On Monday, December 22, 2014 10:36:41 AM UTC-5, Danny D. wrote:
Stormin Mormon wrote, on Mon, 22 Dec 2014 07:54:59 -0500: If you're safe with a VOM, here's the technique: I'm perfectly fine with 120/220V and can easily work with my Fluke 75 on the furnace. I just need to know what to check, bearing in mind that it's not at first obvious where the power comes in yet. I've never seen a furnace where it's not obvious where the power comes in. I'm beginning to agree with Stormin. You can get into the small box, and check for polarity and if the ground is connected. I can't imagine that the power polarity has reversed, on its own, but, as you note, I should check it (since the flashing is hard to understand and one interpretation of the flashes might be that the power polarity is reversed). Of course, that only matters for DC, right? No, you can reverse the hot and neutral on AC. But as I said before, it's virtually impossible for that to have happened and I doubt anything to do with the power to the furnace is the problem. So I'd need to know *where* the DC is coming from, since the line voltage is AC (yes, I know a neutral isn't the same as a hot, nor even the same as a ground, but, in terms of polarity, switching a neutral with a hot shouldn't matter for AC motors or step-down transformers (which I presume exist near the circuit board). I hesitate to suggest people open up safety boxes and work with live power, some folks can't do that safely. Prefer not to go into a lot of detail on an open forum. I have no problem whatsoever working around power. |
#42
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 11:12 AM, Danny D. wrote:
My Fluke 75 is a good meter, which I've had for something like 30 years. So, *using* a meter isn't at all a problem. The problem is knowing what measurements to take. To that end, this control board summary is a start: https://c4.staticflickr.com/8/7511/1...a7b9a83c_h.jpg As is this wiring control schematic: https://c1.staticflickr.com/9/8616/1...d2721b93_h.jpg And, of course, as is the overall furnace circuit schematic: https://c4.staticflickr.com/8/7560/1...e91c4626_b.jpg All of which I'm new to, but, which I will print and pore over to see what basic control and power inputs to test with my trusty DMM. Black is hot, white is neutral, and green is ground. You test at the little box I mentioned earlier. If it's the 31 code, I suspect you've got a bad limit switch, not enough air flow, and the limit switch finally gave out. I've seen two of those, this year so far. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#43
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 11:16 AM, Danny D. wrote:
trader_4 wrote, on Mon, 22 Dec 2014 06:51:01 -0800: Besides, I'd bet 99% that nothing is wrong with the power. I'll check that the white (neutral) has no voltage difference with green or bare (ground), and that the black (hot) has line voltage (120VAC) to both the neutral and ground, but, like you, I am 99.9% sure that can't possibly be the problem. The problem is "probably" described in this flow chart though... https://c4.staticflickr.com/8/7506/1...6bb628a5_c.jpg With that clogged air filter, I'd be thinking bad thermal limit switch. I replaced one this year in my own furnace, and one about a week later for a customer. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#44
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Mon, 22 Dec 2014 08:21:13 -0800:
I've never seen a furnace where it's not obvious where the power comes in. I'm beginning to agree with Stormin. OK. Fair enough. I haven't looked hard enough mainly because I really don't think the problem is a reversed polarity on the AC circuit. First off, the thing is AC, so, "most" AC items don't care whether the hot or neutral are reversed anyway; but more importantly, nothing was done to reverse the hot and neutral. Looking at my pictures, clearly the line voltage comes in right at the middle, from the overhanging flexible metal BX cable: https://c4.staticflickr.com/8/7516/1...72dc89861a.jpg So, I'll pop off the cover of the box on the inside of that connection - but - really - that will just tell me what I already know must be the case - which is that the AC "line voltage" isn't reversed. But, I'll check it - and report back - with pictures. |
#45
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 11:21 AM, trader_4 wrote:
bearing in mind that it's not at first obvious where the power comes in yet. I've never seen a furnace where it's not obvious where the power comes in. I'm beginning to agree with Stormin. CY: Hello! BX cable on top, to small box. Earth to Danny! Of course, that only matters for DC, right? No, you can reverse the hot and neutral on AC. But as I said before, it's virtually impossible for that to have happened and I doubt anything to do with the power to the furnace is the problem. CY: I've seen reversed polarity, and also open grounds. I hesitate to suggest people open up safety boxes and work with live power, some folks can't do that safely. Prefer not to go into a lot of detail on an open forum. I have no problem whatsoever working around power. CY: Well, in that case, the job is completed, and you can post about it. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#46
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Mon, 22 Dec 2014 08:21:13 -0800:
No, you can reverse the hot and neutral on AC. But as I said before, it's virtually impossible for that to have happened and I doubt anything to do with the power to the furnace is the problem. I agree that hot and neutral *can* be reversed, but, from a practical standpoint, other than the safety of two-wire grounded items, it makes no difference. So, when they're talking polarity reversal in the continuous-blink scenario, I wonder if they're talking about the DC voltage, where polarity can make a huge difference. I doubt either one was reversed, simply because nothing was touched, but, methinks they may be talking DC and not AC anyway. Nonetheless, I'll pop that box off in the middle of the furnace and measure the voltages (yes, I know what all the colors mean, including white, black, red, if it's there, and green or bare). I didn't check if it's 220V, but that just means there will be two hots and a neutral, instead of a hot and a neutral. |
#47
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Monday, December 22, 2014 11:34:27 AM UTC-5, Danny D. wrote:
trader_4 wrote, on Mon, 22 Dec 2014 08:21:13 -0800: No, you can reverse the hot and neutral on AC. But as I said before, it's virtually impossible for that to have happened and I doubt anything to do with the power to the furnace is the problem. I agree that hot and neutral *can* be reversed, but, from a practical standpoint, other than the safety of two-wire grounded items, it makes no difference. So, when they're talking polarity reversal in the continuous-blink scenario, I wonder if they're talking about the DC voltage, where polarity can make a huge difference. No, they are talking about polarity reversed at the incoming AC, ie hot and neutral. How would you ever get DC reversed on the circuit board? |
#48
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Monday, December 22, 2014 11:24:39 AM UTC-5, Stormin Mormon wrote:
On 12/22/2014 11:12 AM, Danny D. wrote: My Fluke 75 is a good meter, which I've had for something like 30 years. So, *using* a meter isn't at all a problem. The problem is knowing what measurements to take. To that end, this control board summary is a start: https://c4.staticflickr.com/8/7511/1...a7b9a83c_h.jpg As is this wiring control schematic: https://c1.staticflickr.com/9/8616/1...d2721b93_h.jpg And, of course, as is the overall furnace circuit schematic: https://c4.staticflickr.com/8/7560/1...e91c4626_b.jpg All of which I'm new to, but, which I will print and pore over to see what basic control and power inputs to test with my trusty DMM. Black is hot, white is neutral, and green is ground. You test at the little box I mentioned earlier. If it's the 31 code, I suspect you've got a bad limit switch, not enough air flow, and the limit switch finally gave out. I've seen two of those, this year so far. It's nothing to do with airflow. He says he gets the flashing from the LEDs indicating a fault as soon as power is applied, before there is even a call for heat. |
#49
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 11:29 AM, Danny D. wrote:
Looking at my pictures, clearly the line voltage comes in right at the middle, from the overhanging flexible metal BX cable: https://c4.staticflickr.com/8/7516/1...72dc89861a.jpg So, I'll pop off the cover of the box on the inside of that connection - but - really - that will just tell me what I already know must be the case - which is that the AC "line voltage" isn't reversed. But, I'll check it - and report back - with pictures. We'd expect nothing less from the professional you are. - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#50
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 11:39 AM, trader_4 wrote:
On Monday, December 22, 2014 11:24:39 AM UTC-5, Stormin Mormon wrote: If it's the 31 code, I suspect you've got a bad limit switch, not enough air flow, and the limit switch finally gave out. I've seen two of those, this year so far. It's nothing to do with airflow. He says he gets the flashing from the LEDs indicating a fault as soon as power is applied, before there is even a call for heat. On my own furnace, I did get a fault code when it powered up, and turned out to be a bad limit. So my personal experience is..... - .. Christopher A. Young Learn about Jesus www.lds.org .. |
#51
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 12:49:48 -0500:
But, I'll check it - and report back - with pictures. We'd expect nothing less from the professional you are. I gathered the testing equipment: https://c4.staticflickr.com/8/7541/1...ea2b8a1c_b.jpg I turned off the wall switch (it's turned on in this pic): https://c4.staticflickr.com/8/7498/1...481232cf_b.jpg I removed the cover of the inlex box from the BX cable: https://c4.staticflickr.com/8/7511/1...594e782c_b.jpg I separated the hot (black), neutral (white) & ground (green): https://c4.staticflickr.com/8/7573/1...1a9fd07a_b.jpg Turning power on, I tested neutral to ground at 0 volts AC: https://c4.staticflickr.com/8/7533/1...a061993a_b.jpg Turning power on, I tested hot to ground at nominally 120VAC. https://c1.staticflickr.com/9/8638/1...8709828b_b.jpg Turning power on, I tested hot to neutral at nominally 120VAC. https://c4.staticflickr.com/8/7490/1...7fb5ddc8_b.jpg I turned the power off, and reconnected the wires as before. If the power is reversed, it's not at the inlet BX cable connection to the unit. What I mostly want to find is the big red button that says "reset", but I don't see it. I see a bunch of smaller limit resets, all of which I've pressed already. |
#52
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 11:31:41 -0500:
CY: I've seen reversed polarity, and also open grounds. The grounds seem good, tested from green to the metal case. https://c1.staticflickr.com/9/8561/1...45432dbc_c.jpg |
#53
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
I agree that hot and neutral *can* be reversed, but, from a practical standpoint, other than the safety of two-wire grounded items, it makes no difference. I suggest you read my previous post that explains how the flame sensor circuit works. You can lead a horse to water...... Mark |
#54
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Mon, 22 Dec 2014 08:37:51 -0800:
No, they are talking about polarity reversed at the incoming AC, ie hot and neutral. How would you ever get DC reversed on the circuit board? The incoming power, at least at the BX cable coming into the furnace, is not reversed, but, clearly "something" is wrong, so I do appreciate the advice as to what to look for. A few things I did in the meantime, which "may" have changed the situation is that I opened up all the vents in the house, most of which had been closed for some reason (almost certainly since last winter), which means the vent airflow was certainly stifled. I opened all the suckers: https://c4.staticflickr.com/8/7563/1...ca4af62b_b.jpg And all the blowers: https://c4.staticflickr.com/8/7478/1...a422228b_b.jpg And, I ascertained that there is no V-shaped filter in the top (left) side of the furnace itself: https://c4.staticflickr.com/8/7491/1...8312f3fe_c.jpg This lack of v-shaped filters is apparently normal, as it is described on the furnace cover sticker, which says: "Horizontal furnace: Filters are located external of furnace. Consult installer for location." https://c4.staticflickr.com/8/7474/1...0f645731_c.jpg Interestingly, since most of the vents were closed, I might assume the furnace had shut off due to lack of air, but I can't find what the sticker also says is the "RESET" button: "Auxiliary limit control may be located on blower housing or top of furnace. To RESET, push button on control firmly. Refer to USERS MANUAL for more information. Call qualified serviceman if failure continues." Also, the sticker talks about a "fusible link", which I also haven't found yet: https://c1.staticflickr.com/9/8575/1...a6bf6b65_c.jpg "This furnace is equipped with a fusible element or manual reset limit switch in burnder compartment and/or draft diverter to protect against overheat conditions that can result from inadequate combustion air supply or blocked vent conditions." Just in case, I hit all the reset buttons I could find, starting with the two manual limit switches: https://c4.staticflickr.com/8/7496/1...acc7329a_c.jpg When I press the brown button on the manual limit switch, nothing happens (I had expected a spring-loaded type of interaction): https://c4.staticflickr.com/8/7490/1...550d1ee2_c.jpg I pressed the brown button on the blocked vent tube switch: https://c4.staticflickr.com/8/7580/1...19b8f191_c.jpg There were no buttons on the flame sensor and hot surface igniter, so, I merely wiggled the wires to ensure they were on snugly: https://c1.staticflickr.com/9/8651/1...7fe7ca9f_c.jpg I suspect this is the backside of the fusible link, which likewise, I wiggled the wires to ensure they were on tightly: https://c4.staticflickr.com/8/7498/1...4fb55b63_b.jpg I also flipped the on-off switch, on the gas valve itself, a few times: https://c1.staticflickr.com/9/8681/1...d011aced_c.jpg I also wiggled all the wires and connections on the control board: https://c1.staticflickr.com/9/8631/1...4bb7c59e_c.jpg I'll run another series of tests, and see if any of that made a difference. |
#55
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
makolber wrote, on Mon, 22 Dec 2014 10:24:18 -0800:
I suggest you read my previous post that explains how the flame sensor circuit works. You can lead a horse to water...... Mark Hi Mark, I had read your suggestion and followed it as much as possible. There is a flame sensor, and a hot igniter, which are located he https://c1.staticflickr.com/9/8651/1...7fe7ca9f_c.jpg I don't know yet how to physically 'test' them, but they do not appear to be damaged. There is absolutely no water, and the ground appears good but I need to run more tests on ground to be doubly sure. The good news is that, after wiggling everything and opening all the vents, and replacing the batteries, I called for heat just now: https://c4.staticflickr.com/8/7553/1...1d83ee2a_b.jpg First the first time all winter, the igniter lit after the blower motor ran for a minute or so! https://c4.staticflickr.com/8/7566/1...a8d7692c_c.jpg Then, for the first time, the flame and igniter went on: https://c4.staticflickr.com/8/7554/1...38cbbba7_c.jpg Then, just the flame went on, for about 10 seconds or so: https://c4.staticflickr.com/8/7550/1...b9901d66_c.jpg This happened three times, in quick succession, and then the furnace went back to the blinking. I will post the blinking video separately, as it seems to be blinking a different code now. |
#56
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
"Danny D." wrote in message ... makolber wrote, on Mon, 22 Dec 2014 10:24:18 -0800: I suggest you read my previous post that explains how the flame sensor circuit works. You can lead a horse to water...... Mark Hi Mark, I had read your suggestion and followed it as much as possible. There is a flame sensor, and a hot igniter, which are located he https://c1.staticflickr.com/9/8651/1...7fe7ca9f_c.jpg I don't know yet how to physically 'test' them, but they do not appear to be damaged. There is absolutely no water, and the ground appears good but I need to run more tests on ground to be doubly sure. The good news is that, after wiggling everything and opening all the vents, and replacing the batteries, I called for heat just now: https://c4.staticflickr.com/8/7553/1...1d83ee2a_b.jpg First the first time all winter, the igniter lit after the blower motor ran for a minute or so! https://c4.staticflickr.com/8/7566/1...a8d7692c_c.jpg Then, for the first time, the flame and igniter went on: https://c4.staticflickr.com/8/7554/1...38cbbba7_c.jpg Then, just the flame went on, for about 10 seconds or so: https://c4.staticflickr.com/8/7550/1...b9901d66_c.jpg This happened three times, in quick succession, and then the furnace went back to the blinking. I will post the blinking video separately, as it seems to be blinking a different code now. Now that all that went on, it might be time to check the air flow switch. It will be something after the blower mounted on the air chamber. It is a switch that will probably show open and when you have air flow it will close. If it does show open, and never closes when the blower starts up, you have low air flow. Either the blower is not turning or the switch could be bad. If it shows open, hook the two wires together and see if the furnace stays running. Or place your meter across the wires and see if they stay closed. You can probably go to ground from one of the contacts and one side will always have voltage and the other one will not. Get on the one without the voltage and see if it ever gets the voltage. --- This email has been checked for viruses by Avast antivirus software. http://www.avast.com |
#57
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 11:26:40 -0500:
With that clogged air filter, I'd be thinking bad thermal limit switch. I replaced one this year in my own furnace, and one about a week later for a customer. Partial success! After all the fiddling, I'm finally getting the thermal igniter to ignite, and the flames go on three times, and then shut off, so, that's a partial success, I guess. First, the LED was solid red for a minute or so: https://www.flickr.com/photos/98287134@N02/16082030575/ But then, it quickly switched to what appeared to be a code #12: https://www.flickr.com/photos/98287134@N02/16081998125/ Then, the flames went on three times and then off within seconds with a resulting LED blinking code of what appears to be #34: https://www.flickr.com/photos/98287134@N02/16081950225/ Given all those inconsistencies within the span of 15 minutes, I'm not sure if things are changing or if there are more than one problem or if the thing just needs to settle down, because those blink codes are changing depending on what is happening with the blower. https://c4.staticflickr.com/8/7505/1...4f42e6c5_c.jpg The gas valve is definitely turned on, and there is plenty of gas on the stove and in the 500 gallon propane tank. https://c4.staticflickr.com/8/7508/1...4311f464_k.jpg I will doublecheck that the metal case is grounded, and, I will sand or steel wool the flame sensor and check the amperage if my Fluke 75 can get down that low. 34: Ignition proving failu Control will try three more times before a lockout #14 occurs. If flame signal lost after trial for ignition period, blower will come on for 90-second recycle delay. Check for: - Oxide buildup on flame sensor (clean with fine sandpaper) - Proper flame sense microamps (0.5microamps DC minimum) - Gas valve turned off (manual shutoff valve, low inlet gas pressure) - Green wire MUST be connected to furnace sheet metal - Inadequate flame carryover or rough ignition 14: Ignition Lockout: Control will auto-reset after three hours. Refer to #34. 12: Blower on after power up: (115V or 24V) Blower runs for 90 seconds, if unit is powered up during a call for heat (R-W closed). https://c4.staticflickr.com/8/7545/1...d3f7f629_c.jpg |
#58
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Monday, December 22, 2014 2:39:04 PM UTC-5, Ralph Mowery wrote:
"Danny D." wrote in message ... makolber wrote, on Mon, 22 Dec 2014 10:24:18 -0800: I suggest you read my previous post that explains how the flame sensor circuit works. You can lead a horse to water...... Mark Hi Mark, I had read your suggestion and followed it as much as possible. There is a flame sensor, and a hot igniter, which are located he https://c1.staticflickr.com/9/8651/1...7fe7ca9f_c.jpg I don't know yet how to physically 'test' them, but they do not appear to be damaged. There is absolutely no water, and the ground appears good but I need to run more tests on ground to be doubly sure. The good news is that, after wiggling everything and opening all the vents, and replacing the batteries, I called for heat just now: https://c4.staticflickr.com/8/7553/1...1d83ee2a_b.jpg First the first time all winter, the igniter lit after the blower motor ran for a minute or so! https://c4.staticflickr.com/8/7566/1...a8d7692c_c.jpg Then, for the first time, the flame and igniter went on: https://c4.staticflickr.com/8/7554/1...38cbbba7_c.jpg Then, just the flame went on, for about 10 seconds or so: https://c4.staticflickr.com/8/7550/1...b9901d66_c.jpg This happened three times, in quick succession, and then the furnace went back to the blinking. I will post the blinking video separately, as it seems to be blinking a different code now. Now that all that went on, it might be time to check the air flow switch. It will be something after the blower mounted on the air chamber. It is a switch that will probably show open and when you have air flow it will close. If it does show open, and never closes when the blower starts up, you have low air flow. Either the blower is not turning or the switch could be bad. If it shows open, hook the two wires together and see if the furnace stays running. It's not an air handler blower issue. He gets the flashing trouble indication as soon as power is applied, without any call for heat, without the furnace firing, without the blower ever starting. |
#59
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LED blinks constantly)
"trader_4" wrote in message ... It's not an air handler blower issue. He gets the flashing trouble indication as soon as power is applied, without any call for heat, without the furnace firing, without the blower ever starting. He was getting that flashing , but he just said the heater tried to start after he did all the resetting and checking later on. The heater could have came on at the very start and failed. This could have tripped a safety device and he finally reset it, only to have it fault again on the restart attempt. --- This email has been checked for viruses by Avast antivirus software. http://www.avast.com |
#60
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Monday, December 22, 2014 4:55:35 PM UTC-5, Ralph Mowery wrote:
"trader_4" wrote in message ... It's not an air handler blower issue. He gets the flashing trouble indication as soon as power is applied, without any call for heat, without the furnace firing, without the blower ever starting. He was getting that flashing , but he just said the heater tried to start after he did all the resetting and checking later on. Again, "tried to start", is not an air handler blower problem. If the blower failed, there were clogged filters, etc, the furnace would fire up. run for several minutes, then shut off with a failure code. The heater could have came on at the very start and failed. This could have tripped a safety device and he finally reset it, only to have it fault again on the restart attempt. Two problems with that: 1 - It has continous blinking, ie abnormal LED as soon as power is restored. It's not firing and then reporting a problem. 2 - If it fired at the very start and failed, it's also not a blower problem. The blower typically comes on about 2 mins into the whole startup. For it to reach an over temp and shut down, would require a lot longer. --- This email has been checked for viruses by Avast antivirus software. http://www.avast.com |
#61
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed(red LED blinks constantly)
trader_4 wrote:
On Monday, December 22, 2014 4:55:35 PM UTC-5, Ralph Mowery wrote: "trader_4" wrote in message ... It's not an air handler blower issue. He gets the flashing trouble indication as soon as power is applied, without any call for heat, without the furnace firing, without the blower ever starting. He was getting that flashing , but he just said the heater tried to start after he did all the resetting and checking later on. Again, "tried to start", is not an air handler blower problem. If the blower failed, there were clogged filters, etc, the furnace would fire up. run for several minutes, then shut off with a failure code. The heater could have came on at the very start and failed. This could have tripped a safety device and he finally reset it, only to have it fault again on the restart attempt. Two problems with that: 1 - It has continous blinking, ie abnormal LED as soon as power is restored. It's not firing and then reporting a problem. 2 - If it fired at the very start and failed, it's also not a blower problem. The blower typically comes on about 2 mins into the whole startup. For it to reach an over temp and shut down, would require a lot longer. --- This email has been checked for viruses by Avast antivirus software. http://www.avast.com Hi, First, I'd just clean the flame sensor to get one thing out of the way. I never ran into failed sensor but dirty one which did not work well. Rubbing it with emery cloth always made it work again. |
#62
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Ralph Mowery wrote, on Mon, 22 Dec 2014 14:43:24 -0500:
Now that all that went on, it might be time to check the air flow switch. It will be something after the blower mounted on the air chamber. It is a switch that will probably show open and when you have air flow it will close. If it does show open, and never closes when the blower starts up, you have low air flow. Either the blower is not turning or the switch could be bad. If it shows open, hook the two wires together and see if the furnace stays running. Or place your meter across the wires and see if they stay closed. You can probably go to ground from one of the contacts and one side will always have voltage and the other one will not. Get on the one without the voltage and see if it ever gets the voltage. Do you think this might be the air-flow switch, bolted into the side of the air chamber? https://c4.staticflickr.com/8/7527/1...d908b870_b.jpg I tested it and it seems to be a short (which is probably what it is supposed to be). https://c4.staticflickr.com/8/7540/1...18ee847c_b.jpg It might be a temperature switch though... or a fusible link? https://c4.staticflickr.com/8/7498/1...4fb55b63_b.jpg |
#63
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Tony Hwang wrote, on Mon, 22 Dec 2014 15:58:34 -0700:
First, I'd just clean the flame sensor to get one thing out of the way. I never ran into failed sensor but dirty one which did not work well. Rubbing it with emery cloth always made it work again. The flame sensor is supposed to have 50 microamps, but I couldn't measure that low with my Fluke 75 DMM: https://c4.staticflickr.com/8/7463/1...2757e870_b.jpg So I removed the flame sensor to take a look at its condition: https://c4.staticflickr.com/8/7475/1...8647f174_b.jpg That flame sensor was in surprisingly good shape, as is everything: https://c4.staticflickr.com/8/7517/1...71745c49_b.jpg Even so, I steel wooled the small amount of oxide, just to be safe: https://c4.staticflickr.com/8/7539/1...d5cf70c5_b.jpg |
#64
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 1:10 PM, Danny D. wrote:
Stormin Mormon wrote, on Mon, 22 Dec 2014 12:49:48 -0500: But, I'll check it - and report back - with pictures. We'd expect nothing less from the professional you are. I gathered the testing equipment: https://c4.staticflickr.com/8/7541/1...ea2b8a1c_b.jpg I turned off the wall switch (it's turned on in this pic): https://c4.staticflickr.com/8/7498/1...481232cf_b.jpg I removed the cover of the inlex box from the BX cable: https://c4.staticflickr.com/8/7511/1...594e782c_b.jpg I separated the hot (black), neutral (white) & ground (green): https://c4.staticflickr.com/8/7573/1...1a9fd07a_b.jpg Turning power on, I tested neutral to ground at 0 volts AC: https://c4.staticflickr.com/8/7533/1...a061993a_b.jpg Turning power on, I tested hot to ground at nominally 120VAC. https://c1.staticflickr.com/9/8638/1...8709828b_b.jpg Turning power on, I tested hot to neutral at nominally 120VAC. https://c4.staticflickr.com/8/7490/1...7fb5ddc8_b.jpg I turned the power off, and reconnected the wires as before. If the power is reversed, it's not at the inlet BX cable connection to the unit. What I mostly want to find is the big red button that says "reset", but I don't see it. I see a bunch of smaller limit resets, all of which I've pressed already. Sounds properly polaraized. The big reset is usually to switch off the AC power for several seconds. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#65
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 11:24:38 -0500:
Black is hot, white is neutral, and green is ground. You test at the little box I mentioned earlier. I double checked all the grounds, and they're good. https://c1.staticflickr.com/9/8597/1...62d59465_z.jpg |
#66
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 1:51 PM, Danny D. wrote:
trader_4 wrote, on Mon, 22 Dec 2014 08:37:51 -0800: No, they are talking about polarity reversed at the incoming AC, ie hot and neutral. How would you ever get DC reversed on the circuit board? The incoming power, at least at the BX cable coming into the furnace, is not reversed, but, clearly "something" is wrong, so I do appreciate the advice as to what to look for. A few things I did in the meantime, which "may" have changed the situation is that I opened up all the vents in the house, most of which had been closed for some reason (almost certainly since last winter), which means the vent airflow was certainly stifled. I opened all the suckers: https://c4.staticflickr.com/8/7563/1...ca4af62b_b.jpg And all the blowers: https://c4.staticflickr.com/8/7478/1...a422228b_b.jpg And, I ascertained that there is no V-shaped filter in the top (left) side of the furnace itself: https://c4.staticflickr.com/8/7491/1...8312f3fe_c.jpg This lack of v-shaped filters is apparently normal, as it is described on the furnace cover sticker, which says: "Horizontal furnace: Filters are located external of furnace. Consult installer for location." https://c4.staticflickr.com/8/7474/1...0f645731_c.jpg Interestingly, since most of the vents were closed, I might assume the furnace had shut off due to lack of air, but I can't find what the sticker also says is the "RESET" button: "Auxiliary limit control may be located on blower housing or top of furnace. To RESET, push button on control firmly. Refer to USERS MANUAL for more information. Call qualified serviceman if failure continues." Also, the sticker talks about a "fusible link", which I also haven't found yet: https://c1.staticflickr.com/9/8575/1...a6bf6b65_c.jpg "This furnace is equipped with a fusible element or manual reset limit switch in burnder compartment and/or draft diverter to protect against overheat conditions that can result from inadequate combustion air supply or blocked vent conditions." Just in case, I hit all the reset buttons I could find, starting with the two manual limit switches: https://c4.staticflickr.com/8/7496/1...acc7329a_c.jpg When I press the brown button on the manual limit switch, nothing happens (I had expected a spring-loaded type of interaction): https://c4.staticflickr.com/8/7490/1...550d1ee2_c.jpg I pressed the brown button on the blocked vent tube switch: https://c4.staticflickr.com/8/7580/1...19b8f191_c.jpg There were no buttons on the flame sensor and hot surface igniter, so, I merely wiggled the wires to ensure they were on snugly: https://c1.staticflickr.com/9/8651/1...7fe7ca9f_c.jpg I suspect this is the backside of the fusible link, which likewise, I wiggled the wires to ensure they were on tightly: https://c4.staticflickr.com/8/7498/1...4fb55b63_b.jpg I also flipped the on-off switch, on the gas valve itself, a few times: https://c1.staticflickr.com/9/8681/1...d011aced_c.jpg I also wiggled all the wires and connections on the control board: https://c1.staticflickr.com/9/8631/1...4bb7c59e_c.jpg I'll run another series of tests, and see if any of that made a difference. Might have been someone, suggested low air flow, and a bad limit switch. Trader, was that you? -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#67
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 19:37:57 -0500:
Sounds properly polaraized. The big reset is usually to switch off the AC power for several seconds. While I have an AC on/off switch: https://c4.staticflickr.com/8/7498/1...481232cf_b.jpg I don't seem to have that big red button inside the blower compartment: https://c4.staticflickr.com/8/7491/1...8312f3fe_z.jpg Yet, the manual implies that there can be an "AUXILIARY LIMIT SWITCH (WHEN USED)"; but mine doesn't seem to have that switch. https://c4.staticflickr.com/8/7541/1...4c0debcd_z.jpg |
#68
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 2:43 PM, Ralph Mowery wrote:
Now that all that went on, it might be time to check the air flow switch. It will be something after the blower mounted on the air chamber. It is a switch that will probably show open and when you have air flow it will close. If it does show open, and never closes when the blower starts up, you have low air flow. Either the blower is not turning or the switch could be bad. If it shows open, hook the two wires together and see if the furnace stays running. Or place your meter across the wires and see if they stay closed. You can probably go to ground from one of the contacts and one side will always have voltage and the other one will not. Get on the one without the voltage and see if it ever gets the voltage. With a new filter, and open vents, should be much improved air flow. Lets see who spots the non sequitor. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#69
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On 12/22/2014 7:26 PM, Danny D. wrote:
Do you think this might be the air-flow switch, bolted into the side of the air chamber? https://c4.staticflickr.com/8/7527/1...d908b870_b.jpg I tested it and it seems to be a short (which is probably what it is supposed to be). https://c4.staticflickr.com/8/7540/1...18ee847c_b.jpg It might be a temperature switch though... or a fusible link? https://c4.staticflickr.com/8/7498/1...4fb55b63_b.jpg The thing with two rods, sleeves, and what looks like a coin cell, is a thermal cutout. It "should" be self resetting. Continuity is good. Does not measure air flow. -- .. Christopher A. Young Learn about Jesus www.lds.org .. |
#70
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 20:16:27 -0500:
The thing with two rods, sleeves, and what looks like a coin cell, is a thermal cutout. It "should" be self resetting. Continuity is good. Does not measure air flow. Seems reasonable. I don't know what measures air flow. This is a "pressure sensor", with a black tube connected to the air chamber; but I don't know how to test it yet: https://c4.staticflickr.com/8/7516/1...46b2ae86_c.jpg |
#71
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 19:39:38 -0500:
Might have been someone, suggested low air flow, and a bad limit switch. Trader, was that you? Seems reasonable. My hypothesis, at the moment, is that all the vents where shut which (maybe) caused a "limit switch" to open up? If only I could turn that limit switch back on. I wish I could find a "master reset" which doesn't seem to exist. I've pressed all the limit switch buttons I could find already. Here's the latest video after cleaning the flame sensor and hooking up the DMM in DC amps mode at the 300ma range with the flame sensor hooked in series with the DMM: https://www.flickr.com/photos/98287134@N02/15464227533/ As before, the blower started up & then the induced draft motor spun up, & then the igniter lit up orange, & then there were flames which soon shut down. The flames happened three times, all the while the LED blinked #34. When the flames died the third time, the furnace shut down & the LED blinked #14. https://c4.staticflickr.com/8/7521/1...32e0de5a_z.jpg 34 IGNITION PROVING FAILURE - Control will try three more times before a lockout #14 occurs. If flame signal lost after trial for ignition period, blower will come on for 90 second recycle delay. Check for: - Oxide buildup on flame sensor (clean with fine sandpaper). - Proper flame sense microamps (.5 microamps D.C. minimum). - Gas valve turned off. - Manual shut-off valve. - Low inlet gas pressure. - Green wire MUST be connected to furnace sheet metal. - Inadequate flame carryover or rough ignition. 14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34. |
#72
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Stormin Mormon wrote, on Mon, 22 Dec 2014 20:11:18 -0500:
With a new filter, and open vents, should be much improved air flow. Lets see who spots the non sequitor. I'm not sure I understand ... non sequitor === an inference that does not follow from the premises; specifically : a fallacy resulting from a simple conversion of a universal affirmative proposition or from the transposition of a condition and its consequent. - a statement (as a response) that does not follow logically from or is not clearly related to anything previously said. Anyway, I did *try* to run the "component test" as described he https://c4.staticflickr.com/8/7521/1...32e0de5a_c.jpg COMPONENT TEST To initiate the component test sequence,shut OFF the room thermostat or disconnect the "R" thermostat lead. Briefly short the TEST terminal to the Com 24V terminal. Status LED will flash code and then turn ON the inducer motor. The inducer motor will run for the entire component test. The hot surface ignitor, blower motor-heat speed, and blower motor-cool speed will be turned ON for 10-15 seconds each". I first removed the RED wire from the (R) terminal block screw, but when I held down the door switch and then at the same time I touched the COM terminal to the TEST terminal, nothing happened: https://c4.staticflickr.com/8/7554/1...08719d7e_b.jpg So, I belatedly realized they must be talking about removing the RED (R) terminal at the thermostat itself, so, put back the Red wire onto the (R) terminal at the furnace, and then went down to the thermostat and removed the two red wires from that thermostat. Then, back up at the furnace, I added this orange wire to the COM terminal so that I could hold down the door switch and then touch the orange wire momentarily to the TEST blade on the control board: https://c4.staticflickr.com/8/7560/1...b61ec375_c.jpg I'm not exactly sure what happened in this component test, but, a bunch of things went on, and that was it. For example, the inducer motor ran, and the igniter lit for a few seconds, but, I didn't see anything else happen that told me any data. Maybe I missed something in the so-called "component" test? |
#73
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Danny D. wrote, on Fri, 19 Dec 2014 23:56:58 +0000:
Debugging suggestions are requested, and very helpful. Thanks! Here's where the Bryant 373LAV horizontal furnace stands tonight. Blower starts, inducer motor starts, igniter starts, flame starts, flame shuts down. Three times the igniter ignites the flame but three times, the flame shuts down within seconds. All the while it displays code #34. At the end of the sequence, it shuts down and displays code #14. Video: https://www.flickr.com/photos/98287134@N02/15464227533/ Schematic: https://www.flickr.com/photos/98287134@N02/15460746143/ Codes: https://www.flickr.com/photos/98287134@N02/16083106532/ 34 IGNITION PROVING FAILURE - Control will try three more times before a lockout #14 occurs. If flame signal lost after trial for ignition period, blower will come on for 90 second recycle delay. Check for: - Oxide buildup on flame sensor (clean with fine sandpaper). - Proper flame sense microamps (.5 microamps D.C. minimum). - Gas valve turned off. - Manual shut-off valve. - Low inlet gas pressure. - Green wire MUST be connected to furnace sheet metal. - Inadequate flame carryover or rough ignition. 14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34. |
#74
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Monday, December 22, 2014 8:52:22 PM UTC-5, Danny D. wrote:
Danny D. wrote, on Fri, 19 Dec 2014 23:56:58 +0000: Debugging suggestions are requested, and very helpful. Thanks! Here's where the Bryant 373LAV horizontal furnace stands tonight. Blower starts, inducer motor starts, igniter starts, flame starts, flame shuts down. Three times the igniter ignites the flame but three times, the flame shuts down within seconds. All the while it displays code #34. At the end of the sequence, it shuts down and displays code #14. Video: https://www.flickr.com/photos/98287134@N02/15464227533/ Schematic: https://www.flickr.com/photos/98287134@N02/15460746143/ Codes: https://www.flickr.com/photos/98287134@N02/16083106532/ 34 IGNITION PROVING FAILURE - Control will try three more times before a lockout #14 occurs. If flame signal lost after trial for ignition period, blower will come on for 90 second recycle delay. Check for: - Oxide buildup on flame sensor (clean with fine sandpaper). - Proper flame sense microamps (.5 microamps D.C. minimum). - Gas valve turned off. - Manual shut-off valve. - Low inlet gas pressure. - Green wire MUST be connected to furnace sheet metal. - Inadequate flame carryover or rough ignition. 14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34. Ok, so now the question that might shed some light on what's going on is, what changed that allowed the furnace to get this far? Previously, it would come up with a flashing LED trouble indication as soon as power was put on, without firing at all. Now, it's firing, then shutting down because it thinks it hasn't lit. I think that may be relevant, because initially you had continous LED flashes that the chart says corresponds to reversed polarity. While the polarity isn't reveresed, I wonder if it will also give that code if the ground is missing? I ask that because the flame sensor is single wire and depends on a ground path back to the controller board. Is it possible there is a bad ground connection between the controller board and the furnace metal? Other than that, the most obvious and direct possibility is that the flame sensor is bad. If you'd had this code, this behavior from the beginning, that would be the logical place to start. But what's odd is how it behaved very differently initially, unless that was something to do with you having the safety switch open, how you were starting it, etc. |
#75
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
trader_4 wrote, on Tue, 23 Dec 2014 04:44:15 -0800:
Ok, so now the question that might shed some light on what's going on is, what changed that allowed the furnace to get this far? Previously, it would come up with a flashing LED trouble indication as soon as power was put on, without firing at all. Now, it's firing, then shutting down because it thinks it hasn't lit. I agree with you. The manual says: "NOTE: If the polarity is not correct, the STATUS LED on the control center will flash rapidly and prevent the furnace from heating. The control system also requires an earth ground for proper operation of the control and flame sensing." So, *both* the old and new LED indications point to a suspected lack of "earth" ground (among other things). Plus, the constant flashing stopped just about when I started testing the power connections (although, I didn't *change* anything). I wiggled everything. But I left the wiring as it was before. Yet, suddenly, it stopped flashing constantly, and, instead, the error migrated from a power problem to short cycling (which now implicates either the flame sensor or the flame sensor control circuit). Yet, the flame sensor has only one wire, so, ground is clearly the case. I think that may be relevant, because initially you had continous LED flashes that the chart says corresponds to reversed polarity. While the polarity isn't reveresed, I wonder if it will also give that code if the ground is missing? I ask that because the flame sensor is single wire and depends on a ground path back to the controller board. Is it possible there is a bad ground connection between the controller board and the furnace metal? I'm thinking the same thing. A bad ground could cause the flame proving electrode not to have its requisite 5 microamps to 6 microamps. In the schematic, there are two "Note #5" comments, each next to the "GV" which is the gas valve Note #5 says: "5. This wire must be connected to furnace sheetmetal for control to detect flame." https://www.flickr.com/photos/98287134@N02/15460746143/ I'll need to check that, remove it, sand it, clean it, & re-test. I suspect ground is critical for the flame-sensing circuit, because the DC current is only 5 or 6 microamperes, which is so low, I'm going to have to figure out *how* to test it using coils of wire wrapped around an ammeter. Other than that, the most obvious and direct possibility is that the flame sensor is bad. If you'd had this code, this behavior from the beginning, that would be the logical place to start. But what's odd is how it behaved very differently initially, unless that was something to do with you having the safety switch open, how you were starting it, etc. Looking at the troubleshooting flow chart, it does now imply that either the flame proving electrode is bad, or that the control to that flame sensor is bad. https://www.flickr.com/photos/98287134@N02/15894320489/ I agree with you: 1. Today I will clean all the grounds. 2. I will check that "Note #5" wire listed in the schematic. 3. I will re-clean the flame sensing electrode (just in case). 4. I will figure out how to measure 5 or 6 microamperes (and it can be as low as half a microampere). |
#76
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Danny D. wrote, on Tue, 23 Dec 2014 13:21:56 +0000:
So, *both* the old and new LED indications point to a suspected lack of "earth" ground (among other things). Found a service manual online, by the way: http://manualslib.com/manual/22390/B...es-373lav.html |
#77
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Danny D. wrote, on Tue, 23 Dec 2014 14:36:38 +0000:
Found a service manual online, by the way: http://manualslib.com/manual/22390/B...es-373lav.html Here's a better link to the service manual so you can see the schematic and troubleshooting flowchart: http://dms.hvacpartners.com/docs/100...00/SP04-62.pdf |
#78
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
On Tuesday, December 23, 2014 9:37:04 AM UTC-5, Danny D. wrote:
Danny D. wrote, on Tue, 23 Dec 2014 13:21:56 +0000: So, *both* the old and new LED indications point to a suspected lack of "earth" ground (among other things). If the ground is affecting the flame sensor, then it't the ground path from the metal cabinet/frame of the furnace to the control board. That's where I'd be looking. There must be a ground wire that goes from the control board to the frame and the frame is also grounded to the incoming AC. |
#79
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
it is difficult to measure the 5 uA using a VOM.
I think you are on the right track. Check all the grounds This means the controller ground to the AC supply and ALSO the furnace chassis ground to the AC supply. Check that the flame sensor insulator is clean so that there is no partial short to ground of the flame sensor output whick is a very small DC voltage or current realtive to funrace chassis ground. Check that the flame sensor probe is not very dirty but I don't see how that would casue the original symptom, but culd casue the symptoms you have now. Check that the flame sensor probe does not touch metal but is properly touching the flame. The flame sensor probe acts as a tiny battery and the controller needs to sense that current. THe flame sensor current is relative to the furnce ground which needs to be connectd to the AC ground and to the controller ground.. I guess also make sure the burner jets are also grounded to the chassis. The flame is grounded to the burner jets actually. Mark |
#80
Posted to alt.home.repair
|
|||
|
|||
Bryant propane heater can't possibly be wired reversed (red LEDblinks constantly)
Looking up videos on troubleshooting a Bryant 373LAV flame sensor,
these guys clean it with a brand new five-dollar bill: https://www.youtube.com/watch?featur...qL4lnk#t=13 0 This looks like a similar furnace to mine, with a similar issue, and this guy does not recommend cleaning the flame sensor: https://www.youtube.com/watch?featur...KsZhc0#t=36 6 After replacing the flame sensor, he shows the whole cycle: https://www.youtube.com/watch?featur...KsZhc0#t=95 0 These guys use #0000 fine steel wool to clean the flame sensor: https://www.youtube.com/watch?featur...gBB_R4#t=34 4 https://www.youtube.com/watch?featur...qlGfZv8Es#t=59 All say not to touch the sensor with fingers, which I didn't know when I first had cleaned it. But, interestingly, *all* (of those) simply clean or replace the flame sensor without *any* of them testing it for the 5 or 6 uamps of control current. (I'll google separately for videos *testing* the flame sensor circuit but this is already long.) Normally, I test things before replacing them, but, none of the technicians in the youtube videos I've found bothered to test it before replacing it. Even so, I might buy a spare flame sensor and igniter, and keep it next to the furnace. Any suggestions as to good suppliers? |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Why is my immersion heater wired with 4mm cable?! | UK diy | |||
Bryant Plus 90 furnace (gas heater) error code 33 | Home Repair | |||
12v dc DVD player wired incorrectly ie. polarity reversed to a 12v dc battery pack | Home Repair | |||
POSSIBLY OFF TOPIC: Screwfix electric heater. | UK diy | |||
Central Heater: water constantly running | UK diy |