All right, I'm feeling mildly dumb and a little sheepish not to mention
slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. Excellent structural condition, lovely hardwood floors albeit in need of a refinishing. Paid for a home inspection prior to placing a bid on house. Inspector noted some electrical items that would be against code now for new construction but nothing major (things like clothes washer sharing a circuit with other receptacles, lack of GFCIs in the kitchen, etc.) all receptacles in house are three prong type and tested OK with cheap little $5 circuit tester. All visible wiring was old BX w/ cloth covered conductors and inspector said that grounding through the armor of the BX while not the way we do things now was perfectly OK. So I was feeling pretty good about things electrically, and that gave me a good feeling about the house, as I automatically anticipated issues with lack of grounds etc. in a house of this age. Well some of the receps. were a little loose and old looking so I bought a pack of new ones and proceeded to replace them. Basement went fine. Got to the first floor and identified some issues that will be easy to rectify. Then I got to the three oldest circuits in the house, one of which started life as the general first floor circuit and another the general second floor circuit (the latter of which still serves the entire second floor.) The third is a lighting only circuit which serves the lights at the stair landings. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. I don't have a big problem with that on a lighting only circuit but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, but this isn't the way we do things now, so it bothers me a little bit. questions: 1) is this actually an acceptable method of retrofitting receptacles to grounded type? I suspect not, but you never can tell. 2) if not, is this the kind of thing that would generally be covered by a home warranty? We did spend the $$ for one, although AFAIK it generally only covers things like appliances etc. I don't blame the inspector for missing this one; he would have had to pull a receptacle either on the south side of the first floor or somewhere on the second floor to identify this issue; there's a lot of wiring visible in the basement but it is all either BX or obviously recently added Romex which does contain a ground, so there was no reason to believe that this wasn't consistent throughout the house. However, the transition from exposed BX to hidden NM seems to be original to the house as far as I can tell; I wonder why that would be? Any help, thoughts, advice, etc. greatly appreciated. thanks, nate (it's a good thing the girlie was planning on repainting, I guess...) -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#2
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Nate Nagel wrote:
All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. Excellent structural condition, lovely hardwood floors albeit in need of a refinishing. Paid for a home inspection prior to placing a bid on house. Inspector noted some electrical items that would be against code now for new construction but nothing major (things like clothes washer sharing a circuit with other receptacles, lack of GFCIs in the kitchen, etc.) all receptacles in house are three prong type and tested OK with cheap little $5 circuit tester. All visible wiring was old BX w/ cloth covered conductors and inspector said that grounding through the armor of the BX while not the way we do things now was perfectly OK. So I was feeling pretty good about things electrically, and that gave me a good feeling about the house, as I automatically anticipated issues with lack of grounds etc. in a house of this age. Well some of the receps. were a little loose and old looking so I bought a pack of new ones and proceeded to replace them. Basement went fine. Got to the first floor and identified some issues that will be easy to rectify. Then I got to the three oldest circuits in the house, one of which started life as the general first floor circuit and another the general second floor circuit (the latter of which still serves the entire second floor.) The third is a lighting only circuit which serves the lights at the stair landings. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. I don't have a big problem with that on a lighting only circuit but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, but this isn't the way we do things now, so it bothers me a little bit. questions: 1) is this actually an acceptable method of retrofitting receptacles to grounded type? I suspect not, but you never can tell. 2) if not, is this the kind of thing that would generally be covered by a home warranty? We did spend the $$ for one, although AFAIK it generally only covers things like appliances etc. I don't blame the inspector for missing this one; he would have had to pull a receptacle either on the south side of the first floor or somewhere on the second floor to identify this issue; there's a lot of wiring visible in the basement but it is all either BX or obviously recently added Romex which does contain a ground, so there was no reason to believe that this wasn't consistent throughout the house. However, the transition from exposed BX to hidden NM seems to be original to the house as far as I can tell; I wonder why that would be? Any help, thoughts, advice, etc. greatly appreciated. Definitely not kosher to connect the receptical ground terminal to the neutral terminal. Consider replacing those recepticles with GFCI types with "ground not connected" labels applied to them. If you can definitely confirm upstream and downstream recepticals you could use GFCI recepticals in the upstream ones and continue using recepticals without ground holes on the downstream ones, or use grounding type recepticals with the same "ground not connected" stickers on them. As always, clear this stuff with your local electrical inspector he/she may or may not go along with my ideas. Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) "Rudeness is the weak man's imitation of strength." |
#3
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
It is not correct to wire outlets in that fashion, and I wouldn't expect
your home warranty to cover it, because it's not "broken" or something that broke down, just improperly wired outlets. For people protection you can install GFCI outlets, but it doesn't help for equipment that needs to be grounded, for that you'll need to run grounded cables to those locations "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. Excellent structural condition, lovely hardwood floors albeit in need of a refinishing. Paid for a home inspection prior to placing a bid on house. Inspector noted some electrical items that would be against code now for new construction but nothing major (things like clothes washer sharing a circuit with other receptacles, lack of GFCIs in the kitchen, etc.) all receptacles in house are three prong type and tested OK with cheap little $5 circuit tester. All visible wiring was old BX w/ cloth covered conductors and inspector said that grounding through the armor of the BX while not the way we do things now was perfectly OK. So I was feeling pretty good about things electrically, and that gave me a good feeling about the house, as I automatically anticipated issues with lack of grounds etc. in a house of this age. Well some of the receps. were a little loose and old looking so I bought a pack of new ones and proceeded to replace them. Basement went fine. Got to the first floor and identified some issues that will be easy to rectify. Then I got to the three oldest circuits in the house, one of which started life as the general first floor circuit and another the general second floor circuit (the latter of which still serves the entire second floor.) The third is a lighting only circuit which serves the lights at the stair landings. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. I don't have a big problem with that on a lighting only circuit but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, but this isn't the way we do things now, so it bothers me a little bit. questions: 1) is this actually an acceptable method of retrofitting receptacles to grounded type? I suspect not, but you never can tell. 2) if not, is this the kind of thing that would generally be covered by a home warranty? We did spend the $$ for one, although AFAIK it generally only covers things like appliances etc. I don't blame the inspector for missing this one; he would have had to pull a receptacle either on the south side of the first floor or somewhere on the second floor to identify this issue; there's a lot of wiring visible in the basement but it is all either BX or obviously recently added Romex which does contain a ground, so there was no reason to believe that this wasn't consistent throughout the house. However, the transition from exposed BX to hidden NM seems to be original to the house as far as I can tell; I wonder why that would be? Any help, thoughts, advice, etc. greatly appreciated. thanks, nate (it's a good thing the girlie was planning on repainting, I guess...) -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#4
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob |
#5
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Bob F wrote:
"Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#6
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Nate Nagel wrote:
Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate You can still buy ungrounded receptacles and put things back like original. Most circuits don't really need a ground, like the upstairs bedroom convenience outlets. Where you really need grounds (bathroom, kitchen counters near the sink, your computer UPS, etc,) you can run a separate green wire back to the service panel ground (or to the nearest grounding electrode conductor, if that is easier.) The ground wire does not have to run with the current-carrying wires if you are updating old work. You can also install a GFCI breaker and then use 3-wire receptacles, leaving the ground terminal disconnected. In this case, you technically need to put a sticker that says "GFCI Protected. No Equipment Ground." on each of the grounding outlets that has a floating ground. You can also protect circuits by wiring them thru the LOAD terminals of a GFCI receptacle. The most practical solution will probably end up being a mixture of these methods. HTH :-) Bob |
#7
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
i would run a seperate ground wire to the effected outlets.
how many are a problem? 5 10 50? most older homes have few outlets, might be time to upgrade. do not connect grounds to neutrals in the right situation it can kill........ |
#8
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
zxcvbob wrote:
Nate Nagel wrote: Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate You can still buy ungrounded receptacles and put things back like original. Most circuits don't really need a ground, like the upstairs bedroom convenience outlets. Where you really need grounds (bathroom, kitchen counters near the sink, your computer UPS, etc,) you can run a separate green wire back to the service panel ground (or to the nearest grounding electrode conductor, if that is easier.) The ground wire does not have to run with the current-carrying wires if you are updating old work. You can also install a GFCI breaker and then use 3-wire receptacles, leaving the ground terminal disconnected. In this case, you technically need to put a sticker that says "GFCI Protected. No Equipment Ground." on each of the grounding outlets that has a floating ground. You can also protect circuits by wiring them thru the LOAD terminals of a GFCI receptacle. The most practical solution will probably end up being a mixture of these methods. HTH :-) Bob that may be doable at least upstairs; is it kosher to run, say, THHN without conduit or greenfield or would I need some kind of plenum rated wire? Please excuse the dumb questions; I know a lot about fire alarm but just enough to be dangerous about plain old electrical stuff. Since I really like this house (and paid enough for it!) I'd like to "do it right" whenever possible, and certainly would like to be able to say with a straight face to any prospective buyers in the future that everything is up to snuff. nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#9
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Nate Nagel wrote:
zxcvbob wrote: Nate Nagel wrote: Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate You can still buy ungrounded receptacles and put things back like original. Most circuits don't really need a ground, like the upstairs bedroom convenience outlets. Where you really need grounds (bathroom, kitchen counters near the sink, your computer UPS, etc,) you can run a separate green wire back to the service panel ground (or to the nearest grounding electrode conductor, if that is easier.) The ground wire does not have to run with the current-carrying wires if you are updating old work. You can also install a GFCI breaker and then use 3-wire receptacles, leaving the ground terminal disconnected. In this case, you technically need to put a sticker that says "GFCI Protected. No Equipment Ground." on each of the grounding outlets that has a floating ground. You can also protect circuits by wiring them thru the LOAD terminals of a GFCI receptacle. The most practical solution will probably end up being a mixture of these methods. HTH :-) Bob that may be doable at least upstairs; is it kosher to run, say, THHN without conduit or greenfield or would I need some kind of plenum rated wire? Please excuse the dumb questions; I know a lot about fire alarm but just enough to be dangerous about plain old electrical stuff. Since I really like this house (and paid enough for it!) I'd like to "do it right" whenever possible, and certainly would like to be able to say with a straight face to any prospective buyers in the future that everything is up to snuff. nate From what I can tell, the electric code is silent about that. I just run a #12 green THHN / THWN-2 wire inside the wall cavities, staple to the ceiling joists, etc. I run them as neatly as possible and where they are unlikely to be physically abused. I ground them at a big split-bolt connector on the main grounding electrode conductor a couple of feet from where it goes into the electric panel. I have an older house, and I'm trying to get one properly grounded duplex outlet in each room, and I don't worry about the ungrounded convenience outlets. All the basement, bathroom, and utility room outlets are grounded and GFCI'ed (except the outlet for the freezers.) All the kitchen outlets are grounded except for one that I couldn't get a ground wire to so I installed a GFCI receptacle. (the one that I couldn't ground just happened to be the outlet close to the sink) Bob |
#10
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Electrical really isn't that difficult for a homeowner to do. You can
get a book on how to do it at the local library. I am a sheetmetal man and I rewired my whole house without any problems and it passed the city inspection with ease. It had four fuses for the whole house. I ripped out the fuse panel and replaced it with circuit breakers. I had a ranch type home and that made it easier. If you are talking first floor, I would pull the receptacle, and then go into the basement and drill a hole through the floor and sill plate into the wall now run new wire through the hole and pull it out through where the receptical was removed. They have new plastic boxes that can go right back into the hole with no nailing required. As you tighten a screw, a plastic flag flips out and secures the box to the drywall. Then run that wire under the the floor to the box and hook it up. If you are talking the second floor, it is pretty much the same, but I would go up to the attic. If you have any other questions, just ask Pat Nate Nagel wrote: All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. Excellent structural condition, lovely hardwood floors albeit in need of a refinishing. Paid for a home inspection prior to placing a bid on house. Inspector noted some electrical items that would be against code now for new construction but nothing major (things like clothes washer sharing a circuit with other receptacles, lack of GFCIs in the kitchen, etc.) all receptacles in house are three prong type and tested OK with cheap little $5 circuit tester. All visible wiring was old BX w/ cloth covered conductors and inspector said that grounding through the armor of the BX while not the way we do things now was perfectly OK. So I was feeling pretty good about things electrically, and that gave me a good feeling about the house, as I automatically anticipated issues with lack of grounds etc. in a house of this age. Well some of the receps. were a little loose and old looking so I bought a pack of new ones and proceeded to replace them. Basement went fine. Got to the first floor and identified some issues that will be easy to rectify. Then I got to the three oldest circuits in the house, one of which started life as the general first floor circuit and another the general second floor circuit (the latter of which still serves the entire second floor.) The third is a lighting only circuit which serves the lights at the stair landings. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. I don't have a big problem with that on a lighting only circuit but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, but this isn't the way we do things now, so it bothers me a little bit. questions: 1) is this actually an acceptable method of retrofitting receptacles to grounded type? I suspect not, but you never can tell. 2) if not, is this the kind of thing that would generally be covered by a home warranty? We did spend the $$ for one, although AFAIK it generally only covers things like appliances etc. I don't blame the inspector for missing this one; he would have had to pull a receptacle either on the south side of the first floor or somewhere on the second floor to identify this issue; there's a lot of wiring visible in the basement but it is all either BX or obviously recently added Romex which does contain a ground, so there was no reason to believe that this wasn't consistent throughout the house. However, the transition from exposed BX to hidden NM seems to be original to the house as far as I can tell; I wonder why that would be? Any help, thoughts, advice, etc. greatly appreciated. thanks, nate (it's a good thing the girlie was planning on repainting, I guess...) -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#11
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() "RBM" rbm2(remove wrote in message ... It is not correct to wire outlets in that fashion, and I wouldn't expect your home warranty to cover it, because it's not "broken" or something that broke down, just improperly wired outlets. For people protection you can install GFCI outlets, but it doesn't help for equipment that needs to be grounded, for that you'll need to run grounded cables to those locations What equipment "needs" to be grounded? You may find that today the answer is: not much! Most audio/visual stuff (TVs, Stereos) doesn't have a ground. I have a window A/C that has a GFCI built into the plug (which does have a ground). But there isn't a ground wire to the case of the A/C. |
#12
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Things like computers "need" to be grounded
"John Gilmer" wrote in message ... "RBM" rbm2(remove wrote in message ... It is not correct to wire outlets in that fashion, and I wouldn't expect your home warranty to cover it, because it's not "broken" or something that broke down, just improperly wired outlets. For people protection you can install GFCI outlets, but it doesn't help for equipment that needs to be grounded, for that you'll need to run grounded cables to those locations What equipment "needs" to be grounded? You may find that today the answer is: not much! Most audio/visual stuff (TVs, Stereos) doesn't have a ground. I have a window A/C that has a GFCI built into the plug (which does have a ground). But there isn't a ground wire to the case of the A/C. |
#13
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
In article , Nate Nagel wrote:
but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, No, it isn't, not even theoretically. This makes it possible for the chassis of any piece of equipment plugged into the outlet to become electrically live, and it's not at all safe. but this isn't the way we do things now, so it bothers me a little bit. Should bother you _a_lot_. questions: 1) is this actually an acceptable method of retrofitting receptacles to grounded type? I suspect not, but you never can tell. No way. 2) if not, is this the kind of thing that would generally be covered by a home warranty? We did spend the $$ for one, although AFAIK it generally only covers things like appliances etc. No. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#14
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() "RBM" rbm2(remove wrote in message ... Things like computers "need" to be grounded Not at all. They work just fine, thank you, with a "floating" ground. Often, however, where these is a ground provided there is a network which provides a small leakage path between BOTH power conductors and the chassis (ground). The effect of this network would be to cause the chassis get a voltage on the order of 55 volts. There is no shock hazard and the leakage of even several of these systems is not likely to trip a GFCI. There is a lot of "tradition" here. When IBM started making PCs they had a ground. When folks starting making audio/visual stuff include stereos and TVs, there usually wasn't a ground. But both classes of equipment have user exposure to the "chassis." In the audio/visual stuff its from the "RCA" female connectors. In the PC world it's the connector shell including the mouse, keyboard, USB stuff, printer and serial interface. |
#15
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
On Fri, 20 Oct 2006 08:04:56 -0400, John Gilmer wrote:
"RBM" rbm2(remove wrote in message ... Things like computers "need" to be grounded Not at all. They work just fine, thank you, with a "floating" ground. Often, however, where these is a ground provided there is a network which provides a small leakage path between BOTH power conductors and the chassis (ground). The effect of this network would be to cause the chassis get a voltage on the order of 55 volts. There is no shock hazard and the leakage of even several of these systems is not likely to trip a GFCI. There is a lot of "tradition" here. When IBM started making PCs they had a ground. When folks starting making audio/visual stuff include stereos and TVs, there usually wasn't a ground. But both classes of equipment have user exposure to the "chassis." In the audio/visual stuff its from the "RCA" female connectors. In the PC world it's the connector shell including the mouse, keyboard, USB stuff, printer and serial interface. There's a big difference between A/V equipment and computers. Well, at least in Europe, I don't know much about US regulations. Most A/V stuff has reinforced or double insulation. That's why they have a plug without ground. Computers (except some laptops) usually have only 'normal' insulation. A single fault in the insulation can create a connection between the live pole and the cabinet. Without a grounded cabinet, that could be lethal. With grounded cabinet, you just blow a fuse. In case of fire or other damage, the insurance company can give you a hard time, if they find out that you have class I equipment connected to a socket without ground. BTW: the 55 V you mentioned (115 V over here) is more than enough to blow a serial or parallel port when connecting a grounded printer to a non-grounded PC. For me, that's also a good reason to ground my PC. -- Maurice |
#16
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Maurice Janssen wrote:
On Fri, 20 Oct 2006 08:04:56 -0400, John Gilmer wrote: "RBM" rbm2(remove wrote in message ... Things like computers "need" to be grounded Not at all. They work just fine, thank you, with a "floating" ground. Often, however, where these is a ground provided there is a network which provides a small leakage path between BOTH power conductors and the chassis (ground). The effect of this network would be to cause the chassis get a voltage on the order of 55 volts. There is no shock hazard and the leakage of even several of these systems is not likely to trip a GFCI. There is a lot of "tradition" here. When IBM started making PCs they had a ground. When folks starting making audio/visual stuff include stereos and TVs, there usually wasn't a ground. But both classes of equipment have user exposure to the "chassis." In the audio/visual stuff its from the "RCA" female connectors. In the PC world it's the connector shell including the mouse, keyboard, USB stuff, printer and serial interface. There's a big difference between A/V equipment and computers. Well, at least in Europe, I don't know much about US regulations. Most A/V stuff has reinforced or double insulation. That's why they have a plug without ground. Computers (except some laptops) usually have only 'normal' insulation. A single fault in the insulation can create a connection between the live pole and the cabinet. Without a grounded cabinet, that could be lethal. With grounded cabinet, you just blow a fuse. In case of fire or other damage, the insurance company can give you a hard time, if they find out that you have class I equipment connected to a socket without ground. BTW: the 55 V you mentioned (115 V over here) is more than enough to blow a serial or parallel port when connecting a grounded printer to a non-grounded PC. For me, that's also a good reason to ground my PC. I found it interesting to discover that some two prong "wall wart" transformers have a high value resistor (in the order of 500K ohms) connected between the wide plug blade and the secondary of the transformer to drain off static charges from the chassis of whatever it is they are powering. That large a resistance could only deliver about 250 microamps of "shock current" if the receptical it was plugged into was crosswired hot to neutral. Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) "Rudeness is the weak man's imitation of strength." |
#17
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() There's a big difference between A/V equipment and computers. Not really. In both cases there is a transformer isolating the power from the load. I grant that the "switching" power supply used in PCs has a good amount of circuitry (the "switches") before the transformer -- "they convert the incoming AC to DC and then convert it to a higher frequency. At higher frequencies the transformer can be made a LOT smaller. In switching input also lets the power supply accomodate a very large change in input voltages without problem. There is no good reason why "they" could not make a PC power supply that made the PC as safe as your TV without relying upon a ground. Again, I point out that LG (the Korean company, formerly known as Lucky Goldstar) now ships it's Chinese made room air conditions with a GFCI built into the plug but with NO ground wire going to the chassis. I also like to point out that you are somewhat safer if metal objects in your environment "float" rather than be grounded. If your left hand is resting on a well grounded object and your right hand touches something electrically HOT, you may get a fatal shock. If your left hand is resting on a "floating" metal object you might get a little "tingle" when your right hand hits the HOT wire. Tradition counts for a lot is setting standards. BUT, had cheap and reliable GFCI technology been available when electric power was "new" it's quite likely that "grounding" may not have been as important. Well, at least in Europe, I don't know much about US regulations. Most A/V stuff has reinforced or double insulation. That's why they have a plug without ground. Computers (except some laptops) usually have only 'normal' insulation. A single fault in the insulation can create a connection between the live pole and the cabinet. Without a grounded cabinet, that could be lethal. With grounded cabinet, you just blow a fuse. True. Nonetheless, it's possible to make a PC power supply that is as safe as that in your television or DVD player. The next time I have both a dead PC power supply and a dead VCR I will open both up and see whether the PC supply is any more likely to generate a HOT to Ground cross that the VCR. In case of fire or other damage, the insurance company can give you a hard time, if they find out that you have class I equipment connected to a socket without ground. Unless it was the cause of the fire, the insurance company will not say a thing. Moreover, codes permit sockets with ground openings that are not grounded so long as: 1) the circuit is protected by a GFCI; and 2) there is a "not grounded" label applied. Read the installation instructions on your GFCI (I may be making an incorrect assumption about GFCIs "over there."). In the States, the insurance companies have better have a VERY good reason to give your a "hard time." A company that drags its feet over a payment risks paying fines to the regulators and risks being successfully sued by the insured with truly massive "punitive" damages. BTW: the 55 V you mentioned (115 V over here) is more than enough to blow a serial or parallel port when connecting a grounded printer to a non-grounded PC. For me, that's also a good reason to ground my PC. No. It would be current limited. Likewise, if you rub your feet on the carpet in winter and build up a 20,000 volt charge (which happens) you likely would not fry something it you touch a signal pin. It's all a matter of how much energy you can dump into the interface. Your grounded printer would "ground" your PC. No harm, no foul. -- Maurice |
#18
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "Doug Miller" wrote in message t... In article , Nate Nagel wrote: but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, No, it isn't, not even theoretically. This makes it possible for the chassis of any piece of equipment plugged into the outlet to become electrically live, and it's not at all safe. If the two wire circuit (w/o ground) is protected by a GFCI, it's quite safe. Under some circumstances it is more safe than a grounded outlet without a GFCI. If you have an old house replacing behind the wall wiring just to get "grounds" isn't necessary. If you are knocking out walls and/or adding new circuits you new wiring should meet code but so long as you have GFCI protection, there is no reason to fear for your safety with old wiring w/o ground. BUT you should "test" your GFCI using the build in test button. An external GFCI tester will not trip an ungrounded GFCI outlet. |
#19
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
In article , "John Gilmer" wrote:
"Doug Miller" wrote in message et... In article , Nate Nagel wrote: but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, No, it isn't, not even theoretically. This makes it possible for the chassis of any piece of equipment plugged into the outlet to become electrically live, and it's not at all safe. If the two wire circuit (w/o ground) is protected by a GFCI, it's quite safe. Under some circumstances it is more safe than a grounded outlet without a GFCI. Well, yes -- but that's not the situation that was being discussed here. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#20
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
zxcvbob wrote:
Nate Nagel wrote: zxcvbob wrote: Nate Nagel wrote: Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate You can still buy ungrounded receptacles and put things back like original. Most circuits don't really need a ground, like the upstairs bedroom convenience outlets. Where you really need grounds (bathroom, kitchen counters near the sink, your computer UPS, etc,) you can run a separate green wire back to the service panel ground (or to the nearest grounding electrode conductor, if that is easier.) The ground wire does not have to run with the current-carrying wires if you are updating old work. You can also install a GFCI breaker and then use 3-wire receptacles, leaving the ground terminal disconnected. In this case, you technically need to put a sticker that says "GFCI Protected. No Equipment Ground." on each of the grounding outlets that has a floating ground. You can also protect circuits by wiring them thru the LOAD terminals of a GFCI receptacle. The most practical solution will probably end up being a mixture of these methods. HTH :-) Bob that may be doable at least upstairs; is it kosher to run, say, THHN without conduit or greenfield or would I need some kind of plenum rated wire? Please excuse the dumb questions; I know a lot about fire alarm but just enough to be dangerous about plain old electrical stuff. Since I really like this house (and paid enough for it!) I'd like to "do it right" whenever possible, and certainly would like to be able to say with a straight face to any prospective buyers in the future that everything is up to snuff. nate From what I can tell, the electric code is silent about that. I just run a #12 green THHN / THWN-2 wire inside the wall cavities, staple to the ceiling joists, etc. I run them as neatly as possible and where they are unlikely to be physically abused. I ground them at a big split-bolt connector on the main grounding electrode conductor a couple of feet from where it goes into the electric panel. I have an older house, and I'm trying to get one properly grounded duplex outlet in each room, and I don't worry about the ungrounded convenience outlets. All the basement, bathroom, and utility room outlets are grounded and GFCI'ed (except the outlet for the freezers.) All the kitchen outlets are grounded except for one that I couldn't get a ground wire to so I installed a GFCI receptacle. (the one that I couldn't ground just happened to be the outlet close to the sink) Bob Thanks to you and to the others who replied. I have a coworker who is a master electrician as well and he also suggested the separate ground wire, so I think that that may be the plan of attack for the first floor. Here's what I'm thinking: -buy some new circuit breakers. I have four spare spaces in the breaker panel, but I'm going to see if I can get some half-height breakers just in case I want to add a 240V circuit in the future. -split the washer and dryer onto their own circuits. (they are currently sharing circuits; the washer with the hall lighting and the dryer with the dishwasher.) Also run a dedicated circuit to the (gas) stove (currently shared with the hall lighting and clothes washer.) Should this be 20A or is 15A sufficient? I was thinking 15A would be OK but if current code recommends 20A that's what I'll do. -If feasible, provide a new 20A circuit for a single receptacle on the kitchen counter that's currently shared with the 1st floor lighting ckt. (the other is already on a 20A circuit, and I've installed a GFCI receptacle) -Again, if feasible, provide a new 15A circuit dedicated for the bathroom. cut box out of wall and replace single gang box with light switch with double gang box for light switch and GFCI receptacle. Leave pull string up to attic for future installation of an exhaust fan. -On the first floor, run a single green 14AWG THHN from breaker panel to receptacles coming up from below and then dropping back down again, working my way around the perimeter of the house. One homerun for each circuit (there are two.) Light switches and light fixtures remain ungrounded; there seems to be no way to deal with those short of breaking up some very thick and sturdy-looking plaster. -On the second floor, either follow the same plan as above, but dropping down from within the attic, or else find the homerun and ground that back to the breaker panel using the chase behind the bathtub and then completely rewire the rest with 14/2 Romex from the attic (should be possible, although I suspect this house was wired "old style" with switch legs dropping down from the ceiling light fixtures so I may leave the light switches ungrounded.) comments? I'm starting to think that maybe I can do this (assuming, of course, that She Who Must Be Obeyed displays an aptitude as a fish tape operator,) although I'm wondering if I'm approaching the point at which I need to pull a permit. I certainly don't want to **** off the various local agencies as I do need to deal with them at work. nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#21
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Doug Miller wrote:
In article , Nate Nagel wrote: but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, No, it isn't, not even theoretically. This makes it possible for the chassis of any piece of equipment plugged into the outlet to become electrically live, and it's not at all safe. It is functionally identical, so long as the neutral isn't broken. They connect to the same terminal strip at the breaker box, after all. If the neutral is broken, of course, all bets are off, and this is why I brought it up in the first place. nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#22
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
bareceptables 20 amp all by itself GFCI
hair dryers and curling irons are energy piggies. refrigerator 20 amp all by itself. you dont want something tripping fridge circuit NO GFCI! kitchen at least one but preferably 2 20 amp receptable circuits GFCI! gas stove must be GFCI protected. furnace its own 15 or 20 amp circuit. dont want a nuisance trip freezing home... washer and dryer together on their own circuit this is a starting place for electrical upgrades.......... I prefer but dont have each rooms receptables on their own breaker. aone or two circuits for just lights is ideal, minimizes trips by overloads |
#23
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
bareceptables 20 amp all by itself GFCI
hair dryers and curling irons are energy piggies. refrigerator 20 amp all by itself. you dont want something tripping fridge circuit NO GFCI! kitchen at least one but preferably 2 20 amp receptable circuits GFCI! gas stove must be GFCI protected. furnace its own 15 or 20 amp circuit. dont want a nuisance trip freezing home... washer and dryer together on their own circuit this is a starting place for electrical upgrades.......... I prefer but dont have each rooms receptables on their own breaker. aone or two circuits for just lights is ideal, minimizes trips by overloads |
#24
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() If the two wire circuit (w/o ground) is protected by a GFCI, it's quite safe. Under some circumstances it is more safe than a grounded outlet without a GFCI. Well, yes -- but that's not the situation that was being discussed here. What? That's EXACTLY the situation being discussed. |
#25
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() It is functionally identical, so long as the neutral isn't broken. They connect to the same terminal strip at the breaker box, after all. If the neutral is broken, of course, all bets are off, and this is why I brought it up in the first place. Doesn't matter. The rules are the the ground and neutral are bonded at the service entrance or the breaker box. Not afterward. It's no longer code but most older homes with an electric dryer or an electric stove used a three wire plug. The neutral was connected to the chassis of the dryer or stove. In new installations the chassis is connected to a separate ground wire. In theory the "new way" is safer, in practice it doesn't make any difference but electricians don't have a choice. The basic idea behind the grounding scheme is that the protective ground only carries fault currents. |
#26
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
In article , Nate Nagel wrote:
Doug Miller wrote: In article , Nate Nagel wrote: but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, No, it isn't, not even theoretically. This makes it possible for the chassis of any piece of equipment plugged into the outlet to become electrically live, and it's not at all safe. It is functionally identical, so long as the neutral isn't broken. No, it is *not*, as I just pointed out. You seem to be unaware that the neutral wire carries current. If the ground and neutral are interconnected at the receptacle, anyone simultaneously touching the metal chassis of any equipment plugged into that outlet, and anything else that's grounded (e.g. a water pipe or faucet, or simply standing on a concrete floor) makes a parallel path to ground for the current in the neutral conductor -- and enough current can pass through that person's body to cause a significant danger. They connect to the same terminal strip at the breaker box, after all. And that is the *only* place that they are permitted by Code to be connected. The Code _explicitly_prohibits_ interconnections anywhere else. Do you suppose there might actually be a reason for that, or do you think they just did that at random? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#27
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
In article , "John Gilmer" wrote:
If the two wire circuit (w/o ground) is protected by a GFCI, it's quite safe. Under some circumstances it is more safe than a grounded outlet without a GFCI. Well, yes -- but that's not the situation that was being discussed here. What? That's EXACTLY the situation being discussed. Ummmmmm.... maybe I missed it, but where did the original post make any mention of GFCIs?? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#28
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() hair dryers and curling irons are energy piggies. Yeah. Most just use an ungrounded (2 prong) plug and some have a GFCI built into the plug assembly. refrigerator 20 amp all by itself. you dont want something tripping fridge circuit NO GFCI! I have run refrigerators on a GFCI circuit because the outlet was on a counter and I wanted all counter outlets protected. An old fridge tripped out once a year or so (I think during defrost some water got onto the quartz heater wiring) but when we replaced it with a new model (10 years ago) it didn't trip. For my money, a modern fridge would not trip a GFCI unless there is something WRONG! I had a dishwasher on a GFCI but when the door seal leaked the water got the heater terminals wet. Again, it was reasonable to cut the circuit when water was getting into the wires. kitchen at least one but preferably 2 20 amp receptable circuits GFCI! gas stove must be GFCI protected. Yes but the main reason is the "convenience" outlet. furnace its own 15 or 20 amp circuit. dont want a nuisance trip freezing home... Why would it trip? washer and dryer together on their own circuit I have a clothes washer on a GFCI circuit (it's a duplex outlet and something else may be plugged into it.) I know that the washer is supposed to be on it's own circuit but ... Now that you got me going, I wonder whether the over the oven microwave would trip a GFCI. I don't think it would. this is a starting place for electrical upgrades.......... I prefer but dont have each rooms receptables on their own breaker. Our last two places had one circuit PER ROOM. Any trip kills everything (including lights) in the entire room. aone or two circuits for just lights is ideal, minimizes trips by overloads Frankly, we just don't trip the CBs very often. Before I put in the over the oven microwave, we had a coffee maker, toaster, popcorn popper, and microwave on one table. We had to remember to turn off the coffee maker if we were using the toaster and the microwave at the same time. I think the coffee maker and the toaster will still trip a CB every few months. |
#29
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
No but you could pull a bare ground around to each box. How's the access?
-- Steve Barker "Nate Nagel" wrote in message ... Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel |
#30
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() |
#31
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Nate Nagel wrote:
All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. Excellent structural condition, lovely hardwood floors albeit in need of a refinishing. Paid for a home inspection prior to placing a bid on house. Inspector noted some electrical items that would be against code now for new construction but nothing major (things like clothes washer sharing a circuit with other receptacles, lack of GFCIs in the kitchen, etc.) all receptacles in house are three prong type and tested OK with cheap little $5 circuit tester. All visible wiring was old BX w/ cloth covered conductors and inspector said that grounding through the armor of the BX while not the way we do things now was perfectly OK. So I was feeling pretty good about things electrically, and that gave me a good feeling about the house, as I automatically anticipated issues with lack of grounds etc. in a house of this age. Well some of the receps. were a little loose and old looking so I bought a pack of new ones and proceeded to replace them. Basement went fine. Got to the first floor and identified some issues that will be easy to rectify. Then I got to the three oldest circuits in the house, one of which started life as the general first floor circuit and another the general second floor circuit (the latter of which still serves the entire second floor.) The third is a lighting only circuit which serves the lights at the stair landings. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. I don't have a big problem with that on a lighting only circuit but the receptacles installed on the first and second floor are grounding type and it appears that the ground is provided by a jumper at each receptacle between the ground terminal and the neutral. I realize that *theoretically* this is functionally identical, but this isn't the way we do things now, so it bothers me a little bit. questions: 1) is this actually an acceptable method of retrofitting receptacles to grounded type? I suspect not, but you never can tell. 2) if not, is this the kind of thing that would generally be covered by a home warranty? We did spend the $$ for one, although AFAIK it generally only covers things like appliances etc. I don't blame the inspector for missing this one; he would have had to pull a receptacle either on the south side of the first floor or somewhere on the second floor to identify this issue; there's a lot of wiring visible in the basement but it is all either BX or obviously recently added Romex which does contain a ground, so there was no reason to believe that this wasn't consistent throughout the house. However, the transition from exposed BX to hidden NM seems to be original to the house as far as I can tell; I wonder why that would be? Any help, thoughts, advice, etc. greatly appreciated. thanks, nate (it's a good thing the girlie was planning on repainting, I guess...) Nate Those boot leg ground connections are a real danger. If any part of the neutral conductor fails the metal shell of any grounded appliance downstream of the open conductor will be energized through the connected loads to 120 volts. Removing the bootleg grounds and installing ground fault circuit interuptor protection on the affected circuits should be your first order of business. That will provide safety to humans but not to solid state electronics until you can upgrade the wiring. Have your home warranty contract reviewed by a competent attorney. If it has coverage for concealed defect it may cover the steps I have outlined. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
#32
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob Knob and tube went out before the 1940's in almost all parts of the United States which is where the OP is from, I think. H. R. (Bob) Hofmann |
#33
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() Nate Nagel wrote: zxcvbob wrote: Nate Nagel wrote: zxcvbob wrote: Nate Nagel wrote: Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate You can still buy ungrounded receptacles and put things back like original. Most circuits don't really need a ground, like the upstairs bedroom convenience outlets. Where you really need grounds (bathroom, kitchen counters near the sink, your computer UPS, etc,) you can run a separate green wire back to the service panel ground (or to the nearest grounding electrode conductor, if that is easier.) The ground wire does not have to run with the current-carrying wires if you are updating old work. You can also install a GFCI breaker and then use 3-wire receptacles, leaving the ground terminal disconnected. In this case, you technically need to put a sticker that says "GFCI Protected. No Equipment Ground." on each of the grounding outlets that has a floating ground. You can also protect circuits by wiring them thru the LOAD terminals of a GFCI receptacle. The most practical solution will probably end up being a mixture of these methods. HTH :-) Bob that may be doable at least upstairs; is it kosher to run, say, THHN without conduit or greenfield or would I need some kind of plenum rated wire? Please excuse the dumb questions; I know a lot about fire alarm but just enough to be dangerous about plain old electrical stuff. Since I really like this house (and paid enough for it!) I'd like to "do it right" whenever possible, and certainly would like to be able to say with a straight face to any prospective buyers in the future that everything is up to snuff. nate From what I can tell, the electric code is silent about that. I just run a #12 green THHN / THWN-2 wire inside the wall cavities, staple to the ceiling joists, etc. I run them as neatly as possible and where they are unlikely to be physically abused. I ground them at a big split-bolt connector on the main grounding electrode conductor a couple of feet from where it goes into the electric panel. I have an older house, and I'm trying to get one properly grounded duplex outlet in each room, and I don't worry about the ungrounded convenience outlets. All the basement, bathroom, and utility room outlets are grounded and GFCI'ed (except the outlet for the freezers.) All the kitchen outlets are grounded except for one that I couldn't get a ground wire to so I installed a GFCI receptacle. (the one that I couldn't ground just happened to be the outlet close to the sink) Bob Thanks to you and to the others who replied. I have a coworker who is a master electrician as well and he also suggested the separate ground wire, so I think that that may be the plan of attack for the first floor. Here's what I'm thinking: -buy some new circuit breakers. I have four spare spaces in the breaker panel, but I'm going to see if I can get some half-height breakers just in case I want to add a 240V circuit in the future. -split the washer and dryer onto their own circuits. (they are currently sharing circuits; the washer with the hall lighting and the dryer with the dishwasher.) Also run a dedicated circuit to the (gas) stove (currently shared with the hall lighting and clothes washer.) Should this be 20A or is 15A sufficient? I was thinking 15A would be OK but if current code recommends 20A that's what I'll do. -If feasible, provide a new 20A circuit for a single receptacle on the kitchen counter that's currently shared with the 1st floor lighting ckt. (the other is already on a 20A circuit, and I've installed a GFCI receptacle) -Again, if feasible, provide a new 15A circuit dedicated for the bathroom. cut box out of wall and replace single gang box with light switch with double gang box for light switch and GFCI receptacle. Leave pull string up to attic for future installation of an exhaust fan. -On the first floor, run a single green 14AWG THHN from breaker panel to receptacles coming up from below and then dropping back down again, working my way around the perimeter of the house. One homerun for each circuit (there are two.) Light switches and light fixtures remain ungrounded; there seems to be no way to deal with those short of breaking up some very thick and sturdy-looking plaster. -On the second floor, either follow the same plan as above, but dropping down from within the attic, or else find the homerun and ground that back to the breaker panel using the chase behind the bathtub and then completely rewire the rest with 14/2 Romex from the attic (should be possible, although I suspect this house was wired "old style" with switch legs dropping down from the ceiling light fixtures so I may leave the light switches ungrounded.) comments? I'm starting to think that maybe I can do this (assuming, of course, that She Who Must Be Obeyed displays an aptitude as a fish tape operator,) although I'm wondering if I'm approaching the point at which I need to pull a permit. I certainly don't want to **** off the various local agencies as I do need to deal with them at work. nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel You are on the right track to just add the ground wire where possible, it is much easier. My wife has, over the years, become extremely adept at grabbing fishtapes in wall cavities with bent coathangers. WIthout her help, I would still be doing some projects that have been completed years ago. I prefer metal boxes with ears that pull out when the screws at the side of the box are tightened. The plastic boxes with the tabs that rotate out don't have as much area pushing against the back of the sheetrock/plaster as the flat tabs on the metal boxes. Also, the plastic boxes do distort their shape a little while the metal boxes are more rigid. H. R. (Bob) Hofmann |
#35
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Negative. K&T was used up until almost 1950 in rural areas and actually was
overlapped by the early romex. The house i grew up in was K&T and was built in '45. The house I'm rebuilding right now was wired in the early '40's and has cloth romex. Not a knob or tube in sight. Google 'knob and tube' for more info than you want to know. -- Steve Barker wrote in message oups.com... Knob and tube went out before the 1940's in almost all parts of the United States which is where the OP is from, I think. H. R. (Bob) Hofmann |
#36
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Lowes and Home depot both sell them. As do most all other hardware stores.
-- Steve Barker "N8N" wrote in message oups.com... Where do you find metal old work boxes? My local "big box" hardware stores do not have them, although I've seen some of the contractors I work with using them, I believe they get them from supply houses where they have accounts. nate |
#37
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
Don't have a Lowe's, but Home Despot doesn't have them, at least not
out and on the shelf. Unfortunately the quality of help at Home Despot is... not so good, so they look at me blankly when I ask questions. nate Steve Barker LT wrote: Lowes and Home depot both sell them. As do most all other hardware stores. -- Steve Barker "N8N" wrote in message oups.com... Where do you find metal old work boxes? My local "big box" hardware stores do not have them, although I've seen some of the contractors I work with using them, I believe they get them from supply houses where they have accounts. nate |
#38
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]()
N8N wrote:
Don't have a Lowe's, but Home Despot doesn't have them, at least not out and on the shelf. Unfortunately the quality of help at Home Despot is... not so good, so they look at me blankly when I ask questions. nate Steve Barker LT wrote: Lowes and Home depot both sell them. As do most all other hardware stores. -- Steve Barker "N8N" wrote in message oups.com... Where do you find metal old work boxes? My local "big box" hardware stores do not have them, although I've seen some of the contractors I work with using them, I believe they get them from supply houses where they have accounts. nate Nate You are just looking for metal boxes with no permanently mounted brackets. They must have the plaster ears at the top and bottom of the box. You don't need the ones with built in plaster clamps. Just buy as many pairs of Madison Straps as you have boxes to install. You can see a picture of a pair of them at http://www.capeelectric.com/marion/images/raco/rac98.jpg -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
#39
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() N8N wrote: wrote: Nate Nagel wrote: zxcvbob wrote: Nate Nagel wrote: zxcvbob wrote: Nate Nagel wrote: Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate You can still buy ungrounded receptacles and put things back like original. Most circuits don't really need a ground, like the upstairs bedroom convenience outlets. Where you really need grounds (bathroom, kitchen counters near the sink, your computer UPS, etc,) you can run a separate green wire back to the service panel ground (or to the nearest grounding electrode conductor, if that is easier.) The ground wire does not have to run with the current-carrying wires if you are updating old work. You can also install a GFCI breaker and then use 3-wire receptacles, leaving the ground terminal disconnected. In this case, you technically need to put a sticker that says "GFCI Protected. No Equipment Ground." on each of the grounding outlets that has a floating ground. You can also protect circuits by wiring them thru the LOAD terminals of a GFCI receptacle. The most practical solution will probably end up being a mixture of these methods. HTH :-) Bob that may be doable at least upstairs; is it kosher to run, say, THHN without conduit or greenfield or would I need some kind of plenum rated wire? Please excuse the dumb questions; I know a lot about fire alarm but just enough to be dangerous about plain old electrical stuff. Since I really like this house (and paid enough for it!) I'd like to "do it right" whenever possible, and certainly would like to be able to say with a straight face to any prospective buyers in the future that everything is up to snuff. nate From what I can tell, the electric code is silent about that. I just run a #12 green THHN / THWN-2 wire inside the wall cavities, staple to the ceiling joists, etc. I run them as neatly as possible and where they are unlikely to be physically abused. I ground them at a big split-bolt connector on the main grounding electrode conductor a couple of feet from where it goes into the electric panel. I have an older house, and I'm trying to get one properly grounded duplex outlet in each room, and I don't worry about the ungrounded convenience outlets. All the basement, bathroom, and utility room outlets are grounded and GFCI'ed (except the outlet for the freezers.) All the kitchen outlets are grounded except for one that I couldn't get a ground wire to so I installed a GFCI receptacle. (the one that I couldn't ground just happened to be the outlet close to the sink) Bob Thanks to you and to the others who replied. I have a coworker who is a master electrician as well and he also suggested the separate ground wire, so I think that that may be the plan of attack for the first floor. Here's what I'm thinking: -buy some new circuit breakers. I have four spare spaces in the breaker panel, but I'm going to see if I can get some half-height breakers just in case I want to add a 240V circuit in the future. -split the washer and dryer onto their own circuits. (they are currently sharing circuits; the washer with the hall lighting and the dryer with the dishwasher.) Also run a dedicated circuit to the (gas) stove (currently shared with the hall lighting and clothes washer.) Should this be 20A or is 15A sufficient? I was thinking 15A would be OK but if current code recommends 20A that's what I'll do. -If feasible, provide a new 20A circuit for a single receptacle on the kitchen counter that's currently shared with the 1st floor lighting ckt. (the other is already on a 20A circuit, and I've installed a GFCI receptacle) -Again, if feasible, provide a new 15A circuit dedicated for the bathroom. cut box out of wall and replace single gang box with light switch with double gang box for light switch and GFCI receptacle. Leave pull string up to attic for future installation of an exhaust fan. -On the first floor, run a single green 14AWG THHN from breaker panel to receptacles coming up from below and then dropping back down again, working my way around the perimeter of the house. One homerun for each circuit (there are two.) Light switches and light fixtures remain ungrounded; there seems to be no way to deal with those short of breaking up some very thick and sturdy-looking plaster. -On the second floor, either follow the same plan as above, but dropping down from within the attic, or else find the homerun and ground that back to the breaker panel using the chase behind the bathtub and then completely rewire the rest with 14/2 Romex from the attic (should be possible, although I suspect this house was wired "old style" with switch legs dropping down from the ceiling light fixtures so I may leave the light switches ungrounded.) comments? I'm starting to think that maybe I can do this (assuming, of course, that She Who Must Be Obeyed displays an aptitude as a fish tape operator,) although I'm wondering if I'm approaching the point at which I need to pull a permit. I certainly don't want to **** off the various local agencies as I do need to deal with them at work. nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel You are on the right track to just add the ground wire where possible, it is much easier. My wife has, over the years, become extremely adept at grabbing fishtapes in wall cavities with bent coathangers. WIthout her help, I would still be doing some projects that have been completed years ago. I prefer metal boxes with ears that pull out when the screws at the side of the box are tightened. The plastic boxes with the tabs that rotate out don't have as much area pushing against the back of the sheetrock/plaster as the flat tabs on the metal boxes. Also, the plastic boxes do distort their shape a little while the metal boxes are more rigid. H. R. (Bob) Hofmann Where do you find metal old work boxes? My local "big box" hardware stores do not have them, although I've seen some of the contractors I work with using them, I believe they get them from supply houses where they have accounts. nate I haunt non-big-box hardware stores. Bob Hofmann |
#40
![]()
Posted to alt.home.repair,sci.engr.electrical.compliance
|
|||
|
|||
![]() N8N wrote: wrote: Nate Nagel wrote: zxcvbob wrote: Nate Nagel wrote: zxcvbob wrote: Nate Nagel wrote: Bob F wrote: "Nate Nagel" wrote in message ... All right, I'm feeling mildly dumb and a little sheepish not to mention slightly sick here... just bought a house for the first time less than a month ago, and knew that it had some minor wiring "issues" but now that I'm assessing what I have it appears that there are bigger issues than previously anticipated. Anyway, here's the deal. House is a two story colonial with full basement, built late 1940's. It appears that throughout the house wherever the wiring was hidden behind plaster it was run in NM not BX and there is no grounding, period. It's also possible that the wiring could be knob-and-tube in a house of that age. Bob No, it's definitely some early type of NM, although it may not be officially designated as such. There's two plastic-insulated conductors (that must be a pretty early use of same; as far as automotive stuff goes I believe the transition was made about 1955 - at least it was for Studebaker; I have a '55 coupe which (fortunately) has plastic insulation on the wiring) in what appears to be a tar-impregnated cloth jacket. But no ground. I really, REALLY don't want to have to rewire two complete circuits, although at this point it kind of looks like I'm going to have to. I might even have to involve a *gasp* electrician due to the magnitude of what this project looks like it's shaping up to be, which makes my Y-chromosome cower in shame. I suppose I could just install new non-grounded receptacles ahd that would be technically correct, although then I'm back where I started, as there's computer equipment on the second floor, and a UPS theoretically should have a ground... also would feel better if the stuff in the bathroom were grounded (although I was thinking of rewiring the bathroom anyway to meet current code with a dedicated circuit, GFCI, etc. which is somewhat doable as there's a small chase going down to the basement behind the bathtub, and an access panel, so it's "just" a matter of getting a cable from behind the bathtub up into the attic and then back down to the light switch...) I suppose it's not acceptable to cheat and ground stuff to the nearest water pipe... nate You can still buy ungrounded receptacles and put things back like original. Most circuits don't really need a ground, like the upstairs bedroom convenience outlets. Where you really need grounds (bathroom, kitchen counters near the sink, your computer UPS, etc,) you can run a separate green wire back to the service panel ground (or to the nearest grounding electrode conductor, if that is easier.) The ground wire does not have to run with the current-carrying wires if you are updating old work. You can also install a GFCI breaker and then use 3-wire receptacles, leaving the ground terminal disconnected. In this case, you technically need to put a sticker that says "GFCI Protected. No Equipment Ground." on each of the grounding outlets that has a floating ground. You can also protect circuits by wiring them thru the LOAD terminals of a GFCI receptacle. The most practical solution will probably end up being a mixture of these methods. HTH :-) Bob that may be doable at least upstairs; is it kosher to run, say, THHN without conduit or greenfield or would I need some kind of plenum rated wire? Please excuse the dumb questions; I know a lot about fire alarm but just enough to be dangerous about plain old electrical stuff. Since I really like this house (and paid enough for it!) I'd like to "do it right" whenever possible, and certainly would like to be able to say with a straight face to any prospective buyers in the future that everything is up to snuff. nate From what I can tell, the electric code is silent about that. I just run a #12 green THHN / THWN-2 wire inside the wall cavities, staple to the ceiling joists, etc. I run them as neatly as possible and where they are unlikely to be physically abused. I ground them at a big split-bolt connector on the main grounding electrode conductor a couple of feet from where it goes into the electric panel. I have an older house, and I'm trying to get one properly grounded duplex outlet in each room, and I don't worry about the ungrounded convenience outlets. All the basement, bathroom, and utility room outlets are grounded and GFCI'ed (except the outlet for the freezers.) All the kitchen outlets are grounded except for one that I couldn't get a ground wire to so I installed a GFCI receptacle. (the one that I couldn't ground just happened to be the outlet close to the sink) Bob Thanks to you and to the others who replied. I have a coworker who is a master electrician as well and he also suggested the separate ground wire, so I think that that may be the plan of attack for the first floor. Here's what I'm thinking: -buy some new circuit breakers. I have four spare spaces in the breaker panel, but I'm going to see if I can get some half-height breakers just in case I want to add a 240V circuit in the future. -split the washer and dryer onto their own circuits. (they are currently sharing circuits; the washer with the hall lighting and the dryer with the dishwasher.) Also run a dedicated circuit to the (gas) stove (currently shared with the hall lighting and clothes washer.) Should this be 20A or is 15A sufficient? I was thinking 15A would be OK but if current code recommends 20A that's what I'll do. -If feasible, provide a new 20A circuit for a single receptacle on the kitchen counter that's currently shared with the 1st floor lighting ckt. (the other is already on a 20A circuit, and I've installed a GFCI receptacle) -Again, if feasible, provide a new 15A circuit dedicated for the bathroom. cut box out of wall and replace single gang box with light switch with double gang box for light switch and GFCI receptacle. Leave pull string up to attic for future installation of an exhaust fan. -On the first floor, run a single green 14AWG THHN from breaker panel to receptacles coming up from below and then dropping back down again, working my way around the perimeter of the house. One homerun for each circuit (there are two.) Light switches and light fixtures remain ungrounded; there seems to be no way to deal with those short of breaking up some very thick and sturdy-looking plaster. -On the second floor, either follow the same plan as above, but dropping down from within the attic, or else find the homerun and ground that back to the breaker panel using the chase behind the bathtub and then completely rewire the rest with 14/2 Romex from the attic (should be possible, although I suspect this house was wired "old style" with switch legs dropping down from the ceiling light fixtures so I may leave the light switches ungrounded.) comments? I'm starting to think that maybe I can do this (assuming, of course, that She Who Must Be Obeyed displays an aptitude as a fish tape operator,) although I'm wondering if I'm approaching the point at which I need to pull a permit. I certainly don't want to **** off the various local agencies as I do need to deal with them at work. nate -- replace "fly" with "com" to reply. http://home.comcast.net/~njnagel You are on the right track to just add the ground wire where possible, it is much easier. My wife has, over the years, become extremely adept at grabbing fishtapes in wall cavities with bent coathangers. WIthout her help, I would still be doing some projects that have been completed years ago. I prefer metal boxes with ears that pull out when the screws at the side of the box are tightened. The plastic boxes with the tabs that rotate out don't have as much area pushing against the back of the sheetrock/plaster as the flat tabs on the metal boxes. Also, the plastic boxes do distort their shape a little while the metal boxes are more rigid. H. R. (Bob) Hofmann Where do you find metal old work boxes? My local "big box" hardware stores do not have them, although I've seen some of the contractors I work with using them, I believe they get them from supply houses where they have accounts. nate I haunt non-big-box hardware stores. Bob Hofmann |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Grounding wire from panel to gas pipe??? | Home Repair | |||
Easiest way to ground a computer? | Home Repair | |||
electrical interruption | Home Repair | |||
Surface ground water problem | Home Repair | |||
Microwave interferes with AM radio | Home Repair |