When I said "I've got a Japanese Akai S1000 sampler", I actually meant "I'm
selling a Japanese Akai S1000 sampler for someone else". As a result, I
didn't know much about the unit and its condition.

But I asked the owner what she used to do with regards to power supply and
she gave me the transformer that she had been running it off for the past 7
years or so. Surprise surprise - it's a 240V to 115V transformer, and she
said the Akai always worked fine despite being labelled 100V. In other
words, she'd been using an incorrect transformer for years, but it worked
anyway.

A buyer emailed me today from eBay asking if the screen was still bright or
if it had gone dim with age, so I plugged in the sampler using
aforementioned 115V transformer and promptly got an electric shock from an
area on the sampler's case where a bit of the paint had been scratched off,
leaving bare metal. It is worth bearing in mind that I was barefoot and
standing on a concrete garage floor, but nevertheless, this shouldn't
happen. I plugged it in again and the same thing happened. However, when
turned on, the sampler worked fine - it just gave me a shock whenever I
touched the case (a sizeable electric shock, not like static). The owner
said that she'd never experienced this before despite using the sampler with
the same transformer on a UK mains supply.

One thing I noticed about the unit was that it used a 2-pin power lead with
apparently no earth. As in, the socket on the machine only had 2 pins, so
there was no option to use an earthed cable (even though the transformer had
earthed sockets). What's the deal with this? Can anything be done? Obviously
I can't sell a unit on eBay in Very Good Condition if it shocks you when you
plug it in, even if it works fine otherwise.

Is my only option to sell it as-seen with a buyer warning?

Thanks,

--
tj hertz




  #2   Report Post  
Richard Crowley
 
Posts: n/a
Default

"TJ Hertz" wrote ...
When I said "I've got a Japanese Akai S1000 sampler",
I actually meant "I'm selling a Japanese Akai S1000 sampler
for someone else". As a result, I didn't know much about
the unit and its condition.

But I asked the owner what she used to do with regards to
power supply and she gave me the transformer that she had
been running it off for the past 7 years or so. Surprise surprise
- it's a 240V to 115V transformer, and she said the Akai
always worked fine despite being labelled 100V. In other
words, she'd been using an incorrect transformer for years,
but it worked anyway.


Generously-designed equipment can likely take a 15% over-
voltage although it may run warmer (and may reduce its expected
lifespan.) But lots of modern equipment is designed on the very
edge of acceptable ranges, so I wouldn't try it as a rule.

A buyer emailed me today from eBay asking if the screen was
still bright or if it had gone dim with age, so I plugged in the
sampler using aforementioned 115V transformer and promptly
got an electric shock from an area on the sampler's case where
a bit of the paint had been scratched off, leaving bare metal. It
is worth bearing in mind that I was barefoot and standing on a
concrete garage floor, but nevertheless, this shouldn't happen.
I plugged it in again and the same thing happened. However,
when turned on, the sampler worked fine - it just gave me a
shock whenever I touched the case (a sizeable electric shock,
not like static). The owner said that she'd never experienced
this before despite using the sampler with the same transformer
on a UK mains supply.


PLEASE DON'T do that experiment again. We would miss you
if you electrocuted yourself! Seriously! There are SAFE ways
of testing for this that don't put your life or limb at risk.

One thing I noticed about the unit was that it used a 2-pin power
lead with apparently no earth. As in, the socket on the machine
only had 2 pins, so there was no option to use an earthed cable
(even though the transformer had earthed sockets). What's the
deal with this? Can anything be done? Obviously I can't sell a unit
on eBay in Very Good Condition if it shocks you when you plug
it in, even if it works fine otherwise.
Is my only option to sell it as-seen with a buyer warning?


Now that you know about it, and especially now that you have
revealed it in public, you really have no ethical choice but to
disclose it to any potential buyer. If somebody bought it and
electrocuted themselves full disclosure would be your minimum
defense.

If it were me, I would be tempted to fit an IEC power connector
on it (like the kind used for computers), with the green-wire
ground securely bonded to the metal chassis. But mains wiring
is not a project for amateurs. I would think that most consumer
equipment service shops ("TV Repair", etc.) would be equipped
for and experienced with testing and fixing this kind of problem.

Ironically, it may be working just as it was designed back
when it was first sold. But you can't get away without telling
bidders about the hazard today IMHO.


  #3   Report Post  
Beachcomber
 
Posts: n/a
Default


One thing I noticed about the unit was that it used a 2-pin power lead with
apparently no earth. As in, the socket on the machine only had 2 pins, so
there was no option to use an earthed cable (even though the transformer had
earthed sockets). What's the deal with this? Can anything be done? Obviously
I can't sell a unit on eBay in Very Good Condition if it shocks you when you
plug it in, even if it works fine otherwise.

Is my only option to sell it as-seen with a buyer warning?


If you sell this product, even with a warning, you are opening up
yourself to servere liability issues.

An electric shock can be painful under the best conditions and
potentially deadly under the worst conditons.

It's likely that the transformer that the person you bought this from
was providing isolation and hence their claim of no shocks may have
valid.

Beachcomber


  #4   Report Post  
operator jay
 
Posts: n/a
Default


"Richard Crowley" wrote in message
...
"TJ Hertz" wrote ...



One thing I noticed about the unit was that it used a 2-pin power
lead with apparently no earth. As in, the socket on the machine
only had 2 pins, so there was no option to use an earthed cable
(even though the transformer had earthed sockets). What's the
deal with this? Can anything be done? Obviously I can't sell a unit
on eBay in Very Good Condition if it shocks you when you plug
it in, even if it works fine otherwise.
Is my only option to sell it as-seen with a buyer warning?



Someone pointed out the online manual. It has specific mention of earthing
in certain regions. You might want to take a look. Maybe something there
will be worth knowing.

j


  #5   Report Post  
TJ Hertz
 
Posts: n/a
Default

Richard Crowley wrote:
"TJ Hertz" wrote ...
When I said "I've got a Japanese Akai S1000 sampler",
I actually meant "I'm selling a Japanese Akai S1000 sampler
for someone else". As a result, I didn't know much about
the unit and its condition.

But I asked the owner what she used to do with regards to
power supply and she gave me the transformer that she had
been running it off for the past 7 years or so. Surprise surprise
- it's a 240V to 115V transformer, and she said the Akai
always worked fine despite being labelled 100V. In other
words, she'd been using an incorrect transformer for years,
but it worked anyway.


Generously-designed equipment can likely take a 15% over-
voltage although it may run warmer (and may reduce its expected
lifespan.) But lots of modern equipment is designed on the very
edge of acceptable ranges, so I wouldn't try it as a rule.

A buyer emailed me today from eBay asking if the screen was
still bright or if it had gone dim with age, so I plugged in the
sampler using aforementioned 115V transformer and promptly
got an electric shock from an area on the sampler's case where
a bit of the paint had been scratched off, leaving bare metal. It
is worth bearing in mind that I was barefoot and standing on a
concrete garage floor, but nevertheless, this shouldn't happen.
I plugged it in again and the same thing happened. However,
when turned on, the sampler worked fine - it just gave me a
shock whenever I touched the case (a sizeable electric shock,
not like static). The owner said that she'd never experienced
this before despite using the sampler with the same transformer
on a UK mains supply.


PLEASE DON'T do that experiment again. We would miss you
if you electrocuted yourself! Seriously! There are SAFE ways
of testing for this that don't put your life or limb at risk.

One thing I noticed about the unit was that it used a 2-pin power
lead with apparently no earth. As in, the socket on the machine
only had 2 pins, so there was no option to use an earthed cable
(even though the transformer had earthed sockets). What's the
deal with this? Can anything be done? Obviously I can't sell a unit
on eBay in Very Good Condition if it shocks you when you plug
it in, even if it works fine otherwise.
Is my only option to sell it as-seen with a buyer warning?


Now that you know about it, and especially now that you have
revealed it in public, you really have no ethical choice but to
disclose it to any potential buyer. If somebody bought it and
electrocuted themselves full disclosure would be your minimum
defense.


Yeah, I know, and that's probably what I'll do - I was just asking if there
were any ways of fixing it. Obviously if the problem remains I will warn any
buyer.


If it were me, I would be tempted to fit an IEC power connector
on it (like the kind used for computers), with the green-wire
ground securely bonded to the metal chassis. But mains wiring
is not a project for amateurs. I would think that most consumer
equipment service shops ("TV Repair", etc.) would be equipped
for and experienced with testing and fixing this kind of problem.

Ironically, it may be working just as it was designed back
when it was first sold. But you can't get away without telling
bidders about the hazard today IMHO.


I'll take it into a repair shop methinks. Thanks for the help.

TJ

--
tj hertz






  #6   Report Post  
Don Kelly
 
Posts: n/a
Default

"TJ Hertz" wrote in message
k...
When I said "I've got a Japanese Akai S1000 sampler", I actually meant

"I'm
selling a Japanese Akai S1000 sampler for someone else". As a result, I
didn't know much about the unit and its condition.

But I asked the owner what she used to do with regards to power supply and
she gave me the transformer that she had been running it off for the past

7
years or so. Surprise surprise - it's a 240V to 115V transformer, and she
said the Akai always worked fine despite being labelled 100V. In other
words, she'd been using an incorrect transformer for years, but it worked
anyway.

A buyer emailed me today from eBay asking if the screen was still bright

or
if it had gone dim with age, so I plugged in the sampler using
aforementioned 115V transformer and promptly got an electric shock from an
area on the sampler's case where a bit of the paint had been scratched

off,
leaving bare metal. It is worth bearing in mind that I was barefoot and
standing on a concrete garage floor, but nevertheless, this shouldn't
happen. I plugged it in again and the same thing happened. However, when
turned on, the sampler worked fine - it just gave me a shock whenever I
touched the case (a sizeable electric shock, not like static). The owner
said that she'd never experienced this before despite using the sampler

with
the same transformer on a UK mains supply.

One thing I noticed about the unit was that it used a 2-pin power lead

with
apparently no earth. As in, the socket on the machine only had 2 pins, so
there was no option to use an earthed cable (even though the transformer

had
earthed sockets). What's the deal with this? Can anything be done?

Obviously
I can't sell a unit on eBay in Very Good Condition if it shocks you when

you
plug it in, even if it works fine otherwise.

Is my only option to sell it as-seen with a buyer warning?

Thanks,

--
tj hertz

It appears that the original usage was 240V to ground and the transformer is
an autotransformer. Using this transformer with a North American 240/120V
system could put the case at 120V with respect to ground.
If this unit is to be used with a transformer, it will require an isolating
(2 winding) 240/120V transformer and then the case can be grounded.

However, why use the transformer?

Why not connect directly to the 120V outlet. It will be necessary to
determine which lead is the neutral. You will need a voltmeter. If the case
is at 120 or so Volts to ground- reverse the wires to the plug. Check
again-you want a small or negligable voltage between case and ground. Then
set up the plug and leads accordingly (replacing the cord and plug to a 3
prong (hot, neutral and ground) is the best way.
If you have any doubts, a competent electrician can sort it out for you in a
short time- or you warn the potential buyer that it appears that the case is
tied to the neutral and you don't know which wire is neutral and leave the
correction to him/her. You don't want to be responsible for avoidable
injuries.
--
Don Kelly

remove the urine to answer


  #7   Report Post  
TJ Hertz
 
Posts: n/a
Default

Don Kelly wrote:
"TJ Hertz" wrote in message
k...
When I said "I've got a Japanese Akai S1000 sampler", I actually
meant "I'm selling a Japanese Akai S1000 sampler for someone else".
As a result, I didn't know much about the unit and its condition.

But I asked the owner what she used to do with regards to power
supply and she gave me the transformer that she had been running it
off for the past 7 years or so. Surprise surprise - it's a 240V to
115V transformer, and she said the Akai always worked fine despite
being labelled 100V. In other words, she'd been using an incorrect
transformer for years, but it worked anyway.

A buyer emailed me today from eBay asking if the screen was still
bright or if it had gone dim with age, so I plugged in the sampler
using aforementioned 115V transformer and promptly got an electric
shock from an area on the sampler's case where a bit of the paint
had been scratched off, leaving bare metal. It is worth bearing in
mind that I was barefoot and standing on a concrete garage floor,
but nevertheless, this shouldn't happen. I plugged it in again and
the same thing happened. However, when turned on, the sampler worked
fine - it just gave me a shock whenever I touched the case (a
sizeable electric shock, not like static). The owner said that she'd
never experienced this before despite using the sampler with the
same transformer on a UK mains supply.

One thing I noticed about the unit was that it used a 2-pin power
lead with apparently no earth. As in, the socket on the machine only
had 2 pins, so there was no option to use an earthed cable (even
though the transformer had earthed sockets). What's the deal with
this? Can anything be done? Obviously I can't sell a unit on eBay in
Very Good Condition if it shocks you when you plug it in, even if it
works fine otherwise.

Is my only option to sell it as-seen with a buyer warning?

Thanks,

--
tj hertz

It appears that the original usage was 240V to ground and the
transformer is an autotransformer. Using this transformer with a
North American 240/120V system could put the case at 120V with
respect to ground.
If this unit is to be used with a transformer, it will require an
isolating (2 winding) 240/120V transformer and then the case can be
grounded.

However, why use the transformer?

Why not connect directly to the 120V outlet. It will be necessary to
determine which lead is the neutral. You will need a voltmeter. If
the case is at 120 or so Volts to ground- reverse the wires to the
plug. Check again-you want a small or negligable voltage between case
and ground. Then set up the plug and leads accordingly (replacing
the cord and plug to a 3 prong (hot, neutral and ground) is the best
way.
If you have any doubts, a competent electrician can sort it out for
you in a short time- or you warn the potential buyer that it appears
that the case is tied to the neutral and you don't know which wire is
neutral and leave the correction to him/her. You don't want to be
responsible for avoidable injuries.


So basically, you're saying find out which way the thing should be connected
in order to let the case be neutral, replace the mains end of the cable with
a 3-pin plug so that it can't be connected the wrong way, and glue/fix the
sampler end of the cable into the sampler so it can't be reversed (or label
which way it should go)? And this would fix the electric shock problem, but
still leave the unit unearthed?

I'll let an electrician deal with it because I have neither a
volt/multimeter nor any spare 3-pin plugs (you don't see many in the UK),
but I'd like to know what's going on anyway.

Thanks

--
tj hertz




  #8   Report Post  
Richard Crowley
 
Posts: n/a
Default

"Don Kelly" wrote ...
However, why use the transformer?

Why not connect directly to the 120V outlet.


Are those common in England? I've never seen any.
  #9   Report Post  
Steve Urbach
 
Posts: n/a
Default

On Tue, 31 May 2005 18:29:35 -0700, "Richard Crowley"
wrote:

"Don Kelly" wrote ...
However, why use the transformer?

Why not connect directly to the 120V outlet.


Are those common in England? I've never seen any.

On the shaving mirror in hotels G. I just would not plug good
electronics into it :O


, _
, | \ MKA: Steve Urbach
, | )erek No JUNK in my email please
, ____|_/ragonsclaw
, / / / Running United Devices "Cure For Cancer" Project 24/7 Have you helped?
http://www.grid.org
  #10   Report Post  
w_tom
 
Posts: n/a
Default

Ioslation transformer must still have the secondary (the 120
volt side) connected back to the building safety ground. If
not, then the appliance will 'float' - can become electrically
hot. If the transformer is properly designed, then either it
has such a connection OR it has a dedicated grounding wire
terminal to make that necessary connection.

TJ Hertz wrote:
Yeah, I know, and that's probably what I'll do - I was just asking
if there were any ways of fixing it. Obviously if the problem
remains I will warn any buyer.
...



  #11   Report Post  
Phil Allison
 
Posts: n/a
Default


"w_tom"

Ioslation transformer must still have the secondary (the 120
volt side) connected back to the building safety ground.



** Making it no longer an "isolation " transformer.


If not, then the appliance will 'float' - can become electrically
hot.



** The appliance's AC supply wiring will float - but nothing else since
it is all insulated from that wiring.


If the transformer is properly designed, then either it
has such a connection OR it has a dedicated grounding wire
terminal to make that necessary connection.



** A step-down / isolation transformer ought to have a ground terminal on
the outlet that connects to the METALWORK of the appliance via the third pin
of the plug.




........... Phil









  #12   Report Post  
Scott Dorsey
 
Posts: n/a
Default

In article , w_tom wrote:
Ioslation transformer must still have the secondary (the 120
volt side) connected back to the building safety ground. If
not, then the appliance will 'float' - can become electrically
hot. If the transformer is properly designed, then either it
has such a connection OR it has a dedicated grounding wire
terminal to make that necessary connection.


No, that's the point of isolation. Because the appliance floats, it can
become "hot" but the leakage current has no reference to the building
ground so if you touch the hot case, no current will flow through you.

Not that a safety ground isn't _still_ a good idea, mind you.
--scott


--
"C'est un Nagra. C'est suisse, et tres, tres precis."
  #13   Report Post  
Dimitrios Tzortzakakis
 
Posts: n/a
Default

Yes, that's why in all around the world the neutral of LV distribution
transformers is earthed (so I learned in my studies) so that you get
schocked and know that electricity is dangerous (no joke) AND because in a
neighborhood e.g. someone would be touching a live phase and someone else
another, so that both would be exposed to the line to line voltage which is
380 V in Europe (220 V in USA).However this happens only in LV, in MV, HV
and EHV there's no need for a reference to ground, because the windings of
the substation transformer are in delta, ungrounded.This doesn't make the
voltage not dangerous, I was told some horror stories back in Kozani.

--
Tzortzakakis Dimitrios
major in electrical engineering, freelance electrician
FH von Iraklion-Kreta, freiberuflicher Elektriker
dimtzort AT otenet DOT gr
Ο "Scott Dorsey" έγραψε στο μήνυμα
...
In article , w_tom

wrote:
Ioslation transformer must still have the secondary (the 120
volt side) connected back to the building safety ground. If
not, then the appliance will 'float' - can become electrically
hot. If the transformer is properly designed, then either it
has such a connection OR it has a dedicated grounding wire
terminal to make that necessary connection.


No, that's the point of isolation. Because the appliance floats, it can
become "hot" but the leakage current has no reference to the building
ground so if you touch the hot case, no current will flow through you.

Not that a safety ground isn't _still_ a good idea, mind you.
--scott


--
"C'est un Nagra. C'est suisse, et tres, tres precis."



  #14   Report Post  
Don Kelly
 
Posts: n/a
Default

"Dimitrios Tzortzakakis" wrote in message
...
Yes, that's why in all around the world the neutral of LV distribution
transformers is earthed (so I learned in my studies) so that you get
schocked and know that electricity is dangerous (no joke) AND because in a
neighborhood e.g. someone would be touching a live phase and someone else
another, so that both would be exposed to the line to line voltage which

is
380 V in Europe (220 V in USA).However this happens only in LV, in MV, HV
and EHV there's no need for a reference to ground, because the windings of
the substation transformer are in delta, ungrounded.This doesn't make the
voltage not dangerous, I was told some horror stories back in Kozani.

--
Tzortzakakis Dimitrios
major in electrical engineering, freelance electrician
FH von Iraklion-Kreta, freiberuflicher Elektriker
dimtzort AT otenet DOT gr

---------------
In LV, MV , HV and RHV. the transformer windings can be and often are in Y.-
.. The most common connection is Delta Wye with the HV side in Wye with
direct or impedance grounding. There are good technical and economic reasons
for that. The next most common connection is probably Y-Y -delta for
supplying EHV lines . Note that even at 4160V distribution the supply
transformer is Y on the 4160V side.
Ground faults are the most common faults on transmission lines. This means
that the unfaulted phases will see overvoltages- not good. In addition,
protective relaying problems are increased and arcing faults which are not
detected and often undetectable can occur because of capacitive coupling.
The grounding eliminates these problems as well as problems due to the line
floating up and down due to atmospheric effects (thus stressing the
insulation). The use of a Y system makes life a lot easier.

--
Don Kelly

remove the urine to answer


Ο "Scott Dorsey" έγραψε στο μήνυμα
...
In article , w_tom

wrote:
Ioslation transformer must still have the secondary (the 120
volt side) connected back to the building safety ground. If
not, then the appliance will 'float' - can become electrically
hot. If the transformer is properly designed, then either it
has such a connection OR it has a dedicated grounding wire
terminal to make that necessary connection.


No, that's the point of isolation. Because the appliance floats, it can
become "hot" but the leakage current has no reference to the building
ground so if you touch the hot case, no current will flow through you.

Not that a safety ground isn't _still_ a good idea, mind you.
--scott


--
"C'est un Nagra. C'est suisse, et tres, tres precis."





  #16   Report Post  
Rich Grise
 
Posts: n/a
Default

On Tue, 31 May 2005 14:44:52 +0000, TJ Hertz wrote:

... promptly got an electric shock from an
area on the sampler's case where a bit of the paint had been scratched off,
leaving bare metal. It is worth bearing in mind that I was barefoot and
standing on a concrete garage floor, but nevertheless, this shouldn't
happen.


This is correct. Standing barefoot on a concrete garage floor while
dicking around with anything plugged into mains should never happen.

Good Luck - you'll need it.
Rich

  #17   Report Post  
Rich Grise
 
Posts: n/a
Default

On Tue, 31 May 2005 09:15:40 -0700, Richard Crowley wrote:

"TJ Hertz" wrote ...


shock whenever I touched the case (a sizeable electric shock,
not like static). The owner said that she'd never experienced
this before despite using the sampler with the same transformer
on a UK mains supply.


PLEASE DON'T do that experiment again. We would miss you
if you electrocuted yourself! Seriously! There are SAFE ways
of testing for this that don't put your life or limb at risk.


Nah - we'll just nominate him for this year's Darwin award.

Cheers!
Rich

  #18   Report Post  
Bob Stephens
 
Posts: n/a
Default

On Fri, 03 Jun 2005 15:24:55 GMT, Rich Grise wrote:

This is correct. Standing barefoot on a concrete garage floor while
dicking around with anything plugged into mains should never happen.


Word up.

  #19   Report Post  
tater schuld
 
Posts: n/a
Default

"Rich Grise" wrote in message
news
On Tue, 31 May 2005 14:44:52 +0000, TJ Hertz wrote:

... promptly got an electric shock from an
area on the sampler's case where a bit of the paint had been scratched

off,
leaving bare metal. It is worth bearing in mind that I was barefoot and
standing on a concrete garage floor, but nevertheless, this shouldn't
happen.


This is correct. Standing barefoot on a concrete garage floor while
dicking around with anything plugged into mains should never happen.

Good Luck - you'll need it.
Rich

NOTE: this experience happened in the U.S.A. and other countries may differ

a friend of mine had a phonograph player in his basement. the unit operated
fine, but if you touched a metal part of the player, and a metal support
post in the basement, you would get a mild shock (about half of what I've
gotten from touching 110v mains by accident)

Later on in life, I found out that if you attempt to bypass the safety
feature of polarized p,ugs for non-grounded equipment, or if the electrical
outlet was wired incorrectly, this happens.

as you are on a foriegn system, I cannot be sure, but I'd advise to switch
the live and neutral lines. and also put an earth line in there also.



--
Tater
President of MARS Club (NAR #660)
www.mars-rocketry.com
KC9ESF
NAR #79654 L1
EAA #703312
remove spam spelled backwards to reply





  #20   Report Post  
Scott Dorsey
 
Posts: n/a
Default

tater schuld wrote:
NOTE: this experience happened in the U.S.A. and other countries may differ

a friend of mine had a phonograph player in his basement. the unit operated
fine, but if you touched a metal part of the player, and a metal support
post in the basement, you would get a mild shock (about half of what I've
gotten from touching 110v mains by accident)


This is because it was a hot chassis player. That is no longer acceptable
in the US, but it was very popular for many years for cheap consumer electronics
to operate without a power transformer and use a hot chassis. For almost
any cheap table radio, record player, or TV set made before 1970 this was
the case, and for a lot of TV sets well into the eighties it remained the
case.

Later on in life, I found out that if you attempt to bypass the safety
feature of polarized p,ugs for non-grounded equipment, or if the electrical
outlet was wired incorrectly, this happens.


That just makes the problem worse, yes.

as you are on a foriegn system, I cannot be sure, but I'd advise to switch
the live and neutral lines. and also put an earth line in there also.


Grounding is a good idea, but if there is chassis leakage, that is bad and
it should be fixed if possible.
--scott
--
"C'est un Nagra. C'est suisse, et tres, tres precis."
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power shower electrical shocks Dave UK diy 4 June 4th 04 07:54 PM
FS: 110V portable isolating transformer for power tools etc. Mike Tomlinson UK diy 2 May 24th 04 06:31 PM
electric power shower Franglais UK diy 10 May 10th 04 12:37 PM
Why 110v power tools? Parish UK diy 63 March 26th 04 10:12 PM
Electric fence power indicator? Neon? Andy Dingley UK diy 17 October 13th 03 12:57 PM


All times are GMT +1. The time now is 05:47 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"