On Oct 12, 6:41*pm, "RBM" wrote:
wrote in message

...
On Oct 12, 7:56 am, "RBM" wrote:





"RBM" wrote in message


...


"Mikepier" wrote in message
....
Last week, I posted about running 12/2 wire for a kitchen reno. Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a question.

  #42   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 13, 5:36*pm, "RBM" wrote:
wrote in message

...
On Oct 12, 6:41 pm, "RBM" wrote:





wrote in message


...
On Oct 12, 7:56 am, "RBM" wrote:


"RBM" wrote in message


...


"Mikepier" wrote in message
...
Last week, I posted about running 12/2 wire for a kitchen reno. Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.


I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.


15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected, but all the counter outlets do. A 15 amp GFCI outlet has a
20
amp feed through


Just to clarify. A single 15 amp outlet can't be installed on a 20 amp
dedicated circuit, but a duplex is fine


- Hide quoted text -


- Show quoted text -- Hide quoted text -


- Show quoted text -


This is another example of things in the code that don't seem to make
any sense, at least to me. If one can install multiple 15 amp
outlets on a 20 amp circuit, why the restriction on installing just
one?


And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit, but you can't install multiple 20's on a
15 amp circuit.


Why the big distinction between single versus multiple outlets?


The feed through of a 15 amp outlet is 20 amps. You cannot install a 20
amp
outlet on a 15 amp circuit Nec 210.21 B3- Hide quoted text -


- Show quoted text -


NEC 210.21(B)(3) starts off by saying that section only applies to
circuits with more than one outlet. * We are talking about a SINGLE
outlet. * In which case, the following section applies:

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

Since the 20 amp outlet has a rating greater than the 15 amp circuit,
it may be used. * *Now, I would agree it doesn't make much, but that
is what is says, and hence was my point.

That text is only part of the article, the table clarifies the rest. There
is no ambiguity in the table.- Hide quoted text -

- Show quoted text -


I agree there is no abiguity in the table. The problem is the table
applies to circuits with two or more receptacles and we are talking
about a circuit with just one.

210.21 (B) (3)
Receptacle Ratings. Where connected to a branch circuit supplying TWO
OR MORE receptacles or outlets, receptacle ratings shall conform to
the values listed in Table 210.21 (B) (3)....



Here;s the section that covers the single receptacle:

21210.21 (B) (1)
Single receptacle on an individual branch circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.



  #43   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default 15A outlets on 20A circuits


wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 10:47 pm, (Doug Miller) wrote:

In article
,
wrote:


And I have to disagree on that one. I can find the code section for
you later,


Yeah, you do that. We'll wait.


You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.







but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.


Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.


But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.


It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.


Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?



Hence, a 20A single outlet can be use on a 15
amp circuit.


No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".


Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:

"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"

The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.



I agree that it doesn't make any sense to me.


Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.


Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.

I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -



That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.

It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.

I see what you're reading, but there is no text that says any receptacle,
single or duplex, can have a rating higher than the circuit feeding it.


  #44   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default 15A outlets on 20A circuits


wrote in message
...
On Oct 12, 6:41 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 7:56 am, "RBM" wrote:





"RBM" wrote in message


...


"Mikepier" wrote in message
...
Last week, I posted about running 12/2 wire for a kitchen reno. Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.


I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.


15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected, but all the counter outlets do. A 15 amp GFCI outlet has a
20
amp feed through


Just to clarify. A single 15 amp outlet can't be installed on a 20 amp
dedicated circuit, but a duplex is fine


- Hide quoted text -


- Show quoted text -- Hide quoted text -


- Show quoted text -


This is another example of things in the code that don't seem to make
any sense, at least to me. If one can install multiple 15 amp
outlets on a 20 amp circuit, why the restriction on installing just
one?

And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit, but you can't install multiple 20's on a
15 amp circuit.

Why the big distinction between single versus multiple outlets?

The feed through of a 15 amp outlet is 20 amps. You cannot install a 20
amp
outlet on a 15 amp circuit Nec 210.21 B3- Hide quoted text -

- Show quoted text -



Again, here's what the section you are referring to says. From 2008
NEC,

210.21 (B) (3)
Receptacle Ratings. Where connected to a branch circuit supplying TWO
OR MORE receptacles or outlets, receptacle ratings shall conform to
the values listed in Table 210.21 (B) (3)....


The added emphasis is mine. We are talking about a SINGLE receptacle,
so that section and it's table do not apply. Section 210.21 (B) (1),
which preceeds it, specifically addresses the case of a single
receptacle.

21210.21 (B) (1)
Single receptacle on an individual branch circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


Do you not agree that a single 20 amp outlet on a 15 amp circuit meets
that requirement? Note that I'm not saying it makes sense to me, but
it's clearly what it says.

No, I respect your logic, but I think that the Nec is written in an often
incoherent legalese, which is why I use the handbook. It says that it can't
be less than, but it doesn't say that it can be greater than. I think from
a practical perspective, one should be able to expect a 20 amp receptacle to
be fed by a 20 amp circuit



  #46   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default 15A outlets on 20A circuits

In article , wrote:
On Wed, 13 Oct 2010 02:49:40 GMT,
(Doug Miller)
wrote:

In article , bud--

wrote:

Most of the thread uses 210.21. It says what you say above, which I
agree is odd.


No, it doesn't. Read Table 210.21(B)(3). The permitted receptacle ratings on a


15A circuit are "not over 15". On a 20A circuit, it's "15 or 20".

A while back I ran across 406.3-A which, IMHO, prohibits almost all 20A
single receptacles on a 15A circuit:


Never mind that. Table 210.21(B)(3) prohibits *all* 20A receptacles, single or


duplex, on a 15A circuit.

15/20A receptacles "shall be installed only on circuits of the voltage
class and current for which they are rated." This applies only to
"grounding-type" receptacles, so you presumably could put an ungrounded
20A single receptacle as the only receptacle on a 15A circuit (and only
in those cases where you can use an ungrounded receptacle). Oddness
remains, but is greatly limited.


No, you can't. 15A circuits may not have receptacles rated over 15A. Period.
There are no exceptions.

When you lookk at it logically - from an electrical point of view -
it would make more sense to allow a 20 amp receptacle on a 15 amp
circuit than the other way around. Look at it from this point of view.
A 20 amp receptacle ic designed to handle 20 amp loads - on a 15 amp
circuit it is protected to 15 amps. This is definitely safe as nothing
can operate above its rated or protected current .


No, it is not "definitely safe". It's of questionable safety at best

A 15 amp receptacle is designed for a 15 amp load and when installed
on a 20 amp circuit is protected at 20 amps and wired with wiring that
is rated at 20 amps. The receptacle is now the week link, and being
somewhat resistive in nature it is succeptible to overload damage if a
load plugged into it draws more than it's rated current - as it is
"protected" to a current higher than its rating.. This definitely has
the possibility of being unsafe as the receptacle can operate above
its rated current.

No, it can't, because any device that draws enough current to overload a 15A
circuit is not permitted to have a plug that will fit into a 15A receptacle.
It will have a plug that fits only into 20A receptacles. That's why a 20A
receptacle has a different configuration.
  #48   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default 15A outlets on 20A circuits

On Wed, 13 Oct 2010 18:41:13 -0400, "RBM" wrote:


wrote in message
.. .
On Wed, 13 Oct 2010 02:36:56 GMT, (Doug Miller)
wrote:

In article
,
wrote:

And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit,

It says no such thing.

If it is fused at 15 amps it doesn't matter what kind of plug is on
the end (as long as it is rated for at LEAST 15 amps - the circuit is
protected. - code issues - if any- aside.


According to the article it does matter. First of all, in legalese, saying
"not less than" doesn't mean that it can be greater than. It just can't be
less than. Second, the table in the same article shows that a receptacle on
a 15 amp circuit cant' be rated over 15 amps.
Personally, I'd like to know that if I have an appliance that has a 20 amp
plug on it, and I find a 20 amp receptacle that I can plug it into, a 15 amp
breaker isn't limiting the current.

You don't understand english very well - particularly when boolian
logic is involved.

"not less than" means exactly that. Equal to or greater than equals
not less than. PERIOD.

And a 15 amp breaker does not LIMIT current - it interrupts current
when current excedes the limit.
Limitting current would controll the current by reducing voltage to
hold the current to the maximum limit.

A 20 amp 115/125 volt receptacle also accepts 15 amp plugs perfectly.
  #50   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default 15A outlets on 20A circuits

On Wed, 13 Oct 2010 16:33:24 -0700 (PDT), wrote:

On Oct 13, 5:42Â*pm, "RBM" wrote:
wrote in message

...
On Oct 12, 10:47 pm, (Doug Miller) wrote:

In article
,
wrote:


And I have to disagree on that one. I can find the code section for
you later,


Yeah, you do that. We'll wait.


You didn't have to wait long. Â* Here it is. Â*No need to get sarcastic
and snippy.

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

That is clear as day. Â*A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. Â*If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.







but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.


Wrong. It says you can't use a 20A outlet on a 15A circuit, period. You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases, without
regard to how many there are.


But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.


It says no such thing. It is, for example, a violation to put a 50A outlet
on
a 20A circuit.


Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?



Hence, a 20A single outlet can be use on a 15
amp circuit.


No, it cannot. Look at Table 210.21(B)(3), where it lists the permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating is
"not over 15".


Yes, let's look at that section. Â* In the same section where it starts
to explain those tables it starts off with:

"210.21(B)(3) Receptacle Ratings. Â*Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"

The added emphasis is mine. Â*Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.



I agree that it doesn't make any sense to me.


Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.


Actually it's quite clear that you're the one who's wrong here. Â* A
simple admission to that and apollogy for getting snippy will suffice.

I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -



That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.

It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.

It actually makes a lot of sense, as I stated in an earlier post.
What does NOT make any sense is a 15 amp plug on a 20 amp circuit


  #51   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default 15A outlets on 20A circuits

On Wed, 13 Oct 2010 20:02:46 -0400, "RBM" wrote:


wrote in message
...
On Oct 12, 6:41 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 7:56 am, "RBM" wrote:





"RBM" wrote in message


...


"Mikepier" wrote in message
...
Last week, I posted about running 12/2 wire for a kitchen reno. Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.


I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.


15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected, but all the counter outlets do. A 15 amp GFCI outlet has a
20
amp feed through


Just to clarify. A single 15 amp outlet can't be installed on a 20 amp
dedicated circuit, but a duplex is fine


- Hide quoted text -


- Show quoted text -- Hide quoted text -


- Show quoted text -


This is another example of things in the code that don't seem to make
any sense, at least to me. If one can install multiple 15 amp
outlets on a 20 amp circuit, why the restriction on installing just
one?

And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit, but you can't install multiple 20's on a
15 amp circuit.

Why the big distinction between single versus multiple outlets?

The feed through of a 15 amp outlet is 20 amps. You cannot install a 20
amp
outlet on a 15 amp circuit Nec 210.21 B3- Hide quoted text -

- Show quoted text -



Again, here's what the section you are referring to says. From 2008
NEC,

210.21 (B) (3)
Receptacle Ratings. Where connected to a branch circuit supplying TWO
OR MORE receptacles or outlets, receptacle ratings shall conform to
the values listed in Table 210.21 (B) (3)....


The added emphasis is mine. We are talking about a SINGLE receptacle,
so that section and it's table do not apply. Section 210.21 (B) (1),
which preceeds it, specifically addresses the case of a single
receptacle.

21210.21 (B) (1)
Single receptacle on an individual branch circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


Do you not agree that a single 20 amp outlet on a 15 amp circuit meets
that requirement? Note that I'm not saying it makes sense to me, but
it's clearly what it says.

No, I respect your logic, but I think that the Nec is written in an often
incoherent legalese, which is why I use the handbook. It says that it can't
be less than, but it doesn't say that it can be greater than. I think from
a practical perspective, one should be able to expect a 20 amp receptacle to
be fed by a 20 amp circuit


Not reasonable.
You have a multibranch 15 amp circuit with 4 duplex 15 amp
receptacles. You think it is only reasonable to expect to be able to
plug 8 15 amp devices into the circuit??
Give your head a shake.
  #52   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default 15A outlets on 20A circuits


wrote in message
news
On Wed, 13 Oct 2010 20:02:46 -0400, "RBM" wrote:


wrote in message
...
On Oct 12, 6:41 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 7:56 am, "RBM" wrote:





"RBM" wrote in message

...

"Mikepier" wrote in message
...
Last week, I posted about running 12/2 wire for a kitchen reno.
Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.

I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the
fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.

15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected, but all the counter outlets do. A 15 amp GFCI outlet has
a
20
amp feed through

Just to clarify. A single 15 amp outlet can't be installed on a 20 amp
dedicated circuit, but a duplex is fine

- Hide quoted text -

- Show quoted text -- Hide quoted text -

- Show quoted text -

This is another example of things in the code that don't seem to make
any sense, at least to me. If one can install multiple 15 amp
outlets on a 20 amp circuit, why the restriction on installing just
one?

And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit, but you can't install multiple 20's on a
15 amp circuit.

Why the big distinction between single versus multiple outlets?

The feed through of a 15 amp outlet is 20 amps. You cannot install a 20
amp
outlet on a 15 amp circuit Nec 210.21 B3- Hide quoted text -

- Show quoted text -



Again, here's what the section you are referring to says. From 2008
NEC,

210.21 (B) (3)
Receptacle Ratings. Where connected to a branch circuit supplying TWO
OR MORE receptacles or outlets, receptacle ratings shall conform to
the values listed in Table 210.21 (B) (3)....


The added emphasis is mine. We are talking about a SINGLE receptacle,
so that section and it's table do not apply. Section 210.21 (B) (1),
which preceeds it, specifically addresses the case of a single
receptacle.

21210.21 (B) (1)
Single receptacle on an individual branch circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


Do you not agree that a single 20 amp outlet on a 15 amp circuit meets
that requirement? Note that I'm not saying it makes sense to me, but
it's clearly what it says.

No, I respect your logic, but I think that the Nec is written in an often
incoherent legalese, which is why I use the handbook. It says that it
can't
be less than, but it doesn't say that it can be greater than. I think
from
a practical perspective, one should be able to expect a 20 amp receptacle
to
be fed by a 20 amp circuit


Not reasonable.
You have a multibranch 15 amp circuit with 4 duplex 15 amp
receptacles. You think it is only reasonable to expect to be able to
plug 8 15 amp devices into the circuit??
Give your head a shake.


No, but I would expect to be able to plug in one 15 amp device, and I would
be correct, unlike having a 20 amp receptacle on a 15 amp circuit, where the
same expectation wouldn't be met. Must just be my Boolean logic


  #53   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default 15A outlets on 20A circuits

On Thu, 14 Oct 2010 01:10:34 GMT, (Doug Miller)
wrote:

In article ,
wrote:
On Wed, 13 Oct 2010 02:49:40 GMT,
(Doug Miller)
wrote:

In article , bud--

wrote:

Most of the thread uses 210.21. It says what you say above, which I
agree is odd.

No, it doesn't. Read Table 210.21(B)(3). The permitted receptacle ratings on a


15A circuit are "not over 15". On a 20A circuit, it's "15 or 20".

A while back I ran across 406.3-A which, IMHO, prohibits almost all 20A
single receptacles on a 15A circuit:

Never mind that. Table 210.21(B)(3) prohibits *all* 20A receptacles, single or


duplex, on a 15A circuit.

15/20A receptacles "shall be installed only on circuits of the voltage
class and current for which they are rated." This applies only to
"grounding-type" receptacles, so you presumably could put an ungrounded
20A single receptacle as the only receptacle on a 15A circuit (and only
in those cases where you can use an ungrounded receptacle). Oddness
remains, but is greatly limited.

No, you can't. 15A circuits may not have receptacles rated over 15A. Period.
There are no exceptions.

When you lookk at it logically - from an electrical point of view -
it would make more sense to allow a 20 amp receptacle on a 15 amp
circuit than the other way around. Look at it from this point of view.
A 20 amp receptacle ic designed to handle 20 amp loads - on a 15 amp
circuit it is protected to 15 amps. This is definitely safe as nothing
can operate above its rated or protected current .


No, it is not "definitely safe". It's of questionable safety at best


You obviously do not understand electrical theory any more than you
understand the code book.

You explain to me how a 20 amp receptacle on a 15 amp fused/protected
circuit is a safety issue.

Give it your best crack.

A 15 amp receptacle is designed for a 15 amp load and when installed
on a 20 amp circuit is protected at 20 amps and wired with wiring that
is rated at 20 amps. The receptacle is now the week link, and being
somewhat resistive in nature it is succeptible to overload damage if a
load plugged into it draws more than it's rated current - as it is
"protected" to a current higher than its rating.. This definitely has
the possibility of being unsafe as the receptacle can operate above
its rated current.

No, it can't, because any device that draws enough current to overload a 15A
circuit is not permitted to have a plug that will fit into a 15A receptacle.
It will have a plug that fits only into 20A receptacles. That's why a 20A
receptacle has a different configuration.

No, you are wrong. 100%
The fuse is their to prevent damage due to, and protect against FAULT
CURRENT. Any device, irregardless of it's rating, can draw excessive
current due to a FAULT. And a 15 amp plug fits a 20 amp receptacle.

By your logic, twisted as it is, all 15 amp receptacles on a
multi-branch circuit would have to be designed, built, and installed
in such a way that if anything was plugged into one receptacle drawing
close to 15 amps (or anything with a 15 amp plug, for that matter) ,
it would be impossible to plug anything else into any other receptacle
on the circuit.

That's not the way it works (thankfully), nor should it.

The "ring wiring" system used (at least untill recently) in brittain
and some parts of europe makes sense, with fused outlets. There is
also a proposed standard (smart home) that would have each plug
identify the rated current of the device and centrally monitor the
current draw, shutting the device down if current ratings are exceded
without shutting down anything else. This system uses RFID chips for
identity - and yes - it IS being worked on - I know one of the
engineers involved in the project.
  #54   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,733
Default 15A outlets on 20A circuits

On 10/13/2010 4:44 PM, RBM wrote:
"Steve wrote in message
...
On 10/13/2010 9:35 AM, bud-- wrote:
Steve Barker wrote:
On 10/12/2010 6:29 PM, RBM wrote:
wrote in message
...
On Tue, 12 Oct 2010 07:55:15 -0400, wrote:


wrote in message
...

Last week, I posted about running 12/2 wire for a kitchen reno. Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.

I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the
fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.

15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected,
but all the counter outlets do. A 15 amp GFCI outlet has a 20 amp
feed
through


He is NOT using a GFCI on the fridge. Read it again.
NEVER use a GFCI on a fridge or freezer.

I misread that, but just for clarification, the Nec requires GFCI
protection
by receptacle location, not by what you're planning to plug into the
outlet.
Every receptacle in a garage, or unfinished part of a basement
requires GFCI
protection, even if you plan to plug in a fridge or freezer


UNLESS.... there's always an exception.


All but one of the exceptions disappeared in the 2008 NEC. (The
remaining one is for alarm panels.)

The NEC panel does not see a problem with refrigeration on GFCI. In
commercial kitchens plug-in refrigeration (15/20A, 120V) is required to
be on GFCIs. The UL allowed leakage is around 0.5mA if I remember right.


I only know what my local AHJ goes by. And that is the 2005 version. They
just switched (last year) from the 1994 version. I'm sure there'll be no
switching again for quite some time.G

Also, i think some of the confusion comes from the interpretation of the
term "single outlet". SINGLE outlet does NOT mean a duplex outlet. And
SINGLE (non gfci) outlets are allowed in basement and garages on a circuit
for sump pumps and refrigerators. Whereas nothing else can be plugged
into them without unplugging the device the outlet was intended for. Has
this been eliminated for the 2008 version?

--
Steve Barker
remove the "not" from my address to email


Yes it has. There are no longer any exceptions



guess i'll be breaking that rule then. I will NOT put a sump pump on a
gfci. period.

--
Steve Barker
remove the "not" from my address to email
  #56   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default 15A outlets on 20A circuits

On Wed, 13 Oct 2010 22:21:22 -0400, "RBM" wrote:


wrote in message
news
On Wed, 13 Oct 2010 20:02:46 -0400, "RBM" wrote:


wrote in message
...
On Oct 12, 6:41 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 7:56 am, "RBM" wrote:





"RBM" wrote in message

...

"Mikepier" wrote in message
...
Last week, I posted about running 12/2 wire for a kitchen reno.
Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.

I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the
fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.

15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected, but all the counter outlets do. A 15 amp GFCI outlet has
a
20
amp feed through

Just to clarify. A single 15 amp outlet can't be installed on a 20 amp
dedicated circuit, but a duplex is fine

- Hide quoted text -

- Show quoted text -- Hide quoted text -

- Show quoted text -

This is another example of things in the code that don't seem to make
any sense, at least to me. If one can install multiple 15 amp
outlets on a 20 amp circuit, why the restriction on installing just
one?

And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit, but you can't install multiple 20's on a
15 amp circuit.

Why the big distinction between single versus multiple outlets?

The feed through of a 15 amp outlet is 20 amps. You cannot install a 20
amp
outlet on a 15 amp circuit Nec 210.21 B3- Hide quoted text -

- Show quoted text -


Again, here's what the section you are referring to says. From 2008
NEC,

210.21 (B) (3)
Receptacle Ratings. Where connected to a branch circuit supplying TWO
OR MORE receptacles or outlets, receptacle ratings shall conform to
the values listed in Table 210.21 (B) (3)....


The added emphasis is mine. We are talking about a SINGLE receptacle,
so that section and it's table do not apply. Section 210.21 (B) (1),
which preceeds it, specifically addresses the case of a single
receptacle.

21210.21 (B) (1)
Single receptacle on an individual branch circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


Do you not agree that a single 20 amp outlet on a 15 amp circuit meets
that requirement? Note that I'm not saying it makes sense to me, but
it's clearly what it says.

No, I respect your logic, but I think that the Nec is written in an often
incoherent legalese, which is why I use the handbook. It says that it
can't
be less than, but it doesn't say that it can be greater than. I think
from
a practical perspective, one should be able to expect a 20 amp receptacle
to
be fed by a 20 amp circuit


Not reasonable.
You have a multibranch 15 amp circuit with 4 duplex 15 amp
receptacles. You think it is only reasonable to expect to be able to
plug 8 15 amp devices into the circuit??
Give your head a shake.


No, but I would expect to be able to plug in one 15 amp device, and I would
be correct, unlike having a 20 amp receptacle on a 15 amp circuit, where the
same expectation wouldn't be met. Must just be my Boolean logic

lots of 20 amp plugged devices will actually run on 15 amps under
"normal" conditions but can draw up to 20 (or even more) under
cold-start or other special, but not fault, conditions.

And you can ONLY expect to plug in one 15 amp device if it is a
DEDICATED outlet. - which is the only time a 20 amp receptacle IS
allowed on a 15 amp circuit under current code.
  #57   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 13, 8:49*pm, (Doug Miller) wrote:
In article , wrote:

On Oct 12, 10:36=A0pm, (Doug Miller) wrote:
In article .=

com, wrote:


And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit,


It says no such thing.


Actually it does:


It does not.



" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."


You stopped reading too soon. Table 210.21(B)(3) specifically lists the
permissible rating of receptacles on a 15A circuit as "not over 15A".


It's you who either can't read, or more likely, as usually, will not
simply admit that there was something that you didn't know about and
were wrong. I already pointed out that the table you are referring
to, Table 210.21(B)(3), DOES NOT APPLY because it starts off by
clearly saying right there in plain English that the table applies to
circuits with TWO OR MORE receptacles. You do understand that TWO
receptacles is not the same thing as ONE receptacle, don;t you?

Here again is what you are relying on to make your case:


"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"



We are talking about a SINGLE receptacle. The rules for receptacles
are clearly seperated in the NEC into two cases, circuits with single
receptacles and circuits with multiple receptacles. Multiple outlets
are covered by the section with the table you keep trying to use.
The code covers single outlets in the section just before it, 210.21(B)
(1):

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."


Since 20 amps is greater than 15 amps, the 20 amp receptacle may be
used
on a circuit where it is the only receptacle. Following your process,
one coud use a table in the code that says it applies to circuits less
than 600 volts and apply it to circuits over 600 volts or vice
versa. Somehow I think it doesn't work that way. Anyone who wants
to read the sections in the actual NEC, and make up their own minds,
which I encourage, it's available online he


http://www.nfpa.org/aboutthecodes/Ab...&EditionID=238

It's a good resource for everyone to have. After you have the book
open, click on the TOC button in the lower left to bring up the table
of contents, then go to section 2, flip through a few pages until you
get to 210.21 It's all there in a few short, clear paragraphs.






  #58   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 13, 10:08*pm, "RBM" wrote:
wrote in message

...





On Wed, 13 Oct 2010 16:30:46 -0400, wrote:


On Wed, 13 Oct 2010 14:29:30 -0500, wrote:


For example, they even put a green ground screw on switches
now. *WHY? *If the switch is in a metal box, it's grounded by the
screws, but even in a plastic box, that small piece of metal on the
front of the switch is covered by a plastic plate.


You are only properly grounded in a metal box if the device is listed
as self grounding (a spring or brass clip on the yoke)
In a plastic box, there is no guarantee the plate will be plastic and
you still have metal screws. Before the grounded switches, *they only
allowed plastic screws on switch plates but that rule was not followed
much either


.In almost 60 years I've NEVER seen a plastic plate screw.


They do exist:http://www.mcfeelys.com/product/0610...Switchplat...- Hide quoted text -

- Show quoted text -


Yes, I've seen and used plastic plate screws too.
  #59   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 13, 6:41*pm, "RBM" wrote:
wrote in message

...

On Wed, 13 Oct 2010 02:36:56 GMT, (Doug Miller)
wrote:


In article
,
wrote:


And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit,


It says no such thing.

If it is fused at 15 amps it doesn't matter what kind of plug is on
the end (as long as it is rated for at LEAST 15 amps - the circuit is
protected. - code issues - if any- aside.


According to the article it does matter. First of all, in legalese, saying
"not less than" doesn't mean that it can be greater than. It just can't be
less than.


This isn't much of a case of legalese, which is usually used to refer
to long, winding sentences that are difficult to decipher. This is
one short, direct sentence. Saying it can't be "less than" leaves
open exactly two possibilities:

A - It can equal to

B - It can be greater than

Either of those options is valid and not restricted. If they wanted
to retrict it to just A, all they had to do was say the receptacle has
to be equal to the circuit rating.

Let's take some other examples. Suppose the law says that on a
certain section of road you must maintain a vehicle speed not less
than 40MPH. Would you argue they mean I can't drive at 55MPH? Or
that a section of the plumbing code says a pipe must be rated not less
than 160 PSI. Does that mean I can't use a pipe rated at 250 PSI ?







Second, the table in the same article shows that a receptacle on
a 15 amp circuit cant' be rated over 15 amps.
Personally, I'd like to know that if I have an appliance that has a 20 amp
plug on it, and I find a 20 amp receptacle that I can plug it into, a 15 amp
breaker isn't limiting the current.


On that I agree with you 100%, which is why I brought up the issue in
the first place. Like you and I think 99% of the rest of the world, I
would not put a 20 amp receptacle on any 15 amp circuit, as at the
very least, it leads to confusion.
  #60   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default 15A outlets on 20A circuits

RBM wrote:
wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 10:47 pm, (Doug Miller) wrote:

In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.

You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.







but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.

Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?



Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".

Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:

"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"

The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.



I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.

Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.

I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -



That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.

It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.

I see what you're reading, but there is no text that says any receptacle,
single or duplex, can have a rating higher than the circuit feeding it.




  #61   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default 15A outlets on 20A circuits

wrote:
On Thu, 14 Oct 2010 01:10:34 GMT,
(Doug Miller)
wrote:

In article ,
wrote:
On Wed, 13 Oct 2010 02:49:40 GMT,
(Doug Miller)
wrote:

In article , bud--
wrote:
Most of the thread uses 210.21. It says what you say above, which I
agree is odd.
No, it doesn't. Read Table 210.21(B)(3). The permitted receptacle ratings on a
15A circuit are "not over 15". On a 20A circuit, it's "15 or 20".
A while back I ran across 406.3-A which, IMHO, prohibits almost all 20A
single receptacles on a 15A circuit:
Never mind that. Table 210.21(B)(3) prohibits *all* 20A receptacles, single or
duplex, on a 15A circuit.

15/20A receptacles "shall be installed only on circuits of the voltage
class and current for which they are rated." This applies only to
"grounding-type" receptacles, so you presumably could put an ungrounded
20A single receptacle as the only receptacle on a 15A circuit (and only
in those cases where you can use an ungrounded receptacle). Oddness
remains, but is greatly limited.
No, you can't. 15A circuits may not have receptacles rated over 15A. Period.
There are no exceptions.
When you lookk at it logically - from an electrical point of view -
it would make more sense to allow a 20 amp receptacle on a 15 amp
circuit than the other way around. Look at it from this point of view.
A 20 amp receptacle ic designed to handle 20 amp loads - on a 15 amp
circuit it is protected to 15 amps. This is definitely safe as nothing
can operate above its rated or protected current .

No, it is not "definitely safe". It's of questionable safety at best


You obviously do not understand electrical theory any more than you
understand the code book.

You explain to me how a 20 amp receptacle on a 15 amp fused/protected
circuit is a safety issue.

Give it your best crack.


trader already did in a perfectly good answer (below).

A 15 amp receptacle is designed for a 15 amp load and when installed
on a 20 amp circuit is protected at 20 amps and wired with wiring that
is rated at 20 amps. The receptacle is now the week link, and being
somewhat resistive in nature it is succeptible to overload damage if a
load plugged into it draws more than it's rated current - as it is
"protected" to a current higher than its rating.. This definitely has
the possibility of being unsafe as the receptacle can operate above
its rated current.

No, it can't, because any device that draws enough current to overload a 15A
circuit is not permitted to have a plug that will fit into a 15A receptacle.
It will have a plug that fits only into 20A receptacles. That's why a 20A
receptacle has a different configuration.

No, you are wrong. 100%
The fuse is their to prevent damage due to, and protect against FAULT
CURRENT. Any device, irregardless of it's rating, can draw excessive
current due to a FAULT.


What a brilliant idea. We can ignore current trips at a little over the
circuit rating and just trip on fault current - maybe 80A and higher.


By your logic, twisted as it is, all 15 amp receptacles on a
multi-branch circuit would have to be designed, built, and installed
in such a way that if anything was plugged into one receptacle drawing
close to 15 amps (or anything with a 15 amp plug, for that matter) ,
it would be impossible to plug anything else into any other receptacle
on the circuit.


I posted earlier that a 15A duplex receptacle is rated for a total 20A
in both halves.

There have been a couple posts that a 15A receptacle is rated 20A
wire-through.


That's not the way it works (thankfully), nor should it.


You appear to have little idea of "the way it works". Perhaps the cold
electrons in Canada behave differently.

Else you should stick to cars. There is no shock hazard and less to burn
down.

--
bud--
  #62   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default 15A outlets on 20A circuits

RBM wrote:
wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 10:47 pm, (Doug Miller) wrote:

In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.

You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.







but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.

Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?



Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".

Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:

"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"

The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.



I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.

Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.

I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -



That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.

It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A circuit

But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.

Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).


I see what you're reading, but there is no text that says any receptacle,
single or duplex, can have a rating higher than the circuit feeding it.


[RBM]
There is text that you can put a 20A receptacle on a 15A circuit.

There is no text in 210 that you can't have a higher rating, like 20A
(or 50A, or 100A) as the single receptacle.

There is text in 406.3 that you can't put a 20A receptacle on a 15A
circuit. This is what we all (except one) expect.

--
bud--
  #63   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default 15A outlets on 20A circuits

wrote:
On Wed, 13 Oct 2010 22:21:22 -0400, "RBM" wrote:

wrote in message
news
On Wed, 13 Oct 2010 20:02:46 -0400, "RBM" wrote:

wrote in message
...
On Oct 12, 6:41 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 7:56 am, "RBM" wrote:





"RBM" wrote in message
...
"Mikepier" wrote in message
...
Last week, I posted about running 12/2 wire for a kitchen reno.
Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.
I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the
fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.
15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected, but all the counter outlets do. A 15 amp GFCI outlet has
a
20
amp feed through
Just to clarify. A single 15 amp outlet can't be installed on a 20 amp
dedicated circuit, but a duplex is fine
- Hide quoted text -
- Show quoted text -- Hide quoted text -
- Show quoted text -
This is another example of things in the code that don't seem to make
any sense, at least to me. If one can install multiple 15 amp
outlets on a 20 amp circuit, why the restriction on installing just
one?

And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit, but you can't install multiple 20's on a
15 amp circuit.

Why the big distinction between single versus multiple outlets?

The feed through of a 15 amp outlet is 20 amps. You cannot install a 20
amp
outlet on a 15 amp circuit Nec 210.21 B3- Hide quoted text -

- Show quoted text -

Again, here's what the section you are referring to says. From 2008
NEC,

210.21 (B) (3)
Receptacle Ratings. Where connected to a branch circuit supplying TWO
OR MORE receptacles or outlets, receptacle ratings shall conform to
the values listed in Table 210.21 (B) (3)....


The added emphasis is mine. We are talking about a SINGLE receptacle,
so that section and it's table do not apply. Section 210.21 (B) (1),
which preceeds it, specifically addresses the case of a single
receptacle.

21210.21 (B) (1)
Single receptacle on an individual branch circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


Do you not agree that a single 20 amp outlet on a 15 amp circuit meets
that requirement? Note that I'm not saying it makes sense to me, but
it's clearly what it says.

No, I respect your logic, but I think that the Nec is written in an often
incoherent legalese, which is why I use the handbook. It says that it
can't
be less than, but it doesn't say that it can be greater than. I think
from
a practical perspective, one should be able to expect a 20 amp receptacle
to
be fed by a 20 amp circuit


Not reasonable.
You have a multibranch 15 amp circuit with 4 duplex 15 amp
receptacles. You think it is only reasonable to expect to be able to
plug 8 15 amp devices into the circuit??
Give your head a shake.

No, but I would expect to be able to plug in one 15 amp device, and I would
be correct, unlike having a 20 amp receptacle on a 15 amp circuit, where the
same expectation wouldn't be met. Must just be my Boolean logic

lots of 20 amp plugged devices will actually run on 15 amps under
"normal" conditions but can draw up to 20 (or even more) under
cold-start or other special, but not fault, conditions.


Maybe circuit breakers could include a feature that gives a delayed trip
for motor starting current and incandescent inrush. Oh, wait, every
circuit breaker already has that feature. And a lot of fuses.

And a device is not rated 20A because of momentary conditions. It is
rated 20A (or over 15A) because that is what it draws under normal
conditions.


And you can ONLY expect to plug in one 15 amp device if it is a
DEDICATED outlet. - which is the only time a 20 amp receptacle IS
allowed on a 15 amp circuit under current code.


Maybe you can in Canada, but in the US you can' install a 20A receptacle
on a 15A circuit (406.3-B).

--
bud--
  #65   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 14, 11:53*am, bud-- wrote:
RBM wrote:
wrote in message
....
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message


....
On Oct 12, 10:47 pm, (Doug Miller) wrote:


In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.


" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."


That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.


but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?


Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:


"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"


The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.


I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.


I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -


That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. *If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. * And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.


It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A circuit

But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.

Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).



I see what you're reading, but there is no text that says any receptacle,
single or duplex, can have a rating higher than the circuit feeding it.


[RBM]
There is text that you can put a 20A receptacle on a 15A circuit.

There is no text in 210 that you can't have a higher rating, like 20A
(or 50A, or 100A) as the single receptacle.

There is text in 406.3 that you can't put a 20A receptacle on a 15A
circuit. This is what we all (except one) expect.

--
bud--- Hide quoted text -

- Show quoted text -


I don't think the issue ever was what we expect. I would not have
expected the code to allow a 20 amp receptacle on a 15 amp circuit
either, which is why I brought it up in the first place. I also would
not wire a circuit that way, because it's misleading at best. But
what one expects and what is actually written in the code can be two
different things.

I think there are actually three differing opinions on this subject.
It looks like cl and I read the code as allowing a single 20 amp
receptacle on a 15 amp circuit. Doug makes the claim, which I think
is totally bogus, that the table in 210.21 (B) (3) says it is not
allowed. But that is just plain wrong, because that table is
preceeded by verbage that says it applies to circuits with two or more
receptacles. I believe you and I agree on that point.

Then there is your position, which is that while not prohibited by
section 210, it is prohibited by 406.3. That is a new point, which I
had never heard used before. But let;s look at what that says. It
doesn't actually say you can't put a 20A receptacle on a 15A
circuit. What it says is this:

406.3 (A)

"Grounding type receptacles shall be installed only on circuits of the
voltage class and current for which they are rated, except as provided
in Table 210.21 (B)(2) and Table 210.21(B)(3)."


A 20A receptable is rated to handle 0 through 20 amps of current. A
15 amp circuit falls in that range, so I would interpret the above to
mean that the 20A receptacle is permitted. Especially in view of the
fact that when they specifically address the issue of a single outlet
they could have just said that in the case of a single outlet you must
use a receptacle with a rating equal to the circuit, but they did not
and instead said this:

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


Suppose instead of talking about receptacles, 406.3 talked about wire
and said wire gauge shall only be installed on circuits of the voltage
class and current for which it is rated. Would that mean that I
couldn't use 12 gauge wire on a 15 amp circuit?


  #66   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default 15A outlets on 20A circuits

On Thu, 14 Oct 2010 10:46:04 -0500, bud--
wrote:

wrote:
On Thu, 14 Oct 2010 01:10:34 GMT, (Doug Miller)
wrote:

In article ,
wrote:
On Wed, 13 Oct 2010 02:49:40 GMT,
(Doug Miller)
wrote:

In article , bud--
wrote:
Most of the thread uses 210.21. It says what you say above, which I
agree is odd.
No, it doesn't. Read Table 210.21(B)(3). The permitted receptacle ratings on a
15A circuit are "not over 15". On a 20A circuit, it's "15 or 20".
A while back I ran across 406.3-A which, IMHO, prohibits almost all 20A
single receptacles on a 15A circuit:
Never mind that. Table 210.21(B)(3) prohibits *all* 20A receptacles, single or
duplex, on a 15A circuit.

15/20A receptacles "shall be installed only on circuits of the voltage
class and current for which they are rated." This applies only to
"grounding-type" receptacles, so you presumably could put an ungrounded
20A single receptacle as the only receptacle on a 15A circuit (and only
in those cases where you can use an ungrounded receptacle). Oddness
remains, but is greatly limited.
No, you can't. 15A circuits may not have receptacles rated over 15A. Period.
There are no exceptions.
When you lookk at it logically - from an electrical point of view -
it would make more sense to allow a 20 amp receptacle on a 15 amp
circuit than the other way around. Look at it from this point of view.
A 20 amp receptacle ic designed to handle 20 amp loads - on a 15 amp
circuit it is protected to 15 amps. This is definitely safe as nothing
can operate above its rated or protected current .
No, it is not "definitely safe". It's of questionable safety at best


You obviously do not understand electrical theory any more than you
understand the code book.

You explain to me how a 20 amp receptacle on a 15 amp fused/protected
circuit is a safety issue.

Give it your best crack.


trader already did in a perfectly good answer (below).


I don't see anything SAFETY relatee anywhere in trader's post. All
he's talking is inconvenience.

A 15 amp receptacle is designed for a 15 amp load and when installed
on a 20 amp circuit is protected at 20 amps and wired with wiring that
is rated at 20 amps. The receptacle is now the week link, and being
somewhat resistive in nature it is succeptible to overload damage if a
load plugged into it draws more than it's rated current - as it is
"protected" to a current higher than its rating.. This definitely has
the possibility of being unsafe as the receptacle can operate above
its rated current.

No, it can't, because any device that draws enough current to overload a 15A
circuit is not permitted to have a plug that will fit into a 15A receptacle.
It will have a plug that fits only into 20A receptacles. That's why a 20A
receptacle has a different configuration.

No, you are wrong. 100%
The fuse is their to prevent damage due to, and protect against FAULT
CURRENT. Any device, irregardless of it's rating, can draw excessive
current due to a FAULT.


What a brilliant idea. We can ignore current trips at a little over the
circuit rating and just trip on fault current - maybe 80A and higher.


By your logic, twisted as it is, all 15 amp receptacles on a
multi-branch circuit would have to be designed, built, and installed
in such a way that if anything was plugged into one receptacle drawing
close to 15 amps (or anything with a 15 amp plug, for that matter) ,
it would be impossible to plug anything else into any other receptacle
on the circuit.


I posted earlier that a 15A duplex receptacle is rated for a total 20A
in both halves.

Not germain to the discussion at hand. You guys seem to think it's
your "god given right" to expect to be able to plug a 15 amp device
into any 15 amp receptacle in a building and not have a breaker trip.

That can ONLY happen if every receptacle in the building is a split on
a double breaker. I only know of one house where that is the case -
every receptacle in the house is a 20 amp, separately supplied direct
from one of several 400 amp panels distributed throughout the house.
About half of them are also remotely switched. Took a very good
electrician several months to wire that monstrosity.

There have been a couple posts that a 15A receptacle is rated 20A
wire-through.


That's not the way it works (thankfully), nor should it.


You appear to have little idea of "the way it works". Perhaps the cold
electrons in Canada behave differently.

Else you should stick to cars. There is no shock hazard and less to burn
down.


  #67   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default 15A outlets on 20A circuits

On Thu, 14 Oct 2010 10:53:36 -0500, bud--
wrote:

RBM wrote:
wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 10:47 pm, (Doug Miller) wrote:

In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.







but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?



Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:

"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"

The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.



I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.

I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -



That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.

It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A circuit

But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.

Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).


A 20 amp receptacle is going to outlast even the hospital duty 15 amp
receptacle under moderate to heavy use. Absolutely no reason you
cannot use a 20 amp receptacle anywhere in your house that code allows
it, or anywhere in the house PERIOD if code is not in effect. Just
like there is nothing stopping you from using AWG 12 wiring throught
the entire house. The entire house can be wired for 20 amp circuits,
and protected by 15 amp breakers or fuses without posing ANY safety
issues. There will be cost issues, and IF you attempt to plug in a 20
amp device the breaker will eventually trip. The advantage is, all you
need to do is install a 20 amp breaker in place of the 15 and any
outlet in the house can instantly become a 20 amp circuit.

I see what you're reading, but there is no text that says any receptacle,
single or duplex, can have a rating higher than the circuit feeding it.


[RBM]
There is text that you can put a 20A receptacle on a 15A circuit.

There is no text in 210 that you can't have a higher rating, like 20A
(or 50A, or 100A) as the single receptacle.

There is text in 406.3 that you can't put a 20A receptacle on a 15A
circuit. This is what we all (except one) expect.


  #68   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default 15A outlets on 20A circuits


wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message

...
On Oct 12, 10:47 pm, (Doug Miller) wrote:

In article
,
wrote:


And I have to disagree on that one. I can find the code section for
you later,


Yeah, you do that. We'll wait.


You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.







but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.


Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.


But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.


It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.


Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?



Hence, a 20A single outlet can be use on a 15
amp circuit.


No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".


Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:

"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"

The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.



I agree that it doesn't make any sense to me.


Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.


Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.

I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -



That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.

It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


  #69   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default 15A outlets on 20A circuits


wrote in message
...
On Oct 14, 11:53 am, bud-- wrote:
RBM wrote:
wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message


...
On Oct 12, 10:47 pm, (Doug Miller) wrote:


In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.


" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."


That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.


but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A
outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?


Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle
rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:


"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"


The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.


I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.


I think the reason for that initial statement in the code, is because a
40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15
amp
circuit- Hide quoted text -


That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.


It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A
circuit

But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.

Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).



I see what you're reading, but there is no text that says any
receptacle,
single or duplex, can have a rating higher than the circuit feeding it.


[RBM]
There is text that you can put a 20A receptacle on a 15A circuit.

There is no text in 210 that you can't have a higher rating, like 20A
(or 50A, or 100A) as the single receptacle.

There is text in 406.3 that you can't put a 20A receptacle on a 15A
circuit. This is what we all (except one) expect.

--
bud--- Hide quoted text -

- Show quoted text -


I don't think the issue ever was what we expect. I would not have
expected the code to allow a 20 amp receptacle on a 15 amp circuit
either, which is why I brought it up in the first place. I also would
not wire a circuit that way, because it's misleading at best. But
what one expects and what is actually written in the code can be two
different things.

I think there are actually three differing opinions on this subject.
It looks like cl and I read the code as allowing a single 20 amp
receptacle on a 15 amp circuit. Doug makes the claim, which I think
is totally bogus, that the table in 210.21 (B) (3) says it is not
allowed. But that is just plain wrong, because that table is
preceeded by verbage that says it applies to circuits with two or more
receptacles. I believe you and I agree on that point.

Then there is your position, which is that while not prohibited by
section 210, it is prohibited by 406.3. That is a new point, which I
had never heard used before. But let;s look at what that says. It
doesn't actually say you can't put a 20A receptacle on a 15A
circuit. What it says is this:

406.3 (A)

"Grounding type receptacles shall be installed only on circuits of the
voltage class and current for which they are rated, except as provided
in Table 210.21 (B)(2) and Table 210.21(B)(3)."


A 20A receptable is rated to handle 0 through 20 amps of current. A
15 amp circuit falls in that range, so I would interpret the above to
mean that the 20A receptacle is permitted. Especially in view of the
fact that when they specifically address the issue of a single outlet
they could have just said that in the case of a single outlet you must
use a receptacle with a rating equal to the circuit, but they did not
and instead said this:

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


Suppose instead of talking about receptacles, 406.3 talked about wire
and said wire gauge shall only be installed on circuits of the voltage
class and current for which it is rated. Would that mean that I
couldn't use 12 gauge wire on a 15 amp circuit?


OK Trader, After looking it over, and over, I think I'm starting to agree
with you. The table is clearly prefaced by the text referring to other than
single receptacles. I question if it may be an oversight as it sure doesn't
make any sense to me, or you and Bud for that matter. Now I'm curious to get
the opinion of one of the local electrical inspectors, not that that's
necessarily definitive


  #70   Report Post  
Posted to alt.home.repair
Roy Roy is offline
external usenet poster
 
Posts: 410
Default 15A outlets on 20A circuits

On Oct 14, 5:19*pm, "RBM" wrote:
wrote in message

...
On Oct 14, 11:53 am, bud-- wrote:



RBM wrote:
wrote in message
....
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message


....
On Oct 12, 10:47 pm, (Doug Miller) wrote:


In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.


" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."


That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.


but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A
outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?


Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle
rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:


"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"


The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.


I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.


I think the reason for that initial statement in the code, is because a
40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15
amp
circuit- Hide quoted text -


That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.


It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A
circuit


But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.


Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).


I see what you're reading, but there is no text that says any
receptacle,
single or duplex, can have a rating higher than the circuit feeding it.



  #71   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 14, 7:19*pm, "RBM" wrote:
wrote in message

...
On Oct 14, 11:53 am, bud-- wrote:





RBM wrote:
wrote in message
....
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message


....
On Oct 12, 10:47 pm, (Doug Miller) wrote:


In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.


" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."


That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.


but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A
outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?


Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle
rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:


"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"


The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.


I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.


I think the reason for that initial statement in the code, is because a
40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15
amp
circuit- Hide quoted text -


That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.


It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A
circuit


But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.


Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).


I see what you're reading, but there is no text that says any
receptacle,
single or duplex, can have a rating higher than the circuit feeding it.

  #72   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default 15A outlets on 20A circuits

wrote:
On Oct 14, 11:53 am, bud-- wrote:
RBM wrote:
wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message
...
On Oct 12, 10:47 pm, (Doug Miller) wrote:
In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.
" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."
That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.
but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?
Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:
"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"
The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.
I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.
I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -
That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.
It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.

[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A circuit

But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.

Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).



I see what you're reading, but there is no text that says any receptacle,
single or duplex, can have a rating higher than the circuit feeding it.

[RBM]
There is text that you can put a 20A receptacle on a 15A circuit.

There is no text in 210 that you can't have a higher rating, like 20A
(or 50A, or 100A) as the single receptacle.

There is text in 406.3 that you can't put a 20A receptacle on a 15A
circuit. This is what we all (except one) expect.

--
bud--- Hide quoted text -

- Show quoted text -


I don't think the issue ever was what we expect. I would not have
expected the code to allow a 20 amp receptacle on a 15 amp circuit
either, which is why I brought it up in the first place. I also would
not wire a circuit that way, because it's misleading at best. But
what one expects and what is actually written in the code can be two
different things.

I think there are actually three differing opinions on this subject.
It looks like cl and I read the code as allowing a single 20 amp
receptacle on a 15 amp circuit. Doug makes the claim, which I think
is totally bogus, that the table in 210.21 (B) (3) says it is not
allowed. But that is just plain wrong, because that table is
preceeded by verbage that says it applies to circuits with two or more
receptacles. I believe you and I agree on that point.

Then there is your position, which is that while not prohibited by
section 210, it is prohibited by 406.3. That is a new point, which I
had never heard used before. But let;s look at what that says. It
doesn't actually say you can't put a 20A receptacle on a 15A
circuit. What it says is this:

406.3 (A)

"Grounding type receptacles shall be installed only on circuits of the
voltage class and current for which they are rated, except as provided
in Table 210.21 (B)(2) and Table 210.21(B)(3)."


A 20A receptable is rated to handle 0 through 20 amps of current. A
15 amp circuit falls in that range, so I would interpret the above to
mean that the 20A receptacle is permitted. Especially in view of the
fact that when they specifically address the issue of a single outlet
they could have just said that in the case of a single outlet you must
use a receptacle with a rating equal to the circuit, but they did not
and instead said this:

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


A 40A receptacle is rated to handle 0-40A. Would it be allowed on a 15A
circuit?

The rule should be expected to be in the article on receptacles, which
is 406.

The rule is (leaving some details out) that for 15 and 20A circuits,
receptacles "shall be be installed only on circuits of the voltage
class and current for which they are rated" (same as you quoted). On a
15A branch circuit you can only install a 15A receptacle and on a 20A
circuit you can only install a 20A receptacle. You match the receptacle
rating to the branch circuit rating. In 406.3-A it does not say
'voltage class and a current not less than the branch circuit'.

Then there is the exception - Table 210.21 (B)(2) and (B)(3). They allow
a 15A receptacle on a 20A circuit. There is no reference to 210.21-B-1
(single receptacles).

There is not a problem with a 15A receptacle on a 20A branch circuit
because listed plug-in equipment is apparently tested to be safe on 20A
circuits (which it all can be plugged into). And a 15A receptacle is
rated for 20A total.

The problem with installing a 20A receptacle on a 15A circuit is
obvious to everyone (with one exception). It does not make sense the NEC
would allow that (although the NEC does make mistakes). IMHO it is not
allowed in 406.3-A. It is not explicitly allowed in 210.21-B-1. Would
210.21-B-1 allow a 40A receptacle on a 15A circuit?

But there is a difference. While 406.3-A is specific to 15 and 20A
branch circuits, 210.21-B-1 (single receptacle) is general, including
for instance a 60A receptacle on a 40A circuit - allowed by 210 and not
covered by 406-3-A. For 15 and 20A circuits use 406.3-A.


Suppose instead of talking about receptacles, 406.3 talked about wire
and said wire gauge shall only be installed on circuits of the voltage
class and current for which it is rated. Would that mean that I
couldn't use 12 gauge wire on a 15 amp circuit?


But 406.3 isn't about wire gauge and there are reasons to use a larger
size wire.

There are obvious reasons (to most people) why you don't want a 20A
receptacle on a common 15A circuit.

==================
The Holt discussions did not consider 406.3.

--
bud--
  #73   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 15, 11:35*am, bud-- wrote:
wrote:
On Oct 14, 11:53 am, bud-- wrote:
RBM wrote:
wrote in message
....
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message
....
On Oct 12, 10:47 pm, (Doug Miller) wrote:
In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.
" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."
That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.
but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?
Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:
"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"
The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.
I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.
I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -
That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. *If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. * And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.
It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.
[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A circuit


But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.


Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).


I see what you're reading, but there is no text that says any receptacle,
single or duplex, can have a rating higher than the circuit feeding it.

  #74   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 14, 2:59*pm, wrote:
On Thu, 14 Oct 2010 10:53:36 -0500, bud--
wrote:





RBM wrote:
wrote in message
....
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message


....
On Oct 12, 10:47 pm, (Doug Miller) wrote:


In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.


" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."


That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.


but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?


Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:


"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"


The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.


I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice..


I think the reason for that initial statement in the code, is because a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15 amp
circuit- Hide quoted text -


That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. *If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. * And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.


It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.


[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A circuit


But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.


Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).


A 20 amp receptacle is going to outlast even the hospital duty 15 amp
receptacle under moderate to heavy use. Absolutely no reason you
cannot use a 20 amp receptacle anywhere in your house that code allows
it, or anywhere in the house PERIOD if code is not in effect. Just
like there is nothing stopping you from using AWG 12 wiring throught
the entire house. The entire house can be wired for 20 amp circuits,
and protected by 15 amp breakers or fuses without posing ANY safety
issues. There will be cost issues, and IF you attempt to plug in a 20
amp device the breaker will eventually trip.



I think everyone here, except possibly you, agrees at this point that
in the USA, the ONLY place code MAY allow doing what you describe is
on a 15A circuit with a 20A single outlet. That was what the
discussion was about. NEC 210 clearly prohibits putting 20A
receptacles on any 15A circuit with more than one outlet. So, to do
what you suggest, you'd have to use a single 20A outlet, not a duplex
one, and do a homerun back to the panel for each outlet. That indeed
involves cost issues, because your basic 15A duplex outlet would now
be replaced by two single outlets with two cable runs back to the
panel and two 15A breakers. And the point to doing it would be?
To confuse people who see a 20A outlet and think they can plug in a 16
to 20A load? And it's currently very much up in the air if code even
allows it in the case of a single outlet. I'm starting to lean
towards that it does not.



The advantage is, all you
need to do is install a 20 amp breaker in place of the 15 and any
outlet in the house can instantly become a 20 amp circuit.


And if you thought you might want 20A outlets in the future, the
reason for doing it the way you proposed, as opposed to just wiring
the place with a 20A breaker, 20A outlets wherever you want them to
begin with, which would cost less than half and give them to you right
away, would be?


  #75   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default 15A outlets on 20A circuits


"bud--" wrote in message
.. .
wrote:
On Oct 14, 11:53 am, bud-- wrote:
RBM wrote:
wrote in message
...
On Oct 13, 5:42 pm, "RBM" wrote:
wrote in message
...
On Oct 12, 10:47 pm, (Doug Miller) wrote:
In article
,
wrote:
And I have to disagree on that one. I can find the code section for
you later,
Yeah, you do that. We'll wait.
You didn't have to wait long. Here it is. No need to get sarcastic
and snippy.
" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."
That is clear as day. A 20 amp single receptacle has an ampere rating
greater than that of the circuit, hence it MAY be used. If they
wanted to prohibit using a 20 amp or greater single receptacle on a 15
amp circuit, all they had to do was say the receptacle has to have a
rating EQUAL to the circuit.
but essentially it comes down to this. The code draws a
distinction between circuits with only one outlet and those with
more
than one. With more than one outlet, it says you can't use a 20A
outlet on 15A circuit.
Wrong. It says you can't use a 20A outlet on a 15A circuit, period.
You've
apparently become confused by the provision that you can put 15A
outlets
on a
20A circuit as long as there's more than one outlet. That's perfectly
OK.
Putting a 20A outlet on a 15A circuit is a violation in all cases,
without
regard to how many there are.
But for a circuit with only ONE outlet, the
code says the outlet rating must have a current rating at least
equal
to the circuit rating.
It says no such thing. It is, for example, a violation to put a 50A
outlet
on
a 20A circuit.
Actually it does say exactly what I said it does, as shown above.
You're the one who's confused, which is OK, but why the attitude?
Hence, a 20A single outlet can be use on a 15
amp circuit.
No, it cannot. Look at Table 210.21(B)(3), where it lists the
permissible
receptacle ratings. For a 15-amp circuit, the maximum receptacle
rating
is
"not over 15".
Yes, let's look at that section. In the same section where it starts
to explain those tables it starts off with:
"210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit
supplying TWO or MORE receptacles or outlets, receptacle ratings shall
conform to the values listed in Table 210.21(B)(3)"
The added emphasis is mine. Since we are talking about using a SINGLE
20 amp outlet on a 15 amp circuit, those tables do NOT apply.
I agree that it doesn't make any sense to me.
Doesn't make any sense to me either. Of course, that's because you're
completely wrong about the rules.
Actually it's quite clear that you're the one who's wrong here. A
simple admission to that and apollogy for getting snippy will suffice.
I think the reason for that initial statement in the code, is because
a 40
amp receptacle can be wired with a 40 or 50 amp circuit, but the table
makes
it perfectly clear that a 20 amp receptacle can't be wired with a 15
amp
circuit- Hide quoted text -
That table is preceeded by the statement, which I provided and is
shown above, that says it applies to circuits with TWO or more
receptacles. If they wanted it to apply to ALL receptacles, including
single outlet ones, they could have simply omitted the word TWO, but
they did not. And the section right before it clearly covers the
case of a SINGLE receptacle and allows a receptacle with a current
rating equal to or greater than the circuit to be used.
It doesn't make a lot of sense to me, but that is what it says and it
allows using a single 20 amp receptacle on a 15 amp circuit.
[trader]
I agree that 210 does not prohibit a single 20A receptacle on a 15A
circuit

But a 20A receptacle is virtually never allowed under 406.3-B. It would
make sense to at least point to 406 in 210. The logic is probably that
406 (Receptacles...) is the primary article and is modified by 210.
There is a reference to 210 in 406.3.

Most people would not be dumb enough to want a 20A receptacle on a 15A
circuit (there seems to be one exception).



I see what you're reading, but there is no text that says any
receptacle,
single or duplex, can have a rating higher than the circuit feeding it.
[RBM]
There is text that you can put a 20A receptacle on a 15A circuit.

There is no text in 210 that you can't have a higher rating, like 20A
(or 50A, or 100A) as the single receptacle.

There is text in 406.3 that you can't put a 20A receptacle on a 15A
circuit. This is what we all (except one) expect.

--
bud--- Hide quoted text -

- Show quoted text -


I don't think the issue ever was what we expect. I would not have
expected the code to allow a 20 amp receptacle on a 15 amp circuit
either, which is why I brought it up in the first place. I also would
not wire a circuit that way, because it's misleading at best. But
what one expects and what is actually written in the code can be two
different things.

I think there are actually three differing opinions on this subject.
It looks like cl and I read the code as allowing a single 20 amp
receptacle on a 15 amp circuit. Doug makes the claim, which I think
is totally bogus, that the table in 210.21 (B) (3) says it is not
allowed. But that is just plain wrong, because that table is
preceeded by verbage that says it applies to circuits with two or more
receptacles. I believe you and I agree on that point.

Then there is your position, which is that while not prohibited by
section 210, it is prohibited by 406.3. That is a new point, which I
had never heard used before. But let;s look at what that says. It
doesn't actually say you can't put a 20A receptacle on a 15A
circuit. What it says is this:

406.3 (A)

"Grounding type receptacles shall be installed only on circuits of the
voltage class and current for which they are rated, except as provided
in Table 210.21 (B)(2) and Table 210.21(B)(3)."


A 20A receptable is rated to handle 0 through 20 amps of current. A
15 amp circuit falls in that range, so I would interpret the above to
mean that the 20A receptacle is permitted. Especially in view of the
fact that when they specifically address the issue of a single outlet
they could have just said that in the case of a single outlet you must
use a receptacle with a rating equal to the circuit, but they did not
and instead said this:

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.


A 40A receptacle is rated to handle 0-40A. Would it be allowed on a 15A
circuit?

The rule should be expected to be in the article on receptacles, which is
406.

The rule is (leaving some details out) that for 15 and 20A circuits,
receptacles "shall be be installed only on circuits of the voltage class
and current for which they are rated" (same as you quoted). On a 15A
branch circuit you can only install a 15A receptacle and on a 20A circuit
you can only install a 20A receptacle. You match the receptacle rating to
the branch circuit rating. In 406.3-A it does not say 'voltage class and a
current not less than the branch circuit'.

Then there is the exception - Table 210.21 (B)(2) and (B)(3). They allow a
15A receptacle on a 20A circuit. There is no reference to 210.21-B-1
(single receptacles).

There is not a problem with a 15A receptacle on a 20A branch circuit
because listed plug-in equipment is apparently tested to be safe on 20A
circuits (which it all can be plugged into). And a 15A receptacle is rated
for 20A total.

The problem with installing a 20A receptacle on a 15A circuit is obvious
to everyone (with one exception). It does not make sense the NEC would
allow that (although the NEC does make mistakes). IMHO it is not allowed
in 406.3-A. It is not explicitly allowed in 210.21-B-1. Would 210.21-B-1
allow a 40A receptacle on a 15A circuit?

But there is a difference. While 406.3-A is specific to 15 and 20A branch
circuits, 210.21-B-1 (single receptacle) is general, including for
instance a 60A receptacle on a 40A circuit - allowed by 210 and not
covered by 406-3-A. For 15 and 20A circuits use 406.3-A.


Suppose instead of talking about receptacles, 406.3 talked about wire
and said wire gauge shall only be installed on circuits of the voltage
class and current for which it is rated. Would that mean that I
couldn't use 12 gauge wire on a 15 amp circuit?


But 406.3 isn't about wire gauge and there are reasons to use a larger
size wire.

There are obvious reasons (to most people) why you don't want a 20A
receptacle on a common 15A circuit.

==================
The Holt discussions did not consider 406.3.

--
bud--



For me, 406.3A is the most confusing. If it were based solely on 210.21,
it's clear that the table doesn't cover single receptacles, and that single
receptacles must be rated not less than the circuit. 406.3A uses the term
"of the voltage, class and current" , it doesn't say "not less than", or
anything that offers flexibility, other than to use the table in 210.21B3,
which is not applicable to single receptacles.
In conclusion, I'm still scratchin my head, other than the fact that, while
there is no danger in using a receptacle rated higher than the circuit,
there is no practical reason to do it, and it could just lead to confusion.




  #76   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default 15A outlets on 20A circuits

On Oct 17, 12:10*pm, wrote:
On Sun, 17 Oct 2010 09:59:30 -0500, bud--
wrote:

As I said, IMHO a 20A receptacle on a 15A circuit can be tagged under
403.6-A. Greg?


I would tag it and have the installer explain to me why he did it.
I agree there is some ambiguous language in the text of 210.21(B)(3)
but when 406.3(A) directly addresses table 210.21(B)(3) it seems clear
to me.


The problem is that 210.21(b)(3) clearly says it and the table apply
to circuits with more than one receptacle. And everyone is in
agreement that using a 20A outlet on a 15A circuit with more than one
receptacle is not allowed. It's 210.21(b)(1) that addresses the
issue of a single outlet.



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Graf - Encyclopedia of Electronic Circuits - File 01 of 14 - Graf - Encyclopedia of Electronic Circuits - Vol 1.pdf (01/68) Dave Electronic Schematics 22 May 6th 08 03:05 AM
Graf - Encyclopedia of Electronic Circuits - File 08 of 14 - Graf - Encyclopedia of Electronic Circuits - Vol .vol00+01.PAR2 (2/2) Andy Cap[_2_] Electronic Schematics 0 May 2nd 08 10:24 AM
Graf - Encyclopedia of Electronic Circuits - File 07 of 14 - Graf - Encyclopedia of Electronic Circuits - Vol .par2 (1/1) Andy Cap[_2_] Electronic Schematics 0 May 2nd 08 10:24 AM
kitchen circuits 15 amp vs 20 amp outlets tr Home Repair 36 November 17th 06 12:02 AM
What is the norm on kitchen/rest of house outlets/circuits Jack Home Repair 3 April 28th 06 08:13 AM


All times are GMT +1. The time now is 02:17 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"