On Oct 13, 5:36*pm, "RBM" wrote:
wrote in message

...
On Oct 12, 6:41 pm, "RBM" wrote:





wrote in message


...
On Oct 12, 7:56 am, "RBM" wrote:


"RBM" wrote in message


...


"Mikepier" wrote in message
...
Last week, I posted about running 12/2 wire for a kitchen reno. Well
all the circuits are run. I decided on running all 12/2 instead of
12/3 and splitting circuits. Looking ahead to outlets, had a
question.
I think I know the answer, but just wanted to confirm.


I ran 4 new circuits for the fridge, microwave/range hood, and
counter
outlets. Am I allowed to use regular 15A outlets? For the counter
outlets, I am using regular 15A Decora and GFI's, and for the fridge,
microwave just wanted to use regular outlets, like the kind you can
get a 10Pk for like $5 at Lowes.


15 amp outlets are fine. The refrigerator doesn't need to be GFCI
protected, but all the counter outlets do. A 15 amp GFCI outlet has a
20
amp feed through


Just to clarify. A single 15 amp outlet can't be installed on a 20 amp
dedicated circuit, but a duplex is fine


- Hide quoted text -


- Show quoted text -- Hide quoted text -


- Show quoted text -


This is another example of things in the code that don't seem to make
any sense, at least to me. If one can install multiple 15 amp
outlets on a 20 amp circuit, why the restriction on installing just
one?


And while we're at it, the code also says you can use a 20 amp single
outlet on a 15 amp circuit, but you can't install multiple 20's on a
15 amp circuit.


Why the big distinction between single versus multiple outlets?


The feed through of a 15 amp outlet is 20 amps. You cannot install a 20
amp
outlet on a 15 amp circuit Nec 210.21 B3- Hide quoted text -


- Show quoted text -


NEC 210.21(B)(3) starts off by saying that section only applies to
circuits with more than one outlet. * We are talking about a SINGLE
outlet. * In which case, the following section applies:

" 210.21 Outlet Devices.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit."

Since the 20 amp outlet has a rating greater than the 15 amp circuit,
it may be used. * *Now, I would agree it doesn't make much, but that
is what is says, and hence was my point.

That text is only part of the article, the table clarifies the rest. There
is no ambiguity in the table.- Hide quoted text -

- Show quoted text -


I agree there is no abiguity in the table. The problem is the table
applies to circuits with two or more receptacles and we are talking
about a circuit with just one.

210.21 (B) (3)
Receptacle Ratings. Where connected to a branch circuit supplying TWO
OR MORE receptacles or outlets, receptacle ratings shall conform to
the values listed in Table 210.21 (B) (3)....



Here;s the section that covers the single receptacle:

21210.21 (B) (1)
Single receptacle on an individual branch circuit. A single
receptacle installed on an individual branch circuit shall have an
ampere rating not less than that of the branch circuit.