On 8/19/2013 12:55 PM, Bill wrote:
A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The power transmission system, that feeds your transformer on the pole outside your house, is indeed 3 phase, on the _input_ side of the transformer, as I clearly stated earlier. -- eWoodShop: www.eWoodShop.com Wood Shop: www.e-WoodShop.net https://plus.google.com/114902129577517371552/posts http://www.custommade.com/by/ewoodshop/ KarlCaillouet@ (the obvious) |
#82
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 13:52:28 -0500, Swingman wrote:
On 8/19/2013 12:55 PM, Bill wrote: A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The power transmission system, that feeds your transformer on the pole outside your house, is indeed 3 phase, on the _input_ side of the transformer, as I clearly stated earlier. Not every where in the United States, the co-op to my house and over the entire system is single phase, they have only single phase generators at the power house. But I would bet that my cost per kilo watt is cheaper that most. |
#83
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
In article ,
Swingman wrote: On 8/18/2013 7:20 PM, Larry W wrote: In article , Swingman wrote: Look at it this way ... when one hot wire is negative, the other is positive, so the two hot wires complete the circuit together because they are "out of phase". IOW, 240 volt wiring is powered by 2 - 120 volt hot wires that are 180 degrees out of phase. Guaranteed. I'd rather look at it this way... When one wire is negative, the other is positive. so the 2 wires complete the circuit together becasue they are IN PHASE with each other. Guaranteed. Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. I guess we can agree to disagree here. To me, the 2 120 volt conductors are in phase, just at equal and opposite polarity at any given time. Which is not the case when compared to conductors from either of the other 2 power distribution conductors, which truly are out of phase. -- Better to be stuck up in a tree than tied to one. Larry W. - Baltimore Maryland - lwasserm(a)sdf. lonestar.org |
#84
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On 8/19/2013 10:55 AM, Markem wrote:
On Mon, 19 Aug 2013 10:05:39 -0500, Leon lcb11211@swbelldotnet wrote: On 8/19/2013 8:18 AM, Markem wrote: On Mon, 19 Aug 2013 06:54:36 -0500, Swingman wrote: Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. Your understanding of electrical things is not very good. I have many years as an electronic tech. I have tested with an oscilloscope your theory and proved it wrong. The two legs of a 240V are in phase. But in the end it really does not matter because everthing electrical will still work as long as it ain't broke. Mark FWIW I once had a newly appointed CPA that worked for me. He did not understand the importance of using the next sequentially numbered box of invoices when the previous box was empty. Kind of like the woman who asked my friend the teller, "what do mean, I still have checks" when she was told she was over drawn. I think you may have missed my point. He, the CPA, was constantly reminding me of his education and knowledge of all aspects of accounting. It did mot make him right, just a mediocre accountant. |
#85
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 17:20:13 -0500, Leon lcb11211@swbelldotnet
wrote: On 8/19/2013 10:55 AM, Markem wrote: On Mon, 19 Aug 2013 10:05:39 -0500, Leon lcb11211@swbelldotnet wrote: On 8/19/2013 8:18 AM, Markem wrote: On Mon, 19 Aug 2013 06:54:36 -0500, Swingman wrote: Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. Your understanding of electrical things is not very good. I have many years as an electronic tech. I have tested with an oscilloscope your theory and proved it wrong. The two legs of a 240V are in phase. But in the end it really does not matter because everthing electrical will still work as long as it ain't broke. Mark FWIW I once had a newly appointed CPA that worked for me. He did not understand the importance of using the next sequentially numbered box of invoices when the previous box was empty. Kind of like the woman who asked my friend the teller, "what do mean, I still have checks" when she was told she was over drawn. I think you may have missed my point. He, the CPA, was constantly reminding me of his education and knowledge of all aspects of accounting. It did mot make him right, just a mediocre accountant. Twas an insult then, oh well. |
#86
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On 8/19/2013 10:52 AM, Markem wrote:
http://en.m.wikipedia.org/wiki/Split_phase The two halves of the transformer are 180 degrees apart, not the signal. Question what do you get when you add 120 and -120? Mark You do realize that we are talking "AC" not "DC"... |
#87
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Larry W wrote:
In article , Swingman wrote: On 8/18/2013 7:20 PM, Larry W wrote: In article , Swingman wrote: Look at it this way ... when one hot wire is negative, the other is positive, so the two hot wires complete the circuit together because they are "out of phase". IOW, 240 volt wiring is powered by 2 - 120 volt hot wires that are 180 degrees out of phase. Guaranteed. I'd rather look at it this way... When one wire is negative, the other is positive. so the 2 wires complete the circuit together becasue they are IN PHASE with each other. Guaranteed. Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. I guess we can agree to disagree here. To me, the 2 120 volt conductors are in phase, just at equal and opposite polarity at any given time. I think we may be better off if you turn your keyboard upside down. It will still be in phase, it will just have opposite polarity. Did you notice that if you shift the periodic graph to the left or right, i.e. do a "phase-shift"), that the graphs will coincide. That's where the terminology comes from. Which is not the case when compared to conductors from either of the other 2 power distribution conductors, which truly are out of phase. |
#88
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On 8/19/2013 5:23 PM, Markem wrote:
On Mon, 19 Aug 2013 17:20:13 -0500, Leon lcb11211@swbelldotnet wrote: On 8/19/2013 10:55 AM, Markem wrote: On Mon, 19 Aug 2013 10:05:39 -0500, Leon lcb11211@swbelldotnet wrote: On 8/19/2013 8:18 AM, Markem wrote: On Mon, 19 Aug 2013 06:54:36 -0500, Swingman wrote: Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. Your understanding of electrical things is not very good. I have many years as an electronic tech. I have tested with an oscilloscope your theory and proved it wrong. The two legs of a 240V are in phase. But in the end it really does not matter because everthing electrical will still work as long as it ain't broke. Mark FWIW I once had a newly appointed CPA that worked for me. He did not understand the importance of using the next sequentially numbered box of invoices when the previous box was empty. Kind of like the woman who asked my friend the teller, "what do mean, I still have checks" when she was told she was over drawn. I think you may have missed my point. He, the CPA, was constantly reminding me of his education and knowledge of all aspects of accounting. It did mot make him right, just a mediocre accountant. Twas an insult then, oh well. No, not an insult just that he was not always as right as he though he was. |
#89
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 13:55:57 -0400, Bill
wrote: Swingman wrote: On 8/19/2013 10:52 AM, Markem wrote: On Mon, 19 Aug 2013 09:45:19 -0500, Swingman wrote: Markem wrote: On Mon, 19 Aug 2013 09:00:09 -0500, Swingman wrote: Markem wrote: On Mon, 19 Aug 2013 06:54:36 -0500, Swingman wrote: Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. Your understanding of electrical things is not very good. I have many years as an electronic tech. I have tested with an oscilloscope your theory and proved it wrong. The two legs of a 240V are in phase. But in the end it really does not matter because everthing electrical will still work as long as it ain't broke. Mark Then you should know the difference between electric and electronic. I do, do you? You just think you do ... read the second sentence and weep: http://en.m.wikipedia.org/wiki/Split_phase The two halves of the transformer are 180 degrees apart, not the signal. Question what do you get when you add 120 and -120? Yes, one takes the difference (not does addition). Although I'm surprised the 2 halves are 180 degree apart. A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The main AC distribution system is indeed three phase, with the phases 120 degrees apart. However, most residential areas only get one of the three high voltage phases, and that is stepped down to 120/240V in a single phase transformer. The center of the 240 volt secondary of that transformer is grounded, and becomes the Neutral. The two ends of the secondary become the two 120V "hots". Because they come from opposite ends of the 240 V winding, there is 240 V between them. The two hot wires can be described as 180 degrees out of phase (although this description upsets some people). You could also say that one hot wire is inverted relative to the other - when wire A is at +120V and rising, wire B is at -120V and falling, so you will measure 240V between the hot wires. -- Peter Bennett, VE7CEI Vancouver BC peterbb (at) telus.net Vancouver Power Squadron: http://vancouver.powersquadron.ca |
#90
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 13:52:28 -0500, Swingman wrote:
On 8/19/2013 12:55 PM, Bill wrote: A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The power transmission system, that feeds your transformer on the pole outside your house, is indeed 3 phase, on the _input_ side of the transformer, as I clearly stated earlier. Since the power wiring is overhead here, I can see the HV wiring. Three phases head north along the street. At each east/west lane, one of the three phases has a connection to a HV wire running along the lane, so the transformer feeding my house only sees a single phase of HV, and all the houses in my block are on the same phase. The adjacent blocks north and south are on the other two phases. -- Peter Bennett, VE7CEI Vancouver BC peterbb (at) telus.net Vancouver Power Squadron: http://vancouver.powersquadron.ca |
#91
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Markem wrote in
: On Mon, 19 Aug 2013 17:00:39 +0000 (UTC), Doug Miller wrote: Markem wrote in news:8mf4195abgnv84pjhaa9juqgj01kv60tuo@ 4ax.com: The two halves of the transformer are 180 degrees apart, not the signal. Question what do you get when you add 120 and -120? Wrong question. The correct question is, "what is the potential difference between -120V and +120V?" If you answered "zero" you fail. I notice you didn't attempt to answer this one. Why is that, I wonder? |
#92
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
"Peter Bennett" wrote: Peter Bennett, VE7CEI Vancouver BC peterbb (at) telus.net Vancouver Power Squadron: http://vancouver.powersquadron.ca ----------------------------------------------------------- Great organization. You're boating safety classes are a winner. Coming from this ragbagger, that's quiet a complimentG. Lew |
#93
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 23:58:31 +0000 (UTC), Doug Miller
wrote: Markem wrote in : On Mon, 19 Aug 2013 17:00:39 +0000 (UTC), Doug Miller wrote: Markem wrote in news:8mf4195abgnv84pjhaa9juqgj01kv60tuo@ 4ax.com: The two halves of the transformer are 180 degrees apart, not the signal. Question what do you get when you add 120 and -120? Wrong question. The correct question is, "what is the potential difference between -120V and +120V?" If you answered "zero" you fail. I notice you didn't attempt to answer this one. Why is that, I wonder? Because how you stated it is obvious and need not be answered. Nor do I need to engage you. |
#94
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On 8/19/2013 11:08 AM, Markem wrote:
On Mon, 19 Aug 2013 13:43:36 -0400, "Mike Marlow" wrote: Correct me if I am wrong, but you seem to be focused on a phase shift in your use of the term "phase", which is not the only proper use of the term. Both legs of a 240V are 120V each, if you look at them on an oscilloscope the peaks and valleys match each other, they are in phase with each other, ... When you use an oscilloscope to look at the two hot wires of a 240 volt circuit (in the US) you will see that the positive peak of one wire corresponds to the negative peak of the other wire and vice versa. (This assumes that both signals are measured relative to the neutral.) I.e. one signal looks like the other signal plus a 180 degree phase shift. The two signals are commonly referred to as being 180 degrees out of phase. Dan PS: If you actually try this experiment, please use some caution. Most oscilloscopes are not designed to handle this high of a voltage on their inputs. Also incorrectly connecting the signals can result in dangerous high voltages in unexpected places. I.e "Please read and understand all of the safety information related to the use of your equipment." |
#95
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Markem wrote in news:e6n419h2c3jm9dnd8ngfisbv0nplrr1ol7
@4ax.com: On Mon, 19 Aug 2013 13:43:36 -0400, "Mike Marlow" wrote: Correct me if I am wrong, but you seem to be focused on a phase shift in your use of the term "phase", which is not the only proper use of the term. Both legs of a 240V are 120V each, if you look at them on an oscilloscope the peaks and valleys match each other, they are in phase with each other, Not having looked at this on an o-scope, I'm not prepared to say anything about what you do or don't see on a scope... but I will say that you are 100% dead wrong about the peaks and valleys matching in the circuit. If they did -- if the peaks on each leg matched the peaks on the other, and likewise for the valleys -- the potential difference between the two legs would be zero. It is not. It is 240V RMS. The peaks on one leg occur at the same time as the valleys on the other, and vice versa. 3 phase power has 3 power legs each shifted 120 degrees in phase. And single-phase center-tapped 240/120 has two power legs shifted 180 degrees in phase. Now if anyone doubts what I am say it really does not matter, our electrical devices and power tools will continue to work. And the reason that they work is that the peaks on one leg of center-tapped 240/120 service match the valleys on the other leg. If you want to experiment with and oscilloscope and prove me wrong go ahead you will not be able to do that. The fact that 240volt circuits work is sufficient to prove you wrong. |
#96
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Bill wrote in :
Markem wrote: On Mon, 19 Aug 2013 13:43:36 -0400, "Mike Marlow" wrote: Correct me if I am wrong, but you seem to be focused on a phase shift in your use of the term "phase", which is not the only proper use of the term. Both legs of a 240V are 120V each, if you look at them on an oscilloscope the peaks and valleys match each other, they are in phase with each other, 3 phase power has 3 power legs each shifted 120 degrees in phase. I copied the following from Wikipedia: If two conductors are energized with ac voltages that are the same magnitude and in-phase, there will be no voltage difference between them. If the voltages are the same magnitude and one voltage is delayed one-half cycle with respect to the other, the voltage between the two will be double. Absolutely correct. I think this is consistent with what everyone except Markem is saying. Correct again. |
#97
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
|
#98
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The power transmission system, that feeds your transformer on the pole outside your house, is indeed 3 phase, on the _input_ side of the transformer, as I clearly stated earlier. Since the power wiring is overhead here, I can see the HV wiring. Three phases head north along the street. At each east/west lane, one of the three phases has a connection to a HV wire running along the lane, so the transformer feeding my house only sees a single phase of HV, and all the houses in my block are on the same phase. The adjacent blocks north and south are on the other two phases. Yep - I suspect that Swingman was referring to the transmission 3 phase ... not the distribution feeder level. which can be 3 phase or single phase. jt --- news://freenews.netfront.net/ - complaints: --- |
#99
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Did you notice that if you shift the periodic graph to the left or right, i.e. do a "phase-shift"), that the graphs will coincide. That's where the terminology comes from. .. OK is that a Phase Angle ? or a Load Angle ? ...... now let's move on and discuss reactive power ! - just kidding - this has been flogged to death - I hope. jt --- news://freenews.netfront.net/ - complaints: --- |
#100
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
wrote:
A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The power transmission system, that feeds your transformer on the pole outside your house, is indeed 3 phase, on the _input_ side of the transformer, as I clearly stated earlier. Since the power wiring is overhead here, I can see the HV wiring. Three phases head north along the street. At each east/west lane, one of the three phases has a connection to a HV wire running along the lane, so the transformer feeding my house only sees a single phase of HV, and all the houses in my block are on the same phase. The adjacent blocks north and south are on the other two phases. Yep - I suspect that Swingman was referring to the transmission 3 phase ... not the distribution feeder level. which can be 3 phase or single phase. jt You don't have to "suspect", I clearly stated same, more than once. 😊 -- www.ewoodshop.com |
#101
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
wrote: .. OK is that a Phase Angle ? or a Load Angle ? ..... now let's move on and discuss reactive power ! - just kidding - this has been flogged to death - I hope. --------------------------------------------------------------- Not until 208Y/120V/3PH/60HZ/4 wire Y is addressed and flogged to death. Lew |
#102
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Markem wrote in
: On Mon, 19 Aug 2013 23:58:31 +0000 (UTC), Doug Miller wrote: Markem wrote in m: On Mon, 19 Aug 2013 17:00:39 +0000 (UTC), Doug Miller wrote: Markem wrote in news:8mf4195abgnv84pjhaa9juqgj01kv60tuo@ 4ax.com: The two halves of the transformer are 180 degrees apart, not the signal. Question what do you get when you add 120 and -120? Wrong question. The correct question is, "what is the potential difference between -120V and +120V?" If you answered "zero" you fail. I notice you didn't attempt to answer this one. Why is that, I wonder? Because how you stated it is obvious and need not be answered. I agree that it is indeed obvious -- but your previous posts give the strong impression that it is not at all obvious to *you*. Nor do I need to engage you. Translation: I'm right, but you won't admit it... |
#103
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Tue, 20 Aug 2013 03:32:28 +0000 (UTC), Doug Miller
wrote: Translation: I'm right, but you won't admit it... Wrong conclusion |
#104
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Let me startover what I am saying is there is only one 60 hz signal
across the center tapped transformer. Both leads are the same signal the and do switch polarity 180 degrees at the same time. When you reference to the neutral and check both with an oscilloscope you see that the peaks and valleys match on the sine wave adding the together you get the full 240v. My problem has been in the description creating an image in my mind of two sine waves out of phase with each other. The potential of both of the hot leads oscillates at the same time and are always 180 degrees apart on the sine wave. So in the end it was how I interperted what was being said and creating an image of what was being said as not fully correct in my head. Does that make any sense? Mark |
#105
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On 8/20/2013 9:18 AM, Markem wrote:
The potential of both of the hot leads oscillates at the same time and are always 180 degrees apart on the sine wave. So in the end it was how I interperted what was being said and creating an image of what was being said as not fully correct in my head. Does that make any sense? Yep, no problem ... understandably, and basically what I was trying to convey in cautioning about separating "electrical" and "electronics". There is a difference, often subtle, but a difference nonetheless. No problem ... you were basically gentlemanly about the entire issue, AAMOF, remarkably so considering it was an electrical thread on the wRec .... to your credit. LOL -- eWoodShop: www.eWoodShop.com Wood Shop: www.e-WoodShop.net https://plus.google.com/114902129577517371552/posts http://www.custommade.com/by/ewoodshop/ KarlCaillouet@ (the obvious) |
#106
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Markem wrote:
Let me startover what I am saying is there is only one 60 hz signal across the center tapped transformer. Both leads are the same signal the and do switch polarity 180 degrees at the same time. When you reference to the neutral and check both with an oscilloscope you see that the peaks and valleys match on the sine wave adding the together you get the full 240v. My problem has been in the description creating an image in my mind of two sine waves out of phase with each other. The potential of both of the hot leads oscillates at the same time and are always 180 degrees apart on the sine wave. So in the end it was how I interperted what was being said and creating an image of what was being said as not fully correct in my head. Does that make any sense? Yes - it does. This is one of the more common difficulties when people talk about phase, polarity, center tap, etc. But - to me what is most impressive is your decision to step back from the rhetoric of "I'm right/you're wrong because you just don't see it", that kind of overtakes conversations like this. Not that anyone is being intentionally disruptive, but the nature of usenet conversations is that they become "if you paid attention to what I said..." kinds of things and it's really obvious that the parties talking are simply not understanding each other. I'm not accusing you of that rhetoric - it's what happens in newsgroup discussions. I'm applauding you for stepping back from what naturally occurs and enabling the understanding that two or more people are really saying the same thing even though it did not appear to be so. Symantics and all that crap. So - you are wrong. You took a high road for admitting it. I took an even higher road by complimenting you. Ain't I good? -- -Mike- |
#107
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Mike Marlow wrote:
Markem wrote: Let me startover what I am saying is there is only one 60 hz signal across the center tapped transformer. Both leads are the same signal the and do switch polarity 180 degrees at the same time. When you reference to the neutral and check both with an oscilloscope you see that the peaks and valleys match on the sine wave adding the together you get the full 240v. My problem has been in the description creating an image in my mind of two sine waves out of phase with each other. The potential of both of the hot leads oscillates at the same time and are always 180 degrees apart on the sine wave. So in the end it was how I interperted what was being said and creating an image of what was being said as not fully correct in my head. Does that make any sense? Yes - it does. This is one of the more common difficulties when people talk about phase, polarity, center tap, etc. But - to me what is most impressive is your decision to step back from the rhetoric of "I'm right/you're wrong because you just don't see it", that kind of overtakes conversations like this. Not that anyone is being intentionally disruptive, but the nature of usenet conversations is that they become "if you paid attention to what I said..." kinds of things and it's really obvious that the parties talking are simply not understanding each other. I'm not accusing you of that rhetoric - it's what happens in newsgroup discussions. I'm applauding you for stepping back from what naturally occurs and enabling the understanding that two or more people are really saying the same thing even though it did not appear to be so. Symantics and all that crap. So - you are wrong. You took a high road for admitting it. I took an even higher road by complimenting you. Ain't I good? By the way - I'm known as the Peace-Keeper around here. You can count on me to be understanding... -- -Mike- |
#108
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Tue, 20 Aug 2013 12:16:25 -0400, "Mike Marlow"
wrote: So - you are wrong. You took a high road for admitting it. I took an even higher road by complimenting you. Ain't I good? Not wrong, just not communicating. You might even be grand. Mark |
#109
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 17:31:29 -0700, Dan Coby
wrote: On 8/19/2013 11:08 AM, Markem wrote: On Mon, 19 Aug 2013 13:43:36 -0400, "Mike Marlow" wrote: Correct me if I am wrong, but you seem to be focused on a phase shift in your use of the term "phase", which is not the only proper use of the term. Both legs of a 240V are 120V each, if you look at them on an oscilloscope the peaks and valleys match each other, they are in phase with each other, ... When you use an oscilloscope to look at the two hot wires of a 240 volt circuit (in the US) you will see that the positive peak of one wire corresponds to the negative peak of the other wire and vice versa. (This assumes that both signals are measured relative to the neutral.) I.e. one signal looks like the other signal plus a 180 degree phase shift. The two signals are commonly referred to as being 180 degrees out of phase. Dan PS: If you actually try this experiment, please use some caution. Most oscilloscopes are not designed to handle this high of a voltage on their inputs. Also incorrectly connecting the signals can result in dangerous high voltages in unexpected places. I.e "Please read and understand all of the safety information related to the use of your equipment." Simple, safe way to "play in the sandbox". Get yourself a simple center tapped fillament transformer out of your "way back box" - or a transformer from a full wave rectified (non bridge) power supply. Then plug the primary into the 110 volt SINGLE PHASE power supply. You now have a low voltage version of the north american 3 wire power distribution system with a safe approxemately 12 volt (depending on the transformer) output that you can play with on the scope. If you want to go a bit farther in your "playing" get 2 bell transformers, or other low voltage single secondary transformers and connect the primaries in series, then check the "separate" secondaries - which are in effect a split center tapped winding that you can connect in phase and 180 degrees out of phase by simply changing the connection. Each secondary will give you, say, 10 volts when separated, and either 0 or 20 when connected, either in or out of phase - however you want to define that. |
#110
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 13:55:57 -0400, Bill
wrote: Swingman wrote: On 8/19/2013 10:52 AM, Markem wrote: On Mon, 19 Aug 2013 09:45:19 -0500, Swingman wrote: Markem wrote: On Mon, 19 Aug 2013 09:00:09 -0500, Swingman wrote: Markem wrote: On Mon, 19 Aug 2013 06:54:36 -0500, Swingman wrote: Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. Your understanding of electrical things is not very good. I have many years as an electronic tech. I have tested with an oscilloscope your theory and proved it wrong. The two legs of a 240V are in phase. But in the end it really does not matter because everthing electrical will still work as long as it ain't broke. Mark Then you should know the difference between electric and electronic. I do, do you? You just think you do ... read the second sentence and weep: http://en.m.wikipedia.org/wiki/Split_phase The two halves of the transformer are 180 degrees apart, not the signal. Question what do you get when you add 120 and -120? Yes, one takes the difference (not does addition). Although I'm surprised the 2 halves are 180 degree apart. A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The difference is 240v, not zero, as you seem to want to imply. Might want to start thinking along the lines of alternating current ... your electronic background maybe making the forest hard to see for the trees. (TIA for keeping this informative and not ending up as a typical wRec electrical thread). There often ARE 3 hots on the pole. The main distribution circuit IS 3 phase - but each transformer hangs on one phase, giving you single phase power to the service, unless you need and pay for a 3 phase circuit. Many MURBs have 3 phase services Some of them are 120/208, working with a single 3 phase transformer, but more and more are running 120/240 with 3 separate center tapped transformers in the vault. Even a lot of industries with 3 phase power are running 120/240 for lighting and office power, derived from a center tapped secondary transformer connected to one leg of the 3 phase servive, rather than running 120/208 or other "3 phase" power schemes. |
#111
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 14:23:22 -0500, Markem
wrote: On Mon, 19 Aug 2013 13:52:28 -0500, Swingman wrote: On 8/19/2013 12:55 PM, Bill wrote: A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The power transmission system, that feeds your transformer on the pole outside your house, is indeed 3 phase, on the _input_ side of the transformer, as I clearly stated earlier. Not every where in the United States, the co-op to my house and over the entire system is single phase, they have only single phase generators at the power house. But I would bet that my cost per kilo watt is cheaper that most. Extremely rare, in the whole north american scheme of things - and that means you are independent of the national grid. |
#112
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 16:55:42 -0700, Peter Bennett
wrote: On Mon, 19 Aug 2013 13:52:28 -0500, Swingman wrote: On 8/19/2013 12:55 PM, Bill wrote: A relative told me there were 3 hots at the pole (but he has a factory background, where 3-phase in the norm). The power transmission system, that feeds your transformer on the pole outside your house, is indeed 3 phase, on the _input_ side of the transformer, as I clearly stated earlier. Since the power wiring is overhead here, I can see the HV wiring. Three phases head north along the street. At each east/west lane, one of the three phases has a connection to a HV wire running along the lane, so the transformer feeding my house only sees a single phase of HV, and all the houses in my block are on the same phase. The adjacent blocks north and south are on the other two phases. That is correct - in most parts of North America. When the wiring is underground, it is done virtually the same way. |
#113
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
On Mon, 19 Aug 2013 17:29:26 -0500, Leon lcb11211@swbelldotnet
wrote: On 8/19/2013 5:23 PM, Markem wrote: On Mon, 19 Aug 2013 17:20:13 -0500, Leon lcb11211@swbelldotnet wrote: On 8/19/2013 10:55 AM, Markem wrote: On Mon, 19 Aug 2013 10:05:39 -0500, Leon lcb11211@swbelldotnet wrote: On 8/19/2013 8:18 AM, Markem wrote: On Mon, 19 Aug 2013 06:54:36 -0500, Swingman wrote: Nope. In the US the transformer for most residential power taps one of the 3 phases in the power distribution system, which is why it is called single phase, even though there are 2 hot legs. The transformer center tap on the pole is grounded and also connected to a wire called neutral. This provides two output voltages relative to ground or neutral. Each is 120 V, but they are 180 degrees out of phase with respect to each other. Your understanding of electrical things is not very good. I have many years as an electronic tech. I have tested with an oscilloscope your theory and proved it wrong. The two legs of a 240V are in phase. But in the end it really does not matter because everthing electrical will still work as long as it ain't broke. Mark FWIW I once had a newly appointed CPA that worked for me. He did not understand the importance of using the next sequentially numbered box of invoices when the previous box was empty. Kind of like the woman who asked my friend the teller, "what do mean, I still have checks" when she was told she was over drawn. I think you may have missed my point. He, the CPA, was constantly reminding me of his education and knowledge of all aspects of accounting. It did mot make him right, just a mediocre accountant. Twas an insult then, oh well. No, not an insult just that he was not always as right as he though he was. I know lots of those- - - - - Not just accountants either. |
#114
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
|
#115
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
In article ,
Doug Miller wrote: (Larry W) wrote in : I guess we can agree to disagree here. To me, the 2 120 volt conductors are in phase, just at equal and opposite polarity at any given time. But that is *by definition* out of phase. Well, if that is your definition then you may as well say that any pair of wires carrying current to a load in an AC circuit are 180d out of phase. Makes just as much sense, no need to complicate things by bringing up edison circuits or center-tapped transformers. -- There is always an easy solution to every human problem -- neat, plausible, and wrong." (H L Mencken) Larry W. - Baltimore Maryland - lwasserm(a)sdf. lonestar. org |
#116
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
|
#117
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
Larry W wrote:
In article , Doug Miller wrote: (Larry W) wrote in : I guess we can agree to disagree here. To me, the 2 120 volt conductors are in phase, just at equal and opposite polarity at any given time. But that is *by definition* out of phase. Well, if that is your definition then you may as well say that any pair of wires carrying current to a load in an AC circuit are 180d out of phase. Makes just as much sense, no need to complicate things by bringing up edison circuits or center-tapped transformers. This is a "group discussion'. Lots of people are reading the questions and answers. I assure you I learned some things I found interesting in the thread. Especially how "1-phase" is transformed into two legs. What is the nature of a transformer that does that? I assume it would have a long lifespan. |
#118
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
|
#119
Posted to rec.woodworking
|
|||
|
|||
Electrical question (I know this is a WW forum)
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Is this a metalworking forum or a political forum??? | Metalworking | |||
electrical question!?!?! | Home Repair | |||
Awesome new electrical forum... | Home Repair | |||
Electrical Question | Metalworking | |||
a great electrical engineering forum site | Electronics |