Wiring&breaker for lighting circuit
Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps.
So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore |
#2
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
|
#3
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
|
#4
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
Sorry, I should have described more.
These lights are in 4 separate areas/rooms of the basement, on 4 separate switches. Approx 6 lights per room/switch. |
#5
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
|
#6
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sunday, September 27, 2015 at 8:31:46 PM UTC-5, wrote:
Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. One with 12 and the other 13 light fixtures with the circuits joined to the hot and neutral in the switch box. You'd need to use a deep switch box to make sure there's enough room for the wiring. ^_^ [8~{} Uncle Smart Monster |
#7
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sunday, September 27, 2015 at 9:29:13 PM UTC-5, wrote:
Sorry, I should have described more. These lights are in 4 separate areas/rooms of the basement, on 4 separate switches. Approx 6 lights per room/switch. Feed a central junction box with a 20 amp circuit using #12. You can tie the 4 separate #14 circuits together in that junction box. Remember to put the junction box where it's accessible. ^_^ [8~{} Uncle Sparky Monster |
#8
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster
wrote: On Sunday, September 27, 2015 at 8:31:46 PM UTC-5, wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. One with 12 and the other 13 light fixtures with the circuits joined to the hot and neutral in the switch box. You'd need to use a deep switch box to make sure there's enough room for the wiring. ^_^ [8~{} Uncle Smart Monster You are not supposed to use #14 at all if you have a 20A breaker. |
#9
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
|
#11
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
That applies to *outlets* (180VA per single/dual), not circuits that are
used exclusively for hardwired lighting devices. Understood. This would be a dedicated lighting circuit, or circuits. Absolutely no outlets on it. Outlets will have separate circuit(s) and breaker(s). |
#12
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sunday, September 27, 2015 at 10:10:58 PM UTC-5, Seymore4Head wrote:
On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster wrote: On Sunday, September 27, 2015 at 8:31:46 PM UTC-5, wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. One with 12 and the other 13 light fixtures with the circuits joined to the hot and neutral in the switch box. You'd need to use a deep switch box to make sure there's enough room for the wiring. ^_^ [8~{} Uncle Smart Monster You are not supposed to use #14 at all if you have a 20A breaker. You're right but I've never seen a 20 amp breaker not trip when a #14 wire was connected to it and shorted. I haven't read the code on it but there is a guy who posts here in the group who is/was an electrical inspector. The #18 wire in a light fixture is tied to 20 amp circuits all the time. The #14 circuits could probably allowed because there is little or no chance of 20 amps being on a lighting circuit unless you were to screw resistance heater elements into all the light sockets. A 20 amp AFCI breaker would protect the circuit much better. ^_^ [8~{} Uncle Doubting Monster |
#13
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
|
#14
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster
wrote: The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. That is not legal on a 20a circuit, even if it works. |
#15
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sun, 27 Sep 2015 20:11:09 -0700, Don Y
wrote: On 9/27/2015 7:09 PM, wrote: On Sun, 27 Sep 2015 18:31:43 -0700 (PDT), wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore No. You are limited to the number of "devices" on the circuit Generally accepted as 8 on 15 amp and 12 on 20 IIRC.. I'd wire it on 2 circuits, with either 2 rings, or rows, or every second lamp on opposite circuits. I'd use an edison circuit,or at least a double (120/240) breaker powering a 2 pole contactor controlled by a single switch if you want all lights on at once all the time. I have an application where 3 circuits are controlled by a 3 pole (3 phase) contactor controlling 3 circuits of lighting on one switch - 12 potlights per circuit, 20 amp breakers. Originally 75 watt incandescents, currently running 9 watt LEDs. That applies to *outlets* (180VA per single/dual), not circuits that are used exclusively for hardwired lighting devices. .... and only applies in commercial in the US |
#16
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
|
#17
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 12:58:21 AM UTC-5, wrote:
On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster wrote: The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. That is not legal on a 20a circuit, even if it works. Yea I know and have never done it. The last time I wired a whole building I used #14 and #12 stranded THHN in EMT. I knew you'd be the expert on the code but I don't understand what the OP is worried about if he uses LED lighting. The A19 60w bulb equivalent draws 10 watts or less and the 100 watt equivalent LED bulb uses 14.5 watts. If he lit his whole house with LED bulbs it would probably draw less than 20 amps total. I find it hard to believe he'd put 75w bulbs in every fixture and run them all at the same time. If his fixtures are capable of using 75w bulbs, is it a code requirement that the lighting circuit be capable of powering all 13 fixtures at the same time if 75w bulbs are used? I don't know where my Ugly's Electrical Reference Book is and it's not the newest edition anyway. ^_^ [8~{} Uncle Curious Monster |
#18
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sun, 27 Sep 2015 21:42:02 -0700 (PDT), Uncle Monster
wrote: On Sunday, September 27, 2015 at 10:10:58 PM UTC-5, Seymore4Head wrote: On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster wrote: On Sunday, September 27, 2015 at 8:31:46 PM UTC-5, wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. One with 12 and the other 13 light fixtures with the circuits joined to the hot and neutral in the switch box. You'd need to use a deep switch box to make sure there's enough room for the wiring. ^_^ [8~{} Uncle Smart Monster You are not supposed to use #14 at all if you have a 20A breaker. You're right but I've never seen a 20 amp breaker not trip when a #14 wire was connected to it and shorted. I haven't read the code on it but there is a guy who posts here in the group who is/was an electrical inspector. The #18 wire in a light fixture is tied to 20 amp circuits all the time. The #14 circuits could probably allowed because there is little or no chance of 20 amps being on a lighting circuit unless you were to screw resistance heater elements into all the light sockets. A 20 amp AFCI breaker would protect the circuit much better. ^_^ [8~{} Uncle Doubting Monster That is the idiot clause. (240.4(D)) that says unless otherwise permitted in the code 14 ga wire shall be protected by a 15a breaker. (12=20, 10=30) It forces the 80% rule on "small conductors" I could tell you where it is otherwise permitted but your head might explode (like a legal 40a breaker on 14ga wire) When you start talking about "fixture wire" (your 18 ga example) that has to be part of a "listed" assembly, typically U/L listing. Typically 18 ga wire has a design ampacity of 7a but in a listed assembly where the load is controlled it can be protected by a 20a breaker. You are dealing with 2 issues, "overload" and "short circuit" protection. An overload is simply having too much load on the wire. Short circuit protection is a bolted fault where there is essentially no limit to the current but the resistance of the wire and the breaker, An 18 ga wire, less than 50 feet long will operate a 20 a breaker in a bolted fault. At least that is the thinking. You can still get in plenty of trouble with extension cords but we were talking about lamps. |
#19
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 1:49:58 AM UTC-5, wrote:
On Sun, 27 Sep 2015 21:42:02 -0700 (PDT), Uncle Monster wrote: On Sunday, September 27, 2015 at 10:10:58 PM UTC-5, Seymore4Head wrote: On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster wrote: On Sunday, September 27, 2015 at 8:31:46 PM UTC-5, wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. One with 12 and the other 13 light fixtures with the circuits joined to the hot and neutral in the switch box. You'd need to use a deep switch box to make sure there's enough room for the wiring. ^_^ [8~{} Uncle Smart Monster You are not supposed to use #14 at all if you have a 20A breaker. You're right but I've never seen a 20 amp breaker not trip when a #14 wire was connected to it and shorted. I haven't read the code on it but there is a guy who posts here in the group who is/was an electrical inspector. The #18 wire in a light fixture is tied to 20 amp circuits all the time. The #14 circuits could probably allowed because there is little or no chance of 20 amps being on a lighting circuit unless you were to screw resistance heater elements into all the light sockets. A 20 amp AFCI breaker would protect the circuit much better. ^_^ [8~{} Uncle Doubting Monster That is the idiot clause. (240.4(D)) that says unless otherwise permitted in the code 14 ga wire shall be protected by a 15a breaker. (12=20, 10=30) It forces the 80% rule on "small conductors" I could tell you where it is otherwise permitted but your head might explode (like a legal 40a breaker on 14ga wire) When you start talking about "fixture wire" (your 18 ga example) that has to be part of a "listed" assembly, typically U/L listing. Typically 18 ga wire has a design ampacity of 7a but in a listed assembly where the load is controlled it can be protected by a 20a breaker. You are dealing with 2 issues, "overload" and "short circuit" protection. I've repaired a lot of melted wiring that never tripped a breaker but luckily it was in UL listed boxes and enclosures. It was usually due to a bad connection that cause increasing resistance with temperature. Some even arced but didn't trip the breaker which wasn't an arc fault type. o_O An overload is simply having too much load on the wire. Short circuit protection is a bolted fault where there is essentially no limit to the current but the resistance of the wire and the breaker, An 18 ga wire, less than 50 feet long will operate a 20 a breaker in a bolted fault. At least that is the thinking. You can still get in plenty of trouble with extension cords but we were talking about lamps. I worked with #14 high temp silicone and fiberglass insulated wire in some circuits and that stuff was carrying much more than 15 amps. I did come across something about uninsulated conductors in open air being rated at much higher current than insulated wire. I remember reading about power strips and extension cords not being allowed in New York City. Are you familiar with the strict limits on the use of extension cords in NYC? o_O [8~{} Uncle Sparky Monster |
#20
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 12:42:09 AM UTC-4, Uncle Monster wrote:
On Sunday, September 27, 2015 at 10:10:58 PM UTC-5, Seymore4Head wrote: On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster wrote: On Sunday, September 27, 2015 at 8:31:46 PM UTC-5, wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. One with 12 and the other 13 light fixtures with the circuits joined to the hot and neutral in the switch box. You'd need to use a deep switch box to make sure there's enough room for the wiring. ^_^ [8~{} Uncle Smart Monster You are not supposed to use #14 at all if you have a 20A breaker. You're right but I've never seen a 20 amp breaker not trip when a #14 wire was connected to it and shorted. A direct short is only one failure mode that a breaker protects against and it happens so quickly that the wire doesn't get a chance to overheat so an undersized conductor would easily pass that. The other failure is an overload, which will heat up the wire continuously over a long period. Even there, considerable margin is in the code, so in most cases, a 14 conductor on a 20 breaker isn't going to start a fire. But the code margin is there for a reason and most cases don't matter if you happen to have the one that does. I haven't read the code on it but there is a guy who posts here in the group who is/was an electrical inspector. The #18 wire in a light fixture is tied to 20 amp circuits all the time. The #14 circuits could probably allowed because there is little or no chance of 20 amps being on a lighting circuit unless you were to screw resistance heater elements into all the light sockets. A 20 amp AFCI breaker would protect the circuit much better. ^_^ [8~{} Uncle Doubting Monster |
#21
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sun, 27 Sep 2015 23:08:00 -0400, Seymore4Head
wrote: On Sun, 27 Sep 2015 19:56:38 -0700 (PDT), Uncle Monster wrote: On Sunday, September 27, 2015 at 8:31:46 PM UTC-5, wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore The breaker is there to protect the wiring. I you're really worried about overloading the circuit, you can feed the switch with #12 then split the lights into two strings wired with #14. One with 12 and the other 13 light fixtures with the circuits joined to the hot and neutral in the switch box. You'd need to use a deep switch box to make sure there's enough room for the wiring. ^_^ [8~{} Uncle Smart Monster You are not supposed to use #14 at all if you have a 20A breaker. Correct. This is a good location for an "edison" or multiwire circuit. He needs AT LEAST 2 circuits, whether 15 or 20 amp. |
#22
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sun, 27 Sep 2015 20:11:09 -0700, Don Y
wrote: On 9/27/2015 7:09 PM, wrote: On Sun, 27 Sep 2015 18:31:43 -0700 (PDT), wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore No. You are limited to the number of "devices" on the circuit Generally accepted as 8 on 15 amp and 12 on 20 IIRC.. I'd wire it on 2 circuits, with either 2 rings, or rows, or every second lamp on opposite circuits. I'd use an edison circuit,or at least a double (120/240) breaker powering a 2 pole contactor controlled by a single switch if you want all lights on at once all the time. I have an application where 3 circuits are controlled by a 3 pole (3 phase) contactor controlling 3 circuits of lighting on one switch - 12 potlights per circuit, 20 amp breakers. Originally 75 watt incandescents, currently running 9 watt LEDs. That applies to *outlets* (180VA per single/dual), not circuits that are used exclusively for hardwired lighting devices. As long as he doesn't tack on "one" convenience outlet he might get away with it. Local interpretations vary. |
#23
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On 9/28/2015 5:34 AM, wrote:
On Sun, 27 Sep 2015 20:11:09 -0700, Don Y wrote: On 9/27/2015 7:09 PM, wrote: On Sun, 27 Sep 2015 18:31:43 -0700 (PDT), wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore No. You are limited to the number of "devices" on the circuit Generally accepted as 8 on 15 amp and 12 on 20 IIRC.. I'd wire it on 2 circuits, with either 2 rings, or rows, or every second lamp on opposite circuits. I'd use an edison circuit,or at least a double (120/240) breaker powering a 2 pole contactor controlled by a single switch if you want all lights on at once all the time. I have an application where 3 circuits are controlled by a 3 pole (3 phase) contactor controlling 3 circuits of lighting on one switch - 12 potlights per circuit, 20 amp breakers. Originally 75 watt incandescents, currently running 9 watt LEDs. That applies to *outlets* (180VA per single/dual), not circuits that are used exclusively for hardwired lighting devices. As long as he doesn't tack on "one" convenience outlet he might get away with it. Local interpretations vary. This is the problem ^^^^^^^^^^^^^^^^^^^^^ In most areas, there is no way to appeal an inspector's ruling. So, if inspector misinterprets the Code (or, is "having a bad day"), you're stuck with his ruling. |
#24
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On 9/27/2015 11:02 PM, Uncle Monster wrote:
On Sunday, September 27, 2015 at 9:29:13 PM UTC-5, wrote: Sorry, I should have described more. These lights are in 4 separate areas/rooms of the basement, on 4 separate switches. Approx 6 lights per room/switch. Feed a central junction box with a 20 amp circuit using #12. You can tie the 4 separate #14 circuits together in that junction box. Remember to put the junction box where it's accessible. ^_^ [8~{} Uncle Sparky Monster I don't think this is allowed or even a good idea. I'd go with 2 15 amp circuits to provide some light if one breaker trips (someone suggested). |
#25
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
Uncle Monster writes:
On Sunday, September 27, 2015 at 10:10:58 PM UTC-5, Seymore4Head wrote: You are not supposed to use #14 at all if you have a 20A breaker. You're right but I've never seen a 20 amp breaker not trip when a #14 wire = was connected to it and shorted. It's not short-circuits that one worries about, but rather the heating caused by the higher resistance of the smaller diameter conductors over the longer term. |
#26
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 8:32:17 AM UTC-4, wrote:
This is a good location for an "edison" or multiwire circuit. He needs AT LEAST 2 circuits, whether 15 or 20 amp. Feel free to keep making things up. Show us the code sections that say at least two circuits are required. |
#27
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
If we are going to talk code, lets speak the language so nobody gets
misinformation. ;-) Point taken and agreed. To summarize and rephrase: the subject is a lighting circuit(s) on which there will be 4 groups of luminaires (one group in each "room" of the basement, and each group having 4-6 luminaires), and each group is activated via separate switches; and NO receptacles will be installed on this/these dedicated circuits. And it seems that even though it is NOT prohibited by the NEC, the concensus is that I should split this into two 15amp lighting circuits for two reasons: easier to work with 14awg, and better design such that a tripped breaker wont plunge the entire basement into darkness. Did I get all that right? All comments appreciated. |
#28
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
If we are going to talk code, lets speak the language so nobody gets
misinformation. ;-) Point taken and agreed. To summarize and rephrase: house is located in New York, the subject is a lighting circuit(s) on which there will be 4 groups of luminaires (one group in each "room" of the basement, and each group having 4-6 luminaires, and each luminaire being rated at 75watts by its manufacturer), and each group is activated via separate switches; and NO receptacles will be installed on this/these dedicated circuits. And it seems that even though it is NOT prohibited by the NEC, the concensus is that I should split this into two 15amp lighting circuits for two reasons: easier to work with 14awg, and better design such that a tripped breaker wont plunge the entire basement into darkness. Did I get all that right? All comments appreciated. |
#29
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
If we are going to talk code, lets speak the language so nobody gets
misinformation. ;-) Point taken and agreed. To summarize and rephrase: house is located in New York, the subject is a lighting circuit(s) on which there will be 4 groups of luminaires (one group in each "room" of the basement, and each group having 4-6 luminaires, and each luminaire being rated at 75watts by its manufacturer), and each group is activated via separate switches; and NO receptacles will be installed on this/these dedicated circuits. And even though the NEC does not prohibit me from wiring this via 12awg and one 20amp breaker, the concensus is that I should split this into two 15amp lighting circuits for two reasons: easier to work with 14awg, and better design such that a tripped breaker wont plunge the entire basement into darkness. Did I get all that right? All comments appreciated. |
#30
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 7:44:02 AM UTC-5, Art Todesco wrote:
On 9/27/2015 11:02 PM, Uncle Monster wrote: On Sunday, September 27, 2015 at 9:29:13 PM UTC-5, wrote: Sorry, I should have described more. These lights are in 4 separate areas/rooms of the basement, on 4 separate switches. Approx 6 lights per room/switch. Feed a central junction box with a 20 amp circuit using #12. You can tie the 4 separate #14 circuits together in that junction box. Remember to put the junction box where it's accessible. ^_^ [8~{} Uncle Sparky Monster I don't think this is allowed or even a good idea. I'd go with 2 15 amp circuits to provide some light if one breaker trips (someone suggested). Actually it would violate code to tie #14 TO #12 on a 20 AMP circuit. The OP wrote that he's using LED bulbs that operate on 9 watts each. The 13 LED bulbs will draw about one amp all together. I'm quite sure a single 15 amp circuit will handle that. ^_^ [8~{} Uncle LED Monster |
#31
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 9:52:28 AM UTC-4, wrote:
If we are going to talk code, lets speak the language so nobody gets misinformation. ;-) Point taken and agreed. To summarize and rephrase: house is located in New York, the subject is a lighting circuit(s) on which there will be 4 groups of luminaires (one group in each "room" of the basement, and each group having 4-6 luminaires, and each luminaire being rated at 75watts by its manufacturer), and each group is activated via separate switches; and NO receptacles will be installed on this/these dedicated circuits. And even though the NEC does not prohibit me from wiring this via 12awg and one 20amp breaker, the concensus is that I should split this into two 15amp lighting circuits for two reasons: easier to work with 14awg, and better design such that a tripped breaker wont plunge the entire basement into darkness. Did I get all that right? All comments appreciated. I believe GFRE who's the authority on code issues, said that you can put it all on one 14 amp circuit if you want to. I agree with two circuits being marginally better though, from the blackout standpoint. But I can't recall a breaker here ever tripping on a circuit that is dedicated to lighting. I can recall plenty of cases where the utility has gone down, plunging everything into darkness. Since that's survivable and in my world actually occurs with some frequency, the additional benefit of having two lighting circuits is a nit, IMO. |
#32
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 8:52:28 AM UTC-5, wrote:
If we are going to talk code, lets speak the language so nobody gets misinformation. ;-) Point taken and agreed. To summarize and rephrase: house is located in New York, the subject is a lighting circuit(s) on which there will be 4 groups of luminaires (one group in each "room" of the basement, and each group having 4-6 luminaires, and each luminaire being rated at 75watts by its manufacturer), and each group is activated via separate switches; and NO receptacles will be installed on this/these dedicated circuits. And even though the NEC does not prohibit me from wiring this via 12awg and one 20amp breaker, the concensus is that I should split this into two 15amp lighting circuits for two reasons: easier to work with 14awg, and better design such that a tripped breaker wont plunge the entire basement into darkness. Did I get all that right? All comments appreciated. That's what you should do and it will keep you out of trouble if it's ever inspected. I have lamps plugged into wall outlets so if the lighting circuit trips, I have light. I even use LED bulbs in my desk lights which are plugged into the UPS units on my computer table. If you're worried about safety, put up an LED emergency light in your basement hallway or stairwell. ^_^ [8~{} Uncle Basement Monster |
#33
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
ultimately whats the cost and work effort between 2 15 amp lighting circuits, or one perhaps code compliant but questionable single circuit alternative.
better to go with the 2 15 amp circuits.... |
#34
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Sunday, September 27, 2015 at 11:10:28 PM UTC-4, Don Y wrote:
circuit so I can let light stream in through an open doorway, etc. Also, have you considered using LED *fixtures*? That would seem to be the best observation. OP is worried about 75W times X number of fixtures, etc. For new work, the obvious solution today is an LED fixture that is just that and won't accept an incandescent. |
#35
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Mon, 28 Sep 2015 00:32:25 -0700 (PDT), Uncle Monster
wrote: I've repaired a lot of melted wiring that never tripped a breaker but luckily it was in UL listed boxes and enclosures. It was usually due to a bad connection that cause increasing resistance with temperature. Some even arced but didn't trip the breaker which wasn't an arc fault type. o_O U/L does not certify that there will not be a fire, only that it will be totally contained in the equipment. An overload is simply having too much load on the wire. Short circuit protection is a bolted fault where there is essentially no limit to the current but the resistance of the wire and the breaker, An 18 ga wire, less than 50 feet long will operate a 20 a breaker in a bolted fault. At least that is the thinking. You can still get in plenty of trouble with extension cords but we were talking about lamps. I worked with #14 high temp silicone and fiberglass insulated wire in some circuits and that stuff was carrying much more than 15 amps. I did come across something about uninsulated conductors in open air being rated at much higher current than insulated wire. I remember reading about power strips and extension cords not being allowed in New York City. Are you familiar with the strict limits on the use of extension cords in NYC? o_O No idea but I do know NYC has adopted the NEC after 100 years of having their own code. That doesn't mean all the inspectors agree. |
#36
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Mon, 28 Sep 2015 05:41:27 -0700, Don Y
wrote: On 9/28/2015 5:34 AM, wrote: On Sun, 27 Sep 2015 20:11:09 -0700, Don Y wrote: On 9/27/2015 7:09 PM, wrote: On Sun, 27 Sep 2015 18:31:43 -0700 (PDT), wrote: Hi. I'm laying out my basement lighting. I expect to have 25 recessed lights, each is 75watt max rating (even though I will use LED, I know I must still assume max rating of fixture). 25x75=1875watts/120V = 15.6amps. So, I cannot use one 15amp breaker and 14awg wire. Can I wire all the lights with 12awg and a 20amp breaker? All comments appreciated. Thanks Theodore No. You are limited to the number of "devices" on the circuit Generally accepted as 8 on 15 amp and 12 on 20 IIRC.. I'd wire it on 2 circuits, with either 2 rings, or rows, or every second lamp on opposite circuits. I'd use an edison circuit,or at least a double (120/240) breaker powering a 2 pole contactor controlled by a single switch if you want all lights on at once all the time. I have an application where 3 circuits are controlled by a 3 pole (3 phase) contactor controlling 3 circuits of lighting on one switch - 12 potlights per circuit, 20 amp breakers. Originally 75 watt incandescents, currently running 9 watt LEDs. That applies to *outlets* (180VA per single/dual), not circuits that are used exclusively for hardwired lighting devices. As long as he doesn't tack on "one" convenience outlet he might get away with it. Local interpretations vary. This is the problem ^^^^^^^^^^^^^^^^^^^^^ In most areas, there is no way to appeal an inspector's ruling. So, if inspector misinterprets the Code (or, is "having a bad day"), you're stuck with his ruling. That is not really true but if the boss (AHJ) agrees you are stuck. In Florida the AHJ is the state, not the local BO. There are no "local codes". Just be sure you are right before you go through that process. At the end of the day, it may come down to what plan review said about your plans. Not "built to plan" is a slam dunk for the inspector.. OTOH in residential there is no 180va rule on receptacles and you would win that fight if some inspector tried to enforce it..I have never seen one try. It is a basic concept in residential load calculations that you do it by square footage, not receptacle count. The receptacle placement requirements pretty much assure you will have plenty you never use. |
#37
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
|
#38
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Mon, 28 Sep 2015 07:14:38 -0700 (PDT), Uncle Monster
wrote: If you're worried about safety, put up an LED emergency light in your basement hallway or stairwell. ^_^ Excellent idea for anyone. |
#39
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Monday, September 28, 2015 at 11:40:54 AM UTC-5, wrote:
On Mon, 28 Sep 2015 07:14:38 -0700 (PDT), Uncle Monster wrote: If you're worried about safety, put up an LED emergency light in your basement hallway or stairwell. ^_^ Excellent idea for anyone. I have a bunch of small UPS units which need new 12 volt batteries that I can get for $10 each. I plan to replace the batteries and connect one small ups to each LED table lamp in the house. I already have 3kw capacity with all the ups units around the house on all the computers and network gear. I'd be sitting at the computer working and the only way I knew there was a power failure was because of the clicking and beeping from the ups units. I've never bought a new ups for myself, everything I have is rescued and repaired. ^_^ [8~{} Uncle Backup Monster |
#40
Posted to alt.home.repair
|
|||
|
|||
Wiring&breaker for lighting circuit
On Mon, 28 Sep 2015 16:10:27 -0700 (PDT), Uncle Monster
wrote: On Monday, September 28, 2015 at 11:40:54 AM UTC-5, wrote: On Mon, 28 Sep 2015 07:14:38 -0700 (PDT), Uncle Monster wrote: If you're worried about safety, put up an LED emergency light in your basement hallway or stairwell. ^_^ Excellent idea for anyone. I have a bunch of small UPS units which need new 12 volt batteries that I can get for $10 each. I plan to replace the batteries and connect one small ups to each LED table lamp in the house. I already have 3kw capacity with all the ups units around the house on all the computers and network gear. I'd be sitting at the computer working and the only way I knew there was a power failure was because of the clicking and beeping from the ups units. I've never bought a new ups for myself, everything I have is rescued and repaired. ^_^ I still have one of the old school battery lights with the big incandescent floods When the battery dies I may look at a LED replacement although if I just put LED bulbs in there, it would last forever on the battery. I do have a switch in it that puts the lights in series if I want and makes the battery last a real long time. That is still plenty of walking around light. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Lighting circuit wiring at CU mcb | UK diy | |||
Wrong wiring for lighting circuit | UK diy | |||
Lighting ring off, circuit breaker still on | UK diy | |||
Circuit Breaker Wiring Question ? | Home Repair | |||
Odd lighting circuit wiring | UK diy |