Metalworking (rec.crafts.metalworking) Discuss various aspects of working with metal, such as machining, welding, metal joining, screwing, casting, hardening/tempering, blacksmithing/forging, spinning and hammer work, sheet metal work.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Greg Deputy
 
Posts: n/a
Default What should a new 240v circuit cost?

I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?


  #2   Report Post  
Lucky Strike
 
Posts: n/a
Default

Get 3 quotes and then decide what's reasonable.

Usually you get what you pay for. You don't describe what you are getting.

one 240V 10A switch 2 feet from the mains = you are getting screwed
240V 200A service full of breakers, 100' run of cable to the pole and a new
meter = sounds reasonable

"Greg Deputy" wrote in message
...
I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet

right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?




  #3   Report Post  
jim rozen
 
Posts: n/a
Default

In article , Greg Deputy says...

I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?


Around here the labor cost would be about 100 per hour.

That means (aside from the materials cost which would be
probably 25 dollars or so) they should be working full
time for ten hours at this. Seems like a pretty long time
to install one branch circuit.

Is there some other issue for the installation that would
drive up the price?

What have the other folks who've come in to bid estimated?

Jim


--
==================================================
please reply to:
JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com
==================================================
  #4   Report Post  
Peter Grey
 
Posts: n/a
Default

Just FYI...

I had a 240 circuit put in my garage. The garage is 60 feet from the panel
which is inside the house. The electrician came through the wall of the
house, ran conduit to the garage (not a straight shot - it followed the edge
of a deck), ran conduit in the garage to two plugs, and wired the whole
thing. It cost about $1200. I live in San Francisco where I suspect the
rates are as high as anywhere.

Peter
"Greg Deputy" wrote in message
...
I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet
right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?




  #5   Report Post  
Pete C.
 
Posts: n/a
Default



Greg Deputy wrote:

I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?


You don't give a lot of details, but if we assume you're talking about
something like a welder outlet right next to the main panel in an
exposed location in a garage and there are no "problems" such as a full
or obsolete panel:

1 50A 2 pole circuit breaker $10-20 depending on brand
1 50A receptacle $20-$40 depending on type
1 box to mount receptacle in $5
1 offset nipple to connect box to panel $5
12' of 6 ga THHN wire $10

Figure 1 hour of labor for a simple installation.

So I'd say up to about $200 is reasonable, much more than that would be
suspect in my opinion. As mentioned earlier that is based on an
uncomplicated installation, a full or obsolete panel could well require
a lot of extra work and justify a higher cost.

I'm not a licensed electrician, but I've done plenty of my own work so I
have a good idea of time and materials.

For a price comparison, a friend of mine recently upgraded the service
in his house from 60A fuses to a 100A breaker panel and a new meter
socket. As the homeowner he can do his own work and pull permits, etc.

While he had added a circuit here and there in the past he was a little
leery of tackling a project this size. As the more experienced
electrician I gave him the "service upgrade 101" class.

The project probably took him about 10-12 hours of work total. The
materials cost was about $300. The inspector *loved* the work and
commented that it was a neater job than many done by commercial
electricians he's inspected.

Pete C.


  #6   Report Post  
Jim Stewart
 
Posts: n/a
Default

Greg Deputy wrote:
I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?


I am not an electrician.

First specify how many amps. The price will
be somewhat dependant on this.

I installed a 50 ampere subpanel with a 6
gauge feeder in my garage. The run to the
main breaker panel was about 60 feet. The
total materials cost, including the new
breaker in the main panel and a couple
breakers in the subpanel was about $200.
The permit and inspection by the city was
about $50.

I don't think $1000 is too far out of line.
The job will take some time and electricians
aren't cheap.

  #7   Report Post  
Greg Deputy
 
Posts: n/a
Default

Thanks for all the responses!

To add some details, i'm looking to add a 60A circuit in my garage, right
next to the circuitbox. Nothing in the way, no problems, plenty of room in
the breaker box for the additonal breakers. The guy who came to give an
'estimate' just had a book, and his book said $700 for a new 40A 240v branch
circuit, $950 for a 50A. If I wanted him to run conduit and wire to the
other side of the garage where a lathe is going, it would be more.

Even funnier, the guy said his company was expensive, and he'd be happy to
come in on the weekend and do it for half the price on his own time....


"Greg Deputy" wrote in message
...
I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet

right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?




  #8   Report Post  
jim rozen
 
Posts: n/a
Default

In article , Ignoramus24456 says...

Some pix of it can be seen he

http://igor.chudov.com/projects/Curt.../02_Installed/


Nice installation.

*ahem*

The 120 volt receptactles are installed upside down - the
ground connection goes on top, the way the 240 volt ones
were done.

Just a nit pick!

Jim


--
==================================================
please reply to:
JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com
==================================================
  #9   Report Post  
Greg Deputy
 
Posts: n/a
Default

Yeah, the next electrician said he'd do the outlet right next to the panel
for $100. Meithinks the first guy is trying to rip me off....

I'm probably going to have him run it to the other side of the garage,
wouldnt i have to get it inspected or something to make sure its up to code
if I did it?

"Ignoramus24456" wrote in message
...
On Wed, 2 Mar 2005 13:04:54 -0800, Greg Deputy wrote:
Thanks for all the responses!

To add some details, i'm looking to add a 60A circuit in my garage,

right
next to the circuitbox.


Do you mean right next to your main electrical panel?

Nothing in the way, no problems, plenty of room in the breaker box
for the additonal breakers. The guy who came to give an 'estimate'
just had a book, and his book said $700 for a new 40A 240v branch
circuit, $950 for a 50A. If I wanted him to run conduit and wire to
the other side of the garage where a lathe is going, it would be
more.

Even funnier, the guy said his company was expensive, and he'd be happy

to
come in on the weekend and do it for half the price on his own time....


If you are going to run a single short circuit all within the garage,
any $$amount is too expensive. This is a perfect beginner level
project for you to do. ask questions in alt.home.repair, get a permit
if you like, and go ahead.

i


"Greg Deputy" wrote in message
...
I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including

any
sort of wire runs, but to just put in a branch circuit with an outlet

right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?






--



  #10   Report Post  
Pete C.
 
Posts: n/a
Default



jim rozen wrote:

In article , Ignoramus24456 says...

Some pix of it can be seen he

http://igor.chudov.com/projects/Curt.../02_Installed/


Nice installation.

*ahem*

The 120 volt receptactles are installed upside down - the
ground connection goes on top, the way the 240 volt ones
were done.

Just a nit pick!

Jim

--
==================================================
please reply to:
JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com
==================================================


I've seen a lot of debate about that with various reasonings.

The ground pin up so anything metal falling on it hits ground and not
hot argument would seem to cover a pretty low probability event.

The ground pin up so that gravity will tend to push the hot and neutral
in instead of pulling them out seems to be a cover for low quality
outlets and many connections have cords pulled in directions other than
that of gravity.

Either way, you will find that a substantial percentage of wall warts
are clearly designed for ground down mounting, even ones without a
ground pin.

The last time I looked through the NEC book I don't recall reading
anything about receptacle orientation. Granted that was the 2002 edition
and I wasn't specifically looking for such a thing. I'm not sure where
my code book is at the moment.

Personally I don't think it really makes much difference which way they
are mounted, particularly when you consider the case of horizontally
mounted outlets. In that case should the ground be on the left or the
right???

Pete C.


  #11   Report Post  
Pete C.
 
Posts: n/a
Default



Greg Deputy wrote:

Yeah, the next electrician said he'd do the outlet right next to the panel
for $100. Meithinks the first guy is trying to rip me off....

I'm probably going to have him run it to the other side of the garage,
wouldnt i have to get it inspected or something to make sure its up to code
if I did it?

"Ignoramus24456" wrote in message
...
On Wed, 2 Mar 2005 13:04:54 -0800, Greg Deputy wrote:
Thanks for all the responses!

To add some details, i'm looking to add a 60A circuit in my garage,

right
next to the circuitbox.


Do you mean right next to your main electrical panel?

Nothing in the way, no problems, plenty of room in the breaker box
for the additonal breakers. The guy who came to give an 'estimate'
just had a book, and his book said $700 for a new 40A 240v branch
circuit, $950 for a 50A. If I wanted him to run conduit and wire to
the other side of the garage where a lathe is going, it would be
more.

Even funnier, the guy said his company was expensive, and he'd be happy

to
come in on the weekend and do it for half the price on his own time....


If you are going to run a single short circuit all within the garage,
any $$amount is too expensive. This is a perfect beginner level
project for you to do. ask questions in alt.home.repair, get a permit
if you like, and go ahead.

i


"Greg Deputy" wrote in message
...
I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including

any
sort of wire runs, but to just put in a branch circuit with an outlet
right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?






--


It may vary by location, but usually the homeowner can do their own
work, but they need to pull a permit and have it inspected just like any
other job.

Pete C.
  #12   Report Post  
jw
 
Posts: n/a
Default

That seems ridiculously expensive from the description you have given.
Point of reference, I had a whole new 3 phase service install from the
pole to my shop for $1600.
I am a more than competent "sparky", but playing with "hot"
transformers is not something that I am willing to do. I farmed this
one out. Otherwise, I have done all of my wiring at home/shop. As
close to NEC as practical.

JW

  #13   Report Post  
Ecnerwal
 
Posts: n/a
Default

In article ,
"Pete C." wrote:
Personally I don't think it really makes much difference which way they
are mounted, particularly when you consider the case of horizontally
mounted outlets. In that case should the ground be on the left or the
right???


Left, so that the uppermost blade is the neutral blade, not the hot
blade.

--
Cats, Coffee, Chocolate...vices to live by
  #14   Report Post  
Tim Wescott
 
Posts: n/a
Default

jim rozen wrote:

In article , Ignoramus24456 says...


Some pix of it can be seen he

http://igor.chudov.com/projects/Curt.../02_Installed/



Nice installation.

*ahem*

The 120 volt receptactles are installed upside down - the
ground connection goes on top, the way the 240 volt ones
were done.

Just a nit pick!

Jim


A long long time ago when my Parent's shop was inspected by OSHA we got
dinged (but not cited) for having outlets with the ground pin up, the
reasoning being that with the pin down the last thing that'll go will be
the safety ground.

Since then I've always installed them with ground pin down, and IIRC
most power strips have them down when the writing is correct.

Of course the inspectors seemed to be much more heavily schooled in the
idea that if you have employees you're automatically evil than they were
in electrical theory, but still...

--

Tim Wescott
Wescott Design Services
http://www.wescottdesign.com
  #15   Report Post  
Tim Wescott
 
Posts: n/a
Default

Greg Deputy wrote:

Yeah, the next electrician said he'd do the outlet right next to the panel
for $100. Meithinks the first guy is trying to rip me off....

I'm probably going to have him run it to the other side of the garage,
wouldnt i have to get it inspected or something to make sure its up to code
if I did it?

"Ignoramus24456" wrote in message
...

On Wed, 2 Mar 2005 13:04:54 -0800, Greg Deputy wrote:

Thanks for all the responses!

To add some details, i'm looking to add a 60A circuit in my garage,


right

next to the circuitbox.


Do you mean right next to your main electrical panel?


Nothing in the way, no problems, plenty of room in the breaker box
for the additonal breakers. The guy who came to give an 'estimate'
just had a book, and his book said $700 for a new 40A 240v branch
circuit, $950 for a 50A. If I wanted him to run conduit and wire to
the other side of the garage where a lathe is going, it would be
more.

Even funnier, the guy said his company was expensive, and he'd be happy


to

come in on the weekend and do it for half the price on his own time....


If you are going to run a single short circuit all within the garage,
any $$amount is too expensive. This is a perfect beginner level
project for you to do. ask questions in alt.home.repair, get a permit
if you like, and go ahead.

i


"Greg Deputy" wrote in message
...

I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including


any

sort of wire runs, but to just put in a branch circuit with an outlet

right

next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?

It'll vary from state to state but here in Oregon anything that's not a
repair should be inspected. Of course if you own the place nobody will
know if you do the work yourself, but that can cause trouble down the
road if you have a fire -- even if it's from a gasoline tanker running
into your house and bursting into flames the insurance company will try
to pin it on uninspected work.

From what I hear the inspectors are generally on your side as a
homeowner if you're reasonable, but that will vary from inspector to
inspector, and as a function of the quality of your work.

--

Tim Wescott
Wescott Design Services
http://www.wescottdesign.com


  #16   Report Post  
DoN. Nichols
 
Posts: n/a
Default

In article , Pete C. wrote:

[ ... ]

You don't give a lot of details, but if we assume you're talking about
something like a welder outlet right next to the main panel in an
exposed location in a garage and there are no "problems" such as a full
or obsolete panel:


Pete,

Could you please change the format of your munged address? The
format which you used:



generates problems (the inner set of '' and '' cause the problems when
I try to save a copy of what you posted. Since I run my own news
server, I could go in and edit the offending string so I could save it,
but most don't have the privilege -- or the knowledge -- to do this, and
can be stuck unable to save an article. One modification which I have
tested, and which at least works on my system is:



(Substituting "{}" for "", which at least has no problems on my
system.)

I wish that spammers would go away, so nobody would feel the
need to do this.

Thanks,
DoN.
--
Email: | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
--- Black Holes are where God is dividing by zero ---
  #17   Report Post  
Pete C.
 
Posts: n/a
Default



"DoN. Nichols" wrote:

In article , Pete C. wrote:

[ ... ]

You don't give a lot of details, but if we assume you're talking about
something like a welder outlet right next to the main panel in an
exposed location in a garage and there are no "problems" such as a full
or obsolete panel:


Pete,

Could you please change the format of your munged address? The
format which you used:



generates problems (the inner set of '' and '' cause the problems when
I try to save a copy of what you posted. Since I run my own news
server, I could go in and edit the offending string so I could save it,
but most don't have the privilege -- or the knowledge -- to do this, and
can be stuck unable to save an article. One modification which I have
tested, and which at least works on my system is:



(Substituting "{}" for "", which at least has no problems on my
system.)

I wish that spammers would go away, so nobody would feel the
need to do this.

Thanks,
DoN.
--
Email: | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
--- Black Holes are where God is dividing by zero ---


De-munged, or at least differently munged. I used the . since that
should be legal for any system. Until recently I had a fully bogus
address there since I didn't intend for anyone to respond "off-line".

Pete C.
  #18   Report Post  
Pete C.
 
Posts: n/a
Default



Ecnerwal wrote:

In article ,
"Pete C." wrote:
Personally I don't think it really makes much difference which way they
are mounted, particularly when you consider the case of horizontally
mounted outlets. In that case should the ground be on the left or the
right???


Left, so that the uppermost blade is the neutral blade, not the hot
blade.

--
Cats, Coffee, Chocolate...vices to live by


Makes some sense, but if I were an inspector I'd be much happier to see
people installing spec grade receptacles diagonally than to see
residential grade installed at all, ground up or down.

The quality of the residential grade receptacles goes from "iffy" from
the major brands to "downright scary" for lesser brands.

Pete C.
  #19   Report Post  
jim rozen
 
Posts: n/a
Default

In article , Tim Wescott says...

A long long time ago when my Parent's shop was inspected by OSHA we got
dinged (but not cited) for having outlets with the ground pin up, the
reasoning being that with the pin down the last thing that'll go will be
the safety ground.


Look closely at the a hubbell receptacle. The name appears
rightside up when the ground pin is on the top. That's what
hubbell thinks on the subject, anyway. g

I understand the reason for the ground pin being on top has
to do with the idea that any foreign object which falls down
on the plug will encounter the ground pin rather than a
hot lead - if the plug were partly loose.

Jim


--
==================================================
please reply to:
JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com
==================================================
  #20   Report Post  
Lucky Strike
 
Posts: n/a
Default

I'd be just as weary of the $100 as the $1000 guy.

Are you adding a new panel or just a plug? $100 might just about cover the
materials cost for wire, breakers and a small box.

If you are planning on running more equipment you mind as well go 100A or
better. Mind as well go 200A now that the wife has seen the $1000 quote.

Just think - you are running a welder or a plasma cutter, the air compressor
kicks in and your 60A breaker trips...doh!

"Greg Deputy" wrote in message
...
Yeah, the next electrician said he'd do the outlet right next to the panel
for $100. Meithinks the first guy is trying to rip me off....

I'm probably going to have him run it to the other side of the garage,
wouldnt i have to get it inspected or something to make sure its up to

code
if I did it?

"Ignoramus24456" wrote in message
...
On Wed, 2 Mar 2005 13:04:54 -0800, Greg Deputy

wrote:
Thanks for all the responses!

To add some details, i'm looking to add a 60A circuit in my garage,

right
next to the circuitbox.


Do you mean right next to your main electrical panel?

Nothing in the way, no problems, plenty of room in the breaker box
for the additonal breakers. The guy who came to give an 'estimate'
just had a book, and his book said $700 for a new 40A 240v branch
circuit, $950 for a 50A. If I wanted him to run conduit and wire to
the other side of the garage where a lathe is going, it would be
more.

Even funnier, the guy said his company was expensive, and he'd be

happy
to
come in on the weekend and do it for half the price on his own

time....

If you are going to run a single short circuit all within the garage,
any $$amount is too expensive. This is a perfect beginner level
project for you to do. ask questions in alt.home.repair, get a permit
if you like, and go ahead.

i


"Greg Deputy" wrote in message
...
I'm needing to get a new 240v circuit installed in my garage. I had

an
electrician come out, and they wanted $1000 to do it. Not including

any
sort of wire runs, but to just put in a branch circuit with an outlet
right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?






--







  #21   Report Post  
jim rozen
 
Posts: n/a
Default

In article , Pete C." "aux3 says...

The ground pin up so anything metal falling on it hits ground and not
hot argument would seem to cover a pretty low probability event.


Sure. But I like having belt + suspenders in operation there.

The ground pin up so that gravity will tend to push the hot and neutral
in instead of pulling them out seems to be a cover for low quality
outlets and many connections have cords pulled in directions other than
that of gravity.


It's not at all clear to me that either orientation will tend to
keep any particular conductor socked home any better. I think I'll
go by hubbell's recommendations.

Jim


--
==================================================
please reply to:
JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com
==================================================
  #22   Report Post  
jim rozen
 
Posts: n/a
Default

In article , Ignoramus24456 says...

...Ground up is said to be better if something metallic falls
on a not fully inserted plug, that's a fair thought, but how likely is
that to happen?


I've seen it happen.

Jim


--
==================================================
please reply to:
JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com
==================================================
  #23   Report Post  
DoN. Nichols
 
Posts: n/a
Default

In article , Pete C. wrote:

"DoN. Nichols" wrote:


In article , Pete C. wrote:


[ ... ]

Pete,

Could you please change the format of your munged address? The
format which you used:



generates problems


[ ... ]

De-munged, or at least differently munged. I used the . since that
should be legal for any system. Until recently I had a fully bogus
address there since I didn't intend for anyone to respond "off-line".


Thank you. I don't mind people replying off-line -- as long as
they don't do both off-line and on-line without telling me so.

Thanks again,
DoN.
--
Email: | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
--- Black Holes are where God is dividing by zero ---
  #24   Report Post  
DoN. Nichols
 
Posts: n/a
Default

In article ,
jim rozen wrote:
In article , Tim Wescott says...

A long long time ago when my Parent's shop was inspected by OSHA we got
dinged (but not cited) for having outlets with the ground pin up, the
reasoning being that with the pin down the last thing that'll go will be
the safety ground.


Look closely at the a hubbell receptacle. The name appears
rightside up when the ground pin is on the top. That's what
hubbell thinks on the subject, anyway. g


O.K. I've seen some which had the label rightside up when the
ground pin was down.

I understand the reason for the ground pin being on top has
to do with the idea that any foreign object which falls down
on the plug will encounter the ground pin rather than a
hot lead - if the plug were partly loose.


That makes a certain amount of sense.

However, with the ground pin down, the typical moulded connector
is a more natural fit into the hand, thus discouraging attempting to
remove it by yanking on the cord.

Anybody have an orientation for the twist-loc connectors? :-)

Enjoy,
DoN.
--
Email: | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
--- Black Holes are where God is dividing by zero ---
  #25   Report Post  
SteveF
 
Posts: n/a
Default


"jim rozen" wrote in message
...
In article , Ignoramus24456 says...

...Ground up is said to be better if something metallic falls
on a not fully inserted plug, that's a fair thought, but how likely is
that to happen?


I've seen it happen.

Jim



When I was about 12 I was reaching down behind the sofa to plug in a vacuum
cleaner and my finger slipped across the contacts. Got an interesting
lesson in electricity.

Steve.




  #26   Report Post  
Bruce L. Bergman
 
Posts: n/a
Default

On Wed, 2 Mar 2005 11:49:59 -0800, "Greg Deputy"
wrote:

I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet right
next to the breaker box in the garage. That seems kinda steep.


You must have done everything wrong to get a quote that high -

* Called a Union company that's going to send 3 people out to do the
work of one man.

* Have a power panel that takes oddball obsolete breakers, or your
panel is stuffed full requiring new twin breakers to make room, or
installing a sub-panel and re-routing the power to other devices.

(And in that case, I'd say rather than fight with an antique or
undersized service, swap the whole main service out. Kick it up from
70A/100A/125A to 200A, or from 200A to 400A. That'll be expensive to
do, but you pay once and you're done with it for another 30+ years.)

* And the city/county permit filing fees, including an hour for a
Licensed Engineer to create certified drawings and a panel schedule,
an hour for someone to run to the Building & Safety office to file the
permit, and an hour or two (or four...) of the Electrician's time to
sit around waiting for the inspector to arrive - the final inspection
itself taking 5 minutes...

Any electricians out there want to tell me what I should expect to pay?


If the panel is in good shape and has a space available, and you are
going right below the panel (or right behind it for panels mounted on
the outside of the garage wall) with your welder receptacle, my
guesstimate would be $250 to $300. And if the planets are all aligned
(and it's drop dead easy) $175-ish.

No permit for small stuff like that unless the locality is
ultra-picky (which all of ours aren't) - it's either done right or it
isn't done, you don't need the city to tell you...

-- Bruce --
--
Bruce L. Bergman, Woodland Hills (Los Angeles) CA - Desktop
Electrician for Westend Electric - CA726700
5737 Kanan Rd. #359, Agoura CA 91301 (818) 889-9545
Spamtrapped address: Remove the python and the invalid, and use a net.
  #27   Report Post  
Larry Jaques
 
Posts: n/a
Default

On Wed, 2 Mar 2005 11:49:59 -0800, the inscrutable "Greg Deputy"
spake:

I'm needing to get a new 240v circuit installed in my garage. I had an
electrician come out, and they wanted $1000 to do it. Not including any
sort of wire runs, but to just put in a branch circuit with an outlet right
next to the breaker box in the garage. That seems kinda steep. Any
electricians out there want to tell me what I should expect to pay?


When I moved here 3 years ago, it took me about 4 hours to remove the
wallboard behind the service panel, go up in the attic, run 3 new 240v
lines, mount them to boxes and outlets, and put covers on them. (I
should remove that wallboard and staple those wires, then run emt
conduit to the 2 exposed outlets to make it code-legal.)

Parts:

250' of 12/2 grounded Romex - $17.95 on sale (I used about half)
3 ea. L6-20R twist-lock outlets @ 6.95 each - $20.85
3 ea. L6-20P twist-lock plugs @ 8.95 each - $26.85
3 ea. metal outlet boxes @ $0.28 each - $0.84
1 ea. 4x8x7/16" chipboard @ 6.95 - $6.95

Labor: 4 hours @ $65/hr $260


SubTotals: $73.44 in parts and $260 labor


Grand total if I paid myself: $333.44


I would feel that an electrician was ripping me off if he charged over
$500 for the job. (Double the parts prices and higher labor.)

Get some more quotes or find someone to do the final hookup for
cheaper and do the main work yourself. Except for crawling around the
rafters, the work is not hard.

--
Remember: Every silver lining has a cloud.
----
http://diversify.com Comprehensive Website Development
  #28   Report Post  
Gunner
 
Posts: n/a
Default

On 2 Mar 2005 22:53:37 GMT, Ignoramus24456
wrote:

On 2 Mar 2005 14:33:48 -0800, jim rozen wrote:
In article , Tim Wescott says...

A long long time ago when my Parent's shop was inspected by OSHA we got
dinged (but not cited) for having outlets with the ground pin up, the
reasoning being that with the pin down the last thing that'll go will be
the safety ground.


Look closely at the a hubbell receptacle. The name appears
rightside up when the ground pin is on the top. That's what
hubbell thinks on the subject, anyway. g

I understand the reason for the ground pin being on top has
to do with the idea that any foreign object which falls down
on the plug will encounter the ground pin rather than a
hot lead - if the plug were partly loose.


Hubbell receptacles are also good enough so that a plug that is
inserted, stays inserted.

i


Sometimes, .no matter how hard you pull.
Gunner



Lathe Dementia. Recognized as one of the major sub-strains of the
all-consuming virus, Packratitis. Usual symptoms easily recognized
and normally is contracted for life. Can be very contagious.
michael
  #29   Report Post  
Gunner
 
Posts: n/a
Default

On 2 Mar 2005 15:19:22 -0800, jim rozen
wrote:

In article , Ignoramus24456 says...

...Ground up is said to be better if something metallic falls
on a not fully inserted plug, that's a fair thought, but how likely is
that to happen?


I've seen it happen.

Jim


a 4' steel ruler in my shop comes to mind. Scared the hell out me.

Gunner


Lathe Dementia. Recognized as one of the major sub-strains of the
all-consuming virus, Packratitis. Usual symptoms easily recognized
and normally is contracted for life. Can be very contagious.
michael
  #31   Report Post  
Lucky Strike
 
Posts: n/a
Default


"Ignoramus24456" wrote in message
...
On Wed, 2 Mar 2005 17:34:48 -0500, Lucky Strike

wrote:
I'd be just as weary of the $100 as the $1000 guy.

Are you adding a new panel or just a plug? $100 might just about cover

the
materials cost for wire, breakers and a small box.


A subpanel costs $19.99 at home despot. Breakers are about $8
each. wire is 39 cents per foot. A outlet box costs $1. Can't see it
getting to $100 without a long cable run, which the OP indicated is
not in his plans.


How many times have you gone into a buddies house and they start bitching
that they ran out of panel space for their new saw...? Or that they are
tripping over extension cords...

What does $20 get you? Space for 4 breakers?
$20 box
$32 breakers
$39 for 100' cable
------------------------
$91 + taxes

Pretty close to $100. Oh yah, how are you going to strap the cable to the
walls? Maybe run BX instead?

Or do you go to the Borg 6 times because you keep forgetting things and
short ordering cable?

If you are planning on running more equipment you mind as well go 100A

or
better. Mind as well go 200A now that the wife has seen the $1000

quote.

200A may require extensive modification of the service entrance.


Go big or go home....

Just think - you are running a welder or a plasma cutter, the air

compressor
kicks in and your 60A breaker trips...doh!


That's why compressors have disconnects on them .

i


It sucks when you are half way through a cut on the plasma when it kicks out
for low air. Oh well, fire up the a/c for 5 minutes then get back to her
later...

;-)



  #32   Report Post  
Lucky Strike
 
Posts: n/a
Default

it still sparks from hot to ground too

"Gunner" wrote in message
...
On 2 Mar 2005 15:19:22 -0800, jim rozen
wrote:

In article , Ignoramus24456 says...

...Ground up is said to be better if something metallic falls
on a not fully inserted plug, that's a fair thought, but how likely is
that to happen?


I've seen it happen.

Jim


a 4' steel ruler in my shop comes to mind. Scared the hell out me.

Gunner


Lathe Dementia. Recognized as one of the major sub-strains of the
all-consuming virus, Packratitis. Usual symptoms easily recognized
and normally is contracted for life. Can be very contagious.
michael



  #33   Report Post  
jim rozen
 
Posts: n/a
Default

In article , Lucky Strike says...

it still sparks from hot to ground too


If it hits the ground first it's less likely to
get to the hot.

Jim


--
==================================================
please reply to:
JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com
==================================================
  #34   Report Post  
Lucky Strike
 
Posts: n/a
Default


Well, the OP said that the run was very short. Figure one 10 foot
conduit and a few feet of cable.

Or do you go to the Borg 6 times because you keep forgetting things and
short ordering cable?


That, unfortunately, happens a lot. I was lucky with the cable length
for my subpanel project, I ordered 80 feet on nothing more than a
hunch, and ended up using about 75 feet out that 80. As far as
forgetting stuff, Imust confess, it happens too much.


Me too. That's why I keep a roll of 12/3 BX kicking around!


  #35   Report Post  
Gunner
 
Posts: n/a
Default

On Thu, 3 Mar 2005 08:25:48 -0500, Ned Simmons
wrote:

In article ,
says...
On 2 Mar 2005 15:19:22 -0800, jim rozen
wrote:

In article , Ignoramus24456 says...

...Ground up is said to be better if something metallic falls
on a not fully inserted plug, that's a fair thought, but how likely is
that to happen?

I've seen it happen.

Jim


a 4' steel ruler in my shop comes to mind. Scared the hell out me.


The blade of tape measure while taking a measurement behind the
refrigerator. It shorted across the hot pin of the plug and the
refrigerator's condenser resulting in an expensive hiss.

Ned Simmons



Owwww...!

Gunner


Lathe Dementia. Recognized as one of the major sub-strains of the
all-consuming virus, Packratitis. Usual symptoms easily recognized
and normally is contracted for life. Can be very contagious.
michael


  #36   Report Post  
Martin H. Eastburn
 
Posts: n/a
Default

Gunner wrote:

On 2 Mar 2005 22:53:37 GMT, Ignoramus24456
wrote:


On 2 Mar 2005 14:33:48 -0800, jim rozen wrote:

In article , Tim Wescott says...


A long long time ago when my Parent's shop was inspected by OSHA we got
dinged (but not cited) for having outlets with the ground pin up, the
reasoning being that with the pin down the last thing that'll go will be
the safety ground.

Look closely at the a hubbell receptacle. The name appears
rightside up when the ground pin is on the top. That's what
hubbell thinks on the subject, anyway. g

I understand the reason for the ground pin being on top has
to do with the idea that any foreign object which falls down
on the plug will encounter the ground pin rather than a
hot lead - if the plug were partly loose.


Hubbell receptacles are also good enough so that a plug that is
inserted, stays inserted.

i



Sometimes, .no matter how hard you pull.
Gunner



Lathe Dementia. Recognized as one of the major sub-strains of the
all-consuming virus, Packratitis. Usual symptoms easily recognized
and normally is contracted for life. Can be very contagious.
michael

I used Hubbell connectors up to the 300 amp - 5 wire - 3 phase ones.

I started with the 220 V 50 amp stile and worked up to the big Blue ones. :-)
That was in another life. Wish I had a few big ones around now!
Just have some small ones.

Martin

--
Martin Eastburn, Barbara Eastburn
@ home at Lion's Lair with our computer
NRA LOH, NRA Life
NRA Second Amendment Task Force Charter Founder
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFUE, HSPF and COP, how do they relate? [email protected] Home Ownership 37 February 23rd 05 04:03 PM
Help changing circuit breakers Terry Home Repair 13 September 25th 04 10:35 PM
Power cost of idle electric water heater Phil Sherrod Home Ownership 50 April 2nd 04 04:55 PM
Convert radial (cooker) circuit to socket circuit Chi UK diy 3 December 23rd 03 05:48 PM
Case of the unknown circuit David Hearn UK diy 4 November 10th 03 04:12 PM


All times are GMT +1. The time now is 05:13 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"