What could cause this:
GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? |
#2
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"DerbyDad03" wrote in message ... What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? Sounds like a typical digital meter with the ground wire not attached at the breaker box. Or at least some where between the GFCI and breaker box. Check the ground at the breaker and also at any place it may connect in between. |
#3
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On 2/26/2012 1:54 PM, DerbyDad03 wrote:
What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? first thought is to **** can the digital and use an analog meter. Then retest. -- Steve Barker remove the "not" from my address to email |
#4
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 4:04*pm, Steve Barker wrote:
On 2/26/2012 1:54 PM, DerbyDad03 wrote: What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? first thought is to **** can the digital and use an analog meter. *Then retest. -- Steve Barker remove the "not" from my address to email ....or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. |
#5
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"DerbyDad03" wrote in message ... On Feb 26, 4:04 pm, Steve Barker wrote: first thought is to **** can the digital and use an analog meter. Then retest. -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. Most do not understand this. That is why you are seeing such oddball voltages on the circuit. |
#6
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
DerbyDad03 wrote: What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? Hmmm, Are you using DVM? No analog meter? GND is missing. |
#7
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
Ralph Mowery wrote: wrote in message ... On Feb 26, 4:04 pm, Steve wrote: first thought is to **** can the digital and use an analog meter. Then retest. -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. Most do not understand this. That is why you are seeing such oddball voltages on the circuit. Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. |
#8
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. |
#9
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery"
wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. |
#10
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
When wires are next to each other, and carrying AC (such as in Romex, and
under load). The power wire tends to put a tiny bit of voltage into the nearby wire, acting as though it were a transformer. What you are reading is probably that stray, induced voltage. it shows on your meter, because the meter consumes nearly zero of the power in what's being read. If you had any kind of load at all between H and G, the ghost voltage would disappear instantly. The voltage is also called "ghost reading" or some such name. Christopher A. Young Learn more about Jesus www.lds.org .. "DerbyDad03" wrote in message ... What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? |
#11
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 4:41*pm, "Ralph Mowery" wrote:
"DerbyDad03" wrote in message ... On Feb 26, 4:04 pm, Steve Barker wrote: first thought is to **** can the digital and use an analog meter. Then retest. -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. *Most do not understand this. That is why you are seeing such oddball voltages on the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Still think it's operator error? |
#12
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 5:32*pm, "
wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. |
#13
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 14:58:44 -0800 (PST), DerbyDad03
wrote: On Feb 26, 4:41*pm, "Ralph Mowery" wrote: "DerbyDad03" wrote in message ... On Feb 26, 4:04 pm, Steve Barker wrote: first thought is to **** can the digital and use an analog meter. Then retest. -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. *Most do not understand this. That is why you are seeing such oddball voltages on the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Still think it's operator error? No, it sounds like the open ground your three-light tester told you it was. Are there any other outlets on that circuit? Test them, too. |
#14
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03
wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. Essentially, you do have an open ground, like the TLT was telling you. Where it is in the next question. Use the TLT on another outlet in this circuit. Testing both an outlet before and one after will nail it down pretty well. If the one after is fine, then there is a good chance that the fault is within the GFCI itself. |
#15
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"DerbyDad03" wrote in message ... -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. Most do not understand this. That is why you are seeing such oddball voltages on the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Still think it's operator error? Not so much as operator error, but a case where the operator does not understand how it is possiable. We (the others and myself) are just trying to educate you about how it is possiable for a meter to show voltages like what you have. WE go through this almost once a month here where someone has a digital meter and will see the same thing. I think several others mentioned a digital meter before you told us what you were using. |
#16
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 6:45*pm, "
wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. |
#17
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 7:19*pm, "Ralph Mowery" wrote:
"DerbyDad03" wrote in message ... -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. Most do not understand this. That is why you are seeing such oddball voltages on the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Still think it's operator error? Not so much as operator error, but a case where the operator does not understand how it is possiable. We (the others and myself) are just trying to educate you about how it is possiable for a meter to show voltages like what you have. *WE go through this almost once a month here where someone has a digital meter and will see the same thing. I think several others mentioned a digital meter before you told us what you were using. So are you saying that with an open ground an analog meter would not show any reading between the hot or neutral and the ground prong at the receptacle? |
#18
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 11:54:58 -0800 (PST), DerbyDad03
wrote: What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? Get an analog meter, with a needle, and use that. It has other advantages too. You can watch a capaciitor charge from the battery in the ohmmeter and see it accept current more slowly as it charges. You can with all but the smallest caps tell if it's good or not, IMO, excpet for whether it is no good at higher voltages than the meter battery. I think I read that the cheap harbor freight digiital meters only have 1Meg resistance, or 1 meg per volt conceivabley, when meaasureing voltage, but even that is a lot higher than most analog meters at 50K/v iirc. |
#19
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 7:19*pm, "Ralph Mowery" wrote:
"DerbyDad03" wrote in message ... -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. Most do not understand this. That is why you are seeing such oddball voltages on the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Still think it's operator error? Not so much as operator error, but a case where the operator does not understand how it is possiable. We (the others and myself) are just trying to educate you about how it is possiable for a meter to show voltages like what you have. *WE go through this almost once a month here where someone has a digital meter and will see the same thing. I think several others mentioned a digital meter before you told us what you were using.- Hide quoted text - - Show quoted text - Plugging a light bulb into the circuit doesn't change anything because it doesn't introduce any ground current. It's just flowing current between hot and neutral and you already know that voltage is normal. In a properly grounded circuit, you could hook a light bulb between hot and ground and it should light. If you try that in the problem circuit, my bet is that it will not light, because you have an open ground somewhere along the circuit. The circuit tester showed there was no ground. With the high impedance meter whenyou connect it between hot and an unconnected ground wire, you're going to get a reading of some in between voltage because whatever ground wire is there has capacitance, inductance, etc. |
#20
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 13:31:48 -0800 (PST), DerbyDad03
wrote: On Feb 26, 4:04*pm, Steve Barker wrote: On 2/26/2012 1:54 PM, DerbyDad03 wrote: What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? first thought is to **** can the digital and use an analog meter. *Then retest. -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. Steve did seem to say the meter was bad, but my first reply to you doesn't say that. It's just not suitable for this applicatoin, perhaps. I don't think the other receptacles prove much. Induced voltages depend on what is nearby to induce them. . |
#21
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 11:54:58 -0800 (PST), DerbyDad03
wrote: What could cause this: GFCI on a supposedly grounded circuit. Wires appear to be installed correctly at the GFCI. 3 light tester shows Open Ground. It doesn't change my other posts much, but I must admit I didnt' notice this. Duh. Why not fix the open ground and then measure again. 115V between hot and neutral 54V between hot and ground lug 46V between neutral and ground lug Thoughts? |
#22
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 14:58:44 -0800 (PST), DerbyDad03
wrote: On Feb 26, 4:41*pm, "Ralph Mowery" wrote: "DerbyDad03" wrote in message ... On Feb 26, 4:04 pm, Steve Barker wrote: first thought is to **** can the digital and use an analog meter. Then retest. -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. *Most do not understand this. That is why you are seeing such oddball voltages on the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. I don't think the stray voltage we talked about is affected by turning on a lamp. The lamp draws only from the hot wire and normally returns only though the neutral . You have a problem with the ground. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Still think it's operator error? |
#23
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
DerbyDad03 wrote: On Feb 26, 7:19 pm, "Ralph wrote: wrote in message ... -- Steve Barker remove the "not" from my address to email ...or I could test 3 other grounded circuits in the same house and see what that same meter reads. In all three cases the meter reads: 115V between hot and neutral 115V between hot and ground lug 0V between neutral and ground lug I'm guessing the meter's fine and the problem is with the circuit. The meter is fine, it is the meter operator. Many digital meters will not load a circuit so that even the smallest ammount of induced voltage will show up. Most do not understand this. That is why you are seeing such oddball voltages on the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Still think it's operator error? Not so much as operator error, but a case where the operator does not understand how it is possiable. We (the others and myself) are just trying to educate you about how it is possiable for a meter to show voltages like what you have. WE go through this almost once a month here where someone has a digital meter and will see the same thing. I think several others mentioned a digital meter before you told us what you were using. So are you saying that with an open ground an analog meter would not show any reading between the hot or neutral and the ground prong at the receptacle? Hi, B4 you ask that question, do you understand the difference between high impedance and low impedance measuring instrument and inductive coupling? Low impedance ones will load the circuit down so ghost voltages won't show vs. high impedance meter. You have to know what to expect with your meter at certain test condition lest you should get carried away chasing the ghost. Do an experiment. With your meter set in voltage reading, hold test leads with your fingers, most likely you will see some reading. Another experiment, put a light bulb across hot and ground lead which showed voltage reading, does the bulb come on? at 57V, it should burn at least half brightness. That voltage was bogus(ghost) value. |
#24
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"DerbyDad03" wrote in message ... So are you saying that with an open ground an analog meter would not show any reading between the hot or neutral and the ground prong at the receptacle? Yes. It may show a voltage, but it will be a lot lower if it does. YOu may think of what is going on similar to a car battery. It will start the car. If you have 8 D cell batteries in series for 12 volts and try to start the car, it will not. The D cells can not supply the current for the load. The induced voltage or whatever people want to call it is at a very low current. Most digital meters will not have much of a load and will show a higher voltage than the analog meters. If you put a digital meter and analog meter on the same wires at the same time, they will both show the same voltage. Take the digital meter off and the analog meter will hardly show any more voltage. Put both back on and then take the analog meter off and the digital meter will show a much higher voltage. |
#25
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03
wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. You can probably do that without removing the outlet from the box. You should also be able to inspect the connection without pulling it. Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent). |
#26
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 4:30*pm, DerbyDad03 wrote:
On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. You're homing in on the solution. My best guess..... loose connection between panel & GFI box. btw those three light testers can be fooled by some unusual conditions here's a link to a website http://www.thecircuitdetective.com/test.htm Scroll down about half way & there is a detailed discussion of the 3- prong plug in tester. These plug-in testers are handy but not perfect, they can give misleading results in some situations. cheers Bob |
#27
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 27, 2:57*am, DD_BobK wrote:
On Feb 26, 4:30*pm, DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. You're homing in on the solution. My best guess..... *loose connection between panel & GFI box. btw those three light testers can be fooled by some unusual conditions here's a link to a website http://www.thecircuitdetective.com/test.htm Scroll down about half way & there is a detailed discussion of the 3- prong plug in tester. These plug-in testers are handy but not perfect, they can give misleading results in some situations. cheers Bob- Hide quoted text - - Show quoted text - There's also a minor, but interesting issue with those testers. With the latest method of installing 3 prong receptacles with the ground prong up, the testers (at least mine) are manufactured upside down. When you plug one into a "ground prong up" receptacle, you can't read the chart and have to remember to reverse the light indications since they are "backwards" when the tester is plugged in. |
#28
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 26, 10:53*pm, "
wrote: On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground.. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? *Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. *The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. *You can probably do that without removing the outlet from the box. *You should also be able to inspect the connection without pulling it. *Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? *You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. *That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent).- Hide quoted text - - Show quoted text - In all honesty, I had already pulled the GFCI just to eliminate it as a factor before I ran my suicide cord. I replaced it with a 3 prong receptacle and disconnected the downstream devices so that there was only the single 3 prong receptacle on the run. When it still showed the open ground - even though there was a ground wire attached - that's when I started tracing back and found the prvious junction box. I'll be opening that tonight to look at the ground situation. As far as pulling a new grounded run from the panel to the junction box, you asked "Why bother?" Well, this is the last room in the house without 3 prong grounded receptacles. That's why I started by adding the GFCI - so I could at least install 3 prong receptacles downstream, mainly for the convenience of having 3 prong receptacles available. Eventually, I want to run grounded romex to all of the downstream receptacles, but that is going to require moving some storage in the basement so it's going to take some time. Since the feed to the junction box has a ground wire, it appeared that things would flow fairly smoothly in the forward direction from the junction box on. Now that I'm showing an open ground, I have to go backward and at a minimum find out why. I'm just not comfortable knowing that a non-grounded ground wire is attached in the junction box and at the GFCI. It'll gnaw at me until I fix it. |
#29
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On 2/26/2012 4:27 PM, Ralph Mowery wrote:
"Tony wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. This can be rather bizarre the first time you see it. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Fluke has a small gizmo (SV225) that plugs into the meter jacks, then the meter leads plug into it. It adds a relatively low resistance across the leads to eliminate phantom voltage. http://www.fluke.com/Fluke/usen/Acce....htm?PID=56696 -- bud-- |
#30
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 27, 10:29*am, bud-- wrote:
On 2/26/2012 4:27 PM, Ralph Mowery wrote: "Tony *wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. This can be rather bizarre the first time you see it. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Fluke has a small gizmo (SV225) that plugs into the meter jacks, then the meter leads plug into it. It adds a relatively low resistance across the leads to eliminate phantom voltage. http://www.fluke.com/Fluke/usen/Acce...Chargers-and-A... -- bud-- The site says: "It can be used with all modern meters with standard input spacing." I wonder if their own Model 75 series is considered "modern" and/or "standard". It would have been nice if they followed that statement with an actual measurement so that readers could easily determine if the device was compatible with the meter they own. BTW...does that statement mean that it can't be used with "old" meters with standard input spacing? ;-) |
#31
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On 2/27/2012 10:38 AM, DerbyDad03 wrote:
On Feb 27, 10:29 am, wrote: On 2/26/2012 4:27 PM, Ralph Mowery wrote: "Tony wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. This can be rather bizarre the first time you see it. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Fluke has a small gizmo (SV225) that plugs into the meter jacks, then the meter leads plug into it. It adds a relatively low resistance across the leads to eliminate phantom voltage. http://www.fluke.com/Fluke/usen/Acce...Chargers-and-A... -- bud-- The site says: "It can be used with all modern meters with standard input spacing." I wonder if their own Model 75 series is considered "modern" and/or "standard". It would have been nice if they followed that statement with an actual measurement so that readers could easily determine if the device was compatible with the meter they own. BTW...does that statement mean that it can't be used with "old" meters with standard input spacing? ;-) My Fluke has the jacks on 3/4" centers. I would call the probe plugs shielded banana plugs (plastic cylinder around the plug). I assume the Fluke adampter can be used with any meter with 3/4" spaced shielded banana plugs. Or I would guess you could cut off the insulating shield and use it with 3/4" spaced banana jacks. My Simpson 260 has jacks on 5/8" centers - wouldn't work. All measuring tools have limitations. Part of the challenge of making measurements is knowing what the limitations are. For something like you are doing I would commonly use a pig-tail socket and a 40W bulb as a 'voltmeter'. I use a neon test light a lot more than I use a meter. -- bud-- |
#32
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Mon, 27 Feb 2012 06:27:01 -0800 (PST), DerbyDad03
wrote: On Feb 26, 10:53*pm, " wrote: On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? *Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. *The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. *You can probably do that without removing the outlet from the box. *You should also be able to inspect the connection without pulling it. *Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? *You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. *That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent).- Hide quoted text - - Show quoted text - In all honesty, I had already pulled the GFCI just to eliminate it as a factor before I ran my suicide cord. I replaced it with a 3 prong receptacle and disconnected the downstream devices so that there was only the single 3 prong receptacle on the run. When it still showed the open ground - even though there was a ground wire attached - that's when I started tracing back and found the prvious junction box. I'll be opening that tonight to look at the ground situation. As far as pulling a new grounded run from the panel to the junction box, you asked "Why bother?" Well, this is the last room in the house without 3 prong grounded receptacles. That's why I started by adding the GFCI - so I could at least install 3 prong receptacles downstream, mainly for the convenience of having 3 prong receptacles available. Eventually, I want to run grounded romex to all of the downstream receptacles, but that is going to require moving some storage in the basement so it's going to take some time. My point is that, in your case, you don't need a ground to install 3-prong receptacles. The GFCI does the job. The GFCI doesn't need a ground, either. Everything should be good as it is. Well, except the ungrounded 3-prong outlets have to be marked "ungrounded". Since the feed to the junction box has a ground wire, it appeared that things would flow fairly smoothly in the forward direction from the junction box on. Now that I'm showing an open ground, I have to go backward and at a minimum find out why. I'm just not comfortable knowing that a non-grounded ground wire is attached in the junction box and at the GFCI. It'll gnaw at me until I fix it. OK, there is that. There's more than one reason I wouldn't buy a house with no grounds. ;-) |
#33
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 27, 9:27*am, DerbyDad03 wrote:
On Feb 26, 10:53*pm, " wrote: On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? *Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. *The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. *You can probably do that without removing the outlet from the box. *You should also be able to inspect the connection without pulling it. *Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? *You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. *That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent).- Hide quoted text - - Show quoted text - In all honesty, I had already pulled the GFCI just to eliminate it as a factor before I ran my suicide cord. I replaced it with a 3 prong receptacle and disconnected the downstream devices so that there was only the single 3 prong receptacle on the run. When it still showed the open ground - even though there was a ground wire attached - that's when I started tracing back and found the prvious junction box. You could just take a light bulb and temporarily connect it between hot and ground as a simple test. Open ground, it's not going to light. No need to remove or change anything. |
#34
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"DD_BobK" wrote in message
news:8e96f96c-2f03-468c-b2fd- btw those three light testers can be fooled by some unusual conditions here's a link to a website http://www.thecircuitdetective.com/test.htm Scroll down about half way & there is a detailed discussion of the 3- prong plug in tester. That's a great resource! Thanks for posting it. Especially useful were the possible causes of "dim" readings which I've seen once or twice. I saved a couple of thousand on this house just by going around to every outlet with a 3 pronged tester and discovering that the seller's son had replaced most of the two prong outlets with grounded outlets without any connection to ground!!!! (Except for his room in the basement, where he had run a ground to act as a neutral to install a programmble light switch.) Didn't discover that until after the sale when I pulled down the ceiling. The older the house, the more likely someone's done something stupid. I wouldn't buy a house without using one to test as many outlets as I could possibly test. I discovered back then, too, that in a really old house with very few outlets, one that has nothing plugged into or that has been painted over is very likely to be bad. -- Bobby G. |
#35
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 27, 1:40*pm, "
wrote: On Mon, 27 Feb 2012 06:27:01 -0800 (PST), DerbyDad03 wrote: On Feb 26, 10:53*pm, " wrote: On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? *Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. *The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. *You can probably do that without removing the outlet from the box. *You should also be able to inspect the connection without pulling it. *Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? *You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. *That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent).- Hide quoted text - - Show quoted text - In all honesty, I had already pulled the GFCI just to eliminate it as a factor before I ran my suicide cord. I replaced it with a 3 prong receptacle and disconnected the downstream devices so that there was only the single 3 prong receptacle on the run. When it still showed the open ground - even though there was a ground wire attached - that's when I started tracing back and found the prvious junction box. I'll be opening that tonight to look at the ground situation. As far as pulling a new grounded run from the panel to the junction box, you asked "Why bother?" Well, this is the last room in the house without 3 prong grounded receptacles. That's why I started by adding the GFCI - so I could at least install 3 prong receptacles downstream, mainly for the convenience of having 3 prong receptacles available. Eventually, I want to run grounded romex to all of the downstream receptacles, but that is going to require moving some storage in the basement so it's going to take some time. My point is that, in your case, you don't need a ground to install 3-prong receptacles. *The GFCI does the job. *The GFCI doesn't need a ground, either. Everything should be good as it is. *Well, except the ungrounded 3-prong outlets have to be marked "ungrounded". Since the feed to the junction box has a ground wire, it appeared that things would flow fairly smoothly in the forward direction from the junction box on. Now that I'm showing an open ground, I have to go backward and at a minimum find out why. I'm just not comfortable knowing that a non-grounded ground wire is attached in the junction box and at the GFCI. It'll gnaw at me until I fix it. OK, there is that. *There's more than one reason I wouldn't buy a house with no grounds. *;-)- Hide quoted text - - Show quoted text - I know how a GFCI works with regards to the grounds. I've posted on that very subject in this forum many times. At this point it is really just the presence of ground wires that don't do anything that irks me. In the long run (no pun intended) I do plan to rewire the circuit to provide the equipment ground to the downstream receptacles but the GFCI will suffice for now. What's that old saying? It's only temporary...unless it works. |
#36
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 27, 1:40*pm, "
wrote: On Mon, 27 Feb 2012 06:27:01 -0800 (PST), DerbyDad03 wrote: On Feb 26, 10:53*pm, " wrote: On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? *Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. *The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. *You can probably do that without removing the outlet from the box. *You should also be able to inspect the connection without pulling it. *Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? *You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. *That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent).- Hide quoted text - - Show quoted text - In all honesty, I had already pulled the GFCI just to eliminate it as a factor before I ran my suicide cord. I replaced it with a 3 prong receptacle and disconnected the downstream devices so that there was only the single 3 prong receptacle on the run. When it still showed the open ground - even though there was a ground wire attached - that's when I started tracing back and found the prvious junction box. I'll be opening that tonight to look at the ground situation. As far as pulling a new grounded run from the panel to the junction box, you asked "Why bother?" Well, this is the last room in the house without 3 prong grounded receptacles. That's why I started by adding the GFCI - so I could at least install 3 prong receptacles downstream, mainly for the convenience of having 3 prong receptacles available. Eventually, I want to run grounded romex to all of the downstream receptacles, but that is going to require moving some storage in the basement so it's going to take some time. My point is that, in your case, you don't need a ground to install 3-prong receptacles. *The GFCI does the job. *The GFCI doesn't need a ground, either. Everything should be good as it is. *Well, except the ungrounded 3-prong outlets have to be marked "ungrounded". Since the feed to the junction box has a ground wire, it appeared that things would flow fairly smoothly in the forward direction from the junction box on. Now that I'm showing an open ground, I have to go backward and at a minimum find out why. I'm just not comfortable knowing that a non-grounded ground wire is attached in the junction box and at the GFCI. It'll gnaw at me until I fix it. OK, there is that. *There's more than one reason I wouldn't buy a house with no grounds. *;-)- Hide quoted text - - Show quoted text - Forgot to mention this: It's not a house with no grounds, it's a house with *some* grounds. Even though the older wires seem to be of the same cloth covered vintage, some of them have grounds, some of them don't and in (at least) this particular case, some have ground wires that aren't really grounded. Any new circuits that I've run in the past 20 or so years have all been grounded. Except for some of the lighting circuits (two of which include a shared neutral) this group is the last of the ungrounded receptacles. |
#37
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"Robert Green" wrote in message ... "DD_BobK" wrote in message news:8e96f96c-2f03-468c-b2fd- btw those three light testers can be fooled by some unusual conditions here's a link to a website http://www.thecircuitdetective.com/test.htm Scroll down about half way & there is a detailed discussion of the 3- prong plug in tester. That's a great resource! Thanks for posting it. Especially useful were the possible causes of "dim" readings which I've seen once or twice. I saved a couple of thousand on this house just by going around to every outlet with a 3 pronged tester and discovering that the seller's son had replaced most of the two prong outlets with grounded outlets without any connection to ground!!!! (Except for his room in the basement, where he had run a ground to act as a neutral to install a programmble light switch.) I do not recall seeing any mention where someone connects the ground and neutral together at the outlet. This has been done in the older homes where there is no ground wire and fakes out the tester. |
#38
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Mon, 27 Feb 2012 13:29:42 -0800 (PST), DerbyDad03
wrote: On Feb 27, 1:40*pm, " wrote: On Mon, 27 Feb 2012 06:27:01 -0800 (PST), DerbyDad03 wrote: On Feb 26, 10:53*pm, " wrote: On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? *Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. *The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. *You can probably do that without removing the outlet from the box. *You should also be able to inspect the connection without pulling it. *Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? *You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. *That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent).- Hide quoted text - - Show quoted text - In all honesty, I had already pulled the GFCI just to eliminate it as a factor before I ran my suicide cord. I replaced it with a 3 prong receptacle and disconnected the downstream devices so that there was only the single 3 prong receptacle on the run. When it still showed the open ground - even though there was a ground wire attached - that's when I started tracing back and found the prvious junction box. I'll be opening that tonight to look at the ground situation. As far as pulling a new grounded run from the panel to the junction box, you asked "Why bother?" Well, this is the last room in the house without 3 prong grounded receptacles. That's why I started by adding the GFCI - so I could at least install 3 prong receptacles downstream, mainly for the convenience of having 3 prong receptacles available. Eventually, I want to run grounded romex to all of the downstream receptacles, but that is going to require moving some storage in the basement so it's going to take some time. My point is that, in your case, you don't need a ground to install 3-prong receptacles. *The GFCI does the job. *The GFCI doesn't need a ground, either. Everything should be good as it is. *Well, except the ungrounded 3-prong outlets have to be marked "ungrounded". Since the feed to the junction box has a ground wire, it appeared that things would flow fairly smoothly in the forward direction from the junction box on. Now that I'm showing an open ground, I have to go backward and at a minimum find out why. I'm just not comfortable knowing that a non-grounded ground wire is attached in the junction box and at the GFCI. It'll gnaw at me until I fix it. OK, there is that. *There's more than one reason I wouldn't buy a house with no grounds. *;-)- Hide quoted text - - Show quoted text - Forgot to mention this: It's not a house with no grounds, it's a house with *some* grounds. Yeah, I got that. Even though the older wires seem to be of the same cloth covered vintage, some of them have grounds, some of them don't and in (at least) this particular case, some have ground wires that aren't really grounded. That's a problem. It may be hard to get it all together if you can't trust anything. Any new circuits that I've run in the past 20 or so years have all been grounded. Except for some of the lighting circuits (two of which include a shared neutral) this group is the last of the ungrounded receptacles. Shared neutral? Ick. I'd never do that. |
#39
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
On Feb 27, 1:40*pm, "
wrote: On Mon, 27 Feb 2012 06:27:01 -0800 (PST), DerbyDad03 wrote: On Feb 26, 10:53*pm, " wrote: On Sun, 26 Feb 2012 16:30:14 -0800 (PST), DerbyDad03 wrote: On Feb 26, 6:45*pm, " wrote: On Sun, 26 Feb 2012 14:59:42 -0800 (PST), DerbyDad03 wrote: On Feb 26, 5:32*pm, " wrote: On Sun, 26 Feb 2012 17:27:42 -0500, "Ralph Mowery" wrote: "Tony Hwang" wrote in message ... Hi, I always have Simpson 260 handy working on problem like this. Fluke is for some other use. It might not show up in the circuits in a house, but at work on some of the 480 volt 3 phase circuits I could show some of the same things with a Simpson 260. *Start with the voltage on the highest scale and don't worry about the voltage, just pay attention on how far up the meter goes, then switch to the lower ranges in order. *On many of the 'phantom' voltages, the pointer on the meter will not move very far up or down. I have an assortment of Fluke and other meters I can use, but mostly grab the 260 and the old analog Amprobe for current measurments. I do not have one to check it out, but I understand that some of the newer digital test meters have a low input resistance to help eliminate the 'phantom' voltage problem. Just plug an incandescent light bulb into the circuit. With a lamp plugged into the same GFCI, and turned on, I get the same "oddball" readings at the GFCI. With no load on 2 other circuits that I tested, I get the expected readings of 0 between ground and neutral, 115V between hot and ground. Fluke 75 multimeter. Read my later reply, after you'd posted this information. *Essentially, you do have an open ground, like the TLT was telling you. *Where it is in the next question. *Use the TLT on another outlet in this circuit. *Testing both an outlet before and one after will nail it down pretty well. *If the one after is fine, then there is a good chance that the fault is within the GFCI itself. Well, at least we've stopped talking about the meter and/or the operator, which so many wanted to blame as the cause. We? *Well, the reason the meter is reading what it is, is because of its high impedance. "Testing both an outlet before and one after will nail it down pretty well." Can't do that. There is no receptacle before the GFCI and everything after it is ungrounded. The GFCI was installed so that 3 pronged receptacles could be installed downstream. Obviously, they'll all read "open ground". I guess your only option is to shut off the circuit and pull the GFCI. *The easiest thing to do is to measure the continuity of the outlet itself from the ground hole contacts to the screw. *You can probably do that without removing the outlet from the box. *You should also be able to inspect the connection without pulling it. *Else, you're going to have to pull it. BTW, since there are no grounds in this house, how did the GFCI get one? *You do know that it really doesn't need one, in this case. However, here's the latest: I opened the junction box just before the GFCI and disconnected the line in Romex feed, which had a ground wire. I then ran a suicide cord from a known good receptacle in my shop to the Romex going to the GFCI. The GFCI now reads correctly when using the tester and there are no strange readings between the current carriers and ground. Same meter, same operator. ;-) Oops. *That means it's a broken wire - much work. I traced the original Romex back to another junction box which houses a light fixture over the utility tub. That box has 2 other wires associated with it, one obviously being the feed but the other one disappears up into a wall. I'll need to open that box to see if there's a ground in there, otherwise I'll be pulling a new wire from the panel to the GFCI's junction box. Again, why bother? Too late to play now, SWMBO is cooking and killing that circuit kills the kitchen lights too. Dinner here was ruined (priority interrupt from real estate agent).- Hide quoted text - - Show quoted text - In all honesty, I had already pulled the GFCI just to eliminate it as a factor before I ran my suicide cord. I replaced it with a 3 prong receptacle and disconnected the downstream devices so that there was only the single 3 prong receptacle on the run. When it still showed the open ground - even though there was a ground wire attached - that's when I started tracing back and found the prvious junction box. I'll be opening that tonight to look at the ground situation. As far as pulling a new grounded run from the panel to the junction box, you asked "Why bother?" Well, this is the last room in the house without 3 prong grounded receptacles. That's why I started by adding the GFCI - so I could at least install 3 prong receptacles downstream, mainly for the convenience of having 3 prong receptacles available. Eventually, I want to run grounded romex to all of the downstream receptacles, but that is going to require moving some storage in the basement so it's going to take some time. My point is that, in your case, you don't need a ground to install 3-prong receptacles. *The GFCI does the job. *The GFCI doesn't need a ground, either. Everything should be good as it is. *Well, except the ungrounded 3-prong outlets have to be marked "ungrounded". Since the feed to the junction box has a ground wire, it appeared that things would flow fairly smoothly in the forward direction from the junction box on. Now that I'm showing an open ground, I have to go backward and at a minimum find out why. I'm just not comfortable knowing that a non-grounded ground wire is attached in the junction box and at the GFCI. It'll gnaw at me until I fix it. OK, there is that. *There's more than one reason I wouldn't buy a house with no grounds. *;-) I found the problem. As a recap, the junction box just below the GFCI receptacle had a feed wire with a ground, which I connected to the ground of the wire that went up the GFCI. However, the GFCI read "open ground". When I used a suicide cord with a known good ground as the feed to that junction box, the tester showed that the GFCI was wired correctly. So now I had to go looking for the open ground upstream of that junction box. I traced the original feed wire to another junction box that held a light fixture above the utility sink. The box had a feed wire coming in and 2 wires coming out. When I dropped the light fixture, here's what I found: The ground from the feed wire was wire nutted to the 3 neutrals. The ground in the wire that ran to the GFCI's junction box was cut back to about a 1/2 inch and folded neatly back along the insulation. The other wire that left the box had no ground wire. Luckily, there was enough slack in the wire I was working with that I was able to pull enough into the junction box to expose the ground wire and connect it to the ground wire of the feed. The tester now reads correctly at the GFCI. I won't even fathom a guess as to why they would have wired the ground with the neutrals and then cut back the other ground. Why not just connect the grounds as long as they were in the box? Who knows... |
#40
Posted to alt.home.repair
|
|||
|
|||
Electrical Question GFCI & Open ground
"DerbyDad03" wrote in message news:2f775e55-52cb-I traced the original feed wire to another junction box that held a light fixture above the utility sink. The box had a feed wire coming in and 2 wires coming out. When I dropped the light fixture, here's what I found: The ground from the feed wire was wire nutted to the 3 neutrals. The ground in the wire that ran to the GFCI's junction box was cut back to about a 1/2 inch and folded neatly back along the insulation. The other wire that left the box had no ground wire. Luckily, there was enough slack in the wire I was working with that I was able to pull enough into the junction box to expose the ground wire and connect it to the ground wire of the feed. The tester now reads correctly at the GFCI. I won't even fathom a guess as to why they would have wired the ground with the neutrals and then cut back the other ground. Why not just connect the grounds as long as they were in the box? Who knows... Just as most said, a disconnected ground somewhere between the GFCI and breaker box. Thanks for letting us know what the problem was. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
+1 testing a GFCI where no ground is available? | Home Repair | |||
Bathroom GFCI with no ground? | Home Repair | |||
Electrical question: a gfci AND a lighting circuit | Home Repair | |||
electrical ground/neutral question | Home Repair |