Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#201
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Danny D. wrote, on Fri, 19 Dec 2014 23:56:58 +0000:
It just started getting cold in California, so, the heater power was turned on, and ... and ... and ... uh ... um ... no heat. https://c4.staticflickr.com/8/7508/1...4311f464_k.jpg Update! The heater certainly hasn't been turned on in a year, and maybe in two years (as last year was warm). I don't remember, but, anyway, the problem first looked like a reverse wire but the code was basically constantly blinking. As far as I can tell, that just means whatever old code was in there has been wiped from the memory, so, it just blinked incessantly to tell us that. Anyway, we narrowed the problem to the fact that the flame wasn't sensed, and, that meant only one of three things: 1. Bad flame sensor 2. Bad ground for the flame sensor circuit (through the flame) 3. Bad control board sensing of the flame sensor circuit. I cleaned the flame sensor to no avail. Replacing the $20 flame sensor solved the problem! It's amazing that a simple stainless steel rod could fail, but, it apparently did! Who knows why or how. The way the flame sensor works is that 90VAC (nominal) is sent to the flame sensor, which is just a steel rod with a single electrical connection. When there is a flame, electrons flow from the steel rod to the chassis ground of the burners through the flame (rectifying the 90VAC to DC). The flame sensor circuit on the control board senses the 5ua of DC current, and keeps the relays on which control the propane gas flow. The moment the 5ua of current isn't sensed, the control board shuts down the relays controlling the flame, which is what was happening. So, there was nothing wrong with the furnace, other than the flame wasn't being sensed. With the new flame sensor, everything is working fine. https://c1.staticflickr.com/9/8565/1...6ed2ba81_b.jpg What is almost incompressible to me is HOW the flame sensor failed. It wasn't dirty. It wasn't shorted. It's just a steel rod! The ceramic wasn't visibly cracked. I just don't get it, but, it is what it is. |
#202
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
On Wed, 31 Dec 2014 05:22:55 +0000 (UTC), "Danny D."
wrote: Danny D. wrote, on Fri, 19 Dec 2014 23:56:58 +0000: It just started getting cold in California, so, the heater power was turned on, and ... and ... and ... uh ... um ... no heat. https://c4.staticflickr.com/8/7508/1...4311f464_k.jpg Update! The heater certainly hasn't been turned on in a year, and maybe in two years (as last year was warm). I don't remember, but, anyway, the problem first looked like a reverse wire but the code was basically constantly blinking. As far as I can tell, that just means whatever old code was in there has been wiped from the memory, so, it just blinked incessantly to tell us that. Anyway, we narrowed the problem to the fact that the flame wasn't sensed, and, that meant only one of three things: 1. Bad flame sensor 2. Bad ground for the flame sensor circuit (through the flame) 3. Bad control board sensing of the flame sensor circuit. I cleaned the flame sensor to no avail. Replacing the $20 flame sensor solved the problem! It's amazing that a simple stainless steel rod could fail, but, it apparently did! Who knows why or how. The way the flame sensor works is that 90VAC (nominal) is sent to the flame sensor, which is just a steel rod with a single electrical connection. When there is a flame, electrons flow from the steel rod to the chassis ground of the burners through the flame (rectifying the 90VAC to DC). The flame sensor circuit on the control board senses the 5ua of DC current, and keeps the relays on which control the propane gas flow. The moment the 5ua of current isn't sensed, the control board shuts down the relays controlling the flame, which is what was happening. So, there was nothing wrong with the furnace, other than the flame wasn't being sensed. With the new flame sensor, everything is working fine. https://c1.staticflickr.com/9/8565/1...6ed2ba81_b.jpg What is almost incompressible to me is HOW the flame sensor failed. It wasn't dirty. It wasn't shorted. It's just a steel rod! The ceramic wasn't visibly cracked. I just don't get it, but, it is what it is. Congratulations on fixing the problem. However, from an education point of view, your statement that the flame sensor is just a hunk of stainless steel is NOT correct. Google "thermocouple" and see how they work. The current does not go through the flame. It is generated by two pieces of dissimilar metals creating a voltage which then causes a tiny current to flow and be sensed. They can and do go bad. |
#203
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater, and now Donner party questions
On 12/28/2014 8:36 PM, Oren wrote:
Think about Donner Pass over the mountains. Folks became cannibals to survive. Ate members of their party that died from the elements. https://en.wikipedia.org/wiki/Donner_Pass#Weather "...The pass was named after a later group of California-bound emigrants. In early November 1846 the Donner Party found the route blocked by snow and was forced to spend the winter on the east side of the mountains. Of the 81 emigrants, only 45 survived to reach California; some of them resorted to cannibalism to survive." Interesting question. The Wiki page totally did not have this information. The Donner party was a group of..... kind of people. What did the Donner group have in common? The Donners were travelling why? I know.... does anyone else? - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#204
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 12:01 AM, Danny D. wrote:
The house has three separate furnaces. Two are down, and have been down for a couple of years. We usually don't bother using them. It rarely gets below freezing - maybe once a year or twice at most. No snow (a dusting once every five years). We use warm blankets. Lots of them! The only problem is I'm soured on down. I bought perhaps ten down blankets over the years, mostly at Costco, and while they're soft, they tear and bunch up in the wash, so much that I'm not going to buy down ever again. We have goose feathers all over the house. Thanks, didn't know. Hey, hope you can get heat before you have to eat your grand kids. So, the Bryant in question was ... uh.... the last straw? Furnaces of a feather flock together? One bad apple done spoil the whole bunch? -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#205
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 12:05 AM, Danny D. wrote:
Danny D. wrote, on Sun, 28 Dec 2014 02:41:33 +0000: Did you get the new flame sensor in? It's supposed to arrive on Tuesday due to the holidays. Woo hoo! Who would have thought a stainless steel rod could fail! https://c1.staticflickr.com/9/8565/1...6ed2ba81_b.jpg The moment I put the new one in, the heater worked like a charm! https://c4.staticflickr.com/8/7522/1...39c96820_c.jpg The meter still read 0.0 microamps, so, I'm sure the fuse was already blown before I got it! https://c4.staticflickr.com/8/7563/1...5a45a263_c.jpg You guys were right all along! Thanks for the follow up. Good to know you at least have "some" heat, now. I hope it's enough to keep your house comfortable. No resorting to canibalism for your family, this year. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#206
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
On Wed, 31 Dec 2014 04:31:14 +0000 (UTC), "Danny D."
wrote in Unfortunately, if you own a BMW, and if you do all your own work, you're forced to learn a LOT about the thing. Next time buy a Honda. |
#207
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Wednesday, December 31, 2014 12:06:02 AM UTC-5, Danny D. wrote:
Danny D. wrote, on Sun, 28 Dec 2014 02:41:33 +0000: Did you get the new flame sensor in? It's supposed to arrive on Tuesday due to the holidays. Woo hoo! Who would have thought a stainless steel rod could fail! https://c1.staticflickr.com/9/8565/1...6ed2ba81_b.jpg The moment I put the new one in, the heater worked like a charm! https://c4.staticflickr.com/8/7522/1...39c96820_c.jpg The meter still read 0.0 microamps, so, I'm sure the fuse was already blown before I got it! https://c4.staticflickr.com/8/7563/1...5a45a263_c.jpg You guys were right all along! So, what's the logical conclusion here? That something changed in the properties of the metal? That's about all that's left, isn't it? The insulator isn't shorted, it had continuity from tip to wire, etc..... Funny thing, in the limited reading I did about flame sensors, I didn't see anything about the metal needing to be special. Only that it needed to be clean and you cleaned it up with sandpaper or steel wool, etc. I'm left wondering what the actualy failure was. Good to hear you got it going though and good info for the future. |
#208
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 12:22 AM, Danny D. wrote:
With the new flame sensor, everything is working fine. https://c1.staticflickr.com/9/8565/1...6ed2ba81_b.jpg What is almost incompressible to me is HOW the flame sensor failed. It wasn't dirty. It wasn't shorted. It's just a steel rod! The ceramic wasn't visibly cracked. I just don't get it, but, it is what it is. I've forgotten that information. But still, results is what counts. I've also replaced a couple sensor rods. Now, on to the next repair. With 500 posts, 50 Flickr pictures, and 4,000 reply posts from the list. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#209
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 6:21 AM, Pat wrote:
.... Congratulations on fixing the problem. However, from an education point of view, your statement that the flame sensor is just a hunk of stainless steel is NOT correct. Google "thermocouple" and see how they work. The current does not go through the flame. It is generated by two pieces of dissimilar metals creating a voltage which then causes a tiny current to flow and be sensed. They can and do go bad. Flame sensors of this type are _not_ thermocouples and indeed the current is carried by the flame (actually ions produced by the combustion process). Thermocouples are also used, but they're entirely different. It is correct, however, that the flame detector is quite a bit more than just a chunk of SS... http://www.gayesco.com/Prod_Flame_Rods.htm -- |
#210
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
On Wed, 31 Dec 2014 09:00:35 -0600, dpb wrote:
On 12/31/2014 6:21 AM, Pat wrote: ... Congratulations on fixing the problem. However, from an education point of view, your statement that the flame sensor is just a hunk of stainless steel is NOT correct. Google "thermocouple" and see how they work. The current does not go through the flame. It is generated by two pieces of dissimilar metals creating a voltage which then causes a tiny current to flow and be sensed. They can and do go bad. Flame sensors of this type are _not_ thermocouples and indeed the current is carried by the flame (actually ions produced by the combustion process). Thermocouples are also used, but they're entirely different. It is correct, however, that the flame detector is quite a bit more than just a chunk of SS... http://www.gayesco.com/Prod_Flame_Rods.htm Thank you for the education. I was not aware of that type. |
#211
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater, and now Donner party questions
On Wed, 31 Dec 2014 08:14:38 -0500, Stormin Mormon
wrote: On 12/28/2014 8:36 PM, Oren wrote: Think about Donner Pass over the mountains. Folks became cannibals to survive. Ate members of their party that died from the elements. https://en.wikipedia.org/wiki/Donner_Pass#Weather "...The pass was named after a later group of California-bound emigrants. In early November 1846 the Donner Party found the route blocked by snow and was forced to spend the winter on the east side of the mountains. Of the 81 emigrants, only 45 survived to reach California; some of them resorted to cannibalism to survive." Interesting question. The Wiki page totally did not have this information. The Donner party was a group of..... kind of people. What did the Donner group have in common? The Donners were travelling why? I know.... does anyone else? http://mormonhistoricsites.org/wp-content/uploads/2013/05/NJ9.1_Dorius.pdf |
#212
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
On Wed, 31 Dec 2014 05:05:34 +0000 (UTC), "Danny D."
wrote: Woo hoo! Who would have thought a stainless steel rod could fail! https://c1.staticflickr.com/9/8565/1...6ed2ba81_b.jpg The moment I put the new one in, the heater worked like a charm! https://c4.staticflickr.com/8/7522/1...39c96820_c.jpg Good job Danny. |
#213
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Wed, 31 Dec 2014 08:18:12 -0500:
Thanks for the follow up. Good to know you at least have "some" heat, now. Two out of three is pretty good, compared to 1 out of 3 before. |
#214
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Wed, 31 Dec 2014 05:29:47 -0800:
I'm left wondering what the actualy failure was. I am clueless. Maybe cracked ceramic that only opened up under red hot heating of the metal rod? Even then, what's the failure mode? It would just be easier for the electrons to get to the chassis (which is what they're trying to do through the flame). I really do not understand the failure mode, especially as this thing is clean as can be. I wish I understood HOW it failed. |
#215
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
VinnyB wrote, on Wed, 31 Dec 2014 07:22:32 -0600:
Next time buy a Honda. We don't do FWD. But a Toyota will work fine! |
#216
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Pat wrote, on Wed, 31 Dec 2014 07:21:06 -0500:
your statement that the flame sensor is just a hunk of stainless steel is NOT correct. Google "thermocouple" We thought the same thing too... at first. |
#217
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
dpb wrote, on Wed, 31 Dec 2014 09:00:35 -0600:
indeed the current is carried by the flame (actually ions produced by the combustion process). I find it interesting that the electrons flow, in effect, backward, in the opposite direction of the flame, from the stainless steel rod, along the flame, back to the burner metal to ground. |
#218
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
On Wed, 31 Dec 2014 23:37:23 +0000 (UTC), "Danny D."
wrote: trader_4 wrote, on Wed, 31 Dec 2014 05:29:47 -0800: I'm left wondering what the actualy failure was. I am clueless. Maybe cracked ceramic that only opened up under red hot heating of the metal rod? Even then, what's the failure mode? It would just be easier for the electrons to get to the chassis (which is what they're trying to do through the flame). I really do not understand the failure mode, especially as this thing is clean as can be. I wish I understood HOW it failed. My guess is the metal expands and opens a crack in the ceramic (not visible). I've read about this on a gas grill and stove igniters. Don't recall the details - sorry. I was hinting about it earlier in the thread. Would that be a short to ground? |
#219
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
dpb wrote, on Wed, 31 Dec 2014 09:00:35 -0600:
the flame detector is quite a bit more than just a chunk of SS... http://www.gayesco.com/Prod_Flame_Rods.htm PHYSICAL CONFIGURATION 1. The flame rod consists of a center electrode and an outer metallic sheath. 2. The electrode is isolated from the outer sheath by an insulating material. 3. The end of the flame rod, in the flame path, has a special high temperature hermetic seal with a threaded adaptor which is connected to the center electrode. 4. A high temperature sensing rod is attached to the threaded adaptor. I'm confused. Is the "outer sheath" the ceramic? Or, is the outer sheath the stainless steel rod exterior? |
#220
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 5:48 PM, Danny D. wrote:
dpb wrote, on Wed, 31 Dec 2014 09:00:35 -0600: the flame detector is quite a bit more than just a chunk of SS... http://www.gayesco.com/Prod_Flame_Rods.htm PHYSICAL CONFIGURATION 1. The flame rod consists of a center electrode and an outer metallic sheath. 2. The electrode is isolated from the outer sheath by an insulating material. 3. The end of the flame rod, in the flame path, has a special high temperature hermetic seal with a threaded adaptor which is connected to the center electrode. 4. A high temperature sensing rod is attached to the threaded adaptor. I'm confused. Is the "outer sheath" the ceramic? Or, is the outer sheath the stainless steel rod exterior? As it says, the center electrode is isolated from the outer metallic sheath by the ceramic. IOW, it's a center rod in the center of a ceramic insulator all surrounded by the outer case that you see. It's not a "rod" at all but a composite assembly that looks solid from the outside. -- |
#221
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 5:45 PM, Danny D. wrote:
dpb wrote, on Wed, 31 Dec 2014 09:00:35 -0600: indeed the current is carried by the flame (actually ions produced by the combustion process). I find it interesting that the electrons flow, in effect, backward, in the opposite direction of the flame, from the stainless steel rod, along the flame, back to the burner metal to ground. The primary direction of current flow is determined by the relative sizes of the two electrodes...iow, it's determined by the geometry of the detector in relationship to the burner to set up the current flow as desired. I didn't find a readable text(*); perhaps the Robertshaw publication will help some... http://www.google.com/url?sa=t&rct=j...63_RevB_1.pdf& ei=t6KkVL29G4qFyQSRw4KYAw&usg=AFQjCNEdbUKV1Mm-cBkT8B4Ui1HGDtt9xg (*) And, while am a MS Physics guy, I'm not going to try because I find as soon as I do I end delving far too deeply and confound rather than explain... -- |
#222
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Wednesday, December 31, 2014 8:14:03 PM UTC-5, dpb wrote:
On 12/31/2014 5:48 PM, Danny D. wrote: dpb wrote, on Wed, 31 Dec 2014 09:00:35 -0600: the flame detector is quite a bit more than just a chunk of SS... http://www.gayesco.com/Prod_Flame_Rods.htm PHYSICAL CONFIGURATION 1. The flame rod consists of a center electrode and an outer metallic sheath. 2. The electrode is isolated from the outer sheath by an insulating material. 3. The end of the flame rod, in the flame path, has a special high temperature hermetic seal with a threaded adaptor which is connected to the center electrode. 4. A high temperature sensing rod is attached to the threaded adaptor. I'm confused. Is the "outer sheath" the ceramic? Or, is the outer sheath the stainless steel rod exterior? As it says, the center electrode is isolated from the outer metallic sheath by the ceramic. IOW, it's a center rod in the center of a ceramic insulator all surrounded by the outer case that you see. It's not a "rod" at all but a composite assembly that looks solid from the outside. -- IDK what flame sensor you have there, but from the dimensions it looks like it's a foot or more long, 1/2" in diameter and certainly not for a typical home furnace. The one Danny has pics of does look like a small rod, mounted on an insulator, connected to a wire. The descriptions I've read about rod to flame conductivity also don't say anything special about the reqts for the rod. They just say that a metal rod inserted into a flame will conduct a current when voltage is applied. That would seem to coincide with what he has, ie a metal rod on an insulator mount. |
#223
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 7:52 PM, trader_4 wrote:
.... IDK what flame sensor you have there, but from the dimensions it looks like it's a foot or more long, 1/2" in diameter and certainly not for a typical home furnace. The one Danny has pics of does look like a small rod, mounted on an insulator, connected to a wire. The descriptions I've read about rod to flame conductivity also don't say anything special about the reqts for the rod. They just say that a metal rod inserted into a flame will conduct a current when voltage is applied. That would seem to coincide with what he has, ie a metal rod on an insulator mount. Those are commercial for larger boilers, etc., but the physics is the same. There must be an isolated section for the current flow; otherwise it would also be grounded. The _precise_ configuration is immaterial... -- |
#224
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Thursday, January 1, 2015 9:25:28 AM UTC-5, dpb wrote:
On 12/31/2014 7:52 PM, trader_4 wrote: ... IDK what flame sensor you have there, but from the dimensions it looks like it's a foot or more long, 1/2" in diameter and certainly not for a typical home furnace. The one Danny has pics of does look like a small rod, mounted on an insulator, connected to a wire. The descriptions I've read about rod to flame conductivity also don't say anything special about the reqts for the rod. They just say that a metal rod inserted into a flame will conduct a current when voltage is applied. That would seem to coincide with what he has, ie a metal rod on an insulator mount. Those are commercial for larger boilers, etc., but the physics is the same. There must be an isolated section for the current flow; otherwise it would also be grounded. The _precise_ configuration is immaterial... -- I agree. The isolated section is the metal rod with a wire attached. It's housed in a ceramic insulator that holds it and keeps it isolated from the furnace metal. The flame completes the circuit. The controller board sends it a small current, at about 90V?. If the flame is there, the controller detects that current is flowing, because the flame can conduct a small current, it actually rectifies it. I had no idea how this worked before, but that's what I learned from googling. I haven't seen anything about any special requirements beyond that. And the pics Danny posted of his flame sensors sure look like just a metal rod housed in a ceramic insulator. So, from everything I've seen so far about how it works, the physics, etc it sounds like just a metal rod. So, if that's right, then the question remains, what failed in Danny's detector? There have been so many posts, I'm unsure of is what exactly he measured, what the readings were, etc. I think he measured that there was infinite resistance between rod and furnace metal, ie no shorting of the insulator. I think he verified conductivity from end of wire to tip of rod, but not sure what exactly he measured there. So, I don't understand what could be wrong with the old one...... |
#225
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/31/2014 12:09 AM, Danny D. wrote:
Stormin Mormon wrote, on Mon, 29 Dec 2014 10:01:01 -0500: Danny will soon have to eat his grand kids to stay alive? We're still feeding them to fatten 'em up first! https://c4.staticflickr.com/8/7522/1...f6b75fee_b.jpg I'd eat Gretel first, Hansel can still help fix the overhead deck you had blow down. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#226
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 01/01/2015 8:41 AM, trader_4 wrote:
.... So, if that's right, then the question remains, what failed in Danny's detector? There have been so many posts, I'm unsure of is what exactly he measured, what the readings were, etc. I think he measured that there was infinite resistance between rod and furnace metal, ie no shorting of the insulator. I think he verified conductivity from end of wire to tip of rod, but not sure what exactly he measured there. So, I don't understand what could be wrong with the old one...... I'd guess the measurements he took aren't precise enough (or weren't actually measuring what thought he was is also a possibility of course). Being as it's a minute current, _any_ breakdown in the insulation and/or hermetic seal could lead to having enough leakage current to essentially short out the actual current but still measure a high (but not infinite) impedance. Hypothesis; we don't have enough info to be able to diagnose remotely exactly. The key is it doesn't work; a new one does. That's good enough for me... In a "former life" was responsible for incore self-powered neutron detectors for a particular commercial power reactor vendor. These are essentially a current source also in the 100-1000 nano-amp range and are a swaged leadwire on a Rh emitter surrounded by a ceramic in a metallic sheath. (Sound familiar?) Their OD is only about 1/16", the lead wire and ceramic are thus tiny. Turned out that even though one could measure a very high bulk resistance between the emitter and sheath that miniscule locations along the length of the detector could have very localized thin spots and become a shunt path for leakage currents. Also turned out that moisture could infiltrate the end seal and gradually diffuse down the length of the detector over time. This also reduced the overall resistance and showed up as a systematically lower output signal but of great variability as again the existence of the surface roughness and local thickness made exponential changes in local conductivity. The detectors had been tested for years at the corporate research reactor without ever discovering the issues--turned out it required the higher power density of the real thing for the issue to become significant. While they're not identical, given the similarity in construction and function I can imagine many such similar scenarios with these devices. Mostly I imagine it is a moisture infiltration problem with these as a first guess. In the end, the reactor detector problems turned out to be a secondary blessing; I got a MS thesis out of it while it kept me gainfully employed to pay for the course work while working around the issues for operating reactors w/o requiring warranty replacements and solving the manufacturing problems for new product. -- |
#227
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Oren wrote, on Wed, 31 Dec 2014 15:46:19 -0800:
My guess is the metal expands and opens a crack in the ceramic (not visible). I've read about this on a gas grill and stove igniters. Don't recall the details - sorry. I was hinting about it earlier in the thread. Would that be a short to ground? I just noticed this, so sorry for not responding sooner. I'm still amazed that the heat sensor was bad, simply because there was almost nothing to it. I guess if, under heat, a crack allows electrons to "jump" to ground, both ways, then the control board wouldn't measure any DC current (because it would be AC). I'm guessing though. |
#228
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Wed, 31 Dec 2014 17:52:16 -0800:
IDK what flame sensor you have there, but from the dimensions it looks like it's a foot or more long, 1/2" in diameter and certainly not for a typical home furnace. The one Danny has pics of does look like a small rod, mounted on an insulator, connected to a wire. The one I have is only a couple of inches long, and maybe something like 1/8 of an inch in diameter of the rod itself. |
#229
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Thu, 01 Jan 2015 06:41:52 -0800:
So, if that's right, then the question remains, what failed in Danny's detector? There have been so many posts, I'm unsure of is what exactly he measured, what the readings were, etc. I think he measured that there was infinite resistance between rod and furnace metal, ie no shorting of the insulator. I think he verified conductivity from end of wire to tip of rod, but not sure what exactly he measured there. So, I don't understand what could be wrong with the old one...... All this is true. I'm "guessing" that a crack developed in the ceramic that allowed electrons to flow both ways to the metal chassis that the assembly was bolted to. But that's just a guess. |
#230
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
UPDATE:
The heater has been working (although it has been almost 70 degrees lately) just fine with the new flame sensor. Apparently, this is what happened: 1. Heater wasn't working for so long that it "forgot" the prior error code, so it was just blinking incessantly. 2. Eventually, the heater got around to blinking a code for a bad flame sensor circuit. 3. The observation was the flames would light and then shut off within seconds, four times, and then lockout would occur until the power to the furnace was turned off and back on. 4. All measurements to determine whether the flame sensor was broken had failed, mainly because 5uA is hard to measure and because the meter I had borrowed must have a blown fuse. 5. However, replacing the flame sensor worked. How the flame sensor failed is a mystery, as it clearly was not tarnished (it was sanded with steel wool, emery cloth, and a file, over subsequent attempts). The ceramic "looked" intact, but may have developed a fault such as a crack. The assumption is that the flame sensor failed, although the only proof of that is that the new flame sensor worked as soon as it was installed. Thanks for all your help and advice. Who knew that the flames form part of an electrical circuit! |
#231
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
If you really want to verify a bad flame sensor, wait till spring,
and put the bad one back in, and see if the problem comes back. But wait till spring Mark |
#232
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
makolber wrote, on Fri, 09 Jan 2015 18:16:08 -0800:
But wait till spring |
#233
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
On Sat, 10 Jan 2015 00:11:04 +0000 (UTC), "Danny D."
wrote: 5. However, replacing the flame sensor worked. How the flame sensor failed is a mystery, as it clearly was not tarnished (it was sanded with steel wool, emery cloth, and a file, over subsequent attempts). The ceramic "looked" intact, but may have developed a fault such as a crack. The assumption is that the flame sensor failed, although the only proof of that is that the new flame sensor worked as soon as it was installed. Thanks for all your help and advice. Doesn't the flame sensor have a "special" metallic coating? Sanding it off will damage the sensor? Who knew that the flames form part of an electrical circuit! I think my HVAC furnace has a safety feature. When the flame goes out the gas shuts down the gas valve. Wonder if it via the sensor? |
#234
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Why is my immersion heater wired with 4mm cable?! | UK diy | |||
Bryant Plus 90 furnace (gas heater) error code 33 | Home Repair | |||
12v dc DVD player wired incorrectly ie. polarity reversed to a 12v dc battery pack | Home Repair | |||
POSSIBLY OFF TOPIC: Screwfix electric heater. | UK diy | |||
Central Heater: water constantly running | UK diy |