Yikes, blown the suppy company neutral fuse ...
There I was tonight in this super newly installed electric shower (oh,
and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? -- Adrian C |
#2
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
"Adrian C" wrote in message
... There I was tonight in this super newly installed electric shower (oh, and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? -- Adrian C Is it because neutrals are not fused now - in case a neutral only blows it could leave the circuits live. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Adrian C wrote:
There I was tonight in this super newly installed electric shower (oh, and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? There shouldn't be a neutral fuse by the standards of the past mumble decades, which is why he was surprised. If it that ancient, they might well replace the cutout completely now or real soon. At the very least, it's almost certain he'll replace the neutral fuse with a solid link at least for now and replace the live fuse. Another issue is what the cutout is actually rated at - you can't bung a 100A fuse in any ancient old crap. But a 60A supply fuse should cope OK with a shower plus reasonable other loads unless you spend an hour in the shower while running the leccy cooker and fan heaters flat out. As a very general rule of thumb, a typical fuse in this class (and there are a few classes of cutout fuse) will take around 30 mins to blow at double it's rated load, ie 120A for a 60A fuse so you can get away with a bit. -- Tim Watts |
#4
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Tim Watts wrote:
Adrian C wrote: There I was tonight in this super newly installed electric shower (oh, and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? There shouldn't be a neutral fuse by the standards of the past mumble decades, which is why he was surprised. If it that ancient, they might well replace the cutout completely now or real soon. At the very least, it's almost certain he'll replace the neutral fuse with a solid link at least for now and replace the live fuse. I suspect that is what will happen. And no sales talk at all -- Adam |
#5
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Tue, 31 Aug 2010 22:25:44 +0100, Adrian C
wrote: There I was tonight in this super newly installed electric shower (oh, and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? I find the distribution people (the ones who actually install and maintain the supply rather than the ones to whom you pay your bill) (Mine's CE, formerly NEDL (nee NEEB)) are usually down-to-earth (no pun intended) engineers rather than sales-orientated types. Normally the neutral "fuse" nowadays is bypassed with a solid bar to avoid the whole system becoming live if a neutral fuse should rupture rather than the line one. -- Frank Erskine Sunderland |
#6
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Normally the neutral "fuse" nowadays is bypassed with a solid bar to avoid the whole system becoming live if a neutral fuse should rupture rather than the line one. I've not met a neutral "board" fuse, but I remember my Grandmother had a metal-clad fuse-box with a fuse in the live and neutral of each circuit. I think its installation had a lot to do with equipment shortages during the war. Incidentally all the sockets were those Wylex ones with in-line pins. -- Graham. %Profound_observation% |
#7
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Tue, 31 Aug 2010 22:25:44 +0100, Adrian C
wrote: There I was tonight in this super newly installed electric shower (oh, and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? When I did something similar (worked on a socket while live to avoid disturbing SWMBO while she was watching Tarnation Street) I didn't get billed because the fuse was 60A in a 4 bed house. Derek |
#8
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 31 Aug, 22:44, Tim Watts wrote:
Adrian C wrote: There I was tonight in this super newly installed electric shower (oh, and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? There shouldn't be a neutral fuse by the standards of the past mumble decades, which is why he was surprised. If it that ancient, they might well replace the cutout completely now or real soon. At the very least, it's almost certain he'll replace the neutral fuse with a solid link at least for now and replace the live fuse. Another issue is what the cutout is actually rated at - you can't bung a 100A fuse in any ancient old crap. But a 60A supply fuse should cope OK with a shower plus reasonable other loads unless you spend an hour in the shower while running the leccy cooker and fan heaters flat out. As a very general rule of thumb, a typical fuse in this class (and there are a few classes of cutout fuse) will take around 30 mins to blow at double it's rated load, ie 120A for a 60A fuse so you can get away with a bit. -- Tim Watts- Hide quoted text - - Show quoted text - I think this post is a load of ********. There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Tue, 31 Aug 2010 22:25:44 +0100, Adrian C wrote:
The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. There was aprogramme within the Supply Industry to remove all rewireable fuses back in the 1970's - 80's from memory. Needless to say not all were replaced, although managers were declaring in returns that they were. The replacement will be at their expense. -- The Wanderer The older I get the better I used to be! |
#10
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
harry wrote:
I think this post is a load of ********. There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. You sure about that? -- Tim Watts |
#11
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 01/09/2010 07:17, harry wrote:
I think this post is a load of ********. There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Well, this house was built in 1932, and rewired in 1970. Fuses are dead centre of this pic - so these would have been 1930s DC fuses? http://i912.photobucket.com/albums/a...rthestairs.jpg Not suprised, I have here this GPO relic my ADSL passes through ... http://i912.photobucket.com/albums/a...r/IMG_2832.jpg Electicity company peeps due today, and for interest will be snapping the replacements they fit. -- Adrian C |
#12
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 07:17, harry wrote:
I think this post is a load of ********. *There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. * Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Friend of mine moved house last year. Their 1920s house (in an area that was one of the last DC supply areas in the country) still had two fuses, and electrics to match. This wasn't even picked up on the survey. I have a neutral fuse here, although it's on a supply that was removed in 2000. Some other equipment adjacent to it is '80s dated though, and no-one thought to remove the neutral fuse at the time. I think it was installed on a 1950s AC overhead supply. If a neutral fuse fails, you're well rid of it. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 31 Aug, 23:17, Frank Erskine wrote:
I find the distribution people (the ones who actually install and maintain the supply rather than the ones to whom you pay your bill) (Mine's CE, formerly NEDL (nee NEEB)) are usually down-to-earth (no pun intended) engineers rather than sales-orientated types. Amen to that! Western Power Distribution in my case. I have a billing problem at present. "Good Energy" are trying to bill me £1500, for £120 of electricity I've already paid for, through a supply that has been disconnected for 10 years, when I'm not even a Good Energy customer. The only people who've been at all helpful in resolving this have been WPD, even though billing is the one part of it that isn't even their problem. |
#14
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Not suprised, I have here this GPO relic my ADSL passes through ... http://i912.photobucket.com/albums/a...r/IMG_2832.jpg i got one of them too! what does it do if anything? could *anyone* remove/replace with something less obvious? if only BT is it a chargeable to get it changed? Jim K |
#15
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Adrian C wrote:
On 01/09/2010 07:17, harry wrote: I think this post is a load of ********. There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Well, this house was built in 1932, and rewired in 1970. Fuses are dead centre of this pic - so these would have been 1930s DC fuses? http://i912.photobucket.com/albums/a...rthestairs.jpg Cripes. That looks EXACTLY like my old house looked. Also rewired in the 70's. Badly. |
#16
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
"harry" wrote in message ... I think this post is a load of ********. There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. I suspect there are still many neutral fuses left sitting undisturbed. The ESQC Regulations 7(2) do require DNOs to remove them: http://www.legislation.gov.uk/uksi/2...ulation/7/made and the guidance says they must do it by 2013: http://www.decc.gov.uk/assets/decc/w.../file26709.pdf Regards Bruce |
#17
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Andy Dingley wrote: On 1 Sep, 07:17, harry wrote: I think this post is a load of ********. *There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. * Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Friend of mine moved house last year. Their 1920s house (in an area that was one of the last DC supply areas in the country) still had two fuses, and electrics to match. This wasn't even picked up on the survey. I have a neutral fuse here, although it's on a supply that was removed in 2000. Some other equipment adjacent to it is '80s dated though, and no-one thought to remove the neutral fuse at the time. I think it was installed on a 1950s AC overhead supply. If a neutral fuse fails, you're well rid of it. Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, and there is no discrimination at the sockets between live and neutral, together with random variation from socket to socket as to whether it offers an earth. From my trips to Norway, I have looked at their standard domestic electrical setup and shuddered. Cartridge fuses in both live and neutral at the consumer unit, unshuttered sockets with mixed live and neutral - and two pin plugs that can be inserted either way round. And they wonder why they have so many electrically-caused house fires. Oh, and ring circuits are unheard of. Sid |
#18
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 11:45, Sidney Endon-Lee wrote:
Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, If you've already taken the route of two-pin connections and relying on insulation more than an earthed case, then there's less need to avoid the fused neutral. You have however lost the benefits of metal cases being earthed, for protection against internal shorts to that case. |
#19
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Andy Dingley wrote:
On 1 Sep, 11:45, Sidney Endon-Lee wrote: Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, If you've already taken the route of two-pin connections and relying on insulation more than an earthed case, then there's less need to avoid the fused neutral. You have however lost the benefits of metal cases being earthed, for protection against internal shorts to that case. Thinking back to my pole mounted transformer, which I think had a neutral fuse, its actually not really clear which is live and which is neutral. You CREATED a neutral by driving a stake into the ground, and connecting one side of the supply to it. I am not sure which side of the fuse that was. I can envisage a situation where someone shorts the live side to earth upstream of the fuse..then maybe a neutral side fuse makes sense. Anyway, glad its all gone now. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Wed, 01 Sep 2010 03:45:06 -0700, Sidney Endon-Lee wrote:
Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, and there is no discrimination at the sockets between live and neutral, together with random variation from socket to socket as to whether it offers an earth. From my trips to Norway, I have looked at their standard domestic electrical setup and shuddered. Cartridge fuses in both live and neutral at the consumer unit, unshuttered sockets with mixed live and neutral - and two pin plugs that can be inserted either way round. And they wonder why they have so many electrically-caused house fires. Oh, and ring circuits are unheard of. That sounds like my setup here in the US... two modern breaker panels, load control relays, four ancient fuse boxes (mixture of barrel and screw- in fuses), a big knife switch for the well pump, a plethora of wall socket types (some grounded, some not), and a mixture of modern wire and old cloth-covered stuff. Most of it's 110V, some of it's 220. cheers Jules |
#21
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Wed, 1 Sep 2010 02:24:19 -0700 (PDT), Jim K
wrote: Not suprised, I have here this GPO relic my ADSL passes through ... http://i912.photobucket.com/albums/a...r/IMG_2832.jpg i got one of them too! what does it do if anything? could *anyone* remove/replace with something less obvious? if only BT is it a chargeable to get it changed? As it stands it's only a fuseholder. The carbon surge protectors will have been removed - their capacitance would be far too great for ADSL. Fuses are no longer fitted at subscribers' premises (with perhaps a very few exceptions) so it could be replaced by a standard Block Terminal. Normally the master socket (NTE5) is fitted at this point so that all the subsequent internal wiring is the responsibility of the subscriber! -- Frank Erskine |
#22
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 10:24, Jim K wrote:
Not suprised, I have here this GPO relic my ADSL passes through ... http://i912.photobucket.com/albums/a...r/IMG_2832.jpg i got one of them too! what does it do if anything? could *anyone* remove/replace with something less obvious? if only BT is it a chargeable to get it changed? Jim K I guess it is at the junction of where the external wire enters your property and picks up the internal cable. It is a junction/protection box which often had dummy fuses if fed from an underground cable. Only BT Openreach can officially remove it, but assuming it feeds a standard BT Master Socket, which includes protection, you could bypass it with a modern box like this one http://www.run-it-direct.co.uk/BT77B.html and I doubt anybody would find out. There are only two wires in and two wires out. John |
#23
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Tue, 31 Aug 2010 23:17:58 -0700 (PDT), harry wrote:
On 31 Aug, 22:44, Tim Watts wrote: Adrian C wrote: There I was tonight in this super newly installed electric shower (oh, and gas - but that's for another tale) and using it for the first time. 10.5kW, 44Amps or thereabouts. Wired via an RCD and spliced into the existing meter tails to the existing consumer unit. My thoughts are on how great this mains pressure shower actually is. Then the lights went out. Silence. Great Call for SWMBO. Nothing. She'd left the house to potter in the garden shed. I'm wet, covered in soap suds, can't see a thing, where is the blinkin torch... Ah, the meter ain't displaying. We've blown the supplier main fuse. All other fuses, trips and RCDs fine. The guy from the emergency electrical service sorts it out, and we are back on again. However, our supplier fuses are old - probably 50 or 60 years - and from his comments look to be wired with 30 amp fuse wire. That said, the shower overload has taken out both the live and neutral fuse wires. He whistles though his teeth, sez "neutral, that is weird" and trundles off with a promise to be back tomorrow to uprate the fuses to a more consumer friendly 100 amps. I can't see anything strange in the neutral fuse expiring, it has been on duty for ages - and the overload of our new shower has shown it the cards. So why is this guy whistling through his teeth? Is tomorrow going to be a likely sales opportunity for his company? There shouldn't be a neutral fuse by the standards of the past mumble decades, which is why he was surprised. If it that ancient, they might well replace the cutout completely now or real soon. At the very least, it's almost certain he'll replace the neutral fuse with a solid link at least for now and replace the live fuse. Another issue is what the cutout is actually rated at - you can't bung a 100A fuse in any ancient old crap. But a 60A supply fuse should cope OK with a shower plus reasonable other loads unless you spend an hour in the shower while running the leccy cooker and fan heaters flat out. As a very general rule of thumb, a typical fuse in this class (and there are a few classes of cutout fuse) will take around 30 mins to blow at double it's rated load, ie 120A for a 60A fuse so you can get away with a bit. -- Tim Watts- Hide quoted text - - Show quoted text - I think this post is a load of ********. There hasn't been fuses in neutrals since the days of DC (ie 1930s). Oh, I'm afraid there have, and still are. They should have gone long since, but there are still lots around. I used to work for the electricity board. So did I. Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. You'd think so. -- The Wanderer The future isn't what it used to be. |
#24
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Wed, 01 Sep 2010 14:08:17 +0100, The Natural Philosopher wrote:
Andy Dingley wrote: On 1 Sep, 11:45, Sidney Endon-Lee wrote: Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, If you've already taken the route of two-pin connections and relying on insulation more than an earthed case, then there's less need to avoid the fused neutral. You have however lost the benefits of metal cases being earthed, for protection against internal shorts to that case. Thinking back to my pole mounted transformer, which I think had a neutral fuse, Nope, never. its actually not really clear which is live and which is neutral. Depends whether it's a two wire, split phase, or three phase transformer. You CREATED a neutral by driving a stake into the ground, and connecting one side of the supply to it. I am not sure which side of the fuse that was. Rubbish. Consumer earth rods have nothing to do with earthing the incoming supply neutral. The supply company *always* earthed their system to create a neutral. That went back as far as the 1922 Electricity Supply Regulations, now superceded by the Electricity Safety, Quality and Continuity Regulations 2002. Oh, and that goes for hv and ehv systems as well. I can envisage a situation where someone shorts the live side to earth upstream of the fuse..then maybe a neutral side fuse makes sense. Unfortunately what you envisage makes no sense, given that the neutral must always remain intact since the introduction of PME. Neutral Inversion, OTOH, can be a problem, particularly in rural areas, but that requires two or three things to have gone wrong, both with a customer's installation and the supply network. Please don't try spouting on matters about which you have not the first idea. -- The Wanderer Life is a catastrophic success. |
#25
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 11:45, Sidney Endon-Lee wrote:
Andy Dingley wrote: On 1 Sep, 07:17, harry wrote: I think this post is a load of ********. *There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. * Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Friend of mine moved house last year. Their 1920s house (in an area that was one of the last DC supply areas in the country) still had two fuses, and electrics to match. This wasn't even picked up on the survey. I have a neutral fuse here, although it's on a supply that was removed in 2000. Some other equipment adjacent to it is '80s dated though, and no-one thought to remove the neutral fuse at the time. I think it was installed on a 1950s AC overhead supply. If a neutral fuse fails, you're well rid of it. Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, and there is no discrimination at the sockets between live and neutral, together with random variation from socket to socket as to whether it offers an earth. From my trips to Norway, I have looked at their standard domestic electrical setup and shuddered. Cartridge fuses in both live and neutral at the consumer unit, unshuttered sockets with mixed live and neutral - and two pin plugs that can be inserted either way round. And they wonder why they have so many electrically-caused house fires. Maybe it's the same reason so many fires are blamed on "electrical faults" here... I have read that Norway uses 230v three-phase supplies, with no neutral, so single-phase appliances are connected between two phases, therefore both wires are live. Oh, and ring circuits are unheard of. Ring circuits and fused plugs were introduced in the UK to save copper etc. in the post-WW2 rebuilding programme, they have a number of disadvantages. Sid |
#26
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 13:56, Andy Dingley wrote:
On 1 Sep, 11:45, Sidney Endon-Lee wrote: Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, If you've already taken the route of two-pin connections and relying on insulation more than an earthed case, then there's less need to avoid the fused neutral. You have however lost the benefits of metal cases being earthed, for protection against internal shorts to that case. This is 'Class 0' protection, which has not been permitted in the UK for many years, and is now on the way out on the Continent, it relies on there being no extraneous conductive parts and an insulating floor to limit shock current, even there it was prohibited in conductive locations such as concrete floors, kitchens, bathrooms, cellars etc. |
#27
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 09:44, Adrian C wrote:
On 01/09/2010 07:17, harry wrote: I think this post is a load of ********. *There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. * Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Well, this house was built in 1932, and rewired in 1970. Fuses are dead centre of this pic - so these would have been 1930s DC fuses? http://i912.photobucket.com/albums/a...rthestairs.jpg Not suprised, I have here this GPO relic my ADSL passes through ... http://i912.photobucket.com/albums/a...r/IMG_2832.jpg Electicity company peeps due today, and for interest will be snapping the replacements they fit. -- Adrian C That is 1930's gear. They must be damned ingompetent to leave such stuff about. The last time saw equipment like that was in the early 60's and that was overlooked from 30 years before that. I wonder who fitted that new meter? The incoming cable looks fairly dodgy too. |
#28
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 21:28, "alexander.keys1" wrote:
On 1 Sep, 11:45, Sidney Endon-Lee wrote: Andy Dingley wrote: On 1 Sep, 07:17, harry wrote: I think this post is a load of ********. *There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. * Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Friend of mine moved house last year. Their 1920s house (in an area that was one of the last DC supply areas in the country) still had two fuses, and electrics to match. This wasn't even picked up on the survey. I have a neutral fuse here, although it's on a supply that was removed in 2000. Some other equipment adjacent to it is '80s dated though, and no-one thought to remove the neutral fuse at the time. I think it was installed on a 1950s AC overhead supply. If a neutral fuse fails, you're well rid of it. Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, and there is no discrimination at the sockets between live and neutral, together with random variation from socket to socket as to whether it offers an earth. From my trips to Norway, I have looked at their standard domestic electrical setup and shuddered. Cartridge fuses in both live and neutral at the consumer unit, unshuttered sockets with mixed live and neutral - and two pin plugs that can be inserted either way round. And they wonder why they have so many electrically-caused house fires. Maybe it's the same reason so many fires are blamed on "electrical faults" here... I have read that Norway uses 230v three-phase supplies, with no neutral, so single-phase appliances are connected between two phases, therefore both wires are live. Oh, and ring circuits are unheard of. Ring circuits and fused plugs were introduced in the UK to save copper etc. in the post-WW2 rebuilding programme, they have a number of disadvantages. Sid- Hide quoted text - - Show quoted text -- Hide quoted text - - Show quoted text - Which are? |
#29
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 21:28, "alexander.keys1" wrote:
On 1 Sep, 11:45, Sidney Endon-Lee wrote: Andy Dingley wrote: On 1 Sep, 07:17, harry wrote: I think this post is a load of ********. *There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. * Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Friend of mine moved house last year. Their 1920s house (in an area that was one of the last DC supply areas in the country) still had two fuses, and electrics to match. This wasn't even picked up on the survey. I have a neutral fuse here, although it's on a supply that was removed in 2000. Some other equipment adjacent to it is '80s dated though, and no-one thought to remove the neutral fuse at the time. I think it was installed on a 1950s AC overhead supply. If a neutral fuse fails, you're well rid of it. Interestingly, in large parts of continental Europe, it is standard to have both live and neutral fuses, and there is no discrimination at the sockets between live and neutral, together with random variation from socket to socket as to whether it offers an earth. From my trips to Norway, I have looked at their standard domestic electrical setup and shuddered. Cartridge fuses in both live and neutral at the consumer unit, unshuttered sockets with mixed live and neutral - and two pin plugs that can be inserted either way round. And they wonder why they have so many electrically-caused house fires. Maybe it's the same reason so many fires are blamed on "electrical faults" here... I have read that Norway uses 230v three-phase supplies, with no neutral, so single-phase appliances are connected between two phases, therefore both wires are live. Oh, and ring circuits are unheard of. Ring circuits and fused plugs were introduced in the UK to save copper etc. in the post-WW2 rebuilding programme, they have a number of disadvantages. Sid- Hide quoted text - - Show quoted text -- Hide quoted text - - Show quoted text - In days of yore in the UK there were three wire DC sytems that were 120/240 volt. There were two fuses on these sytems Most supplied from local mines and factories, ie not part of a national grid. The wealthy had their own supply run from gas engines or similar. |
#30
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep, 22:09, harry wrote:
On 1 Sep, 09:44, Adrian C wrote: On 01/09/2010 07:17, harry wrote: I think this post is a load of ********. *There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. * Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Well, this house was built in 1932, and rewired in 1970. Fuses are dead centre of this pic - so these would have been 1930s DC fuses? http://i912.photobucket.com/albums/a...rthestairs.jpg Not suprised, I have here this GPO relic my ADSL passes through ... http://i912.photobucket.com/albums/a...r/IMG_2832.jpg Electicity company peeps due today, and for interest will be snapping the replacements they fit. -- Adrian C That is 1930's gear. *They must be damned ingompetent to leave such stuff about. *The last time *saw equipment like that was in the early 60's and that was overlooked from 30 years before that. *I wonder who fitted that new meter? *The incoming cable looks fairly dodgy too.- Hide quoted text - - Show quoted text - Sometimes there were AC sytems where there was a centre tap to the transformer winding so both poles were live to earth, ergo both poles were fused. There was no neutral. Similar to 110volt tool transformers today. |
#31
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Wed, 1 Sep 2010 13:28:47 -0700 (PDT), "alexander.keys1"
wrote: Ring circuits and fused plugs were introduced in the UK to save copper etc. in the post-WW2 rebuilding programme, they have a number of disadvantages. Probably the biggest disadvantage of early ring circuits was that a lot of leccies didn't really understand them, and took each end of the ring to a separate fuse. If one fuse blew for any reason the whole (non) ring was then fed from one fuse, albeit probably only 15A (unless they'd doubled the 15A fuse wire in the carrier). -- Frank Erskine |
#32
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On 1 Sep,
harry wrote: I think this post is a load of ********. There hasn't been fuses in neutrals since the days of DC (ie 1930s). I used to work for the electricity board. Someone would have removed equipment like that when the meter/supply cable was replaced years ago. No electrician who sees such a thing is going to fail to report it. Extra sockets 15A and 5A) were fitted to my parent's house in 1957. A new fuse box was installed with double pole fusing, and TRS cable. This was installed by NEEB. It was replaced with SP fusing, PVC cable and 13A sockets in the mid 60s. -- B Thumbs Change lycos to yahoo to reply |
#33
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
"harry" wrote in message ... On 1 Sep, 21:28, "alexander.keys1" wrote: snip : Ring circuits and fused plugs were introduced in the UK : to save copper etc. in the post-WW2 rebuilding programme, : they have a number of disadvantages. : Which are? I take it that you have never come across the bolt being used as a 'fusible' link within the a Bullshi... sorry BS1363 plug that is feeding a device that draws 3amp via a similar rated length of flex. I take it that you have never come across the situation were an faulty appliance fails to blow the fusible wire within the Bull****... sorry BS1363 plug but trips out the much more sensitive CB on the panel, taking out all other devices connected to that circuit (which in a house can be the entire power circuit. The ONLY two advantage of ring circuits is installation cost and smaller size of fuse/CB panel. -- Regards, Jerry. |
#34
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
Jerry wrote: "harry" wrote in message ... On 1 Sep, 21:28, "alexander.keys1" wrote: snip : Ring circuits and fused plugs were introduced in the UK : to save copper etc. in the post-WW2 rebuilding programme, : they have a number of disadvantages. : Which are? I take it that you have never come across the bolt being used as a 'fusible' link within the a Bullshi... sorry BS1363 plug that is feeding a device that draws 3amp via a similar rated length of flex. I take it that you have never come across the situation were an faulty appliance fails to blow the fusible wire within the Bull****... sorry BS1363 plug but trips out the much more sensitive CB on the panel, taking out all other devices connected to that circuit (which in a house can be the entire power circuit. The ONLY two advantage of ring circuits is installation cost and smaller size of fuse/CB panel. -- Regards, Jerry. Jerry, I am happy for you that you are so certain. I suggest you practise 'thinking around the problem' a little more, and also clarifying your thinking. There are benefits and disadvantages to ring and spur circuits; and benefits and disadvantages to fuses and circuit breakers; and benefits and disadvantages to having fuses in plug-tops or at the consumer unit. Different choices will be better in different situations, and it is well worth understanding that. It is not the case that one method is unambiguously better than all the others in all situations. To give an example: generally, domestic lighting circuits are not ring circuits, even though the circuit serving sockets frequently is. You might like to reflect on why that is. You may also like to reflect on why it is not uncommon for kitchens to have a ring circuit separate from the other circuits in a dwelling; and why immersion heaters are usually put on their own spur. And to start things off, what do you think the function of a plug-top fuse is? Regards, SId |
#35
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Thu, 02 Sep 2010 09:14:39 +0100, Jerry wrote:
I take it that you have never come across the bolt being used as a 'fusible' link within the a Bullshi... sorry BS1363 plug that is feeding a device that draws 3amp via a similar rated length of flex. And this never happens with other fuses? Of course it does. Anyway, it's quite hard to use abol;t with many modern moulded plugs. And no, I haven't come across it. Anyone who does that has probably done lots of other dangerous things too. I take it that you have never come across the situation were an faulty appliance fails to blow the fusible wire within the Bull****... sorry BS1363 plug but trips out the much more sensitive CB on the panel, taking out all other devices connected to that circuit (which in a house can be the entire power circuit. Pretty badly designed if it's the ONLY power circuit - our house has five rings. -- Use the BIG mirror service in the UK: http://www.mirrorservice.org *lightning protection* - a w_tom conductor |
#36
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
"Bob Eager" wrote in message ... : On Thu, 02 Sep 2010 09:14:39 +0100, Jerry wrote: : : I take it that you have never come across the bolt being used as : a 'fusible' link within the a Bullshi... sorry BS1363 plug that is : feeding a device that draws 3amp via a similar rated length of flex. : : And this never happens with other fuses? Of course it does. Anyway, it's : quite hard to use abol;t with many modern moulded plugs. ********, it only need metal the same dia of the BS fuse, rather than having to dismantle a distribution board, take out a CB and replace even with a higher rated unit never mind a solid bridge. : : And no, I haven't come across it. Anyone who does that has probably done : lots of other dangerous things too. Your point being what, exactly?... : : I take it that you have never come across the situation were an faulty : appliance fails to blow the fusible wire within the Bull****... sorry : BS1363 plug but trips out the much more sensitive CB on the panel, : taking out all other devices connected to that circuit (which in a house : can be the entire power circuit. : : Pretty badly designed if it's the ONLY power circuit - our house has five : rings. : Only if you are being a pedantic fool and taking the meaning of the word "House" to me a multi floor dwelling rather than the more usual generic meaning of the word as a place were people live. Anyway, even if there was multiple ring circuits one faulty device will still take out all devices being powered from that circuit rather than just the one or two that would be on a radial circuit. -- Regards, Jerry. |
#37
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
alexander.keys1 wrote: I have read that Norway uses 230v three-phase supplies, with no neutral, so single-phase appliances are connected between two phases, therefore both wires are live. I was sufficiently intrigued to look that up, and you are completely correct - that standard domestic supply in Norway is IT, so the voltage from phase to neutral is about 133 V , and the voltage between phases is 230V. However, all new systems are now required to be TN. I don't know if there are any standards in Norway for the phase to ground/earth voltage i.e. by how much neutral can float. I guess that means all appliance and light switches need to be dual pole. It's a very different system to the UK. |
#38
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
"Sidney Endon-Lee" wrote in message ... : : : Jerry wrote: : "harry" wrote in message : ... : On 1 Sep, 21:28, "alexander.keys1" : wrote: : : snip : : Ring circuits and fused plugs were introduced in the UK : : to save copper etc. in the post-WW2 rebuilding programme, : : they have a number of disadvantages. : : : Which are? : : I take it that you have never come across the bolt being used as : a 'fusible' link within the a Bullshi... sorry BS1363 plug that : is feeding a device that draws 3amp via a similar rated length : of flex. : : I take it that you have never come across the situation were an : faulty appliance fails to blow the fusible wire within the : Bull****... sorry BS1363 plug but trips out the much more : sensitive CB on the panel, taking out all other devices connected : to that circuit (which in a house can be the entire power : circuit. : : The ONLY two advantage of ring circuits is installation cost and : smaller size of fuse/CB panel. : -- : Regards, Jerry. : : Jerry, : : I am happy for you that you are so certain. I suggest you practise : 'thinking around the problem' a little more, Who says I have not 'though through these problems', perhaps that IS why I have come to the conclusions I have... and also clarifying your : thinking. There are benefits and disadvantages to ring and spur : circuits; Err, spur circuits are supplied from ring circuits, thus they are one and the same, duh! and benefits and disadvantages to fuses and circuit : breakers; and benefits and disadvantages to having fuses in plug-tops : or at the consumer unit. Different choices will be better in different : situations, and it is well worth understanding that. It is not the : case that one method is unambiguously better than all the others in : all situations. : : To give an example: generally, domestic lighting circuits are not ring : circuits, even though the circuit serving sockets frequently is. Most of the domestic lighting circuits I've ever come across of based on looping in and out of ceiling (rose) fittings, thus one faulty fitting will trip all the lights on that circuit, hence why there will/should always be two lighting circuits (one usually for stair-well lighting) protected independently of each other BECAUSE the design failings of loop-in, loop-out circuits are recognised and accepted - one out, all out, so to speak!... You : might like to reflect on why that is. You may also like to reflect on : why it is not uncommon for kitchens to have a ring circuit separate : from the other circuits in a dwelling; and why immersion heaters are : usually put on their own spur. And to start things off, what do you : think the function of a plug-top fuse is? : Perhaps you should do the reflecting, WHY is it usual to install such circuits, perhaps if you actually thought through the actual issues then you would realise that you have made a very good argument against ring circuits! -- Regards, Jerry. |
#39
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
On Thu, 02 Sep 2010 10:33:19 +0100, Jerry wrote:
taking out all other devices connected to that circuit (which in a house : can be the entire power circuit. : : Pretty badly designed if it's the ONLY power circuit - our house has five : rings. : Only if you are being a pedantic fool and taking the meaning of the word "House" to me a multi floor dwelling rather than the more usual generic meaning of the word as a place were people live. Anyway, even if there was multiple ring circuits one faulty device will still take out all devices being powered from that circuit rather than just the one or two that would be on a radial circuit. No pedantry - you don't seem to understand at all. Never mind - it'll ne OK when you finish Key Stage 2. -- Use the BIG mirror service in the UK: http://www.mirrorservice.org *lightning protection* - a w_tom conductor |
#40
Posted to uk.d-i-y
|
|||
|
|||
Yikes, blown the suppy company neutral fuse ...
"Bob Eager" wrote in message ... : On Thu, 02 Sep 2010 10:33:19 +0100, Jerry wrote: : : taking out all other devices connected to that circuit (which : in a house : : can be the entire power circuit. : : : : Pretty badly designed if it's the ONLY power circuit - our house has : five : : rings. : : : : Only if you are being a pedantic fool and taking the meaning of the word : "House" to me a multi floor dwelling rather than the more usual generic : meaning of the word as a place were people live. Anyway, even if there : was multiple ring circuits one faulty device will still take out all : devices being powered from that circuit rather than just the one or two : that would be on a radial circuit. : : No pedantry - you don't seem to understand at all. Whhhoooossshhhh, unless you are makintg a very good case for radial circuits in small houses, flats and bungellows! : : Never mind - it'll ne OK when you finish Key Stage 2. Just because you are still at Key Stage 1, repeating, unquestioned, all your are being told parrot fashion, you think everyone else is... -- Regards, Jerry. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Cause of blown fuse. | Electronics Repair | |||
Have I blown a fuse, or what? | Home Repair | |||
Blown fuse | Home Repair | |||
Blown Fuse | Electronics Repair | |||
Blown Fuse: Need help identifying value | Electronics Repair |