When (if ever) can 14ga wire be used with 20A circuit breaker?
Can wiring to a light off a 20A circuit be done in 14ga wire?
What about wiring to an upstream 15A receptacle? Or, does all wiring on a 20A circuit breaker need to be at least 12ga? Thanks |
#2
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
"blueman" wrote in message ... Can wiring to a light off a 20A circuit be done in 14ga wire? What about wiring to an upstream 15A receptacle? Or, does all wiring on a 20A circuit breaker need to be at least 12ga? That is correct; with the slight exception if the #14 wire has a separate 15a breaker on it. Some people will use #14 on a lighting switch leg, on the theory that it couldn't possibly see more than a couple amps; but it is a code violation. |
#3
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
You simply cannot use 14ga wire on a 20 amp circuit.
Any electical inspector that sees that in a box will simply flag it and make you change the line or the breaker. (just as an FYI) If you pull too much near the 15amp side and exceed the limits it wont stop for another 5amps. In effect you can be overloading the line. It may not happen on your lighting idea, but why bother with the risk for a few bucks more on getting the correct wire. Using 12ga on a 15amp is perfectly fine. Its nice that down the road if you need to upgrade you can just change the outlets and breaker and you got a 20amp line. Tom |
#4
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
blueman wrote:
Can wiring to a light off a 20A circuit be done in 14ga wire? It will work just fine for a switched light but is technically a code violation, even if the wire ampacity is 20A (which 14 gauge THHN-2 is.) You could argue that you were using the 10 foot tap rule (or 25 foot, I don't remember which would apply better here), but you'll get shot down. What about wiring to an upstream 15A receptacle? No. What if somebody plugs a 10A load into both halves of the duplex receptacle, or extends the circuit someday? Or, does all wiring on a 20A circuit breaker need to be at least 12ga? Yes. 12 ga is not that much more expensive than 14 ga, and your time is worth something; do the job right. Best regards, Bob |
#5
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
blueman wrote:
Can wiring to a light off a 20A circuit be done in 14ga wire? What about wiring to an upstream 15A receptacle? Or, does all wiring on a 20A circuit breaker need to be at least 12ga? Thanks I would say never. I hear folks say it can be used between switch and bulb, but that just does not seem right. Breaker protects the wiring, nothing more nothing less. Perhaps someone puts in a heavy duty bulb of some sort that is broken and begins to draw lots of current. The circuitry wont be protected by the breaker. An all around bad idea. To put it simply, the wiring should _always_ match the breaker. -- Thank you, "Then said I, Wisdom [is] better than strength: nevertheless the poor man's wisdom [is] despised, and his words are not heard." Ecclesiastes 9:16 |
#6
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
"blueman" wrote in message ... Can wiring to a light off a 20A circuit be done in 14ga wire? What about wiring to an upstream 15A receptacle? Or, does all wiring on a 20A circuit breaker need to be at least 12ga? Thanks This depends on the situation. If the box has #12 and your UL listed light fixture is #14 probably #16 then it is fine. If your adding the #14 yourself no must be #12. Open your electric water heater some day, you will have at least #10 feeding #12. It is inside a UL listed and labeled appliance, there for ok doky. |
#7
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
"SQLit" wrote in message ... "blueman" wrote in message ... Can wiring to a light off a 20A circuit be done in 14ga wire? What about wiring to an upstream 15A receptacle? Or, does all wiring on a 20A circuit breaker need to be at least 12ga? Thanks This depends on the situation. If the box has #12 and your UL listed light fixture is #14 probably #16 then it is fine. Huh? What are you saying? If your adding the #14 yourself no must be #12. Open your electric water heater some day, you will have at least #10 feeding #12. It is inside a UL listed and labeled appliance, there for ok doky. Yeah, I noticed mine is. I presumed that was because the #12 wires are THHN and between two things rated for higher temperatures. No? Still, it seemed like a foolish place to save $0.02. |
#8
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
Toller wrote:
If your adding the #14 yourself no must be #12. Open your electric water heater some day, you will have at least #10 feeding #12. It is inside a UL listed and labeled appliance, there for ok doky. Yeah, I noticed mine is. I presumed that was because the #12 wires are THHN and between two things rated for higher temperatures. No? Still, it seemed like a foolish place to save $0.02. If the wires melt and burn within the water heater housing, what is the end result? -- Thank you, "Then said I, Wisdom [is] better than strength: nevertheless the poor man's wisdom [is] despised, and his words are not heard." Ecclesiastes 9:16 |
#9
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
|
#10
Posted to alt.home.repair
|
|||
|
|||
When (if ever) can 14ga wire be used with 20A circuit breaker?
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Commercial mains wiring: 12ga wire for 30 amp load? | Electronics Repair | |||
Home circuit breaker box question | Electronics Repair | |||
Locating Circuit Breaker( | Home Repair | |||
circuit breaker question! | Home Repair | |||
Strange not-quite-240 high-voltage smoke problem... short? circuit breaker? | Home Repair |