#1
![]() |
|||
|
|||
![]()
Sorry, "American Electrics" was getting far too OT, and rather long so
here it is: Given the opportunity (and let's ignore backwards compatibility, at least to begin with), how would you redesign our domestic final circuits to be completely idiot proof? Although the system we have at present is probably the most recently designed in the world, are there any things about it which, with today's technology, could be seen as compromises? Particular examples brought up on the AE thread (and elsewhere over the last few months): * a ring circuit with a break in one of the live conductors will overload one leg as it is fused at 30/32A and the cable is only good for 20A (27A under ideal circumstances) * fuses in the appliance plugs can be bypassed, while MCBs screwed into the consumer unit are less likely to be. * fused appliance plugs are better for isolating faults to a single appliance as (usually) the plug fuse will blow before the MCB. * on the other hand, in a "dead short" situation, this isn't always the case even with a 3A fuse and 32A MCB (I've proved it several times :-) * radials using fused plugs can be rated up to 32A, but need at least 4mm2 cable, and often 6mm2 cable which is both more expensive, and much more difficult to work with than the 2.5mm2 cable used for 32A rings. * unfused appliance plugs (less problem with tampering) would mandate radials with a very low MCB rating and hence a large number of radials; one per room or even more. * either that, or they would mandate fuse protection inside every appliance and while a lot (TV, video etc) already have this, it's going to be difficult persuading manufacturers to bung a fuse inside a £3 table lamp. * unfused appliance plugs will *always* take out the circuit MCB on a fault, and hence tracing the appliance which caused the fault can be tricky since there are likely to be several candidates. Erm, I'm sure I've missed some things out. Go on then, what's the ideal? Sub mains to each room with a mini-CU in every room, with MCBs feeding individual outlets (don't laugh, it has been suggested)? Appliance plugs with built-in MCBs rather than replaceable cartridge fuses? Sockets with built-in MCBs, or RCBOs? Talking of RCDs, what about changing the way we use these things? Have fun :-) Hwyl! M. -- Martin Angove: http://www.tridwr.demon.co.uk/ Two free issues: http://www.livtech.co.uk/ Living With Technology .... Beware of quantum ducks. Quark! Quark! |
#2
![]() |
|||
|
|||
![]()
In article ,
Martin Angove wrote: Go on then, what's the ideal? Sub mains to each room with a mini-CU in every room, with MCBs feeding individual outlets (don't laugh, it has been suggested)? Appliance plugs with built-in MCBs rather than replaceable cartridge fuses? Sockets with built-in MCBs, or RCBOs? Talking of RCDs, what about changing the way we use these things? Given that all appliances come with fitted plugs these days, it would be easy to make the use of the wrong fuse impossible, by making the design of the fuse and fuse carrier different for the appropriate size. And you could also make the sale of '13 amp' extension leads not rated at 13 amps illegal. Unless using proprietary non 13 amp connectors like some garden tools etc, use. The idea of having a mini CU in every room is total overkill. Just how often does an MCB trip and cause a problem in the average house? Since this is a DIY group, when re-wiring your house, simply put in an adequate number of circuits. The extra costs in materials is pennies. Then any nuisance tripping will be more localised - if it ever happens. Makes sense to perhaps have the hall and stairs lighting on its own circuit. -- *Drugs may lead to nowhere, but at least it's the scenic route * Dave Plowman London SW To e-mail, change noise into sound. |
#3
![]() |
|||
|
|||
![]()
In message , "Dave Plowman (News)"
wrote Given that all appliances come with fitted plugs these days, it would be easy to make the use of the wrong fuse impossible, I'm sure that I could make my roll of aluminium foil fit any size of fuse receptacle. -- Alan |
#4
![]() |
|||
|
|||
![]()
In article ,
Martin Angove writes: Sorry, "American Electrics" was getting far too OT, and rather long so here it is: The beginning of the thread was an interesting discussion. However, there was nothing new posted for many days -- just the same misunderstandings being repeated over again. You probably just started it all over again :-( -- Andrew Gabriel |
#5
![]() |
|||
|
|||
![]()
In article ,
Alan wrote: Given that all appliances come with fitted plugs these days, it would be easy to make the use of the wrong fuse impossible, I'm sure that I could make my roll of aluminium foil fit any size of fuse receptacle. I'd say you'd find that difficult with blade type fuses as used in cars. However, the idea was to make the system foolproof. Not c**t proof. -- *To err is human. To forgive is against company policy. Dave Plowman London SW To e-mail, change noise into sound. |
#6
![]() |
|||
|
|||
![]()
Martin Angove wrote:
Given the opportunity (and let's ignore backwards compatibility, at least to begin with), how would you redesign our domestic final circuits to be completely idiot proof? I don't think that's possible, or desirable. You might better ask how we can redesign motor cars to be idiot proof, as they cause far far more deaths and serious accidents than electrical wiring (or even appliances) * a ring circuit with a break in one of the live conductors will overload one leg as it is fused at 30/32A and the cable is only good for 20A (27A under ideal circumstances) A current-balance MCB that trips the ring if the imbalance between the two legs exceeds a certain proportion of the total is probably feasible, and could probably be combined into a single-circuit RCBO. Ring overloading and high point load really only occurs in kitchens, domestically. Treating all hob/ovens, washing machines, tumble driers and dishwashers as fixed heating appliances and mandating points for these to be provided with each point rated at 10A or actual load if greater (in the same way we rate lighting points at 100W) would in almost all cases provide at least 4 sockets (they could be on their own 32A ring, or radial, or multiple 15A radials) in the kitchen, and take these appliances off the general purpose ring. The gp ring should be able to cope with other loads, deep fryer, combi microwave, as these are fairly intermittent anyway. All those appliances are plumbed in or otherwise non-portable anyway, so there is no disadvantage to restricting their use, unlike a toastie-maker or microwave whcih might be used in a teenager's room. Such provision is also more easily enforced because these appliances are usually *fitted* by tradesmen and in kitchens comes under (or can be brought under) Part P for the fixed wiring. * unfused appliance plugs (less problem with tampering) would mandate radials with a very low MCB rating and hence a large number of radials; one per room or even more. * unfused appliance plugs will *always* take out the circuit MCB on a fault, and hence tracing the appliance which caused the fault can be tricky since there are likely to be several candidates. Yesm that is a step back to the 'good old days' ... Sockets with built-in MCBs, or RCBOs? Is an alternative, but the difficulty with removing the plug fuse is backwards compatbility, which cannot be ignored. We can't have new unfused appliances being plugged into old high-current rings, and any use of adapters or requiring householders to change plugs is going to send the death rate shooting up. Talking of RCDs, what about changing the way we use these things? Like, using them correctly instead of whole-house? Owain |
#7
![]() |
|||
|
|||
![]() "Dave Plowman (News)" wrote in message ... In article , Alan wrote: Given that all appliances come with fitted plugs these days, it would be easy to make the use of the wrong fuse impossible, I'm sure that I could make my roll of aluminium foil fit any size of fuse receptacle. I'd say you'd find that difficult with blade type fuses as used in cars. However, the idea was to make the system foolproof. Not c**t proof. "The problem with designing something completely foolproof is to under estimate the ingenuity of a complete fool." - Douglas Adams Adam |
#8
![]() |
|||
|
|||
![]() "Alan" wrote in message ... In message , "Dave Plowman (News)" wrote Given that all appliances come with fitted plugs these days, it would be easy to make the use of the wrong fuse impossible, I'm sure that I could make my roll of aluminium foil fit any size of fuse receptacle. Or find a nail, bolt or bit of wire that will fit, the final protection needs to be taken away from the idiots who can and have done such things. |
#9
![]() |
|||
|
|||
![]()
Wadsworth wrote:
"Dave Plowman (News)" wrote in message ... In article , Alan wrote: Given that all appliances come with fitted plugs these days, it would be easy to make the use of the wrong fuse impossible, I'm sure that I could make my roll of aluminium foil fit any size of fuse receptacle. I'd say you'd find that difficult with blade type fuses as used in cars. However, the idea was to make the system foolproof. Not c**t proof. "The problem with designing something completely foolproof is to under estimate the ingenuity of a complete fool." - Douglas Adams Adam I'm with Alan and ARWadsworth on this one. Anyone stupid enough to try doing unnatural things with stuff that's there to protect them, that they don't understand, deserves everything that they get. Even if its ultimately a Darwin Award ![]() At the end of the day any system that depends for its safety on measures that are accessible to "idiots" is going to be compromised, for the reasons articulated by Mr Adams. Personally my view is that we need to do our best to make the system totally safe for the average user who follows the rules, and make it very difficult for the average DIYer to mess up. However, we are unlikely to ever be able to cope with the lunatic fringe who are actively trying to circumvent the safety systems, and we probably shouldn't even try ... Cheers Richard |
#10
![]() |
|||
|
|||
![]() Martin Angove wrote: * either that, or they would mandate fuse protection inside every appliance and while a lot (TV, video etc) already have this, it's going to be difficult persuading manufacturers to bung a fuse inside a £3 table lamp. Every US set of Xmas lights has a fuse inside the connecting plugs, and some of these sell for $2! Doesn't seem like a problem to me, but if the fuse is inside the appliance, then replacing it may give access problems, as it already does in TVs. Regards Capitol |
#11
![]() |
|||
|
|||
![]() "Richard Appleby" wrote in message ... Wadsworth wrote: snip "The problem with designing something completely foolproof is to under estimate the ingenuity of a complete fool." - Douglas Adams I'm with Alan and ARWadsworth on this one. Anyone stupid enough to try doing unnatural things with stuff that's there to protect them, that they don't understand, deserves everything that they get. Even if its ultimately a Darwin Award ![]() At the end of the day any system that depends for its safety on measures that are accessible to "idiots" is going to be compromised, for the reasons articulated by Mr Adams. Personally my view is that we need to do our best to make the system totally safe for the average user who follows the rules, and make it very difficult for the average DIYer to mess up. However, we are unlikely to ever be able to cope with the lunatic fringe who are actively trying to circumvent the safety systems, and we probably shouldn't even try ... The point is, it doesn't need a lunatic, let the person who has never put the wrong fuse in a BS1363 plug just get things working cast the first stone, let the person who then remembers to replace it A.S.A.P cast the second... Nothing can be made completely foolproof, but requiring more than a cheap tea-spoon to access the fuse in a moulded on BS1363 plug is not even trying. There are people changing fuses in plugs who know nothing about electrics and are clueless as to the importance of the fuse or it's rating. |
#12
![]() |
|||
|
|||
![]() "Capitol" wrote in message ... Martin Angove wrote: * either that, or they would mandate fuse protection inside every appliance and while a lot (TV, video etc) already have this, it's going to be difficult persuading manufacturers to bung a fuse inside a £3 table lamp. Every US set of Xmas lights has a fuse inside the connecting plugs, and some of these sell for $2! Doesn't seem like a problem to me, but if the fuse is inside the appliance, then replacing it may give access problems, as it already does in TVs. Does it? IMO what it does means is that those who are with clue can and those without don't... |
#13
![]() |
|||
|
|||
![]()
On Sat, 30 Jul 2005 12:14:02 +0100, Martin Angove
wrote: Given the opportunity (and let's ignore backwards compatibility, at least to begin with), how would you redesign our domestic final circuits to be completely idiot proof? Making things idiot proof is trivial. Making things proof against intelligent beings is impossible. -- Peter Parry. http://www.wpp.ltd.uk/ |
#14
![]() |
|||
|
|||
![]()
In message ws.net,
":::Jerry::::" wrote Nothing can be made completely foolproof, but requiring more than a cheap tea-spoon to access the fuse in a moulded on BS1363 plug is not even trying. Make it more difficult and it will be easier to cut off the plug and hold the bare wires into the socket with a couple of match sticks - or preferably with a couple of nails.. For something to be safe you don't make it impossible to fix without special tools. Having to take something apart to replace a fuse isn't safe. People are going to see if the fix works before reassembling the item. While I guess everyone on this group may have a set of screwdrivers and/or security bit readily to hand many households don't have these items. -- Alan |
#15
![]() |
|||
|
|||
![]()
In message ws.net,
":::Jerry::::" writes "Capitol" wrote in message ... Martin Angove wrote: * either that, or they would mandate fuse protection inside every appliance and while a lot (TV, video etc) already have this, it's going to be difficult persuading manufacturers to bung a fuse inside a £3 table lamp. Every US set of Xmas lights has a fuse inside the connecting plugs, and some of these sell for $2! Doesn't seem like a problem to me, but if the fuse is inside the appliance, then replacing it may give access problems, as it already does in TVs. Does it? IMO what it does means is that those who are with clue can and those without don't... But what about he who thinks he has a clue ? -- geoff |
#16
![]() |
|||
|
|||
![]()
:::Jerry:::: wrote:
Or find a nail, bolt or bit of wire that will fit, the final protection needs to be taken away from the idiots who can and have done such things. You should work in government! That sounds like just the sort of attitude the ODPM would love ;-) The problem with such nannyism, is that in any many cases you can't take the facilities away from the "few idiots" without causing major irritation to the majority of (competant) people in the process. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#17
![]() |
|||
|
|||
![]()
In article ws.net,
:::Jerry:::: wrote: The point is, it doesn't need a lunatic, let the person who has never put the wrong fuse in a BS1363 plug just get things working cast the first stone, let the person who then remembers to replace it A.S.A.P cast the second... I can only remember having to replace one or two fuses, and those were 13 amp types. Most appliances which are fused at less than 13 amp will be things like AV equipment and have internal fuses which will blow first anyway. If you're continually replacing fuses, as you say, then you need to look into the reasons for this. -- *Money isn't everything, but it sure keeps the kids in touch. Dave Plowman London SW To e-mail, change noise into sound. |
#18
![]() |
|||
|
|||
![]()
In message , raden
wrote Does it? IMO what it does means is that those who are with clue can and those without don't... But what about he who thinks he has a clue ? In the past you had to employ a Corgi registered fitter for gas but with plastic pipes and push fittings anyone can now do it. -- Alan |
#19
![]() |
|||
|
|||
![]()
In article ws.net,
":::Jerry::::" writes: The point is, it doesn't need a lunatic, let the person who has never put the wrong fuse in a BS1363 plug just get things working cast the first stone, let the person who then remembers to replace it A.S.A.P cast the second... As pointed out already, you can't put a wrong fuse in a 13A plug. All appliance cords and appliancs are required to remain safe when protected at 16A nowadays, so all* BS1362 fuse values are OK. *Minor exception, but strictly 1A BS1362 fuses should not be used in BS1363 plugs because they are not ASTA approved and would therefore result in a PAT test failure of the appliance. -- Andrew Gabriel |
#20
![]() |
|||
|
|||
![]()
On Sun, 31 Jul 2005 10:00:22 +0100, Alan
wrote: In message , raden wrote Does it? IMO what it does means is that those who are with clue can and those without don't... But what about he who thinks he has a clue ? In the past you had to employ a Corgi registered fitter for gas but with plastic pipes and push fittings anyone can now do it. There has never and is no legislation requiring you to employ a CORGI registered fitter. However, somebody who does gas fitting professionally must be CORGI registered. It is a requirement that anybody doing gas fitting be competent; but given this pre-requisite, the law does not prevent you doing your own. You may not use plastic pipe nor push fittings for gas. -- ..andy To email, substitute .nospam with .gl |
#21
![]() |
|||
|
|||
![]()
In message , Andy Hall
wrote You may not use plastic pipe nor push fittings for gas. Wrong - Transco use plastic pipes ! -- Alan |
#22
![]() |
|||
|
|||
![]()
In article ,
Alan wrote: You may not use plastic pipe nor push fittings for gas. Wrong - Transco use plastic pipes ! Not with push on fittings. Nor could you obtain fittings to connect their stuff to your cooker. -- *How many roads must a man travel down before he admits he is lost? * Dave Plowman London SW To e-mail, change noise into sound. |
#23
![]() |
|||
|
|||
![]()
On Sun, 31 Jul 2005 11:16:27 +0100, Alan
wrote: In message , Andy Hall wrote You may not use plastic pipe nor push fittings for gas. Wrong - Transco use plastic pipes ! I meant within premises, obviously.... -- ..andy To email, substitute .nospam with .gl |
#24
![]() |
|||
|
|||
![]() "Alan" wrote in message ... In message , raden wrote Does it? IMO what it does means is that those who are with clue can and those without don't... But what about he who thinks he has a clue ? In the past you had to employ a Corgi registered fitter for gas but with plastic pipes and push fittings anyone can now do it. Gas can't be plastic. |
#26
![]() |
|||
|
|||
![]()
In article ,
Huge wrote: In the past you had to employ a Corgi registered fitter for gas but with plastic pipes and push fittings anyone can now do it. There has never and is no legislation requiring you to employ a CORGI registered fitter. However, somebody who does gas fitting professionally must be CORGI registered. It is a requirement that anybody doing gas fitting be competent; but given this pre-requisite, the law does not prevent you doing your own. You may not use plastic pipe nor push fittings for gas. Forgot to engage your sense of humour? Trouble is pratts like Drivel see such things posted here and believe them. And it's bad enough him flooding a house because he can't make a decent plastic pipe joint. Gawd knows what the end result would be when he uses this for gas. -- *Okay, who stopped the payment on my reality check? * Dave Plowman London SW To e-mail, change noise into sound. |
#27
![]() |
|||
|
|||
![]() "Dave Plowman (News)" wrote in message ... In article ws.net, :::Jerry:::: wrote: The point is, it doesn't need a lunatic, let the person who has never put the wrong fuse in a BS1363 plug just get things working cast the first stone, let the person who then remembers to replace it A.S.A.P cast the second... I can only remember having to replace one or two fuses, and those were 13 amp types. Most appliances which are fused at less than 13 amp will be things like AV equipment and have internal fuses which will blow first anyway. You live a sheltered life then... If you're continually replacing fuses, as you say, then you need to look into the reasons for this. No one has said anything about having to continually replace fuses. |
#28
![]() |
|||
|
|||
![]() "Andrew Gabriel" wrote in message .. . In article ws.net, ":::Jerry::::" writes: The point is, it doesn't need a lunatic, let the person who has never put the wrong fuse in a BS1363 plug just get things working cast the first stone, let the person who then remembers to replace it A.S.A.P cast the second... As pointed out already, you can't put a wrong fuse in a 13A plug. All appliance cords and appliancs are required to remain safe when protected at 16A nowadays, so all* BS1362 fuse values are OK. So if fuse rating of below 13A are irrelivant, why are they still advalible... |
#29
![]() |
|||
|
|||
![]() "John Rumm" wrote in message ... :::Jerry:::: wrote: Or find a nail, bolt or bit of wire that will fit, the final protection needs to be taken away from the idiots who can and have done such things. You should work in government! That sounds like just the sort of attitude the ODPM would love ;-) The problem with such nannyism, is that in any many cases you can't take the facilities away from the "few idiots" without causing major irritation to the majority of (competant) people in the process. Well, lets go back to bare wires and crock-clips, as even the present regulations causes such irritation to the majority, and if they wish to kill themselves then that's Darwinism... |
#30
![]() |
|||
|
|||
![]()
In message , "Dave Plowman (News)"
wrote Nor could you obtain fittings to connect their stuff to your cooker. What's wrong with garden hose and duct tape? -- Alan |
#31
![]() |
|||
|
|||
![]()
In article ws.net,
:::Jerry:::: wrote: I can only remember having to replace one or two fuses, and those were 13 amp types. Most appliances which are fused at less than 13 amp will be things like AV equipment and have internal fuses which will blow first anyway. You live a sheltered life then... I doubt it. But have the sense not to try and run two 3 kW heaters off one extension lead, or to have extension leads that won't carry 13 amps. If you're continually replacing fuses, as you say, then you need to look into the reasons for this. No one has said anything about having to continually replace fuses. You give the impression it's so common to be a serious problem. But if it was, I'd suggest changing to radial circuits would make things worse by having less sockets therefore more overloaded extension leads, etc. I'm trying hard to remember the last plug fuse I had blow - despite having a vast number of electrical appliances. The one I do remember was on a 25" hybrid TV - it said 500 watts but would blow a 5 amp fuse. What appliance have you had a fuse blow on recently? -- *Horn broken. - Watch for finger. Dave Plowman London SW To e-mail, change noise into sound. |
#32
![]() |
|||
|
|||
![]()
In article ,
Huge wrote: Trouble is pratts like Drivel see such things posted here and believe them. And it's bad enough him flooding a house because he can't make a decent plastic pipe joint. Gawd knows what the end result would be when he uses this for gas. Good point [he reluctantly admits]. Perhaps smileys *do* have a place? Naw - keep them guessing. -- *I used to have an open mind but my brains kept falling out * Dave Plowman London SW To e-mail, change noise into sound. |
#33
![]() |
|||
|
|||
![]()
In article ws.net,
":::Jerry::::" writes: "Andrew Gabriel" wrote in message .. . In article ws.net, ":::Jerry::::" writes: The point is, it doesn't need a lunatic, let the person who has never put the wrong fuse in a BS1363 plug just get things working cast the first stone, let the person who then remembers to replace it A.S.A.P cast the second... As pointed out already, you can't put a wrong fuse in a 13A plug. All appliance cords and appliancs are required to remain safe when protected at 16A nowadays, so all* BS1362 fuse values are OK. So if fuse rating of below 13A are irrelivant, why are they still advalible... Well, they don't do any harm either, and BS1362 fuses aren't only used in plugs. -- Andrew Gabriel |
#34
![]() |
|||
|
|||
![]()
Dave Plowman (News) wrote:
In article ws.net, :::Jerry:::: wrote: The point is, it doesn't need a lunatic, let the person who has never put the wrong fuse in a BS1363 plug just get things working cast the first stone, let the person who then remembers to replace it A.S.A.P cast the second... I can only remember having to replace one or two fuses, and those were 13 amp types. Most appliances which are fused at less than 13 amp will be things like AV equipment and have internal fuses which will blow first anyway. Not with you on that one. The function of plug fuses was to protect the lead. An excess of fault current through a damaged and shorted thin cable normally used to carrying half an amp will cause heating and a fire risk. Internal fuses may be ineffective here. -- Adrian C |
#35
![]() |
|||
|
|||
![]() "John Rumm" wrote in message ... :::Jerry:::: wrote: Or find a nail, bolt or bit of wire that will fit, the final protection needs to be taken away from the idiots who can and have done such things. You should work in government! That sounds like just the sort of attitude the ODPM would love ;-) You are pathetic. The point is how to make a circuit idiot proof. We are not interested in your Little Middle England pro Tory and anti Blair crap. |
#36
![]() |
|||
|
|||
![]() "Alan" wrote in message ... In message , Andy Hall wrote You may not use plastic pipe nor push fittings for gas. Wrong - Transco use plastic pipes ! Only for underground work. Plastic pipes are not allowed overground, apart from the stubs emerging from the ground. |
#37
![]() |
|||
|
|||
![]()
Dave Plowman (News) wrote:
Trouble is pratts like Drivel see such things posted here and believe them. And it's bad enough him flooding a house because he can't make a decent plastic pipe joint. Gawd knows what the end result would be when he uses this for gas. If in his own house, a lot fewer postings to this group. Owain |
#38
![]() |
|||
|
|||
![]()
In message , Doctor Drivel
writes "John Rumm" wrote in message ... :::Jerry:::: wrote: Or find a nail, bolt or bit of wire that will fit, the final protection needs to be taken away from the idiots who can and have done such things. You should work in government! That sounds like just the sort of attitude the ODPM would love ;-) You are pathetic. The point is how to make a circuit idiot proof. We are not interested in your Little Middle England pro Tory and anti Blair crap. You mean this chappie ? http://uncyclopedia.org/wiki/Tony_Blair -- geoff |
#39
![]() |
|||
|
|||
![]() "Dave Plowman (News)" wrote in message ... In article , Huge wrote: In the past you had to employ a Corgi registered fitter for gas but with plastic pipes and push fittings anyone can now do it. There has never and is no legislation requiring you to employ a CORGI registered fitter. However, somebody who does gas fitting professionally must be CORGI registered. It is a requirement that anybody doing gas fitting be competent; but given this pre-requisite, the law does not prevent you doing your own. You may not use plastic pipe nor push fittings for gas. Forgot to engage your sense of humour? Trouble is pratts like This man never serviced his gas boiler for 18 years and was advising others to do the same. Take no notice of him. On personal contact you would ignore him, but on the internet his views come up. Sad but true. Whe you see his name, have a prat alert in your mind, and move on. |
#40
![]() |
|||
|
|||
![]()
In message , Alan
writes In message , "Dave Plowman (News)" wrote Nor could you obtain fittings to connect their stuff to your cooker. What's wrong with garden hose and duct tape? As my brother found when he moved into his new house -- geoff |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Planit Millennium II [2 CDs] new !, and other Kitchen Design 3D programscheap software for fitted kitchen design | Woodworking | |||
Planit Millennium II [2 CDs] new !, and other Kitchen Design 3D programscheap software for fitted kitchen design | Woodworking | |||
Is it a radial or ring circuit? | UK diy | |||
central heating - flow & return circuit design | UK diy | |||
Design - Cultural Factors | Woodworking |