"DaveC" wrote in message
al.net...
I've got several remote alarm sensors triggered by 120vac relays. When

power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed.

Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power

is
OK. Will a series diode and shunt cap do the trick? If so, what size cap?

If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw

Thanks,
--
Please, no "Go Google this" replies. I wouldn't
ask a question here if I hadn't done that already.

DaveC


Hi. Hmm, sorry but you should Goo.... Altavista this. Use the term 'delay
relay'. Here's one:
http://www.automatictiming.com/pages...layrelays.html

The more run-of-the-mill parts places don't sell them, but relay specialists
do (not sure what the situation is in your area).
Farnell also have these (they're possibly easier to use):
http://au.farnell.com/jsp/endecaSear...erDisplay=true

(They operate USA too, I just didn't have the link handy)

Cheers.

Ken


  #2   Report Post  
majortom
 
Posts: n/a
Default

What would be the purpose of setting off ur alarm every time power
fails??
Not being nosey, it's just that the only alarm panels (fire/security)
I've seen had some form of
battery backup, whether it be Nicad, Lead Acid, etc. to keep the system
running
normally under power failure.

  #3   Report Post  
 
Posts: n/a
Default

Not being nosey, it's just that the only alarm panels
(fire/security)
I've seen had some form of
battery backup, whether it be Nicad, Lead Acid, etc. to keep the

system

Yes, but they still dial home to report AC loss.

  #4   Report Post  
majortom
 
Posts: n/a
Default

k, then yeah the brit guy above pointing toward the time delay relays
might be a way to go...

  #5   Report Post  
legg
 
Posts: n/a
Default

On Tue, 4 Jan 2005 18:09:21 -0800, DaveC wrote:

I've got several remote alarm sensors triggered by 120vac relays. When power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed. Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power is
OK. Will a series diode and shunt cap do the trick? If so, what size cap? If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw


Assuming power is available to make the call, your control circuit
obviously doesn't depend on 120VAC being present, to function. It is
also unlikely that your remote sensors run on 120VAC, as this could
represent an unneccessary safety hazard.

Therefore the delay is best performed in the device's control section,
using the power provided to perform the control function.

5 minutes is an incredibly long delay to ask of a de-energized relay.
It also could represent a signifigant security breach, if ignored. Why
power loss should affect remote sensors is a question you should raise
with the vendor.

You should get the liable vendor or service rep to set the product up
to meet realistic expectations that don't compromise security or
convenient function.
...............................................
Imagine if the delay was required of the hardware relay alone -
assuming a 100mW coil , that drops out at 45% of the label voltage;

5 minutes hold-up requires 30j minimum of stored energy.
(.1 x 60 x 5)

If the initial stored voltage was 165V, and drop-out was 75V, the
storage cap required would be 700uF

If the initial stored voltage was 12v and dropout was 5V4, the storage
cap required would be 3 Farads.
.................................................. ..

This example used an extremely sensitive device - your referenced part
consumes 80 times the power in the example and would require 80 times
the stored energy, 80 times the capacitance.

The obvious source of stored energy for any controlled delay is the
controller's supply.

RL



  #6   Report Post  
NSM
 
Posts: n/a
Default


"DaveC" wrote in message
al.net...
| I've got several remote alarm sensors triggered by 120vac relays. When
power
| fails, the alarm calls the right folks.
|
| Problem is that even the small power glitches get these guys out of bed.
Not
| a good thing.
|
| How can I delay the de-energizing of these relays? 5 minutes without power
is
| OK. Will a series diode and shunt cap do the trick? If so, what size cap?
If
| not, what're my options?

The normal method is a relay with a hydraulic delay. This means you don't
need a no fail power supply. However these days, if you have backup power,
there are solid state equivalents.

For your method you would need a large cap run off say, 12 VDC - maybe 1000
uF and up.

N


  #7   Report Post  
John G
 
Posts: n/a
Default


"DaveC" wrote in message
al.net...
So the answer is... no.

If power fails at the remote site, so does the control circuitry and
its
power. So a traditional delay relay won't work.

The relay, powered by mains, simply opens the wireless sensor's sense
circuit
when power goes away. I just want it to do so after waiting a few
minutes to
see if power comes back on.

The alarm isn't for security purposes, just for letting those
responsible
know that certain things have occurred, one of which is power fail.
The
sensor is a wireless device run on a lithium battery, and is a
packaged deal
so has no spare power available. The relay's not near the alarm CPU,
so that
power isn't available, either.

Suggestions for a simple mains-powered circuit that will open a pair
of
contacts about 5 minutes after de-energizing? If it's to be
battery-powered,
it needs to be super-low drain. I rather keep battery replacements
down to
every 2 years, at most.

An idea that just struck me: the presence of mains power could keep
this
circuit de-energized. When power fails, the battery is connected to
the
circuit which starts the countdown. When zero is reached (ie, 5
minutes have
passed), a pair of contacts would open. And the energizing circuit
(triggering these contacts) would only have to be a one-shot; once the
alarm
is triggered, the circuit could de-energize. That way the battery is
utilized
only briefly, during power-fail situations. How might I construct such
a
circuit?

Thanks,
--
Please, no "Go Google this" replies. I wouldn't
ask a question here if I hadn't done that already.

DaveC

This is an invalid return address
Please reply in the news group


I never cease to be amazed at the questions asked in this NG from people
who do not have a clue from grade school experiments about electronics
but want to design or modify industrial situations where some manager
should be putting up the money to employ a competent engineer skilled in
the particular area.

Relying on poorly informed advice is asking for trouble and a sure
course to the courts for a damages claim.
--
John G

Wot's Your Real Problem?


  #8   Report Post  
John Woodgate
 
Posts: n/a
Default

I read in sci.electronics.design that DaveC wrote (in
et) about 'Delay on a
mains-powered relay?', on Tue, 4 Jan 2005:
I've got several remote alarm sensors triggered by 120vac relays. When
power fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed.
Not a good thing.

How can I delay the de-energizing of these relays? 5 minutes without
power is OK. Will a series diode and shunt cap do the trick? If so, what
size cap?


Impractically big. If you get one big enough, Feerguy will want to hear
from you. (;-)

If not, what're my options?


Back-up battery and inverter. A standard UPS would probably do. Do you
know how much power the system consumes?
--
Regards, John Woodgate, OOO - Own Opinions Only.
The good news is that nothing is compulsory.
The bad news is that everything is prohibited.
http://www.jmwa.demon.co.uk Also see http://www.isce.org.uk
  #9   Report Post  
 
Posts: n/a
Default

In alt.engineering.electrical DaveC wrote:
The relay, powered by mains, simply opens the wireless sensor's sense
circuit when power goes away. I just want it to do so after waiting a
few minutes to see if power comes back on.


Can you use a solid state relay or a DIP relay, instead of the
presumably larger relay you're using now? If so, the coil current
will be much less, and you might be able to get away with something
like a wall transformer, a big capacitor, and the relay. The time
delay won't be very exact, but it may work for your application.

Matt Roberds

  #10   Report Post  
Frithiof Andreas Jensen
 
Posts: n/a
Default


"DaveC" wrote in message
al.net...

How can I delay the de-energizing of these relays?


Use a Thermal Relay - maybe called "Delay Relay". Best approach is to find
out what the format/socket is, then one of the suppliers of process control
gear will have something that plug into it.




  #11   Report Post  
Tony Williams
 
Posts: n/a
Default

In article et,
DaveC wrote:

How can I delay the de-energizing of these relays? 5 minutes
without power is OK.


Use something like this maybe. View in fixed width font.
____
+---------+ +------|AC +DC|---+-----+ +----Out
| | | | | _|_ |
)||( | Bridge | +|C | | o |
120Vac )||(18Vac |Rectifier| === | RL|----|N/O
)||( | | | |_ _| o |
| | | | | | |
+---------+ +------|AC____-DC|---+-----+ +----Out

A 120:18V transformer on the mains, bridge rectifier,
capacitor smoothing, and 24V comms relay.

Relays have an On/Off hysteresis. Once it has been
energised, a 24V comms relay will not then release
until the voltage has reduced to below about 8V.

24V sinking to 8V is not far off T = R*C.

A standard 24Vdc high sensitivity comms relay has a coil
resistance of about 2900 ohms. If C= 47000uF then the
the relay will be held closed for about 136 secs after a
mains failure.

A 47000uF (at 35vdc working) is not cheap, and the thing
is a little clunky, but easy to put together and not much
to go wrong.

--
Tony Williams.
  #12   Report Post  
No Spam
 
Posts: n/a
Default

DaveC wrote:
I've got several remote alarm sensors triggered by 120vac relays. When power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed. Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power is
OK. Will a series diode and shunt cap do the trick? If so, what size cap? If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw

Thanks,


Someone suggested hydraulic. I was thinking pneumatic.
Checkout:
http://ecatalog.squared.com/catalog/.../17321027.html

Not cheap but do have a 5 min +/- 12% version.
  #13   Report Post  
Wayne Tiffany
 
Posts: n/a
Default

I don't know what is powering the relays, but can you use a UPS to keep it
powered, but then time out?

WT

"No Spam" wrote in message
...
DaveC wrote:
I've got several remote alarm sensors triggered by 120vac relays. When
power fails, the alarm calls the right folks. Problem is that even the
small power glitches get these guys out of bed. Not a good thing.

How can I delay the de-energizing of these relays? 5 minutes without
power is OK. Will a series diode and shunt cap do the trick? If so, what
size cap? If not, what're my options?

The relay is similar to this one: http://tinyurl.com/6pppw

Thanks,


Someone suggested hydraulic. I was thinking pneumatic. Checkout:
http://ecatalog.squared.com/catalog/.../17321027.html

Not cheap but do have a 5 min +/- 12% version.



  #14   Report Post  
Dimitrios Tzortzakakis
 
Posts: n/a
Default

No.These relays are designed to work in ac.There's no way in storing ac in a
capacitor and diode circuit.Only expensive inverter designs.You need some
engineer to construct a dedicated circuit, maybe with battery, for your
purposes.

--
Tzortzakakis Dimitri?s
major in electrical engineering, freelance electrician
FH von Iraklion-Kreta, freiberuflicher Elektriker
dimtzort AT otenet DOT gr
? "DaveC" ?????? ??? ??????
al.net...
I've got several remote alarm sensors triggered by 120vac relays. When

power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed.

Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power

is
OK. Will a series diode and shunt cap do the trick? If so, what size cap?

If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw

Thanks,
--
Please, no "Go Google this" replies. I wouldn't
ask a question here if I hadn't done that already.

DaveC

This is an invalid return address
Please reply in the news group



  #15   Report Post  
CJT
 
Posts: n/a
Default

John G wrote:
"DaveC" wrote in message
al.net...

So the answer is... no.

If power fails at the remote site, so does the control circuitry and
its
power. So a traditional delay relay won't work.

The relay, powered by mains, simply opens the wireless sensor's sense
circuit
when power goes away. I just want it to do so after waiting a few
minutes to
see if power comes back on.

The alarm isn't for security purposes, just for letting those
responsible
know that certain things have occurred, one of which is power fail.
The
sensor is a wireless device run on a lithium battery, and is a
packaged deal
so has no spare power available. The relay's not near the alarm CPU,
so that
power isn't available, either.

Suggestions for a simple mains-powered circuit that will open a pair
of
contacts about 5 minutes after de-energizing? If it's to be
battery-powered,
it needs to be super-low drain. I rather keep battery replacements
down to
every 2 years, at most.

An idea that just struck me: the presence of mains power could keep
this
circuit de-energized. When power fails, the battery is connected to
the
circuit which starts the countdown. When zero is reached (ie, 5
minutes have
passed), a pair of contacts would open. And the energizing circuit
(triggering these contacts) would only have to be a one-shot; once the
alarm
is triggered, the circuit could de-energize. That way the battery is
utilized
only briefly, during power-fail situations. How might I construct such
a
circuit?

Thanks,
--
Please, no "Go Google this" replies. I wouldn't
ask a question here if I hadn't done that already.

DaveC

This is an invalid return address
Please reply in the news group



I never cease to be amazed at the questions asked in this NG from people
who do not have a clue from grade school experiments about electronics
but want to design or modify industrial situations where some manager
should be putting up the money to employ a competent engineer skilled in
the particular area.

Relying on poorly informed advice is asking for trouble and a sure
course to the courts for a damages claim.


Engineering in the U.S. has never had the political clout needed for
effective enforcement of registration laws. A PE license carries with
it almost no recognition in a world where just about anyone can get
away with calling themselves an engineer (except where public funds are
involved). Doctors and lawyers, and even beauticians, have done a
better job getting their expertise recognized IMHO.

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .


  #17   Report Post  
Rob Gaddi
 
Posts: n/a
Default

Cheap microcontroller circuit, grounded to the low side of the wireless
sensor's sense contacts. Use the existing relay to signal the uC, and a
mosfet to open the connection. Depending on how much power the wireless
is providing to monitor the sense you may even be able to power just off
that, but if not, decently careful design on a ultra-low power
microcontroller should allow you to run for practically the shelf life
of the battery.

DaveC wrote:
So the answer is... no.

If power fails at the remote site, so does the control circuitry and its
power. So a traditional delay relay won't work.

The relay, powered by mains, simply opens the wireless sensor's sense circuit
when power goes away. I just want it to do so after waiting a few minutes to
see if power comes back on.

The alarm isn't for security purposes, just for letting those responsible
know that certain things have occurred, one of which is power fail. The
sensor is a wireless device run on a lithium battery, and is a packaged deal
so has no spare power available. The relay's not near the alarm CPU, so that
power isn't available, either.

Suggestions for a simple mains-powered circuit that will open a pair of
contacts about 5 minutes after de-energizing? If it's to be battery-powered,
it needs to be super-low drain. I rather keep battery replacements down to
every 2 years, at most.

An idea that just struck me: the presence of mains power could keep this
circuit de-energized. When power fails, the battery is connected to the
circuit which starts the countdown. When zero is reached (ie, 5 minutes have
passed), a pair of contacts would open. And the energizing circuit
(triggering these contacts) would only have to be a one-shot; once the alarm
is triggered, the circuit could de-energize. That way the battery is utilized
only briefly, during power-fail situations. How might I construct such a
circuit?

Thanks,


  #18   Report Post  
Richard Henne
 
Posts: n/a
Default

If you're in the US, try http://www.Grainger.com and do a key word
search using 120V off delay relay. You should be able to find something
that would work.

DaveC wrote:
I've got several remote alarm sensors triggered by 120vac relays. When power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed. Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power is
OK. Will a series diode and shunt cap do the trick? If so, what size cap? If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw

Thanks,

  #19   Report Post  
NSM
 
Posts: n/a
Default


"DaveC" wrote in message
al.net...
| So the answer is... no.
|
| If power fails at the remote site, so does the control circuitry and its
| power. So a traditional delay relay won't work.

Look for a spring powered timer then. They use an AC clock motor to hold
them at, say, 5 minutes. When the power goes off the spring unwinds until
the clock goes to zero and the contacts close/open. When the power is
restored the motor rewinds the timer to 5 minutes. Looks a bit like a cheap
cooking timer on a frame.

http://www.thomasregisterdirectory.c...0014366_1.html

N


  #20   Report Post  
NSM
 
Posts: n/a
Default


"CJT" wrote in message
...

| It's an AC relay. Just how do you intend to attach that "big capacitor?"

Obviously use a light (0.5W) DC relay!

http://www.nteinc.com/relay_web/R16.html

N




  #21   Report Post  
 
Posts: n/a
Default

DaveC wrote:

So the answer is... no.

If power fails at the remote site, so does the control circuitry and its
power. So a traditional delay relay won't work.

The relay, powered by mains, simply opens the wireless sensor's sense circuit
when power goes away. I just want it to do so after waiting a few minutes to
see if power comes back on.

The alarm isn't for security purposes, just for letting those responsible
know that certain things have occurred, one of which is power fail. The
sensor is a wireless device run on a lithium battery, and is a packaged deal
so has no spare power available. The relay's not near the alarm CPU, so that
power isn't available, either.

Suggestions for a simple mains-powered circuit that will open a pair of
contacts about 5 minutes after de-energizing? If it's to be battery-powered,
it needs to be super-low drain. I rather keep battery replacements down to
every 2 years, at most.

An idea that just struck me: the presence of mains power could keep this
circuit de-energized. When power fails, the battery is connected to the
circuit which starts the countdown. When zero is reached (ie, 5 minutes have
passed), a pair of contacts would open. And the energizing circuit
(triggering these contacts) would only have to be a one-shot; once the alarm
is triggered, the circuit could de-energize. That way the battery is utilized
only briefly, during power-fail situations. How might I construct such a
circuit?

Thanks,


Refer to the post by Tony Williams. There might be a cheaper way.
As he mentioned, the capacitor is expensive - you'll pay over
$15.00 dollars for one. The alternative described below would cost
a lot less. The super caps would cost you $1.70 for 2. The opto costs
50 cents. The voltage regulator costs another 50 cents. You can
get 2 10 K pots for a dollar. Add another dollar for the 1000uf
cap and resistor. I assume same price for the transformer as in
the relay design. You'll save at least $10.00 per sensor, if
the idea works. Since you have a number of sensors, it seems worth at
least trying one as proposed below. I do not know if it is practical
for you, or if it will work, since I don't have specs on the
existing setup.

You *may* be able to use an optoisolator, a super cap, and a
potientiometer instead of the relay. The potientiometer would allow
you to adjust the delay time. You would need to use a lower voltage
transformer and a regulator IC. The cost would be a lot lower. The
key is the current sense loop - without specs, I don't know if an
optoisolator will work. Here's the details if you decide to try it.

Here's Tony's circuit, modified for an optoisolator:

View in fixed width font.
____
+----+ +---|AC +DC|--+--7809---+---+-------+
| | | | | | +|C2 | __|__
)||( | | +|C1 | === R1 | + |--+Sense
120 )||(12 |Rect. | === | | | |Opto |
Vac )||(Vac| | | | +|C3 P-+ |__-__|--+Loop
)||( | | | | === | | |
| | | | | | | | | |
+----+ +---|AC_-DC|--+---+-----+---+--+----+

C1 is a 1000 uf 25 volt cap. C2 and C3 are .1 farad 5 volt super caps.
(Allelectronics sells these for 85 cents each) R1 is a 100 ohm
1/4 watt resistor. P is a 10K potentiometer. The opto is a 4N35.
The 7809 is a 9 volt three terminal IC voltage regulator.
The sense loop is connected to the existing relay points at present.
I don't know which is + and which is minus, but polarity is important
when you connect it to the opto.
  #22   Report Post  
legg
 
Posts: n/a
Default

On Wed, 05 Jan 2005 10:39:55 -0700, Richard Henne
wrote:

http://www.Grainger.com


You're right. They appear to do it all for you for $85.00. Notice the
total power consumption is 180mW, so the 'relay' must be quite low
power to be included in the budget.

http://makeashorterlink.com/?M2F312B2A

RL
  #23   Report Post  
 
Posts: n/a
Default

DaveC wrote:

So the answer is... no.

If power fails at the remote site, so does the control circuitry and its
power. So a traditional delay relay won't work.

The relay, powered by mains, simply opens the wireless sensor's sense circuit
when power goes away. I just want it to do so after waiting a few minutes to
see if power comes back on.

The alarm isn't for security purposes, just for letting those responsible
know that certain things have occurred, one of which is power fail. The
sensor is a wireless device run on a lithium battery, and is a packaged deal
so has no spare power available. The relay's not near the alarm CPU, so that
power isn't available, either.

Suggestions for a simple mains-powered circuit that will open a pair of
contacts about 5 minutes after de-energizing? If it's to be battery-powered,
it needs to be super-low drain. I rather keep battery replacements down to
every 2 years, at most.

An idea that just struck me: the presence of mains power could keep this
circuit de-energized. When power fails, the battery is connected to the
circuit which starts the countdown. When zero is reached (ie, 5 minutes have
passed), a pair of contacts would open. And the energizing circuit
(triggering these contacts) would only have to be a one-shot; once the alarm
is triggered, the circuit could de-energize. That way the battery is utilized
only briefly, during power-fail situations. How might I construct such a
circuit?

Thanks,


Here's an even better mod to Tony's circuit. You need
4 parts - all available from Allelectronics:
5 volt regulated wall wart p/n DCTX-512 $3.50
Minature 4.5 volt relay p/n RLY-639 $0.75
1N4001 diode (1 needed) p/n 1N4001 15 for $1.00
1 farad 5.5 volt super cap p/n CBC-12 $3.50

D
Wall + ------|---+-----+
Wart +|C |
=== Relay
| |
- -----------+-----+

I suspect the relay will stay energized longer
than 5 minutes. You can add a second diode to
reduce the time. You might need to add resistance
in parallel with the super cap to reduce it further.
This depends on the characteristics of the relay -
I don't have one to test.

Ed
  #24   Report Post  
Bill Kaszeta / Photovoltaic Resources
 
Posts: n/a
Default

On Tue, 4 Jan 2005 18:09:21 -0800, DaveC wrote:

I've got several remote alarm sensors triggered by 120vac relays. When power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed. Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power is
OK. Will a series diode and shunt cap do the trick? If so, what size cap? If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw

Thanks,
--
Please, no "Go Google this" replies. I wouldn't
ask a question here if I hadn't done that already.

DaveC

This is an invalid return address
Please reply in the news group

It is likely that your wireless device has an input circuit with a dc voltage
across the inputs when the input is open (that is how the open contacts
are sensed). One side is likely common with one terminal of the
battery.

You should try putting a power FET device across the input (source
and drain) and using a capacitor from source to gate to hold the
FET on for a period after your relay opens. A resistor across the
capacitor sets the discharge period. I would start with 470 MF and
1meg resistor for 4-5 minutes delay (depends on gate voltage on
turn-off, device specific).

If the battery negative is common to one of the input terminals,
use a N-channel FET (I did something similar with an IRF520,
way over kill on current, but you are not likely to damage it).
If the wireless device voltage is only 3 volts, you will need a
FET designed for logic level gate voltages.

Connect as follows:
Source of FET to - input terminal
Drain of FET to the other input terminal
Capacitor negative (use 16V cap) to Source
Capacitor positive to Gate
1 meg resistor across capacitor
100K resistor to battery +, other side of 100K to one of your relay contacts
Other relay contact to Gate.

Use a grounded soldering iron as the FET gate can be
damaged by static electricity.

If the battery positive is common to one of the input terminals,
use a P-channel FET and reverse all polarities listed above.

When the relay contacts are closed, the 100K resistor uses the
battery to charge the capacitor. Voltage on the capacitor keeps
the FET ON.

When the relay contacts open (on power fail) the capacitor holds
a charge while the 1 meg resistor discharges the capacitor. At
some low voltage on the Gate, the wireless sensor will detect an
open circuit and send the alarm. Experiment with resistance and
capacitance to get an acceptable time delay.

If you shop the parts, likely cost per circuit is
USD $2.00-4 .00.
Bill Kaszeta
Photovoltaic Resources Int'l
Tempe Arizona USA

  #25   Report Post  
CJT
 
Posts: n/a
Default

DaveC wrote:
I've got several remote alarm sensors triggered by 120vac relays. When power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed. Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power is
OK. Will a series diode and shunt cap do the trick? If so, what size cap? If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw

Thanks,


Here's what you do. Put a cheap answering machine on the same power
circuit that you're trying to monitor, and connect it to the phone line
that the call gets made on.

Tell the guys that when they get a call (they'll still be awakened, so
perhaps this is not a perfect solution) to call back to that number.
If the answering machine answers, it has power, and hence so does the
equipment. If the answering machine fails to answer, get in the truck.

;-)


--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .


  #27   Report Post  
Paul Hovnanian P.E.
 
Posts: n/a
Default

DaveC wrote:

I've got several remote alarm sensors triggered by 120vac relays. When power
fails, the alarm calls the right folks.

Problem is that even the small power glitches get these guys out of bed. Not
a good thing.

How can I delay the de-energizing of these relays? 5 minutes without power is
OK. Will a series diode and shunt cap do the trick? If so, what size cap? If
not, what're my options?

The relay is similar to this one:

http://tinyurl.com/6pppw

Thanks,
--
Please, no "Go Google this" replies. I wouldn't
ask a question here if I hadn't done that already.


Look for a TDDO (Time Delay Drop Out) relay.

--
Paul Hovnanian
------------------------------------------------------------------
Reject nihilism!
  #28   Report Post  
James Sweet
 
Posts: n/a
Default


"NSM" wrote in message news:jDJCd.44550$Y72.1684@edtnps91...

"DaveC" wrote in message
al.net...
| I've got several remote alarm sensors triggered by 120vac relays. When
power
| fails, the alarm calls the right folks.
|
| Problem is that even the small power glitches get these guys out of bed.
Not
| a good thing.
|
| How can I delay the de-energizing of these relays? 5 minutes without

power
is
| OK. Will a series diode and shunt cap do the trick? If so, what size

cap?
If
| not, what're my options?

The normal method is a relay with a hydraulic delay. This means you don't
need a no fail power supply. However these days, if you have backup power,
there are solid state equivalents.

For your method you would need a large cap run off say, 12 VDC - maybe

1000
uF and up.

N



Just put a delay circuit in between the relay contacts and whatever
(assuming low voltage) signal the control to the alarm panel. A 555 IC
driving a small low voltage relay should do the trick.


  #29   Report Post  
NSM
 
Posts: n/a
Default


"James Sweet" wrote in message
news:fA3Dd.26413$2X6.14665@trnddc07...

| But it sounds like the 120v coil is used to detect mains failure, power
goes
| out, relay loses power, contacts open/close, triggering the alarm. The
relay
| can be left alone, you only have to mess with the low voltage signal it
| switches.

If he wants to use a cap to delay it the lower power the better. Even a reed
relay will work OK and keep the cap size down. That's the key - run from a
rectifier circuit.

N


  #30   Report Post  
NSM
 
Posts: n/a
Default


"Ross Herbert" wrote in message
...

| It seems to me that the OP would prefer to use what hardware exists
| now in order to minimise expense and the complexity involved in a
| complete re-design of what he now has. The relay he is using now is a
| 3 pole changeover unit so depending upon what is currently connected
| to the relay contacts will have some bearing on what he can do in the
| easiest and most cost effective manner.

....

I remember small, inexpensive delays that used an AC clock motor to wind
them up. When the power went off they ran down and switched contacts. I
suggested that previously.

N




  #31   Report Post  
 
Posts: n/a
Default

wrote:

In alt.engineering.electrical
wrote:


+----+ +---|AC +DC|--+--7809---+---+-------+
| | | | | | +|C2 | __|__
)||( | | +|C1 | === R1 | + |--+Sense
120 )||(12 |Rect. | === | | | |Opto |
Vac )||(Vac| | | | +|C3 P-+ |__-__|--+Loop
)||( | | | | === | | |
| | | | | | | | | |
+----+ +---|AC_-DC|--+---+-----+---+--+----+

C1 is a 1000 uf 25 volt cap. C2 and C3 are .1 farad 5 volt super caps.
(Allelectronics sells these for 85 cents each)



The 85 cent ones (CBC-125) are 1 F, 2.5 V.


No, the CBC-125 is not the one I had in mind. I should have made it clearer.
It is CBC-131, which is 85 cents in qty 10 and is .1 (point one) uf at
5 volts,
not 1 uf at 2.5 volts. The CBC-125 is $1.00 each in qty 10

Some optos will work as low as 50 ua, from what I have read. The question
that is not answered is what his sense loop needs (how much current at
what sense voltage) and of course whether the opto will permit that current
over the full delay time.

snip

Digi-Key has Cooper PowerStor capacitors
that come already packaged as two 2.5 V caps in series to get a 5 V
rating for $4.20 to $10 quantity 1.


That's good to know. I gave a quick try searching for super caps in
Mouser and came up empty. (Doesn't mean they don't have them -
I didn't give it much of an effort.)

Your second idea, using the CBC-11/CBC-12 1 F 5.5 V memory back-up
capacitors, may or may not work.

I agree. I don't know that it will work for sure, but I strongly suspect
it will. It is guaranteed to give *some* delay - the question is, how
much. At least it avoids the question of the sense loop voltage and
current requirements. (We know it has to be small from his brief
description, but not whether an opto's vce would prevent operation.)
What I didn't know is implied in your next sentence:

Some of these capacitors are made for
very low current (microamps, CMOS memory) and not the tens to hundreds
of milliamps you'd need for a relay or the 10-20 milliamps you'd need
for an optoisolator or solid state relay.


What happens if you place a 10 to 30 ma load on one of those caps?
The relay I specified will draw about 30 mA at ~ 4.4 volts and should
continue to stay energized down to 10 mA and possibly below that
as the voltage decays. The relay I *meant* to specify is RLY-635
(not 639). I had them both written down on my scratch sheet
when I looked up the parts. I think the 639 will work - but the
635 would give more delay. The 635 relay has a 500 ohm coil and
would draw 8.8 mA to start, and would probably still be energized
when the voltage dropped to 1.67, where it would draw about 3.3 mA.

Time will tell. As is typical with OP's we may never hear how he
makes out. But I already ordered all the parts I specified for the
second idea, and will test to see what kind of delay I can get. We
just have to wait a bit for the shipment to arrive.

Matt Roberds



  #32   Report Post  
No Spam
 
Posts: n/a
Default

Ross Herbert wrote:
On Fri, 07 Jan 2005 12:35:17 GMT, Ross Herbert
wrote:


On Thu, 06 Jan 2005 16:00:50 GMT, "NSM" wrote:


"Ross Herbert" wrote in message
...

| It seems to me that the OP would prefer to use what hardware exists
| now in order to minimise expense and the complexity involved in a
| complete re-design of what he now has. The relay he is using now is a
| 3 pole changeover unit so depending upon what is currently connected
| to the relay contacts will have some bearing on what he can do in the
| easiest and most cost effective manner.

...

I remember small, inexpensive delays that used an AC clock motor to wind
them up. When the power went off they ran down and switched contacts. I
suggested that previously.

N


Granted, such a device will work but it is hardly an elegant technical
solution. The whole idea of technology in industry is to make the
operation and maintenance of equipment reliable as possible without
having to worry about remembering to "wind up that timing relay".



PS. Not having seen one of these wind up relays I suppose it would be
possible for it to be automatically wound up again by a motor when
power was restored.


See http://www.automatictiming.com/pdf_atc/305E_data.pdf

No manual "wind up" required.
  #33   Report Post  
Zak
 
Posts: n/a
Default

Ross Herbert wrote:

PS. Not having seen one of these wind up relays I suppose it would be
possible for it to be automatically wound up again by a motor when
power was restored.


They are used as hall lighting realys in apartment staircases. Press
button, winds up, light on.

Realease button, winds down... delay... lights out.



Thomas
  #34   Report Post  
NSM
 
Posts: n/a
Default


"Ross Herbert" wrote in message
...

| Granted, such a device will work but it is hardly an elegant technical
| solution. The whole idea of technology in industry is to make the
| operation and maintenance of equipment reliable as possible without
| having to worry about remembering to "wind up that timing relay".

No, no 'remembering' required. When you apply power, the clock motor winds
the mechanism up to the preset stop. When the power goes off, the spring
unwinds until the switch actuates. Fully automatic.

Also, the http://www.automatictiming.com product is far too complex. The
ones I remember look like a small kitchen timer mounted on a bracket, and
usually have a center screw to loosen to set the delay. Wish I could find a
picture/web page.

N


  #35   Report Post  
John Fields
 
Posts: n/a
Default

On Tue, 4 Jan 2005 22:42:13 -0800, DaveC wrote:

So the answer is... no.

If power fails at the remote site, so does the control circuitry and its
power. So a traditional delay relay won't work.

The relay, powered by mains, simply opens the wireless sensor's sense circuit
when power goes away. I just want it to do so after waiting a few minutes to
see if power comes back on.

The alarm isn't for security purposes, just for letting those responsible
know that certain things have occurred, one of which is power fail. The
sensor is a wireless device run on a lithium battery, and is a packaged deal
so has no spare power available. The relay's not near the alarm CPU, so that
power isn't available, either.

Suggestions for a simple mains-powered circuit that will open a pair of
contacts about 5 minutes after de-energizing? If it's to be battery-powered,
it needs to be super-low drain. I rather keep battery replacements down to
every 2 years, at most.

An idea that just struck me: the presence of mains power could keep this
circuit de-energized. When power fails, the battery is connected to the
circuit which starts the countdown. When zero is reached (ie, 5 minutes have
passed), a pair of contacts would open. And the energizing circuit
(triggering these contacts) would only have to be a one-shot; once the alarm
is triggered, the circuit could de-energize. That way the battery is utilized
only briefly, during power-fail situations.


---
Yes, that's the way I'd do it.
---

How might I construct such a circuit?


---
Depends...

1. How long does the relay have to stay ON/OFF to trigger the alarm?

2. Do you have to stay with the relays you're now using?

3. If you can change relays what are your limitations? That is, will
the relays be used for alarm triggering only or will they also be
doing something else in the non-alarm-triggering state?





--
John Fields


  #36   Report Post  
 
Posts: n/a
Default

In alt.engineering.electrical wrote:
The 85 cent ones (CBC-125) are 1 F, 2.5 V.


No, the CBC-125 is not the one I had in mind. I should have made it
clearer. It is CBC-131, which is 85 cents in qty 10 and is .1
(point one) uf at 5 volts, not 1 uf at 2.5 volts. The CBC-125 is
$1.00 each in qty 10


Ah. I need a newer (paper) All catalog - I wasn't checking their site.

What I didn't know is implied in your next sentence:


Some of these capacitors are made for very low current (microamps,
CMOS memory) and not the tens to hundreds of milliamps you'd need
for a relay or the 10-20 milliamps you'd need for an optoisolator
or solid state relay.


What happens if you place a 10 to 30 ma load on one of those caps?


The voltage collapses. Another way to say what I said above is that
the caps have a high internal resistance / impedance / ESR.

As an example, look at pages 872 and 873 of the current Digi-Key
catalog, T051. On 872 are the Cooper PowerStor capacitors. The "A"
series has a 1 F 2.5 V cap with 0.090 ohm ESR (@ 1 KHz). DC will be
different, but: if you charged one of these caps to 2.5 V and then
shorted the leads, the initial current would be 2.5 / 0.09 or 28 A.
The "B" series (what All sells) has a 1 F 2.5 V at 0.4 ohm ESR: 6.3 A.
At the top left of page 873 are the Panasonic memory backup type
capacitors. One is 1 F 5.5 V with 30 ohm ESR, or 180 mA max short
circuit current. (As a fairer comparison with the Coopers, charging
this one to only 2.5 V would yield an 83 mA short circuit current.)
So, 10 to 30 mA might be doable with the memory backup capacitor,
but not too much more.

As is typical with OP's we may never hear how he makes out.


I don't know... now he's trying to avoid falling down a well...

Matt Roberds

  #37   Report Post  
James Sweet
 
Posts: n/a
Default


"DaveC" wrote in message
al.net...
On Fri, 7 Jan 2005 16:07:32 -0800, DaveC wrote
(in article et):

Thanks for all the great ideas. All of this makes my (volunteer) job

much
easier.


A new twist to the challenge:

The output needs to be a one-shot, momentary-close event. In other words,

5
minutes after power fails, the contacts need to close and open again. This
alerts the alarm to the power out-condition, and clears the alarm sense

line
for another event to be reported.

Ideas?



Use a 555 timer IC in a one-shot configuration. You could even use a 556
dual timer and use one for the 5 minute delay and the other for the pulse to
close the relay.


  #38   Report Post  
Rich Grise
 
Posts: n/a
Default

On Sat, 08 Jan 2005 10:01:54 -0800, DaveC wrote:

On Fri, 7 Jan 2005 16:07:32 -0800, DaveC wrote
(in article et):

Thanks for all the great ideas. All of this makes my (volunteer) job much
easier.


A new twist to the challenge:

The output needs to be a one-shot, momentary-close event. In other words, 5
minutes after power fails, the contacts need to close and open again. This
alerts the alarm to the power out-condition, and clears the alarm sense line
for another event to be reported.

Ideas?


Sure. Use the battery and charger and switch from an emergency light. Use
the 6V or whatever to power a two-555 circuit, or for a more accurate five
minutes, use a 4060. And you could use another output from the
4060 to turn itself off until power comes back on.

Good Luck!
Rich


  #39   Report Post  
John Fields
 
Posts: n/a
Default

On Fri, 7 Jan 2005 15:59:38 -0800, DaveC wrote:

On Fri, 7 Jan 2005 11:26:30 -0800, John Fields wrote
(in article ):

Depends...

1. How long does the relay have to stay ON/OFF to trigger the alarm?


Tech support guy would check with the engineers on Monday, but...
SWAG: 100 ms. A few (he wasn't willing to guess) microamps @ 3v

2. Do you have to stay with the relays you're now using?


No.

3. If you can change relays what are your limitations? That is, will
the relays be used for alarm triggering only or will they also be
doing something else in the non-alarm-triggering state?


Dedicated to alarm trigger only.


---
OK, I posted a circuit for you on abse.

If you need a circuit description let me know and I'll post one over
there.


--
John Fields
  #40   Report Post  
 
Posts: n/a
Default

wrote:

In alt.engineering.electrical
wrote:


The 85 cent ones (CBC-125) are 1 F, 2.5 V.


No, the CBC-125 is not the one I had in mind. I should have made it
clearer. It is CBC-131, which is 85 cents in qty 10 and is .1
(point one) uf at 5 volts, not 1 uf at 2.5 volts. The CBC-125 is
$1.00 each in qty 10



Ah. I need a newer (paper) All catalog - I wasn't checking their site.



What I didn't know is implied in your next sentence:





Some of these capacitors are made for very low current (microamps,
CMOS memory) and not the tens to hundreds of milliamps you'd need
for a relay or the 10-20 milliamps you'd need for an optoisolator
or solid state relay.


What happens if you place a 10 to 30 ma load on one of those caps?



The voltage collapses. Another way to say what I said above is that
the caps have a high internal resistance / impedance / ESR.

As an example, look at pages 872 and 873 of the current Digi-Key
catalog, T051. On 872 are the Cooper PowerStor capacitors. The "A"
series has a 1 F 2.5 V cap with 0.090 ohm ESR (@ 1 KHz). DC will be
different, but: if you charged one of these caps to 2.5 V and then
shorted the leads, the initial current would be 2.5 / 0.09 or 28 A.
The "B" series (what All sells) has a 1 F 2.5 V at 0.4 ohm ESR: 6.3 A.
At the top left of page 873 are the Panasonic memory backup type
capacitors. One is 1 F 5.5 V with 30 ohm ESR, or 180 mA max short
circuit current. (As a fairer comparison with the Coopers, charging
this one to only 2.5 V would yield an 83 mA short circuit current.)
So, 10 to 30 mA might be doable with the memory backup capacitor,
but not too much more.



As is typical with OP's we may never hear how he makes out.



I don't know... now he's trying to avoid falling down a well...

Matt Roberds



Matt,

Thanks! Good info. I'm wondering what he is really trying
to accomplish, too. I'll post the results I get, once
the parts arrive.

Ed
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mains powered smoke detector with alarm accept loop. Z UK diy 8 May 20th 04 02:45 AM
Using a mains powered lamp in a lighting circuit James W UK diy 8 January 9th 04 05:30 PM
Mains failure gennie switching Chris Wilson Electronics Repair 7 November 9th 03 12:31 AM
Mains failure generator switching tips? Chris Wilson UK diy 5 October 15th 03 12:12 AM


All times are GMT +1. The time now is 06:40 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"