On Thu, 09 Feb 2006 08:41:35 -0500, dnoyeB
wrote:


Open your electric water heater some day, you will have at least #10
feeding
#12.
It is inside a UL listed and labeled appliance, there for ok doky.


Yeah, I noticed mine is. I presumed that was because the #12 wires are THHN
and between two things rated for higher temperatures. No?
Still, it seemed like a foolish place to save $0.02.



If the wires melt and burn within the water heater housing, what is the
end result?

--
Thank you,



A 4500w water heater only pulls 18.75a. There is plenty of safety
factor in a #12 as a "fixture wire" but if it is protected by a 30a
breaker the "branch circuit" conductors must be #10.



if it only pulls 18.75a, why not put 12 everywhere? Protection is not
tied to the loading of the appliance, its tied to what happens under
failure conditions. If that appliance fails with a resistive short, it
can pull up to the load allowed by the circuit protection.

More likely they ensure that melted and burned wires wont start a fire
within the appliance. And that the appliance is obviously bad anyway so
loosing some wiring is not a significant penalty. You dont want to
loose wiring in your wall due to a bad appliance.

So 12 is not 'safe' in terns of it not failing, but in that if it does
fail, its not goign to cause any additional significant damage.



--