#1
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
Here is a picture of the incoming wires to my main circuit breaker:
http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires *back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? If we follow those three wires *forward* to the first circuit breaker, what do they look like (in terms of connection to the literal earth of the ground)? Note: This question is an offshoot of a 220v dryer question; but this question is asked to get to the root of *what* it is that is entering the house in the first place. |
#2
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
Danny D'Amico wrote:
Here is a picture of the incoming wires to my main circuit breaker: http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires *back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? If we follow those three wires *forward* to the first circuit breaker, what do they look like (in terms of connection to the literal earth of the ground)? Note: This question is an offshoot of a 220v dryer question; but this question is asked to get to the root of *what* it is that is entering the house in the first place. Hmmm, Your question has been answered more than once throughout this thread. If still did not get it. You really ought to follow the wires upto the main breaker panel. One note: Gnd and Neutral is connected together but they are not same in functionality in the circuit. |
#3
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 01:42:15 +0000 (UTC), Danny D'Amico
wrote: Here is a picture of the incoming wires to my main circuit breaker: http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires *back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? ?? They're wires. It looks the same. If we follow those three wires *forward* to the first circuit breaker, what do they look like (in terms of connection to the literal earth of the ground)? It's wires. It looks the same. Note: This question is an offshoot of a 220v dryer question; but this question is asked to get to the root of *what* it is that is entering the house in the first place. The same as it does at the transformer and the dryer. |
#4
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
Danny D'Amico wrote:
Here is a picture of the incoming wires to my main circuit breaker: http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires *back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? If we follow those three wires *forward* to the first circuit breaker, what do they look like (in terms of connection to the literal earth of the ground)? Note: This question is an offshoot of a 220v dryer question; but this question is asked to get to the root of *what* it is that is entering the house in the first place. Hi, How is your house electric system grounded? I still think your dryer is not grounded well. Measure between the dryer chassis(body) and ground point in Ohm scale on your meter. Do you read zero Ohm or fraction of Ohm? Also you should read zero Ohm between gnd(dryer body) and neutral on your dryer. If it is all OK, some one else mentioned heating element sagging when hot rubbing on the dryer chassis not enough to kick the breaker but give spark and shock specially when hand is moist(doing washing) I think this thread is coming to an end. |
#5
|
|||
|
|||
This web page won't put up my posts if they're more than about 10 or 15 lines long.
Danny: In the following e-mail address, each letter has been replaced with the letter or symbol to the right of it on a standard Qwerty keyboard. If you can e-mail me, I'll send you a write-up that answers your question on what goes on both upstream and downstream of your electrical panel. m l r ; r n s u # o ; p d / m r y Leave out the spaces and type the letters to the left of the ones shown above to get my correct e-mail address. I put spaces in because if you type the letters r and n without a space between them, it looks like an m, and for this to work, the e-mail address you type has to be exactly correct. So far as an electrical spark inside the dryer goes, I would look for any wires inside the dryer that are rubbing against the rotating dryer drum. In time, the drum will rub it's way through the insulation, and contact the copper conductor. Then, depending on WHICH wire is rubbing against the drum, you can get a shock from the dryer by touching the drum while it's running, or only when the heating element is heating, or only during the Permanent Press cool down cycle, or whatever. I'd at least make sure that no wires are touching the rotating drum. Last edited by nestork : November 18th 13 at 07:30 AM |
#6
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On 11/17/2013 08:42 PM, Danny D'Amico wrote:
Here is a picture of the incoming wires to my main circuit breaker: http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires*back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? 180 out of phase aka 2-phase or split-phase. |
#7
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Sunday, November 17, 2013 8:42:15 PM UTC-5, Danny D'Amico wrote:
Here is a picture of the incoming wires to my main circuit breaker: http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires *back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? If we follow those three wires *forward* to the first circuit breaker, what do they look like (in terms of connection to the literal earth of the ground)? Note: This question is an offshoot of a 220v dryer question; but this question is asked to get to the root of *what* it is that is entering the house in the first place. All of the above has been explained to you in the other thread you started. |
#8
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Sunday, November 17, 2013 8:42:15 PM UTC-5, Danny D'Amico wrote:
Here is a picture of the incoming wires to my main circuit breaker: http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires *back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? If we follow those three wires *forward* to the first circuit breaker, what do they look like (in terms of connection to the literal earth of the ground)? Note: This question is an offshoot of a 220v dryer question; but this question is asked to get to the root of *what* it is that is entering the house in the first place. I may have worked for your dad in Miami before George Bush and the CIA kidnapped me and broke my back. Violently overthrow the US government |
#9
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 2:22:35 AM UTC-5, nestork wrote:
This web page won't put up my posts if they're more than about 10 or 15 lines long. Danny: In the following e-mail address, each letter has been replaced with the letter or symbol to the right of it on a standard Qwerty keyboard. If you can e-mail me, I'll send you a write-up that answers your question on what goes on both upstream and downstream of your electrical panel. m l r ; r n s u # o ; p d / m r y Leave out the spaces and type the letters to the left of the ones shown above to get my correct e-mail address. I put spaces in because if you type the letters r and n without a space between them, it looks like an m, and for this to work, the e-mail address you type has to be exactly correct. Good grief. What's next, NSA level encryption? |
#10
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
I hate to display ignorance, and I know I should know this.
But maybe somebody can explain. The power lines are 3 phase, meaning they're 120 degrees out of phase to each other allowing 3 wires to carry what 6 wires should (since they're generated by 3 sets of coils at the power plant). The house is fed by just one of these wires, through a center tap transformer. That transformer sends 3 wires to the house: Neutral, +120 volts, -120 volts. Connect the two hots and you get 240, connect either hot to the neutral and you get 120. Your safety ground is bonded to the neutral and so you should also have 120 from any hot wire to the ground. Neutral is the center tap. Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. |
#11
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 9:39:55 AM UTC-5, TimR wrote:
I hate to display ignorance, and I know I should know this. But maybe somebody can explain. The power lines are 3 phase, meaning they're 120 degrees out of phase to each other allowing 3 wires to carry what 6 wires should (since they're generated by 3 sets of coils at the power plant). The 6 vs three makes no sense. The house is fed by just one of these wires, through a center tap transformer. That transformer sends 3 wires to the house: Neutral, +120 volts, -120 volts. Connect the two hots and you get 240, connect either hot to the neutral and you get 120. Your safety ground is bonded to the neutral and so you should also have 120 from any hot wire to the ground. Neutral is the center tap. Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. All the neutrals are tied to ground. Why would you expect the neutral on the secondary to not be at ground level? In the strictist sense, if you take a center tap transformer, the secondary side doesn't have to have any relationship to the potential on the primary side. It's can be completely seperate, it's a seperate winding not connected to the primary. What and how you hook it up determines what level anything is referenced to. In the power transformer case, the center tap (neutral) is tied to ground. |
#12
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 9:48:27 AM UTC-5, wrote:
Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. All the neutrals are tied to ground. Why would you expect the neutral on the secondary to not be at ground level? In the strictist sense, if you take a center tap transformer, the secondary side doesn't have to have any relationship to the potential on the primary side. It's can be completely seperate, it's a seperate winding not connected to the primary. What and how you hook it up determines what level anything is referenced to. In the power transformer case, the center tap (neutral) is tied to ground. Well, you're not seeing the problem. I wish I could draw here. Your transformer has two wires going in, and three going out. I don't know what primary is in my neighbor hood, let's say 2400 vac for an example. Which two wires do we use? You only have the choice of leg to leg, or leg to neutral. Choose leg to neutral: use a 10 to 1 turns ratio, your secondary will be 240 volts line to line. Then center tap it, and you get 120 from each line to center. BUT: why would center tap be anywhere near neutral? Choose leg to leg: does the same problem exist? Once it gets into the house I understand how it works, but on the pole I'm hazy. By the way you are dead wrong on the 6 wires thing. That part I do remember. |
#13
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On 11/18/2013 9:08 AM, TimR wrote:
On Monday, November 18, 2013 9:48:27 AM UTC-5, wrote: Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. All the neutrals are tied to ground. Why would you expect the neutral on the secondary to not be at ground level? In the strictist sense, if you take a center tap transformer, the secondary side doesn't have to have any relationship to the potential on the primary side. It's can be completely seperate, it's a seperate winding not connected to the primary. What and how you hook it up determines what level anything is referenced to. In the power transformer case, the center tap (neutral) is tied to ground. Well, you're not seeing the problem. I wish I could draw here. Your transformer has two wires going in, and three going out. I don't know what primary is in my neighbor hood, let's say 2400 vac for an example. Which two wires do we use? You only have the choice of leg to leg, or leg to neutral. Choose leg to neutral: use a 10 to 1 turns ratio, your secondary will be 240 volts line to line. Then center tap it, and you get 120 from each line to center. BUT: why would center tap be anywhere near neutral? The secondary centertap is the "neutral" because it carries the imballance of the current in the secondary hot wires - the ends of the 240V winding. That is a common definition of a "neutral". The secondary has no relationship to the primary, it is isolated from the primary. The secondary relationship to earth depends on how the secondary is connected. The "neutral" (centertap) is earthed at the transformer. The neutral is then also earthed at the building. That limits the maximum voltage in the building with respect to the earth. Choose leg to leg: does the same problem exist? Once it gets into the house I understand how it works, but on the pole I'm hazy. By the way you are dead wrong on the 6 wires thing. That part I do remember. |
#14
|
|||
|
|||
|
#15
|
|||
|
|||
On the wiring diagram of a telephone pole transformer on that web site:
The "black" and "red" (or L1 and L2) power supply cables that come into your house each carrying 120 VAC are connected to the low voltage side of the transformer. The white neutral wire coming into your house is connected to the center tap of the transformer. The transformer converts 7200 VAC single phase power into 240 VAC single phase power, but the center tap is near zero voltage all the time and so you end up with "pseudo two phase 120 VAC" power. That is, single phase 240 VAC power that's been broken into two pieces, each 120 VAC, and each 180 degrees out of phase with the other. Last edited by nestork : November 18th 13 at 05:15 PM |
#16
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
Danny D'Amico writes:
Here is a picture of the incoming wires to my main circuit breaker: http://farm3.staticflickr.com/2886/1...21cf1404_o.gif If we follow those three wires *back* to the nearest transformer, what do they look like (in terms of phase relationship to each other)? Typical US residential distribution (many details omitted for simplification). +------+ | |---------------- L1 (Line 1) L1 ----| Pole | 120VAC 14KVAC | Pig |--------| 240VAC L2 ----| | 120V | N ----| |---------------- L2 (Line 2) +------+ | | |------- N (Ground_ED_ conductor) | gnd Anywhere from 11,000 to 30,000 VAC, single-phase + transmission neutral, enters the transformer which has a primary winding and a secondary winding used to drop the distribution voltage to the service voltage. The secondary winding is 'center-tapped' and connected to GND. L1 and L2 are connected to the main breaker in your service entrance panel. The N conductor from the pole pig is connected to the grounded (neutral) bus-bar in the service entrance. The grounding bus-bar in your service entrance is connected to a service ground associated with the premises and that bus-bar is bonded to the grounded bus-bar in your service entrance (and _only_ in your service entrance, not downstream subpanels). Note that the primary side of the pole pig is single phase for most residential applications. The secondary side splits that single phase. |
#17
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 10:08:23 AM UTC-5, TimR wrote:
On Monday, November 18, 2013 9:48:27 AM UTC-5, wrote: Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. All the neutrals are tied to ground. Why would you expect the neutral on the secondary to not be at ground level? In the strictist sense, if you take a center tap transformer, the secondary side doesn't have to have any relationship to the potential on the primary side. It's can be completely seperate, it's a seperate winding not connected to the primary. What and how you hook it up determines what level anything is referenced to. In the power transformer case, the center tap (neutral) is tied to ground. Well, you're not seeing the problem. I wish I could draw here. Your transformer has two wires going in, and three going out. I don't know what primary is in my neighbor hood, let's say 2400 vac for an example. Which two wires do we use? You only have the choice of leg to leg, or leg to neutral. It's one of the 3 primary phases to primary neutral. Choose leg to neutral: use a 10 to 1 turns ratio, your secondary will be 240 volts line to line. Then center tap it, and you get 120 from each line to center. BUT: why would center tap be anywhere near neutral? The center tap has no relation in terms of potential difference to anything other than the two ends of the secondary, until you connect it to something. The center is called the neutral and as part of the installation, it's run to the house and also tied to ground. Now the neutral of the transformer is at the same potential as ground. Choose leg to leg: does the same problem exist? Once it gets into the house I understand how it works, but on the pole I'm hazy. By the way you are dead wrong on the 6 wires thing. That part I do remember. You would go from 6 wires to 3 wires in a distributions system if and only if you were to consider the 6 wire system as the only other alternative to deliver power. That is that you have fixed in stone that you're to have a generator with 3 windings, delivering 3 phases via 6 wires to the load. Of course if you start with that, then a balanced 3 phase load reduces the wires in half. But that isn't the real world. No one would do it that way to begin with. There are other alternatives and even a single phase system can deliver the same power without 2X the wires. 3 phase does use less copper and is better for other reasons as well. But it's not a miracle. The current carrying capability of the conductors is what it is and 3 wires can't suddenly carry the same current as 6. As i recall, the reduction in copper you get with 3 phase is around 25%. |
#18
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
See if this diagram helps to understand:
http://www.samlexamerica.com/support...Circuit s.pdf --- This email is free from viruses and malware because avast! Antivirus protection is active. http://www.avast.com |
#19
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 12:57:11 PM UTC-5, SRN wrote:
See if this diagram helps to understand: http://www.samlexamerica.com/support...Circuit s.pdf Good diagram. So primary is leg to ground, and secondary center tap is forced to ground. Makes sense. Is primary ever leg to leg in residential? |
#20
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 06:39:55 -0800 (PST), TimR
wrote: I hate to display ignorance, and I know I should know this. But maybe somebody can explain. The power lines are 3 phase, meaning they're 120 degrees out of phase to each other Yes. allowing 3 wires to carry what 6 wires should (since they're generated by 3 sets of coils at the power plant). Kinda sorta. The house is fed by just one of these wires, through a center tap transformer. Yes. That transformer sends 3 wires to the house: Neutral, +120 volts, -120 volts. Well... There are two AC wires that are opposite, yes. If you said they were +120wt and -120wt, you would have a point (w being the angular frequency, or 2*Pi*f and t=time). Connect the two hots and you get 240, connect either hot to the neutral and you get 120. Yes. Your safety ground is bonded to the neutral and so you should also have 120 from any hot wire to the ground. Assuming no faults and ideal wires, sure. Neutral is the center tap. Yes. ...which is grounded. Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, Yes. Almost always, though it really doesn't matter. then the center tap should be above neutral on the secondary (house) side, right? No. The center tap is grounded at both the transformer and the entrance panel. It *is* ground. Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. It is. I don't see your problem. You described things pretty well. |
#21
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 07:08:23 -0800 (PST), TimR
wrote: On Monday, November 18, 2013 9:48:27 AM UTC-5, wrote: Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. All the neutrals are tied to ground. Why would you expect the neutral on the secondary to not be at ground level? In the strictist sense, if you take a center tap transformer, the secondary side doesn't have to have any relationship to the potential on the primary side. It's can be completely seperate, it's a seperate winding not connected to the primary. What and how you hook it up determines what level anything is referenced to. In the power transformer case, the center tap (neutral) is tied to ground. Well, you're not seeing the problem. I wish I could draw here. Your transformer has two wires going in, and three going out. I don't know what primary is in my neighbor hood, let's say 2400 vac for an example. Which two wires do we use? You only have the choice of leg to leg, or leg to neutral. Choose leg to neutral: use a 10 to 1 turns ratio, your secondary will be 240 volts line to line. Then center tap it, and you get 120 from each line to center. Pick one. It doesn't matter. BUT: why would center tap be anywhere near neutral? Because that's how it's wired. You *DEFINED* it as being 0V and connected it to ground. Choose leg to leg: does the same problem exist? No. There is no problem. Remember that transformers isolate. The secondary can be at any voltage you desire it to be, regardless of the primary (within the breakdown limits of the transformer, obviously). You connected one of it's secondary terminals to ground, defining that as 0V. Everything else falls out from there. You could have connected it to 1000V, but that wouldn't be smart. ;-) Once it gets into the house I understand how it works, but on the pole I'm hazy. There isn't any difference how it's connected there. You may have heard of "Delta" or "Wye" connections. Delta, connects the primary of the transformer between phases. A "Wye" connection would be from phase to ground. In the US, almost all loads are connected as "Wyes" and generators as "Deltas". I'm sure there are exceptions but that's what you'll find on your pole. By the way you are dead wrong on the 6 wires thing. That part I do remember. Trader is dead wrong about a lot. |
#22
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 1:54:55 PM UTC-5, wrote:
On Mon, 18 Nov 2013 06:39:55 -0800 (PST), TimR wrote: I hate to display ignorance, and I know I should know this. But maybe somebody can explain. The power lines are 3 phase, meaning they're 120 degrees out of phase to each other Yes. allowing 3 wires to carry what 6 wires should (since they're generated by 3 sets of coils at the power plant). Kinda sorta. The house is fed by just one of these wires, through a center tap transformer. Yes. That transformer sends 3 wires to the house: Neutral, +120 volts, -120 volts. Well... There are two AC wires that are opposite, yes. If you said they were +120wt and -120wt, you would have a point (w being the angular frequency, or 2*Pi*f and t=time). And if you said they were 180 different in phase from each other, relative to the neutral, you would also be correct. KRW only understands opposites, not phase. Connect the two hots and you get 240, connect either hot to the neutral and you get 120. Yes. Yes because the two hots are 180 deg out of phase with each other. If they weren't you wouldn't get 240V Your safety ground is bonded to the neutral and so you should also have 120 from any hot wire to the ground. Assuming no faults and ideal wires, sure. Neutral is the center tap. Yes. ...which is grounded. Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, Yes. Almost always, though it really doesn't matter. then the center tap should be above neutral on the secondary (house) side, right? No. The center tap is grounded at both the transformer and the entrance panel. It *is* ground. The center tap is by definition the neutral. Connecting it to ground ties it to ground potential. It's like if you had a battery in your hand, and someone saying the negative terminal is above earth/ground potential. It makes no sense. It has no realtion to anything when it's not hooked up to anything. Hook the neg end of the battery to ground and now that end is at ground potential. Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. It is. I don't see your problem. You described things pretty well. |
#23
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
Thanks everybody, that was very helpful.
|
#24
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 11:11:06 -0800 (PST), "
wrote: On Monday, November 18, 2013 1:54:55 PM UTC-5, wrote: On Mon, 18 Nov 2013 06:39:55 -0800 (PST), TimR wrote: I hate to display ignorance, and I know I should know this. But maybe somebody can explain. The power lines are 3 phase, meaning they're 120 degrees out of phase to each other Yes. allowing 3 wires to carry what 6 wires should (since they're generated by 3 sets of coils at the power plant). Kinda sorta. The house is fed by just one of these wires, through a center tap transformer. Yes. That transformer sends 3 wires to the house: Neutral, +120 volts, -120 volts. Well... There are two AC wires that are opposite, yes. If you said they were +120wt and -120wt, you would have a point (w being the angular frequency, or 2*Pi*f and t=time). And if you said they were 180 different in phase from each other, relative to the neutral, you would also be correct. Wrong. KRW only understands opposites, not phase. No, unlike the stupid lying ass, Trader, I know the difference. more lies snipped |
#25
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 4:52:51 PM UTC-5, wrote:
And if you said they were 180 different in phase from each other, relative to the neutral, you would also be correct. Wrong. KRW only understands opposites, not phase. No, unlike the stupid lying ass, Trader, I know the difference. more lies snipped Here, so everyone can see who's a liar and who knows what they are talking about. From the IEEE (Institute of Electrical and Electronic Engineers), a paper delivered at a rural electric power conference: "Distribution engineers have treated the standard "singlephase" distribution transformer connection as single phase because from the primary side of the transformer these connections are single phase and in the case of standard rural distribution single phase line to ground. However, with the advent of detailed circuit modeling we are beginning to see distribution modeling and analysis being accomplished past the transformer to the secondary. Which now brings into focus the reality that standard 120/240 secondary systems are not single phase line to ground systems, instead they are three wire systems with two phases and one ground wires. Further, the standard 120/240 secondary is different from the two phase primary system in that the secondary phases are separated by 180 degrees instead of three phases separated by 120 degrees. " Anyone following the discussion can read it and see that the IEEE engineers are saying EXACTLY what I've been saying all along. It couldn't be any more specific and on point. That IEEE paper is 100% in agreement with everything I've said. Of course krw will snip it and ignore it, instead of learning. |
#26
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 1:14:09 PM UTC-5, TimR wrote:
On Monday, November 18, 2013 12:57:11 PM UTC-5, SRN wrote: See if this diagram helps to understand: http://www.samlexamerica.com/support...Circuit s.pdf Good diagram. So primary is leg to ground, and secondary center tap is forced to ground. Makes sense. And note what else it says. It has one hot leg labled "Phase A", the other "Phase B". That means there are two phases present. Next, look at the note: "The phase of hot leg 2 (Phase B) is in the opposite direction, ie 180 degrees apart from the phase of hot leg 1 (Phase A)." Perhaps you can explain it now to krw that this document clearly shows two phases present and that they are 180 deg out of phase with each other. It's precisely in agreement with what I've been saying for two days now. |
#27
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 13:39:26 -0800 (PST), "
wrote: On Monday, November 18, 2013 2:01:42 PM UTC-5, wrote: On Mon, 18 Nov 2013 07:08:23 -0800 (PST), TimR wrote: On Monday, November 18, 2013 9:48:27 AM UTC-5, wrote: Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. All the neutrals are tied to ground. Why would you expect the neutral on the secondary to not be at ground level? In the strictist sense, if you take a center tap transformer, the secondary side doesn't have to have any relationship to the potential on the primary side. It's can be completely seperate, it's a seperate winding not connected to the primary. What and how you hook it up determines what level anything is referenced to. In the power transformer case, the center tap (neutral) is tied to ground. Well, you're not seeing the problem. I wish I could draw here. Your transformer has two wires going in, and three going out. I don't know what primary is in my neighbor hood, let's say 2400 vac for an example. Which two wires do we use? You only have the choice of leg to leg, or leg to neutral. Choose leg to neutral: use a 10 to 1 turns ratio, your secondary will be 240 volts line to line. Then center tap it, and you get 120 from each line to center. Pick one. It doesn't matter. BUT: why would center tap be anywhere near neutral? Because that's how it's wired. You *DEFINED* it as being 0V and connected it to ground. Choose leg to leg: does the same problem exist? No. There is no problem. Remember that transformers isolate. The secondary can be at any voltage you desire it to be, regardless of the primary (within the breakdown limits of the transformer, obviously). You connected one of it's secondary terminals to ground, defining that as 0V. Everything else falls out from there. You could have connected it to 1000V, but that wouldn't be smart. ;-) Once it gets into the house I understand how it works, but on the pole I'm hazy. There isn't any difference how it's connected there. You may have heard of "Delta" or "Wye" connections. Delta, connects the primary of the transformer between phases. A "Wye" connection would be from phase to ground. In the US, almost all loads are connected as "Wyes" and generators as "Deltas". I'm sure there are exceptions but that's what you'll find on your pole. By the way you are dead wrong on the 6 wires thing. That part I do remember. Trader is dead wrong about a lot. So you too believe that the same amount of power that's delivered by 3 wires with 3 phase would require 6 wires, twice the amount of copper to deliver any other way? Stop lying, Trader, and LEARN TO READ. snipped more of the lying sack of ****'s lies You're as bad as Malformed. |
#28
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is.
your confusion is becasue you don't understand how a transformer works. The pri and secondary are isolated from each other. The center tap of the sec has NO RELATIONSHIP to the primary. Think of the secondary as seperate floating power supply not related to the primary. The center tap of the secondary is neutral or ground ONLY becasue it gets connected to ground. Since it is connected to ground the two ends become +120 and -120 relative to neutral. Mark |
#29
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Monday, November 18, 2013 4:52:51 PM UTC-5, wrote:
On Mon, 18 Nov 2013 11:11:06 -0800 (PST), " wrote: On Monday, November 18, 2013 1:54:55 PM UTC-5, wrote: On Mon, 18 Nov 2013 06:39:55 -0800 (PST), TimR wrote: I hate to display ignorance, and I know I should know this. But maybe somebody can explain. The power lines are 3 phase, meaning they're 120 degrees out of phase to each other Yes. allowing 3 wires to carry what 6 wires should (since they're generated by 3 sets of coils at the power plant). Kinda sorta. The house is fed by just one of these wires, through a center tap transformer. Yes. That transformer sends 3 wires to the house: Neutral, +120 volts, -120 volts. Well... There are two AC wires that are opposite, yes. If you said they were +120wt and -120wt, you would have a point (w being the angular frequency, or 2*Pi*f and t=time). And if you said they were 180 different in phase from each other, relative to the neutral, you would also be correct. Wrong. KRW only understands opposites, not phase. No, unlike the stupid lying ass, Trader, I know the difference. more lies snipped Yes you have to snip them because they are irrefutable and show that you;re wrong. Typical, more name calling when you've lost an argument. Is the IEEE lying too? Here from the peer reviewed IEEE, a paper presented at a conference of power engineers: http://ieeexplore.ieee.org/xpl/artic...number=4520128 "Distribution engineers have treated the standard "singlephase" distribution transformer connection as single phase because from the primary side of the transformer these connections are single phase and in the case of standard rural distribution single phase line to ground. However, with the advent of detailed circuit modeling we are beginning to see distribution modeling and analysis being accomplished past the transformer to the secondary. Which now brings into focus the reality that standard 120/240 secondary systems are not single phase line to ground systems, instead they are three wire systems with two phases and one ground wires. Further, the standard 120/240 secondary is different from the two phase primary system in that the secondary phases are separated by 180 degrees instead of three phases separated by 120 degrees. " Or how about this: http://www.assocpower.com/index.php?Single-Phase-Power A split-phase (240/120V) power system is a 3-wire, single-phase, mid-point neutral system, which consists of two 120V "voltage sources"; connected out-of-phase by 180 electrical degrees with a neutral connection between them. Or this: http://www.samlexamerica.com/support...Circuit s.pdf "The phase of hot leg 2 (phase B) is in the opposite direction, ie 180 deg apart from the phase of hot leg 1 (phase A)" "The secondary of the distribution transformer has a grounded center tap and is wound in a manner that supplies two 120V AC phases which are 180 deg out of phase with each other (split phases)" They even go on to talk about using a oscilloscopet to look at them and say: "This indicates that the two 120V AC voltages are 180 deg out of phase" Go ahead, snip those truths too and keep making an ass of yourself. |
#30
|
|||
|
|||
Quote:
I find the first diagram on this web page that was posted by SRN helpful: http://www.samlexamerica.com/support...Circuit s.pdf It shows the primary side of the distribution transformer connected between the 7200 VAC carried by the single phase wire and ground. What I can't figure out here, tho, is that if the distribution transformer on the telephone pole is connected to ground, then it's connected via the ground wire that goes down the pole and is wrapped around the base of the telephone pole. So far as I know, that ground wire is not insulated, so that anyone that touches that ground wire would get a 7200 volt shock, which would surely kill them. So, I think that wiring diagram is mostly correct, but I think there's a problem with the primary side of the transformer connected to ground via the telephone pole's grounding wire. |
#31
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Tuesday, November 19, 2013 12:03:14 PM UTC-5, nestork wrote:
;3151685 Wrote: Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. your confusion is becasue you don't understand how a transformer works. The pri and secondary are isolated from each other. The center tap of the sec has NO RELATIONSHIP to the primary. Think of the secondary as seperate floating power supply not related to the primary. The center tap of the secondary is neutral or ground ONLY becasue it gets connected to ground. Since it is connected to ground the two ends become +120 and -120 relative to neutral. Mark Mark: I find the first diagram on this web page that was posted by SRN helpful: http://tinyurl.com/ly24tjo Don't let krw see that. The reference clearly says that with a spit-phase 240v/120v service, there are two phases present and they differ by 180 degrees. He says that just can't be. It shows the primary side of the distribution transformer connected between the 7200 VAC carried by the single phase wire and ground. What I can't figure out here, tho, is that if the distribution transformer on the telephone pole is connected to ground, then it's connected via the ground wire that goes down the pole and is wrapped around the base of the telephone pole. So far as I know, that ground wire is not insulated, so that anyone that touches that ground wire would get a 7200 volt shock, which would surely kill them. Even if it were only connected that way, you would only get a shock if the ground wire were broken and you grabbed the energized end. Otherwise if you grabbed an intact wire, the only voltage present would be whatever there is due to the small resistance of the wire, which would result in a small voltage drop across the wire run. The 7200 volts is across the transformer. The 25 ft of copper wire only drops a few volts, depending on the current flowing in it and the resistance of the wire. Actually the transformer is typically connected to a primary neutral. The primary neutral is in turn connected to ground much like on the secondary (house) side. It's not necessarily at every transformer, but periodically along the run. Other transformers connected to the same neutral, but from different phases, will balance out and reduce the current flowing in the neutral. So, I think that wiring diagram is mostly correct, but I think there's a problem with the primary side of the transformer connected to ground via the telephone pole's grounding wire. Yes, IMO, they should have shown the primary connected to a neutral, not just ground. |
#32
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Tuesday, November 19, 2013 12:03:14 PM UTC-5, nestork wrote:
;3151685 Wrote: Here's what I'm not getting at the moment. What are the connections to that transformer? If it is 3 phase leg to neutral on the primary side, then the center tap should be above neutral on the secondary (house) side, right? Which would mean that house neutral is NOT at ground level. But I'm pretty sure it is. your confusion is becasue you don't understand how a transformer works. The pri and secondary are isolated from each other. The center tap of the sec has NO RELATIONSHIP to the primary. Think of the secondary as seperate floating power supply not related to the primary. The center tap of the secondary is neutral or ground ONLY becasue it gets connected to ground. Since it is connected to ground the two ends become +120 and -120 relative to neutral. Mark Mark: I find the first diagram on this web page that was posted by SRN helpful: http://tinyurl.com/ly24tjo It shows the primary side of the distribution transformer connected between the 7200 VAC carried by the single phase wire and ground. What I can't figure out here, tho, is that if the distribution transformer on the telephone pole is connected to ground, then it's connected via the ground wire that goes down the pole and is wrapped around the base of the telephone pole. So far as I know, that ground wire is not insulated, so that anyone that touches that ground wire would get a 7200 volt shock, which would surely kill them. So, I think that wiring diagram is mostly correct, but I think there's a problem with the primary side of the transformer connected to ground via the telephone pole's grounding wire. -- nestork OK.. in the diagram, the top of the primary is connected to 7200Volts and the bottom of the primary is connected to ground. THe voltage on the wire connected to ground is close to 0. It doesn't matter that some of the current passing through that wire started out at 7200 Volts. As long as the wire is connected to ground, it is ground. So someone can touch that wire with no problem. BUT.. if the ground connection to the wire should come loose, then the wire will have a high voltage on it and would be dangerous, becuase it has current in it "that is trying to get to ground" and can't. That is actually the same danger in the 3 wire dreyer circuit. The ground and neutral share the same wire and if the connection to that wire comes loose, the "ground wire" will have dangerous voltage on it. On the pole transformer, ther bottom side of the primary coil is connected to ground, but the wire you see running down the pole is NOT the ONLY connection to ground. All the grounds in the entire distribution system are connected together so if the ground to one particular pole should come loose, the wire is still probably at ground due to all the other connections. But if I saw a loose ground wire running down a pole, I still would not want to touch it. Mark |
#33
|
|||
|
|||
Mark:
But, if what you're saying is true, then there is power flowing to ground through the primary coil of every distribution transformer in the USA and Canada 24 hours per day, 7 days per week, 365 days per year. And, with a voltage of 7200 volts driving that current, it would seem to me there would be a significant current flowing in the 40 or 50 foot cable going down from the transformer to the ground. Why don't those cables get warm to the touch? Is it entirely the impedance of the primary coil in the transformer? There is a 24 VAC doorbell transformer in every house in the USA and Canada. 120 Volt power is flowing through the primary coil of those transformers 24/7/365 and yet no one seems to be concerned about that power wastage. The only thing that makes sense to me here is that the impedance of the primary coil in distribution transformers is so high that the current flow to ground is actually very small despite the driving voltage being so high. And, I expect the same would be true for 24 VAC household transformers. That's why there's no big push on to save energy there like there is for light bulbs and appliances. Last edited by nestork : November 20th 13 at 02:17 AM |
#34
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
wrote in message ... On Tuesday, November 19, 2013 12:03:14 PM UTC-5, nestork wrote: snip Don't let krw see that. The reference clearly says that with a spit-phase 240v/120v service, there are two phases present and they differ by 180 degrees. He says that just can't be. http://www.allaboutcircuits.com/vol_2/chpt_10/1.html more snip They used to provide a protective cover for the transformer ground. In the old days it was a U-shaped channel milled out of wood. |
#35
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Tuesday, November 19, 2013 8:50:23 PM UTC-5, nestork wrote:
Mark: But, if what you're saying is true, then there is power flowing to ground through the primary coil of every distribution transformer in the USA and Canada 24 hours per day, 7 days per week, 365 days per year. And, with a voltage of 7200 volts driving that current, it would seem to me there would be a significant current flowing in the 40 or 50 foot cable going down from the transformer to the ground. Why don't those cables get warm to the touch? All the power isn't flowing in those ground wires. You typically have a neutral that is shared by multiple transformers. Each transformer isn't connected to the same phase, they are connected to phases in a distributed fashion. That means that the current in the neutral is only the unbalanced portion. If you had 3 transformers for 3 groups of houses, each on a seperate primary phase, with equal loads, the neutral current would sum to zero. And then you have the neutral grounded periodically along it's run, with a heavy, properly sized, ground wire, capable of handling the current through it. Is it entirely the impedance of the primary coil in the transformer? There is a 24 VAC doorbell transformer in every house in the USA and Canada. 120 Volt power is flowing through the primary coil of those transformers 24/7/365 and yet no one seems to be concerned about that power wastage. And, the only thing that makes sense here is that the impedance of the primary coil is so high that the current flow to ground is actually very small. Ditto for household transformers. -- nestork |
#36
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Sun, 17 Nov 2013 19:14:56 -0700, Tony Hwang wrote:
Gnd and Neutral is connected together but they are not same in functionality in the circuit. For some reason, I didn't see this thread, and assumed it hadn't posted. So I apologize for not having answered any issues. I've learned a lot. For example, the ground and the neutral, in my house, are connected together in the main panel, but not in the sub panels. I've learned the neutrals are different than grounds in other ways. For example, they never branch (they always stay with their associated hot wires). They only meet at the main breaker panel. The grounds, on the other hand, go all over the place. Plus, most of the time, they're not insulated (although they may also be green). |
#37
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Tue, 19 Nov 2013 18:03:14 +0100, nestork wrote:
I find the first diagram on this web page that was posted by SRN helpful: Here's a PNG of that diagram, for reference: http://farm8.staticflickr.com/7292/1...4ba18de1_o.png In the dryer thread, it was noted that most USA circuit breakers are *not* arrayed in AB-AB-AB format; but in AA-BB-AA-BB format. I'm not sure what that means though... |
#38
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 06:48:27 -0800, wrote:
The 6 vs three makes no sense. Here are six distribution wires, by the way ... http://farm8.staticflickr.com/7456/1...349dd5b6_o.gif |
#39
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 07:08:23 -0800, TimR wrote:
By the way you are dead wrong on the 6 wires thing. That part I do remember. I was always of the opinion that the ground was the second set of three wires. That is, the power company grabs electrons from the ground, and then it sends those electrons over three wires, 120 degrees out of phase, and then the electrons return to the power company through the ground. It's a huge loop. At least the way I understand it. BTW, here are six wires, but they're not the same thing! http://farm8.staticflickr.com/7456/1...349dd5b6_o.gif |
#40
Posted to alt.home.repair
|
|||
|
|||
How does the typical mains power connect in the USA anyway?
On Mon, 18 Nov 2013 18:09:29 +0100, nestork wrote:
This web site explains it fairly well: http://tinyurl.com/y4syno6 That was interesting. Notice the 7200V primary side of the transformer didn't look grounded in the picture (but it must have been). Right? Also, the ground (literally) was stated as being part of the circuit (although I would have like them to complete the circuit at your lamp, and then *back* to the power company (via the ground). |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Mains Water Pressure. What is "typical"? | UK diy | |||
QUESTION: How to connect a power supply to my home power grid? | Electronics | |||
Power switched off at mains but still power to sockets | UK diy | |||
Can't connect power, GFCI weird? | Home Ownership | |||
Can't connect power, GFCI weird? | Electronics Repair |