Using #14 wire for one light on 20A breaker
I am wondering how the code views this. I was just wiring my barn and
ran out of 12-2 romex. Rather than buy more, I decided to just use 14-2 since I had 200 feet of it. This 14-2 is only going to one light, one of those porcelin fixtures that are rated at 100W. As far as safety, I am not worried in the least. It's only going to run one 100W bulb (or less). As far as being inspected, I am also not worried. In barns and sheds they really dont care, unless there are bare wires or some obvious danger source. I'm just curious how the code views that? For example, if I but a common house type ceiling fixture, they generally have 8 inches or up to several feet (on a chandlier) of #14 standed wire as part of the fixture. So, if I am running a 20A circuit I am already using #14 in the circuit. In my case, I have one center light fed by #12, and one light on the left another on the right. Each of those lights are fed off the center light with about 16 feet of #14. Thanks Mark |
#2
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
wrote in message ... I am wondering how the code views this. I was just wiring my barn and ran out of 12-2 romex. Rather than buy more, I decided to just use 14-2 since I had 200 feet of it. This 14-2 is only going to one light, one of those porcelin fixtures that are rated at 100W. As far as safety, I am not worried in the least. It's only going to run one 100W bulb (or less). As far as being inspected, I am also not worried. In barns and sheds they really dont care, unless there are bare wires or some obvious danger source. I'm just curious how the code views that? For example, if I but a common house type ceiling fixture, they generally have 8 inches or up to several feet (on a chandlier) of #14 standed wire as part of the fixture. So, if I am running a 20A circuit I am already using #14 in the circuit. In my case, I have one center light fed by #12, and one light on the left another on the right. Each of those lights are fed off the center light with about 16 feet of #14. The problem, as the NEC sees it is two fold. If somehow the light started drawing too much current, the breaker would not protect the wiring. Or, if that seems too farfetched, someone after you might change the light without realizing the wire is inadequate. |
#3
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
|
#4
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
OH, but that would have cost $8.
-- Steve Barker "dpb" wrote in message ups.com... wrote: Me being me, I'd probably have just got another roll of 12 and finished it out simply for the self-aesthetics of the job and knowing that eventually I'd use that roll for other stuff around the place, but again, that's just me having had to grow up under my grandpa and dad... |
#5
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
Hummm... I just figured out why there are so many barn fires in which
insurance companies refuse to pay for damages! wrote in message I am wondering how the code views this. I was just wiring my barn and ran out of 12-2 romex. Rather than buy more, I decided to just use 14-2 since I had 200 feet of it. This 14-2 is only going to one light, one of those porcelin fixtures that are rated at 100W. As far as safety, I am not worried in the least. It's only going to run one 100W bulb (or less). As far as being inspected, I am also not worried. In barns and sheds they really dont care, unless there are bare wires or some obvious danger source. I'm just curious how the code views that? For example, if I but a common house type ceiling fixture, they generally have 8 inches or up to several feet (on a chandlier) of #14 standed wire as part of the fixture. So, if I am running a 20A circuit I am already using #14 in the circuit. In my case, I have one center light fed by #12, and one light on the left another on the right. Each of those lights are fed off the center light with about 16 feet of #14. Thanks Mark |
#6
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
|
#7
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
On Mon, 11 Dec 2006 15:50:26 GMT, "Toller" wrote:
wrote in message .. . I am wondering how the code views this. I was just wiring my barn and ran out of 12-2 romex. Rather than buy more, I decided to just use 14-2 since I had 200 feet of it. This 14-2 is only going to one light, one of those porcelin fixtures that are rated at 100W. As far as safety, I am not worried in the least. It's only going to run one 100W bulb (or less). As far as being inspected, I am also not worried. In barns and sheds they really dont care, unless there are bare wires or some obvious danger source. I'm just curious how the code views that? For example, if I but a common house type ceiling fixture, they generally have 8 inches or up to several feet (on a chandlier) of #14 standed wire as part of the fixture. So, if I am running a 20A circuit I am already using #14 in the circuit. In my case, I have one center light fed by #12, and one light on the left another on the right. Each of those lights are fed off the center light with about 16 feet of #14. The problem, as the NEC sees it is two fold. If somehow the light started drawing too much current, the breaker would not protect the wiring. Or, if that seems too farfetched, someone after you might change the light without realizing the wire is inadequate. Back when they still used knob and tube, you'd just stick a ceramic fixture with a 15A fuse in it between the heavy wiring and the lighter wiring. Do they still make things like that, or is it a full-blown sub-panel or nothing? --Goedjn |
#8
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
On Mon, 11 Dec 2006 10:53:59 -0600, "Steve Barker LT"
wrote: OH, but that would have cost $8. Where can you buy 50 feet of 12-2 for $8. Please tell me. I'll but 100 rolls immediately. |
#9
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
In article . com, dpb wrote:
wrote: I am wondering how the code views this. I was just wiring my barn and ran out of 12-2 romex. Rather than buy more, I decided to just use 14-2 since I had 200 feet of it. This 14-2 is only going to one light, one of those porcelin fixtures that are rated at 100W. As far as safety, I am not worried in the least. It's only going to run one 100W bulb (or less). As far as being inspected, I am also not worried. In barns and sheds they really dont care, unless there are bare wires or some obvious danger source. I'm just curious how the code views that? ... In my case, I have one center light fed by #12, and one light on the left another on the right. Each of those lights are fed off the center light with about 16 feet of #14. If you don't care, why ask? By code, it's not up to snuff, because code is designed to protect the fixed wiring, not the fixtures or other end load. I agree it's not an inherent safety hazard as described as long as the use remains as is. I would be somewhat suprised if an inspection (assuming you're in a place where zoning applies and it will be inspected) didn't point it out as a deficiency, but that would be dependent on, as you say, what your local inspector's penchant/foibles is/are... Of course, you can easily alleviate the issue by putting a 15A breaker in the panel for that lighting circuit and be over-sized rather than under-sized in a portion of the circuit. Me being me, I'd probably have just got another roll of 12 and finished it out simply for the self-aesthetics of the job and knowing that eventually I'd use that roll for other stuff around the place, but again, that's just me having had to grow up under my grandpa and dad... http://www.ci.longmont.co.us/bldgins...ial/wiring.htm Code actually requires all wiring in a branch circuit to be of the same size. However, I cannot guarantee that this item is in the NEC as opposed to being merely in a local building code. I am under the impression that at least most items in that page are actually specified by NEC. - Don Klipstein ) |
#10
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
In , Doug Miller wrote:
In ,marad : I'm just curious how the code views that? As a violation. For example, if I but a common house type ceiling fixture, they generally have 8 inches or up to several feet (on a chandlier) of #14 standed wire as part of the fixture. So, if I am running a 20A circuit I am already using #14 in the circuit. Fixture wires generally have a much higher temperature rating than supply wires, which enables them to carry higher current on smaller wires. Since resistance increases with temperature, actual ampacity does not increase much with an increase in temperature rating. And ampacity according to the code does not increase at all. - Don Klipstein ) |
#12
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
|
#13
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
Don Klipstein wrote:
Since resistance increases with temperature, actual ampacity does not increase much with an increase in temperature rating. And ampacity according to the code does not increase at all. I'm going to have to disagree with that. For simplicity, look at the "single conductor in free air" tables. (The other tables show it too, just the absolute values are lower.) With 60-90C rated insulation, a #14 wire is rated for 20A. With 110-125C rated insulation, that same size wire is rated for 40A. If you go up to 200C insulation, you can put 45A through it. Chris |
#14
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
No, he said he needed 16 feet. That's $8. You can buy it by the foot also.
-- Steve Barker wrote in message ... On Mon, 11 Dec 2006 10:53:59 -0600, "Steve Barker LT" wrote: OH, but that would have cost $8. Where can you buy 50 feet of 12-2 for $8. Please tell me. I'll but 100 rolls immediately. |
#15
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
|
#16
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
In article , Chris Friesen wrote:
Don Klipstein wrote: Since resistance increases with temperature, actual ampacity does not increase much with an increase in temperature rating. And ampacity according to the code does not increase at all. I'm going to have to disagree with that. For simplicity, look at the "single conductor in free air" tables. (The other tables show it too, just the absolute values are lower.) With 60-90C rated insulation, a #14 wire is rated for 20A. With 110-125C rated insulation, that same size wire is rated for 40A. If you go up to 200C insulation, you can put 45A through it. Somehow, I suspect that upgrading from 110 or 125 C insulation to 200 C insulation only improving ampacity from 40 to 45 amps supports my point! Meanwhile, also consider that wiring in a building is usually not single conductor in free air, but 2 at least current-carrying conductors close to each other and heating each other up with a sheath around them and the environment outside the sheath usually not being "free air". Add to this the fact that extra high temperature rating wire is used more where ambient temperature is higher, and I see good reason for AWG 14 romex to be only allowed by code to be used in circuits up to 15 amps regardless of temperature rating. - Don Klipstein ) |
#17
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
In article , (Don Klipstein) wrote:
In article , Doug Miller wrote: In article , (Don Klipstein) wrote: In , Doug Miller wrote: In ,marad : I'm just curious how the code views that? As a violation. For example, if I but a common house type ceiling fixture, they generally have 8 inches or up to several feet (on a chandlier) of #14 standed wire as part of the fixture. So, if I am running a 20A circuit I am already using #14 in the circuit. Fixture wires generally have a much higher temperature rating than supply wires, which enables them to carry higher current on smaller wires. Since resistance increases with temperature, actual ampacity does not increase much with an increase in temperature rating. The temperature rating of a conductor depends on its *insulation*, not the conductor itself. Ampacity *does* increase substantially with an increase in temperature rating, due to the ability of the insulation to withstand a higher conductor temperature. Example: for copper wire, #8 TW has an ampacity of 40 amps; #8 THHN has an ampacity of 55 amps. Another example: #18 copper wire is permitted to carry 14 amps, IF it has 90 deg C insulation (e.g. THHN or THHW). And ampacity according to the code does not increase at all. This simply is not true. See NEC Table 310.16 for abundant proof that the Code absolutely does recognize increased ampacity for increased temperature ratings. This sounds to me specific to appliance cords, as opposed to romex. Nope, wrong again. It applies to *all* premises wiring covered by the NEC. There's a lot more than just "romex" involved. Like I said... See NEC Table 310.16 -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#18
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
|
#19
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
In article , Doug Miller wrote:
In article , (Don Klipstein) wrote: In article , Chris Friesen wrote: Don Klipstein wrote: Since resistance increases with temperature, actual ampacity does not increase much with an increase in temperature rating. And ampacity according to the code does not increase at all. I'm going to have to disagree with that. For simplicity, look at the "single conductor in free air" tables. (The other tables show it too, just the absolute values are lower.) With 60-90C rated insulation, a #14 wire is rated for 20A. With 110-125C rated insulation, that same size wire is rated for 40A. If you go up to 200C insulation, you can put 45A through it. Somehow, I suspect that upgrading from 110 or 125 C insulation to 200 C insulation only improving ampacity from 40 to 45 amps supports my point! Quite the opposite: it clearly contradicts your assertion that it "does not increase at all". I did state that my "does not increase at all" was a code matter, on which I would concede on appliance cords but I insist remains the case with romex. And, of course, the difference between 20A at 60 deg and 40A at 125 deg makes that contradiction even more clear. So you have cited a data point opposing my point as well as a data point supporting my point (200C single conductor in free air good for 45 amps). Meanwhile, also consider that wiring in a building is usually not single conductor in free air, but 2 at least current-carrying conductors close to each other and heating each other up with a sheath around them and the environment outside the sheath usually not being "free air". That was just an example -- and maybe not a real good one. But it does show that (not to put too fine a point on it) you don't know what you're talking about when you say that "ampacity according to the code does not increase at all". That's just not true. Sure is true with most wiring, such as permanently installed wiring! Code says 15 amps for AWG 14 regardless of temperature rating for permanently installed wiring! See NEC Table 310.16 for abundant proof that the ampacity of a conductor -- ANY conductor, ANY size -- absolutely DOES increase with increasing temperature rating of the insulation. I google for that and find a nice chart: http://www.houwire.com/products/tech...cle310_16.html I see close to the top a line entry for 14 AWG, with no ampacities being the 15 amps for 14 AWG permanently installed wiring, and I have already conceded on the specific issue of appliance cords. Along with this chart showing higher ampacities for specific cable types of which I think 97% or so is not "permanently installed wiring". In addition, the code's limits for "permanently installed wiring" do not appear to me to be increased above 15 amps for 14 AWG or 20 amps for 12 AWG on the basis of such wiring being allowed for "permanently installed wiring" (most of these cable types are not) and such cable types having special ampacity higher than 15 amps for 14 AWG and 20 amps for 12 AWG. Add to this the fact that extra high temperature rating wire is used more where ambient temperature is higher, and I see good reason for AWG 14 romex to be only allowed by code to be used in circuits up to 15 amps regardless of temperature rating. That's a completely separate issue from the ampacity of the wire, which Code specifies as being, for example, 25A with THHN insulation. But does the Code allow AWG 14 with THNN insulation to be used in permanently installed wiring in a building in circuits protected by fuses or breakers of more than 15 amps? Since I conceded on appliance cords, I still consider the issue of permanently installed wiring to be valid! In a separate article, Code limits the overcurrent protection for 14 and 12 ga conductors to 15 and 20 amps, respectively, despite their having a higher ampacity. Starting to sound like what I am saying, especially in terms of code? -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. - Don Klipstein ) |
#20
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
|
#21
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
In article , (Don Klipstein) wrote:
In article , Doug Miller wrote: In article , (Don Klipstein) wrote: In article , Chris Friesen wrote: Don Klipstein wrote: Since resistance increases with temperature, actual ampacity does not increase much with an increase in temperature rating. And ampacity according to the code does not increase at all. I'm going to have to disagree with that. For simplicity, look at the "single conductor in free air" tables. (The other tables show it too, just the absolute values are lower.) With 60-90C rated insulation, a #14 wire is rated for 20A. With 110-125C rated insulation, that same size wire is rated for 40A. If you go up to 200C insulation, you can put 45A through it. Somehow, I suspect that upgrading from 110 or 125 C insulation to 200 C insulation only improving ampacity from 40 to 45 amps supports my point! Quite the opposite: it clearly contradicts your assertion that it "does not increase at all". I did state that my "does not increase at all" was a code matter, Yes, you did -- and I have repeatedly pointed out that this is not correct, that the Code absolutely does recognize increased ampacity with increasing conductor temperature. The entire Code is online he http://nfpa-acs-01.gvpi.net:8080/rrs...NFPASTD/7005SB I refer you to Table 310.16. on which I would concede on appliance cords but I insist remains the case with romex. You're commenting in a vacuum, based on a lack of knowledge. Read the Code. You're wrong. And, of course, the difference between 20A at 60 deg and 40A at 125 deg makes that contradiction even more clear. So you have cited a data point opposing my point as well as a data point supporting my point (200C single conductor in free air good for 45 amps). Read the Code. You're wrong. Table 310.16. Meanwhile, also consider that wiring in a building is usually not single conductor in free air, but 2 at least current-carrying conductors close to each other and heating each other up with a sheath around them and the environment outside the sheath usually not being "free air". That was just an example -- and maybe not a real good one. But it does show that (not to put too fine a point on it) you don't know what you're talking about when you say that "ampacity according to the code does not increase at all". That's just not true. Sure is true with most wiring, such as permanently installed wiring! Code says 15 amps for AWG 14 regardless of temperature rating for permanently installed wiring! Read the Code. You're wrong. Table 310.16. See NEC Table 310.16 for abundant proof that the ampacity of a conductor -- ANY conductor, ANY size -- absolutely DOES increase with increasing temperature rating of the insulation. I google for that and find a nice chart: http://www.houwire.com/products/tech...cle310_16.html I see close to the top a line entry for 14 AWG, with no ampacities being the 15 amps for 14 AWG permanently installed wiring, and I have already conceded on the specific issue of appliance cords. Along with this chart showing higher ampacities for specific cable types of which I think 97% or so is not "permanently installed wiring". In addition, the code's limits for "permanently installed wiring" do not appear to me to be increased above 15 amps for 14 AWG or 20 amps for 12 AWG on the basis of such wiring being allowed for "permanently installed wiring" (most of these cable types are not) and such cable types having special ampacity higher than 15 amps for 14 AWG and 20 amps for 12 AWG. Read the Code. You're wrong. Table 310.16. Add to this the fact that extra high temperature rating wire is used more where ambient temperature is higher, and I see good reason for AWG 14 romex to be only allowed by code to be used in circuits up to 15 amps regardless of temperature rating. That's a completely separate issue from the ampacity of the wire, which Code specifies as being, for example, 25A with THHN insulation. But does the Code allow AWG 14 with THNN insulation to be used in permanently installed wiring in a building in circuits protected by fuses or breakers of more than 15 amps? No -- but that's because the Code builds the "80% rule" into the overcurrent protection limits for 10, 14, and 12ga conductors, not because of any limits on the conductor's ability to carry current. It's for additional safety. But if you would actually READ THE CODE, you'd find out that the ampacities are in fact considerably higher than the permitted overcurrent protection. It's two separate issues. Since I conceded on appliance cords, I still consider the issue of permanently installed wiring to be valid! Read the Code. You're wrong. Table 310.16. In a separate article, Code limits the overcurrent protection for 14 and 12 ga conductors to 15 and 20 amps, respectively, despite their having a higher ampacity. Starting to sound like what I am saying, especially in terms of code? No, it's NOT starting to sound like what you're saying. You said that, according to Code, conductor ampacity "does not increase at all" with increased conductor temperature rating, and that simply is not true. Not for fixture wires. Not for appliance cords. Not for permanently installed wiring. Not true at all. READ THE CODE. Table 310.16. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#22
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
Abe wrote: Why not avoid any potential problems and just buy a 15 amp breaker for a few bucks? .. Exactly: Had one situation where we realzed that a circuit extended out to shed from a 20 amp circuit included some #14AWG. We quickly changed out the 20 amp breaker to 15 amp not because of any problems but a) to meet code b) Demonstrate for an in impending insurance inspection (the first in the 36 years since house was built!) that wiring was built and maintained to standard. Reminds me got one cracked duplex at the bench must change it. And although its indoors think I'll make the first one on that run a GFI. |
#23
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
In , Doug Miller wrote in
part: No -- but that's because the Code builds the "80% rule" into the overcurrent protection limits for 10, 14, and 12ga conductors, not because of any limits on the conductor's ability to carry current. It's for additional safety. But if you would actually READ THE CODE, you'd find out that the ampacities are in fact considerably higher than the permitted overcurrent protection. It's two separate issues. OK, I learned something here - the issue that I was thinking of, where 15 amps is the limit for AWG 14 permanently installed wiring regardless of its temperature rating, is called "permitted overcurrent protection". - Don Klipstein ) |
#24
Posted to alt.home.repair
|
|||
|
|||
Using #14 wire for one light on 20A breaker
wrote:
Hire a professional On Mon, 11 Dec 2006 09:12:41 -0600, wrote: I am wondering how the code views this. I was just wiring my barn and ran out of 12-2 romex. Rather than buy more, I decided to just use 14-2 since I had 200 feet of it. This 14-2 is only going to one light, one of those porcelin fixtures that are rated at 100W. This is a do-it-yourself NG. What are you doing here? John As far as safety, I am not worried in the least. It's only going to run one 100W bulb (or less). As far as being inspected, I am also not worried. In barns and sheds they really dont care, unless there are bare wires or some obvious danger source. I'm just curious how the code views that? For example, if I but a common house type ceiling fixture, they generally have 8 inches or up to several feet (on a chandlier) of #14 standed wire as part of the fixture. So, if I am running a 20A circuit I am already using #14 in the circuit. In my case, I have one center light fed by #12, and one light on the left another on the right. Each of those lights are fed off the center light with about 16 feet of #14. Thanks Mark |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
14 Wire on 20amp Breaker... | Home Repair | |||
Help tracing breaker and wire | Home Repair | |||
When (if ever) can 14ga wire be used with 20A circuit breaker? | Home Repair | |||
When to use 15A vs. 20A circuits (and #14 vs #12 wire)? | Home Repair | |||
Breaker and wire size? | Woodworking |