Can I use 'bell wire' for a room thermostat for the combi boiler, or is it
under-rated for that job?

--
Mark BR


  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,155
Default Bell wire rating

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?


The room thermostat will be mandling mains voltage. You need proper T + E.

--
From KT24

Using a RISC OS computer running v5.18

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Bell wire rating

On Thursday, October 4, 2012 9:20:18 AM UTC+1, Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is it

under-rated for that job?


It can handle the current ok, and the voltage, but the insulation is inadequate to comply with current law.


NT
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Bell wire rating

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?


Only if the thermostat is low voltage, which very few are. The insulation
on bell wire is only suitable for low voltage.

--
*Don't squat with your spurs on *

Dave Plowman London SW
To e-mail, change noise into sound.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 137
Default Bell wire rating

"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Bell wire rating

On 04/10/2012 09:16, Mark BR wrote:

Can I use 'bell wire' for a room thermostat for the combi boiler, or is it
under-rated for that job?


In terms of current carrying capacity, it is probably adequate, however
it is not well enough insulated to carry mains voltage.

The exception to this may be if the combi has a 24V option for controls.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 28
Default Bell wire rating


"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.

Thanks for all the comments.

--
Mark BR


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Bell wire rating

Mark BR wrote:
"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?

Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.

You could strangle harry with it.

Thanks for all the comments.

--
Mark BR




--
Ineptocracy

(in-ep-toc-ra-cy) a system of government where the least capable to
lead are elected by the least capable of producing, and where the
members of society least likely to sustain themselves or succeed, are
rewarded with goods and services paid for by the confiscated wealth of a
diminishing number of producers.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Bell wire rating

On 05/10/2012 09:28, Mark BR wrote:
"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.

Thanks for all the comments.

--
Mark BR


'Volt free' = the thermostat contacts are provided 'dry' - that is an
isolated pair of switched poles.
The boiler end would have to apply some voltage in order to work out if
they are open or closed. Could be as little as 3.3 or 5v, or 240 VAC


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9
Default Bell wire rating

在 2012年10月4日星期四UTC+8下午4时20分18秒 ,Mark BR写道:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is it

under-rated for that job?



--

Mark BR


http://www.cheapuggbootsonline2012.co.uk/
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9
Default Bell wire rating

在 2012年10月4日星期四UTC+8下午4时20分18秒 ,Mark BR写道:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is it

under-rated for that job?



--

Mark BR


http://www.cheapuggbootsonline2012.co.uk/
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Bell wire rating

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or is it


under-rated for that job?




In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.


Bell wire is capable, just not lawful. And burying it in plaster can't be counted as a 2nd layer of insulation


NT
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Fri, 05 Oct 2012 09:28:41 +0100, Mark BR wrote:


"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.


Wire speakers up all over the house.

--
http://petersparrots.com
http://petersphotos.com

101 Dalmatians and Peter Pan are the only two Disney animated features in which both the parents are present and don't die throughout the movie.


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or is it


under-rated for that job?




In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.


Bell wire is capable, just not lawful. And burying it in plaster can't be counted as a 2nd layer of insulation


Plaster conducts does it?

--
http://petersparrots.com
http://petersphotos.com

"Sir, your daughter says she loves me, she can't live without me, and wants to marry me."
"And you're asking my permission to marry her?"
"No, I'm asking you to make her leave me the hell alone!!"
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,453
Default Bell wire rating

Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it

under-rated for that job?



In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.


Bell wire is capable, just not lawful. And burying it in plaster can't be
counted as a 2nd layer of insulation


Plaster conducts does it?


More than you know - especially if slightly damp!
--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"A fanatic is one who can't change his mind and won't change the subject."

  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it

under-rated for that job?



In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.

Bell wire is capable, just not lawful. And burying it in plaster can't be
counted as a 2nd layer of insulation


Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even tingle.

--
http://petersparrots.com
http://petersphotos.com

He saw her in her birthday suit swimming by the pier
She said, "Please go away," but he pretended not to hear.
"If you don't go I'll stay in here 'til it's dark."
'That's OK by me," he said, "I only came to feed the shark."
-- Benny Hill
  #19   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Bell wire rating

Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi
boiler, or is it

under-rated for that job?



In terms of current carrying capacity, it is probably
adequate, however it is not well enough insulated to carry mains
voltage.



The exception to this may be if the combi has a 24V option
for controls.

Bell wire is capable, just not lawful. And burying it in
plaster can't be counted as a 2nd layer of insulation

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't
even tingle.



How was the ECT?

--
Adam


  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,453
Default Bell wire rating

Lieutenant Scott wrote:

On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it

under-rated for that job?



In terms of current carrying capacity, it is probably adequate,
however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for
controls.

Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.

Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.

Just because you *can* use bell wire, does not mean you *should*.

--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."



  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Fri, 26 Oct 2012 22:12:58 +0100, ARW wrote:

Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi
boiler, or is it

under-rated for that job?



In terms of current carrying capacity, it is probably
adequate, however it is not well enough insulated to carry mains
voltage.



The exception to this may be if the combi has a 24V option
for controls.

Bell wire is capable, just not lawful. And burying it in
plaster can't be counted as a 2nd layer of insulation

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't
even tingle.



How was the ECT?


TENS is more fun.

--
http://petersparrots.com
http://petersphotos.com

When Mike got arrested, the police told him, "Anything you say will be held against you."
Mike smiled and simply replied, "Jessica Simpson's boobs."
  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Fri, 26 Oct 2012 22:47:09 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:



Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.

Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.

Just because you *can* use bell wire, does not mean you *should*.


The old days? Fairy lights still are like that (except the LED ones).

All I'm concerned with is fire, nevermind a little shock now and then.

--
http://petersparrots.com
http://petersphotos.com

A man's home is his castle, in a manor of speaking.
  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,453
Default Bell wire rating

Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED ones).


I suggest you look a little closer.

I think you will find they are double insulated and marked Class II, not
Class O.




All I'm concerned with is fire, nevermind a little shock now and then.


Do you remove items from your toaster with metal implements?

--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."

  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Bell wire rating

On Friday, October 26, 2012 10:47:12 PM UTC+1, Tim Watts wrote:
Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:
On Fri, 05 Oct 2012 10:57:39 +0100, wrote:
On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:


Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it
under-rated for that job?


In terms of current carrying capacity, it is probably adequate,
however
it is not well enough insulated to carry mains voltage.
The exception to this may be if the combi has a 24V option for
controls.
Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation
Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.
Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.
Just because you *can* use bell wire, does not mean you *should*.


True, but that argument appears to suggest it would be safe to use buried in plaster, but its still not allowed.


NT
  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 10:49:54 +0100, wrote:

On Friday, October 26, 2012 10:47:12 PM UTC+1, Tim Watts wrote:
Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:
On Fri, 05 Oct 2012 10:57:39 +0100, wrote:
On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:


Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it
under-rated for that job?


In terms of current carrying capacity, it is probably adequate,
however
it is not well enough insulated to carry mains voltage.
The exception to this may be if the combi has a 24V option for
controls.
Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation
Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.
Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.
Just because you *can* use bell wire, does not mean you *should*.


True, but that argument appears to suggest it would be safe to use buried in plaster, but its still not allowed.


Not allowed isn't always anything to do with safe. It's paperpushers making **** up.

--
http://petersparrots.com
http://petersphotos.com

A female friend of mine was admitted to a private hospital to try to
lose weight. Naturally I sent her flowers.

I received a "thank-you" note several days later; it said, "Thanks for
the flowers, they were delicious!"
  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 08:54:28 +0100, Tim Watts wrote:

Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED ones).


I suggest you look a little closer.

I think you will find they are double insulated and marked Class II, not
Class O.


I guess I haven't got that new fairy lights then. The wire is stranded copper with one sheath of plastic. Two such wires glued together.

No point in making the wire safer, the danger would be from the flimsy little bulbs which would make up to 240 volts available to your fingers (or mouth in the case of a baby eating one).

All I'm concerned with is fire, nevermind a little shock now and then.


Do you remove items from your toaster with metal implements?


I've had several shocks from the mains, it's not dangerous.

--
http://petersparrots.com
http://petersphotos.com

Peter is listening to "Eagles - Hotel California"
  #28   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Bell wire rating

Lieutenant Scott wrote:
On Sat, 27 Oct 2012 08:54:28 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED
ones).


I suggest you look a little closer.

I think you will find they are double insulated and marked Class
II, not Class O.


I guess I haven't got that new fairy lights then. The wire is
stranded copper with one sheath of plastic. Two such wires glued
together.
No point in making the wire safer, the danger would be from the
flimsy little bulbs which would make up to 240 volts available to
your fingers (or mouth in the case of a baby eating one).
All I'm concerned with is fire, nevermind a little shock now and
then.


Do you remove items from your toaster with metal implements?


I've had several shocks from the mains, it's not dangerous.


And it caused no brain damage at all.

--
Adam


  #29   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 14:16:59 +0100, ARW wrote:

Lieutenant Scott wrote:
On Sat, 27 Oct 2012 08:54:28 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED
ones).

I suggest you look a little closer.

I think you will find they are double insulated and marked Class
II, not Class O.


I guess I haven't got that new fairy lights then. The wire is
stranded copper with one sheath of plastic. Two such wires glued
together.
No point in making the wire safer, the danger would be from the
flimsy little bulbs which would make up to 240 volts available to
your fingers (or mouth in the case of a baby eating one).
All I'm concerned with is fire, nevermind a little shock now and
then.

Do you remove items from your toaster with metal implements?


I've had several shocks from the mains, it's not dangerous.


And it caused no brain damage at all.


I don't tend to insert the wires into my ears.

--
http://petersparrots.com
http://petersphotos.com

Philosophy is questions that may never be answered. Religion is answers that may never be questioned.
  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,453
Default Bell wire rating

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"
--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."



  #31   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and those that tell others they're doing it wrong. I prefer the first kind.

--
http://petersparrots.com
http://petersphotos.com

A little girl asked her mother, "Can I go outside and play with the boys?"
Her mother replied, "No, you can't play with the boys, they're too rough."
The little girl thought about it for a few moments and asked, "If I can find a smooth one, can I play with him?"
  #32   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,020
Default Bell wire rating

"ARW" wrote:
Lieutenant Scott wrote:

[snip]

I've had several shocks from the mains, it's not dangerous.


And it caused no brain damage at all.


One cannot damage that which does not exist.

Which appears to be your point.

--
DarWin|
_/ _/
  #33   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Bell wire rating

In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.


Really? I'd say it accounts for your fried brain.

--
*Gravity is a myth, the earth sucks *

Dave Plowman London SW
To e-mail, change noise into sound.
  #34   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 15:43:24 +0100, Dave Plowman (News) wrote:

In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.


Really? I'd say it accounts for your fried brain.


I didn't insert the wires into my ears.

--
http://petersparrots.com
http://petersphotos.com

He was so unlucky . . .
Last week, his inflatable doll ran off with his airbag.
  #35   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Bell wire rating

Lieutenant Scott wrote:
On Sat, 27 Oct 2012 15:43:24 +0100, Dave Plowman (News)
wrote:
In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.


Really? I'd say it accounts for your fried brain.


I didn't insert the wires into my ears.


You are still a thick daft ****.

--
Adam




  #36   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 16:11:45 +0100, ARW wrote:

Lieutenant Scott wrote:
On Sat, 27 Oct 2012 15:43:24 +0100, Dave Plowman (News)
wrote:
In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.

Really? I'd say it accounts for your fried brain.


I didn't insert the wires into my ears.


You are still a thick daft ****.


Show your working.

--
http://petersparrots.com
http://petersphotos.com

The only differences between lawyers and prostitutes are that prostitutes are generally better looking and more honest about how they make a living.
  #37   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,453
Default Bell wire rating

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?
--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"She got her looks from her father. He's a plastic surgeon."

  #38   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 16:28:46 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?


That's just greed.

--
http://petersparrots.com
http://petersphotos.com

A man has six items in his bathroom: toothbrush and toothpaste, shaving cream, razor, a bar of soap, and a towel.
The average number of items in the typical woman's bathroom is 337. A man would not be able to identify more than 20 of these items.
  #39   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,918
Default Bell wire rating

On Sat, 27 Oct 2012 16:28:46 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?


You only get let into such committees if you're a health and safety conscious ****t.

--
http://petersparrots.com
http://petersphotos.com

A man has six items in his bathroom: toothbrush and toothpaste, shaving cream, razor, a bar of soap, and a towel.
The average number of items in the typical woman's bathroom is 337. A man would not be able to identify more than 20 of these items.
  #40   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,453
Default Bell wire rating

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 16:28:46 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper
pushers"

There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?


That's just greed.


Oh do stop being a ****.


--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wire Door Bell to Ring LOUD Out Back? tim birr Home Repair 6 September 25th 10 05:00 AM
Dispense with bell wire? Yvonne[_2_] UK diy 7 August 12th 09 05:14 PM
Bell Wire Q TheScullster UK diy 21 April 21st 09 06:45 PM
wire size and amp rating Karl Townsend Metalworking 8 August 30th 07 02:18 PM
Wirefree bell push to wired bell Duncan UK diy 5 June 4th 06 09:14 PM


All times are GMT +1. The time now is 06:38 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright 2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"