#201
|
|||
|
|||
Owain wrote:
Jim Michaels wrote: Two 16amp radials equal one 32amp ring. House with 3 rings versus one with 6 (or more) radials. How do they really differ in capacity? Because you can put three 10A appliances on one 32A ring in *any* socket combination. You can only put one on each 16A radial, so two radials will only feed two such appliances, *one on each radial*. If you try plugging both into the same radial you will overload the circuit. Hence you have the stupid situation of having to think "I can't plug this in here but I can plug it in over there". Yes, and if I want a double socket for my kettle and toaster it would require two radials to the same location. At which point all the wiring for a ring is in place. -- David Clark $message_body_include ="PLES RING IF AN RNSR IS REQIRD" |
#202
|
|||
|
|||
On Mon, 08 Aug 2005 00:01:16 -0500, Jim Michaels
wrote: On Sun, 07 Aug 2005 13:40:46 +0100, John Rumm wrote: Jim Michaels wrote: So if I fit a BS1363 plug cap with a 32amp fuse and 4mm lead it would be acceptable to power an arc welder (or other device) drawing 30amps from any ring that is handy? No, the plug itself is only rated for 13A. As is the socket. And nobody sees a problem with 13a sockets on a 32amp circuit? No, because they are engineered to way above 13A in terms of the contacts. The 13A refers to the maximum current taken through a plug via the fuse. They are of a substantially higher quality as well - $10 and up being typical rather than 99c. -- ..andy To email, substitute .nospam with .gl |
#203
|
|||
|
|||
Jim Michaels wrote:
No of course it wouldn't and you know it; it is presenting an unacceptable point load. Ring circuits are *designed* around certain parameters all of which work *together* So two 3kW kettles in a double socket is not acceptable? It's not desirable, but in a domestic environment (and I've lived in shared houses with two kettles, to cater for the home-from-work tea stampede) they're only going to be used occasionally. In a commercial kitchen (which could include a house doing B&B) more appropriate provision should be made. Ring circuits should only be installed where they are *suitable for the load*. Owain |
#204
|
|||
|
|||
Jim Michaels wrote:
And nobody sees a problem with 13a sockets on a 32amp circuit? No more than a 100A service fuse on a ????A ring main off a substation. Owain |
#205
|
|||
|
|||
In article ,
Jim Michaels writes: So two 3kW kettles in a double socket is not acceptable? People don't generally have two kettles in the same place, but it would be no problem given a 3kW kettle can't be on for long anyway. -- Andrew Gabriel |
#206
|
|||
|
|||
In article ,
Jim Michaels writes: And nobody sees a problem with 13a sockets on a 32amp circuit? No, they're fused at 13A max. I don't have a copy of BS1363, but I think manufacturers are required to show their 13A plugs and sockets will run at 26A for a hour without any problems, and are then required to overload test them to destruction, and to show they don't fail in grossly unsafe ways. The test requirements for BS1363 products are one of the most onerous of any test procedure. -- Andrew Gabriel |
#207
|
|||
|
|||
Jim Michaels wrote:
And nobody sees a problem with 13a sockets on a 32amp circuit? No. They are fused at (a maximum) of 13A anyway. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#208
|
|||
|
|||
Jim Michaels wrote:
So two 3kW kettles in a double socket is not acceptable? It is not ideal, but in a domestic situation you can generally ignore such loads in your diversity calculations since they are such short duration. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#209
|
|||
|
|||
In article , Andrew
Gabriel wrote: I don't have a copy of BS1363, but I think manufacturers are required to show their 13A plugs and sockets will run at 26A for a hour without any problems, When you look at American or Australian plugs with a fraction of the metal in the pins I wouldn't expect any. -- Tony Bryer SDA UK 'Software to build on' http://www.sda.co.uk Free SEDBUK boiler database browser http://www.sda.co.uk/qsedbuk.htm [Latest version QSEDBUK 1.10 released 4 April 2005] |
#210
|
|||
|
|||
In article ,
Jim Michaels wrote: And nobody sees a problem with 13a sockets on a 32amp circuit? In practice few sockets round the house are likely to be loaded to anything near this, since heavy *continuous* loads like heating ain't normally done off the ring main. The likely sockets which will have this sort of loading - but not *continuous* - are in the kitchen, where there will usually be a separate ring. And the wiring for the average ring is capable of carrying more than 32 amps anyway. -- *Before they invented drawing boards, what did they go back to? Dave Plowman London SW To e-mail, change noise into sound. |
#211
|
|||
|
|||
In article ,
Owain wrote: So two 3kW kettles in a double socket is not acceptable? It's not desirable, but in a domestic environment (and I've lived in shared houses with two kettles, to cater for the home-from-work tea stampede) they're only going to be used occasionally. In a commercial kitchen (which could include a house doing B&B) more appropriate provision should be made. Ring circuits should only be installed where they are *suitable for the load*. Yup. Commercial installations where continuous loads can be accurately calculated are likely to use radial circuits - even if fitted with 13 amp outlets. If you intended heating every room in a house with a fan heater etc on all the time to give 'central' heating, a ring wouldn't be appropriate. Load diversity is the key, and it's applied to things normally fed via a radial in the home like cookers and hobs too. -- *If I throw a stick, will you leave? Dave Plowman London SW To e-mail, change noise into sound. |
#212
|
|||
|
|||
In article ,
Jim Michaels wrote: So if I fit a BS1363 plug cap with a 32amp fuse and 4mm lead it would be acceptable to power an arc welder (or other device) drawing 30amps from any ring that is handy? Either the socket is adequate for the 32amp circuit it is on or it isn't. Relying on whatever is plugged into it to not draw too much is far from idiot proof, it isn't even non expert proof. Are you trying to say that all sockets on radials are capable of carrying the full rating of that radial as a continuous load? Because this doesn't seem to be the case in most counties. Anyone want to buy non-fused BS1363 style plugs? They've got nothing to do with BS1363, and have no type approval anywhere. -- *When companies ship Styrofoam, what do they pack it in? * Dave Plowman London SW To e-mail, change noise into sound. |
#213
|
|||
|
|||
In article ,
"Dave Plowman (News)" writes: In article , Jim Michaels wrote: Either the socket is adequate for the 32amp circuit it is on or it isn't. Relying on whatever is plugged into it to not draw too much is far from idiot proof, it isn't even non expert proof. It could be that the countries which use BS1363 plugs also happen to have fewer idiots than those that don't, but I rather doubt that's the reason it's gtenerally regarded as the safest plug in the world. Anyone want to buy non-fused BS1363 style plugs? They've got nothing to do with BS1363, and have no type approval anywhere. Not to mention the 6 months in prison and £5000 fine for anyone importing them into the UK. -- Andrew Gabriel |
#215
|
|||
|
|||
In article t,
Chip writes: On 09 Aug 2005 20:21:59 GMT,it is alleged that (Andrew Gabriel) spake thusly in uk.d-i-y: Not to mention the 6 months in prison and 5000 fine for anyone importing them into the UK. The world *finally* went crazy. 6months and a fine for a plug? It's aimed at stopping importers from importing non-compliant goods. It seems to work -- it's sufficiently rare to come across a non-conforming 13A plug in the UK that most people have never seen one at all. The main market for non-conforming 13A plugs were cheap goods made in China for Hong Kong residents to buy when visiting and take home to Hong Kong. However, the Hong Kong authorities have started becoming more strict with this insisting on full BS1363 compliance, and it may be the market for non-conforming 13A plugs becomes too small to remain viable. It was interesting to see how expensive that non-conforming cordset was -- more expensive than conforming ones in the UK. -- Andrew Gabriel |
#216
|
|||
|
|||
On 09 Aug 2005 21:52:20 GMT,it is alleged that
(Andrew Gabriel) spake thusly in uk.d-i-y: In article t, Chip writes: On 09 Aug 2005 20:21:59 GMT,it is alleged that (Andrew Gabriel) spake thusly in uk.d-i-y: Not to mention the 6 months in prison and 5000 fine for anyone importing them into the UK. The world *finally* went crazy. 6months and a fine for a plug? It's aimed at stopping importers from importing non-compliant goods. It seems to work -- it's sufficiently rare to come across a non-conforming 13A plug in the UK that most people have never seen one at all. The main market for non-conforming 13A plugs were cheap goods made in China for Hong Kong residents to buy when visiting and take home to Hong Kong. However, the Hong Kong authorities have started becoming more strict with this insisting on full BS1363 compliance, and it may be the market for non-conforming 13A plugs becomes too small to remain viable. It was interesting to see how expensive that non-conforming cordset was -- more expensive than conforming ones in the UK. I am hoping the fine is for 'importing and offering for sale' rather than aimed at the hapless tourist who obtains one while overseas for whatever reason. (I think this is probably the case.) I do recall coming across a batch of these in 1991 or 92, while doing safety tests on new IT equipment. They turned up with a batch of printers from the middle east (I believe iraq uses BS1363 /style/ outlets). Possibly due to 'oh, iraq is now the bad guy, we have to offload these cords somewhere'. The cord was BASEC approved, and the IEC connector was fine, so we fitted MK toughplugs, 5A fuses, and billed for it. Also noted is the lack of sleeving on the prongs, and likely non-electrical grade metal used for the pins. -- There are three things which I consider excellent advice. First, don't smoke to excess. Second, don't drink to excess. Third, don't marry to excess. - Mark Twain |
#217
|
|||
|
|||
In article t,
Chip wrote: Not to mention the 6 months in prison and 5000 fine for anyone importing them into the UK. The world *finally* went crazy. 6months and a fine for a plug? Yup. Should be the death sentence. Since only wallies like Jim seem think it a good idea. Every appliance capable of being plugged into a ring main in the UK comes already fitted with a suitably fused 13 amp plug. By law. Those - domestically - that aren't, like some cookers and showers need permanent wiring in the form of a radial, and why not since they're unlikely to be moved to other rooms. If you really want them to be plugged in rather than hard wired, then suitable BS connectors are available. At a price. Look at any commercial kitchen for a clue. The snag comes with some possibly domestic hobby appliances like large arc welders and air compressors which fall outside the 13 amp limit, but are readily available. Let Darwin's law apply for those so foolish to spend lots of money on those, but expect to modify the wiring on them to use them on the 13 amp socket in their garage. They're just more wallies. -- *He who laughs last, thinks slowest. Dave Plowman London SW To e-mail, change noise into sound. |
#218
|
|||
|
|||
In article t,
Chip writes: (Andrew Gabriel) spake thusly in uk.d-i-y: Not to mention the 6 months in prison and 5000 fine for anyone importing them into the UK. I am hoping the fine is for 'importing and offering for sale' rather than aimed at the hapless tourist who obtains one while overseas for whatever reason. (I think this is probably the case.) Yes although you would be very wise to work out in advance how you could show you do not "possess for supply" (Plugs and Sockets Regs 1994, Consumer Protection Act 1987), i.e. it's for your use. However, Customs can still confiscate and destroy (not sure what Act that would be under -- probably something to do with importing unsafe goods), and there may be potential penalties too. -- Andrew Gabriel |
#219
|
|||
|
|||
Chip wrote:
Also noted is the lack of sleeving on the prongs, and likely non-electrical grade metal used for the pins. I have lots of plugs with no sleeving, is that part of the Standard? And non-electrical grade metal? Wassatallabahtden? |
#220
|
|||
|
|||
On Tue, 09 Aug 2005 22:00:27 GMT, Chip
wrote: On 09 Aug 2005 21:52:20 GMT,it is alleged that (Andrew Gabriel) spake thusly in uk.d-i-y: In article t, Chip writes: On 09 Aug 2005 20:21:59 GMT,it is alleged that (Andrew Gabriel) spake thusly in uk.d-i-y: Not to mention the 6 months in prison and 5000 fine for anyone importing them into the UK. The world *finally* went crazy. 6months and a fine for a plug? It's aimed at stopping importers from importing non-compliant goods. It seems to work -- it's sufficiently rare to come across a non-conforming 13A plug in the UK that most people have never seen one at all. The main market for non-conforming 13A plugs were cheap goods made in China for Hong Kong residents to buy when visiting and take home to Hong Kong. However, the Hong Kong authorities have started becoming more strict with this insisting on full BS1363 compliance, and it may be the market for non-conforming 13A plugs becomes too small to remain viable. It was interesting to see how expensive that non-conforming cordset was -- more expensive than conforming ones in the UK. I am hoping the fine is for 'importing and offering for sale' rather than aimed at the hapless tourist who obtains one while overseas for whatever reason. (I think this is probably the case.) The basis for this is the regulations surrounding the use of the CE mark on many products, certainly electrical stuff. The wording in the EU Directives is "placing on the market" and applies to a manufacturer or representative such as a distributor. It has been interpreted differently in different countries and the policing done in different ways. The UK has taken the view that it means importing and selling and is policed mainly by exception. This has meant that Trading Standards shoulder most of the responsibility for that and that it is mainly policing by exception. Thus, in practice, import for own use does not trigger anything, and probably the import and sale of the odd cord here and there. Other countries have policing by Customs and that is a different proposition. In practice, in the UK, there have been few prosecutions related to sale of products not conforming to standards. It is more likely that these would happen in the event of something bad happening. -- ..andy To email, substitute .nospam with .gl |
#221
|
|||
|
|||
In article ,
"PC Paul" writes: Chip wrote: Also noted is the lack of sleeving on the prongs, and likely non-electrical grade metal used for the pins. I have lots of plugs with no sleeving, is that part of the Standard? It is now. You cannot sell such appliances without changing the plugs first. That even applies if you take them along to a car boot sale to sell yourself or to a fate. Unsleeved pins are not a cause for a PAT test fail, although some companies have a policy to replace such plugs during PAT testing. The even older 13A plugs without the base broadening near the live and neutral pins is a PAT test failure, although you are very unlikely to find any of these nowadays. And non-electrical grade metal? Wassatallabahtden? Dunno. Many not solid brass bins? -- Andrew Gabriel |
#222
|
|||
|
|||
In article ,
Andy Hall writes: The basis for this is the regulations surrounding the use of the CE mark on many products, certainly electrical stuff. The wording in the EU Directives is "placing on the market" and applies to a manufacturer or representative such as a distributor. It has been interpreted differently in different countries and the policing done in different ways. The UK has taken the view that it means importing and selling and is policed mainly by exception. This has meant that Trading Standards shoulder most of the responsibility for that and that it is mainly policing by exception. Thus, in practice, import for own use does not trigger anything, and probably the import and sale of the odd cord here and there. Other countries have policing by Customs and that is a different proposition. Actually, illegal plugs is one of the things Trading Standards are quite proactive on. It tends to be done at point of sale rather than at import though. In practice, in the UK, there have been few prosecutions related to sale of products not conforming to standards. It is more likely that these would happen in the event of something bad happening. Plugs and Sockets Regs breaches accounted for 15 prosecutions over the 5 year period up to 2003. -- Andrew Gabriel |
#223
|
|||
|
|||
|
#224
|
|||
|
|||
Jim Michaels wrote:
Yup. Should be the death sentence. Since only wallies like Jim seem think it a good idea. What are "wallies", I assume it is derogatory, it does not show up on the first few pages of Google, nor a standard dictionary? Wally is china. Your granny might have lived in a tenement with a wally close (the common stair having tiled walls which was a bit posher than painted) and had wally dugs on the mantlepiece. She also probably had wallies which she kept in a glass of water beside the bed (china i.e. false teeth). Owain |
#225
|
|||
|
|||
In article ,
Jim Michaels wrote: Either the socket is adequate for the 32amp circuit it is on or it isn't. Relying on whatever is plugged into it to not draw too much is far from idiot proof, it isn't even non expert proof. Are you trying to say that all sockets on radials are capable of carrying the full rating of that radial as a continuous load? Because this doesn't seem to be the case in most counties. It certainly is in the US. So you have one socket outlet per radial circuit? How incredibly wasteful of cable etc and this also means the vast majority of households won't have adequate numbers of sockets and rely on unsafe extension leads for what are in effect permanent installations. Anyone want to buy non-fused BS1363 style plugs? They've got nothing to do with BS1363, and have no type approval anywhere. They seem to fit into BS1363 sockets and effectively bypass a linchpin of the BS1363 system. You can probably find cheap copy brake pads for your car where the pad material is totally unsuitable, but will fit. Would you think this a good idea for your car, and therefore the safety of your family? And it doesn't take many seconds to think of similar things where unscrupulous makers sell totally unsafe products. -- *Before they invented drawing boards, what did they go back to? Dave Plowman London SW To e-mail, change noise into sound. |
#226
|
|||
|
|||
In article ,
Jim Michaels wrote: Are you trying to say that all sockets on radials are capable of carrying the full rating of that radial as a continuous load? Because this doesn't seem to be the case in most counties. It certainly is in the US. Any single socket on a circuit is capable of the full capacity of the circuit. So you have one socket outlet per radial circuit? Sometimes, not usually. Err, please explain this. If you have a 10 amp socket (for example) the radial must be protected by a 10 amp MCB, etc. If you have more than one 10 amp socket, then either the radial will trip if you try to load both to 10 amps, or a 20 amp MCB and wiring would allow a 10 amp socket to be overloaded by your resident idiot. How incredibly wasteful of cable etc and this also means the vast majority of households won't have adequate numbers of sockets and rely on unsafe extension leads for what are in effect permanent installations. As a minimum a socket is required to be within 6 feet horizontally of everyplace along a wall in residential rooms. Above the kitchen work tops in is 2 feet. So just how many ways does the average US CU or whatever contain? Anyone want to buy non-fused BS1363 style plugs? They've got nothing to do with BS1363, and have no type approval anywhere. They seem to fit into BS1363 sockets and effectively bypass a linchpin of the BS1363 system. You can probably find cheap copy brake pads for your car where the pad material is totally unsuitable, but will fit. Would you think this a good idea for your car, and therefore the safety of your family? And it doesn't take many seconds to think of similar things where unscrupulous makers sell totally unsafe products. This thread was about idiot proof designs. You just can't make things idiot proof where unscrupulous manufacturers are allowed to sell products which contravene standards. And fools buy them. Trading Standards in the UK would come down very hard on anyone selling such things - and rightly so. I was merely pointing out how resourceful some idiots appear to be. You seem to be pointing out the beauty of a so called 'free market' economy where anyone can sell anything. Drugs which claim to cure cancer? Drugs which say on the box are 'X' and look like it but are chalk? Is this what you want? -- *Rehab is for quitters Dave Plowman London SW To e-mail, change noise into sound. |
#227
|
|||
|
|||
On Fri, 12 Aug 2005 19:28:07 +0100,it is alleged that "Dave Plowman
(News)" spake thusly in uk.d-i-y: I am sure Jim will come back with answers on this, but from my knowledge the answers are as follows: [snip] Err, please explain this. If you have a 10 amp socket (for example) the radial must be protected by a 10 amp MCB, etc. If you have more than one 10 amp socket, then either the radial will trip if you try to load both to 10 amps, or a 20 amp MCB and wiring would allow a 10 amp socket to be overloaded by your resident idiot. Usually US outlets are 15A rated on a 15 or 20A circuit, (A 20A circuit MUST contain more than one outlet). The average varies depending on age of the property, but is probably 4-5 outlets + a light or 2 per circuit. Diversity means breaker trips are relatively rare, much as with a UK ring, only on a smaller scale. [snip] As a minimum a socket is required to be within 6 feet horizontally of everyplace along a wall in residential rooms. Above the kitchen work tops in is 2 feet. So just how many ways does the average US CU or whatever contain? Current NEC requirements specify a maximum of 42 ways (the panel is usually around 18" by 2'6"). Canadian codes allow for 42 ways in a lighting and general power panel. Older 60 or 100 amp services may have as few as 12 ways. [snip] Certainly the US system is in no way idiot proof, it contains more shortcomings than the UK system in respect of potential overloads through abuse, and it is also simpler to abuse (no chunks of 6" nail required). However (Just IMHO) when abused, the UK system is more capable of damage due to the higher power levels available, 32A @ 230v as opposed to 20A @ 120v, both however are more than capable of starting a fire. -- Life is a whim of several billion cells to be you for a while. |
#228
|
|||
|
|||
"Jim Michaels" wrote in message ... On Fri, 12 Aug 2005 19:28:07 +0100, "Dave Plowman (News)" wrote: In article , Jim Michaels wrote: Are you trying to say that all sockets on radials are capable of carrying the full rating of that radial as a continuous load? Because this doesn't seem to be the case in most counties. It certainly is in the US. Any single socket on a circuit is capable of the full capacity of the circuit. So you have one socket outlet per radial circuit? Sometimes, not usually. Err, please explain this. If you have a 10 amp socket (for example) the radial must be protected by a 10 amp MCB, etc. If you have more than one 10 amp socket, then either the radial will trip if you try to load both to 10 amps, or a 20 amp MCB and wiring would allow a 10 amp socket to be overloaded by your resident idiot. You are basically correct. Clearer phrasing... Any SINGLE socket or a combination of sockets on a circuit can be loaded to the rating of the circuit. big snip of interesting exchanges ... I've been browsing at the posts in this thread ... it suddenly dawned on me, why - in most USAian TV shows - albeit mostly filmed in Canada - whenever somebody is offered tea, the actor pours water from a kettle boiling on a hob. I can't remember when I, or my acquaintances, didn't use an electric kettle - hang on ! I _do_ remember! It was in 1987! On the morning of the hurricane strike; I uncovered the kettle from the back of the cupboard -blew off the dust - and put in on the gas hob ... course I had to strike a match 'cos the 'leccy was off! Different folks, different volts/stokes - different appliances! -- Brian |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Planit Millennium II [2 CDs] new !, and other Kitchen Design 3D programscheap software for fitted kitchen design | Woodworking | |||
Planit Millennium II [2 CDs] new !, and other Kitchen Design 3D programscheap software for fitted kitchen design | Woodworking | |||
Is it a radial or ring circuit? | UK diy | |||
central heating - flow & return circuit design | UK diy | |||
Design - Cultural Factors | Woodworking |