Ground it to the home system.
I don't know the code details, but there is bare wire, known as "bonding wire", that code requires run without any splices from the box to the actual ground. The important thing is that the ground be redundantly robust. If there is a ground fault, a hot-to-ground leak in a powered appliance would raise the potential of the chassis above ground. Unlike neutral, which code says is to be bonded to ground at only one point, it is considered good engineering practice to "grid the ground", meaning multiple connections. I would run an unspliced length of bonding wire from your box to the generator. Additional ground connections, such as a cold-water ground would provide redundancy. "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i |
#2
|
|||
|
|||
"Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i What does a grounding rod cost??? |
#3
|
|||
|
|||
I bought some ground rod this spring, and I seem to recall that they were
about $8 for an 8' length. It's a simple steel rod, sharpened point and coated with copper. I was surprised how inexpensive it was. "Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 17:55:16 GMT, Doug Kanter wrote: "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i What does a grounding rod cost??? I am not sure, I think that about $40, I may be mistaken. Plus, I have to pound it in, it could bend, right now everything is frozen, etc etc etc. i |
#4
|
|||
|
|||
There are a couple of issues here.
Grounding the generator frame can be done via the Equipment Grounding Conductor in the cable you connect it with (to the building electrode). Certainly driving an additional rod when the ground thaws (~$10 plus about $5 worth of hardware) is a safer approach but it will still have to be bonded back to the house via the EGC. The other issue is grounding the neutral. If your transfer equipment switches the neutral you will need to ground the neutral in the generator. In most cases the transfer switch only transfers the hot legs so you leave the neutral isolated in the generator (as most portable generators are shipped). This grounds the neutral via your main bonding jumper in the service panel. |
#5
|
|||
|
|||
Depending on how the generator will be used, it may not require a connection
to a grounding electrode system. The NEC states that it you will have cord-and-plug connected equipment through the receptacles mounted on the gen, then it doesn't require grounding of the frame. Also if this is the case, then ensure that the manufacturer has bonded (connected) the neutral and ground within the generator, as it is a separately derived source. If the previous is not the case, then you must connect it to a grounding electrode system. If your are serving a premises with a grounding electrode system, it must be the same, meaning connect directly to it, or drive a rod and connect the rod to the existing grounding electrode system. It must be one grounding system, not isolated. There are lots of other things to consider like how you will transfer the loads to the gen, and such, but go carefully. "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i |
#6
|
|||
|
|||
Greg,
NEC-2002 250.34(C) that requires the neutral to ground bond only if the generator is a separately derived source. It is only a separately derived source if the neutral of the sources are switched. See 250.20(D) FPN No1 "Greg" wrote in message ... There are a couple of issues here. Grounding the generator frame can be done via the Equipment Grounding Conductor in the cable you connect it with (to the building electrode). Certainly driving an additional rod when the ground thaws (~$10 plus about $5 worth of hardware) is a safer approach but it will still have to be bonded back to the house via the EGC. The other issue is grounding the neutral. If your transfer equipment switches the neutral you will need to ground the neutral in the generator. In most cases the transfer switch only transfers the hot legs so you leave the neutral isolated in the generator (as most portable generators are shipped). This grounds the neutral via your main bonding jumper in the service panel. |
#7
|
|||
|
|||
I bought 5/8" copper-clad steel ground rods for $8.xx earlier in the
year, but for the past couple of months or more they have been $13.xx at the same store. The price of steel products has been skyrocketing, allegedly because of the construction boom in China. Perce On 12/27/04 01:10 pm Bughunter tossed the following ingredients into the ever-growing pot of cybersoup: I bought some ground rod this spring, and I seem to recall that they were about $8 for an 8' length. It's a simple steel rod, sharpened point and coated with copper. I was surprised how inexpensive it was. |
#8
|
|||
|
|||
Ron and I agree. I was just trying to avoid some of the NEC speak that confuses
people. The point is you only want one bonding point between the neutral and ground and if the transfer equipment doesn't switch neutral that will be the jumper in your service panel. (Separately derived source is NEC speak for a system where the neutral is switched too so it will have separate bonding jumpers that go with the source). All the frame grounding will be bonded, no matter what the transfer scheme. Adding another electrode only insures that the ground on the case is more closely referenced to the dirt under your feet when you are standing there. Depending on where you live "ground shift" is more or less of a problem. Here is the sandbox (Florida) I have seen 35 volt transients across 30-40 feet between buildings. |
#9
|
|||
|
|||
You are connecting this to your home wiring with a transfer switch that
switches only the hot connection. Is that correct? I used to have a link to a long article that went into extreme detail and all that, but have misplaced it. Oh well. Anyhow... If your generator ground is bonded to generator neutral, you MUST use a transfer switch that switches both hot and neutral, and you MUST ground the generator. If your generator is not bonded (and no normally available generators are bonded afaik, but your monster...) then you can switch only the hot and MUST NOT ground the generator. The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. |
#10
|
|||
|
|||
In article ,
"Robert Morein" wrote: Ground it to the home system. I don't know the code details, but there is bare wire, known as "bonding wire", that code requires run without any splices from the box to the actual ground. That's right you don't know the code details so shouldn't be offering advice. |
#11
|
|||
|
|||
I don't think that these rods are especially susceptible to corrosion.
I believe that the steel core is a standard feature. Yes, they look like solid copper but it's just a copper coating on the outside. One of the rods in my home corroded and had to be replaced, but it took nearly 30 years. I can handle $8 - $15 maintenance expense every 30 years or so. Life may be shorter if you have more acidic soil. You can drive into pretty hard ground with a good sized sledge hammer, but you are all done if you hit a hard rock. Lots of little firm taps works better than big swings, with less chance of bending the rod. Work slow until you get most of the rod into the ground, than you can take bigger swings. NEC code has a spec for the amount of resistance that you must shoot for, I think it was something like 8 ohms. I did not see any description of how you actually measure it. If you can't get it on the first rod, you have to drive in a second. But, even if you don't do any better with the second, you can stop at two. I guess they figure if you don't get it after driving two rods, you chances of doing better with several is slim. There are other possibilities, including buried mesh screens, and even attaching to rebar inside the concrete of the structure. Most of the other methods require a bit of pre-planning or more work to install. If you buy steel cored copper rods, also pick up some heavy duty clamps brass or copper clamps that are made for this purpose to attach your ground wire to the rod. Usually, you use #6 braided copper with no insulator. "Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 18:10:22 GMT, Bughunter wrote: I bought some ground rod this spring, and I seem to recall that they were about $8 for an 8' length. It's a simple steel rod, sharpened point and coated with copper. I was surprised how inexpensive it was. This is nice. Steel, I am sure, does not bend as easily either. Is there any issue with corrosion impeding conductivity? i "Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 17:55:16 GMT, Doug Kanter wrote: "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i What does a grounding rod cost??? I am not sure, I think that about $40, I may be mistaken. Plus, I have to pound it in, it could bend, right now everything is frozen, etc etc etc. i -- |
#12
|
|||
|
|||
On 27 Dec 2004 17:35:58 GMT, Ignoramus24153
wrote: I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i I believe like any sub-panel, the ground must run back to the main panel. Sorry that I can't remember what article this is in, maybe someone else can help with that. later, tom @ www.Stuff4Free.biz |
#13
|
|||
|
|||
On 27 Dec 2004 18:00:27 GMT, Ignoramus24153
wrote: On Mon, 27 Dec 2004 17:55:16 GMT, Doug Kanter wrote: "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i What does a grounding rod cost??? I am not sure, I think that about $40, I may be mistaken. Plus, I have to pound it in, it could bend, right now everything is frozen, etc etc etc. i I heard a great tip for this. Use your hammer drill but on 'hammer only'. Let the machine do the work. hth, tom @ www.FindMeShelter.com |
#14
|
|||
|
|||
On Mon, 27 Dec 2004 13:58:54 -0500, "Percival P. Cassidy"
wrote: I bought 5/8" copper-clad steel ground rods for $8.xx earlier in the year, but for the past couple of months or more they have been $13.xx at the same store. The price of steel products has been skyrocketing, allegedly because of the construction boom in China. Don't forget the higher steel taxes the Unions had imposed on all steel imports. Perce On 12/27/04 01:10 pm Bughunter tossed the following ingredients into the ever-growing pot of cybersoup: I bought some ground rod this spring, and I seem to recall that they were about $8 for an 8' length. It's a simple steel rod, sharpened point and coated with copper. I was surprised how inexpensive it was. |
#16
|
|||
|
|||
Our transfer switch switches both hots and the neutral.
Steve Spence Dir., Green Trust http://www.green-trust.org toller wrote: You are connecting this to your home wiring with a transfer switch that switches only the hot connection. Is that correct? I used to have a link to a long article that went into extreme detail and all that, but have misplaced it. Oh well. Anyhow... If your generator ground is bonded to generator neutral, you MUST use a transfer switch that switches both hot and neutral, and you MUST ground the generator. If your generator is not bonded (and no normally available generators are bonded afaik, but your monster...) then you can switch only the hot and MUST NOT ground the generator. The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. |
#17
|
|||
|
|||
"Steve Spence" wrote in message ... Our transfer switch switches both hots and the neutral. Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. You change from mains to generator by turning the mains breaker off and the generator breaker on. The neutral doesn't have a switch on it that I saw. |
#18
|
|||
|
|||
NEC code has a spec for the amount of resistance
that you must shoot for, I think it was something like 8 ohms 25 ohms If you can't get it on the first rod, you have to drive in a second. .... I guess they figure if you don't get it after driving two rods, you chances of doing better with several is slim. Exactly There are other possibilities, including buried mesh screens, 1/4" 1 foot square copper plate (2 square feet counting both sides) attaching to rebar inside the concrete of the structure. Probably the best grounding electrode AKA a Ufer ground (H.George Ufer invented it) brass or copper clamps Bronze. May look like brass or copper at a quick glance Usually, you use #6 braided copper Solid. |
#19
|
|||
|
|||
No, I don't touch the breaker box. I don't have a separate breaker for
the generator. I'm on inverter until I turn on the generator. the auto transfer switch then switches the loads from inverter to generator. There are two relays in the box, one switches the two hots, the other switches the neutral. when the gen is shut off, it switches the loads back to inverter. you can see a picture of it at http://www.green-trust.org/wiki/inde...olar_PV_System Steve Spence Dir., Green Trust http://www.green-trust.org toller wrote: "Steve Spence" wrote in message ... Our transfer switch switches both hots and the neutral. Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. You change from mains to generator by turning the mains breaker off and the generator breaker on. The neutral doesn't have a switch on it that I saw. |
#20
|
|||
|
|||
On Mon, 27 Dec 2004 22:57:03 GMT, "Bughunter" wrote:
You can drive into pretty hard ground with a good sized sledge hammer, but you are all done if you hit a hard rock. Lots of little firm taps works better than big swings, with less chance of bending the rod. Work slow until you get most of the rod into the ground, than you can take bigger swings. Even better http://www.kencove.com/ShopDetail.ph...r&recordID=TPD Fancy version above isn't required for only a few jobs... a piece of pipe with a heavy multi-layered cap is fine for pounding ground rods, at which point many electricians finish the job using a hack saw. :-) Wayne |
#21
|
|||
|
|||
Our transfer switch switches both hots and the neutral.
Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. Some "alternate energy" systems are installed as separately derived sources so they would use transfer equipment that switches the neutral. (perhaps as part of protection for transients when the system is not connected to the building ground) On the other hand most "generator" transfer switches for portable generators will not switch the neutral since the standard on portable generators is an isolated ground. If used as a stand alone generator on a job site there is no advantage to grounding the neutral, in fact it adds a hazard. Fixed in place, pad mount generators can go either way. They will have a grounding strap in the wiring compartment that you connect or disconnect, depending on how you are installing them. This whole deal can get pretty complicated to describe but the end objective is to only have one point where ground and neutral is connected, no matter how the system is switched. When I am inspecting a complex system I have to draw it out sometimes to sort out what is going on. |
#22
|
|||
|
|||
toller wrote:
"Steve Spence" wrote in message ... Our transfer switch switches both hots and the neutral. Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. You change from mains to generator by turning the mains breaker off and the generator breaker on. The neutral doesn't have a switch on it that I saw. Depends on the design of the transfer switch, I have one outside that is set up for three phase and has four poles on the switch body. Dave |
#23
|
|||
|
|||
Get a grounding rod and bang it into the earth, then, use the
appropriate connector to fasten 1/4" solid flexible copper to ; fasten the other end to the generators ground connector. Thats exactly what im about to do to my portable generator. |
#24
|
|||
|
|||
"Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 12:49:39 -0500, Robert Morein wrote: Ground it to the home system. I don't know the code details, but there is bare wire, known as "bonding wire", that code requires run without any splices from the box to the actual ground. The important thing is that the ground be redundantly robust. If there is a ground fault, a hot-to-ground leak in a powered appliance would raise the potential of the chassis above ground. That ground connection should be faultless and super safe and excessive, is a great point. Unlike neutral, which code says is to be bonded to ground at only one point, it is considered good engineering practice to "grid the ground", meaning multiple connections. i am not so sure, myself, I remember reading otherwise. That would be for the neutral. What they don't permit is a second isolated ground: See http://enginova.com/iso_ground.htm The reason redundant grounds are permitted is because of lightning. The only way to shield equipment in a building effectively is by grounding the structure itself, to make a pseudo-Faraday cage. A Faraday cage is simply a box with walls made of conducting material, so that everything within is at the same potential. In wood frame buildings, this is done by running ground wires all over the place, with multiple connections. That way, if there is something approaching a direct strike, every part of the building will remain at the same potential, and the activities within will be unaffected. See http://www.lightningsafety.com/nlsi_lhm/lpts.html They do not endorse multiple ground rods. However, that is not part of the NEC code. This page advocates redundant grounds: http://www.leminstruments.com/ground...ectrodes.shtml I would run an unspliced length of bonding wire from your box to the generator. Additional ground connections, such as a cold-water ground would provide redundancy. Thanks. i "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i -- |
#25
|
|||
|
|||
"Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 19:11:34 GMT, toller wrote: [snip] The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. I will check and post updates. I am not sure just what possible dangers to the generator could be created by unbonding. I recently spoke to a professional electrician who confided that although prohibited by the NEC, multiple hot-neutral bonds are quite common. He has seen the question raised in professional meetings, and the answers were always sketchy. It seems that some electronic equipment is affected by noise impressed onto ground, but the problem is overrated. |
#26
|
|||
|
|||
"Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 23:32:14 -0500, Robert Morein wrote: "Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 19:11:34 GMT, toller wrote: [snip] The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. I will check and post updates. I am not sure just what possible dangers to the generator could be created by unbonding. I recently spoke to a professional electrician who confided that although prohibited by the NEC, multiple hot-neutral bonds are quite common. He has seen the question raised in professional meetings, and the answers were always sketchy. Hot-neutral bonds????????????????? Any time turn something on you get a hot-neutral bond, though usually a high resistance one. Second hand information from a "professional electrician"... geez, when I see some of the work done in the past on my house by professional; my 23a water heater was run with #12 on a 30a breaker, a multiwire circuit was all on the same leg, etc. |
#27
|
|||
|
|||
toller wrote:
Hot-neutral bonds????????????????? Any time turn something on you get a hot-neutral bond, though usually a high resistance one. Second hand information from a "professional electrician"... geez, when I see some of the work done in the past on my house by professional; my 23a water heater was run with #12 on a 30a breaker, a multiwire circuit was all on the same leg, etc. A bond implies no -middle man- sort of load between two conductors. The gentleman meant to say ground to neutral connections. The guy doing your wiring should have been fired. A number twelve wire suitable for house wiring is usually rated for 20 amps. Heating loads have to use no more than 80 percent of the wire 'ampacity. So, his number 12 was good for only 16 amps in this situation. a 30 amp (#10) wire would have barely met the legal requirements (.8 X 30 = 24) -- "The day Microsoft makes something that doesn't suck is probably the day they start making vacuum cleaners." Ernst Jan Plugge |
#28
|
|||
|
|||
"Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 23:32:14 -0500, Robert Morein wrote: "Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 19:11:34 GMT, toller wrote: [snip] The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. I will check and post updates. I am not sure just what possible dangers to the generator could be created by unbonding. I recently spoke to a professional electrician who confided that although prohibited by the NEC, multiple hot-neutral bonds are quite common. He has seen the question raised in professional meetings, and the answers were always sketchy. Hot-neutral bonds????????????????? Oops!!!! |
#29
|
|||
|
|||
On Tue, 28 Dec 2004 05:32:06 GMT, m II
wrote: toller wrote: Hot-neutral bonds????????????????? Any time turn something on you get a hot-neutral bond, though usually a high resistance one. Second hand information from a "professional electrician"... geez, when I see some of the work done in the past on my house by professional; my 23a water heater was run with #12 on a 30a breaker, a multiwire circuit was all on the same leg, etc. A bond implies no -middle man- sort of load between two conductors. The gentleman meant to say ground to neutral connections. The guy doing your wiring should have been fired. A number twelve wire suitable for house wiring is usually rated for 20 amps. Heating loads have to use no more than 80 percent of the wire 'ampacity. So, his number 12 was good for only 16 amps in this situation. a 30 amp (#10) wire would have barely met the legal requirements (.8 X 30 = 24) I wonder if the water heater woudl be considered a 'continous load' like a houses heating, but it does make sense even without the derating, #12 shouldn't be used on a 30am breaker. I'm guessing it was a typo. later, tom @ www.FindMeShelter.com |
#30
|
|||
|
|||
Ignoramus24153 wrote:
On Mon, 27 Dec 2004 23:32:14 -0500, Robert Morein wrote: "Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 19:11:34 GMT, toller wrote: [snip] The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. I will check and post updates. I am not sure just what possible dangers to the generator could be created by unbonding. I recently spoke to a professional electrician who confided that although prohibited by the NEC, multiple hot-neutral bonds are quite common. He has seen the question raised in professional meetings, and the answers were always sketchy. Hot-neutral bonds????????????????? i I have done that many times, it's why I'm always buying new screwdrivers. Quite a show when it happens :-( Dave |
#31
|
|||
|
|||
I do not know exactly what the code says, but I do know what makes sense
from a safety perspective. The neutrals of all circuits should be connected to ground at ONLY one place - in your main service panel. There must be no grounding of neutrals in sub panels. Ranges etc. connected to sub panel circuts should use a 4 pin connector (hot, hot, neutral, ground). The ground wire from your main panel may be connected to multiple grounds and it's best if these are close together. Two grounding rods are frequently used for a lower resistance ground path and better reliability. Do not ever use a pipe as a ground. The water supply line may be PVC or may be changed to PVC at some time in the future and you would have no ground. Since a good ground is so important, use the gauge wire required by code or larger, protect it where required and never allow a splice in it. Use only the best quality U/L approved grounding clamps and be sure all contacting surfaces are clean and tight. All of this applies to your generator too. For best safety, if your generator is outside, it should be physically close to your system ground. If the code requires anything less, it should be changed. |
#32
|
|||
|
|||
I do not know exactly what the code says, but I do know what makes sense
from a safety perspective. The neutrals of all circuits should be connected to ground at ONLY one place - in your main service panel. There must be no grounding of neutrals in sub panels. Ranges etc. connected to sub panel circuts should use a 4 pin connector (hot, hot, neutral, ground). The ground wire from your main panel may be connected to multiple grounds and it's best if these are close together. Two grounding rods are frequently used for a lower resistance ground path and better reliability. Do not ever use a pipe as a ground. The water supply line may be PVC or may be changed to PVC at some time in the future and you would have no ground. Since a good ground is so important, use the gauge wire required by code or larger, protect it where required and never allow a splice in it. Use only the best quality U/L approved grounding clamps and be sure all contacting surfaces are clean and tight. All of this applies to your generator too. For best safety, if your generator is outside, it should be physically close to your system ground. If the code requires anything less, it should be changed. |
#33
|
|||
|
|||
wrote in message ... On Tue, 28 Dec 2004 05:32:06 GMT, m II wrote: toller wrote: Hot-neutral bonds????????????????? Any time turn something on you get a hot-neutral bond, though usually a high resistance one. Second hand information from a "professional electrician"... geez, when I see some of the work done in the past on my house by professional; my 23a water heater was run with #12 on a 30a breaker, a multiwire circuit was all on the same leg, etc. A bond implies no -middle man- sort of load between two conductors. The gentleman meant to say ground to neutral connections. The guy doing your wiring should have been fired. A number twelve wire suitable for house wiring is usually rated for 20 amps. Heating loads have to use no more than 80 percent of the wire 'ampacity. So, his number 12 was good for only 16 amps in this situation. a 30 amp (#10) wire would have barely met the legal requirements (.8 X 30 = 24) I wonder if the water heater woudl be considered a 'continous load' like a houses heating, but it does make sense even without the derating, #12 shouldn't be used on a 30am breaker. I'm guessing it was a typo. No typo, stupidity. They also put three 20a circuits on a 50a breaker. I replaced the #10 with #12, and put each 20a circuit on its own 20a breaker. |
#34
|
|||
|
|||
|
#35
|
|||
|
|||
In article ,
Ignoramus24153 wrote: I believe that the neutral is bonded to the frame. I also expect to have a transfer switch that will only switch hots. i plan on having separate neutral and ground wires going from home to the genset. If the previous is not the case, then you must connect it to a grounding electrode system. If your are serving a premises with a grounding electrode system, it must be the same, meaning connect directly to it, or drive a rod and connect the rod to the existing grounding electrode system. It must be one grounding system, not isolated. There are lots of other things to consider like how you will transfer the loads to the gen, and such, but go carefully. That's exactly why I want to explore opinions and come up with a solid plan. I do not want to have the generator grounded separately without need. i For my operations, I have all the gensets wired with the Neutral, Ground, and both Hot Legs comming out as sperate wires. They then connect to the Main Transfer Switch where both Hot Legs and Neutral, are switched. The Neutral and Ground are Bonded at the MAIN 240Vac Panel, which is where the Grounding Rod is also connected. At the 240/120Vac Transformer, the Neutral on the 240Vac winding goes back to the Neutral at the Main Panel, and one side of the 120Vac winding is brought to the Neutral Buss in the 120Vac SubPanel, which is also Bonded to the Ground Rod, to establish Neutral and ground for the secondary side of the Transformer. One Breaker in the 120Vac SubPanel feeds the Input to my 4024 Trace inverter, which then feeds the 120Vac Inverted SubPanel, where the Neutral and Ground are not bonded. This is because the Ground Connection on the Inverter is common to both Input and Output, therefor the bonding in the 120Vac SubPanel sets the Ground on both sides of the Inverter. The 120Vac Inverted SubPanel then feeds the Cabin Subpanel, as well as the ToolShed and GenShed Circuits. Bruce in alaska -- add a 2 before @ |
#36
|
|||
|
|||
I've seen this "IgnoramusXXXXX" stuff for years. What is the story?
|
#37
|
|||
|
|||
toller wrote:
No typo, stupidity. They also put three 20a circuits on a 50a breaker. I replaced the #10 with #12, and put each 20a circuit on its own 20a breaker. 12 with 10..g mike |
#38
|
|||
|
|||
"Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 23:32:14 -0500, Robert Morein wrote: "Ignoramus24153" wrote in message ... On Mon, 27 Dec 2004 19:11:34 GMT, toller wrote: [snip] The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. I will check and post updates. I am not sure just what possible dangers to the generator could be created by unbonding. I recently spoke to a professional electrician who confided that although prohibited by the NEC, multiple hot-neutral bonds are quite common. He has seen the question raised in professional meetings, and the answers were always sketchy. Hot-neutral bonds????????????????? I am sure that he is referring to multiple bonding points to the neutral. Your supposed to do it once at the service. The neutral is a "grounded current carrying conductor" Having it grounded/bonded in more than one place just increases the probability of something going wrong. Does it happen you bet, is it correct. NO If you ground to your service, best in my opinion. Use the same size ground wire as your service. You are creating an "supplemental ground" for the service. Any ground conductor smaller than the ground for the service could create a weak link in the grounding. Bonding to the metallic piping systems is required. This may not be a problem if you are able to come off of the ground bar in the service. Assuming that the metallic piping systems are bonded currently. Personally I like and use only switched neutral transfer panels. Solid neutral switches are available and a little cheaper. I have had to many problems with sensitive electronics over the years. If my customer insists then they find someone else to do the job. Almost all that have in the past have come "crawling back" for me to fix it AFTER the damage was done. They are very careful not to discuss or complain about price. Having two sources of power is not rocket science. It is problematic when incorrectly installed. If you land on a solid neutral block, you will have a the possibility of current traveling to your generator while it is off. Switching the neutral with the phases assures that the generator will be completely isolated when not being used. |
#39
|
|||
|
|||
Ignoramus24153 wrote:
I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? This may help things.. http://www.cat.com/cda/components/se...language Id=7 -- "Build a man a fire, and he'll be warm for a day. Set a man on fire, and he'll be warm for the rest of his life." Terry Pratchett |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Replacement engine for Colemate Generator | Metalworking | |||
Generator FAQ | Metalworking | |||
Generator Grounding | UK diy | |||
Grounding Rod *and* Rebar for service grounds? | Home Repair |