Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
I'd apprecaite some feedback on my plan for wiring electrical outlets
in my basement (which I'm in the process of finishing)... I'm finishing about 2/3 of my basement with the remaining 1/3 being a dedicated storage area. The perimeter of the finished area is about 180 feet and I'm planning on having about 20 recepticals. I will only be using a fraction of the recepticals at any given time but I just want to make sure I always have one in the spot I need it, so I'm throwing in extra ones. I plan on using 12-2 copper wire with a 20A breaker & 20A rated outlets. At first I was considering using 14-2 with a 15A breaker but I'm concerned about voltage drop over my relatively long 180foot run. The extra cost and hassle of installing the 12-2 is something I don't have any issues with so I decided to go that route. I'll be routing the 12-2 through traditional wood frame 2x4 walls I have setup against my poured concrete basement walls. I have already drilled 3/4 inch holes in the studs. I'm installing the outlets so that they are 18inches above the basement floor and spaced less that 12feet apart (no more than 6feet from a doorway). The routing of the wiring through the wall is at least 12inches above the outlets. Any feedback on my plan? Anything I should look out for or consider? Anything I should watch out for using 12-2 with a 20A breaker? Thanks, Kevin |
#2
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
I know GFCI's aren't required for finished basements, but my personal
preference is for them anywhere in a basement, even the finished part (in my case it's one GFCI with the rest after it). I believe you are correct in that you need to use the heavier gauge wire for that length fo a run. |
#3
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Basements can be dark. Run a seperate branch for lighting and receptacles,
so if you trip a breaker running a dehumidifier and a skill saw at the same time, you are not fumbling in the dark. 12-2 is recommended for any receptacles, #14 should be reserved for lighting IMO. You don't need to pay extra for 20A receptacles, standard 15A plugs are fine (same for switches) unless you are dedicating one to a 20A load like an air conditioner. While you have the walls open, you have a chance to add ventilation for radon if that is an issue wrote in message ups.com... I'd apprecaite some feedback on my plan for wiring electrical outlets in my basement (which I'm in the process of finishing)... I'm finishing about 2/3 of my basement with the remaining 1/3 being a dedicated storage area. The perimeter of the finished area is about 180 feet and I'm planning on having about 20 recepticals. I will only be using a fraction of the recepticals at any given time but I just want to make sure I always have one in the spot I need it, so I'm throwing in extra ones. I plan on using 12-2 copper wire with a 20A breaker & 20A rated outlets. At first I was considering using 14-2 with a 15A breaker but I'm concerned about voltage drop over my relatively long 180foot run. The extra cost and hassle of installing the 12-2 is something I don't have any issues with so I decided to go that route. I'll be routing the 12-2 through traditional wood frame 2x4 walls I have setup against my poured concrete basement walls. I have already drilled 3/4 inch holes in the studs. I'm installing the outlets so that they are 18inches above the basement floor and spaced less that 12feet apart (no more than 6feet from a doorway). The routing of the wiring through the wall is at least 12inches above the outlets. Any feedback on my plan? Anything I should look out for or consider? Anything I should watch out for using 12-2 with a 20A breaker? Thanks, Kevin |
#4
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
wrote in message ups.com... I'd apprecaite some feedback on my plan for wiring electrical outlets in my basement (which I'm in the process of finishing)... I'm finishing about 2/3 of my basement with the remaining 1/3 being a dedicated storage area. The perimeter of the finished area is about 180 feet and I'm planning on having about 20 recepticals. I will only be using a fraction of the recepticals at any given time but I just want to make sure I always have one in the spot I need it, so I'm throwing in extra ones. I plan on using 12-2 copper wire with a 20A breaker & 20A rated outlets. At first I was considering using 14-2 with a 15A breaker but I'm concerned about voltage drop over my relatively long 180foot run. The extra cost and hassle of installing the 12-2 is something I don't have any issues with so I decided to go that route. I'll be routing the 12-2 through traditional wood frame 2x4 walls I have setup against my poured concrete basement walls. I have already drilled 3/4 inch holes in the studs. I'm installing the outlets so that they are 18inches above the basement floor and spaced less that 12feet apart (no more than 6feet from a doorway). The routing of the wiring through the wall is at least 12inches above the outlets. Any feedback on my plan? Anything I should look out for or consider? Anything I should watch out for using 12-2 with a 20A breaker? Thanks, Kevin You may want to check code but I don't think you can put 20 receptacles on one circuit regardless of how many you don't plan to use. I know my local code here says no more than 10 "devices" on a single circuit (a receptacle being a single device), regardless of what amperage it's rated for (15 or 20). I'm no code expert but thought I'd mention this as something for you to research! Cheers, cc |
#5
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
wrote in message ups.com... I'd apprecaite some feedback on my plan for wiring electrical outlets in my basement (which I'm in the process of finishing)... I'm finishing about 2/3 of my basement with the remaining 1/3 being a dedicated storage area. The perimeter of the finished area is about 180 feet and I'm planning on having about 20 recepticals. I will only be using a fraction of the recepticals at any given time but I just want to make sure I always have one in the spot I need it, so I'm throwing in extra ones. I plan on using 12-2 copper wire with a 20A breaker & 20A rated outlets. I'd certainly use more than one line/breaker for that many recepticals. Every receptical on my main floor is on one breaker. I can't run the microwave and vacuum cleaner at the same time. That's one future project. Bob |
#6
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Thanks for your feedback guys. I forgot to mention that the lighting
will be on a sepearate 15A circuit (the circuit is already there si I will just use it as is with a couple more lights added to it. CC- I will check into the number of outlets, but research I have done thus far has not indicated any limit except for in non-residential (commercial) applications. I'll probably stick with the 20A outlets just incase. I can't imagine using anything in my basement that will draw that much but the price for the capability isn't that great. scott21- With regard to the GFCI... are you recommending that I place one GFCI at the front of my cable run with the rest being conventional outlets? Bob- I feel your pain with your breaker problem! My microwave is somehow on the same circuit as my kitchen & dining room lights as well as my outdoor landscape lighting. Every once in a while If I have them all on, the microwave will cause the breaker to kick. I need to check if a 15A circuit was used...the run is pretty long so maybe the current draw is higher because of the current drop as well. One of these days I'm going to run a dedicated line for that microwave. In my basement, I don't see anything more than a TV or stereo, computer, & refridgerator going at the same time so I'm pretty sure I'll be safe with the 20A circuit (especially with the lights on their own circuit). Any and all feedback is appreciated! Thanks, Kevin |
#7
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
You are correct about the number of outlets on a circuit. In residential
wiring you need a 15 amp circuit for each 600 square feet . In commercial wiring it's 1.5 amps per outlet wrote in message ups.com... Thanks for your feedback guys. I forgot to mention that the lighting will be on a sepearate 15A circuit (the circuit is already there si I will just use it as is with a couple more lights added to it. CC- I will check into the number of outlets, but research I have done thus far has not indicated any limit except for in non-residential (commercial) applications. I'll probably stick with the 20A outlets just incase. I can't imagine using anything in my basement that will draw that much but the price for the capability isn't that great. scott21- With regard to the GFCI... are you recommending that I place one GFCI at the front of my cable run with the rest being conventional outlets? Bob- I feel your pain with your breaker problem! My microwave is somehow on the same circuit as my kitchen & dining room lights as well as my outdoor landscape lighting. Every once in a while If I have them all on, the microwave will cause the breaker to kick. I need to check if a 15A circuit was used...the run is pretty long so maybe the current draw is higher because of the current drop as well. One of these days I'm going to run a dedicated line for that microwave. In my basement, I don't see anything more than a TV or stereo, computer, & refridgerator going at the same time so I'm pretty sure I'll be safe with the 20A circuit (especially with the lights on their own circuit). Any and all feedback is appreciated! Thanks, Kevin |
#8
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
If you use 12-3 wire and a double breaker instead, you can easily wire each
of those 20 receptacles so that the top plug is one branch and the bottom is another branch. Additional cost and labor is trivial. You may not see much more than a TV, stereo and a few lights down there but a future owner might see a workshop or an excercise room with many heavy loads (tredmill, tanning lamp, dehumidifier, fans, space heater) . "RBM" rbm2(remove wrote in message ... You are correct about the number of outlets on a circuit. In residential wiring you need a 15 amp circuit for each 600 square feet . In commercial wiring it's 1.5 amps per outlet wrote in message ups.com... Thanks for your feedback guys. I forgot to mention that the lighting will be on a sepearate 15A circuit (the circuit is already there si I will just use it as is with a couple more lights added to it. CC- I will check into the number of outlets, but research I have done thus far has not indicated any limit except for in non-residential (commercial) applications. I'll probably stick with the 20A outlets just incase. I can't imagine using anything in my basement that will draw that much but the price for the capability isn't that great. scott21- With regard to the GFCI... are you recommending that I place one GFCI at the front of my cable run with the rest being conventional outlets? Bob- I feel your pain with your breaker problem! My microwave is somehow on the same circuit as my kitchen & dining room lights as well as my outdoor landscape lighting. Every once in a while If I have them all on, the microwave will cause the breaker to kick. I need to check if a 15A circuit was used...the run is pretty long so maybe the current draw is higher because of the current drop as well. One of these days I'm going to run a dedicated line for that microwave. In my basement, I don't see anything more than a TV or stereo, computer, & refridgerator going at the same time so I'm pretty sure I'll be safe with the 20A circuit (especially with the lights on their own circuit). Any and all feedback is appreciated! Thanks, Kevin |
#9
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
yeah DONT cheap out add a extra breaker!!
If your breaker cabinet is full you can get 1/2 width breakers to increase the number. you also want to consider ethernet, phone, satellite or cable to runs. i would protect hopefully the 2 20 amp outlet runs each with a GFCI or GFCI breaker. home inspectors here make the lkack of them in a basement a big issue... came up selling a home recently....... |
#10
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Thanks a lot for the double breaker & 12-3 wire suggestion. I think I
will definitely go that route as I have room in my box for it!! Time to take out my book and read up on that. I greatly appreciate everybody's feedback! kevin |
#11
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
In article et,
PipeDown wrote: If you use 12-3 wire and a double breaker instead, you can easily wire each of those 20 receptacles so that the top plug is one branch and the bottom is another branch. Additional cost and labor is trivial. Better yet, alternate phases between boxes, but don't split the outlets within the box unless you decide to add some switched outlets, in which case you could split an outlet for the switch leg. If you do add switched outlets, do it as part of a quad box, so that there are at least two unswitched outlets in the box. If you know you are going to have a fridge/freezer, add a dedicated 20a circuit for it. one less obvious point, add an outlet somewhere near the door where you would never consider putting any furniture (and thus covering the outlet) for the vaccum cleaner. could be on a narrow wall, or in the box with the switches. You may not see much more than a TV, stereo and a few lights down there but a future owner might see a workshop or an excercise room with many heavy loads (tredmill, tanning lamp, dehumidifier, fans, space heater) . I would figure on at least 4 circuits.. 2 staggered along the wall, 1 for the fridge, and 1 for lighting. -- -- Welcome My Son, Welcome To The Machine -- Bob Vaughan | techie @ tantivy.net | | P.O. Box 19792, Stanford, Ca 94309 | -- I am Me, I am only Me, And no one else is Me, What could be simpler? -- |
#12
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
|
#13
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
wrote in message ups.com... I'd apprecaite some feedback on my plan for wiring electrical outlets in my basement (which I'm in the process of finishing)... I'm finishing about 2/3 of my basement with the remaining 1/3 being a dedicated storage area. The perimeter of the finished area is about 180 feet and I'm planning on having about 20 recepticals. I will only be using a fraction of the recepticals at any given time but I just want to make sure I always have one in the spot I need it, so I'm throwing in extra ones. I plan on using 12-2 copper wire with a 20A breaker & 20A rated outlets. At first I was considering using 14-2 with a 15A breaker but I'm concerned about voltage drop over my relatively long 180foot run. The extra cost and hassle of installing the 12-2 is something I don't have any issues with so I decided to go that route. I'll be routing the 12-2 through traditional wood frame 2x4 walls I have setup against my poured concrete basement walls. I have already drilled 3/4 inch holes in the studs. I'm installing the outlets so that they are 18inches above the basement floor and spaced less that 12feet apart (no more than 6feet from a doorway). The routing of the wiring through the wall is at least 12inches above the outlets. Any feedback on my plan? Anything I should look out for or consider? Anything I should watch out for using 12-2 with a 20A breaker? Thanks, Kevin I concur that you should have more than one receptacle circuit. I would also put the refrigerator on its own circuit. Here in New Jersey it is required to have at least one GFI receptacle in the unfinished space and it is also a requirement to have a three way switch at the top and bottom of the basement stairs for the lights near and over the stairs. We are also required to have a ceiling mounted interconnected smoke detector within three feet of the bottom step of the basement stairs. You should also have a GFI receptacle near the furnace/air conditioning/water heater space for servicing purposes. You might also want to install cable TV and phone jacks in a few places. John Grabowski http://www.mrelectrician.tv |
#14
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
wrote in message oups.com... Thanks a lot for the double breaker & 12-3 wire suggestion. I think I will definitely go that route as I have room in my box for it!! Time to take out my book and read up on that. I greatly appreciate everybody's feedback! Be aware that having both phases in one box means there is a 240 volt shock hazard when working in that box. I would choose to not mix phases. Running 2-4 wires from the breaker box is really easy at this point. Adding them later is not. Don't scrimp on wire when it's so easy to add more circuits. When you use a portable heater, buy a treadmill or power saw , etc. you might be glad. Bob |
#15
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
I'd run 12-3 and put every other outlet on a circuit. Two circuits, and
you'll never have a problem. Use a 20A double pole breaker. Be sure to pigtail out when you land the outlets. -- Steve Barker wrote in message ups.com... Any feedback on my plan? Anything I should look out for or consider? Anything I should watch out for using 12-2 with a 20A breaker? Thanks, Kevin |
#16
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
No more than 10 plug ins on circuit. Plug ins no further than 6 feet
apart. You need more plug ins (180 lineal feet divided by 6' = nominal 30 plug ins.) -- Jim McLaughlin Reply address is deliberately munged. If you really need to reply directly, try: jimdotmclaughlinatcomcastdotcom And you know it is a dotnet not a dotcom address. wrote in message ups.com... I'd apprecaite some feedback on my plan for wiring electrical outlets in my basement (which I'm in the process of finishing)... I'm finishing about 2/3 of my basement with the remaining 1/3 being a dedicated storage area. The perimeter of the finished area is about 180 feet and I'm planning on having about 20 recepticals. I will only be using a fraction of the recepticals at any given time but I just want to make sure I always have one in the spot I need it, so I'm throwing in extra ones. I plan on using 12-2 copper wire with a 20A breaker & 20A rated outlets. At first I was considering using 14-2 with a 15A breaker but I'm concerned about voltage drop over my relatively long 180foot run. The extra cost and hassle of installing the 12-2 is something I don't have any issues with so I decided to go that route. I'll be routing the 12-2 through traditional wood frame 2x4 walls I have setup against my poured concrete basement walls. I have already drilled 3/4 inch holes in the studs. I'm installing the outlets so that they are 18inches above the basement floor and spaced less that 12feet apart (no more than 6feet from a doorway). The routing of the wiring through the wall is at least 12inches above the outlets. Any feedback on my plan? Anything I should look out for or consider? Anything I should watch out for using 12-2 with a 20A breaker? Thanks, Kevin |
#17
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
You are misinterpreting two separate rules
"Jim McLaughlin" jim.mclaughlin wrote in message . .. No more than 10 plug ins on circuit. Plug ins no further than 6 feet apart. You need more plug ins (180 lineal feet divided by 6' = nominal 30 plug ins.) -- Jim McLaughlin Reply address is deliberately munged. If you really need to reply directly, try: jimdotmclaughlinatcomcastdotcom And you know it is a dotnet not a dotcom address. wrote in message ups.com... I'd apprecaite some feedback on my plan for wiring electrical outlets in my basement (which I'm in the process of finishing)... I'm finishing about 2/3 of my basement with the remaining 1/3 being a dedicated storage area. The perimeter of the finished area is about 180 feet and I'm planning on having about 20 recepticals. I will only be using a fraction of the recepticals at any given time but I just want to make sure I always have one in the spot I need it, so I'm throwing in extra ones. I plan on using 12-2 copper wire with a 20A breaker & 20A rated outlets. At first I was considering using 14-2 with a 15A breaker but I'm concerned about voltage drop over my relatively long 180foot run. The extra cost and hassle of installing the 12-2 is something I don't have any issues with so I decided to go that route. I'll be routing the 12-2 through traditional wood frame 2x4 walls I have setup against my poured concrete basement walls. I have already drilled 3/4 inch holes in the studs. I'm installing the outlets so that they are 18inches above the basement floor and spaced less that 12feet apart (no more than 6feet from a doorway). The routing of the wiring through the wall is at least 12inches above the outlets. Any feedback on my plan? Anything I should look out for or consider? Anything I should watch out for using 12-2 with a 20A breaker? Thanks, Kevin |
#18
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
a 10 receptable per breaker is good common sense rule.
espically if you ever lived in a home like mine where way too many outlets were on the same circuit. hey turn the fan and blender off so i can turn on the floodlight to put out the garbage I have upgraded endlessely to fix such issues.... |
#21
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
On Wed, 10 May 2006 20:37:44 -0700, "Jim McLaughlin" jim.mclaughlin
wrote: No more than 10 plug ins on circuit. Plug ins no further than 6 feet apart. There is no logical reason for a limit on the number of recepticals on a circut, nor was it, (last version I checked) in the NEC. The only general requirement for the number of circuts falls out of the requirement for 3watts/sqft of available power, and the limit of 20A per circut. OTOH, there's no such thing as too much available power, and it's a whole lot cheaper to run circuts all at the same time than to come back and add another one. |
#22
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
" writes:
What do you mean when you say: "Be sure to pigtail out when you land the outlets." ? I think they mean: before installing the outlet, install a 6" wire to the receptacle connectors. Then, connect *that* to the box wiring. This gives you extra pull out room and lets you leave the box wiring mostly alone for swaping the unit out. Probably has some other benefits as well. You might have to use larger boxes to handle the extra wire. -- May no harm befall you, flip Ich habe keine Ahnung was das bedeutet, oder vielleicht doch? In my email replace SeeEmmYou.EeeDeeYou with CMU.EDU |
#23
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
According to Goedjn :
On Wed, 10 May 2006 23:34:39 +0000 (UTC), (Bob Vaughan) wrote: Better yet, alternate phases between boxes, but don't split the outlets within the box unless you decide to add some switched outlets, in which This isn't better. The way most people use rooms, the power hungry equipment tends to clump together, so you want as many DIFFERENT legs accessible at each power-access-point as you can conveniently manage. I'd agree with you with a kitchen, workshop or utility room. Up til very recently (with the advent of GFCI requirements) Canadian electrical code _required_ kitchen counter outlets to be _both_ split, and alternating which receptacle box each cable fed (max two boxes per circuit). Meaning that at any point on the counter between two receptacle boxes, you have _4_ 15A circuits available within 4'. I did that in my workshop counter outlets too. However, in general living space, eg: a rec room, it's not likely to be critical. But if you have the slots, it never hurts. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#24
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Other than allowing the rest of the circuit to function if one of the
outlets dies, what's the benefit to pigtailing the outlets rather than running them all in series ? Is pigtailing the outlets absolutely required if using 12/3 with a double pole breaker and alternating outlets between the two circuits (i.e. outlet1=circuit1, outlet2=circuit2, outlet3=circuit1 etc. ) If I do pigtail the outlets to the main 12/3 line going around my basement, where's the appropriate location for the pigtail connections relative to the main line? Putting the pigtail connection above the box, between two joists, and surrounded by fiberglass insulation doesn't seem correct to me. Also, it seems that the physical connection using the terminal screws on the outlets would be stronger than the connection provided by a wirenut. Thoughts on that?? Thanks, Kevin |
#26
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Thanks a lot. Pigtailing it is, then!
|
#27
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
By pigtailing you avoid the chance that a loose connection on any one outlet
would affect the downstream outlets. It is especially important when using 12-3 to pigtail the neutrals. This way if you have to replace an outlet, you don't "open" your neutral circuit to the downstream outlets. It's just good practice to never use the outlet as a connection by putting 4 wires on it. -- Steve Barker wrote in message oups.com... What do you mean when you say: "Be sure to pigtail out when you land the outlets." ? I'm looking at a wiring diagram in my DIY book and I think I see what you're talking about. But, what's the purpose of the pigtails? They don't look like they perform any function.. |
#28
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
It's not a rule, it's a preference. When I wired houses, I typically
installed seven on a 15 amp circuit wrote in message ups.com... a 10 receptable per breaker is good common sense rule. espically if you ever lived in a home like mine where way too many outlets were on the same circuit. hey turn the fan and blender off so i can turn on the floodlight to put out the garbage I have upgraded endlessely to fix such issues.... |
#29
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
It's perfectly fine to install four wires on a receptacle, it is however
illegal to have a neutral in a three wire Edison circuit dependent upon a device "Steve Barker LT" wrote in message ... By pigtailing you avoid the chance that a loose connection on any one outlet would affect the downstream outlets. It is especially important when using 12-3 to pigtail the neutrals. This way if you have to replace an outlet, you don't "open" your neutral circuit to the downstream outlets. It's just good practice to never use the outlet as a connection by putting 4 wires on it. -- Steve Barker wrote in message oups.com... What do you mean when you say: "Be sure to pigtail out when you land the outlets." ? I'm looking at a wiring diagram in my DIY book and I think I see what you're talking about. But, what's the purpose of the pigtails? They don't look like they perform any function.. |
#30
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Yes, fine. But not recommended.
-- Steve Barker "RBM" rbm2(remove wrote in message ... It's perfectly fine to install four wires on a receptacle, it is however illegal to have a neutral in a three wire Edison circuit dependent upon a device "Steve Barker LT" wrote in message ... By pigtailing you avoid the chance that a loose connection on any one outlet would affect the downstream outlets. It is especially important when using 12-3 to pigtail the neutrals. This way if you have to replace an outlet, you don't "open" your neutral circuit to the downstream outlets. It's just good practice to never use the outlet as a connection by putting 4 wires on it. -- Steve Barker wrote in message oups.com... What do you mean when you say: "Be sure to pigtail out when you land the outlets." ? I'm looking at a wiring diagram in my DIY book and I think I see what you're talking about. But, what's the purpose of the pigtails? They don't look like they perform any function.. |
#31
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Steve Barker LT wrote:
I'd run 12-3 and put every other outlet on a circuit. Two circuits, and you'll never have a problem. Use a 20A double pole breaker. Be sure to pigtail out when you land the outlets. Yes - This is the way I would do it too! Inviato da X-Privat.Org - Registrazione gratuita http://www.x-privat.org/join.php |
#32
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
wrote in message
ups.com... stuff snipped If I do pigtail the outlets to the main 12/3 line going around my basement, where's the appropriate location for the pigtail connections relative to the main line? Putting the pigtail connection above the box, between two joists, and surrounded by fiberglass insulation doesn't seem correct to me. All connections have to be made *inside* the box to prevent sparks from igniting any material inside the wall cavities. If you're going to pigtail, it would be a good idea to use extra deep outlet boxes to accommodate the wire nuts that will be needed. Personally, I'd not bother for two reasons. If you decide to use some sort of automated outlet or dimmer switch, you'll find they are much larger than standard switches and outlets and you'll be facing a very tight fit if you've got three wirenuts to account for. Also, if you wire through the back of the outlets and one outlet dies, it may take the rest of the string with them but that's not such a bad thing. It will tell you with a high degree of certainty which outlet needs attention: the one that's failed closest to the main breakers. Also, it seems that the physical connection using the terminal screws on the outlets would be stronger than the connection provided by a wirenut. Thoughts on that?? I suspect some of the replies you got were assuming you'd use the "backstab" connections on the outlets. IMHO, those are quick and dirty and far more likely to fail than either wire nuts or terminal screws. I just repaired one for a friend whose disposal first became intermittent and then failed completely. The outlet that it drew power from had been badly "backstabbed" and the connection became loose. As soon as she told me that there was another kitchen outlet that was flaky, I realized what the problem was. Whatever you decide, make sure your wire stripping is clean and without nicks. The failure point for outlets and switches, at least in my experience, always seems to be at the point where the copper was nicked by the stripper. -- Bobby G. |
#33
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
In ,
Robert Green wrote: I suspect some of the replies you got were assuming you'd use the "backstab" connections on the outlets. IMHO, those are quick and dirty and far more likely to fail than either wire nuts or terminal screws. I just repaired one for a friend whose disposal first became intermittent and then failed completely. The outlet that it drew power from had been badly "backstabbed" and the connection became loose. As soon as she told me that there was another kitchen outlet that was flaky, I realized what the problem was. You friend was lucky. Our house had all (orignall) outlets backstabbed. One in the family room burned up for some unkown reason (short? arc?). Our insurance company not only paid for the repair of the 3' x 3' hole the firefighters had to make in the dry wall to make sure the small insulation fire was out, but they paid to have an electrican replace that outlet AND rewire every other outlet in the house to use the terminal screws. -- Jim "Remember, an amateur built the Ark; professionals built the Titanic." |
#34
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
|
#35
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
Yes...I'll definitely be pigtailing!!
Thanks for the feedback! Kevin |
#36
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
"Steve Barker LT" wrote in message
By pigtailing you avoid the chance that a loose connection on any one outlet would affect the downstream outlets. It is especially important when using 12-3 to pigtail the neutrals. This way if you have to replace an outlet, you don't "open" your neutral circuit to the downstream outlets. If you had to replace an outlet, you'd have the breaker off at the panel, wouldn't you? Why would you care what happened downstream on a dead circuit branch? I looked in a recent addition of "Wiring Simplified" and they show pigtailing only when the wire feeding the outlet box goes on to another circuit, and not just the string of outlets. They clearly show a string of outlets connected by the two pairs of screws on each side. Their only caveat is that code prohibits more than one wire under a screw terminal. That just means you have no choice but to continue the string of outlets until the end and not wire in any other devices. If they were wrong, I would have hoped someone would have noticed by the 38th edition. :-) I ask because in the new home construction I've encountered, not only were the outlets chained together, they were backstabbed together. Now that's asking for trouble, but for a different reason. Those connections can vibrate loose and if they're on an outside wall, they can work loose by expansion and contraction. It's just good practice to never use the outlet as a connection by putting 4 wires on it. From what I've seen adding more connections to the outlet box doesn't increase reliability. If you pigtail you've got two extra "three wires to one wire nut" connections for each outlet. I've come across more than one "three wire nut" that's got one wire popped out of it. It takes strong hands and a good eye to cut, strip and twist three stiff wires into a nut that will survive repacking into the back of the box. It's not a problem for an electrical pro, but for people doing their own electric al work, it seems a lot easier and lot more reliable if they just daisy chain the outlets using the screw terminals. I'm still not clear on why it would be preferable for even an electrician to make three connections (pigtail) when he could just as easily make only two (pass-thru), especially when we're talking about a string of outlets on a dedicate breaker. What am I missing? -- Bobby G. |
#37
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
In my case, i think the problem is that the neutral wire is shared
between the two alternating circuits. So if the continuity of the neutral circuit is interrupted because of a bad outlet or something, pigtailing will avoid that problem. Anyway, that's my take. Both my Black & Decker DIY books show pigtailing and thats the recommendation I see in these groups so that's with I'M gonna do. :-) Kevin |
#38
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
|
#39
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
According to Robert Green :
"Steve Barker LT" wrote in message By pigtailing you avoid the chance that a loose connection on any one outlet would affect the downstream outlets. It is especially important when using 12-3 to pigtail the neutrals. This way if you have to replace an outlet, you don't "open" your neutral circuit to the downstream outlets. If you had to replace an outlet, you'd have the breaker off at the panel, wouldn't you? Why would you care what happened downstream on a dead circuit branch? It's not uncommon to see shared neutral circuits to not be tiebarred together in the panel. Someone naively turning off one breaker, and pulling out the outlet breaking the neutral (he doesn't get zapped unless something is live and pulling power on the other leg) can result in rather nasty things happening. Especially if the first breaker is turned back on. That downstream may not really be dead in a shared neutral. It happened often enough for our code to require neutral pigtails at least on shared neutral circuits. As yours does. -- Chris Lewis, Una confibula non set est It's not just anyone who gets a Starship Cruiser class named after them. |
#40
Posted to alt.home.repair
|
|||
|
|||
Plan for Basement Electrical Outlets - Feedback Please
" wrote in message ups.com... In my case, i think the problem is that the neutral wire is shared between the two alternating circuits. So if the continuity of the neutral circuit is interrupted because of a bad outlet or something, pigtailing will avoid that problem. Anyway, that's my take. Both my Black & Decker DIY books show pigtailing and thats the recommendation I see in these groups so that's with I'M gonna do. :-) I like pigtailing daisy-chained devices, mainly to avoid the wrestling getting the device into or flush with the box. 4 or 5 short stiff 12-gauge wires can be quite uncooperative to fold up and tuck into a small space. And on some lamp bases I recently hung in the basement, the screw tabs for the wires were flimsy enough that they wanted to bend with 4 wires attached. I did the pigtails, folded the feedwires and nuts up tight into the box, and only had to deal with 2 wires when pushing everything up into place. Much easier. aem sends... |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Electrical Outlet Problem | Home Repair | |||
Overhead electrical service to a storage shed | Home Repair | |||
New Electrical Regs | UK diy | |||
Installing Electrical Outlet In Sink Cabinet | Home Repair | |||
Forthcoming Building Regulations on electrical work (Part P) | UK diy |