I recently constructed a built-in desk and bookshelf in my upstairs
loft.

There was an outlet on the wall that happened to be right where two
bookshelves joined together. I had to remove the cover plate and
outlet in order for the bookshelves to be flush against the wall. I
removed the socket and rejoined the wires together using wire nuts. I
then pushed the wires back into the box and put my shelves in front of
it...without using a cover plate. Its this last part that I'm kinda
regretting now that the built-in is complete.

Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.

  #2   Report Post  
Posted to rec.woodworking
Lee Lee is offline
external usenet poster
 
Posts: 194
Default Electical question

If you twisted the wires ( holds the wires from pulling out of nut)before
the nut was put on and there is no exposed copper at the nut a cover plate
will be fine. The plate is to prevent anyone or thing getting at the wires.
With the cover plate on this should meet code.
I'm taking it for granted that white-white black-black ground- ground where
all done.
"rolsonDesign" wrote in message
ups.com...
I recently constructed a built-in desk and bookshelf in my upstairs
loft.

There was an outlet on the wall that happened to be right where two
bookshelves joined together. I had to remove the cover plate and
outlet in order for the bookshelves to be flush against the wall. I
removed the socket and rejoined the wires together using wire nuts. I
then pushed the wires back into the box and put my shelves in front of
it...without using a cover plate. Its this last part that I'm kinda
regretting now that the built-in is complete.

Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.



  #3   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,123
Default Electical question

On May 15, 5:00 pm, rolsonDesign wrote:
I recently constructed a built-in desk and bookshelf in my upstairs
loft.

There was an outlet on the wall that happened to be right where two
bookshelves joined together. I had to remove the cover plate and
outlet in order for the bookshelves to be flush against the wall. I
removed the socket and rejoined the wires together using wire nuts. I
then pushed the wires back into the box and put my shelves in front of
it...without using a cover plate. Its this last part that I'm kinda
regretting now that the built-in is complete.

Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.


Plates are cheap at 50 cents each. You taped the wirenuts, right?

  #4   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 21
Default Electical question


"rolsonDesign" wrote in message
ups.com...
I recently constructed a built-in desk and bookshelf in my upstairs
loft.

There was an outlet on the wall that happened to be right where two
bookshelves joined together. I had to remove the cover plate and
outlet in order for the bookshelves to be flush against the wall. I
removed the socket and rejoined the wires together using wire nuts. I
then pushed the wires back into the box and put my shelves in front of
it...without using a cover plate. Its this last part that I'm kinda
regretting now that the built-in is complete.

Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.


Does this not become a junction box in this scenario? If so, I always
thought that they need to be easily accessed.


  #5   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,617
Default Electical question


"rolsonDesign" wrote in message
ups.com...
I recently constructed a built-in desk and bookshelf in my upstairs
loft.

There was an outlet on the wall that happened to be right where two
bookshelves joined together. I had to remove the cover plate and
outlet in order for the bookshelves to be flush against the wall. I
removed the socket and rejoined the wires together using wire nuts. I
then pushed the wires back into the box and put my shelves in front of
it...without using a cover plate. Its this last part that I'm kinda
regretting now that the built-in is complete.

Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.

So many interesting answers!

Yes, you needed to have a cover plate. An electrical box is supposed to
contain an electrical fire. Presumably your bookshelves are combustible?
Admittedly, the chances of an arc in the connections severe enough to cause
a fire are very very small, but I wouldn't be comfortable with it. If you
had fastened a piece of sheet metal over the opening, that probably would
have been okay, even if it didn't meet code.




  #6   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 3
Default Electical question

"rolsonDesign" wrote in message
ups.com...
I recently constructed a built-in desk and bookshelf in my upstairs
loft.


[snip]

Opinions? I'm probably breaking major building codes doing that too.


"efgh" wrote in message
news:8Zr2i.22602$Xh3.4308@edtnps90...


Does this not become a junction box in this scenario? If so, I always
thought that they need to be easily accessed.



If I'm understanding you correctly, you have blocked access to a junction
box by constructing the bookshelves over the junction box. If this is what
you have done, then the lack of a cover plate is only part of the problem.

The National Electrical Code requires ALL splices be forever accessible. If
you are required to remove building "finish" materials to gain access to
splices, that does not meet he definition of accessibility.
Secondly, if you sell the house, how will the next owner have any idea where
to look for this splice? Splices do occassionally need attention.

If you've made a decent splice, the lack of a cover in this case is probably
not a safety issue as NO ONE is likely to accidently touch ANY of these
wires.

Gary Kasten
Licensed Electrical Contractor
Kasten Electric Company
St. Peters, MO


  #7   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 931
Default Electical question

rolsonDesign wrote in news:1179262811.280486.79690
@e65g2000hsc.googlegroups.com:

*snip*


Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.


Do it right the first time, and you'll save money in the long run. If
code calls for a cover plate, put a cover plate on. Consider this also:
Electrical boxes are great places for bugs to hide. You don't really
want to have to work on the box and deal with spider webs, do you?

Puckdropper
--
Wise is the man who attempts to answer his question before asking it.

To email me directly, send a message to puckdropper (at) fastmail.fm
  #8   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article . com, rolsonDesign wrote:
I recently constructed a built-in desk and bookshelf in my upstairs
loft.

There was an outlet on the wall that happened to be right where two
bookshelves joined together. I had to remove the cover plate and
outlet in order for the bookshelves to be flush against the wall. I
removed the socket and rejoined the wires together using wire nuts. I
then pushed the wires back into the box and put my shelves in front of
it...without using a cover plate. Its this last part that I'm kinda
regretting now that the built-in is complete.

Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.

The lack of a cover plate is a code violation, yes, but that's the least of
your worries. The National Electrical Code requires all splices and junctions
to be accessible, and specifically defines "accessible" thus:

"Capable of being removed or exposed without damaging the building structure
or finish or not permanently closed in by the structure or finish of the
building."

A junction box that has a built-in bookcase over it does not qualify as
accessible.

The best solution to this problem is to locate the other end of each of the
two cables that enter this box, and disconnect them. Then run a new cable via
a different route, bypassing the segment you just disconnected.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #10   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 10,043
Default Electical question


"Toller" wrote in message

Yes, you needed to have a cover plate. An electrical box is supposed to
contain an electrical fire. Presumably your bookshelves are combustible?
Admittedly, the chances of an arc in the connections severe enough to

cause
a fire are very very small, but I wouldn't be comfortable with it. If you
had fastened a piece of sheet metal over the opening, that probably would
have been okay, even if it didn't meet code.


I wouldn't be comfortable at all.

19 years ago I had a small fire in an interior wall of a 50 year old house
(small, only because my 3 year old daughter came to me at 1:30 PM and
insisted I come look at the "pretty lights" in the living room behind the
clock, and I caught it in time) due to a splice that shorted and caught the
wall on fire.

The splice was in a box, with no lid, and then drywalled over. I had no idea
it was there.

Essentially, it was a time bomb that took 45 years to go off ... thank
goodness in the afternoon, instead of 1:30 in the morning.

--
www.e-woodshop.net
Last update: 2/20/07
KarlC@ (the obvious)







  #11   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,617
Default Electical question


"Swingman" wrote in message
...

"Toller" wrote in message

Yes, you needed to have a cover plate. An electrical box is supposed to
contain an electrical fire. Presumably your bookshelves are combustible?
Admittedly, the chances of an arc in the connections severe enough to

cause
a fire are very very small, but I wouldn't be comfortable with it. If
you
had fastened a piece of sheet metal over the opening, that probably would
have been okay, even if it didn't meet code.


I wouldn't be comfortable at all.

19 years ago I had a small fire in an interior wall of a 50 year old house
(small, only because my 3 year old daughter came to me at 1:30 PM and
insisted I come look at the "pretty lights" in the living room behind the
clock, and I caught it in time) due to a splice that shorted and caught
the
wall on fire.

The splice was in a box, with no lid, and then drywalled over. I had no
idea
it was there.

Essentially, it was a time bomb that took 45 years to go off ... thank
goodness in the afternoon, instead of 1:30 in the morning.

well, I am suggesting metal rather than drywall. There isn't much
difference between sheet metal and a blank box cover.

but, how did the wall catch fire? I would expect the dry wall to be
charred, but it shouldn't have actually caught fire.

I should have had a fire when a mouse chewed through a wire right next to
where we kept napkins. His front half vaporized, but miraculously the
napkins didn't catch.


  #13   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article , "Toller" wrote:

well, I am suggesting metal rather than drywall. There isn't much
difference between sheet metal and a blank box cover.


You're right, there isn't -- using either one to cover an inaccessible box is
still a Code violation. ;-)

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #14   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article , Roy Smith wrote:

But, a built-in bookcase with a built-in hinged door in the back to access
the box probably would. If you do it right, it could be quite unobtrusive,
and completely invisible when the shelf is filled with books. I suspect
that would satisfy both the letter and the spirit of the code.


Another option would be to cut a hole in the back of the built-in directly
over the box, and add an extender ring to the box to bring it flush with the
inside surface of the built-in. Then attach the cover plate of your choice.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #15   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 1,619
Default Electical question


"Swingman" wrote

"Toller" wrote in message

but, how did the wall catch fire? I would expect the dry wall to be
charred, but it shouldn't have actually caught fire.


That's what makes it chilling, eh?

It "shouldn't have", but it did!

By the time I got there the stud the box was attached to was in flames ...
indeed a 'chilling' event.

With a young child in the house, and even after I tore out the drywall all
the way to the ceiling on both sides of the wall, and was absolutely sure
that there was not a spark left (there was no 'fire blocking' of studs in
those days, apparently) to come back to life, I spent that entire night,
and
the next day, awake and on "fire watch".

Shudder every time I recollect it.


I can relate.

It was lucky that you had a bright kid who wanted to show her dad some
"pretty lights".

I moved into a house that had all kinds of compromised electrical work. No
doubt, done by some bumpkin who wanted to "save money" and had no concept of
safety. I went nuts and replaced everything that I could. It already had a
new breaker box and half of the wiring was new. But no ground connections
were made in any of the new wiring.

There was a big basement that was lighted by a number of recycled 8 foot
commercial flouescent fitures. There was one right at the foot of the
stairs. I was coming down the stairs just a week or so after moving in one
day. I smelled something funny coming out of the fixture.

I popped of the cover and some smoke came out. There was varnish dripping
out of the ballast! I immediately turned off the lights and stood vigil
until everything was cool. I then pulled out all the ballasts from all the
fixtures. Every single one of them was melting and a fire was just days
away from happening. He must of got a great deal on these fixtures.

I replaced the ballasts on the lights and everything worked just fine for
the next 24 years. I was quite upset at the time. And I still get a chill
thinking about how close I cane to having a newly purchased house burn to
the ground.





  #16   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 10,043
Default Electical question

"Toller" wrote in message

but, how did the wall catch fire? I would expect the dry wall to be
charred, but it shouldn't have actually caught fire.


That's what makes it chilling, eh?

It "shouldn't have", but it did!

By the time I got there the stud the box was attached to was in flames ...
indeed a 'chilling' event.

With a young child in the house, and even after I tore out the drywall all
the way to the ceiling on both sides of the wall, and was absolutely sure
that there was not a spark left (there was no 'fire blocking' of studs in
those days, apparently) to come back to life, I spent that entire night, and
the next day, awake and on "fire watch".

Shudder every time I recollect it.

--
www.e-woodshop.net
Last update: 2/20/07
KarlC@ (the obvious)


  #17   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 117
Default Electical question


"Doug Miller" wrote in message
.. .
In article , Roy
Smith wrote:

But, a built-in bookcase with a built-in hinged door in the back to access
the box probably would. If you do it right, it could be quite
unobtrusive,
and completely invisible when the shelf is filled with books. I suspect
that would satisfy both the letter and the spirit of the code.


Another option would be to cut a hole in the back of the built-in directly
over the box, and add an extender ring to the box to bring it flush with
the
inside surface of the built-in. Then attach the cover plate of your
choice.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


I guess I have mixed feelings here, I recognize the dangers but have serious
problems with electrician's high hourly rates in particular when the
required job skill level is so low . Basically in this region their only
claim to fame is the fact is they can sign off that the job is in fact to
code regardless of their crappy work.

In my opinion if their rates were reasonable far less people would be doing
basic wiring themselves. Im my case I read the books then wired my complete
shop all the electrician did was to inspect it and confirm it was up to code
and connect it to the mains . The only reason to use a "certified"
electrician was that is all the inspector would accept.....and you know
what, I still considered it expensive .....mjh


  #18   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 347
Default Electical question

On 16 May 2007 05:32:41 GMT, Puckdropper
wrote:

rolsonDesign wrote in news:1179262811.280486.79690
:

*snip*


Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.


Do it right the first time, and you'll save money in the long run. If
code calls for a cover plate, put a cover plate on. Consider this also:
Electrical boxes are great places for bugs to hide. You don't really
want to have to work on the box and deal with spider webs, do you?


So then what type of wiring is it? Romex? Wire in conduit?. If it is
properly installed romex ripping out the drywall to unstapled it would
not work for me. But by passing and disconnecting the romex and
leaving it there very appealing. Wire in conduit piece of cake though.

Side note the new place has a fuse panel, and it is staying.

Mark
(sixoneeight) = 618
  #19   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 10,043
Default Electical question

"Lee Michaels" wrote in message

I replaced the ballasts on the lights and everything worked just fine for
the next 24 years. I was quite upset at the time. And I still get a

chill
thinking about how close I cane to having a newly purchased house burn to
the ground.


You only have to go through that once to get a healthy respect for ALWAYS
following the best electrical practices known to man.

To this day, as a builder, I take a strong personal interest in inspecting
all the electrical work _myself_ before insulation/drywall goes up.

Not to mention that it is a constant battle with sheetrockers who cover up
electrical receptacles (hell, even AC vents) in their haste to get to the
next job.

I _ALWAYS_ take digital pictures of every single wall in the entire house
after electrical, plumbing and HVAC rough-in, and before insulation, put
those photos on a CD, and ultimately give them to the purchaser in the
"house book" we always supply for appliances, fixtures, warranties, etc.

As a homeowner, it is something I appreciate greatly, just for the safety
aspects. And, as a builder, I can't tell you how many times that one
practice has saved my butt during electrical trim out ... and I get to sleep
at night.

--
www.e-woodshop.net
Last update: 2/20/07
KarlC@ (the obvious)


  #20   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article , "mike hide" wrote:

I guess I have mixed feelings here, I recognize the dangers but have serious
problems with electrician's high hourly rates in particular when the
required job skill level is so low . Basically in this region their only
claim to fame is the fact is they can sign off that the job is in fact to
code regardless of their crappy work.

In my opinion if their rates were reasonable far less people would be doing
basic wiring themselves.


I'm afraid I have to disagree with you on a couple of points. IMO, the reason
so many folks go the DIY route has less to do with the hourly rates charged by
electricians than with the widespread misperception that "the the required job
skill level is so low."

It's *not* a low-skill job.

Almost any fool can install residential wiring so that it works. Installing it
so that it works, *and* is safe, isn't quite so simple. I've encountered, and
corrected, these problems (among others) created by the previous owners of my
various homes:

+ light switch in the neutral instead of the hot
+ 14-2 BX made to do the job of 14-3 by using the cable armor as a conductor
+ 3-way switches installed with 12-2, using the ground conductor as a traveler
+ hot and neutral reversed on a receptacle
+ outdoor outlet unprotected by GFCI
+ 20A breaker on a circuit with 14ga wire
+ 30A fuse on a circuit with 14ga wire
+ Romex run through an ungrommeted hole in a steel cold air return duct
+ aluminum wire connected to copper with copper-only wire nuts
+ aluminum wire connected to copper-only receptacles
+ cross-connected neutrals in two junction boxes on different circuits
+ Edison circuits not identifed as such and having no common disconnect
+ 100A overcurrent protection on a circuit dedicated to a 1/2 HP well pump
+ abandoned live wires in circumstances very similar to the one Swingman
described (though without the "pretty colored lights")
+ 60A subpanel fed from another subpanel with 10/3 Romex ...
+ ... attached to the *hot* side of the lugs (so that the only overcurrent
protection for the 10-ga feeder was the 200A service disconnect)

All of these things "work". Not one of them is safe. But because they function
as expected, the idiots who installed them probably didn't give them a second
thought.

I think any person of normal intelligence and mechanical ability, who takes
the trouble to familiarize himself with the proper materials and methods of
installation, and with the applicable portions of the NEC, is capable of
installing residential wiring safely. Trouble is, there are a LOT of people
who don't even know that there IS a National Electrical Code, let alone have
any idea WHY.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


  #21   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 117
Default Electical question


As I said read the book by black and decker written by a professional
electrician andd these problems will not occurr. I have to disagree the
skill level is low all you need to know is what code is and how to implement
it and read the book it certainly is not rocket science . Of course that is
assuming the average electrician can read, which is doubtful in some cases
......mjh
"Doug Miller" wrote in message
t...
In article , "mike hide"
wrote:

I guess I have mixed feelings here, I recognize the dangers but have
serious
problems with electrician's high hourly rates in particular when the
required job skill level is so low . Basically in this region their only
claim to fame is the fact is they can sign off that the job is in fact to
code regardless of their crappy work.

In my opinion if their rates were reasonable far less people would be
doing
basic wiring themselves.


I'm afraid I have to disagree with you on a couple of points. IMO, the
reason
so many folks go the DIY route has less to do with the hourly rates
charged by
electricians than with the widespread misperception that "the the required
job
skill level is so low."

It's *not* a low-skill job.

Almost any fool can install residential wiring so that it works.
Installing it
so that it works, *and* is safe, isn't quite so simple. I've encountered,
and
corrected, these problems (among others) created by the previous owners of
my
various homes:

+ light switch in the neutral instead of the hot
+ 14-2 BX made to do the job of 14-3 by using the cable armor as a
conductor
+ 3-way switches installed with 12-2, using the ground conductor as a
traveler
+ hot and neutral reversed on a receptacle
+ outdoor outlet unprotected by GFCI
+ 20A breaker on a circuit with 14ga wire
+ 30A fuse on a circuit with 14ga wire
+ Romex run through an ungrommeted hole in a steel cold air return duct
+ aluminum wire connected to copper with copper-only wire nuts
+ aluminum wire connected to copper-only receptacles
+ cross-connected neutrals in two junction boxes on different circuits
+ Edison circuits not identifed as such and having no common disconnect
+ 100A overcurrent protection on a circuit dedicated to a 1/2 HP well pump
+ abandoned live wires in circumstances very similar to the one Swingman
described (though without the "pretty colored lights")
+ 60A subpanel fed from another subpanel with 10/3 Romex ...
+ ... attached to the *hot* side of the lugs (so that the only overcurrent
protection for the 10-ga feeder was the 200A service disconnect)

All of these things "work". Not one of them is safe. But because they
function
as expected, the idiots who installed them probably didn't give them a
second
thought.

I think any person of normal intelligence and mechanical ability, who
takes
the trouble to familiarize himself with the proper materials and methods
of
installation, and with the applicable portions of the NEC, is capable of
installing residential wiring safely. Trouble is, there are a LOT of
people
who don't even know that there IS a National Electrical Code, let alone
have
any idea WHY.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.



  #22   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 10,043
Default Electical question

"mike hide" wrote in message

it and read the book it certainly is not rocket science . Of course that

is
assuming the average electrician can read, which is doubtful in some cases


Around here there are many who may well have trouble reading English.

--
www.e-woodshop.net
Last update: 2/20/07
KarlC@ (the obvious)


  #23   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 117
Default Electical question

So no doubt your house is wired to the mexican electrical code ,which is
fine until you open the circuit breaker box and start trying to figure what
all the in spanish breakers control


"Swingman" wrote in message
news
"mike hide" wrote in message

it and read the book it certainly is not rocket science . Of course that

is
assuming the average electrician can read, which is doubtful in some
cases


Around here there are many who may well have trouble reading English.

--
www.e-woodshop.net
Last update: 2/20/07
KarlC@ (the obvious)




  #24   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article , "mike hide" wrote:
So no doubt your house is wired to the mexican electrical code ,which is
fine until you open the circuit breaker box and start trying to figure what
all the in spanish breakers control


Blank labels read the same in any language. g

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #26   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 25
Default Electical question


The best solution to this problem is to locate the other end of each of the
two cables that enter this box, and disconnect them. Then run a new cable via
a different route, bypassing the segment you just disconnected.



That's what I was thinking. It seems as though I will have to cut an
opening in the back of my bookshelf for a new box and then snip the
old wires that go into the old box and re-join them in the new box.

I meant to have the junction box accessable in the first place. I
even went and bought a box -extender for remodels, but when I placed
the two bookshelves together on the wall...the "joint" of the
bookshelves rested right down the middle of the socket. So I removed
the socket, spliced the wires (I twisted them), and screwed the nut on
and pushed them back into the box. No it doesn't make me comfortable
that there are wires behind my built-in, but at the time I didn't
really know what to do.

  #27   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 25
Default Electical question


Another option would be to cut a hole in the back of the built-in directly
over the box, and add an extender ring to the box to bring it flush with the
inside surface of the built-in. Then attach the cover plate of your choice.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


That's what the problem is...there are two bookshelf components that
join each other right over the place where the outlet or junction box
is.

I think my fix for this would be to cut a new hold in the back of the
built-in and through the wall, Then find the wires that lead to the
old junction box and snip them (with the power shut off of course).
Then re-route new wires to the new j-box in the back of my built-in.

  #28   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 10,043
Default Electical question


"rolsonDesign" wrote in message

I think my fix for this would be to cut a new hold in the back of the
built-in and through the wall, Then find the wires that lead to the
old junction box and snip them (with the power shut off of course).
Then re-route new wires to the new j-box in the back of my built-in.


Perhaps this has been asked already: Interior wall? What's on the other
side?

--
www.e-woodshop.net
Last update: 2/20/07
KarlC@ (the obvious)





  #29   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 25
Default Electical question

On May 16, 9:55 am, (Doug Miller) wrote:
In article , "mike hide" wrote:
I guess I have mixed feelings here, I recognize the dangers but have serious
problems with electrician's high hourly rates in particular when the
required job skill level is so low . Basically in this region their only
claim to fame is the fact is they can sign off that the job is in fact to
code regardless of their crappy work.


In my opinion if their rates were reasonable far less people would be doing
basic wiring themselves.


I'm afraid I have to disagree with you on a couple of points. IMO, the reason
so many folks go the DIY route has less to do with the hourly rates charged by
electricians than with the widespread misperception that "the the required job
skill level is so low."

It's *not* a low-skill job.

Almost any fool can install residential wiring so that it works. Installing it
so that it works, *and* is safe, isn't quite so simple. I've encountered, and
corrected, these problems (among others) created by the previous owners of my
various homes:

+ light switch in the neutral instead of the hot
+ 14-2 BX made to do the job of 14-3 by using the cable armor as a conductor
+ 3-way switches installed with 12-2, using the ground conductor as a traveler
+ hot and neutral reversed on a receptacle
+ outdoor outlet unprotected by GFCI
+ 20A breaker on a circuit with 14ga wire
+ 30A fuse on a circuit with 14ga wire
+ Romex run through an ungrommeted hole in a steel cold air return duct
+ aluminum wire connected to copper with copper-only wire nuts
+ aluminum wire connected to copper-only receptacles
+ cross-connected neutrals in two junction boxes on different circuits
+ Edison circuits not identifed as such and having no common disconnect
+ 100A overcurrent protection on a circuit dedicated to a 1/2 HP well pump
+ abandoned live wires in circumstances very similar to the one Swingman
described (though without the "pretty colored lights")
+ 60A subpanel fed from another subpanel with 10/3 Romex ...
+ ... attached to the *hot* side of the lugs (so that the only overcurrent
protection for the 10-ga feeder was the 200A service disconnect)

All of these things "work". Not one of them is safe. But because they function
as expected, the idiots who installed them probably didn't give them a second
thought.

I think any person of normal intelligence and mechanical ability, who takes
the trouble to familiarize himself with the proper materials and methods of
installation, and with the applicable portions of the NEC, is capable of
installing residential wiring safely. Trouble is, there are a LOT of people
who don't even know that there IS a National Electrical Code, let alone have
any idea WHY.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


Then isn't up to the people who come up with the National Electrical
Code to properly make it known to the people who are planning on doing
their own work...I mean, through some sort of PSA can't they say
something like."If you going to do you own electrical work, be sure to
understand and comply with the National Electrical Code."

  #30   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article . com, rolsonDesign wrote:

The best solution to this problem is to locate the other end of each of the
two cables that enter this box, and disconnect them. Then run a new cable via
a different route, bypassing the segment you just disconnected.



That's what I was thinking. It seems as though I will have to cut an
opening in the back of my bookshelf for a new box and then snip the
old wires that go into the old box and re-join them in the new box.


Not if you just bypass it as I outlined above, and abandon it. I'm not sure I
understand where you're going with this.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


  #31   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article .com, rolsonDesign wrote:

Then isn't up to the people who come up with the National Electrical
Code to properly make it known to the people who are planning on doing
their own work...I mean, through some sort of PSA can't they say
something like."If you going to do you own electrical work, be sure to
understand and comply with the National Electrical Code."


In many jurisdictions, it's illegal to do your own electrical work without
getting a permit -- and in some places you can't a permit unless you're a
licensed electrician. The PSAs you suggest could be seen by local enforcement
authorities as an inducement to violate the law.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #32   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 6,375
Default Electical question

In article . com, rolsonDesign wrote:

I think my fix for this would be to cut a new hold in the back of the
built-in and through the wall, Then find the wires that lead to the
old junction box and snip them (with the power shut off of course).
Then re-route new wires to the new j-box in the back of my built-in.


Why??

As it is right now, you have a splice in an inaccessible junction box. Let's
call it Box A. There are two cables in that box, right? Each one goes to
another box somewhere else. Call those Box B and Box C.

Now locate those two boxes. Shut off the power. Disconnect and remove the
cable from Box B that connects to Box A, after taking careful note of exactly
how it's connected to the other cable(s) in the box. Do the same at Box C.

Now run a new cable from Box B directly to Box C, connecting each end exactly
as the old cables were connected.

Turn power back on, and verify that each of the cables you disconnected is
dead.

Done. It no longer matters that Box A is inaccessible, because it's not
connected to anything and therefore is no longer part of your electrical
installation and therefore not subject to the Code.



--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #33   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 692
Default Electical question

On 15 May 2007 14:00:11 -0700, rolsonDesign
wrote:

I recently constructed a built-in desk and bookshelf in my upstairs
loft.

There was an outlet on the wall that happened to be right where two
bookshelves joined together. I had to remove the cover plate and
outlet in order for the bookshelves to be flush against the wall. I
removed the socket and rejoined the wires together using wire nuts. I
then pushed the wires back into the box and put my shelves in front of
it...without using a cover plate. Its this last part that I'm kinda
regretting now that the built-in is complete.

Should I have put a cover plate over that or will the wire nuts be
sufficient? None of the wires were anywhere near crossing each other
but I still have a little anxiety about it. I'm pretty sure I know
what the pro's would do...

Opinions? I'm probably breaking major building codes doing that too.



Here is what I know about elektricity:


Volts X Amps = Watts.

Watts/Volts = Amps.

I = V/r.

P=V X I.

I=P/V.



For everything else I go to the NEC.


I think that you should go there, too.





Regards,

Tom Watson

tjwatson1ATcomcastDOTnet (real email)

http://home.comcast.net/~tjwatson1/
  #34   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 164
Default Electical question

On 17 May 2007 04:39:57 GMT, Puckdropper
wrote:

(Doug Miller) wrote in
et:


Blank labels read the same in any language. g


I'm labeling mine as we blow breakers due to excess current. There's
power to the garage that also includes the kitchen in the next room, 90%
of the house on breaker 15, I guess when they installed the heaters in
the bathrooms they got their own circuits...


and there's a bunch of breakers that I don't know what they're for yet.


My solution to that problem was to...
rip out the kitchen, and redo all the electrical circuits (in the
kitchen), ripping out the BX, replacing it w/grounded romex, adding a
few circuits, rearranging and exchanging breakers, and in the process
figuring out what each and every breaker served. Minor problem that
ensued was a few outlets in the basement are suddenly dead, due to
feeding off one of the old, as yet untraced, disconnected kitchen
lines.

'Course, that may be overkill in your situation...

I delayed figuring out all the circuits until I had to. Surprisingly,
in spite of a rather small # of breaker slots (~18?) I managed to find
enough space in the panel to get in all the circuits I wanted,
including 7 -8 for the kitchen.

Renata



Well, this is what happens when your house wiring "evolves".

Puckdropper


  #35   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 931
Default Electical question

Renata wrote in
:

On 17 May 2007 04:39:57 GMT, Puckdropper
wrote:

(Doug Miller) wrote in
. net:


Blank labels read the same in any language. g


I'm labeling mine as we blow breakers due to excess current.


*trim*


My solution to that problem was to...
rip out the kitchen, and redo all the electrical circuits (in the
kitchen), ripping out the BX, replacing it w/grounded romex, adding a
few circuits, rearranging and exchanging breakers, and in the process
figuring out what each and every breaker served. Minor problem that
ensued was a few outlets in the basement are suddenly dead, due to
feeding off one of the old, as yet untraced, disconnected kitchen
lines.

'Course, that may be overkill in your situation...


*snip*


Renata


Actually, that's underkill. To solve this house's problem, it really
needs to be knocked down and rebuilt. (Blown up... hm... what fun. Too
bad the neighbor's so close. The owners could charge admission for the
event and maybe offset new construction costs.)

Puckdropper
--
Wise is the man who attempts to answer his question before asking it.

To email me directly, send a message to puckdropper (at) fastmail.fm


  #36   Report Post  
Posted to rec.woodworking
external usenet poster
 
Posts: 164
Default Electical question

On 21 May 2007 18:24:58 GMT, Puckdropper
wrote:

Renata wrote in
:

On 17 May 2007 04:39:57 GMT, Puckdropper
wrote:

(Doug Miller) wrote in
.net:


Blank labels read the same in any language. g


I'm labeling mine as we blow breakers due to excess current.


*trim*


My solution to that problem was to...
rip out the kitchen, and redo all the electrical circuits (in the
kitchen), ripping out the BX, replacing it w/grounded romex, adding a
few circuits, rearranging and exchanging breakers, and in the process
figuring out what each and every breaker served. Minor problem that
ensued was a few outlets in the basement are suddenly dead, due to
feeding off one of the old, as yet untraced, disconnected kitchen
lines.

'Course, that may be overkill in your situation...


*snip*


Renata


Actually, that's underkill. To solve this house's problem, it really
needs to be knocked down and rebuilt. (Blown up... hm... what fun. Too
bad the neighbor's so close.


Well..., maybe not. What shape's his house in? Maybe you could make
it a two-fer? In fact, how 'bout the neighborhood...? ;-)

Renata

The owners could charge admission for the
event and maybe offset new construction costs.)

Puckdropper


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electical Problem... [email protected] Electronics Repair 19 February 26th 07 01:57 AM
electical conduit Eigenvector Home Repair 6 June 23rd 06 07:54 AM
Electical problem [email protected] UK diy 0 June 3rd 06 12:15 PM
electical supplies DavidD UK diy 6 January 24th 05 03:51 PM
Residential electical question William Morris Home Repair 30 November 28th 03 03:22 PM


All times are GMT +1. The time now is 07:41 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"