Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 311
Default Using #14 wire for one light on 20A breaker

I am wondering how the code views this. I was just wiring my barn and
ran out of 12-2 romex. Rather than buy more, I decided to just use
14-2 since I had 200 feet of it. This 14-2 is only going to one
light, one of those porcelin fixtures that are rated at 100W.

As far as safety, I am not worried in the least. It's only going to
run one 100W bulb (or less). As far as being inspected, I am also not
worried. In barns and sheds they really dont care, unless there are
bare wires or some obvious danger source. I'm just curious how the
code views that? For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.

In my case, I have one center light fed by #12, and one light on the
left another on the right. Each of those lights are fed off the
center light with about 16 feet of #14.

Thanks

Mark
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,617
Default Using #14 wire for one light on 20A breaker


wrote in message
...
I am wondering how the code views this. I was just wiring my barn and
ran out of 12-2 romex. Rather than buy more, I decided to just use
14-2 since I had 200 feet of it. This 14-2 is only going to one
light, one of those porcelin fixtures that are rated at 100W.

As far as safety, I am not worried in the least. It's only going to
run one 100W bulb (or less). As far as being inspected, I am also not
worried. In barns and sheds they really dont care, unless there are
bare wires or some obvious danger source. I'm just curious how the
code views that? For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.

In my case, I have one center light fed by #12, and one light on the
left another on the right. Each of those lights are fed off the
center light with about 16 feet of #14.

The problem, as the NEC sees it is two fold. If somehow the light started
drawing too much current, the breaker would not protect the wiring. Or, if
that seems too farfetched, someone after you might change the light without
realizing the wire is inadequate.


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,313
Default Using #14 wire for one light on 20A breaker

On Mon, 11 Dec 2006 15:50:26 GMT, "Toller" wrote:


wrote in message
.. .
I am wondering how the code views this. I was just wiring my barn and
ran out of 12-2 romex. Rather than buy more, I decided to just use
14-2 since I had 200 feet of it. This 14-2 is only going to one
light, one of those porcelin fixtures that are rated at 100W.

As far as safety, I am not worried in the least. It's only going to
run one 100W bulb (or less). As far as being inspected, I am also not
worried. In barns and sheds they really dont care, unless there are
bare wires or some obvious danger source. I'm just curious how the
code views that? For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.

In my case, I have one center light fed by #12, and one light on the
left another on the right. Each of those lights are fed off the
center light with about 16 feet of #14.

The problem, as the NEC sees it is two fold. If somehow the light started
drawing too much current, the breaker would not protect the wiring. Or, if
that seems too farfetched, someone after you might change the light without
realizing the wire is inadequate.


Back when they still used knob and tube, you'd just
stick a ceramic fixture with a 15A fuse in it
between the heavy wiring and the lighter wiring.

Do they still make things like that, or is it
a full-blown sub-panel or nothing?

--Goedjn
  #4   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 1,029
Default Using #14 wire for one light on 20A breaker

wrote:
I am wondering how the code views this. I was just wiring my barn and
ran out of 12-2 romex. Rather than buy more, I decided to just use
14-2 since I had 200 feet of it. This 14-2 is only going to one
light, one of those porcelin fixtures that are rated at 100W.

As far as safety, I am not worried in the least. It's only going to
run one 100W bulb (or less). As far as being inspected, I am also not
worried. In barns and sheds they really dont care, unless there are
bare wires or some obvious danger source. I'm just curious how the
code views that? ...
In my case, I have one center light fed by #12, and one light on the
left another on the right. Each of those lights are fed off the
center light with about 16 feet of #14.


If you don't care, why ask?

By code, it's not up to snuff, because code is designed to protect the
fixed wiring, not the fixtures or other end load. I agree it's not an
inherent safety hazard as described as long as the use remains as is.

I would be somewhat suprised if an inspection (assuming you're in a
place where zoning applies and it will be inspected) didn't point it
out as a deficiency, but that would be dependent on, as you say, what
your local inspector's penchant/foibles is/are...

Of course, you can easily alleviate the issue by putting a 15A breaker
in the panel for that lighting circuit and be over-sized rather than
under-sized in a portion of the circuit.

Me being me, I'd probably have just got another roll of 12 and finished
it out simply for the self-aesthetics of the job and knowing that
eventually I'd use that roll for other stuff around the place, but
again, that's just me having had to grow up under my grandpa and dad...


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 317
Default Using #14 wire for one light on 20A breaker

OH, but that would have cost $8.

--
Steve Barker


"dpb" wrote in message
ups.com...
wrote:

Me being me, I'd probably have just got another roll of 12 and finished
it out simply for the self-aesthetics of the job and knowing that
eventually I'd use that roll for other stuff around the place, but
again, that's just me having had to grow up under my grandpa and dad...






  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 41
Default Using #14 wire for one light on 20A breaker

On Mon, 11 Dec 2006 10:53:59 -0600, "Steve Barker LT"
wrote:

OH, but that would have cost $8.


Where can you buy 50 feet of 12-2 for $8. Please tell me. I'll but
100 rolls immediately.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 317
Default Using #14 wire for one light on 20A breaker

No, he said he needed 16 feet. That's $8. You can buy it by the foot also.

--
Steve Barker


wrote in message
...
On Mon, 11 Dec 2006 10:53:59 -0600, "Steve Barker LT"
wrote:

OH, but that would have cost $8.


Where can you buy 50 feet of 12-2 for $8. Please tell me. I'll but
100 rolls immediately.



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,431
Default Using #14 wire for one light on 20A breaker

In article . com, dpb wrote:
wrote:
I am wondering how the code views this. I was just wiring my barn and
ran out of 12-2 romex. Rather than buy more, I decided to just use
14-2 since I had 200 feet of it. This 14-2 is only going to one
light, one of those porcelin fixtures that are rated at 100W.

As far as safety, I am not worried in the least. It's only going to
run one 100W bulb (or less). As far as being inspected, I am also not
worried. In barns and sheds they really dont care, unless there are
bare wires or some obvious danger source. I'm just curious how the
code views that? ...
In my case, I have one center light fed by #12, and one light on the
left another on the right. Each of those lights are fed off the
center light with about 16 feet of #14.


If you don't care, why ask?

By code, it's not up to snuff, because code is designed to protect the
fixed wiring, not the fixtures or other end load. I agree it's not an
inherent safety hazard as described as long as the use remains as is.

I would be somewhat suprised if an inspection (assuming you're in a
place where zoning applies and it will be inspected) didn't point it
out as a deficiency, but that would be dependent on, as you say, what
your local inspector's penchant/foibles is/are...

Of course, you can easily alleviate the issue by putting a 15A breaker
in the panel for that lighting circuit and be over-sized rather than
under-sized in a portion of the circuit.

Me being me, I'd probably have just got another roll of 12 and finished
it out simply for the self-aesthetics of the job and knowing that
eventually I'd use that roll for other stuff around the place, but
again, that's just me having had to grow up under my grandpa and dad...


http://www.ci.longmont.co.us/bldgins...ial/wiring.htm

Code actually requires all wiring in a branch circuit to be of the same
size. However, I cannot guarantee that this item is in the NEC as opposed
to being merely in a local building code. I am under the impression that
at least most items in that page are actually specified by NEC.

- Don Klipstein )
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire for one light on 20A breaker

In article , (Don Klipstein) wrote:

http://www.ci.longmont.co.us/bldgins...ial/wiring.htm

Code actually requires all wiring in a branch circuit to be of the same
size. However, I cannot guarantee that this item is in the NEC as opposed
to being merely in a local building code. I am under the impression that
at least most items in that page are actually specified by NEC.


Must be a local code. The NEC specifies minimum requirements for conductor
sizes, but has no requirement I'm aware of that all conductors on a circuit be
the same size.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 182
Default Using #14 wire for one light on 20A breaker

Hummm... I just figured out why there are so many barn fires in which
insurance companies refuse to pay for damages!


wrote in message
I am wondering how the code views this. I was just wiring my barn and
ran out of 12-2 romex. Rather than buy more, I decided to just use
14-2 since I had 200 feet of it. This 14-2 is only going to one
light, one of those porcelin fixtures that are rated at 100W.

As far as safety, I am not worried in the least. It's only going to
run one 100W bulb (or less). As far as being inspected, I am also not
worried. In barns and sheds they really dont care, unless there are
bare wires or some obvious danger source. I'm just curious how the
code views that? For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.

In my case, I have one center light fed by #12, and one light on the
left another on the right. Each of those lights are fed off the
center light with about 16 feet of #14.

Thanks

Mark





  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,431
Default Using #14 wire for one light on 20A breaker

In , Doug Miller wrote:
In ,marad :

I'm just curious how the code views that?


As a violation.

For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.


Fixture wires generally have a much higher temperature rating than supply
wires, which enables them to carry higher current on smaller wires.


Since resistance increases with temperature, actual ampacity does not
increase much with an increase in temperature rating. And ampacity
according to the code does not increase at all.

- Don Klipstein )
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire for one light on 20A breaker

In article , (Don Klipstein) wrote:
In , Doug Miller wrote:
In ,marad :

I'm just curious how the code views that?


As a violation.

For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.


Fixture wires generally have a much higher temperature rating than supply
wires, which enables them to carry higher current on smaller wires.


Since resistance increases with temperature, actual ampacity does not
increase much with an increase in temperature rating.


The temperature rating of a conductor depends on its *insulation*, not the
conductor itself. Ampacity *does* increase substantially with an increase in
temperature rating, due to the ability of the insulation to withstand a higher
conductor temperature.

Example: for copper wire, #8 TW has an ampacity of 40 amps; #8 THHN has an
ampacity of 55 amps.

Another example: #18 copper wire is permitted to carry 14 amps, IF it has 90
deg C insulation (e.g. THHN or THHW).

And ampacity
according to the code does not increase at all.


This simply is not true. See NEC Table 310.16 for abundant proof that the Code
absolutely does recognize increased ampacity for increased temperature
ratings.


--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,431
Default Using #14 wire for one light on 20A breaker

In article , Doug Miller wrote:
In article , (Don Klipstein) wrote:
In , Doug Miller wrote:
In ,marad :

I'm just curious how the code views that?

As a violation.

For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.

Fixture wires generally have a much higher temperature rating than supply
wires, which enables them to carry higher current on smaller wires.


Since resistance increases with temperature, actual ampacity does not
increase much with an increase in temperature rating.


The temperature rating of a conductor depends on its *insulation*, not the
conductor itself. Ampacity *does* increase substantially with an increase in
temperature rating, due to the ability of the insulation to withstand a higher
conductor temperature.

Example: for copper wire, #8 TW has an ampacity of 40 amps; #8 THHN has an
ampacity of 55 amps.

Another example: #18 copper wire is permitted to carry 14 amps, IF it has 90
deg C insulation (e.g. THHN or THHW).

And ampacity
according to the code does not increase at all.


This simply is not true. See NEC Table 310.16 for abundant proof that the Code
absolutely does recognize increased ampacity for increased temperature
ratings.


This sounds to me specific to appliance cords, as opposed to romex.

- Don Klipstein )
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire for one light on 20A breaker

In article , (Don Klipstein) wrote:
In article , Doug Miller wrote:
In article ,
(Don
Klipstein) wrote:
In , Doug Miller wrote:
In ,marad :

I'm just curious how the code views that?

As a violation.

For example, if I but a common house type ceiling
fixture, they generally have 8 inches or up to several feet (on a
chandlier) of #14 standed wire as part of the fixture. So, if I am
running a 20A circuit I am already using #14 in the circuit.

Fixture wires generally have a much higher temperature rating than supply
wires, which enables them to carry higher current on smaller wires.

Since resistance increases with temperature, actual ampacity does not
increase much with an increase in temperature rating.


The temperature rating of a conductor depends on its *insulation*, not the
conductor itself. Ampacity *does* increase substantially with an increase in
temperature rating, due to the ability of the insulation to withstand a higher


conductor temperature.

Example: for copper wire, #8 TW has an ampacity of 40 amps; #8 THHN has an
ampacity of 55 amps.

Another example: #18 copper wire is permitted to carry 14 amps, IF it has 90
deg C insulation (e.g. THHN or THHW).

And ampacity
according to the code does not increase at all.


This simply is not true. See NEC Table 310.16 for abundant proof that the Code
absolutely does recognize increased ampacity for increased temperature
ratings.


This sounds to me specific to appliance cords, as opposed to romex.


Nope, wrong again. It applies to *all* premises wiring covered by the NEC.
There's a lot more than just "romex" involved.

Like I said... See NEC Table 310.16

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.


  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,185
Default Using #14 wire for one light on 20A breaker

Don Klipstein wrote:

Since resistance increases with temperature, actual ampacity does not
increase much with an increase in temperature rating. And ampacity
according to the code does not increase at all.


I'm going to have to disagree with that.

For simplicity, look at the "single conductor in free air" tables. (The
other tables show it too, just the absolute values are lower.)

With 60-90C rated insulation, a #14 wire is rated for 20A. With
110-125C rated insulation, that same size wire is rated for 40A. If you
go up to 200C insulation, you can put 45A through it.

Chris
  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,431
Default Using #14 wire for one light on 20A breaker

In article , Chris Friesen wrote:
Don Klipstein wrote:

Since resistance increases with temperature, actual ampacity does not
increase much with an increase in temperature rating. And ampacity
according to the code does not increase at all.


I'm going to have to disagree with that.

For simplicity, look at the "single conductor in free air" tables. (The
other tables show it too, just the absolute values are lower.)

With 60-90C rated insulation, a #14 wire is rated for 20A. With
110-125C rated insulation, that same size wire is rated for 40A. If you
go up to 200C insulation, you can put 45A through it.


Somehow, I suspect that upgrading from 110 or 125 C insulation to 200 C
insulation only improving ampacity from 40 to 45 amps supports my point!

Meanwhile, also consider that wiring in a building is usually not single
conductor in free air, but 2 at least current-carrying conductors close to
each other and heating each other up with a sheath around them and the
environment outside the sheath usually not being "free air".

Add to this the fact that extra high temperature rating wire is used
more where ambient temperature is higher, and I see good reason for AWG 14
romex to be only allowed by code to be used in circuits up to 15 amps
regardless of temperature rating.

- Don Klipstein )
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Using #14 wire for one light on 20A breaker

In article , (Don Klipstein) wrote:
In article , Chris Friesen wrote:
Don Klipstein wrote:

Since resistance increases with temperature, actual ampacity does not
increase much with an increase in temperature rating. And ampacity
according to the code does not increase at all.


I'm going to have to disagree with that.

For simplicity, look at the "single conductor in free air" tables. (The
other tables show it too, just the absolute values are lower.)

With 60-90C rated insulation, a #14 wire is rated for 20A. With
110-125C rated insulation, that same size wire is rated for 40A. If you
go up to 200C insulation, you can put 45A through it.


Somehow, I suspect that upgrading from 110 or 125 C insulation to 200 C
insulation only improving ampacity from 40 to 45 amps supports my point!


Quite the opposite: it clearly contradicts your assertion that it "does not
increase at all". And, of course, the difference between 20A at 60 deg and 40A
at 125 deg makes that contradiction even more clear.

Meanwhile, also consider that wiring in a building is usually not single
conductor in free air, but 2 at least current-carrying conductors close to
each other and heating each other up with a sheath around them and the
environment outside the sheath usually not being "free air".


That was just an example -- and maybe not a real good one. But it does show
that (not to put too fine a point on it) you don't know what you're talking
about when you say that "ampacity according to the code does not increase at
all".

That's just not true.

See NEC Table 310.16 for abundant proof that the ampacity of a
conductor -- ANY conductor, ANY size -- absolutely DOES increase with
increasing temperature rating of the insulation.

Add to this the fact that extra high temperature rating wire is used
more where ambient temperature is higher, and I see good reason for AWG 14
romex to be only allowed by code to be used in circuits up to 15 amps
regardless of temperature rating.


That's a completely separate issue from the ampacity of the wire, which Code
specifies as being, for example, 25A with THHN insulation. In a separate
article, Code limits the overcurrent protection for 14 and 12 ga conductors to
15 and 20 amps, respectively, despite their having a higher ampacity.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
14 Wire on 20amp Breaker... [email protected] Home Repair 7 September 1st 06 07:14 PM
Help tracing breaker and wire gsmith97893 Home Repair 9 April 12th 06 06:57 PM
When (if ever) can 14ga wire be used with 20A circuit breaker? blueman Home Repair 9 February 10th 06 06:21 PM
When to use 15A vs. 20A circuits (and #14 vs #12 wire)? Jeffrey J. Kosowsky Home Repair 34 November 2nd 04 07:58 PM
Breaker and wire size? Tony Woodworking 15 March 5th 04 01:20 AM


All times are GMT +1. The time now is 04:20 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"