Earth Sleeving for 10mm T+E?
Hi all
as per the subject - I am (re)making the connections to an isolator switch for an electric shower. The cable is 10mm and due to the construction of the switch I have to twist incoming and outgoing earths together. I can't seem to find 10mm Green/Yellow Earth sleeving online, 6mm seems the largest.. Am I forced to use tape (ugh), or is there a source for the sleeving, or a different approach, that I need appraising of? Thanks J^n |
#2
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
jkn laid this down on his screen :
Hi all as per the subject - I am (re)making the connections to an isolator switch for an electric shower. The cable is 10mm and due to the construction of the switch I have to twist incoming and outgoing earths together. I can't seem to find 10mm Green/Yellow Earth sleeving online, 6mm seems the largest. Am I forced to use tape (ugh), or is there a source for the sleeving, or a different approach, that I need appraising of? 6mm sleeving should fit the earth conductor of 10mm T&E. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 10/05/2018 10:41, jkn wrote:
Hi all as per the subject - I am (re)making the connections to an isolator switch for an electric shower. The cable is 10mm and due to the construction of the switch I have to twist incoming and outgoing earths together. I can't seem to find 10mm Green/Yellow Earth sleeving online, 6mm seems the largest. Am I forced to use tape (ugh), or is there a source for the sleeving, or a different approach, that I need appraising of? Sleeves are generally measure in outer diameter, so allowance of wall thickness has to be considered. https://www.voltimum.co.uk/articles/...-earth-cable-1 suggests the CPC for 10mm conductors is 4sqmm suggesting a diameter of 2.25mm. Even 10sqmm only has a diameter of 3.5mm |
#4
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
Hi Harry
On Thursday, May 10, 2018 at 11:53:14 AM UTC+1, Harry Bloomfield wrote: jkn laid this down on his screen : Hi all as per the subject - I am (re)making the connections to an isolator switch for an electric shower. The cable is 10mm and due to the construction of the switch I have to twist incoming and outgoing earths together. I can't seem to find 10mm Green/Yellow Earth sleeving online, 6mm seems the largest. Am I forced to use tape (ugh), or is there a source for the sleeving, or a different approach, that I need appraising of? 6mm sleeving should fit the earth conductor of 10mm T&E. Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Cheers J^n |
#5
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
jkn used his keyboard to write :
Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Better when carrying out tests, for them not to be twisted together sharing one sleeve. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 10/05/2018 12:05, jkn wrote:
Hi Harry On Thursday, May 10, 2018 at 11:53:14 AM UTC+1, Harry Bloomfield wrote: jkn laid this down on his screen : Hi all as per the subject - I am (re)making the connections to an isolator switch for an electric shower. The cable is 10mm and due to the construction of the switch I have to twist incoming and outgoing earths together. I can't seem to find 10mm Green/Yellow Earth sleeving online, 6mm seems the largest. Am I forced to use tape (ugh), or is there a source for the sleeving, or a different approach, that I need appraising of? 6mm sleeving should fit the earth conductor of 10mm T&E. Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Cheers J^n I think you need a proper mechanical connection, like a decent crimp. You are only sleeving the earth line not the whole cable. Plenty of sleeving available for that. You also need RCD protection. |
#7
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
Andrew Wrote in message:
On 10/05/2018 12:05, jkn wrote: Hi Harry On Thursday, May 10, 2018 at 11:53:14 AM UTC+1, Harry Bloomfield wrote: jkn laid this down on his screen : Hi all as per the subject - I am (re)making the connections to an isolator switch for an electric shower. The cable is 10mm and due to the construction of the switch I have to twist incoming and outgoing earths together. I can't seem to find 10mm Green/Yellow Earth sleeving online, 6mm seems the largest. Am I forced to use tape (ugh), or is there a source for the sleeving, or a different approach, that I need appraising of? 6mm sleeving should fit the earth conductor of 10mm T&E. Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Cheers J^n You also need RCD protection. Even if remaking existing connections? -- Jim K ----Android NewsGroup Reader---- http://usenet.sinaapp.com/ |
#8
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
In article ,
jkn wrote: Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Twisting together then fitting sleeving over both doesn't insulate the earth properly, as it will still be exposed at the sheath end. -- *I stayed up all night to see where the sun went. Then it dawned on me.* Dave Plowman London SW To e-mail, change noise into sound. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 10/05/2018 14:58, Dave Plowman (News) wrote:
In article , jkn wrote: Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Twisting together then fitting sleeving over both doesn't insulate the earth properly, as it will still be exposed at the sheath end. Do you insulate the metal boxes they connect to? |
#10
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
In article ,
dennis@home wrote: On 10/05/2018 14:58, Dave Plowman (News) wrote: In article , jkn wrote: Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Twisting together then fitting sleeving over both doesn't insulate the earth properly, as it will still be exposed at the sheath end. Do you insulate the metal boxes they connect to? The idea of the sleeving is to minimise the possibility of a short. And the end of the outer sheath is often nicely positioned to catch a terminal. Twisting earths together all their length also makes it more difficult to 'page' the runs neatly. But carry on doing this if you are too mean to pay for more lengths of sleeving. -- *I took an IQ test and the results were negative. Dave Plowman London SW To e-mail, change noise into sound. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
Hi Dave
On Thursday, May 10, 2018 at 3:04:49 PM UTC+1, Dave Plowman (News) wrote: In article , jkn wrote: Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Twisting together then fitting sleeving over both doesn't insulate the earth properly, as it will still be exposed at the sheath end. Fair point. The old isolator had two separate (connected, obviously) earth terminals, but I seemed to have used tape for insulator. The new (MK, supposedly better, hmmph) isolator only has one earth terminal and I am anticipating some awkwardness if I have to sleeve each earth separately and then twist them together for the last couple of CMs. But it seems like that is the way... thanks to all for the advice. FWIW I guess I was thinking that '6mm earth sleeving' was 'sleeving for the earth wire in a 6mm T+E cable', whereas I see now that that is not the case... an eBay order for a few metres has just gone in. Cheers J^n |
#12
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 10/05/18 12:37, Harry Bloomfield wrote:
jkn used his keyboard to write : Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Better when carrying out tests, for them not to be twisted together sharing one sleeve. At the CU on a ring, definitely (you need to do end-end and figure-8 tests that require accessing all 6 conductors individually. In devices, I am less convinced it's a problem rather than just a mantra. Adam may shed some light on this, but the only time I can think you'd want to separate conductors in a device is for locating a suspected fault. There's no routine testing I can think of that would need that, *except* if you needed to isolate a branch because it had a sensitive device on the end. If the device *is* the sensitive part, you might take it off and stick a terminal block on the end of the wires. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
Never heard of cross-connection testing?
|
#14
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 10/05/2018 14:58, Dave Plowman (News) wrote:
In article , jkn wrote: Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Twisting together then fitting sleeving over both doesn't insulate the earth properly, as it will still be exposed at the sheath end. Correct and the reg that applies I would say is somewhere in the regs:-) It's the sort of thing that you spot and wonder "What else is wrong?" -- Adam |
#15
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 10/05/2018 15:31, Dave Plowman (News) wrote:
In article , dennis@home wrote: On 10/05/2018 14:58, Dave Plowman (News) wrote: In article , jkn wrote: Well ... I have currently got the incoming and outgoing earths twisted together for a length (2--3 inches), and I doubt it will fit that. I was hoping not to have to separate them and have them joined in the screw terminal. But if that is what people do, fair enough... Twisting together then fitting sleeving over both doesn't insulate the earth properly, as it will still be exposed at the sheath end. Do you insulate the metal boxes they connect to? The idea of the sleeving is to minimise the possibility of a short. And the end of the outer sheath is often nicely positioned to catch a terminal. Twisting earths together all their length also makes it more difficult to 'page' the runs neatly. But carry on doing this if you are too mean to pay for more lengths of sleeving. TBH earth sleeving and the PVC coverings of the L&N cores are not going to do much against a short caused by a socket screw. The live cores should in most cases be semi enclosed inside a terminal to prevent a fault (ie no bare copper sticking out on the live terminals). However I think dennis is asking if the earth sleeving protects against a earth/earth fault between socket and metal back box should you put the socket screw through the green/yellow insulation and catch the cpc (earth) cable with the screw. Now I seem to recall that you always fit an earth flylead between sockets and backboxes. -- Adam |
#16
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
In article ,
ARW wrote: The idea of the sleeving is to minimise the possibility of a short. And the end of the outer sheath is often nicely positioned to catch a terminal. Twisting earths together all their length also makes it more difficult to 'page' the runs neatly. But carry on doing this if you are too mean to pay for more lengths of sleeving. TBH earth sleeving and the PVC coverings of the L&N cores are not going to do much against a short caused by a socket screw. The live cores should in most cases be semi enclosed inside a terminal to prevent a fault (ie no bare copper sticking out on the live terminals). Yes it's unlikely. But if impossible, no point in using sleeving at all. I doubt even dennis needs to know which one is the earth wire with TW&E by its colour. -- *Suicidal twin kills sister by mistake. Dave Plowman London SW To e-mail, change noise into sound. |
#17
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 11/05/18 00:04, Dave Plowman (News) wrote:
In article , ARW wrote: The idea of the sleeving is to minimise the possibility of a short. And the end of the outer sheath is often nicely positioned to catch a terminal. Twisting earths together all their length also makes it more difficult to 'page' the runs neatly. But carry on doing this if you are too mean to pay for more lengths of sleeving. TBH earth sleeving and the PVC coverings of the L&N cores are not going to do much against a short caused by a socket screw. The live cores should in most cases be semi enclosed inside a terminal to prevent a fault (ie no bare copper sticking out on the live terminals). Yes it's unlikely. But if impossible, no point in using sleeving at all. I doubt even dennis needs to know which one is the earth wire with TW&E by its colour. Interestingly the Americans don't use CPC sleeving in any video I've ever seen. And their line terminals are often extremely exposed as a pan head screw you turn the conductor under. That's one case where I think it would have a provable benefit. |
#18
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 11/05/2018 08:24, Tim Watts wrote:
On 11/05/18 00:04, Dave Plowman (News) wrote: In article , Â*Â*Â* ARW wrote: The idea of the sleeving is to minimise the possibility of a short. And the end of the outer sheath is often nicely positioned to catch a terminal. Twisting earths together all their length also makes it more difficult to 'page' the runs neatly. But carry on doing this if you are too mean to pay for more lengths of sleeving. TBH earth sleeving and the PVC coverings of the L&N cores are not going to do much against a short caused by a socket screw. The live cores should in most cases be semi enclosed inside a terminal to prevent a fault (ie no bare copper sticking out on the live terminals). Yes it's unlikely. But if impossible, no point in using sleeving at all. I doubt even dennis needs to know which one is the earth wire with TW&E by its colour. Interestingly the Americans don't use CPC sleeving in any video I've ever seen. And their line terminals are often extremely exposed as a pan head screw you turn the conductor under. That's one case where I think it would have a provable benefit. I'm a bit surprised insulated CPCs haven't been mandated here. Ireland has done so (and with the CPC the same size as the phases). And IIRC the French have had insulated CPCs for years. Safety and harmonisation... -- Robin reply-to address is (intended to be) valid |
#19
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
In article ,
Tim Watts wrote: Yes it's unlikely. But if impossible, no point in using sleeving at all. I doubt even dennis needs to know which one is the earth wire with TW&E by its colour. Interestingly the Americans don't use CPC sleeving in any video I've ever seen. And their line terminals are often extremely exposed as a pan head screw you turn the conductor under. That's one case where I think it would have a provable benefit. it's one of those things. If the cables are correctly paged when fixing the fitting to the box, the earth sleeve is redundant. After all at one time it wasn't sleeved here either. But given a hank of sleeving is so cheap, no reason not to use it anyway. -- *Someday, we'll look back on this, laugh nervously and change the subject Dave Plowman London SW To e-mail, change noise into sound. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
Robin wrote:
I'm a bit surprised insulated CPCs haven't been mandated here. Ireland has done so (and with the CPC the same size as the phases). And IIRC the French have had insulated CPCs for years. Safety and harmonisation... Maybe in 10 months we can import this :-P https://www.jaycar.co.nz/red-black-green/p/WB1568 |
#21
Posted to uk.d-i-y
|
|||
|
|||
Earth Sleeving for 10mm T+E?
On 11/05/2018 10:50, Dave Plowman (News) wrote:
it's one of those things. If the cables are correctly paged when fixing the fitting to the box, the earth sleeve is redundant. After all at one time it wasn't sleeved here either. But given a hank of sleeving is so cheap, no reason not to use it anyway. I have several hanks, because I can never find the damn stuff when I want it. |