Hi, I want to install cabinet lights in my kitchen and I'm not sure if what I want to do is safe (or code compliant).
The lights are an LED panel with a built in transformer, with bare leads intended to be hardwired inside the wall, and a remote switch. Is it ok to install these lights behind an existing 20 amp outlet? The only input specs on the package are "120V". The output specs are "24V, max 14.7W" Thanks! |
#2
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
"car13" wrote in message ... Hi, I want to install cabinet lights in my kitchen and I'm not sure if what I want to do is safe (or code compliant). The lights are an LED panel with a built in transformer, with bare leads intended to be hardwired inside the wall, and a remote switch. Is it ok to install these lights behind an existing 20 amp outlet? The only input specs on the package are "120V". The output specs are "24V, max 14.7W" It should be as safe as any lights. Hopefully the built in transformer will have a fuse internal to it rated for the lights. |
#3
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On 2/22/2016 11:53 AM, car13 wrote:
Hi, I want to install cabinet lights in my kitchen and I'm not sure if what I want to do is safe (or code compliant). The lights are an LED panel with a built in transformer, with bare leads intended to be hardwired inside the wall, and a remote switch. Is it ok to install these lights behind an existing 20 amp outlet? The only input specs on the package are "120V". The output specs are "24V, max 14.7W" Two different issues, here. First, neither the lights nor the circuit will care. The circuit can more than adequately supply the load. And, the lights don't care where their ~15W of power come from (as long as there are no YELLOW electrons involved! Damn pesky things... : ) But, your reference to "behind an existing 20A outlet" suggests you want to hard-wire them to one of the two GFCI counter-top branch circuits intended for use in a kitchen. There, you run afoul of code as you are now installing a fixed load (albeit small) that defeats the purpose of having "two 20A GFCI circuits for SMALL APPLIANCES" [I.e., why not connect the refrigerator there, as well? Ans: don't!] |
#4
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Monday, February 22, 2016 at 2:03:59 PM UTC-5, Don Y wrote:
On 2/22/2016 11:53 AM, car13 wrote: Hi, I want to install cabinet lights in my kitchen and I'm not sure if what I want to do is safe (or code compliant). The lights are an LED panel with a built in transformer, with bare leads intended to be hardwired inside the wall, and a remote switch. Is it ok to install these lights behind an existing 20 amp outlet? The only input specs on the package are "120V". The output specs are "24V, max 14.7W" Two different issues, here. First, neither the lights nor the circuit will care. The circuit can more than adequately supply the load. And, the lights don't care where their ~15W of power come from (as long as there are no YELLOW electrons involved! Damn pesky things... : ) But, your reference to "behind an existing 20A outlet" suggests you want to hard-wire them to one of the two GFCI counter-top branch circuits intended for use in a kitchen. There, you run afoul of code as you are now installing a fixed load (albeit small) that defeats the purpose of having "two 20A GFCI circuits for SMALL APPLIANCES" [I.e., why not connect the refrigerator there, as well? Ans: don't!] IDK exactly what "behind an existing 20A outlet really means", but as far as the code goes, I think you probably have a point regarding code and connecting it to one of the 20A appliance circuits, which are supposed to be only for plug-in appliances. However, it is perfectly safe and for just 14W worth of LED lights, I know what I'd do..... Unless some other circuit is easily available, of course. |
#5
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Monday, February 22, 2016 at 1:53:48 PM UTC-5, car13 wrote:
Hi, I want to install cabinet lights in my kitchen and I'm not sure if what I want to do is safe (or code compliant). The lights are an LED panel with a built in transformer, with bare leads intended to be hardwired inside the wall, and a remote switch. Is it ok to install these lights behind an existing 20 amp outlet? The only input specs on the package are "120V". The output specs are "24V, max 14.7W" Thanks! "Is it ok to install these lights behind an existing 20 amp outlet?" If you install them behind an outlet, they are not going to cast much light. ;-) What do you mean by "behind an outlet"? |
#6
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On 02/22/2016 12:32 PM, DerbyDad03 wrote:
On Monday, February 22, 2016 at 1:53:48 PM UTC-5, car13 wrote: Hi, I want to install cabinet lights in my kitchen and I'm not sure if what I want to do is safe (or code compliant). The lights are an LED panel with a built in transformer, with bare leads intended to be hardwired inside the wall, and a remote switch. Is it ok to install these lights behind an existing 20 amp outlet? The only input specs on the package are "120V". The output specs are "24V, max 14.7W" Thanks! "Is it ok to install these lights behind an existing 20 amp outlet?" If you install them behind an outlet, they are not going to cast much light. ;-) What do you mean by "behind an outlet"? He means wiring them into the wire nuts behind a regular outlet, ie not wiring them to a plug that is plugged into the outlet. Jon |
#7
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy).
|
#8
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Monday, February 22, 2016 at 6:44:43 PM UTC-5, wrote:
Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). In that case... Safe? Probably. Code? Probably not. See trader_4's response for the reason. |
#9
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
|
#10
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
|
#11
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote:
On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. The wires might not be suitable for adding a plug, perhaps because of physical issues, perhaps because of aesthetics. |
#12
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Mon, 22 Feb 2016 10:53:42 -0800 (PST), car13
wrote: Hi, I want to install cabinet lights in my kitchen and I'm not sure if what I want to do is safe (or code compliant). The lights are an LED panel with a built in transformer, with bare leads I missed this part. Bare leads or not, buy a plug and connect it to the leads. You probably need a plug with screw connectors. Do they still sell the small 2-prong ones? Yeah, but nowhere near as many styles as befo http://www.homedepot.com/p/Leviton-1...-0DE/202077705 and maybe these two http://www.homedepot.com/p/Leviton-1...-0WP/100356964 http://www.homedepot.com/p/Leviton-1...-00W/202077684 but the video in all 3 cases is unrelated to the plug, so I can't tell if either of these have screws inside. Probably not. Forget I mentioned them. And if it says Quick in the name, probably won't work either. It's good to save the cords from things one throws away, so you can solder a plug and a few inches of cord onto bare wires or when a plug fails. I have a box of 20 of these already, in various colors. intended to be hardwired inside the wall, Maybe. But maybe meant to be sold in Europe too so they dont' know what plug to put on the end. and a remote switch. Is it ok to install these lights behind an existing 20 amp outlet? The only input specs on the package are "120V". This sort of contradicts that idea, but I still can't imagine selling something that requires wires coming out of the wall beside or through the wall plate. I've done that with my TV co-ax, with my bathroom speaker wires, and with an telephone extension flashing light (for when the bell is off but I'm awake, so I'll know the phone is ringing.) I certainly wouldn't do it with 110V. The output specs are "24V, max 14.7W" IOW max 0.6 amps output. FWIW, if it outputs 14.7w, the input actually used is less than twice** that, less than 1.2 amps. But if the wires short to each other or ground, you'll see a spark far bigger than that. **Twice would mean only 50% efficiency, and transformers are better than that. Thanks! |
#13
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03
wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. How bad can a plug be? Or a 6-in-1? What's your alternative? |
#14
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Mon, 22 Feb 2016 23:27:55 -0500, Micky
wrote: Screw aesthetics. How bad can a plug be? I partly take this back. The big rubber plugs that go on industrial extensions cords would look bad almost anywhere -- I agree -- and those are still easy to get. I guess if that is all there were, that's what I'd use. But HD still sells one model that's small. And I've been planning ahead so I have extra plugs, that I bought to be sure of having one when I need it; I have two really thin plugs meant to go behind a dresser, so they're less than 1/2" thick, with the wire coming out of the side**; I have the cords with plugs permanently attached: and before I throw anything in the trash, I take the cord, or the plug if it unscrews. I'm hoping to go to Guatemala within a couple years, and I think I'll see what they sell. I like shopping for hardware when I'm out of the country, if there's something I need. **I'm saving these for where space is a problem, but if needed I could use them elsewhere and just remember where I'm using them in case I actually do need thin ones. They dont use screws, just metal prongs, but they work with standard lamp cord (which is also becoming less common.) |
#15
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Mon, 22 Feb 2016 12:32:17 -0800 (PST), DerbyDad03
wrote: "Is it ok to install these lights behind an existing 20 amp outlet?" If you install them behind an outlet, they are not going to cast much light. ;-) They will light the space inside the wall, between the 2 studs on each side of that outlet. Maybe he could then put a glass block or two into that wall so the light can be seen. |
#16
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote:
On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. I know you took this back later (partly), but even to have made this comment in the first place was almost enough to make me realize that this conversation probably isn't worth having with you. However, I'll use it as teaching moment. Kitchens are often the most important room in the house and some people put more money into the blending of aesthetics and functionality in a kitchen than they do in any other room. How bad can a plug be? Going back to the aesthetics issue, you have no idea what the wires on the transformer look like. What if they look like this? http://cdn.instructables.com/FQT/ORX...55S5.LARGE.jpg Are you just going to put a plug on these wires? I hope not, but since kitchen aesthetics don't matter to you, maybe you would. As far as extending the bare lead wires with a spare cord, where would store the connections? The wires nuts would have to go in a junction box. After you've done that, how do you plan to have the cord come out of the junction box so you can plug it in? Or a 6-in-1? What's your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. |
#17
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote:
On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. How bad can a plug be? Or a 6-in-1? What's your alternative? The alternative would be to do what he apparently suggested in his first post, wire it into an existing circuit that feeds a receptacle. That may be a code violation, because current code requires 20A circuits for appliances to be plugged in and AFAIK, you can't put other loads on it. But it's a 14W LED and insignificant as far as effecting the ampacity, so I could live with it. I'm not sure it even is a code problem. The 20A circuit reqt for receptacles is relatively new. If he has an older house, not subject to that at the time, IDK if it really is a code violation, ie what says that he can't tap into an existing circuit? He's adding an LED, not adding counter receptacles. |
#18
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Monday, February 22, 2016 at 11:24:31 PM UTC-5, Micky wrote:
This sort of contradicts that idea, but I still can't imagine selling something that requires wires coming out of the wall beside or through the wall plate. I can pretty much guarantee that the install instructions don't say to do it that way. The correct way would be to wire it into a junction box and I would hope that's what the instructions would say. I've done that with my TV co-ax, with my bathroom speaker wires, and with an telephone extension flashing light (for when the bell is off but I'm awake, so I'll know the phone is ringing.) I certainly wouldn't do it with 110V. The output specs are "24V, max 14.7W" IOW max 0.6 amps output. FWIW, if it outputs 14.7w, the input actually used is less than twice** that, less than 1.2 amps. But if the wires short to each other or ground, you'll see a spark far bigger than that. Wrong concept here. What you look at is *power* on both sides. The secondary is 15W, that means ideally, the primary is 15W, giving a current of 125ma at 120V. It will be a bit more than that because of losses, but that's the conversion concept. Using your method, a battery charger that supplies 25A, would be pulling less than 50A? It sure would be less than 50A, because it's on the order of 2.5A @ 120V **Twice would mean only 50% efficiency, and transformers are better than that. See above. You're using equal currents on both sides, when it's actually equal power. |
#19
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tuesday, February 23, 2016 at 8:18:11 AM UTC-5, trader_4 wrote:
On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. How bad can a plug be? Or a 6-in-1? What's your alternative? The alternative would be to do what he apparently suggested in his first post, wire it into an existing circuit that feeds a receptacle. I'm still trying to picture how that would be done from a physical perspective. Assuming the GFCI is in a standard receptacle box, the connections would need to made inside the wall and inside the box. I guess I'd like to see his "bare lead" transformer, but if it's similar to the one that I linked to, it has to be mounted someplace and then the wires have to somehow have to pass through the wall and into the receptacle box. It sounds like flush mount junction box would be required to accept the wires from the transformer (with a proper fitting of course) and then Romex would need to be run from that junction box to the receptacle box. Perhaps there is an existing (remote) junction box for the receptacle circuit that could be used, but then the wires need to be run from the transformer back to the fixture itself. It seems like we are adding more complexity, and therefore possibly more code issues, than just using an existing lighting circuit or even new circuit if need be (and possible). Am I missing something simple on the "physical installation" front? That may be a code violation, because current code requires 20A circuits for appliances to be plugged in and AFAIK, you can't put other loads on it. But it's a 14W LED and insignificant as far as effecting the ampacity, so I could live with it. I'm not sure it even is a code problem. The 20A circuit reqt for receptacles is relatively new. If he has an older house, not subject to that at the time, IDK if it really is a code violation, ie what says that he can't tap into an existing circuit? He's adding an LED, not adding counter receptacles. |
#20
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tuesday, February 23, 2016 at 9:59:32 AM UTC-5, DerbyDad03 wrote:
On Tuesday, February 23, 2016 at 8:18:11 AM UTC-5, trader_4 wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. How bad can a plug be? Or a 6-in-1? What's your alternative? The alternative would be to do what he apparently suggested in his first post, wire it into an existing circuit that feeds a receptacle. I'm still trying to picture how that would be done from a physical perspective. Assuming the GFCI is in a standard receptacle box, the connections would need to made inside the wall and inside the box. I guess I'd like to see his "bare lead" transformer, but if it's similar to the one that I linked to, it has to be mounted someplace and then the wires have to somehow have to pass through the wall and into the receptacle box. It sounds like flush mount junction box would be required to accept the wires from the transformer (with a proper fitting of course) and then Romex would need to be run from that junction box to the receptacle box. Perhaps there is an existing (remote) junction box for the receptacle circuit that could be used, but then the wires need to be run from the transformer back to the fixture itself. It seems like we are adding more complexity, and therefore possibly more code issues, than just using an existing lighting circuit or even new circuit if need be (and possible). Am I missing something simple on the "physical installation" front? I don't think so. Most of the LED things like under counter lights are probably added in some half-assed way by the homeowner or they are made with a transformer that has a plug. I've seen hardwired ones done right with the transformer mounted inside a cabinet or down in the basement. Depending on where it's going, the plug in type could be fine, assuming it's off to the side, behind some counter appliance, etc where the cord isn't objectionable. |
#21
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tuesday, February 23, 2016 at 10:06:16 AM UTC-5, trader_4 wrote:
On Tuesday, February 23, 2016 at 9:59:32 AM UTC-5, DerbyDad03 wrote: On Tuesday, February 23, 2016 at 8:18:11 AM UTC-5, trader_4 wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. How bad can a plug be? Or a 6-in-1? What's your alternative? The alternative would be to do what he apparently suggested in his first post, wire it into an existing circuit that feeds a receptacle. I'm still trying to picture how that would be done from a physical perspective. Assuming the GFCI is in a standard receptacle box, the connections would need to made inside the wall and inside the box. I guess I'd like to see his "bare lead" transformer, but if it's similar to the one that I linked to, it has to be mounted someplace and then the wires have to somehow have to pass through the wall and into the receptacle box. It sounds like flush mount junction box would be required to accept the wires from the transformer (with a proper fitting of course) and then Romex would need to be run from that junction box to the receptacle box. Perhaps there is an existing (remote) junction box for the receptacle circuit that could be used, but then the wires need to be run from the transformer back to the fixture itself. It seems like we are adding more complexity, and therefore possibly more code issues, than just using an existing lighting circuit or even new circuit if need be (and possible). Am I missing something simple on the "physical installation" front? I don't think so. Most of the LED things like under counter lights are probably added in some half-assed way by the homeowner or they are made with a transformer that has a plug. I've seen hardwired ones done right with the transformer mounted inside a cabinet or down in the basement. Depending on where it's going, the plug in type could be fine, assuming it's off to the side, behind some counter appliance, etc where the cord isn't objectionable. But he specifically said: "The lights are an LED panel with a built in transformer, with bare leads intended to be hardwired inside the wall, and a remote switch. " I thought that we discussing his exact situation, not a situation where a plug in type transformer is present. OK, so his transformer isn't like the freestanding one that I linked to, but it sure sounds like that style of transformer is inside the fixture. Bottom line is that he has 2 bare wires that he has to attach to a 110VAC source. |
#22
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
15 amps of lights, on a 20 amp circuit. Does
not leave much capacity for other devices which might be plugged in. -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#24
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tue, 23 Feb 2016 05:27:58 -0800 (PST), trader_4
wrote: On Monday, February 22, 2016 at 11:24:31 PM UTC-5, Micky wrote: ... The output specs are "24V, max 14.7W" IOW max 0.6 amps output. FWIW, if it outputs 14.7w, the input actually used is less than twice** that, less than 1.2 amps. But if the wires short to each other or ground, you'll see a spark far bigger than that. Wrong concept here. Not wrong concept but a calculation that didn't match my concept. Thanks for the correction, |
#25
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tuesday, February 23, 2016 at 11:13:52 AM UTC-5, Stormin Mormon wrote:
15 amps of lights, on a 20 amp circuit. Does not leave much capacity for other devices which might be plugged in. -- . Christopher A. Young learn more about Jesus . www.lds.org . . What 15 amps? It's a an LED, 15 watts. |
#26
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tue, 23 Feb 2016 05:18:00 -0800 (PST), trader_4
wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. How bad can a plug be? Or a 6-in-1? What's your alternative? The alternative would be to do what he apparently suggested in his first For the record, FWIW, I was really just asking Derby because he got my goat. post, wire it into an existing circuit that feeds a receptacle. That may be a code violation, because current code requires 20A circuits for If it's against code, I'm not counting it as an alternative. We're talking about a wire coming straight out of the wall, from an opening in a junction box within the wall, aren't we? How could that not be a code violation? appliances to be plugged in and AFAIK, you can't put other loads on it. But it's a 14W LED and insignificant as far as effecting the ampacity, so I could live with it. I'm not sure it even is a code problem. The 20A circuit reqt for In your other reply to me, iiuc in place of a wire coming out of the wall, from a junction box within the wall, you were suggesting a surface mount junction box. I think that would be less aethetically pleasing than a plug on a wire. receptacles is relatively new. If he has an older house, not subject to that at the time, IDK if it really is a code violation, ie what says that he can't tap into an existing circuit? He's adding an LED, not adding counter receptacles. |
#27
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tue, 23 Feb 2016 04:40:23 -0800 (PST), DerbyDad03
wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. I know you took this back later (partly), Twice. Once in the next two words and once in the follow-up post. To be honest, "Screw aesthetics" was directed to you, not the OP. I know he's not going to ignore aesthetics and I wouldn't either, but you got my goat with the absurd implication that a plug on the end of a wire could be unaesthetic, based perhaps on the absurd idea that a wire he would find** on his transformer could be too ugly for a plug. Most people with kitchens have things with plugs plugged in, the toaster, the blender, a George Foreman grill, a radio, a tv, a microwave, a Mixmaster, one or more device chargers, and maybe other things (an electric rotisserie?). Putting a plug on his cord will not detract from the appearance of the kitchen. **An industrial strength extension cord would look bad plugged into a kitchen outlet, but you won't find that on a 25 watt device. but even to have made this comment in the first place was almost enough to make me realize that this conversation probably isn't worth having with you. However, I'll use it as teaching moment. Kitchens are often the most important room in the house and some people put more money into the blending of aesthetics and functionality in a kitchen than they do in any other room. How bad can a plug be? Going back to the aesthetics issue, you have no idea what the wires on the transformer look like. What if they look like this? http://cdn.instructables.com/FQT/ORX...55S5.LARGE.jpg What's wrong with them? I'd put on the plug whose url I gave in the other post (in reply to his first post). If that didn't leave a long enough wire to mount the box somewhere decent, like under the cabinets hidden by the cabinet skirt (where I have my extra light) I'd add some wire too. Are you just going to put a plug on these wires? I hope not, but since kitchen aesthetics don't matter to you, maybe you would. As far as extending the bare lead wires with a spare cord, where would store the connections? What connections? The wires nuts What wire nuts? If the wire is not long enough, I'd solder more wire to it, with the connections offset from each other so there is no chance of shorting and so the bulge would be smaller, though longer. would have to go in a junction box. After you've done that, how do you plan to have the cord come out of the junction box so you can plug it in? What junction box? Or a 6-in-1? What's your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. That's a total non-answer. What is your alternative? |
#28
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tuesday, February 23, 2016 at 1:11:32 PM UTC-5, Micky wrote:
On Tue, 23 Feb 2016 05:18:00 -0800 (PST), trader_4 wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. How bad can a plug be? Or a 6-in-1? What's your alternative? The alternative would be to do what he apparently suggested in his first For the record, FWIW, I was really just asking Derby because he got my goat. post, wire it into an existing circuit that feeds a receptacle. That may be a code violation, because current code requires 20A circuits for If it's against code, I'm not counting it as an alternative. We're talking about a wire coming straight out of the wall, from an opening in a junction box within the wall, aren't we? How could that not be a code violation? The OP didn't say that was how he was going to do it. It wasn't clear what he was going to do, unless you're a mind reader: "Is it ok to install these lights behind an existing 20 amp outlet?" The possible code violation I was addressing was the issue that Don brought up. Current code requires dedicated 20A circuits for kitchen appliances. If it's a circuit that was subject to that, then according to Don, adding some other wired in load is not code compliant. And I think he's probably right, but I'm not going to go look it up. appliances to be plugged in and AFAIK, you can't put other loads on it. But it's a 14W LED and insignificant as far as effecting the ampacity, so I could live with it. I'm not sure it even is a code problem. The 20A circuit reqt for In your other reply to me, iiuc in place of a wire coming out of the wall, from a junction box within the wall, you were suggesting a surface mount junction box. I think that would be less aethetically pleasing than a plug on a wire. I never suggested a surface mount junction box. If you want another solution, how about finding one of the many other LED alternatives that have transformers that you can plug in? Or at least a transformer that is separate from the led fixture? |
#29
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Mon, 22 Feb 2016 10:53:42 -0800 (PST), car13
wrote: The lights are an LED panel with a built in transformer, with bare leads I really hope those "Bare Leads" are really insulated wire!!! Otherwise there could be a serious fire hazzard as code violation! |
#30
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tuesday, February 23, 2016 at 1:13:06 PM UTC-5, Micky wrote:
On Tue, 23 Feb 2016 04:40:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. I know you took this back later (partly), Twice. Once in the next two words and once in the follow-up post. To be honest, "Screw aesthetics" was directed to you, not the OP. I know he's not going to ignore aesthetics and I wouldn't either, but you got my goat with the absurd implication that a plug on the end of a wire could be unaesthetic, based perhaps on the absurd idea that a wire he would find** on his transformer could be too ugly for a plug. Why do you consider that an absurd implication? He specifically said: "with bare leads intended to be hardwired inside the wall" not "with bare leads intended to have a plug attached" Neither of us know what those "bare leads" look like, but I'm leaning towards them *not* looking like the cord on my KitchenAid Artisan stand mixer. Since he said the leads were "intended to be hardwired inside the wall" we can be pretty sure that they did not use an appliance cord, because appliance cords are not intended to be hardwired inside the wall. Of course, his description could be wrong. Neither of us know, therefore my "implication" is no more absurd than your idea of just soldering on cord with a plug. A picture would, as always, be helpful. Most people with kitchens have things with plugs plugged in, the toaster, the blender, a George Foreman grill, a radio, a tv, a microwave, a Mixmaster, one or more device chargers, and maybe other things (an electric rotisserie?). Putting a plug on his cord will not detract from the appearance of the kitchen. You can't make that assertion without knowing what the "bare leads intended to be hardwired inside the wall" look like. Again, based on his use of the words "intended to be hardwired inside the wall" I lean away from the simple attachment of a plug being aesthetically pleasing. In fact, it may not even be to code. **An industrial strength extension cord would look bad plugged into a kitchen outlet, but you won't find that on a 25 watt device. but even to have made this comment in the first place was almost enough to make me realize that this conversation probably isn't worth having with you. However, I'll use it as teaching moment. Kitchens are often the most important room in the house and some people put more money into the blending of aesthetics and functionality in a kitchen than they do in any other room. How bad can a plug be? Going back to the aesthetics issue, you have no idea what the wires on the transformer look like. What if they look like this? http://cdn.instructables.com/FQT/ORX...55S5.LARGE.jpg What's wrong with them? I'd put on the plug whose url I gave in the other post (in reply to his first post). If that didn't leave a long enough wire to mount the box somewhere decent, like under the cabinets hidden by the cabinet skirt (where I have my extra light) I'd add some wire too. Are you just going to put a plug on these wires? I hope not, but since kitchen aesthetics don't matter to you, maybe you would. As far as extending the bare lead wires with a spare cord, where would store the connections? What connections? The wires nuts What wire nuts? If the wire is not long enough, I'd solder more wire to it, with the connections offset from each other so there is no chance of shorting and so the bulge would be smaller, though longer. would have to go in a junction box. After you've done that, how do you plan to have the cord come out of the junction box so you can plug it in? What junction box? It's obvious that you are picturing a totally different set of leads coming out the device than I am. Once again, a picture would be, as always, helpful. Or a 6-in-1? What's your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. That's a total non-answer. What is your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. That is the only answer I can give until I know what the "bare leads intended to be hardwired inside the wall" actually look like. In the end, that will still be answer, but it will probably have some more details added once I know what he is working with. |
#31
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On 2/23/2016 12:19 PM, trader_4 wrote:
On Tuesday, February 23, 2016 at 11:13:52 AM UTC-5, Stormin Mormon wrote: 15 amps of lights, on a 20 amp circuit. Does not leave much capacity for other devices which might be plugged in. -- . Christopher A. Young learn more about Jesus . www.lds.org . . What 15 amps? It's a an LED, 15 watts. The subject of this thread is a 15 amp cabinet lights. THAT 15 amps. -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#32
Posted to alt.home.repair
|
|||
|
|||
Ping Todd
.... you owe me big time friend. Standing it line for an hour to "cockus". Three minutes to cast my selection on a paper ballot. We need to go back to the primary before 2008 change and vote electronically. I could vote and be gone in 10 minutes at my precinct. Shish. When I signed your tax referendum, twenty minutes to find out anybody that could give it to me -- I was the first one to sign it. Are people paying attention or what? I had to stand beside Donald Trump, Jr. too, while I waited for the petition to be found and listen to 30-50 seconds of his speech of how great his amazing father is. Looked like he had one of those $800 hair cuts for cripes sake. Shish. P.S. you can help vote against that stinking Bllomberg gun initiative in June, please. Oh, the misery I suffered tonight :-) |
#33
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tuesday, February 23, 2016 at 6:32:00 PM UTC-5, Stormin Mormon wrote:
On 2/23/2016 12:19 PM, trader_4 wrote: On Tuesday, February 23, 2016 at 11:13:52 AM UTC-5, Stormin Mormon wrote: 15 amps of lights, on a 20 amp circuit. Does not leave much capacity for other devices which might be plugged in. -- . Christopher A. Young learn more about Jesus . www.lds.org . . What 15 amps? It's a an LED, 15 watts. The subject of this thread is a 15 amp cabinet lights. THAT 15 amps. -- Yes, you're right. Funny no one else commented on that. IDK what that's all about. |
#34
Posted to alt.home.repair
|
|||
|
|||
Ping Todd
On Tuesday, February 23, 2016 at 10:10:40 PM UTC-5, Oren wrote:
... you owe me big time friend. Standing it line for an hour to "cockus". Three minutes to cast my selection on a paper ballot. We need to go back to the primary before 2008 change and vote electronically. I could vote and be gone in 10 minutes at my precinct. Shish. When I signed your tax referendum, twenty minutes to find out anybody that could give it to me -- I was the first one to sign it. Are people paying attention or what? I had to stand beside Donald Trump, Jr. too, while I waited for the petition to be found and listen to 30-50 seconds of his speech of how great his amazing father is. Looked like he had one of those $800 hair cuts for cripes sake. Shish. P.S. you can help vote against that stinking Bllomberg gun initiative in June, please. Oh, the misery I suffered tonight :-) If we could just ban the use of the words "amazing" and "tremendous" we could shut up the whole Trump family. I was watching Donald give a 2 min interview and he used one 3 times, the other twice. |
#35
Posted to alt.home.repair
|
|||
|
|||
Ping Todd
On Wednesday, February 24, 2016 at 8:26:10 AM UTC-5, trader_4 wrote:
On Tuesday, February 23, 2016 at 10:10:40 PM UTC-5, Oren wrote: ... you owe me big time friend. Standing it line for an hour to "cockus". Three minutes to cast my selection on a paper ballot. We need to go back to the primary before 2008 change and vote electronically. I could vote and be gone in 10 minutes at my precinct. Shish. When I signed your tax referendum, twenty minutes to find out anybody that could give it to me -- I was the first one to sign it. Are people paying attention or what? I had to stand beside Donald Trump, Jr. too, while I waited for the petition to be found and listen to 30-50 seconds of his speech of how great his amazing father is. Looked like he had one of those $800 hair cuts for cripes sake. Shish. P.S. you can help vote against that stinking Bllomberg gun initiative in June, please. Oh, the misery I suffered tonight :-) If we could just ban the use of the words "amazing" and "tremendous" we could shut up the whole Trump family. I was watching Donald give a 2 min interview and he used one 3 times, the other twice. Guys...please. It would be "amazing" and "tremendous" if we could limit the discussion in this thread to the installation of the LED fixture. |
#36
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On 02/23/2016 05:32 PM, Stormin Mormon wrote:
[snip] What 15 amps? It's a an LED, 15 watts. The subject of this thread is a 15 amp cabinet lights. THAT 15 amps. So you have a 1800 watt (15A * 120V) light. Maybe it's a warming cabinet (to keep food warm). Put in a dedicated circuit for that. -- "I don't know if God exists, but it would be better for His reputation if He didn't." -- Jules Renard |
#37
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Tue, 23 Feb 2016 13:58:34 -0800 (PST), DerbyDad03
wrote: On Tuesday, February 23, 2016 at 1:13:06 PM UTC-5, Micky wrote: On Tue, 23 Feb 2016 04:40:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. I know you took this back later (partly), Twice. Once in the next two words and once in the follow-up post. To be honest, "Screw aesthetics" was directed to you, not the OP. I know he's not going to ignore aesthetics and I wouldn't either, but you got my goat with the absurd implication that a plug on the end of a wire could be unaesthetic, based perhaps on the absurd idea that a wire he would find** on his transformer could be too ugly for a plug. Why do you consider that an absurd implication? He specifically said: "with bare leads intended to be hardwired inside the wall" not "with bare leads intended to have a plug attached" Neither of us know what those "bare leads" look like, but I'm leaning towards them *not* looking like the cord on my KitchenAid Artisan stand mixer. Since he said the leads were "intended to be hardwired inside the wall" we can be pretty sure that they did not use an appliance cord, because appliance cords are not intended to be hardwired inside the wall. This is all so silly since he could solve most of this by posting back and addressing our questions, implied and explicit. But I took "intended" to refer to a drawing or instructions that came with the light and nothing to do with the wires' actual appearance. If you consider that possibility, we might have opinions closer to each other than they are now. Of course, his description could be wrong. Neither of us know, therefore my "implication" is no more absurd than your idea of just soldering on cord with a plug. A picture would, as always, be helpful. True. Most people with kitchens have things with plugs plugged in, the toaster, the blender, a George Foreman grill, a radio, a tv, a microwave, a Mixmaster, one or more device chargers, and maybe other things (an electric rotisserie?). Putting a plug on his cord will not detract from the appearance of the kitchen. You can't make that assertion without knowing what the "bare leads intended to be hardwired inside the wall" look like. Well, they don't look like alligators. They look like wires. Again, based on his use of the words "intended to be hardwired inside the wall" I lean away from the simple attachment of a plug being aesthetically pleasing. In fact, it may not even be to code. What in the code prevents connecting two 14, 16, or 18 gauge wires to a plug? ........... would have to go in a junction box. After you've done that, how do you plan to have the cord come out of the junction box so you can plug it in? What junction box? It's obvious that you are picturing a totally different set of leads coming out the device than I am. Once again, a picture would be, as always, helpful. Or a 6-in-1? What's your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. That's a total non-answer. What is your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. So as yet, you don't have an alternative. That is the only answer I can give until I know what the "bare leads intended to be hardwired inside the wall" actually look like. In the end, that will still be answer, but it will probably have some more details added once I know what he is working with. |
#38
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
On Wednesday, February 24, 2016 at 12:07:48 PM UTC-5, Micky wrote:
On Tue, 23 Feb 2016 13:58:34 -0800 (PST), DerbyDad03 wrote: On Tuesday, February 23, 2016 at 1:13:06 PM UTC-5, Micky wrote: On Tue, 23 Feb 2016 04:40:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:28:20 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 20:18:23 -0800 (PST), DerbyDad03 wrote: On Monday, February 22, 2016 at 11:04:29 PM UTC-5, Micky wrote: On Mon, 22 Feb 2016 15:44:36 -0800 (PST), wrote: Yep, what Jon said. Sorry, I'm not super familiar with electrical terminology (I'm a mechanical guy). No you may not do that. Why not just get one of those 6 in 1 outlets, that plug into to a duplex outlet (like you have) and have a center screw so they don't pull out when you pull out a plug. They come with 3 prong sockets. These days, even a properly wired house is likely to have many more appliances and little black boxes than the number of receptacles, even if you don't use more than one or two of the big ones at once. He does not have a plug on the end of the leads from the transformer. Yeah, I missed that when replying to his second post, but then I read his first post again. The wires might not be suitable for adding a plug, perhaps because of physical issues, What phyical issues could those be? perhaps because of aesthetics. It's the kitchen. Screw aesthetics. I know you took this back later (partly), Twice. Once in the next two words and once in the follow-up post. To be honest, "Screw aesthetics" was directed to you, not the OP. I know he's not going to ignore aesthetics and I wouldn't either, but you got my goat with the absurd implication that a plug on the end of a wire could be unaesthetic, based perhaps on the absurd idea that a wire he would find** on his transformer could be too ugly for a plug. Why do you consider that an absurd implication? He specifically said: "with bare leads intended to be hardwired inside the wall" not "with bare leads intended to have a plug attached" Neither of us know what those "bare leads" look like, but I'm leaning towards them *not* looking like the cord on my KitchenAid Artisan stand mixer. Since he said the leads were "intended to be hardwired inside the wall" we can be pretty sure that they did not use an appliance cord, because appliance cords are not intended to be hardwired inside the wall. This is all so silly since he could solve most of this by posting back and addressing our questions, implied and explicit. But I took "intended" to refer to a drawing or instructions that came with the light and nothing to do with the wires' actual appearance. If you consider that possibility, we might have opinions closer to each other than they are now. Of course, his description could be wrong. Neither of us know, therefore my "implication" is no more absurd than your idea of just soldering on cord with a plug. A picture would, as always, be helpful. True. Most people with kitchens have things with plugs plugged in, the toaster, the blender, a George Foreman grill, a radio, a tv, a microwave, a Mixmaster, one or more device chargers, and maybe other things (an electric rotisserie?). Putting a plug on his cord will not detract from the appearance of the kitchen. You can't make that assertion without knowing what the "bare leads intended to be hardwired inside the wall" look like. Well, they don't look like alligators. They look like wires. True. They might even look like the wires that come with a bathroom fan. 3 loose wires (18g?) one black, one white, one green. Maybe it's a short run of Romex. Do you feel that putting a plug on those types of wires "will not detract from the appearance of the kitchen?" If you think that either of those will be an OK look, then we have nothing further to discuss. If you agree with me that that that would not be aesthetically pleasing, then I repeat: You can't make that assertion without knowing what the "bare leads intended to be hardwired inside the wall" look like. Again, based on his use of the words "intended to be hardwired inside the wall" I lean away from the simple attachment of a plug being aesthetically pleasing. In fact, it may not even be to code. What in the code prevents connecting two 14, 16, or 18 gauge wires to a plug? I don't know. That's why I said *may*. You keep making statements based on your assumptions of what he is dealing with and I keep leaving it wide open until we know the details. You have no clue what the "bare leads intended to be hardwired inside the wall" look like, yet you keep saying things like "Put a plug on them! Solder on longer wires! It'll be beautiful! It will meet code!" That make no sense. .......... would have to go in a junction box. After you've done that, how do you plan to have the cord come out of the junction box so you can plug it in? What junction box? It's obvious that you are picturing a totally different set of leads coming out the device than I am. Once again, a picture would be, as always, helpful. Or a 6-in-1? What's your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. That's a total non-answer. What is your alternative? My alternative is to wire it per code and keep aesthetics in mind as I'm planning the project. So as yet, you don't have an alternative. That is the only answer I can give until I know what the "bare leads intended to be hardwired inside the wall" actually look like. In the end, that will still be answer, but it will probably have some more details added once I know what he is working with. As I said before, I'm not going to jump to a detail explanation of an alternative until I have all of the facts. My stated alternative covers the general situation based on the facts known at this time. To code and aesthetically pleasing. |
#39
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
Hi everyone,
Thanks for all the feedback! I realize my description might have been bad enough to cause more confusion that I expected. As I mentioned, I'm a mechanical guy so I'm not familiar with electrical terms and I only remember basic stuff from school like P=VI. Check out these two images to see what I'm trying to do. http://imgur.com/HXs2qpZ This image shows the following: - The LED panel (with what I referred to as the three "bare leads") - The outlet on the left is the one I would like to use to power the panel - The remote switch http://imgur.com/37gQ508 This cross section diagram is my attempt to show what I want to do. - The 3 wires coming out of the LED panel would get connected (spliced?) onto corresponding existing wires inside the wall. This is what I mean't by "behind an existing 20amp outlet". - The orange circles show the connection (splice?) points Other points of clarification - The LED panel does not consume 15amps. I can't find the specs in any documentation, but it may or may not be "rated for 15amp circuits". - The LED panel has output specs of 24V, max 14.7W. - The LED panel input spec only says "120V". But, in some other documents, I found a spec that says "Power: 5.3W". Not sure what that means. - I don't want to attach a plug to the cable and plug it into the outlet from the outside. |
#40
Posted to alt.home.repair
|
|||
|
|||
installing 15 amp cabinet lights into a 20 amp circuit
posted for all of us...
Hi everyone, Thanks for all the feedback! I realize my description might have been bad enough to cause more confusion that I expected. As I mentioned, I'm a mechanical guy so I'm not familiar with electrical terms and I only remember basic stuff from school like P=VI. Check out these two images to see what I'm trying to do. http://imgur.com/HXs2qpZ This image shows the following: - The LED panel (with what I referred to as the three "bare leads") You have to run those 129v leads into some kind of jbox. The jbox must be fed. The jbox cannot be inside the wall but it can be mounted creatively. J ad a detailed reply written but the power went out so others can look at your pix and help guide you. I would just use a plug to an existing outlet. -- Tekkie |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Installing second set of lights from first set? | UK diy | |||
Short circuit: Do not connect Icicle lights with C7 or C9 lights? | Electronics Repair | |||
Need Help - Installing Medicine Cabinet | Home Ownership | |||
installing outlet for under cabinet lights in kitchen | Home Repair | |||
installing a 30 amp circuit | Home Repair |