Bell wire rating
 
Can I use 'bell wire' for a room thermostat for the combi boiler, or is it
under-rated for that job?

--
Mark BR



charles October 4th 12 09:27 AM

Bell wire rating
 
In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?


The room thermostat will be mandling mains voltage. You need proper T + E.

--
From KT24

Using a RISC OS computer running v5.18


[email protected] October 4th 12 09:34 AM

Bell wire rating
 
On Thursday, October 4, 2012 9:20:18 AM UTC+1, Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is it

under-rated for that job?


It can handle the current ok, and the voltage, but the insulation is inadequate to comply with current law.


NT

Tim Watts[_2_] October 4th 12 10:24 AM

Bell wire rating
 
wrote:

On Thursday, October 4, 2012 9:20:18 AM UTC+1, Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it

under-rated for that job?


It can handle the current ok, and the voltage, but the insulation is
inadequate to comply with current law.


Wot he said.

You need the appropriate insulation *and* sheathing.

--
Tim Watts
Personal Blog:
http://www.dionic.net/tim/

"A fanatic is one who can't change his mind and won't change the subject."


Dave Plowman (News) October 4th 12 10:29 AM

Bell wire rating
 
In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?


Only if the thermostat is low voltage, which very few are. The insulation
on bell wire is only suitable for low voltage.

--
*Don't squat with your spurs on *

Dave Plowman London SW
To e-mail, change noise into sound.

DerbyBorn[_3_] October 4th 12 02:29 PM

Bell wire rating
 
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.

John Rumm October 4th 12 05:10 PM

Bell wire rating
 
On 04/10/2012 09:16, Mark BR wrote:

Can I use 'bell wire' for a room thermostat for the combi boiler, or is it
under-rated for that job?


In terms of current carrying capacity, it is probably adequate, however
it is not well enough insulated to carry mains voltage.

The exception to this may be if the combi has a 24V option for controls.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/

Mark BR[_2_] October 5th 12 09:28 AM

Bell wire rating
 

"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.

Thanks for all the comments.

--
Mark BR



The Natural Philosopher[_2_] October 5th 12 09:39 AM

Bell wire rating
 
Mark BR wrote:
"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?

Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.

You could strangle harry with it.

Thanks for all the comments.

--
Mark BR




--
Ineptocracy

(in-ep-toc-ra-cy) a system of government where the least capable to
lead are elected by the least capable of producing, and where the
members of society least likely to sustain themselves or succeed, are
rewarded with goods and services paid for by the confiscated wealth of a
diminishing number of producers.

Phil[_18_] October 5th 12 10:06 AM

Bell wire rating
 
On 05/10/2012 09:28, Mark BR wrote:
"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.

Thanks for all the comments.

--
Mark BR


'Volt free' = the thermostat contacts are provided 'dry' - that is an
isolated pair of switched poles.
The boiler end would have to apply some voltage in order to work out if
they are open or closed. Could be as little as 3.3 or 5v, or 240 VAC

[email protected] October 5th 12 10:15 AM

Bell wire rating
 
在 2012年10月4日星期四UTC+8下午4时20分18秒 ,Mark BR写道:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is it

under-rated for that job?



--

Mark BR


http://www.cheapuggbootsonline2012.co.uk/

[email protected] October 5th 12 10:15 AM

Bell wire rating
 
在 2012年10月4日星期四UTC+8下午4时20分18秒 ,Mark BR写道:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is it

under-rated for that job?



--

Mark BR


http://www.cheapuggbootsonline2012.co.uk/

[email protected] October 5th 12 10:57 AM

Bell wire rating
 
On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or is it


under-rated for that job?




In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.


Bell wire is capable, just not lawful. And burying it in plaster can't be counted as a 2nd layer of insulation :)


NT

Lieutenant Scott October 26th 12 08:47 PM

Bell wire rating
 
On Thu, 04 Oct 2012 10:24:49 +0100, Tim Watts wrote:

wrote:

On Thursday, October 4, 2012 9:20:18 AM UTC+1, Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it

under-rated for that job?


It can handle the current ok, and the voltage, but the insulation is
inadequate to comply with current law.


Wot he said.

You need the appropriate insulation *and* sheathing.


Only to comply with the law, otherwise it's fine.

--
http://petersparrots.com
http://petersphotos.com

If people from Poland are called Poles, why aren't people from Holland called Holes?

Lieutenant Scott October 26th 12 08:48 PM

Bell wire rating
 
On Fri, 05 Oct 2012 09:28:41 +0100, Mark BR wrote:


"DerbyBorn" wrote in message
2.222...
"Dave Plowman (News)" wrote in
:

In article ,
Mark BR wrote:
Can I use 'bell wire' for a room thermostat for the combi boiler, or is
it under-rated for that job?




Perhaps someone is reading the wrong message from "Volts Free Contacts"
which is stated on many thermostats.


I did spend some time wondering what 'volts free' actually meant!

OK I've got some 'proper' 240volt twin flex to wire up the thermostat. Wish
I could find a use for half a roll of bell wire.


Wire speakers up all over the house.

--
http://petersparrots.com
http://petersphotos.com

101 Dalmatians and Peter Pan are the only two Disney animated features in which both the parents are present and don't die throughout the movie.

Lieutenant Scott October 26th 12 08:48 PM

Bell wire rating
 
On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or is it


under-rated for that job?




In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.


Bell wire is capable, just not lawful. And burying it in plaster can't be counted as a 2nd layer of insulation :)


Plaster conducts does it?

--
http://petersparrots.com
http://petersphotos.com

"Sir, your daughter says she loves me, she can't live without me, and wants to marry me."
"And you're asking my permission to marry her?"
"No, I'm asking you to make her leave me the hell alone!!"

Tim Watts[_2_] October 26th 12 09:49 PM

Bell wire rating
 
Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it

under-rated for that job?



In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.


Bell wire is capable, just not lawful. And burying it in plaster can't be
counted as a 2nd layer of insulation :)


Plaster conducts does it?


More than you know - especially if slightly damp!
--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"A fanatic is one who can't change his mind and won't change the subject."


Lieutenant Scott October 26th 12 10:03 PM

Bell wire rating
 
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it

under-rated for that job?



In terms of current carrying capacity, it is probably adequate, however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for controls.

Bell wire is capable, just not lawful. And burying it in plaster can't be
counted as a 2nd layer of insulation :)


Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even tingle.

--
http://petersparrots.com
http://petersphotos.com

He saw her in her birthday suit swimming by the pier
She said, "Please go away," but he pretended not to hear.
"If you don't go I'll stay in here 'til it's dark."
'That's OK by me," he said, "I only came to feed the shark."
-- Benny Hill

ARW October 26th 12 10:12 PM

Bell wire rating
 
Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi
boiler, or is it

under-rated for that job?



In terms of current carrying capacity, it is probably
adequate, however it is not well enough insulated to carry mains
voltage.



The exception to this may be if the combi has a 24V option
for controls.

Bell wire is capable, just not lawful. And burying it in
plaster can't be counted as a 2nd layer of insulation :)

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't
even tingle.



How was the ECT?

--
Adam



Tim Watts[_2_] October 26th 12 10:47 PM

Bell wire rating
 
Lieutenant Scott wrote:

On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it

under-rated for that job?



In terms of current carrying capacity, it is probably adequate,
however

it is not well enough insulated to carry mains voltage.



The exception to this may be if the combi has a 24V option for
controls.

Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation :)

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.

Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.

Just because you *can* use bell wire, does not mean you *should*.

--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."


Lieutenant Scott October 26th 12 10:47 PM

Bell wire rating
 
On Fri, 26 Oct 2012 22:12:58 +0100, ARW wrote:

Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:



Can I use 'bell wire' for a room thermostat for the combi
boiler, or is it

under-rated for that job?



In terms of current carrying capacity, it is probably
adequate, however it is not well enough insulated to carry mains
voltage.



The exception to this may be if the combi has a 24V option
for controls.

Bell wire is capable, just not lawful. And burying it in
plaster can't be counted as a 2nd layer of insulation :)

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't
even tingle.



How was the ECT?


TENS is more fun.

--
http://petersparrots.com
http://petersphotos.com

When Mike got arrested, the police told him, "Anything you say will be held against you."
Mike smiled and simply replied, "Jessica Simpson's boobs."

Lieutenant Scott October 26th 12 10:56 PM

Bell wire rating
 
On Fri, 26 Oct 2012 22:47:09 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:

On Fri, 05 Oct 2012 10:57:39 +0100, wrote:

On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:



Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation :)

Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.

Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.

Just because you *can* use bell wire, does not mean you *should*.


The old days? Fairy lights still are like that (except the LED ones).

All I'm concerned with is fire, nevermind a little shock now and then.

--
http://petersparrots.com
http://petersphotos.com

A man's home is his castle, in a manor of speaking.

Tim Watts[_2_] October 27th 12 08:54 AM

Bell wire rating
 
Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED ones).


I suggest you look a little closer.

I think you will find they are double insulated and marked Class II, not
Class O.




All I'm concerned with is fire, nevermind a little shock now and then.


Do you remove items from your toaster with metal implements?

--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."


[email protected] October 27th 12 10:49 AM

Bell wire rating
 
On Friday, October 26, 2012 10:47:12 PM UTC+1, Tim Watts wrote:
Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:
On Fri, 05 Oct 2012 10:57:39 +0100, wrote:
On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:


Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it
under-rated for that job?


In terms of current carrying capacity, it is probably adequate,
however
it is not well enough insulated to carry mains voltage.
The exception to this may be if the combi has a 24V option for
controls.
Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation :)
Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.
Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.
Just because you *can* use bell wire, does not mean you *should*.


True, but that argument appears to suggest it would be safe to use buried in plaster, but its still not allowed.


NT

Tim Watts[_2_] October 27th 12 11:02 AM

Bell wire rating
 
wrote:


True, but that argument appears to suggest it would be safe to use buried
in plaster, but its still not allowed.


Not really - the risk of damaging the single layer of insulation burying in
a masonry structure is too high (nicks from tools, rough brikwork etc) and
plaster is surprisingly conductive (you know, but someone else appears not
to think so).

I knoe it's all troll food in this case, but I'm happy to debate anything :)

--
Tim Watts Personal Blog:
http://www.dionic.net/tim/

"History will be kind to me for I intend to write it."


Lieutenant Scott October 27th 12 02:02 PM

Bell wire rating
 
On Sat, 27 Oct 2012 10:49:54 +0100, wrote:

On Friday, October 26, 2012 10:47:12 PM UTC+1, Tim Watts wrote:
Lieutenant Scott wrote:
On Fri, 26 Oct 2012 21:49:52 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:
On Fri, 05 Oct 2012 10:57:39 +0100, wrote:
On Thursday, October 4, 2012 5:09:52 PM UTC+1, John Rumm wrote:
On 04/10/2012 09:16, Mark BR wrote:


Can I use 'bell wire' for a room thermostat for the combi boiler, or
is it
under-rated for that job?


In terms of current carrying capacity, it is probably adequate,
however
it is not well enough insulated to carry mains voltage.
The exception to this may be if the combi has a 24V option for
controls.
Bell wire is capable, just not lawful. And burying it in plaster can't
be counted as a 2nd layer of insulation :)
Plaster conducts does it?


More than you know - especially if slightly damp!


I've run 240 volts through bellwire, and touched the plastic. Didn't even
tingle.


That's not quite the point. It's about mechanical protection. If the
insulation gets nicked or stressed the failure is likely to propogate to the
core so now your insulation is compromised. With a secondary sheath, that
takes the stress.
Yes I know in the old days we had lamp flex or fairy lights with single
insulation - it would be rated as "Class O" - but it was considered
insufficiently safe so it is not used.
Just because you *can* use bell wire, does not mean you *should*.


True, but that argument appears to suggest it would be safe to use buried in plaster, but its still not allowed.


Not allowed isn't always anything to do with safe. It's paperpushers making **** up.

--
http://petersparrots.com
http://petersphotos.com

A female friend of mine was admitted to a private hospital to try to
lose weight. Naturally I sent her flowers.

I received a "thank-you" note several days later; it said, "Thanks for
the flowers, they were delicious!"

Lieutenant Scott October 27th 12 02:10 PM

Bell wire rating
 
On Sat, 27 Oct 2012 08:54:28 +0100, Tim Watts wrote:

Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED ones).


I suggest you look a little closer.

I think you will find they are double insulated and marked Class II, not
Class O.


I guess I haven't got that new fairy lights then. The wire is stranded copper with one sheath of plastic. Two such wires glued together.

No point in making the wire safer, the danger would be from the flimsy little bulbs which would make up to 240 volts available to your fingers (or mouth in the case of a baby eating one).

All I'm concerned with is fire, nevermind a little shock now and then.


Do you remove items from your toaster with metal implements?


I've had several shocks from the mains, it's not dangerous.

--
http://petersparrots.com
http://petersphotos.com

Peter is listening to "Eagles - Hotel California"

ARW October 27th 12 02:16 PM

Bell wire rating
 
Lieutenant Scott wrote:
On Sat, 27 Oct 2012 08:54:28 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED
ones).


I suggest you look a little closer.

I think you will find they are double insulated and marked Class
II, not Class O.


I guess I haven't got that new fairy lights then. The wire is
stranded copper with one sheath of plastic. Two such wires glued
together.
No point in making the wire safer, the danger would be from the
flimsy little bulbs which would make up to 240 volts available to
your fingers (or mouth in the case of a baby eating one).
All I'm concerned with is fire, nevermind a little shock now and
then.


Do you remove items from your toaster with metal implements?


I've had several shocks from the mains, it's not dangerous.


And it caused no brain damage at all.

--
Adam



Lieutenant Scott October 27th 12 02:24 PM

Bell wire rating
 
On Sat, 27 Oct 2012 14:16:59 +0100, ARW wrote:

Lieutenant Scott wrote:
On Sat, 27 Oct 2012 08:54:28 +0100, Tim Watts
wrote:
Lieutenant Scott wrote:


The old days? Fairy lights still are like that (except the LED
ones).

I suggest you look a little closer.

I think you will find they are double insulated and marked Class
II, not Class O.


I guess I haven't got that new fairy lights then. The wire is
stranded copper with one sheath of plastic. Two such wires glued
together.
No point in making the wire safer, the danger would be from the
flimsy little bulbs which would make up to 240 volts available to
your fingers (or mouth in the case of a baby eating one).
All I'm concerned with is fire, nevermind a little shock now and
then.

Do you remove items from your toaster with metal implements?


I've had several shocks from the mains, it's not dangerous.


And it caused no brain damage at all.


I don't tend to insert the wires into my ears.

--
http://petersparrots.com
http://petersphotos.com

Philosophy is questions that may never be answered. Religion is answers that may never be questioned.

Tim Watts[_2_] October 27th 12 02:40 PM

Bell wire rating
 
Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"
--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."


Lieutenant Scott October 27th 12 02:51 PM

Bell wire rating
 
On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and those that tell others they're doing it wrong. I prefer the first kind.

--
http://petersparrots.com
http://petersphotos.com

A little girl asked her mother, "Can I go outside and play with the boys?"
Her mother replied, "No, you can't play with the boys, they're too rough."
The little girl thought about it for a few moments and asked, "If I can find a smooth one, can I play with him?"

Steve Firth October 27th 12 02:54 PM

Bell wire rating
 
"ARW" wrote:
Lieutenant Scott wrote:

[snip]

I've had several shocks from the mains, it's not dangerous.


And it caused no brain damage at all.


One cannot damage that which does not exist.

Which appears to be your point.

--
DarWin|
_/ _/

Dave Plowman (News) October 27th 12 03:43 PM

Bell wire rating
 
In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.


Really? I'd say it accounts for your fried brain.

--
*Gravity is a myth, the earth sucks *

Dave Plowman London SW
To e-mail, change noise into sound.

Lieutenant Scott October 27th 12 04:09 PM

Bell wire rating
 
On Sat, 27 Oct 2012 15:43:24 +0100, Dave Plowman (News) wrote:

In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.


Really? I'd say it accounts for your fried brain.


I didn't insert the wires into my ears.

--
http://petersparrots.com
http://petersphotos.com

He was so unlucky . . .
Last week, his inflatable doll ran off with his airbag.

ARW October 27th 12 04:11 PM

Bell wire rating
 
Lieutenant Scott wrote:
On Sat, 27 Oct 2012 15:43:24 +0100, Dave Plowman (News)
wrote:
In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.


Really? I'd say it accounts for your fried brain.


I didn't insert the wires into my ears.


You are still a thick daft ****.

--
Adam



Lieutenant Scott October 27th 12 04:14 PM

Bell wire rating
 
On Sat, 27 Oct 2012 16:11:45 +0100, ARW wrote:

Lieutenant Scott wrote:
On Sat, 27 Oct 2012 15:43:24 +0100, Dave Plowman (News)
wrote:
In article op.wmt9kfn7ytk5n5@i7-940,
Lieutenant Scott wrote:
I've had several shocks from the mains, it's not dangerous.

Really? I'd say it accounts for your fried brain.


I didn't insert the wires into my ears.


You are still a thick daft ****.


Show your working.

--
http://petersparrots.com
http://petersphotos.com

The only differences between lawyers and prostitutes are that prostitutes are generally better looking and more honest about how they make a living.

Tim Watts[_2_] October 27th 12 04:28 PM

Bell wire rating
 
Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?
--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"She got her looks from her father. He's a plastic surgeon."


Lieutenant Scott October 27th 12 04:37 PM

Bell wire rating
 
On Sat, 27 Oct 2012 16:28:46 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?


That's just greed.

--
http://petersparrots.com
http://petersphotos.com

A man has six items in his bathroom: toothbrush and toothpaste, shaving cream, razor, a bar of soap, and a towel.
The average number of items in the typical woman's bathroom is 337. A man would not be able to identify more than 20 of these items.

Lieutenant Scott October 27th 12 04:37 PM

Bell wire rating
 
On Sat, 27 Oct 2012 16:28:46 +0100, Tim Watts wrote:

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper pushers"


There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?


You only get let into such committees if you're a health and safety conscious ****t.

--
http://petersparrots.com
http://petersphotos.com

A man has six items in his bathroom: toothbrush and toothpaste, shaving cream, razor, a bar of soap, and a towel.
The average number of items in the typical woman's bathroom is 337. A man would not be able to identify more than 20 of these items.

Tim Watts[_2_] October 27th 12 07:16 PM

Bell wire rating
 
Lieutenant Scott wrote:

On Sat, 27 Oct 2012 16:28:46 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:

On Sat, 27 Oct 2012 14:40:28 +0100, Tim Watts
wrote:

Lieutenant Scott wrote:


Not allowed isn't always anything to do with safe. It's paperpushers
making **** up.


I would hardly describe a bunch of chartered engineers as "paper
pushers"

There are two sets of people in this world. Those that do things, and
those that tell others they're doing it wrong. I prefer the first kind.


You don't suppose that the engineers who sit on the regs committee might
also have other actual jobs too?


That's just greed.


Oh do stop being a ****.


--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"It would be better to live under robber barons than under omnipotent
moral busybodies."



All times are GMT +1. The time now is 10:42 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright 2004 - 2014 DIYbanter