Electrical code question
After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately.
I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary |
#2
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
Ivan Vegvary writes:
After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? It depends. This is commonly known as an "edison circuit". If each of the two breakers were on different legs of the 240v service, then the current in the grounded conductor will cancel out, such that if full load is drawn on both of the two hot conductors, the current flow in the grounded conductor (aka neutral) will sum to zero. If they're on the same leg, then yes, you'll draw 2x the current on the grounded conductor, which would be a code violation. Using a commercial handle-tie 240v breaker is recommended, as it will ensu a) That the two circuits are on opposite legs b) That both circuits must be disconnected simultaneously. |
#3
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Thursday, May 21, 2015 at 11:01:20 AM UTC-4, Scott Lurndal wrote:
To add to that, if you have two 20 amp circuits on opposite legs, the current in the neutral will always be between 0 and 20 amps. Only the unbalanced portion, ie the difference between the two flows in the neutral. For example, 15 amps on one, 5 amps on the other, you have 10 amps in the neutral. |
#4
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Thursday, May 21, 2015 at 10:42:48 AM UTC-4, Ivan Vegvary wrote:
After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary you really did this the best way. makes future troubleshhoting easier, and its a one time expense, so a little extra now doesnt matter. plus witheach item on its own breaker service is easier. |
#5
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On 05/21/2015 10:42 AM, Ivan Vegvary wrote:
After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary My Whirlpool dishwasher and a KitchenAid disposer are on the same 20 amp circuit and never had a problem. I don't know if it meets code but I can't imagine it is unsafe in any way. |
#6
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Thu, 21 May 2015 12:43:38 -0400, Mayhem wrote:
On 05/21/2015 10:42 AM, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary My Whirlpool dishwasher and a KitchenAid disposer are on the same 20 amp circuit and never had a problem. I don't know if it meets code but I can't imagine it is unsafe in any way. Same here. A receptacle under the sink. One side is "hot" for the DW and the GD side is "switched". |
#7
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Thursday, May 21, 2015 at 2:11:38 PM UTC-4, Oren wrote:
On Thu, 21 May 2015 12:43:38 -0400, Mayhem wrote: On 05/21/2015 10:42 AM, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary My Whirlpool dishwasher and a KitchenAid disposer are on the same 20 amp circuit and never had a problem. I don't know if it meets code but I can't imagine it is unsafe in any way. Same here. A receptacle under the sink. One side is "hot" for the DW and the GD side is "switched". I think the potential issue here is whether a 20A circuit has enough capacity to serve both a disposal and a dishwasher. You'd have to see the spec sheets on both. AFAIK, there is no specific reqt for separate circuits, as long as the circuit can handle the current for both. Some cities may have their own rules too. |
#8
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On 5/21/2015 12:43 PM, Mayhem wrote:
On 05/21/2015 10:42 AM, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary My Whirlpool dishwasher and a KitchenAid disposer are on the same 20 amp circuit and never had a problem. I don't know if it meets code but I can't imagine it is unsafe in any way. Did the same here, running two 20 amp lines seemed silly to me. I did run them both at the same time right after I installed them to see if it would trip the breaker while I still had the downstairs wall open. No problems showed up with both under load. Here the disposal only runs while we are cleaning off the plates to put in the dishwasher. The dishwasher isn't turned on until that step is done so in reality they never run at the same time anyway. John |
#9
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
"bob haller" wrote in message
... On Thursday, May 21, 2015 at 10:42:48 AM UTC-4, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary you really did this the best way. makes future troubleshhoting easier, and its a one time expense, so a little extra now doesnt matter. plus witheach item on its own breaker service is easier. +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. |
#11
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Thu, 21 May 2015 20:58:14 -0400, "Robert Green"
wrote: "bob haller" wrote in message ... On Thursday, May 21, 2015 at 10:42:48 AM UTC-4, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary you really did this the best way. makes future troubleshhoting easier, and its a one time expense, so a little extra now doesnt matter. plus witheach item on its own breaker service is easier. +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: Up here they are called "split" circuits, particularly when feeding a single duplex outlet.. |
#12
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Thursday, May 21, 2015 at 11:43:43 AM UTC-5, Mayhem wrote:
On 05/21/2015 10:42 AM, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary My Whirlpool dishwasher and a KitchenAid disposer are on the same 20 amp circuit and never had a problem. I don't know if it meets code but I can't imagine it is unsafe in any way.. It could trip the breaker if the appliances are run at the same time but that's not a safety issue since it shows you have protection for your wiring. A fuse or circuit breaker on house wiring is there to protect the wiring not necessarily the appliance. A gizmo can short out and burn up without drawing enough current to overload the circuit it's plugged into. 8-) [8~{} Uncle Electric Monster |
#13
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Thursday, May 21, 2015 at 4:31:05 PM UTC-5, John wrote:
On 5/21/2015 12:43 PM, Mayhem wrote: On 05/21/2015 10:42 AM, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary My Whirlpool dishwasher and a KitchenAid disposer are on the same 20 amp circuit and never had a problem. I don't know if it meets code but I can't imagine it is unsafe in any way. Did the same here, running two 20 amp lines seemed silly to me. I did run them both at the same time right after I installed them to see if it would trip the breaker while I still had the downstairs wall open. No problems showed up with both under load. Here the disposal only runs while we are cleaning off the plates to put in the dishwasher. The dishwasher isn't turned on until that step is done so in reality they never run at the same time anyway. John If your dishwasher is the type with an electric heating element that's on during the drying cycle, I wonder how much current it draws? 8-) [8~{} Uncle Overload Monster |
#14
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On 5/22/2015 6:01 AM, Uncle Monster wrote:
On Thursday, May 21, 2015 at 4:31:05 PM UTC-5, John wrote: On 5/21/2015 12:43 PM, Mayhem wrote: On 05/21/2015 10:42 AM, Ivan Vegvary wrote: After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? Thanks for explanations and comments. Ivan Vegvary My Whirlpool dishwasher and a KitchenAid disposer are on the same 20 amp circuit and never had a problem. I don't know if it meets code but I can't imagine it is unsafe in any way. Did the same here, running two 20 amp lines seemed silly to me. I did run them both at the same time right after I installed them to see if it would trip the breaker while I still had the downstairs wall open. No problems showed up with both under load. Here the disposal only runs while we are cleaning off the plates to put in the dishwasher. The dishwasher isn't turned on until that step is done so in reality they never run at the same time anyway. John If your dishwasher is the type with an electric heating element that's on during the drying cycle, I wonder how much current it draws? 8-) [8~{} Uncle Overload Monster Dunno - but the breaker has never tripped. John |
#16
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Saturday, May 23, 2015 at 9:08:10 AM UTC-4, Mayhem wrote:
On 05/23/2015 06:39 AM, wrote: On Thu, 21 May 2015 20:58:14 -0400, "Robert Green" wrote: +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. Statistically, multiwire/Edison circuits don't have a bad track record but I still wouldn't have one in my home. Not worth the risk. The risk of what exactly? |
#17
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
|
#19
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
Ivan,
After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? For that kind of "Edison" circuit, the two breakers must be on opposite sides of the incoming 240V supply. That way each 120V "hot" leg is out of phase with the other as the AC cycles back and forth. When one leg is positive, the other leg is negative. The neutral never has more than a single load on it. It's a safe and common way to wire some circuits, but I still prefer to run separate cables for each circuit. That way breakers can be moved around in the panel if needed without fear of overloading the cable (if both breakers were placed on the same phase the neutral would carry twice the load). The cost difference of two cables vs a three-wire cable is usually minimal for most homes. Anthony Watson www.mountainsoftware.com www.watsondiy.com |
#20
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Saturday, May 23, 2015 at 11:22:49 AM UTC-4, HerHusband wrote:
Ivan, After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? For that kind of "Edison" circuit, the two breakers must be on opposite sides of the incoming 240V supply. That way each 120V "hot" leg is out of phase with the other as the AC cycles back and forth. When one leg is positive, the other leg is negative. The neutral never has more than a single load on it. AFAIK, there is no other kind of Edison circuit. The whole point of an Edison circuit *requires* that it be on opposite legs. |
#21
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On 5/23/2015 9:19 AM, trader_4 wrote:
On Saturday, May 23, 2015 at 9:08:10 AM UTC-4, Mayhem wrote: On 05/23/2015 06:39 AM, wrote: On Thu, 21 May 2015 20:58:14 -0400, "Robert Green" wrote: +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. Statistically, multiwire/Edison circuits don't have a bad track record but I still wouldn't have one in my home. Not worth the risk. The risk of what exactly? Suppose you have a heavy resistive load on leg 1 and a light load on leg 2 and then suddenly lose the neutral. What happens to the voltage across the light load on leg 2? Would 230 volts smoke a small radio on leg 2? |
#22
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
"Bill" wrote in message b.com... On 5/23/2015 9:19 AM, trader_4 wrote: On Saturday, May 23, 2015 at 9:08:10 AM UTC-4, Mayhem wrote: On 05/23/2015 06:39 AM, wrote: On Thu, 21 May 2015 20:58:14 -0400, "Robert Green" wrote: +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. Statistically, multiwire/Edison circuits don't have a bad track record but I still wouldn't have one in my home. Not worth the risk. The risk of what exactly? Suppose you have a heavy resistive load on leg 1 and a light load on leg 2 and then suddenly lose the neutral. What happens to the voltage across the light load on leg 2? Would 230 volts smoke a small radio on leg 2? That is what happens when the power company's neutral feeding the house goes haywire. |
#23
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Saturday, May 23, 2015 at 11:49:50 AM UTC-4, Bill wrote:
On 5/23/2015 9:19 AM, trader_4 wrote: On Saturday, May 23, 2015 at 9:08:10 AM UTC-4, Mayhem wrote: On 05/23/2015 06:39 AM, wrote: On Thu, 21 May 2015 20:58:14 -0400, "Robert Green" wrote: +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. Statistically, multiwire/Edison circuits don't have a bad track record but I still wouldn't have one in my home. Not worth the risk. The risk of what exactly? Suppose you have a heavy resistive load on leg 1 and a light load on leg 2 and then suddenly lose the neutral. What happens to the voltage across the light load on leg 2? Would 230 volts smoke a small radio on leg 2? That's a valid point. If it happens, you could wind up with up to ~240V on the unfortunate load side, something that can't happen if it's a regular circuit. |
#24
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
"Bill" wrote in message news:5560a19a$0$34404
stuff snipped The risk of what exactly? Suppose you have a heavy resistive load on leg 1 and a light load on leg 2 and then suddenly lose the neutral. What happens to the voltage across the light load on leg 2? Would 230 volts smoke a small radio on leg 2? Magic smoke will be forced out of the small radio perhaps even a loud magic noise, too. (-: While a reputable electrician would probably not make this particular mistake, it's possible for a future modification or rearrangement of breakers in the panel to inadvertently move one or both individual breakers (especially in older work) so that they both end up on the same 120V leg of the panel - which is improper when a shared neutral is involved. If the split circuit is installed that way, the shared unbalanced load could exceed the rating of the wire. Maybe some NEC expert can tell us when the use of a double-pole breaker became a code requirement for Edison circuits because I know it wasn't always that way (or that way in 1988). My kitchen had an Edison circuit *without* a tied breaker until I rewired it with separate runs. Without the tied breakers or a double pole breaker that kills power to both phases, it is quite possible for someone to be shocked while working on the circuit, since the neutral wire of the supposedly "dead" circuit could be carrying current from the sister "live" circuit. DAMHIKT. (-: There's so little benefit, IMHO, that the risk of using Edison circuits today doesn't seem worth it. If voltage drop is a problem, use a larger diameter wire. If you can't afford the extra wire, check the car's seat cushions for spare change or sell some blood. (-: Besides, the last time we had this discussion I believe I pointed out that because "Romex" 12/2 w/G and 14/2 w/G is so widely used, it can often be had on sale for much less than 12/3 or 14/3 w/G, thus totally negating any real savings in wire costs. Same problem with the 2 pole GFCIs needed to protect an Edison circuit. I can always find a good sale price on the single circuit GFCIs. I don't recall ever seeing a double pole unit on sale. I do recall when I looked at 2P GFCIs they cost way more than 2 separate 1P GFCIs. I recall paying a little more than $10 a pop for 20A Leviton GFCIs just a while back when I ran a new sump pump circuit. http://www.google.com/search?q=cost+dual+pole+GFCI The 2P units Google shows are in the $80-$110 range. So it looks like the Edison circuit is going to end up costing way more than two comparable single branches, at least if you don't pay list price for your components. I don't see the tradeoffs being worth it but obviously some people do. For me it violates the KISS rule. -- Bobby G. |
#25
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Sat, 23 May 2015 11:49:39 -0400, Bill wrote:
On 5/23/2015 9:19 AM, trader_4 wrote: On Saturday, May 23, 2015 at 9:08:10 AM UTC-4, Mayhem wrote: On 05/23/2015 06:39 AM, wrote: On Thu, 21 May 2015 20:58:14 -0400, "Robert Green" wrote: +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. Statistically, multiwire/Edison circuits don't have a bad track record but I still wouldn't have one in my home. Not worth the risk. The risk of what exactly? Suppose you have a heavy resistive load on leg 1 and a light load on leg 2 and then suddenly lose the neutral. What happens to the voltage across the light load on leg 2? Would 230 volts smoke a small radio on leg 2? How is that different than loosing the line neutral (which, statistically is much more likely) Then EVERY circuit in the panel will have extra high voltage on the lower load side, and low voltage on the heavily loaded side/ |
#26
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Sat, 23 May 2015 17:53:06 -0400, "Robert Green"
wrote: "Bill" wrote in message news:5560a19a$0$34404 stuff snipped The risk of what exactly? Suppose you have a heavy resistive load on leg 1 and a light load on leg 2 and then suddenly lose the neutral. What happens to the voltage across the light load on leg 2? Would 230 volts smoke a small radio on leg 2? Magic smoke will be forced out of the small radio perhaps even a loud magic noise, too. (-: While a reputable electrician would probably not make this particular mistake, it's possible for a future modification or rearrangement of breakers in the panel to inadvertently move one or both individual breakers (especially in older work) so that they both end up on the same 120V leg of the panel - which is improper when a shared neutral is involved. If the split circuit is installed that way, the shared unbalanced load could exceed the rating of the wire. Maybe some NEC expert can tell us when the use of a double-pole breaker became a code requirement for Edison circuits because I know it wasn't always that way (or that way in 1988). My kitchen had an Edison circuit *without* a tied breaker until I rewired it with separate runs. Without the tied breakers or a double pole breaker that kills power to both phases, it is quite possible for someone to be shocked while working on the circuit, since the neutral wire of the supposedly "dead" circuit could be carrying current from the sister "live" circuit. DAMHIKT. (-: I believe it was a code requirement long before 1988, at least in Ontario. My 1974 house, with a fuse panel, has ganged fuse pullouts for all the split circuits, and they were a requirement back when I helped my electrician father wiring houses as far back as 1965 or 1966. Canadian code is often much more strict than american code when it comes to safety - so what it was in the US of A is anyone's guess. There's so little benefit, IMHO, that the risk of using Edison circuits today doesn't seem worth it. If voltage drop is a problem, use a larger diameter wire. If you can't afford the extra wire, check the car's seat cushions for spare change or sell some blood. (-: Besides, the last time we had this discussion I believe I pointed out that because "Romex" 12/2 w/G and 14/2 w/G is so widely used, it can often be had on sale for much less than 12/3 or 14/3 w/G, thus totally negating any real savings in wire costs. Same problem with the 2 pole GFCIs needed to protect an Edison circuit. I can always find a good sale price on the single circuit GFCIs. I don't recall ever seeing a double pole unit on sale. I do recall when I looked at 2P GFCIs they cost way more than 2 separate 1P GFCIs. I recall paying a little more than $10 a pop for 20A Leviton GFCIs just a while back when I ran a new sump pump circuit. http://www.google.com/search?q=cost+dual+pole+GFCI The 2P units Google shows are in the $80-$110 range. So it looks like the Edison circuit is going to end up costing way more than two comparable single branches, at least if you don't pay list price for your components. I don't see the tradeoffs being worth it but obviously some people do. For me it violates the KISS rule. |
#27
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Sat, 23 May 2015 15:21:36 +0000 (UTC), HerHusband
wrote: Ivan, After running two separate circuits for my daughter's dishwasher and waste disposal, I was told that I could have simply run a three wire cable (still 2 breakers) from the panel box and fed the appliances separately. I understand the concept, but, there would be 2 hot wires and only one neutral. Would not that neutral carry twice the current it is designed for? For that kind of "Edison" circuit, the two breakers must be on opposite sides of the incoming 240V supply. That way each 120V "hot" leg is out of phase with the other as the AC cycles back and forth. When one leg is positive, the other leg is negative. The neutral never has more than a single load on it. It's a safe and common way to wire some circuits, but I still prefer to run separate cables for each circuit. That way breakers can be moved around in the panel if needed without fear of overloading the cable (if both breakers were placed on the same phase the neutral would carry twice the load). The cost difference of two cables vs a three-wire cable is usually minimal for most homes. Anthony Watson www.mountainsoftware.com www.watsondiy.com You end up needing to use oversized boxes to handle the wire fill in many cases, and again, CANADIAN code requires (or at least required in the past) 2 circuits in the same box to be on a tied breaker or a pullout fuse block whether they are split/siamesed or totally separate. If you kill a circuit in a box, you have (in canada) the assurance that if wired to code, the entire box is deader than a herring. |
#28
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Saturday, May 23, 2015 at 7:04:47 PM UTC-4, wrote:
On Sat, 23 May 2015 11:49:39 -0400, Bill wrote: On 5/23/2015 9:19 AM, trader_4 wrote: On Saturday, May 23, 2015 at 9:08:10 AM UTC-4, Mayhem wrote: On 05/23/2015 06:39 AM, wrote: On Thu, 21 May 2015 20:58:14 -0400, "Robert Green" wrote: +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. Statistically, multiwire/Edison circuits don't have a bad track record but I still wouldn't have one in my home. Not worth the risk. The risk of what exactly? Suppose you have a heavy resistive load on leg 1 and a light load on leg 2 and then suddenly lose the neutral. What happens to the voltage across the light load on leg 2? Would 230 volts smoke a small radio on leg 2? How is that different than loosing the line neutral (which, statistically is much more likely) Then EVERY circuit in the panel will have extra high voltage on the lower load side, and low voltage on the heavily loaded side/ I guess the argument can be made that the less points of potential failure like that, the better. And if it's the service netural that goes open, it's probably less likely that you'd have a big imbalance because for a whole house, there would be many loads on each leg, tending to average things out. So, I think the possibility that you'd see close to 240V appear on one leg would be a lot less. |
#29
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
wrote in message
stuff snipped in line Maybe some NEC expert can tell us when the use of a double-pole breaker became a code requirement for Edison circuits because I know it wasn't always that way (or that way in 1988). My kitchen had an Edison circuit *without* a tied breaker until I rewired it with separate runs. I believe it was a code requirement long before 1988, at least in Ontario. I don't live in Canada. Best I can find is that it became part of the code in 2008, but that's certainly not definitive - just came across a few discussions that seem to indicate that's when the NEC required the tie handle or dual pole breakers. My 1974 house, with a fuse panel, has ganged fuse pullouts for all the split circuits, and they were a requirement back when I helped my electrician father wiring houses as far back as 1965 or 1966. In Canada, perhaps, but I don't think that was the rule in the US based on the reading I've done. Perhaps an American NEC expert has the answer. I know we used to have some NEC-heads here once upon a time. Canadian code is often much more strict than american code when it comes to safety - so what it was in the US of A is anyone's guess. Well, I suspect it's not a guess, but a very clearly documented fact that we just don't have yet and since I cleared my browser history, I can't even provide the cites that implied it was a relatively new code requirement in the US. I believe it became mandatory in 2008, but that's a guess - it wasn't what I was paying attention to. The bottom line for me is WHY would anyone use an Edison circuit and a *very* costly two pole GFCI (compared to two single pole) when they could get by easily with two discrete circuits? It also seems counter-intuitive to plug two power-hungry devices into the same outlet which is what gets done with a split-wire receptacle. Maybe you save some bucks by not having to rough in a second outlet but my personal rule of thumb is that you can't have enough outlets in today's modern kitchen. Using a split-wire receptacle seems to reduce rather than increase the total outlet count. Then, someone might use one of those one-to-six outlet adapters which, depending on how they are wired, will burn up when plugged in because it combines the hots of both sides of the split-wire receptacle. I'm sorry, but just because Canada does it that way doesn't mean it's superior in any way. From what I can determine, it's NOT safer and it's not cheaper. So why bother? If you list out the pros and cons, the biggest con turns out to be the high cost of a two pole GFCI protector. That cost totally negates any potential saving in wiring $ except in huge houses. The fact that 12/3 and 14/3 is far more difficult to find on sale also tends to negate the cost saving. In addition, running two high amperage devices like skillets and toasters out of one outlet box would, IMHO, tend to increase the chances of overheating something in that box. It could be anything from a bad backstab to an improperly inserted plug. And if that neutral back stab fails for any reason, you've got the potential magic smoke problem again. There's also the question of whether bringing 240 volts into a wet kitchen area into one single box is a good idea to begin with. Anything that goes wrong becomes a potentially much more lethal 240 volt event. So what makes an Edison circuit so great that they are mandated in Canada, eh? (-: I still don't see it. A second outlet run to the kitchen would probably cost less, in materials at least, than wiring up an Edison circuit. That second, standard 20A circuit would also be much more likely to survive a repair attempt by a homeowner than an Edison-type circuit. I seem to recall someone here in the past had trouble distinguishing a switched outlet from an Edison circuit, yet another reason to avoid them. I believe the only reason I had an Edison circuit here is that the house was built in the year of the steel penny when copper was in such short supply the US Mint stopped using it to make pennies that year. When WWIII comes and copper becomes incredibly precious *again* I'll consider wiring with Edison circuits, but until then I'm happy with my on-sale $10USD GFCIs, my 250 ft coils of 12/2 w/g (blue, by the way, in case anyone from the color coding of NM wire thread is reading) and my extra *metal* junction and outlet boxes. KISS unless you live in the Great White North, I guess. (-: -- Bobby G. |
#30
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Sunday, May 24, 2015 at 8:11:24 AM UTC-4, wrote:
On Sat, 23 May 2015 10:00:38 -0400, wrote: What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. +1. To an electrician they are absolutely no problem when properly used. Any time there are 2 circuits in a single box, it is the "only" way to be legal. Huh? There is nothing "illegal" about 2 circuits in a box. As usual, he likes to just make it up as he goes. |
#31
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Sunday, May 24, 2015 at 7:15:51 AM UTC-4, Robert Green wrote:
wasn't what I was paying attention to. The bottom line for me is WHY would anyone use an Edison circuit and a *very* costly two pole GFCI (compared to two single pole) when they could get by easily with two discrete circuits? It also seems counter-intuitive to plug two power-hungry devices into the same outlet which is what gets done with a split-wire receptacle. Another factor is if you go the peculiar split receptacle approach that Clare says they use up north, you can forget about having the GFCI at the receptacle, where it's easy to reset/test. I've never seen a receptacle with built-in GFCI that's double pole. So, you'd need a double pole one at the panel. I'd rather have it near where the receptacle is. I don't get the whole idea behind splitting a receptacle and putting each half on different legs. Here I see it done sometimes to put one half on a switch, the other on all the time, on the *same* circuit. That makes sense. Say what you want about Edison circuits, but this Canadian thing, I don't understand what the purpose is all about. And also, if you want to start in about potentially having two different circuits in a box live, it's funny that Edison gets dragged in as the solution. It would seem to me the finger should be pointed at whoever up in Canada required their screwy split outlets. There's also the question of whether bringing 240 volts into a wet kitchen area into one single box is a good idea to begin with. Anything that goes wrong becomes a potentially much more lethal 240 volt event. For the most part, it's not going to create a more lethal environment. If it gets wet, energizes some metal, etc, you still only wind up with 120V to ground. To get 240V, you'd have to somehow wind up across both legs, and that kind of fault would be extremely rare. |
#32
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On 05/24/2015 07:57 AM, wrote:
On Sat, 23 May 2015 09:08:06 -0400, Mayhem wrote: On 05/23/2015 06:39 AM, wrote: On Thu, 21 May 2015 20:58:14 -0400, "Robert Green" wrote: +1 Saving the cost of a single wire and an extra breaker isn't worth the problems that can arise from using Edison circuits. He's dead. They should be, too. (-: -- Bobby G. What "problems"? There are certainly advantages beyond saving 2 wires per circuit. Not the least of which is voltage drop mitigation. (up to 50%). You also get to use smaller/fewer boxes. It is only a problem for people who do not understand what they are looking at and they shouldn't be fooling with them in the first place. Statistically, multiwire/Edison circuits don't have a bad track record but I still wouldn't have one in my home. Not worth the risk. You have several (dryers, ranges and any other 240v appliance with a 120v load), get over it. There's nothing to "get over". The shared 120 volt control circuit contained within the metal cabinet of the 240 volt appliance is typically protected (current limited) by a 1 amp fuse or so. The $10 chinese radio plugged into an Edison circuit wall outlet...not so much. There may also be some on the 120v circuits you do not know about. Not in my home but you are welcome to as many Edison circuits as you like. I fully support your right to do so. It was common to wire bedrooms on a multiwire if they were on the other end of the house and split them out in a ceiling light box. It's also common and code compliant to use clamps on ground rods too but they always seem to corrode and become loose over time. I always use an exothermic CADWELD connection. Does the fact I don't use mechanical clamps bother you too? |
#33
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
|
#34
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
"Mayhem" wrote in message ... On 05/23/2015 07:04 PM, wrote: How is that different than loosing the line neutral (which, statistically is much more likely) Losing the neutral in *my* entrance panel is extremely unlikely. I actually check my panel and meter pan connection every 5 years. Of course the poco neutral is tagged to ground at my panel as well. Then EVERY circuit in the panel will have extra high voltage on the lower load side, and low voltage on the heavily loaded side/ I have lost the power company's neutral TWICE in the past year and a half. Once it just broke in the middle of the span from the pole to the house, and once it broke right at the pole mounted transformer. the first time I had no damage, the second time (when I was not even at home with anything on but maybe a couple security lights) I had a couple of blown GFCI outlets - and I mean BLOWN. Fire! Luckily the wallboard was not flammable, but there were scorch marks, even on the kitchen cabinets. Utility paid off quickly, but it didn't amount to much (maybe I should have put in for a new TV?) |
#35
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On 05/24/2015 11:45 AM, taxed and spent wrote:
I have lost the power company's neutral TWICE in the past year and a half. Once it just broke in the middle of the span from the pole to the house, and once it broke right at the pole mounted transformer. Since you lose poco neutral so frequently, consider having a proper ground rod system installed. |
#36
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
"Mayhem" wrote in message ... On 05/24/2015 11:45 AM, taxed and spent wrote: I have lost the power company's neutral TWICE in the past year and a half. Once it just broke in the middle of the span from the pole to the house, and once it broke right at the pole mounted transformer. Since you lose poco neutral so frequently, consider having a proper ground rod system installed. I do, but that will not end the problems created with a lost neutral. |
#37
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
On Sun, 24 May 2015 06:59:58 -0400, "Robert Green"
wrote: wrote in message stuff snipped in line Maybe some NEC expert can tell us when the use of a double-pole breaker became a code requirement for Edison circuits because I know it wasn't always that way (or that way in 1988). My kitchen had an Edison circuit *without* a tied breaker until I rewired it with separate runs. I believe it was a code requirement long before 1988, at least in Ontario. I don't live in Canada. Best I can find is that it became part of the code in 2008, but that's certainly not definitive - just came across a few discussions that seem to indicate that's when the NEC required the tie handle or dual pole breakers. My 1974 house, with a fuse panel, has ganged fuse pullouts for all the split circuits, and they were a requirement back when I helped my electrician father wiring houses as far back as 1965 or 1966. In Canada, perhaps, but I don't think that was the rule in the US based on the reading I've done. Perhaps an American NEC expert has the answer. I know we used to have some NEC-heads here once upon a time. Canadian code is often much more strict than american code when it comes to safety - so what it was in the US of A is anyone's guess. Well, I suspect it's not a guess, but a very clearly documented fact that we just don't have yet and since I cleared my browser history, I can't even provide the cites that implied it was a relatively new code requirement in the US. I believe it became mandatory in 2008, but that's a guess - it wasn't what I was paying attention to. The bottom line for me is WHY would anyone use an Edison circuit and a *very* costly two pole GFCI (compared to two single pole) when they could get by easily with two discrete circuits? It also seems counter-intuitive to plug two power-hungry devices into the same outlet which is what gets done with a split-wire receptacle. Maybe you save some bucks by not having to rough in a second outlet but my personal rule of thumb is that you can't have enough outlets in today's modern kitchen. Using a split-wire receptacle seems to reduce rather than increase the total outlet count. Then, someone might use one of those one-to-six outlet adapters which, depending on how they are wired, will burn up when plugged in because it combines the hots of both sides of the split-wire receptacle. I'm sorry, but just because Canada does it that way doesn't mean it's superior in any way. From what I can determine, it's NOT safer and it's not cheaper. So why bother? It makes it virtually impossible to overload a circuit when each half of a duplex receptacle is on a separate circuit. You can plug a toaster and a coffemaker into one "outlet" with no danger of overloading it - and only have one wire required to be pulled for each "outlet" - giving you, in effect, a 30 amp circuit. What I have seen done for dual GFCI (And even single gfci) protection is to run from the panel to a box with a gfci outlet, and feed-through from there to the house circuit. The GFCI protector is on the panel board with the electrical service panel, but is not IN the panel (for cases where a gfci or dual gfci is either not available or rediculously over-priced) If you list out the pros and cons, the biggest con turns out to be the high cost of a two pole GFCI protector. That cost totally negates any potential saving in wiring $ except in huge houses. The fact that 12/3 and 14/3 is far more difficult to find on sale also tends to negate the cost saving. In addition, running two high amperage devices like skillets and toasters out of one outlet box would, IMHO, tend to increase the chances of overheating something in that box. It could be anything from a bad backstab to an improperly inserted plug. And if that neutral back stab fails for any reason, you've got the potential magic smoke problem again. There's also the question of whether bringing 240 volts into a wet kitchen area into one single box is a good idea to begin with. Anything that goes wrong becomes a potentially much more lethal 240 volt event. So what makes an Edison circuit so great that they are mandated in Canada, eh? (-: I still don't see it. A second outlet run to the kitchen would probably cost less, in materials at least, than wiring up an Edison circuit. That second, standard 20A circuit would also be much more likely to survive a repair attempt by a homeowner than an Edison-type circuit. I seem to recall someone here in the past had trouble distinguishing a switched outlet from an Edison circuit, yet another reason to avoid them. I believe the only reason I had an Edison circuit here is that the house was built in the year of the steel penny when copper was in such short supply the US Mint stopped using it to make pennies that year. When WWIII comes and copper becomes incredibly precious *again* I'll consider wiring with Edison circuits, but until then I'm happy with my on-sale $10USD GFCIs, my 250 ft coils of 12/2 w/g (blue, by the way, in case anyone from the color coding of NM wire thread is reading) and my extra *metal* junction and outlet boxes. KISS unless you live in the Great White North, I guess. (-: |
#38
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
|
#39
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
wrote in message
... On Sun, 24 May 2015 06:59:58 -0400, "Robert Green" wrote: wrote in message stuff snipped in line I'm sorry, but just because Canada does it that way doesn't mean it's superior in any way. From what I can determine, it's NOT safer and it's not cheaper. So why bother? It makes it virtually impossible to overload a circuit when each half of a duplex receptacle is on a separate circuit. You can plug a toaster and a coffemaker into one "outlet" with no danger of overloading it - and only have one wire required to be pulled for each "outlet" - giving you, in effect, a 30 amp circuit. Disagree. Teaching people to plug high amperage appliances into the SAME outlet is just wrong. They'll tend to generalize and think EVERY outlet can handle 30 or 40A loads. What does your average Joe Homeowner know about Edison circuits? Nada, zip, bupkiss. Because it's SO simple to add an extra box and circuit when you're doing the work, it seems like very false economy to save a little money (maybe - you've read my comments on wire costs and sales) and create an outlet that encourages people to overload *all* outlets because "the one in the kitchen never blows a breaker." Joe Homeowner is hardly likely to know that just those outlets in the kitchen can handle multiple high-amp loads plugged into them. If running large loads out of one duplex outlet is the main reason for using Edison circuits (and it's a weak one IMHO) I counter by saying you can do exactly the same thing with a discrete feed from two breakers at the panel with no shared neutral. Same effect. Then you can pull 40A from one duplex outlet if that's what floats your boat. Doing it with two discrete circuits and no shared neutral means you can use single pole (and MUCH cheaper) GFCIs using the downstream options or GFCI breakers in the circuit panel. I'm still not convinced Edison circuits are saving anyone any money or makes them safer in any way. Mostly what I've heard is "gee, you can run one less conductor" as if that's really a substantial savings in wiring or labor costs. It's not if you're going to run a new cable anyway. What I have seen done for dual GFCI (And even single gfci) protection is to run from the panel to a box with a gfci outlet, and feed-through from there to the house circuit. The GFCI protector is on the panel board with the electrical service panel, but is not IN the panel (for cases where a gfci or dual gfci is either not available or rediculously over-priced) Explain to me again how you can GFCI protect an Edison circuit with two one pole GFCIs? The current in a shared neutral fluctuates with the load on both phases. Only a dual pole GFCI can monitor both hots simultaneously as I understand it. From what I've read at least some people who have tried to install two single pole GFCIs on an Edison circuit have been plagued by nuisance trips. Others have had success, apparently, by separating the shared neutral into two discrete wires before connection to the GFCIs. But that's no longer a true Edison circuit. There may be a proper way to do it, but it seems inordinately "klugy" to try to force two single pole GFCIs to do something they weren't designed to do. It seems a long way to go for very little reward. Just run two circuits instead of an Edison circuit and you can use the much cheaper single pole GFCIs and you can use them in the pass-through mode to protect all downstream outlets. I'm not the only one who isn't sanguine about MWCs: https://www.mikeholt.com/mojonewsarc...200202 18.htm ---------------------------------------------------------------------------- --------------------- Destruction of Equipment. Never remove the grounded (neutral) conductor from the grounded terminal bar in the panelboard if the phase conductors are energized. The grounded (neutral) conductor you remove could be part of a multiwire branch circuit, so this could result in destruction of electrical equipment. More important, even if the return conductor is not part of a multiwire circuit, removing a conductor from the grounded terminal bar when the circuit is energized could result in injury due to shock or arcing. A typical 3-wire circuit is actually two otherwise-separate parallel circuits with a common conductor. If the grounded (neutral) conductor is accidentally opened, the circuit changes from two separate parallel 120 V circuits to one 240 V series circuit. This can result in fires and the total destruction of electrical equipment. For example: A single-phase, 3-wire, 120/240 V circuit supplies a 1,275 W, 120 V hair dryer and a 600 W, 120V television. If the grounded (neutral) conductor is interrupted, it will cause the 120 V television to operate at 163 V and consume 1,110 W of power (instead of 600 W) for only a few seconds before it burns up. Figure Step 1. Determine the resistance of each appliance, R = E2/P. a.. Hair dryer rated 1275 watts at 120 volts. b.. R = E2/P, R = 1202/1275 = 11.3 ohms c.. Television rated 600 watts at 120 volts. d.. R = E2/P, R = 1202/600 = 24 ohms Step 2. Determine the circuit resistance: RT = R1 + R2 a.. RT = 11.3 ohms + 24 ohms = RT = 35.3 ohms Step 3. Determine the current of the circuit: IT = ES/RT a.. IT = 240 V/35.3 ohms = 6.8 A Step 4. Determine the voltage for each appliance: E = IT x Rx a.. Hair dryer: 6.8 A x 11.3 ohms = 76.84 volts b.. Television: 6.8 A x 24 ohms = 163.2 volts The 120 V rated TV in the split second before it burns up or explodes is operating at 163.2 volts. Step 5. Determine the power consumed by each appliance: P = E2/R a.. Hair Dryer: P = 76.82/11.3 = 522 watts b.. Television: P = 163.22/24 = 1100 watts The 600 W, 120 V rated TV will operate at 163 volts and consume 1110 watts. You can kiss this TV goodbye! ---------------------------------------------------------------------------- --------------------- All to save (perhaps) a few bucks on cable costs. Not worth it. -- Bobby G. |
#40
Posted to alt.home.repair
|
|||
|
|||
Electrical code question
wrote in message
You usually run out of sockets long before you run out of amps. No truer words were ever spoken. It seems to me that the MWC *reduces* the available outlet count and encourages people to use "cheaters" like six-way plug-in adapters to get more outlets. They can be pretty dangerous if the hots are connected in the adapter. I've used some. The older ones did tie the neutrals together but the newer ones don't. The cheapest of them had press-fit connectors between the outlets and the internal bus bar of the adapter. When one of the connections came loose, it arced and melted the adapter. -- Bobby G. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Question about electrical code | Home Repair | |||
Electrical Code question | Home Repair | |||
Electrical code question | Home Repair | |||
Electrical code question | Home Repair | |||
Electrical code question... | Home Repair |