boxes and work with live power, some folks can't do that safely. Prefer not to go into a lot of detail on an open forum. Open ground can cause problems, also. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#30
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 07:50:33 -0500:
https://c4.staticflickr.com/8/7576/1...eb92f0c2_b.jpg CY: Yow, that's cruddy. And it looks like the air flow is blocked. Should be open. Is it possible some one walled off the air vent? I stuck my hands in there, and the opening is above. Plus, it used to work, and nobody has touched it since. It *was* embarrassing when I saw that cruddy filter. I almost didn't want to post a picture before I cleaned it. According to the manual, there is supposedly a "v-shaped" set of filters at the blower itself, but I haven't been able to find them yet. |
#31
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 07:50:33 -0500:
CY: That indicated item is the inducer fan. I meant the blower which should be about a foot diameter, and about a foot long. Hope this picture arrives: http://www.meci.com/ebay1/7350905-0510.jpg If the air handler blower isn't running, the furnace will over heat. I found that blower you show after looking at the manual: http://dms.hvacpartners.com//docs/10...0B/OM04-35.pdf Mine is apparently a "downflow" horizontal model (373LAV), whatever "downflow" means (as opposed to "upflow" types). I guess that this means that the air flows "down", which, in the case of my furnace, is sidewise, I presume to the right (but I'm just guessing since the direction of airflow isn't described in the manual). I called Bryant (at 800-428-4326x3), who confirmed the furnace is a series G, which was built within the last 15 years, and actually, based on the serial number, was built in 1999. They will be sending me more detailed manuals, which I will let you know when I get them. |
#32
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 9:20 AM, Danny D. wrote:
Stormin Mormon wrote, on Mon, 22 Dec 2014 07:50:33 -0500: CY: That indicated item is the inducer fan. I meant the blower which should be about a foot diameter, and about a foot long. Hope this picture arrives: http://www.meci.com/ebay1/7350905-0510.jpg If the air handler blower isn't running, the furnace will over heat. I found that blower you show after looking at the manual: http://dms.hvacpartners.com//docs/10...0B/OM04-35.pdf Mine is apparently a "downflow" horizontal model (373LAV), whatever "downflow" means (as opposed to "upflow" types). I guess that this means that the air flows "down", which, in the case of my furnace, is sidewise, I presume to the right (but I'm just guessing since the direction of airflow isn't described in the manual). I called Bryant (at 800-428-4326x3), who confirmed the furnace is a series G, which was built within the last 15 years, and actually, based on the serial number, was built in 1999. They will be sending me more detailed manuals, which I will let you know when I get them. Some applications like mobile homes, the air flows from top to bottom (downflow). Many houses have furnace in the cellar, and are up flow, meaning the conditioned air blows out the top. In the horizontal, doesn't make much difference. Anyhow, good luck and skill. I hesitate to do much electrical coaching on an open list like this. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#33
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Mon, 22 Dec 2014 03:57:10 -0800:
Could be some sensor input is lacking, but then you'd think it would be flashing a code that was in the table. Given what it's doing, my first suspicion would be that it's a bad control board. Did you put a meter on it when power is first applied, verified that it has 120V, ground is OK, etc? I agree with you that the first thing I need to test is power and control inputs. The sad thing is that I don't have a clue how to test that, as only once before did I ever troubleshoot a furnace. I don't even remember if it's AC or DC control inputs. Nor which color wires do what (although I do remember that it's a standard, so, I can look that up). I just received from Bryant two more PDF manuals, in addition to the sparse 12-page 373 LAV Series G "User's Information Manual" that I had already found, namely: a. Installation Start-up, and Operating Instructions (24 pages) b. Service and Maintenance Procedures (16 pages) I can convert the PDF to JPEG and then post the JPG so you can read them, but is there a way to just post the PDF for you to view them to help interpret them? |
#34
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 9:30 AM, Danny D. wrote:
The sad thing is that I don't have a clue how to test that, as only once before did I ever troubleshoot a furnace. I don't even remember if it's AC or DC control inputs. Nor which color wires do what (although I do remember that it's a standard, so, I can look that up). Do you have some friends to call? Someone out there has to know how to use a VOM. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#35
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Monday, December 22, 2014 9:30:56 AM UTC-5, Danny D. wrote:
trader_4 wrote, on Mon, 22 Dec 2014 03:57:10 -0800: Could be some sensor input is lacking, but then you'd think it would be flashing a code that was in the table. Given what it's doing, my first suspicion would be that it's a bad control board. Did you put a meter on it when power is first applied, verified that it has 120V, ground is OK, etc? I agree with you that the first thing I need to test is power and control inputs. The sad thing is that I don't have a clue how to test that, as only once before did I ever troubleshoot a furnace. I don't even remember if it's AC or DC control inputs. Nor which color wires do what (although I do remember that it's a standard, so, I can look that up). I just received from Bryant two more PDF manuals, in addition to the sparse 12-page 373 LAV Series G "User's Information Manual" that I had already found, namely: a. Installation Start-up, and Operating Instructions (24 pages) b. Service and Maintenance Procedures (16 pages) I can convert the PDF to JPEG and then post the JPG so you can read them, but is there a way to just post the PDF for you to view them to help interpret them? The thing is constantly flashing, which according to the table, is polarity reversed. That's virtually impossible, but there could be something wrong with the incoming AC. To test it with a VOM: turn off power, usually via turning off the red safety toggle switch that's mounted near the furnace. get access to the incoming AC, remove wire nuts from hot and neutral, but leave wires twisted together make sure wires are in the air, not touching anything then turn power switch back on with VOM check for 120V from hot (black) to neutral (white). 120V from hot to ground (that tells you it's not reversed polarity and that the ground is likely OK. 0V from neutral to ground Then turn off power and put it back together. You could also do it easier without removing wire nuts if you can find hot/neutral identified on the control board. You could just probe it there. If you're unsure about any of that, or basic electric safety, I agree with Stormin. Either call a friend in who is, or just call for service. Besides, I'd bet 99% that nothing is wrong with the power. |
#36
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 07:54:59 -0500:
If you're safe with a VOM, here's the technique: I'm perfectly fine with 120/220V and can easily work with my Fluke 75 on the furnace. I just need to know what to check, bearing in mind that it's not at first obvious where the power comes in yet. You can get into the small box, and check for polarity and if the ground is connected. I can't imagine that the power polarity has reversed, on its own, but, as you note, I should check it (since the flashing is hard to understand and one interpretation of the flashes might be that the power polarity is reversed). Of course, that only matters for DC, right? So I'd need to know *where* the DC is coming from, since the line voltage is AC (yes, I know a neutral isn't the same as a hot, nor even the same as a ground, but, in terms of polarity, switching a neutral with a hot shouldn't matter for AC motors or step-down transformers (which I presume exist near the circuit board). I hesitate to suggest people open up safety boxes and work with live power, some folks can't do that safely. Prefer not to go into a lot of detail on an open forum. I have no problem whatsoever working around power. |
#37
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 09:28:15 -0500:
Some applications like mobile homes, the air flows from top to bottom (downflow). Based on the additional manuals supplied by Bryant today, I can confirm the air flow comes from the blower at the left (i.e., the top) and out the right (i.e., the bottom). https://c4.staticflickr.com/8/7463/1...a75d2197_b.jpg |
#38
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 10:36 AM, Danny D. wrote:
I hesitate to suggest people open up safety boxes and work with live power, some folks can't do that safely. Prefer not to go into a lot of detail on an open forum. I have no problem whatsoever working around power. I check my hotmail adress every few days, more often if I know an email is coming from a friend. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#39
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 09:38:59 -0500:
Do you have some friends to call? Someone out there has to know how to use a VOM. Heh heh ... I know how to use a DMM as well as anyone here knows how to use one. I have had Simpson (analog) ammeters and voltmeters since I was a young teen, when I was making my own resistance testing equipment long before consumer DMMs were common. My Fluke 75 is a good meter, which I've had for something like 30 years. So, *using* a meter isn't at all a problem. The problem is knowing what measurements to take. To that end, this control board summary is a start: https://c4.staticflickr.com/8/7511/1...a7b9a83c_h.jpg As is this wiring control schematic: https://c1.staticflickr.com/9/8616/1...d2721b93_h.jpg And, of course, as is the overall furnace circuit schematic: https://c4.staticflickr.com/8/7560/1...e91c4626_b.jpg All of which I'm new to, but, which I will print and pore over to see what basic control and power inputs to test with my trusty DMM. |
#40
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Mon, 22 Dec 2014 06:51:01 -0800:
Besides, I'd bet 99% that nothing is wrong with the power. I'll check that the white (neutral) has no voltage difference with green or bare (ground), and that the black (hot) has line voltage (120VAC) to both the neutral and ground, but, like you, I am 99.9% sure that can't possibly be the problem. The problem is "probably" described in this flow chart though... https://c4.staticflickr.com/8/7506/1...6bb628a5_c.jpg |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Why is my immersion heater wired with 4mm cable?! | UK diy | |||
Bryant Plus 90 furnace (gas heater) error code 33 | Home Repair | |||
12v dc DVD player wired incorrectly ie. polarity reversed to a 12v dc battery pack | Home Repair | |||
POSSIBLY OFF TOPIC: Screwfix electric heater. | UK diy | |||
Central Heater: water constantly running | UK diy |