Grounding a generator
Ground it to the home system.
I don't know the code details, but there is bare wire, known as "bonding wire", that code requires run without any splices from the box to the actual ground. The important thing is that the ground be redundantly robust. If there is a ground fault, a hot-to-ground leak in a powered appliance would raise the potential of the chassis above ground. Unlike neutral, which code says is to be bonded to ground at only one point, it is considered good engineering practice to "grid the ground", meaning multiple connections. I would run an unspliced length of bonding wire from your box to the generator. Additional ground connections, such as a cold-water ground would provide redundancy. "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i |
#2
|
|||
|
|||
"Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i What does a grounding rod cost??? |
#3
|
|||
|
|||
There are a couple of issues here.
Grounding the generator frame can be done via the Equipment Grounding Conductor in the cable you connect it with (to the building electrode). Certainly driving an additional rod when the ground thaws (~$10 plus about $5 worth of hardware) is a safer approach but it will still have to be bonded back to the house via the EGC. The other issue is grounding the neutral. If your transfer equipment switches the neutral you will need to ground the neutral in the generator. In most cases the transfer switch only transfers the hot legs so you leave the neutral isolated in the generator (as most portable generators are shipped). This grounds the neutral via your main bonding jumper in the service panel. |
#4
|
|||
|
|||
Greg,
NEC-2002 250.34(C) that requires the neutral to ground bond only if the generator is a separately derived source. It is only a separately derived source if the neutral of the sources are switched. See 250.20(D) FPN No1 "Greg" wrote in message ... There are a couple of issues here. Grounding the generator frame can be done via the Equipment Grounding Conductor in the cable you connect it with (to the building electrode). Certainly driving an additional rod when the ground thaws (~$10 plus about $5 worth of hardware) is a safer approach but it will still have to be bonded back to the house via the EGC. The other issue is grounding the neutral. If your transfer equipment switches the neutral you will need to ground the neutral in the generator. In most cases the transfer switch only transfers the hot legs so you leave the neutral isolated in the generator (as most portable generators are shipped). This grounds the neutral via your main bonding jumper in the service panel. |
#5
|
|||
|
|||
Depending on how the generator will be used, it may not require a connection
to a grounding electrode system. The NEC states that it you will have cord-and-plug connected equipment through the receptacles mounted on the gen, then it doesn't require grounding of the frame. Also if this is the case, then ensure that the manufacturer has bonded (connected) the neutral and ground within the generator, as it is a separately derived source. If the previous is not the case, then you must connect it to a grounding electrode system. If your are serving a premises with a grounding electrode system, it must be the same, meaning connect directly to it, or drive a rod and connect the rod to the existing grounding electrode system. It must be one grounding system, not isolated. There are lots of other things to consider like how you will transfer the loads to the gen, and such, but go carefully. "Ignoramus24153" wrote in message ... I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i |
#6
|
|||
|
|||
Ron and I agree. I was just trying to avoid some of the NEC speak that confuses
people. The point is you only want one bonding point between the neutral and ground and if the transfer equipment doesn't switch neutral that will be the jumper in your service panel. (Separately derived source is NEC speak for a system where the neutral is switched too so it will have separate bonding jumpers that go with the source). All the frame grounding will be bonded, no matter what the transfer scheme. Adding another electrode only insures that the ground on the case is more closely referenced to the dirt under your feet when you are standing there. Depending on where you live "ground shift" is more or less of a problem. Here is the sandbox (Florida) I have seen 35 volt transients across 30-40 feet between buildings. |
#7
|
|||
|
|||
You are connecting this to your home wiring with a transfer switch that
switches only the hot connection. Is that correct? I used to have a link to a long article that went into extreme detail and all that, but have misplaced it. Oh well. Anyhow... If your generator ground is bonded to generator neutral, you MUST use a transfer switch that switches both hot and neutral, and you MUST ground the generator. If your generator is not bonded (and no normally available generators are bonded afaik, but your monster...) then you can switch only the hot and MUST NOT ground the generator. The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. |
#8
|
|||
|
|||
Our transfer switch switches both hots and the neutral.
Steve Spence Dir., Green Trust http://www.green-trust.org toller wrote: You are connecting this to your home wiring with a transfer switch that switches only the hot connection. Is that correct? I used to have a link to a long article that went into extreme detail and all that, but have misplaced it. Oh well. Anyhow... If your generator ground is bonded to generator neutral, you MUST use a transfer switch that switches both hot and neutral, and you MUST ground the generator. If your generator is not bonded (and no normally available generators are bonded afaik, but your monster...) then you can switch only the hot and MUST NOT ground the generator. The article went on for pages about ground loops or somesuch thing (the neutral being grounded in two different places). So, my suggestion is that you find out if you can unbond your generator, since you are unlikely to find a transfer switch to switch both hot and neutral. There is no need to ground the generator separately, since it's ground is not connected to anything except the house ground. |
#9
|
|||
|
|||
"Steve Spence" wrote in message ... Our transfer switch switches both hots and the neutral. Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. You change from mains to generator by turning the mains breaker off and the generator breaker on. The neutral doesn't have a switch on it that I saw. |
#10
|
|||
|
|||
No, I don't touch the breaker box. I don't have a separate breaker for
the generator. I'm on inverter until I turn on the generator. the auto transfer switch then switches the loads from inverter to generator. There are two relays in the box, one switches the two hots, the other switches the neutral. when the gen is shut off, it switches the loads back to inverter. you can see a picture of it at http://www.green-trust.org/wiki/inde...olar_PV_System Steve Spence Dir., Green Trust http://www.green-trust.org toller wrote: "Steve Spence" wrote in message ... Our transfer switch switches both hots and the neutral. Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. You change from mains to generator by turning the mains breaker off and the generator breaker on. The neutral doesn't have a switch on it that I saw. |
#11
|
|||
|
|||
Our transfer switch switches both hots and the neutral.
Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. Some "alternate energy" systems are installed as separately derived sources so they would use transfer equipment that switches the neutral. (perhaps as part of protection for transients when the system is not connected to the building ground) On the other hand most "generator" transfer switches for portable generators will not switch the neutral since the standard on portable generators is an isolated ground. If used as a stand alone generator on a job site there is no advantage to grounding the neutral, in fact it adds a hazard. Fixed in place, pad mount generators can go either way. They will have a grounding strap in the wiring compartment that you connect or disconnect, depending on how you are installing them. This whole deal can get pretty complicated to describe but the end objective is to only have one point where ground and neutral is connected, no matter how the system is switched. When I am inspecting a complex system I have to draw it out sometimes to sort out what is going on. |
#12
|
|||
|
|||
toller wrote:
"Steve Spence" wrote in message ... Our transfer switch switches both hots and the neutral. Steve Spence Dir., Green Trust http://www.green-trust.org Actually I don't think it does. You change from mains to generator by turning the mains breaker off and the generator breaker on. The neutral doesn't have a switch on it that I saw. Depends on the design of the transfer switch, I have one outside that is set up for three phase and has four poles on the switch body. Dave |
#13
|
|||
|
|||
In article ,
"Robert Morein" wrote: Ground it to the home system. I don't know the code details, but there is bare wire, known as "bonding wire", that code requires run without any splices from the box to the actual ground. That's right you don't know the code details so shouldn't be offering advice. |
#14
|
|||
|
|||
On 27 Dec 2004 17:35:58 GMT, Ignoramus24153
wrote: I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? thanks i I believe like any sub-panel, the ground must run back to the main panel. Sorry that I can't remember what article this is in, maybe someone else can help with that. later, tom @ www.Stuff4Free.biz |
#16
|
|||
|
|||
Get a grounding rod and bang it into the earth, then, use the
appropriate connector to fasten 1/4" solid flexible copper to ; fasten the other end to the generators ground connector. Thats exactly what im about to do to my portable generator. |
#17
|
|||
|
|||
Ignoramus24153 wrote:
I am aware that "all generators must be grounded". In the instance of a standby portable generator like this http://igor.chudov.com/tmp/onan/Diesel/ how would I ground it? I have two options: 1. Ground it to a new grounding rod (expensive and involves actual work). 2. Ground it to the home grounding system, such as copper pipes in the utility room, or even better next to the existing home ground connection. Which option here is more legal and more safe? This may help things.. http://www.cat.com/cda/components/se...language Id=7 -- "Build a man a fire, and he'll be warm for a day. Set a man on fire, and he'll be warm for the rest of his life." Terry Pratchett |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Replacement engine for Colemate Generator | Metalworking | |||
Generator FAQ | Metalworking | |||
Generator Grounding | UK diy | |||
Grounding Rod *and* Rebar for service grounds? | Home Repair |