I'm renovating my basement and have a pretty fundamental question about the
romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. |
#2
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() "mdb" wrote in message news ![]() I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. Wire costs a bit more, and its a bit harder to work with, but there is no downside other than that. I haven't used #14 in years. It has the added benefit of reducing voltage drop a little. Properly installed, GFCIs protect the entire circuit. |
#3
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
mdb wrote:
I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. Cutlet Hammer isn't my favorite brand, but it's certainly better than FP. As for 15 Amp circuits, while it theoretically saves you a couple dollars worth of copper, I wouldn't consider it worthwhile. 15 and 20 A circuit breakers cost the same as do all the other devices you'll be using so only the wire would be different. A GFCI circuit breaker will provide protection for everything connected to it. A GFCI receptacle will provide protection for everything connected downstream of it as well as what's plugged into it. A GFCI circuit breaker costs about 5X the price of a GFCI receptacle while providing the same protection. Generally it's best to simply insure that the first device on a given circuit is a GFCI receptacle. |
#4
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
mdb wrote:
I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. I use 15A for lighting circuits, and the occasional dedicated circuit where 15 is enough -- the wire is much easier to work with. I use 20A for all branch circuits. One GFCI can protect the whole circuit, or part of the circuit, or just itself. Depends how and where you wire it. Bob |
#5
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
mdb wrote:
I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. Hi, If you need for 20 Amp circuits for higher demand devices or whatever. There is nothng wrong overdoing anything but economics. Copper price is very high lately. Anything load on GFI breaker or outlet is all protected. |
#6
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() "mdb" wrote in message news ![]() Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? No extra hazard. Your electrician will prefer to work with #14 because it is easier (and therefore quicker) to deal with. Particularly if you might be running power tools, heaters or AC on those outlets, insist on #12. Also, does on GFI protect the entire circuit on which it is located Yes. Vaughn |
#7
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Hi mdb;
mdb wrote: I'm renovating my basement and have a pretty fundamental question about the Romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 Romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 Romex? I concur with the others. I would, and have, used 12-2 Romex 20A circuits on my circuits. (Well, possibly with the exception of the lighting circuits which will most likely be low current.) Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? Yes, the circuit breaker types do protect the entire circuit. As do the receptacle types if wired that way. My basement, like so many, sometimes gets wet when the outside drains are blocked. All the better to use GFIs. Several recomendations: 1. Install larger boxes than the minimum standard code recommends. They are roomier and easier to work with. 2. Install double or triple the number of outlets per wall than the minimum standard code recommends. You can thank me in the future. 3. Use the $1.50 or $2.00 receptacles instead of the cheap $.49 types. They are much better built and sturdier. 4. Don't use the simple push in terminals on the receptacles, use the old fashion screw terminals. The contact resistance is lower, I have measured this. OK, they do pass the UL code, but lower resistance has to be better. Have fun! Duane -- Home of the $35 Solar Tracker Receiver http://www.redrok.com/led3xassm.htm[*] Powered by \ \ \ //| Thermonuclear Solar Energy from the Sun / | Energy (the SUN) \ \ \ / / | Red Rock Energy \ \ / / | Duane C. Johnson Designer \ \ / \ / | 1825 Florence St Heliostat,Control,& Mounts | White Bear Lake, Minnesota === \ / \ | USA 55110-3364 === \ | (651)426-4766 use Courier New Font \ | (my email: address) \ | http://www.redrok.com (Web site) === |
#8
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
"Duane C. Johnson" wrote:
4. Don't use the simple push in terminals on the receptacles, use the old fashion screw terminals. The contact resistance is lower, I have measured this. OK, they do pass the UL code, but lower resistance has to be better. Second this, *do not* use the "push wire" type connections, they are the ones with the little release slots next to the holes. Do not however confuse "push wire" with "back wire" as they are not the same thing. With the better spec grade devices you will find many offer the "back wire" option which is a screw clamp type connection that works well and saves you the fuss of wrapping the wire around the screw. I've become a fan of these back wire clamp connections, particularly when using stranded wire pulled through conduit, where the back clamp eliminates the hassles of stray strands popping out from under the screw when you try to do a wrap around connection. |
#9
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() "mdb" wrote in message news ![]() I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. I agree with all the posts so far regarding this and here are my own reasons for using all 20A stuff: Less wiring voltage drop (already mentioned) and receptacles are usually built better and have thicker copper in them so they hold a plug tighter. Other than that I personally don't find #12 that much harder to work with but then again I have run 4/0 aluminum wire for a main service entrance before. The only rule I am aware of is that a single outlet 20amp circuit must have a 20 amp receptacle (multiple 15 amp receptacles are OK on a 20 amp circuit) but since I use 20 amp receptacles anyway for the better plug retention this is a moot point. |
#10
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() "Daniel Who Wants to Know" wrote in message Other than that I personally don't find #12 that much harder to work with but then again I have run 4/0 aluminum wire for a main service entrance before. Most amateurs try to bend the end of the wire around the screw to form a loop, thus making it difficult. I did the same until I watched an electrician strip the sheathing off about a foot of wire, then stripped the individual wire about 9" from the end and he used the 9" to easily wrap the wire around the screw, then cut off the excess. It was speed and ease over the cost of a foot of wasted wire. |
#11
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Edwin Pawlowski wrote:
"Daniel Who Wants to Know" wrote in message Other than that I personally don't find #12 that much harder to work with but then again I have run 4/0 aluminum wire for a main service entrance before. Most amateurs try to bend the end of the wire around the screw to form a loop, thus making it difficult. I did the same until I watched an electrician strip the sheathing off about a foot of wire, then stripped the individual wire about 9" from the end and he used the 9" to easily wrap the wire around the screw, then cut off the excess. It was speed and ease over the cost of a foot of wasted wire. I've never found any problem with just stripping the normal 3/4" off and using the pliers tip of the combo pliers/stripper/crimper/screw cutters to put the loop in it for hooking over the screw. It takes about a second since you already have the tool in your hand from stripping the wire. That said, as I noted in another post, I've become quite fond of the "back wire" clamp type connections found on many spec grade devices, not to be confused with the terrible "push wire" connections which should never have been approved. |
#12
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Just about all the electricians I know and work with use the hole
in the side of stripper that is made for making the loop that fits on the terminal screw. Insert tip of stripped copper - fold it over the side of the cutter - install on screw. The tips of the strippers can be used to close the loop tight. http://www.mygreenlee.com/Products/main.shtml?p_search=test&greenlee_category_id=100& Submit=Find&portalProcess_2=showGreenleeProductTem plate&upc_number=31889 -- ______________________________ Keep the whole world singing . . . . DanG (remove the sevens) "Edwin Pawlowski" wrote in message et... "Daniel Who Wants to Know" wrote in message Other than that I personally don't find #12 that much harder to work with but then again I have run 4/0 aluminum wire for a main service entrance before. Most amateurs try to bend the end of the wire around the screw to form a loop, thus making it difficult. I did the same until I watched an electrician strip the sheathing off about a foot of wire, then stripped the individual wire about 9" from the end and he used the 9" to easily wrap the wire around the screw, then cut off the excess. It was speed and ease over the cost of a foot of wasted wire. |
#13
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
I guess it's my job to disagree with most of the other posters. 15A
circuits let you work with 14 gauge wire. It is orders of magnitude easier to wire outlets and lights with 14 rather than 12. I use 12 only for workshops and kitchens where they might actually be needed. Most radios, TV's , and computers use less power today than even a decade ago. When was the last time you tripped a 15 A circuit breaker by overloading it? mike "mdb" wrote in message news ![]() I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. |
#14
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
On Sun, 23 Sep 2007 20:22:38 -0400, "Mike Payne"
wrote: I guess it's my job to disagree with most of the other posters. 15A circuits let you work with 14 gauge wire. It is orders of magnitude easier to wire outlets and lights with 14 rather than 12. I use 12 only for workshops and kitchens where they might actually be needed. That makes 2 of us. A friend tried to talk me into using #12 for everything (as he'd done at his own place). When I told him that the bulk of the long runs were one light per circuit, and that nearly all of them would be 12W CFs, he started the "what about the next guy" angle. Sheesh! If there's a next guy, and if he wants to use 150W bulbs, and if he thinks that'll stress the #14, then too bad. :-) Wayne |
#15
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() |
#16
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() |
#17
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
On Sun, 23 Sep 2007 15:53:10 -0500, Pete C. wrote:
"Duane C. Johnson" wrote: 4. Don't use the simple push in terminals on the receptacles, use the old fashion screw terminals. The contact resistance is lower, I have measured this. OK, they do pass the UL code, but lower resistance has to be better. Second this, *do not* use the "push wire" type connections, they are the ones with the little release slots next to the holes. Do not however confuse "push wire" with "back wire" as they are not the same thing. With the better spec grade devices you will find many offer the "back wire" option which is a screw clamp type connection that works well and OK, now I am confused. I recently did a basement (15 amp for the lighting circuits, and 20 amp for the power outlets). I fought for a while with the receptacles that need the 'hook' on the end of the wire to go around the screw. With the 12 gauge wire I was spending an inordinate amount of time swearing at the wire not doing as needed. So I instead used the wee hole on the back of the receptacle - I stripped the end of the wire, pushed it in the hole and then screwed it down with a screw from the side. Is that what you are calling the "back wire"? Cheers, Liam |
#18
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
mdb wrote:
I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. As others have said, there is no real reason to opt for 15A over 20A other than a minor saving in wire cost and the difficulty of working with the heavier wire. But since you are having an electrician do the job it doesn't seem as though either one of those will matter at all to you. But I can vouch for the difficulty factor if you are doing the work yourself. I recently added circuits and changed existing ones while doing a basement remodel and 12-2 wire is incredibly stiffer than 14-2 and pulling it through tight spaces above an existing finished ceiling really slowed me down. Even worse was pulling three 10-3 from the box at one side of the house to my workshop near the other end. That stuff felt like steel bar after a few hours of wrestling with it and if I hadn't been building a convenient soffit to cover ductwork for a goodly part of the run I might still be slaving away at it. Oh, and if you do go with the 20A circuits, make sure that the electrician doesn't cut corners by using lesser-rated receptacles and GFCIs. -- John McGaw [Knoxville, TN, USA] http://johnmcgaw.com |
#19
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
If you are a home builder and are building 50 homes, then you want to cut
costs as much as possible to maximize profit. So 15 amp outlets where not required and as few as possible is the rule. However if you are that same home builder building your own home, then 20 amp outlets everywhere and plenty of them (no 15 amp outlets)... "mdb" wrote in message I'm renovating my basement and have a pretty fundamental question about the romex cable I'll be running throughout the space for lights and wall jacks. I'm having my old Federal Pacific breaker panel (150 amps) replaced with a new Cutler Hammer 200 amp box. Have hired an electrician to do that work for me. But I wondered why I'd bother with 15 amp circuits (14-2 romex). Is there a reason not to simply make all three of the circuits I'll be creating for the new basement 20 amp circuits, using 12-2 romex? Or is there a fire/shock hazard caused by using the higher amperage circuit breakers on those standard circuits. Also, does on GFI protect the entire circuit on which it is located or do I need to install more? My basement, like so many, sometimes gets wet when the outside drains are blocked. |
#20
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() How is this substantially different from putting that 7A wire on a 15A circuit? The circuit breaker is there to protect the wiring in the house (i.e. the 12 or 14 ga wire), not to protect the appliance wire. Appliances typically have their own fuses, basic lamps being one exception. If that 18ga lamp cord gets damaged and shorts, the short circuit current is not limited to the 7A rating of the 18ga cord, and will be well over 20A, tripping the circuit breaker regardless of whether it is a 15A or 20A breaker. If it's in a bedroom, the new AFCI breakers will trip if the cord is damaged and arcing, but not a full short. I agree it is not a serious concern but it is the one argument I have heard about using 20a circuits for general lighting circuits. The key concern is overloads. Both 15 and 20 amp breakers will trip on direct shorts (if they are working properly). There is a tradeoff. 20A circuits have a convenience factor with the ability to delivery a considerable greater amount of power to a given situation. A typical example today would be a home office with multiple monitors, printers, computers and accessories in addition to whatever other routine loads (vacuum cleaners, electric heaters, etc.) are placed on the circuit. That extra 5A capability might just be the difference between adaquate wiring or a long-term headache of a constantly tripping circuit breaker. On the other hand, the subloads on a 20A circuit might (possible) pose a safety issue. The 18 gauge lamp cord example has already been mentioned. The danger being that if the 18 g. wire is overloaded just enough for the 18 g. wire to melt, but not enough to trip a 20A breaker. (In such a case, a 15A circuit breaker might be more likely to trip than a 20A breaker, but not necessarily). This is the reason that most power strips contain their own internal circuit breakers. 15A circuits were standardized during a time when there where few constant electrical loads and the loads were generally light. (a few lamps, a fan, etc.). These days, many people have home entertainment systems, hefty audio amplifiers, air conditioners, computers, big-screen plasma tv's, monitors, laser printers, and a whole lot of loads that could not be imagined 60, 70 or 80 years ago. In my opinion, this makes the argument favor the 20A circuits over 15A circuits, just for the added capacity and convenience. Beachcomber |
#22
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Liam Greenwood wrote:
On Sun, 23 Sep 2007 15:53:10 -0500, Pete C. wrote: "Duane C. Johnson" wrote: 4. Don't use the simple push in terminals on the receptacles, use the old fashion screw terminals. The contact resistance is lower, I have measured this. OK, they do pass the UL code, but lower resistance has to be better. Second this, *do not* use the "push wire" type connections, they are the ones with the little release slots next to the holes. Do not however confuse "push wire" with "back wire" as they are not the same thing. With the better spec grade devices you will find many offer the "back wire" option which is a screw clamp type connection that works well and OK, now I am confused. I recently did a basement (15 amp for the lighting circuits, and 20 amp for the power outlets). I fought for a while with the receptacles that need the 'hook' on the end of the wire to go around the screw. With the 12 gauge wire I was spending an inordinate amount of time swearing at the wire not doing as needed. So I instead used the wee hole on the back of the receptacle - I stripped the end of the wire, pushed it in the hole and then screwed it down with a screw from the side. Is that what you are calling the "back wire"? Cheers, Liam If it the wire from the back was clamped when you screwed it down, that is the good "back wire" type connection. Less prep time and good solid connections, particularly good for stranded wire. Nothing wrong with these connections at all. The "push wire" type have a hole with a flimsy little spring tab that grabs the wire and a little slot next to the hole where you insert a small screwdriver to release the tab if you want to remove the wire. These are the horrendous ones with tiny contact area, low contact pressure and frequent intermittent connections. |
#23
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
clare, at, snyder.on.ca wrote:
On Mon, 24 Sep 2007 16:10:22 GMT, (Beachcomber) wrote: The key concern is overloads. Both 15 and 20 amp breakers will trip on direct shorts (if they are working properly). There is a tradeoff. 20A circuits have a convenience factor with the ability to delivery a considerable greater amount of power to a given situation. A typical example today would be a home office with multiple monitors, printers, computers and accessories in addition to whatever other routine loads (vacuum cleaners, electric heaters, etc.) are placed on the circuit. The CORRECT solution to this situation is a split 15 amp circuit. 15 amps to the top outlet, 15 to the bottom. Done by using 14/3 cable and double breakers. The legal way is a "tied breaker" which means if you blow one, it trips the other as well. This is to prevent half of the box being live. Untied breakers are often used for this reason. Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. The alleged safety concerns of 18ga lamp cord on a 20A vs. 15A circuit are pretty much all bunk. The wire is rated at less than half of what even the 15A circuit is rated at, the 20A circuit introduces no additional risk. In both cases the circuit breaker properly protects what it is designed to protect - the wires in the walls. In neither case is the circuit breaker supposed to be the protection for the lamp cord and the liklihood of a fault developing in the lamp cord that would trip a 15A breaker, but not trip a 20A breaker is virtually non existent. |
#24
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
On Sep 23, 9:42 pm, "Pete C." wrote:
If it's in a bedroom, the new AFCI breakers will trip if the cord is damaged and arcing, but not a full short. I seem to recall seeing that the 2008 version of the NEC will require AFCIs on just about all of the 120Vac circuits, not just the ones for bedrooms. |
#25
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Pete C. wrote:
Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. No, this is not a hinky solution. It's called a splitwire or multiwire circuit, and has been the standard for kitchen counter receptacles in Canada for decades. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. Having every receptacle on its own circuit is ridiculous overkill. Even having two circuits per room is overkill for many rooms. That said, there are some rooms (kitchens, home theaters, home workshops) that would benefit from more circuits, and just about any room would benefit from more receptacles. Chris |
#26
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
In article , "Pete C." wrote:
Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. So? I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. You're not sure how it works, but you're sure it's a "hinky solution." :-) Actually, it's a perfectly fine solution. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. How is having two circuits available at alternating receptacles any improvement over having two circuits available at *every* receptacle? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#27
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Chris Friesen wrote:
Pete C. wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. No, this is not a hinky solution. It's called a splitwire or multiwire circuit, and has been the standard for kitchen counter receptacles in Canada for decades. I'm sure the world will get right on adopting those superior Canadian electrical standards... My kitchen has I believe four separate 20A circuits in it, and it was that way when I got here. I did have to replace the Federal Pacific Stab-Loc main panel incendiary device with a proper Square D QO panel however. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. Having every receptacle on its own circuit is ridiculous overkill. Even having two circuits per room is overkill for many rooms. That said, there are some rooms (kitchens, home theaters, home workshops) that would benefit from more circuits, and just about any room would benefit from more receptacles. My shop is wired with a "quad" every 6', with a "quad" being a 4" square box containing a 20A GFCI duplex receptacle paired with a 20A regular duplex receptacle. Every "quad" is an separate circuit. All wiring is in surface mounted conduit for ease of additions / changes. 240V receptacles are located where needed. The walls are type X fire code sheetrock. I'm pretty happy with it for a home shop. |
#28
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
daestrom wrote:
"Chris Friesen" wrote in message ... Pete C. wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. No, this is not a hinky solution. It's called a splitwire or multiwire circuit, and has been the standard for kitchen counter receptacles in Canada for decades. It's also quite common in office building environment. A variant of this is when you have 3-phase 208VAC available. You can run all three phases and a neutral in the conduit and use a different phase and neutral in each box. There are some issues with the size of the neutral, but I won't go into that here. He's talking about splitting poles / phases on the upper and lower halves of a duplex receptacle, not using a different phase in successive box locations. By using just one phase and neutral in each box, you avoid having higher than 120VAC available in one outlet. This can also be done with residential circuits, use alternating 'hots' in each successive box. So box 1, 3, 5, etc... is off of the first 'hot' and 2, 4, 6, etc... is off the second 'hot'. I'm good with cycling through the phases from box to box, but not splitting upper and lower of a duplex. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. Having every receptacle on its own circuit is ridiculous overkill. Even having two circuits per room is overkill for many rooms. That said, there are some rooms (kitchens, home theaters, home workshops) that would benefit from more circuits, and just about any room would benefit from more receptacles. There are many times I wish there were two receptacle boxes side by side in a 'quad-outlet' arrangement. Just because of the number of things to plug in, not the overall VA requirement. In a modern home office you might need a total of about 400 VA (about 1/3 of a 15A circuit capacity), but it's split into six or more 'plugs' (couple of watts for speakers, couple of watts for radio, couple of watts for cordless phone, 7-15 watts for CFL, rest for computer and printer). I wired my shop with all "quads", each one is a 20A GFCI receptacle paired with a 20A regular receptacle, and each "quad" is a separate circuit. The "quads" are spaced every 6'. The shop has a 125A 32 space Square D QO sub panel. Even my bedroom, with a reading lamp, wireless telephone, alarm clock for me, and an alarm clock for the Mrs., I end up needing an 'adapter' while the four other outlets in the bedroom are empty. Total load: about 11 watts (when the 7 watt CFL reading lamp is on). That's another issue, a zillion tiny loads in one spot. I have a power strip under my night stand for the table lamp, alarm clock, cordless phone charger, cell phone charger, bluetooth headset charger and weather radio (tornado alley). |
#29
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Doug Miller wrote:
In article , "Pete C." wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. So? I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. You're not sure how it works, but you're sure it's a "hinky solution." :-) Actually, it's a perfectly fine solution. It's hinky in my book, and I wouldn't wire it that way. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. How is having two circuits available at alternating receptacles any improvement over having two circuits available at *every* receptacle? It avoids having 240V on a device where most people expect only 120V. I'm fine with cycling through poles / phases box to box, but I don't like it within a single box in a residential application where joe bozo might mess with it. People blow things up with some regularity in industrial environments with three phase "wild leg" delta service, and in an industrial environment they're supposed to have a clue. Give joe bozo homeowner an unexpected red wire in the box and he's likely to blow stuff up too. I think it's an unnecessary risk in a residential environment. |
#30
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() |
#31
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() "Pete C." wrote in message ... Chris Friesen wrote: Pete C. wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. It's called an Edison circuit. It's used all over. There's nothing "hinky" about it. |
#32
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
On Mon, 24 Sep 2007 00:49:33 GMT, "Pete C."
wrote: wrote: On Sun, 23 Sep 2007 20:22:38 -0400, "Mike Payne" wrote: I guess it's my job to disagree with most of the other posters. 15A circuits let you work with 14 gauge wire. It is orders of magnitude easier to wire outlets and lights with 14 rather than 12. I use 12 only for workshops and kitchens where they might actually be needed. That makes 2 of us. A friend tried to talk me into using #12 for everything (as he'd done at his own place). When I told him that the bulk of the long runs were one light per circuit, and that nearly all of them would be 12W CFs, he started the "what about the next guy" angle. Sheesh! If there's a next guy, and if he wants to use 150W bulbs, and if he thinks that'll stress the #14, then too bad. :-) Wayne I have to disagree, I find the "workability" difference between 12 ga and 14 ga virtually unnoticeable. 2 ga copper is a bit of a pain to deal with, but much of anything below that is all the same to me. I don't agree, but even if there was zero workability difference, that wouldn't be a valid reason to spend even a nickel extra on a 12W circuit, or any low-power circuit. The only half-way reasonable argument I've heard for using 12 on low-power circuits is that it's more forgiving of bad workmanship. But anyone who needs that crutch shouldn't be doing electrical work anyway. Lots of people (including me) waste money when they don't need to, but we shouldn't encourage the newbs to do that. Ask any question on Usenet, and far more people will tell you to overdo things than underdo them. If a guy with a normal budget started building a home, and followed the Usenet consensus on how to do it, he'd probably run out of money before he finished the foundation. :-) Wayne |
#33
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
In article , "Pete C." wrote:
Doug Miller wrote: In article , "Pete C." wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. So? I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. You're not sure how it works, but you're sure it's a "hinky solution." :-) Actually, it's a perfectly fine solution. It's hinky in my book, and I wouldn't wire it that way. Fine, don't wire it that way -- but don't tell others it's a bad solution, just because you don't like/understand it. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. How is having two circuits available at alternating receptacles any improvement over having two circuits available at *every* receptacle? It avoids having 240V on a device where most people expect only 120V. So how, exactly, is that an issue? You can't plug a *single* device into both sockets of a duplex receptacle at once. Each socket has only 120V; that there is a 240V potential between the two hots is of no relevance whatever. I'm fine with cycling through poles / phases box to box, but I don't like it within a single box in a residential application where joe bozo might mess with it. People blow things up with some regularity in industrial environments with three phase "wild leg" delta service, and in an industrial environment they're supposed to have a clue. Give joe bozo homeowner an unexpected red wire in the box and he's likely to blow stuff up too. I think it's an unnecessary risk in a residential environment. I'd love to hear your explanation of how this will "blow stuff up." -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#34
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Pete C. wrote:
clare, at, snyder.on.ca wrote: On Mon, 24 Sep 2007 16:10:22 GMT, (Beachcomber) wrote: The key concern is overloads. Both 15 and 20 amp breakers will trip on direct shorts (if they are working properly). There is a tradeoff. 20A circuits have a convenience factor with the ability to delivery a considerable greater amount of power to a given situation. A typical example today would be a home office with multiple monitors, printers, computers and accessories in addition to whatever other routine loads (vacuum cleaners, electric heaters, etc.) are placed on the circuit. The CORRECT solution to this situation is a split 15 amp circuit. 15 amps to the top outlet, 15 to the bottom. Done by using 14/3 cable and double breakers. The legal way is a "tied breaker" which means if you blow one, it trips the other as well. This is to prevent half of the box being live. Untied breakers are often used for this reason. Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. I see people below disagree with "hinky". I don't know the term. However, as the "Joe Blow" guy who messes with outlets occasionally, I would be quite unhappily surprised to discover by accident that I could get 220 between some wires on the same outlet. Yikes. Also, I've got some house intercoms that apparently don't work right when plugged into "different legs" of the 240. On the other hand, if I were doing it to my own house, it won't be a surprise so who cares? (just my 2 cents, etc...) The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. |
#35
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Noozer wrote:
"Pete C." wrote in message ... Chris Friesen wrote: Pete C. wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. It's called an Edison circuit. It's used all over. There's nothing "hinky" about it. No, it is not called an Edison circuit, though it connects to one. Feeding separate 120V devices from a three wire feed is called an "Edison circuit", feeding upper and lower halves of a duplex receptacle from separate legs / phases is not in the definition of an "Edison circuit". |
#36
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
Doug Miller wrote:
In article , "Pete C." wrote: Doug Miller wrote: In article , "Pete C." wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. So? I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. You're not sure how it works, but you're sure it's a "hinky solution." :-) Actually, it's a perfectly fine solution. It's hinky in my book, and I wouldn't wire it that way. Fine, don't wire it that way -- but don't tell others it's a bad solution, just because you don't like/understand it. I understand it, and I recommend against using it in a residential environment for a good reason. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. How is having two circuits available at alternating receptacles any improvement over having two circuits available at *every* receptacle? It avoids having 240V on a device where most people expect only 120V. So how, exactly, is that an issue? You can't plug a *single* device into both sockets of a duplex receptacle at once. Each socket has only 120V; that there is a 240V potential between the two hots is of no relevance whatever. It has plenty of relevance. See below. I'm fine with cycling through poles / phases box to box, but I don't like it within a single box in a residential application where joe bozo might mess with it. People blow things up with some regularity in industrial environments with three phase "wild leg" delta service, and in an industrial environment they're supposed to have a clue. Give joe bozo homeowner an unexpected red wire in the box and he's likely to blow stuff up too. I think it's an unnecessary risk in a residential environment. I'd love to hear your explanation of how this will "blow stuff up." It has a decent potential to "blow stuff up", when Joe Bozo homeowner yanks on the vacuum cleaner cord, cracks the receptacle and goes to replace it. Joe Bozo homeowner who has no business being in the box to begin with and doesn't remember which wire went where. I've seen some pretty screwed up stuff like that and I see no good reason to add this risk when simply installing a separate box and outlet for the $2.50 will eliminate that risk. |
#37
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
On Mon, 24 Sep 2007 17:34:40 GMT, "Pete C."
wrote: clare, at, snyder.on.ca wrote: On Mon, 24 Sep 2007 16:10:22 GMT, (Beachcomber) wrote: The key concern is overloads. Both 15 and 20 amp breakers will trip on direct shorts (if they are working properly). There is a tradeoff. 20A circuits have a convenience factor with the ability to delivery a considerable greater amount of power to a given situation. A typical example today would be a home office with multiple monitors, printers, computers and accessories in addition to whatever other routine loads (vacuum cleaners, electric heaters, etc.) are placed on the circuit. The CORRECT solution to this situation is a split 15 amp circuit. 15 amps to the top outlet, 15 to the bottom. Done by using 14/3 cable and double breakers. The legal way is a "tied breaker" which means if you blow one, it trips the other as well. This is to prevent half of the box being live. Untied breakers are often used for this reason. Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. Not "hinkey" Required by code in kitchen countertop applications in Canada. The breakoff tabs are there for that purpose. You remove them. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. The alleged safety concerns of 18ga lamp cord on a 20A vs. 15A circuit are pretty much all bunk. The wire is rated at less than half of what even the 15A circuit is rated at, the 20A circuit introduces no additional risk. In both cases the circuit breaker properly protects what it is designed to protect - the wires in the walls. In neither case is the circuit breaker supposed to be the protection for the lamp cord and the liklihood of a fault developing in the lamp cord that would trip a 15A breaker, but not trip a 20A breaker is virtually non existent. -- Posted via a free Usenet account from http://www.teranews.com |
#38
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]() |
#39
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
On Mon, 24 Sep 2007 17:38:39 -0700, Roy Terry
wrote: Pete C. wrote: clare, at, snyder.on.ca wrote: On Mon, 24 Sep 2007 16:10:22 GMT, (Beachcomber) wrote: The key concern is overloads. Both 15 and 20 amp breakers will trip on direct shorts (if they are working properly). There is a tradeoff. 20A circuits have a convenience factor with the ability to delivery a considerable greater amount of power to a given situation. A typical example today would be a home office with multiple monitors, printers, computers and accessories in addition to whatever other routine loads (vacuum cleaners, electric heaters, etc.) are placed on the circuit. The CORRECT solution to this situation is a split 15 amp circuit. 15 amps to the top outlet, 15 to the bottom. Done by using 14/3 cable and double breakers. The legal way is a "tied breaker" which means if you blow one, it trips the other as well. This is to prevent half of the box being live. Untied breakers are often used for this reason. Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. I see people below disagree with "hinky". I don't know the term. However, as the "Joe Blow" guy who messes with outlets occasionally, I would be quite unhappily surprised to discover by accident that I could get 220 between some wires on the same outlet. Yikes. Also, I've got some house intercoms that apparently don't work right when plugged into "different legs" of the 240. On the other hand, if I were doing it to my own house, it won't be a surprise so who cares? (just my 2 cents, etc...) It's no surprise anyway if you know what you are doing. 3 colours in the box means their's 220 in there somewhere. Splits will have both red and black "lives" plus the white "nuetral" The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. -- Posted via a free Usenet account from http://www.teranews.com |
#40
![]()
Posted to alt.energy.homepower,alt.home.repair
|
|||
|
|||
![]()
On Tue, 25 Sep 2007 00:58:06 GMT, "Pete C."
wrote: Doug Miller wrote: In article , "Pete C." wrote: Doug Miller wrote: In article , "Pete C." wrote: Doing that will also put the two outlets on opposite poles / phases, giving 240V between the upper and lower hot connections. So? I'm not sure how that works with the ratings of the break off tabs on a duplex receptacle. At any rate a hinky solution at best. You're not sure how it works, but you're sure it's a "hinky solution." :-) Actually, it's a perfectly fine solution. It's hinky in my book, and I wouldn't wire it that way. Fine, don't wire it that way -- but don't tell others it's a bad solution, just because you don't like/understand it. I understand it, and I recommend against using it in a residential environment for a good reason. The truly correct solution is to just install more circuits in locations that need them. Basically instead of the all too common situation of every receptacle in a room being on a single 15A or 20A they should be individual circuits or at least two circuits alternated so any given location is within reach of both circuits. How is having two circuits available at alternating receptacles any improvement over having two circuits available at *every* receptacle? It avoids having 240V on a device where most people expect only 120V. So how, exactly, is that an issue? You can't plug a *single* device into both sockets of a duplex receptacle at once. Each socket has only 120V; that there is a 240V potential between the two hots is of no relevance whatever. It has plenty of relevance. See below. I'm fine with cycling through poles / phases box to box, but I don't like it within a single box in a residential application where joe bozo might mess with it. People blow things up with some regularity in industrial environments with three phase "wild leg" delta service, and in an industrial environment they're supposed to have a clue. Give joe bozo homeowner an unexpected red wire in the box and he's likely to blow stuff up too. I think it's an unnecessary risk in a residential environment. I'd love to hear your explanation of how this will "blow stuff up." It has a decent potential to "blow stuff up", when Joe Bozo homeowner yanks on the vacuum cleaner cord, cracks the receptacle and goes to replace it. Joe Bozo homeowner who has no business being in the box to begin with and doesn't remember which wire went where. I've seen some pretty screwed up stuff like that and I see no good reason to add this risk when simply installing a separate box and outlet for the $2.50 will eliminate that risk. That's not a problem with the solution, it's a problem with the problem - and Joe Bozo is the problem - split circuit or not he's got about a 90% chance of screwing something up. -- Posted via a free Usenet account from http://www.teranews.com |