Hello

I have a single electric socket for my washer which all of a sudden is
only reading 85V. The socket is on its own circuit and I have no idea
why the drop in voltage.

I have removed the socket and tested just the bare wires and get the
same reading.
I have swapped out the circuit breaker (with a known good one) and have
same problem.

What else might be causing this? I am guessing I have a short
somewhere... Any help or suggestions would be appreciated.

Thanks

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default 120V Socket only reading 85V ???

Hello

I checked at the breaker and it was 120... I will double check the wire
connections both at the breaker box and outlet again... Very strange
why this happend all of a sudden. I should be able to check the entire
line in the attick tomorrow to make sure it is not fried somewhere
along the way... In the mean time I am keeping the breaker off.

Thanks

On Dec 11, 1:51 pm, wrote:
wrote:
Hello
I have a single electric socket for my washer which all of a sudden is
only reading 85V. The socket is on its own circuit and I have no idea
why the drop in voltage.
I have removed the socket and tested just the bare wires and get the
same reading.
I have swapped out the circuit breaker (with a known good one) and have
same problem.Are you getting 85V at the breaker? If so, then you've got big problems,

if not then the fault lies in the wiring between the breaker and the
outlet.

Those big problems could be a number of oddball things, possibly power
feeding back through some other device around a break in the system. But
check it the breaker.

What else might be causing this? I am guessing I have a short
somewhere... Any help or suggestions would be appreciated.Thing is, a short that was eating that much power would result in a lot of

heat. You should be able to smell the smoke if this were the case.

John
--
Remove the dead poet to e-mail, tho CC'd posts are unwelcome.
Mean People Suck - It takes two deviations to get cool.
Ask me about joining the NRA.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default 120V Socket only reading 85V ???


ThanksWhat are the other outlets reading on each leg of your 220 in? Maybe the

transformer feeding your house is going bad on one leg? Check each leg and
if one is very dissamaler call your power company and have them look into
it.

Does the washer run OK?

Rich



Nope, washer won't run... I thought it went bad so we ran out and
bought a new one, only to find out the new one wouldnt run either.
Further investigation led me to finding the low voltage issue.

I am not having power issues anywhere else in the house, just this
single circuit.

G



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 818
Default 120V Socket only reading 85V ???

First, some terms.

A "short" is when something is connected, but shouldn't be. An "open"
is something not connected, but should be.

Since you have a VOM, please try reading from the hot to the ground.
If this gives you 110 volts, then the problem is with your neutral.

In any case, it's a good idea every couple years to take a screw
driver and tighten all the neutrals in your breaker box. I know no one
does, but it's a good idea. I've lived at the same adress for 11
years, and not tightened my neutrals.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

wrote in message
oups.com...
Hello

I have a single electric socket for my washer which all of a sudden is
only reading 85V. The socket is on its own circuit and I have no idea
why the drop in voltage.

I have removed the socket and tested just the bare wires and get the
same reading.
I have swapped out the circuit breaker (with a known good one) and
have
same problem.

What else might be causing this? I am guessing I have a short
somewhere... Any help or suggestions would be appreciated.

Thanks


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default 120V Socket only reading 85V ???

OK
I will test the HOT and GROUND and see what voltage I get.

Thanks for the tip.



On Dec 11, 2:28 pm, "Stormin Mormon"
wrote:
First, some terms.

A "short" is when something is connected, but shouldn't be. An "open"
is something not connected, but should be.

Since you have a VOM, please try reading from the hot to the ground.
If this gives you 110 volts, then the problem is with your neutral.

In any case, it's a good idea every couple years to take a screw
driver and tighten all the neutrals in your breaker box. I know no one
does, but it's a good idea. I've lived at the same adress for 11
years, and not tightened my neutrals.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 267
Default 120V Socket only reading 85V ???


Geoff wrote:
OK
I will test the HOT and GROUND and see what voltage I get.



No. Measure hot to neutral. Ideally with some load across the pair,
nearby.

Failing all else, you may want to enlist the services of a pro.
Electrical
power probs can get someone killed, or start a fire. Not good.

J

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default 120V Socket only reading 85V ???

I will check what the circuit reads when having something plugged into
it...

G

Check the voltages at your other outlets. If they read other than 120V,
you might have an open neutral, with other appliances on the
circuit acting as a voltage divider to create a virtual ground.If the OP is using a digital meter, this might also be a completely

dead circuit with an induced voltage on it that will go away if, say, a
lamp is plugged in (which might be a worthwhile test.)

nate


  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default 120V Socket only reading 85V ???

I will test a few more things as suggested here... if I can't figure it
out I will be calling in a pro. Don't worry, I don't want my house to
burn down either.

Thanks everyone for their help / suggestions.
G


On Dec 11, 3:29 pm, wrote:
Geoff wrote:
OK
I will test the HOT and GROUND and see what voltage I get.No. Measure hot to neutral. Ideally with some load across the pair,

nearby.

Failing all else, you may want to enlist the services of a pro.
Electrical
power probs can get someone killed, or start a fire. Not good.

J


  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 22
Default 120V Socket only reading 85V ???


wrote in message
oups.com...
Hello

I have a single electric socket for my washer which all of a sudden is
only reading 85V. The socket is on its own circuit and I have no idea
why the drop in voltage.

I have removed the socket and tested just the bare wires and get the
same reading.
I have swapped out the circuit breaker (with a known good one) and have
same problem.

What else might be causing this? I am guessing I have a short
somewhere... Any help or suggestions would be appreciated.

Thanks


Have you checked your attic for squirrels?? I had one chew right
through the wires, but when I turned on the light, I heard a thump
in the attic...squirrel is no longer chewing..he made a mess!





























  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 458
Default 120V Socket only reading 85V ???

Geoff wrote:
ThanksWhat are the other outlets reading on each leg of your 220
in? Maybe the

transformer feeding your house is going bad on one leg? Check each
leg and if one is very dissamaler call your power company and have
them look into it.

Does the washer run OK?

Rich



Nope, washer won't run... I thought it went bad so we ran out and
bought a new one, only to find out the new one wouldnt run either.
Further investigation led me to finding the low voltage issue.

I am not having power issues anywhere else in the house, just this
single circuit.

G


That pretty much settles it. You said you had 120 at the breaker and 85 at
the plug. Somewhere between the breaker and the plug there is an open - the
wire is broken, a splice is opened up, a wire is off where it passes thru
another outlet, whatever.
The voltage you're reading is called "phantom" voltage and will disappear
if you put any kind of load on it. For instance, plug something into that
outlet and turn it on, but keep it unseated just enough to get your meter
probes on the blades; you'll find it's now reading 0 volts, I'm pretty sure.

HTH
Pop`


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 458
Default 120V Socket only reading 85V ???

Stormin Mormon wrote:
First, some terms.

A "short" is when something is connected, but shouldn't be. An "open"
is something not connected, but should be.

Since you have a VOM, please try reading from the hot to the ground.
If this gives you 110 volts, then the problem is with your neutral.

In any case, it's a good idea every couple years to take a screw
driver and tighten all the neutrals in your breaker box. I know no one
does, but it's a good idea. I've lived at the same adress for 11
years, and not tightened my neutrals.


No, that's NOT a good idea. In fact, it's a good way for somoene who
doesn't know what they're doing to get killed. And probably overtighten all
the connections too. If it was done right, it won't change.

Pop`


  #19   Report Post  
Posted to alt.home.repair
CJT CJT is offline
external usenet poster
 
Posts: 1,155
Default 120V Socket only reading 85V ???

N8N wrote:

CJT wrote:

wrote:


Hello

I have a single electric socket for my washer which all of a sudden is
only reading 85V. The socket is on its own circuit and I have no idea
why the drop in voltage.

I have removed the socket and tested just the bare wires and get the
same reading.
I have swapped out the circuit breaker (with a known good one) and have
same problem.

What else might be causing this? I am guessing I have a short
somewhere... Any help or suggestions would be appreciated.

Thanks


Check the voltages at your other outlets. If they read other than 120V,
you might have an open neutral, with other appliances on the
circuit acting as a voltage divider to create a virtual ground.



If the OP is using a digital meter, this might also be a completely
dead circuit with an induced voltage on it that will go away if, say, a
lamp is plugged in (which might be a worthwhile test.)

nate

Have you calculated how much capacitance (and hence, how many feet of
wire) would be required for that to be so?

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
  #20   Report Post  
Posted to alt.home.repair
CJT CJT is offline
external usenet poster
 
Posts: 1,155
Default 120V Socket only reading 85V ???

Geoff wrote:

I will check what the circuit reads when having something plugged into
it...


Don't forget to turn it on! :-)

G


Check the voltages at your other outlets. If they read other than 120V,
you might have an open neutral, with other appliances on the
circuit acting as a voltage divider to create a virtual ground.If the OP is using a digital meter, this might also be a completely


dead circuit with an induced voltage on it that will go away if, say, a
lamp is plugged in (which might be a worthwhile test.)

nate





--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .


  #22   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default 120V Socket only reading 85V ???

Everyone pretty much nailed the simptoms of the "phantom voltage". I
plugged some Christmas lights (festive I know) into the socket and
re-read the voltage, it dropped to Zero...

I Tested HOT to Ground and get 120V.
Testing HOT to Neutral produced the 0 or 85v (phantom).

So, somewhere in the circuit the Neutral has a bad connection. I will
trace it tomorrow.

Thanks everyone for your assistance...

I also read a little bit about basic home wiring, so I have a better
understanding of what is going on now....

Thanks
Geoff


On Dec 11, 7:26 pm, "Pop`" wrote:

GThat pretty much settles it. You said you had 120 at the breaker and 85 at

the plug. Somewhere between the breaker and the plug there is an open - the
wire is broken, a splice is opened up, a wire is off where it passes thru
another outlet, whatever.
The voltage you're reading is called "phantom" voltage and will disappear
if you put any kind of load on it. For instance, plug something into that
outlet and turn it on, but keep it unseated just enough to get your meter
probes on the blades; you'll find it's now reading 0 volts, I'm pretty sure.

HTH
Pop`


  #23   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 818
Default 120V Socket only reading 85V ???

Do you remember the Aesops fable of the man, the boy and the donkey?
It applies, here.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"Geoff" wrote in message
ups.com...
I will check what the circuit reads when having something plugged into
it...

G

Check the voltages at your other outlets. If they read other than

120V,
you might have an open neutral, with other appliances on the
circuit acting as a voltage divider to create a virtual ground.If

the OP is using a digital meter, this might also be a completely
dead circuit with an induced voltage on it that will go away if,

say, a
lamp is plugged in (which might be a worthwhile test.)

nate



  #24   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 818
Default 120V Socket only reading 85V ???

OK, now we have two opinions. Do I hear three?

More seriously, you're right that unskooled people ought not be
mucking about in panel boxes.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"Pop`" wrote in message
news:BBnfh.5138$bj5.1012@trnddc07...
Stormin Mormon wrote:

In any case, it's a good idea every couple years to take a screw
driver and tighten all the neutrals in your breaker box. I know no

one
does, but it's a good idea. I've lived at the same adress for 11
years, and not tightened my neutrals.


No, that's NOT a good idea. In fact, it's a good way for somoene who
doesn't know what they're doing to get killed. And probably
overtighten all
the connections too. If it was done right, it won't change.

Pop`



  #25   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 818
Default 120V Socket only reading 85V ???

Please remit $87.50 for internet consultation.

--

Christopher A. Young
You can't shout down a troll.
You have to starve them.
..

"Geoff" wrote in message
ups.com...
Everyone pretty much nailed the simptoms of the "phantom voltage". I
plugged some Christmas lights (festive I know) into the socket and
re-read the voltage, it dropped to Zero...

I Tested HOT to Ground and get 120V.
Testing HOT to Neutral produced the 0 or 85v (phantom).

So, somewhere in the circuit the Neutral has a bad connection. I will
trace it tomorrow.

Thanks everyone for your assistance...

I also read a little bit about basic home wiring, so I have a better
understanding of what is going on now....

Thanks
Geoff






Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is Canada 120V or 220v? Phil Marshall Home Repair 18 April 8th 17 03:34 PM
FA: 120V DC motor, rated 2.65 HP William B Noble (don't reply to this address) Metalworking 0 December 14th 05 12:58 AM
120V AC connector Ron Russell Electronics 1 November 17th 05 11:06 AM
how to 220V-->120V? blurp Home Ownership 6 August 27th 04 07:39 PM
250v to 120v jm Electronics Repair 13 August 15th 03 04:02 AM


All times are GMT +1. The time now is 08:22 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"