Hi all
I am doing our bathroom up and we are having a cupboard with a couple sinks on top. The kids want to get electric tooth brushes so am wondering what my options are for providing power to the sink area for then to plug their toothbrushes in. I assume there is no way of putting a socket on the wall between the sinks? Would putting it in the cupboard below the sinks be an option? Also, I am fitting a spa bath. It has an IP55 box underneath to wire the pumps up so I plan to run the power from here to a socket somewhere. Can I put the socket for this in the cupboard too or should it be outside of the bathroom? Thanks in advance all Lee. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Bathroom shaver socket is the usual way - can be installed in Zone 2 over the basins if you like. http://electrical.theiet.org/wiring-...-701/index.cfm "Shaver supply units The minimum degree of protection for equipment installed in zones 1 and 2 is IPX4, or IPX5 where water jets are likely to be used for cleaning purposes. An exception to this requirement is a shaver supply unit complying with BS EN 61558-2-5 which, although it does not meet the requirements of IP4X, is permitted in zone 2 but must be located where direct spray from showers is unlikely. This type of shaver supply unit is the only type that is permitted in a bathroom or shower room." Thanks very much Tim. So this would imply that in the cupboard would be treated as zone 1 (likening it to under the bath but does not need tool to get to) so I couldn't have a socket in there for the spa bath but could have an IPx4 or greater switch [eg a light switch]) I could have the shaver sockets in the cupboard for the toothbrushes though? Also it doesn't seem to give a zone for the sink area. I have seen something that suggests best practice is 60 cm diameter above the basin should be classed as zone 1. Is this correct? thanks again Lee. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 03/09/2017 08:39, wrote:
Hi all I am doing our bathroom up and we are having a cupboard with a couple sinks on top. The kids want to get electric tooth brushes so am wondering what my options are for providing power to the sink area for then to plug their toothbrushes in. The normal solution is an isolated (i.e. transformer type) shaver socket. I assume there is no way of putting a socket on the wall between the sinks? Would putting it in the cupboard below the sinks be an option? Only if its 3m or more from the edge of zone 2! Sonly only very large bathrooms need apply. Also, I am fitting a spa bath. It has an IP55 box underneath to wire the pumps up so I plan to run the power from here to a socket somewhere. Can I put the socket for this in the cupboard too or should it be outside of the bathroom? If the space under the bath is not generally accessible (or only accessible using a tool) then it counts as "outside the zones" and you can install the socket (or probably more appropriately) a switched fused connection unit there. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#6
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 03/09/2017 10:47, wrote:
Bathroom shaver socket is the usual way - can be installed in Zone 2 over the basins if you like. http://electrical.theiet.org/wiring-...-701/index.cfm "Shaver supply units The minimum degree of protection for equipment installed in zones 1 and 2 is IPX4, or IPX5 where water jets are likely to be used for cleaning purposes. An exception to this requirement is a shaver supply unit complying with BS EN 61558-2-5 which, although it does not meet the requirements of IP4X, is permitted in zone 2 but must be located where direct spray from showers is unlikely. This type of shaver supply unit is the only type that is permitted in a bathroom or shower room." Thanks very much Tim. So this would imply that in the cupboard would be treated as zone 1 (likening it to under the bath but does not need tool to get to) so I couldn't have a socket in there for the spa bath but could have an IPx4 or greater switch [eg a light switch]) I could have the shaver sockets in the cupboard for the toothbrushes though? What zone is the cupboard in? If its outside the zones, then normal accessories (except sockets) are ok. Shaver sockets are ok even in zone 2 allowing for the limitations mentioned by Tim above. Also it doesn't seem to give a zone for the sink area. I have seen something that suggests best practice is 60 cm diameter above the basin should be classed as zone 1. Is this correct? The zones extend away from the bath or shower, the sink itself does not not create its own zone. There are a few general rules that apply like using appropriate fittings for the location etc and a bit of common sense; so positioning accessories where they won't be splashed etc. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#7
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
|
#8
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
|
#9
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Thanks all. Especially for the shaver socket tip. I had previously assumed the only difference between them and sockets was dual voltage
The shaver socket on the wall would work best but we have a small splashback and then huge mirror above the sinks so only place would be between the sinks and just off worktop level which seems a bit dodgy to me? So... Looks like best option is shaver sockets in the cupboard below the sinks. In terms of the spa bath then I guess running a feed to the cupboard and installing a ipx4 or better switch to switch it off (or maybe one of those dual pole things that we use to isolate the extractor fan) and then run this to the bath with a waterproof junction box under the bath for extra safety. Sound ok? So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? Thanks again for all your help Lee. |
#10
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 04/09/2017 08:31, wrote:
Thanks all. Especially for the shaver socket tip. I had previously assumed the only difference between them and sockets was dual voltage Note that there are two types of shaver socket. The transformer based ones that are suitable for bathrooms (and usually offer dual voltage) and the non transformer based ones that are not suitable for bathrooms. The shaver socket on the wall would work best but we have a small splashback and then huge mirror above the sinks so only place would be between the sinks and just off worktop level which seems a bit dodgy to me? So... Looks like best option is shaver sockets in the cupboard below the sinks. Another option is a shaver socket built into an over mirror based light fitting. In terms of the spa bath then I guess running a feed to the cupboard and installing a ipx4 or better switch to switch it off (or maybe one of those dual pole things that we use to isolate the extractor fan) and then run this to the bath with a waterproof junction box under the bath for extra safety. Sound ok? Yup you can have a remote switch for the bath feed if you want. You could place the switched fused connection unit in the cupboard, and then have that feed either a junction box or flex outlet the bath if you want. So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? I am not totally clear on exactly what setup you have here, so I will answer the more general questions... If the motor units are double insulated (has the double square logo[1]) then they do not need an earth connection. However you would normally wire the connection point such that one is available in case the motor were changed later and the new one needed one. If needs be, the earth connection can be made of in a spare non connected terminal block. [1] http://wiki.diyfaq.org.uk/index.php/...l_Glossary#1-9 If the motors do require an earth, then the earth of the circuit feeding them should be included into the supplementary bonding in the bathroom. The metal frame of the bath itself is typically not connected to anything outside of the room itself, and hence not capable of introducing any potential into the room. As a result it does not need including in the EQ bonding. See http://wiki.diyfaq.org.uk/index.php/...ng_and_Bonding 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? No that's fine. Note the comments above about including its earth in the bonding for the room. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#11
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
|
#12
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Sorry for the delayed response. Thanks very much both. Very informative. Wiki article explained a lot. I will have a look at the motors later today but now I know what I am looking for.
Thanks Lee. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Sorry for the delayed response. Thanks very much both. Very informative. Wiki article explained a lot. I will have a look at the motors later today but now I know what I am looking for.
Thanks Lee. |
#14
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Monday, 4 September 2017 10:22:49 UTC+1, John Rumm wrote:
On 04/09/2017 08:31, wrote: Thanks all. Especially for the shaver socket tip. I had previously assumed the only difference between them and sockets was dual voltage Note that there are two types of shaver socket. The transformer based ones that are suitable for bathrooms (and usually offer dual voltage) and the non transformer based ones that are not suitable for bathrooms. The shaver socket on the wall would work best but we have a small splashback and then huge mirror above the sinks so only place would be between the sinks and just off worktop level which seems a bit dodgy to me? So... Looks like best option is shaver sockets in the cupboard below the sinks. Another option is a shaver socket built into an over mirror based light fitting. In terms of the spa bath then I guess running a feed to the cupboard and installing a ipx4 or better switch to switch it off (or maybe one of those dual pole things that we use to isolate the extractor fan) and then run this to the bath with a waterproof junction box under the bath for extra safety. Sound ok? Yup you can have a remote switch for the bath feed if you want. You could place the switched fused connection unit in the cupboard, and then have that feed either a junction box or flex outlet the bath if you want. So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? I am not totally clear on exactly what setup you have here, so I will answer the more general questions... If the motor units are double insulated (has the double square logo[1]) then they do not need an earth connection. However you would normally wire the connection point such that one is available in case the motor were changed later and the new one needed one. If needs be, the earth connection can be made of in a spare non connected terminal block. [1] http://wiki.diyfaq.org.uk/index.php/...l_Glossary#1-9 If the motors do require an earth, then the earth of the circuit feeding them should be included into the supplementary bonding in the bathroom. The metal frame of the bath itself is typically not connected to anything outside of the room itself, and hence not capable of introducing any potential into the room. As a result it does not need including in the EQ bonding. See http://wiki.diyfaq.org.uk/index.php/...ng_and_Bonding 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? No that's fine. Note the comments above about including its earth in the bonding for the room. Connecting the bath frame to the motor frame does make it able to introduce 240v in case of fault. I would earth it & feed it from an RCD or include it in equipotential bonding. NT |
#15
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 09/09/2017 12:14, wrote:
On Monday, 4 September 2017 10:22:49 UTC+1, John Rumm wrote: On 04/09/2017 08:31, wrote: Thanks all. Especially for the shaver socket tip. I had previously assumed the only difference between them and sockets was dual voltage Note that there are two types of shaver socket. The transformer based ones that are suitable for bathrooms (and usually offer dual voltage) and the non transformer based ones that are not suitable for bathrooms. The shaver socket on the wall would work best but we have a small splashback and then huge mirror above the sinks so only place would be between the sinks and just off worktop level which seems a bit dodgy to me? So... Looks like best option is shaver sockets in the cupboard below the sinks. Another option is a shaver socket built into an over mirror based light fitting. In terms of the spa bath then I guess running a feed to the cupboard and installing a ipx4 or better switch to switch it off (or maybe one of those dual pole things that we use to isolate the extractor fan) and then run this to the bath with a waterproof junction box under the bath for extra safety. Sound ok? Yup you can have a remote switch for the bath feed if you want. You could place the switched fused connection unit in the cupboard, and then have that feed either a junction box or flex outlet the bath if you want. So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? I am not totally clear on exactly what setup you have here, so I will answer the more general questions... If the motor units are double insulated (has the double square logo[1]) then they do not need an earth connection. However you would normally wire the connection point such that one is available in case the motor were changed later and the new one needed one. If needs be, the earth connection can be made of in a spare non connected terminal block. [1] http://wiki.diyfaq.org.uk/index.php/...l_Glossary#1-9 If the motors do require an earth, then the earth of the circuit feeding them should be included into the supplementary bonding in the bathroom. The metal frame of the bath itself is typically not connected to anything outside of the room itself, and hence not capable of introducing any potential into the room. As a result it does not need including in the EQ bonding. See http://wiki.diyfaq.org.uk/index.php/...ng_and_Bonding 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? No that's fine. Note the comments above about including its earth in the bonding for the room. Connecting the bath frame to the motor frame does make it able to introduce 240v in case of fault. I would earth it & feed it from an RCD or include it in equipotential bonding. If the motor is class I, then its supply earth should be included in the bonding, and the motor casing itself does not need independent connection. If its class II, then its case is not an extraneous conductive path, and so bonding the bath would actually increase the risk rather than lower it. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#16
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Saturday, 9 September 2017 13:28:12 UTC+1, John Rumm wrote:
On 09/09/2017 12:14, tabbypurr wrote: On Monday, 4 September 2017 10:22:49 UTC+1, John Rumm wrote: On 04/09/2017 08:31, wrote: Thanks all. Especially for the shaver socket tip. I had previously assumed the only difference between them and sockets was dual voltage Note that there are two types of shaver socket. The transformer based ones that are suitable for bathrooms (and usually offer dual voltage) and the non transformer based ones that are not suitable for bathrooms. The shaver socket on the wall would work best but we have a small splashback and then huge mirror above the sinks so only place would be between the sinks and just off worktop level which seems a bit dodgy to me? So... Looks like best option is shaver sockets in the cupboard below the sinks. Another option is a shaver socket built into an over mirror based light fitting. In terms of the spa bath then I guess running a feed to the cupboard and installing a ipx4 or better switch to switch it off (or maybe one of those dual pole things that we use to isolate the extractor fan) and then run this to the bath with a waterproof junction box under the bath for extra safety. Sound ok? Yup you can have a remote switch for the bath feed if you want. You could place the switched fused connection unit in the cupboard, and then have that feed either a junction box or flex outlet the bath if you want. So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? I am not totally clear on exactly what setup you have here, so I will answer the more general questions... If the motor units are double insulated (has the double square logo[1]) then they do not need an earth connection. However you would normally wire the connection point such that one is available in case the motor were changed later and the new one needed one. If needs be, the earth connection can be made of in a spare non connected terminal block. [1] http://wiki.diyfaq.org.uk/index.php/...l_Glossary#1-9 If the motors do require an earth, then the earth of the circuit feeding them should be included into the supplementary bonding in the bathroom. The metal frame of the bath itself is typically not connected to anything outside of the room itself, and hence not capable of introducing any potential into the room. As a result it does not need including in the EQ bonding. See http://wiki.diyfaq.org.uk/index.php/...ng_and_Bonding 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? No that's fine. Note the comments above about including its earth in the bonding for the room. Connecting the bath frame to the motor frame does make it able to introduce 240v in case of fault. I would earth it & feed it from an RCD or include it in equipotential bonding. If the motor is class I, then its supply earth should be included in the bonding, and the motor casing itself does not need independent connection. If its class II, then its case is not an extraneous conductive path, Whether the motor can conduct to the bath or water depends on construction details. Class 2 certainly does not preclude it. Class 2 construction is no more a panacea than the other approaches. and so bonding the bath would actually increase the risk rather than lower it. bonding it to what? bathroom-wide equipotential bonding or the motor case? NT |
#17
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Hi all
I have had another look at the setup based on my new knowledge. There are 2 motors connected into a waterproof junction box. Looking at the junction box the incoming earth is connected to the earth going to both motors. There is then an earth wire going from the base of one to the metal framing which the legs are attached to. The motors have screws coming out of the bottom with thick rubber washers on. These screws then fed through a metal board where they are bolted in place. This board is attached to the metal framing.. The motors have a label on them but no mention of class 1 or 2. So... Judging from the about it sounds like I should be fine with wiring the mains into the junction box as normal. With the frame bonded to one motor and it in turn seems to be connected to the incoming earth. On the junction box it has a label from manufacturers saying it is 2.1kW and needs a 16a fuse. Is this ok to be on the ring main I plan to extend and located as a switched fused inside the cupboard. Thanks again all Lee. |
#18
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Sunday, 10 September 2017 15:47:33 UTC+1, wrote:
Hi all I have had another look at the setup based on my new knowledge. There are 2 motors connected into a waterproof junction box. Looking at the junction box the incoming earth is connected to the earth going to both motors. There is then an earth wire going from the base of one to the metal framing which the legs are attached to. The motors have screws coming out of the bottom with thick rubber washers on. These screws then fed through a metal board where they are bolted in place. This board is attached to the metal framing. The motors have a label on them but no mention of class 1 or 2. So... Judging from the about it sounds like I should be fine with wiring the mains into the junction box as normal. With the frame bonded to one motor and it in turn seems to be connected to the incoming earth. On the junction box it has a label from manufacturers saying it is 2.1kW and needs a 16a fuse. Is this ok to be on the ring main I plan to extend and located as a switched fused inside the cupboard. Thanks again all Lee. So the pumps aren't class 2, and need treating as class 1. So you need either RCD or equipotential bonding. NT |
#19
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 09/09/2017 18:11, wrote:
So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? I am not totally clear on exactly what setup you have here, so I will answer the more general questions... If the motor units are double insulated (has the double square logo[1]) then they do not need an earth connection. However you would normally wire the connection point such that one is available in case the motor were changed later and the new one needed one. If needs be, the earth connection can be made of in a spare non connected terminal block. [1] http://wiki.diyfaq.org.uk/index.php/...l_Glossary#1-9 If the motors do require an earth, then the earth of the circuit feeding them should be included into the supplementary bonding in the bathroom. The metal frame of the bath itself is typically not connected to anything outside of the room itself, and hence not capable of introducing any potential into the room. As a result it does not need including in the EQ bonding. See http://wiki.diyfaq.org.uk/index.php/...ng_and_Bonding 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? No that's fine. Note the comments above about including its earth in the bonding for the room. Connecting the bath frame to the motor frame does make it able to introduce 240v in case of fault. I would earth it & feed it from an RCD or include it in equipotential bonding. If the motor is class I, then its supply earth should be included in the bonding, and the motor casing itself does not need independent connection. If its class II, then its case is not an extraneous conductive path, Whether the motor can conduct to the bath or water depends on construction details. Indeed. Class 2 certainly does not preclude it. Class 2 construction is no more a panacea than the other approaches Erm, no. and so bonding the bath would actually increase the risk rather than lower it. bonding it to what? bathroom-wide equipotential bonding or the motor case? If the motor were class I, then they would be functionally equivalent. If the motor is class II, then bonding the bath simply means its now an extraneous conductive path where previously it was not. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#20
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Sunday, 10 September 2017 23:52:29 UTC+1, John Rumm wrote:
On 09/09/2017 18:11, tabbypurr wrote: So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? I am not totally clear on exactly what setup you have here, so I will answer the more general questions... If the motor units are double insulated (has the double square logo[1]) then they do not need an earth connection. However you would normally wire the connection point such that one is available in case the motor were changed later and the new one needed one. If needs be, the earth connection can be made of in a spare non connected terminal block. [1] http://wiki.diyfaq.org.uk/index.php/...l_Glossary#1-9 If the motors do require an earth, then the earth of the circuit feeding them should be included into the supplementary bonding in the bathroom. The metal frame of the bath itself is typically not connected to anything outside of the room itself, and hence not capable of introducing any potential into the room. As a result it does not need including in the EQ bonding. See http://wiki.diyfaq.org.uk/index.php/...ng_and_Bonding 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? No that's fine. Note the comments above about including its earth in the bonding for the room. Connecting the bath frame to the motor frame does make it able to introduce 240v in case of fault. I would earth it & feed it from an RCD or include it in equipotential bonding. If the motor is class I, then its supply earth should be included in the bonding, and the motor casing itself does not need independent connection. If its class II, then its case is not an extraneous conductive path, Whether the motor can conduct to the bath or water depends on construction details. Indeed. Class 2 certainly does not preclude it. Class 2 construction is no more a panacea than the other approaches Erm, no. and so bonding the bath would actually increase the risk rather than lower it. bonding it to what? bathroom-wide equipotential bonding or the motor case? If the motor were class I, then they would be functionally equivalent. If the motor is class II, then bonding the bath simply means its now an extraneous conductive path where previously it was not. you certainly know how to be vague NT |
#21
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 10/09/2017 15:47, wrote:
Hi all I have had another look at the setup based on my new knowledge. There are 2 motors connected into a waterproof junction box. Looking at the junction box the incoming earth is connected to the earth going to both motors. There is then an earth wire going from the base of one to the metal framing which the legs are attached to. The motors have screws coming out of the bottom with thick rubber washers on. These screws then fed through a metal board where they are bolted in place. This board is attached to the metal framing. The motors have a label on them but no mention of class 1 or 2. If the motors have an earth connection in their flex, then they are class I. (generally if its metal cased and not marked as class II then its best to assume class I) So... Judging from the about it sounds like I should be fine with wiring the mains into the junction box as normal. With the frame bonded to one motor and it in turn seems to be connected to the incoming earth. So long as the earth of the circuit feeding the motors is included in the rooms EQ bonding, then you don't need anything else. The protective conductor feeding the motor itself will serve dual purpose as both earth and bonding connection. On the junction box it has a label from manufacturers saying it is 2.1kW and needs a 16a fuse. Is this ok to be on the ring main I plan to extend and located as a switched fused inside the cupboard. Its likely its an induction motor, and will have a high inrush current. Hence the need for a higher rating of fuse than nominal[1] 10A that the 2.1kW rating would suggest. It might be worth tracking down the manual for the motor if you can to see if it actually specifies that the motor *must* have additional protection from a 16A device, or whether it is just highlighting that protection with a 13A fuse in a SFCU etc unlikely to hack it due to the high inrush. If it specifies that it must be protected at 16A device, then it will make your task a little more interesting if you want to feed it from a spur on a 32A ring circuit. You would then probably have to use a MCB, or a HRC cartridge fuse in a suitable enclosure instead. [1] Induction motors also tend to have non unity power factors, which can increase the actual maximum current drawn. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#22
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 11/09/2017 00:01, wrote:
On Sunday, 10 September 2017 23:52:29 UTC+1, John Rumm wrote: On 09/09/2017 18:11, tabbypurr wrote: So... Last 2 questions. 1. The bath has the metal framing connected to one of the motors via an earth lead. However the earth from the mains connection doesn't seem to be connected to it. I would have expected to see an earth coming out of the junction box to connect to the frame. Any thoughts? I am not totally clear on exactly what setup you have here, so I will answer the more general questions... If the motor units are double insulated (has the double square logo[1]) then they do not need an earth connection. However you would normally wire the connection point such that one is available in case the motor were changed later and the new one needed one. If needs be, the earth connection can be made of in a spare non connected terminal block. [1] http://wiki.diyfaq.org.uk/index.php/...l_Glossary#1-9 If the motors do require an earth, then the earth of the circuit feeding them should be included into the supplementary bonding in the bathroom. The metal frame of the bath itself is typically not connected to anything outside of the room itself, and hence not capable of introducing any potential into the room. As a result it does not need including in the EQ bonding. See http://wiki.diyfaq.org.uk/index.php/...ng_and_Bonding 2. I plan to cut into the upstairs ring main to feed this bathroom. Not a spur buy essentially extending the ring. Any issues with this? No that's fine. Note the comments above about including its earth in the bonding for the room. Connecting the bath frame to the motor frame does make it able to introduce 240v in case of fault. I would earth it & feed it from an RCD or include it in equipotential bonding. If the motor is class I, then its supply earth should be included in the bonding, and the motor casing itself does not need independent connection. If its class II, then its case is not an extraneous conductive path, Whether the motor can conduct to the bath or water depends on construction details. Indeed. Class 2 certainly does not preclude it. Class 2 construction is no more a panacea than the other approaches Erm, no. and so bonding the bath would actually increase the risk rather than lower it. bonding it to what? bathroom-wide equipotential bonding or the motor case? If the motor were class I, then they would be functionally equivalent. If the motor is class II, then bonding the bath simply means its now an extraneous conductive path where previously it was not. you certainly know how to be vague I am sure Lee will ask if he is unsure. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#23
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Sunday, September 3, 2017 at 8:39:24 AM UTC+1, wrote:
Hi all I am doing our bathroom up and we are having a cupboard with a couple sinks on top. The kids want to get electric tooth brushes so am wondering what my options are for providing power to the sink area for then to plug their toothbrushes in. I assume there is no way of putting a socket on the wall between the sinks? Would putting it in the cupboard below the sinks be an option? Also, I am fitting a spa bath. It has an IP55 box underneath to wire the pumps up so I plan to run the power from here to a socket somewhere. Can I put the socket for this in the cupboard too or should it be outside of the bathroom? Thanks in advance all Lee. Just get the cheap electric tooth brushes which use standard batteries. You'll thank me when the batteries in the uber expensive rechargeable toothbrushes die 5 minutes after the warranty is up. |
#24
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
|
#25
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Thanks John.
There is no other bonding in the bathroom as all plumbing is plastic as it the bath. Rather than a spur, I was going to break into ring on that floor and extend it to the bathroom. It is a bit of a pain as there isn't a straight forward way (that I can think of) to do it other than go to the nearest socket (bedroom across the landing) and split it there. Rather than have a junction box I was going to add an extra socket besides it to take feed back from the bathroom to rejoin the ring (if you see what I mean). Will try and track down the installation manual for the bath and revert. thanks again Lee. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Monday, 11 September 2017 17:51:11 UTC+1, wrote:
Thanks John. There is no other bonding in the bathroom as all plumbing is plastic as it the bath. Rather than a spur, I was going to break into ring on that floor and extend it to the bathroom. It is a bit of a pain as there isn't a straight forward way (that I can think of) to do it other than go to the nearest socket (bedroom across the landing) and split it there. Rather than have a junction box I was going to add an extra socket besides it to take feed back from the bathroom to rejoin the ring (if you see what I mean). Will try and track down the installation manual for the bath and revert. thanks again Lee. OK - I have managed to find an installation manual online but the electrical piece seems generic across the Duravit range. It says the following... Circuit Breaker - In = 16A RCCB I delta = 30 mA Then for the instructions it says.... Lay a fixed feed cable for power supply: - install seperate circuit breaker and residual current circuit breaker (RCCB) upstream - connect all pole disconnector mains switch upstream located out-side specified protection zones (0-2) - leave 3000mm of feed cable exposed Lay equipotential bonding cables: - leave 3000mm of cable exposed The diagram shows zone 0 in bath; zone 1 above bath and zone 2 extends from bath 600mm So... looking around the web I guess I would need a 16a version of one of these and locate it in the cupboard under the sinks? Assuming it is dual pole? http://www.screwfix.com/p/bg-13a-swi...-rcd-fcu/20523 Any idea what it means by leave 3m of cable / feed cable exposed? thanks Lee. |
#27
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Mon, 11 Sep 2017 03:50:52 -0700 (PDT), "
wrote: On Sunday, September 3, 2017 at 8:39:24 AM UTC+1, wrote: Hi all I am doing our bathroom up and we are having a cupboard with a couple sinks on top. The kids want to get electric tooth brushes so am wondering what my options are for providing power to the sink area for then to plug their toothbrushes in. I assume there is no way of putting a socket on the wall between the sinks? Would putting it in the cupboard below the sinks be an option? Also, I am fitting a spa bath. It has an IP55 box underneath to wire the pumps up so I plan to run the power from here to a socket somewhere. Can I put the socket for this in the cupboard too or should it be outside of the bathroom? Thanks in advance all Lee. Just get the cheap electric tooth brushes which use standard batteries. You'll thank me when the batteries in the uber expensive rechargeable toothbrushes die 5 minutes after the warranty is up. The latest generation of Oral B products contain lithium ion batteries. Not before time - I never understood why I was paying a premium price for an appliance containing an obsolete battery. |
#28
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 11/09/17 18:31, Scott wrote:
I never understood why I was paying a premium price for an appliance containing an obsolete battery. Profit |
#29
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Monday, 11 September 2017 11:50:55 UTC+1, wrote:
Just get the cheap electric tooth brushes which use standard batteries. You'll thank me when the batteries in the uber expensive rechargeable toothbrushes die 5 minutes after the warranty is up. Did that years ago. It didn't last long, the waterproof seal wasn't really waterproof. ISTR there being youtube vids on how to open sealed Oral-Bs & replace the battery. NT |
#30
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 11/09/2017 18:26, wrote:
On Monday, 11 September 2017 17:51:11 UTC+1, wrote: Thanks John. There is no other bonding in the bathroom as all plumbing is plastic as it the bath. If all the circuits that enter the room are protected with a 30mA trip RCD (and the house main EQ bonding is to spec) then you could take advantage of the 17th edition relaxation that allows EQ bonding to be omitted in these cases. Rather than a spur, I was going to break into ring on that floor and extend it to the bathroom. It is a bit of a pain as there isn't a straight forward way (that I can think of) to do it other than go to the nearest socket (bedroom across the landing) and split it there. Rather than have a junction box I was going to add an extra socket besides it to take feed back from the bathroom to rejoin the ring (if you see what I mean). IME Its possible to use crimps or wago terminals in the back of a socket box to join into a ring if you want - so it can all be done at one double socket location. http://wiki.diyfaq.org.uk/index.php/...ket_extensions Having said that, you may be better off putting your additional switched protection adjacent to the socket and running a spur from that to the spa (there is no real advantage to the ring being extended to and from the spa) (is it just a pump or a heater as well? 2+ kW seems like a bit much for just a pump) Will try and track down the installation manual for the bath and revert. OK - I have managed to find an installation manual online but the electrical piece seems generic across the Duravit range. It says the following... Circuit Breaker - In = 16A RCCB I delta = 30 mA Then for the instructions it says.... Lay a fixed feed cable for power supply: - install seperate circuit breaker and residual current circuit breaker (RCCB) upstream - Does your source circuit already include a RCD? (if so, no need for another if the trip threshold on the existing one is = 30mA) connect all pole disconnector mains switch upstream located out-side specified protection zones (0-2) - leave 3000mm of feed cable exposed Under a bath also counts as outside of the zones if you need a tool to access the space. Lay equipotential bonding cables: - leave 3000mm of cable exposed The diagram shows zone 0 in bath; zone 1 above bath and zone 2 extends from bath 600mm So... looking around the web I guess I would need a 16a version of one of these and locate it in the cupboard under the sinks? Assuming it is dual pole? http://www.screwfix.com/p/bg-13a-swi...-rcd-fcu/20523 As I mentioned before, its the "16A version" that makes it more difficult since anything designed to be protected by a BS1361 fuse is not going to work in this situation if you read the manufacturers spec to the letter. (the reality is a 13A fuse is probably more than adequate[1], but they are likely attempting to make their instructions applicable Europe wide where 16A circuits are common and UK style fusing close to appliances is not). Any idea what it means by leave 3m of cable / feed cable exposed? No, that seems a bit odd. [1] Unless all that 2.1kW rally is just down to one big motor, where the inrush could take out a 13A fuse. (in which case a C10 MCB would probably be a good match) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#31
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
|
#32
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Thanks both
The bath has 2 pumps and one includes a heater to keep the water warm during operation. |
#33
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Wednesday, 13 September 2017 07:55:07 UTC+1, wrote:
Thanks both The bath has 2 pumps and one includes a heater to keep the water warm during operation. Hi All, I have now heard back from Durait. Looks like 13amp will be fine thankfully. So from the above, I think I can now use one of these for the bath https://www.toolstation.com/shop/Ele...r+White/p45636 and put it in the cupboards below the sinks. I seem to recall from above that I needn't break the ring and just have this (and the 2 shaver sockets) as a spur from a double socket in an adjacent room. Is it worth wiring the 2 shaver sockets off this RCB too or just have a junction box there (IP4x in case) and wire all 3 off the feed? Thanks again all Lee. |
#34
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 21/09/2017 20:15, wrote:
On Wednesday, 13 September 2017 07:55:07 UTC+1, wrote: Thanks both The bath has 2 pumps and one includes a heater to keep the water warm during operation. Hi All, I have now heard back from Durait. Looks like 13amp will be fine thankfully. Good, I had a feeling that might be the case. So from the above, I think I can now use one of these for the bath https://www.toolstation.com/shop/Ele...r+White/p45636 Sorry if I missed it, but did you mention if the socket circuit already has RCD protection in the CU? and put it in the cupboards below the sinks. I seem to recall from above that I needn't break the ring and just have this (and the 2 shaver sockets) as a spur from a double socket in an adjacent room. Yup pretty much. Is it worth wiring the 2 shaver sockets off this RCB too or just have a junction box there (IP4x in case) and wire all 3 off the feed? Well you could do either... however doing the former treats the whole installation as if you had a fused spur from the ring. Hence you can add any number of things downstream of the spur. (Going with the second option means you are treating the feed from the circuit as an unfused spur, and hence would normally need to keep in mind the total load you could potentially place on the single spur cable. In this case however your ~2kW load plus to shaver sockets will be well below any load you would need to worry about) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus |
#35
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Thanks John
I checked the consumer unit. There is a bank of MCBs and then a RCCB then another bank and another RCCB. I assume the RCCB protects the bank of MCBs to the left of it. Is that correct? If so, the bank of MCBs to the left are... 2xB6 2xB16 2xB32 1xB40 The RCCB is 80A 30mA. 80a seems a bit odd given the total of the MCBs is much more. Unless it only protects the nearest 1 or 2 MCBs? Thanks again for your help Lee. |
#36
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Thanks John
I checked the consumer unit. There is a bank of MCBs and then a RCCB then another bank and another RCCB. I assume the RCCB protects the bank of MCBs to the left of it. Is that correct? If so, the bank of MCBs to the left are... 2xB6 2xB16 2xB32 1xB40 The RCCB is 80A 30mA. 80a seems a bit odd given the total of the MCBs is much more. Unless it only protects the nearest 1 or 2 MCBs? Thanks again for your help Lee. |
#37
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On Sunday, 24 September 2017 08:36:44 UTC+1, wrote:
Thanks John I checked the consumer unit. There is a bank of MCBs and then a RCCB then another bank and another RCCB. I assume the RCCB protects the bank of MCBs to the left of it. Is that correct? If so, the bank of MCBs to the left are... 2xB6 2xB16 2xB32 1xB40 The RCCB is 80A 30mA. 80a seems a bit odd given the total of the MCBs is much more. Unless it only protects the nearest 1 or 2 MCBs? Thanks again for your help Lee. diversity NT |
#38
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 24/09/2017 08:36, wrote:
Thanks John I checked the consumer unit. There is a bank of MCBs and then a RCCB then another bank and another RCCB. That sounds like a typical 17th edition style split load CU, where you have all circuits protected by RCDs, but they are spread out over a pair of devices, so you maintain some discrimination. For example a layout like: http://wiki.diyfaq.org.uk/index.php/...th5-5Fixed.JPG I assume the RCCB protects the bank of MCBs to the left of it. Is that correct? Generally that seems to be the most common arrangement - although it does depend on the brand of CU. Some place the main switch or RCD on the left of the protected block of devices. If so, the bank of MCBs to the left are... 2xB6 2xB16 2xB32 1xB40 It sounds like that there are no non RCD protected circuits (as you might find with a so called "high integrity" CU with provision for some non protected circuits that can be fitted with MCBs or RCBOs: http://wiki.diyfaq.org.uk/index.php/...hIntegrity.JPG The implication of this is that you *do not* need any further RCD protection for the spa pumps / heaters. The RCCB is 80A 30mA. 80a seems a bit odd given the total of the MCBs is much more. Unless it only protects the nearest 1 or 2 MCBs? No it will protect all of them. Finding that the maximum load on all circuits when summed is greater than the rating of some upstream device is not uncommon, but allowances can be made for diversity in the loads. More detail he http://wiki.diyfaq.org.uk/index.php/Diversity -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#39
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
Thanks very much John. Great explanation. Yes the picture us very similar to my arrangement.
I was thinking... Adding the RCD although an extra £10 more than a switched fused spur I thought it would give extra protection so might as well do the RCD one. Am I fooling myself Thanks again. Lee. |
#40
Posted to uk.d-i-y
|
|||
|
|||
Bathroom wiring questions
On 24/09/2017 15:06, wrote:
Thanks very much John. Great explanation. Yes the picture us very similar to my arrangement. I was thinking... Adding the RCD although an extra £10 more than a switched fused spur I thought it would give extra protection so might as well do the RCD one. Am I fooling myself Probably... One might argue in the relatively rare case of one of the RCDs failing (that manifests as a non trip in a situation where it should have), then having a second one will serve as a backup. For all other (more typical) situations it serves no real benefit. (and should you get a trip for any reason, you potentially have devices to reset since you will get no discrimination between the cascaded devices) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
What makes a bathroom a bathroom? | UK diy | |||
Rohl faucet bathroom-----question.. have deep sink bathroom--push updain doesnt open enough.. | Home Repair | |||
Two bathroom doors in one bathroom | Home Repair | |||
Getting An Enclosed Trailer...Questions, Questions, Questions | Metalworking | |||
Non-bathroom light in bathroom | UK diy |