Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
I am a little baffled. I have flood lights that used to work. They stopped
working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? Any suggestions would be great! |
#2
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Meat Plow wrote:
On Tue, 29 May 2007 12:06:52 -0400, CooSer wrote: I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? Any suggestions would be great! Find someone who can troubleshoot it from the source. I don't think you know enough (not an insult) about it. I'bet you are seeing a "phantom" voltage being capacitively coupled past an open circuit. Try this: Screw in just ONE bulb and see if you still find "power" there with your voltage detector. Betcha dont anymore! Then, as a previous poster suggested, find a way to learn more about what you need to know to diagnose and fix the problem, it sounds like it'd be pretty hard to bring you far enough up the learning curve via a newsgroup. Good Luck, Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) The speed of light is 1.8*10^12 furlongs per fortnight. |
#3
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Use something like a pigtail tester. Touch one lead to the interior shell of
the lamp socket, and the other to the tongue at the bottom of the socket. With the switch on you should get a light and not with the switch off. It is possible that the neutral conductor is being broken through the switch instead of the hot leg, and it's also possible that the switch is bad "CooSer" wrote in message ... I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? Any suggestions would be great! |
#4
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"CooSer" wrote in message ... I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. A voltage tester is most often a high-impedance device. What that means, in simple terms, is that it does not load the circuit. You have a circuit that fails under load. Somewhere, there is a bad connection. |
#5
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On Tue, 29 May 2007 16:49:08 -0400, "RBM" rbm2(remove
wrote: it's also possible that the switch is bad Or like me flipping the wrong switch off and on :-)) -- Oren ...through the use of electrical or duct tape, achieve the configuration in the photo.. |
#6
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On May 29, 11:06 am, "CooSer" wrote:
I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? What type is your tester? Is it an inexpensive volt-meter or a neon- bulb or similar? If the former w/ a needle indicator it's quite possible as Jeff says the voltage is phantom. If it is a indicator light type, and the light is being lit, then the voltage is real and the problem is twofold... If you don't find the problem first, post the answer to the question and I'll not start a tome on what else to look for... Although I will ask -- is there more than one location from which to turn the lights on/off from? It's possible the other switch is the problem of voltage. Also, if there is real (not phantom) voltage, and the light doesn't light, then the problem almost certainly has to be in the base--either dirt/corrosion or perhaps the base tab has become flattened to where the bottom of the bulb isn't making contact. But, I'd say first guess of reading a impressed voltage is probably the most likely culprit... |
#7
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"CooSer" wrote in message ... I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? Any suggestions would be great! BTDT, multiple times in various houses for me and relatives. IMHO, most likely cause is that the fixture has crapped out, being out in the weather year round and all. Postive test for that, is to remove fixture, and hang a 3-dollar pigtail socket with a bulb from the wires. The 3 bucks is well invested- even if you only use it every couple years, a pigtail is a handy thing to have around. Outdoor fixtures are cheap. Made cheaply and far away, but cheap. aem sends... |
#8
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Charles" wrote in message . .. "CooSer" wrote in message ... I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. A voltage tester is most often a high-impedance device. What that means, in simple terms, is that it does not load the circuit. You have a circuit that fails under load. Somewhere, there is a bad connection. Phantom? For heavens sake, let's get real here. There is no such thing as a phantom voltage ... there is a voltage that shows up with no load and drops to near zero with a load ... bad connection! |
#9
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
Phantom? For heavens sake, let's get real here. There is no such thing as a phantom voltage ... there is a voltage that shows up with no load and drops to near zero with a load ... bad connection! NO. That is not what he wrote. "In fact, there is power in the sockets whether the switch is on or off." He is using a $6 pseudo-test instrument that is completely unreliable, which can easily pick up inductive transient signals and give a false positive. To CooSer: Get yourself a real mult-meter to test the actual wiring before the fixture. Don't use inductive probes or gimmicky light bulb testers. Use a real voltmeter to test the *wiring* first, then you can work on diagnosing a bad fixture. |
#10
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: Phantom? For heavens sake, let's get real here. There is no such thing as a phantom voltage ... there is a voltage that shows up with no load and drops to near zero with a load ... bad connection! NO. That is not what he wrote. Here is brief tutorial: 1/ Voltage is constant in parallel circuits. 2./ Voltage is distributed in series circuits. 3/ A resistance or impedance will drop some voltage, proportional to current flow. HE/SHE might have a circuit with a bad connection ... good enough to register normal when no load is connected and measured with a high-impedance tester ... but not able to supply a real load. |
#11
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
Here is brief tutorial: 1/ Voltage is constant in parallel circuits. 2./ Voltage is distributed in series circuits. 3/ A resistance or impedance will drop some voltage, proportional to current flow. No ****? I guess nothing changed since I took basic DC/AC circuits in college 20 years ago. HE/SHE might have a circuit with a bad connection ... good enough to register normal when no load is connected and m He/She *might* have an elephant's trunk stuck up the anal orifice too. Nobody knows until we can reliably test it though, eh? So instead of spouting *what if's*, let's direct our friend to actually test the circuit before proclaiming ' bad connection', which is vague in itself and offers no solution to the OP's problem. It very well be a loose or oxidized connection, but you are not following the flow of troubleshooting, nor given any advice on how to find or correct this "phantom" bad connection. |
#12
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On Tue, 29 May 2007 12:06:52 -0400, "CooSer"
wrote: I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? Any suggestions would be great! Any lamp should work in the fixture. Try using the new lamp in another fixture or use a known working bulb the floodlight. You should not be reading voltage with the switch off. Try testing with a reliable tester |
#13
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On 29 May 2007 14:47:45 -0700, dpb wrote:
On May 29, 11:06 am, "CooSer" wrote: I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? What type is your tester? Is it an inexpensive volt-meter or a neon- bulb or similar? If the former w/ a needle indicator it's quite possible as Jeff says the voltage is phantom. If it is a indicator light type, and the light is being lit, then the voltage is real and the problem is twofold... If you don't find the problem first, post the answer to the question and I'll not start a tome on what else to look for... Although I will ask -- is there more than one location from which to turn the lights on/off from? It's possible the other switch is the problem of voltage. Also, if there is real (not phantom) voltage, and the light doesn't light, then the problem almost certainly has to be in the base--either dirt/corrosion or perhaps the base tab has become flattened to where the bottom of the bulb isn't making contact. Any voltage you can measure is a real one ("phantom" doesn't make sense here, meters measure real voltages only). What's different is the source impedance (the effective resistance of the source, which determines how much the voltage drops with load). When dealing with power, you want a LOW source impedance, so the load causes very little voltage drop. With a very high source impedance, the load causes the voltage to drop too low to light the bulb. But, I'd say first guess of reading a impressed voltage is probably the most likely culprit... Yes. -- Mark Lloyd http://notstupid.laughingsquid.com "God was invented by man for a reason, that reason is no longer applicable." |
#14
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On Tue, 29 May 2007 19:14:11 -0400, Terry
wrote: On Tue, 29 May 2007 12:06:52 -0400, "CooSer" wrote: I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? Any suggestions would be great! Any lamp should work in the fixture. Try using the new lamp in another fixture or use a known working bulb the floodlight. You should not be reading voltage with the switch off. Try testing with a reliable tester A disconnected wire (such as this one, with the switch off and no bulb in the socket) running close to a wire carrying AC current will form a transformer and you'll get some voltage. Circuit impedance will be high, and any significant load will drop it to near zero. -- Mark Lloyd http://notstupid.laughingsquid.com "God was invented by man for a reason, that reason is no longer applicable." |
#15
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On May 30, 11:01 am, Mark Lloyd wrote:
On 29 May 2007 14:47:45 -0700, dpb wrote: .... Any voltage you can measure is a real one ("phantom" doesn't make sense here, ... "Phantom" in the sense following -- which you obviously knew and understood but just wanted to be a ... But, I'd say first guess of reading a impressed voltage is probably the most likely culprit... -- |
#16
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Mark Lloyd wrote:
On 29 May 2007 14:47:45 -0700, dpb wrote: On May 29, 11:06 am, "CooSer" wrote: I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? What type is your tester? Is it an inexpensive volt-meter or a neon- bulb or similar? If the former w/ a needle indicator it's quite possible as Jeff says the voltage is phantom. If it is a indicator light type, and the light is being lit, then the voltage is real and the problem is twofold... If you don't find the problem first, post the answer to the question and I'll not start a tome on what else to look for... Although I will ask -- is there more than one location from which to turn the lights on/off from? It's possible the other switch is the problem of voltage. Also, if there is real (not phantom) voltage, and the light doesn't light, then the problem almost certainly has to be in the base--either dirt/corrosion or perhaps the base tab has become flattened to where the bottom of the bulb isn't making contact. Any voltage you can measure is a real one ("phantom" doesn't make sense here, meters measure real voltages only). What's different is the source impedance (the effective resistance of the source, which determines how much the voltage drops with load). When dealing with power, you want a LOW source impedance, so the load causes very little voltage drop. With a very high source impedance, the load causes the voltage to drop too low to light the bulb. But, I'd say first guess of reading a impressed voltage is probably the most likely culprit... Yes. Don't quibble with just me Mark. NEMA recognizes "phantom" as a term too: G http://www.nema.org/stds/eng-bulleti...ulletin-88.pdf Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) The speed of light is 1.8*10^12 furlongs per fortnight. |
#17
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On 30 May 2007 10:41:24 -0700, dpb wrote:
On May 30, 11:01 am, Mark Lloyd wrote: On 29 May 2007 14:47:45 -0700, dpb wrote: ... Any voltage you can measure is a real one ("phantom" doesn't make sense here, ... "Phantom" in the sense following -- At this point, you realized you had nothing to say, and felt an uncontrollable need to say something nasty anyway. which you obviously knew and understood but just wanted to be a ... Sometimes I wish there was a "maturity test" for usenet posters... But, I'd say first guess of reading a impressed voltage is probably the most likely culprit... |
#18
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On Wed, 30 May 2007 16:00:19 -0500, Sam E
wrote: Sometimes I wish there was a "maturity test" for usenet posters... (How do WE fit in? Exclude, yourself!) Can I post as a graduate of 9th grade? -- Oren ...through the use of electrical or duct tape, achieve the configuration in the photo.. |
#19
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Get yourself a real mult-meter to test the actual wiring before the fixture. Don't use inductive probes or gimmicky light bulb testers. Use a real voltmeter to test the *wiring* first, then you can work on diagnosing a bad fixture. What will that accomplish? A real voltmeter has a very high impedance and will give the same result. |
#20
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: Here is brief tutorial: 1/ Voltage is constant in parallel circuits. 2./ Voltage is distributed in series circuits. 3/ A resistance or impedance will drop some voltage, proportional to current flow. No ****? I guess nothing changed since I took basic DC/AC circuits in college 20 years ago. Wow! College. Ain't you sumpin. HE/SHE might have a circuit with a bad connection ... good enough to register normal when no load is connected and m He/She *might* have an elephant's trunk stuck up the anal orifice too. We certainly know that YOU have issues like that. So instead of spouting *what if's*, let's direct our friend to actually test the circuit before proclaiming ' bad connection', which is vague in itself and offers no solution to the OP's problem. Your directions were detailed and impecable. It very well be a loose or oxidized connection, but you are not following the flow of troubleshooting, nor given any advice on how to find or correct this "phantom" bad connection. Oh; and you of course have given sage advice. |
#21
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On May 30, 4:00 pm, Sam E wrote:
On 30 May 2007 10:41:24 -0700, dpb wrote: On May 30, 11:01 am, Mark Lloyd wrote: On 29 May 2007 14:47:45 -0700, dpb wrote: ... .... At this point, you realized you had nothing to say, and felt an uncontrollable need to say something nasty anyway. .... I'd have said nothing further had previous poster not felt obligated to make cheapshot remark initially...at that point I indeed, had something to say which was I didn't appreciate it nor your even cheaper "pile-on"... If you want to correct the rudeness, start w/ the prior poster (or yourself), not me... |
#22
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Don't quibble with just me Mark. NEMA recognizes "phantom" as a term too: G Jeff, in my humble opinion the term "phantom voltage" is not applicable in this case. NEMA and others use it to refer to a capacitively induced voltage into an open circuit and measured by a high-impedance meter. In this case, the voltage is not a phantom but is a real voltage in a circuit with high resistance (due to a bad connection). |
#23
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
No ****? I guess nothing changed since I took basic DC/AC circuits in college 20 years ago. Wow! College. Ain't you sumpin. We learned how to spell fancy words like "something" too! There was also a course that explained "ain't" is not a word. Here is some light reading that I'm sure even you will understand. http://dictionary.reference.com/browse/aint (move your mouse arrow over the underlined text and click the left button, Corky) "—Usage note As a substitute for am not, is not, and are not in declarative sentences, ain't is more common in uneducated speech than in educated" HE/SHE might have a circuit with a bad connection ... good enough to register normal when no load is connected and m He/She *might* have an elephant's trunk stuck up the anal orifice too. We certainly know that YOU have issues like that. Not lately, I have learned to be careful around pachyderms. Oh, sorry.. here you go - http://dictionary.reference.com/browse/pachyderms I saw you on youtube, dude: http://www.youtube.com/watch?v=Bi9gR_uHFG0 So instead of spouting *what if's*, let's direct our friend to actually test the circuit before proclaiming ' bad connection', which is vague in itself and offers no solution to the OP's problem. Your directions were detailed and impecable. Yes they were, thanks. It very well be a loose or oxidized connection, but you are not following the flow of troubleshooting, nor given any advice on how to find or correct this "phantom" bad connection. Oh; and you of course have given sage advice. Thanks again. |
#24
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
"Clancy Wiggum" wrote in message .. . Get yourself a real mult-meter to test the actual wiring before the fixture. Don't use inductive probes or gimmicky light bulb testers. Use a real voltmeter to test the *wiring* first, then you can work on diagnosing a bad fixture. What will that accomplish? A real voltmeter has a very high impedance and will give the same result. No, Corky. A voltmeter will show the gentleman exactly what voltage potential exists at the wiring *before* the fixture. Those stupid $6 LED testers will light up with the smallest amount of induced voltage, telling him nothing. |
#25
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On 30 May 2007 16:59:14 -0700, dpb wrote:
On May 30, 4:00 pm, Sam E wrote: On 30 May 2007 10:41:24 -0700, dpb wrote: On May 30, 11:01 am, Mark Lloyd wrote: On 29 May 2007 14:47:45 -0700, dpb wrote: ... ... At this point, you realized you had nothing to say, and felt an uncontrollable need to say something nasty anyway. ... I'd have said nothing further had previous poster not felt obligated to make cheapshot remark initially...at that point I indeed, had something to say which was I didn't appreciate it nor your even cheaper "pile-on"... If you want to correct the rudeness, start w/ the prior poster (or yourself), not me... What I put in my post was not intended as rudeness, but as honest observation. The fact that you interpreted it that way does mean something. The prior post shows no evidence of rudeness whatsoever. |
#26
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
Don't quibble with just me Mark. NEMA recognizes "phantom" as a term too: G Jeff, in my humble opinion the term "phantom voltage" is not applicable in this case. NEMA and others use it to refer to a capacitively induced voltage into an open circuit and measured by a high-impedance meter. In this case, the voltage is not a phantom but is a real voltage in a circuit with high resistance (due to a bad connection). Yet you still have not told the OP to remove the fixture and test the actual voltage on the feed conductors. Tell me, Corky, how is this man going to find your "bad connection" without removing the fixture and testing the source first, eh? Seems to me that is the very first step - so he knows whether to work on the fixture or go back to the switch. |
#27
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On May 30, 8:03 pm, Sam E wrote:
On 30 May 2007 16:59:14 -0700, dpb wrote: On May 30, 4:00 pm, Sam E wrote: On 30 May 2007 10:41:24 -0700, dpb wrote: On May 30, 11:01 am, Mark Lloyd wrote: On 29 May 2007 14:47:45 -0700, dpb wrote: ... ... At this point, you realized you had nothing to say, and felt an uncontrollable need to say something nasty anyway. ... I'd have said nothing further had previous poster not felt obligated to make cheapshot remark initially...at that point I indeed, had something to say which was I didn't appreciate it nor your even cheaper "pile-on"... If you want to correct the rudeness, start w/ the prior poster (or yourself), not me... What I put in my post was not intended as rudeness, but as honest observation. The fact that you interpreted it that way does mean something. The prior post shows no evidence of rudeness whatsoever. Whatever... |
#28
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: No ****? I guess nothing changed since I took basic DC/AC circuits in college 20 years ago. Wow! College. Ain't you sumpin. We learned how to spell fancy words like "something" too! There was also a course that explained "ain't" is not a word. Here is some light reading that I'm sure even you will understand. Subtle sarcasm just zooms right over your shrunken head. |
#29
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: "Clancy Wiggum" wrote in message . .. Get yourself a real mult-meter to test the actual wiring before the fixture. Don't use inductive probes or gimmicky light bulb testers. Use a real voltmeter to test the *wiring* first, then you can work on diagnosing a bad fixture. What will that accomplish? A real voltmeter has a very high impedance and will give the same result. No, Corky. A voltmeter will show the gentleman exactly what voltage potential exists at the wiring *before* the fixture. Those stupid $6 LED testers will light up with the smallest amount of induced voltage, telling him nothing. Yes, Porky. You obviously do not understand series circuits, Kirchhoff's Laws, and instrument impedance. Just keep digging your hole deeper. |
#30
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: Don't quibble with just me Mark. NEMA recognizes "phantom" as a term too: G Jeff, in my humble opinion the term "phantom voltage" is not applicable in this case. NEMA and others use it to refer to a capacitively induced voltage into an open circuit and measured by a high-impedance meter. In this case, the voltage is not a phantom but is a real voltage in a circuit with high resistance (due to a bad connection). Yet you still have not told the OP to remove the fixture and test the actual voltage on the feed conductors. Tell me, Corky, how is this man going to find your "bad connection" without removing the fixture and testing the source first, eh? Seems to me that is the very first step - so he knows whether to work on the fixture or go back to the switch. Look, Porky. If you have useful input for the OP, tend to it. Don't take cheap shots at others trying to help. |
#31
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
Tell me, Corky, how is this man going to find your "bad connection" without removing the fixture and testing the source first, eh? Seems to me that is the very first step - so he knows whether to work on the fixture or go back to the switch. Look, Porky. If you have useful input for the OP, tend to it. Don't take cheap shots at others trying to help. Corky, what is wrong with my advice? |
#32
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
No, Corky. A voltmeter will show the gentleman exactly what voltage potential exists at the wiring *before* the fixture. Those stupid $6 LED testers will light up with the smallest amount of induced voltage, telling him nothing. Yes, Porky. You obviously do not understand series circuits, Kirchhoff's Laws, and instrument impedance. Just keep digging your hole deeper. Corky, I am familiar with all of those concepts. Please tell me why you refuse to admit that a faulty "test instrument" as the OP described, and used, is proof of your argument that a transient voltage is NOT to blame, and is in fact as you claim a "bad connection". |
#33
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
We learned how to spell fancy words like "something" too! There was also a course that explained "ain't" is not a word. Here is some light reading that I'm sure even you will understand. Subtle sarcasm just zooms right over your shrunken head. Nah.. I just like using you as a chew toy. |
#34
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Mark Lloyd wrote:
A disconnected wire (such as this one, with the switch off and no bulb in the socket) running close to a wire carrying AC current will form a transformer and you'll get some voltage. Circuit impedance will be high, and any significant load will drop it to near zero. Yup. And if the OP is using an inductive "test instrument" he will read a false positive, since he is testing with no-load (bulb unscrewed). |
#35
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: Tell me, Corky, how is this man going to find your "bad connection" without removing the fixture and testing the source first, eh? Seems to me that is the very first step - so he knows whether to work on the fixture or go back to the switch. Look, Porky. If you have useful input for the OP, tend to it. Don't take cheap shots at others trying to help. Corky, what is wrong with my advice? Give some, and I'll let you know. So far, you have offered only criticism. Respond to the OP with how he/she should proceed and then we can take pot shots at you. Or, if you happen to offer sage advice ... then HURRAHS to you Porky. |
#36
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
Corky, what is wrong with my advice? Give some, and I'll let you know. So far, you have offered only criticism. Respond to the OP with how he/she should proceed and then we can take pot shots at you. Or, if you happen to offer sage advice ... then HURRAHS to you Porky. I did, Corky. I asked him to test the input wiring, without the possibility of "phantom" (inductive) voltage, which a voltmeter will provide - despite your claim to the contrary that a voltmeter is a "high impendence device". And can not reliably differentiate, which is bull****. What the hell is your problem with that? You are jumping to conclusions without any measurable data. I asked the OP to provide measurable data, you told him he had a "bad connection" without further steps to diagnose, nor a fix. This was my advice to start the troubleshooting: Message-ID: "Get yourself a real multi-meter to test the actual wiring before the fixture. Don't use inductive probes or gimmicky light bulb testers. Use a real voltmeter to test the *wiring* first, then you can work on diagnosing a bad fixture." |
#37
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: Corky, what is wrong with my advice? Give some, and I'll let you know. So far, you have offered only criticism. Respond to the OP with how he/she should proceed and then we can take pot shots at you. Or, if you happen to offer sage advice ... then HURRAHS to you Porky. I did, Corky. I asked him to test the input wiring, without the possibility of "phantom" (inductive) voltage, which a voltmeter will provide - despite your claim to the contrary that a voltmeter is a "high impendence device". And can not reliably differentiate, which is bull****. A phantom voltage is defined by NEMA as being caused by capacitive coupling among conductors. Inducitve coupling is different (you continue to show your ignorance on these very basic concepts and dig yourself in deeper every time that you post). No big deal here, as neither capacitive coupling or inductive coupling is applicable to this particular situation. This situation is so simple, in terms of troubleshooting, that it merits little discussion. You have promoted the discussion by making snide remarks and very inappropriate comments. Bull**** is in the eye of the beholder and you reek of it, from my viewpoint. A bad connection is a bad connection. Anybody with an ounce of common sense knows how to proceed. Outdoor, low-voltage lighting systems all have, or eventually have, bad connections. Pull up the wires and wiggle the connections and the lights go on and off. What the hell is your problem with that? You are jumping to conclusions without any measurable data. I asked the OP to provide measurable data, you told him he had a "bad connection" without further steps to diagnose, nor a fix. My problem is with twits like you who have probably never fixed a broken flashlight. You feed your ego here via distasteful remarks about things up other's arses, which says a lot about you. |
#38
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
Charles wrote:
horse **** snipped My problem is with twits like you who have probably never fixed a broken flashlight. You feed your ego here via distasteful remarks about things up other's arses, which says a lot about you. HA! Hey Corky, there is only one last thing to say before you plonk me. -- **** YOU -- You have no skills, offer no solutions, have only vitriol to spew, and your breath most likely stinks like crack-whore. I hope you get infected with a really bad case of chlamydia and your penis falls off! Have a nice day. |
#39
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
"Clancy Wiggum" wrote in message ... Charles wrote: horse **** snipped My problem is with twits like you who have probably never fixed a broken flashlight. You feed your ego here via distasteful remarks about things up other's arses, which says a lot about you. HA! Hey Corky, there is only one last thing to say before you plonk me. -- **** YOU -- You have no skills, offer no solutions, have only vitriol to spew, and your breath most likely stinks like crack-whore. I hope you get infected with a really bad case of chlamydia and your penis falls off! Have a nice day. You too, my very sick friend. |
#40
Posted to alt.home.repair
|
|||
|
|||
Outdoor Flood Lights-Juice but no Light
On May 29, 2:06 pm, "CooSer" wrote:
I am a little baffled. I have flood lights that used to work. They stopped working so I replaced the bulbs with indoor/outdoor type flood lights. This did not fix the problem. I checked the sockets with my little $6 voltage detector and there is power. In fact, there is power in the sockets whether the switch is on or off. Now could it not be working because I need a special 'Outdoor' bulb? Or, since I get a power reading with the switch on or off, is there something wrong in the wiring? Any suggestions would be great! It may not be the fact that anything is wrong with the OPs tester. It may be picking up a voltage quite normally capacitively 'induced' through the proximity of various wires even though the switch is 'off'. One of the best testers is a regular lamp bulb. Apart from something stupid like the replacement bulb/s not having a long enough base to screw in and touch the terminals of the lamp socket; very unlikely IMO, it is most probably a switch that has gone defective, or something broken or corroded in the wiring or lamp sockets. From the question raised it appears that the OP does not have much appreciation of how a circuit operates or what a switch does? Accordingly it would be best from a family safety and insurance viewpoint to get someone knowledgeable to fix or at least assist. One problem with misunderstood repairs is that an improper one may 'seem to work'! "Hey look I fixed it". However next time a bulb is to be replaced the switch is in the wrong wire "How come I have a white wire connected to a black wire. That's not what my cousin, neighbour, friend local mechanic told me?" Or something is not properly grounded "What's this yellow/green wire for??" and a person on a ladder gets a shock and falls. Or a wire connected incorrectly "I thought that's where the black wire went before I disconnected it!", gets hot within a wall or fixture or switch box and "FIRE". Insurance cos. many of whom are just looking for a reason NOT to pay out, are not very sympathetic! So be very careful you know what you are doing. Pretty sure knowledgeable people reading this item could come up with anywhere from 9 to 15 'possible' reasons any of which would be plausible and simple to repair But be careful!. Therefore mention this anecdote: The car of a non mechanically inclined young lady driving some distance away from home had been dripping coolant slowly on the ground, which she had ignored. It had now lost most of it and overheated. She called home and discussed it with her father who said "Let it cool down for an hour or so then refill with water and drive slowly to the nearest service station you can find. Then call me, collect, from there and I'll speak to the mechanic for you. After waiting the young lady lifted the hood; took off the oil filler cap and filled up the engine crankcase etc. with water. naturally she never made to the service station and the engine was ruined! So the moral; like electrical wiring, know what you are doing. One little mistake and could be costly! |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Running outdoor Christmas lights without an outdoor outlet | Home Repair | |||