https://standardsdevelopment.bsigrou...208ba39773f4df
Registration needed, sadly no pdf available for download -- |
#2
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 10:11, The Other Mike wrote:
https://standardsdevelopment.bsigrou...208ba39773f4df Registration needed, sadly no pdf available for download Here is a OCR grab of the summary of changes: A summary of the main changes is given below. NOTE: This is not an exhaustive list. Part 1 Scope, object and fundamental principles Regulation 133.1.3 (Selection of equipment) has been modified and now requires a statement on the Electrical Installation Certificate. Part 2 Definitions Definitions have been expanded and modified. Chapter 41 Protection against electric shock This Section contains a number of significant changes. Some of the main ones are mentioned below. The maximum disconnection times stated in Table 41.1 now apply for final circuits up to 63 A with one or more socket-outlets and 32 A for final circuits supplying only fixed connected current-using equipment (Regulation 411.3.2.2). Metallic pipes entering the building having an insulating section at their entrance need not be connected to the protective equipotential bonding. Regulation 411.3.3 has been revised and now applies to socket-outlets with a rated current not exceeding 32 A. The exception to omit RCD protection for a specific labeled socket outlet or where, other than a dwelling, a documented risk assessment determines that RCD protection is not necessary has been deleted. The Regulation now requires RCD protection for all socket outlets. A new Regulation 411.3.4 requires within domestic (household) premises additional protection by an RCD with a rated residual operating current not exceeding 30 mA shall be provided for AC final circuits supplying luminaires. Regulation 411.4.3 has been modified to include that no switching or isolating device shall be inserted in the PEN conductor. Regulation 411.44 and 411.4.5 have been redrafted. The Regulations concerning IT systems (411.6) have been reorganized. Regulations 411.6.3.1 and 411.6.3.2 have been deleted and 411.6.4 redrafted and a new Regulation 411.6.5 inserted. A new Regulation group (419) has been inserted where automatic disconnection according to Regulation 411.3.2 is not feasible such as electronic equipment with limited short-circuit current. Chapter 42 Protection against thermal effects A newr Regulation 421.7 has been introduced for the installation of arc fault detection devices (AFDDs) to mitigate the risk of fire in final circuits of a fixed installation due to the effect of arc fault currents. Regulation 422.2.1 has been redrafted to take into account the requirements of the European Construction Regulations (CPR) which defines specific provisions necessary for all wire and cables permanently installed in Construction Work. Regulation 422.3.4 has also been modified to refer only to fire performance classes (Euroclasses). Chapter 44 Protection against voltage disturbances and electromagnetic disturbances Section 443, which deals with protection against overvoltages of atmospheric origin or due to switching has been redrafted. The AQ criteria (conditions of external influence for lightning) for determining if protection against transient overvoltage is needed is no longer be included in BS 7671. Instead, protection against transient overvoltage has to be provided where the consequence caused by overvoltage affects human life, public services and cultural heritage, and commercial or industrial activity. For all other cases, a risk assessment has to be performed in order to determine if protection against transient overvoltage is required. There is an exception not to provide protection for single dwelling units in certain situations. Chapter 46 Devices for isolation and switching A new Chapter 46 has been introduced. This deals with non-automatic local and remote isolation and switching measures which prevent or remove dangers associated with electrical installations or electrically powered equipment. Also switching for the control of circuits or equipment. Where electrically powered equipment is within the scope of BS EN 60204, only the requirements of that standard apply. Chapter 52 Selection and erection of wiring systems Regulation 521.11. 201 giving requirements for the methods of support of wiring systems in escape routes has been replaced by a new Regulation 521.10.202. This is a significant change. The new Regulation 521.10.202 requires cables to be adequately supported against their premature collapse in the event of a fire. This applies throughout the installation. Not just in escape routes. Regulation 522.8.10 concerning buried cables has been modified to include an exception for SELV cables. Regulation 527.1.3 has also been modified to refer only to fire performance classes (Euroclasses). Chapter 53 Protection, isolation, switching, control and monitoring This Chapter has been completely revised and deals with general requirements for isolation, switching, control and monitoring and with the requirements for selection and erection of the devices provided to fulfil such functions. Section 534 Devices for protection against overvoltage This Section focuses mainly on the requirements for the selection and erection of SPDs for protection against transient overvoltages where required by Section 443, the BS EN 62305 series, or as otherwise stated. Section 534 has been completely revised. The most significant technical change refers to the selection requirements for the voltage protection level. Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Two new regulations (542.2.3 and 542.2.8) have been introduced concerning foundation earth electrodes. Two new regulations (543.3.3.101 and 543.3.3.102) have been introduced. These give requirements for the insertion of a switching device ir protective conductor in situations where an installation is supplied from more than one source of energy. Chapter 55 Other equipment Regulation 550.1 introduces a new scope. Regulation 559.10 Ground-recessed luminaires. For group-recessed luminaires, the selection and erection shall take account of the guidance given in Table A.l of BS EN 60598-2-13. Part 6 Inspection and testing Part 6 has been completely restructured including the numbering to align with the CENELEC standard. Chapter 61,62, and 63 have been deleted and the content of these chapters have been moved to Chapter 64 and Chapter 65 as appropriate. Section 704 Construction and demolition site installations This Section contains a number of small changes including requirements for external influences, and modifications to Regulation 704.410.3.6 concerning the protective measures of obstacles and placing out of reach and electrical separation. Section 708 Electrical installations in caravan/camping parks and similar locations This Section contains a number of changes including requirements for socket-outlets, RCD protection, and operational conditions and external influences. Section 710 Medical locations This Section contains a number of small changes including Table 710, Regulation 710.415.2.1 and 710.415.2.3 concerning equipotential bonding. Section 715 Extra-low voltage lighting installations This Section contains only minor changes including modifications to Regulation 715.524.201. Section 721 Electrical installations in caravans and motor caravans This Section contains a number of changes including requirements electrical separation, RCDs, proximity to non-electrical services and protective bonding conductors. Section 722 Electric vehicle charging installations This Section contains a significant change to Regulation 722.411.4.1 concerning the use of a PME supply. The exception concerning reasonably practicable has been deleted. Changes have also been made to requirements for external influences, RCDs, socket-outlets and connectors. Section 730 Onshore units of electrical shore connections for inland navigation vessels This is a completely new Section. This Section applies to onshore installations dedicated to the supply of inland navigation vessels for commercial and administrative purpose, berthed in ports and berths. Most, if not all, of the measures used to reduce the risks in marinas equally apply for electrical shore connections for inland navigation vessels. One of the major differences between supplies to vessels in a typical marina and electrical shore connections for inland navigation vessels is the size of the supply needed. Section 753 Floor and ceiling heating systems This Section has been completely revised. The scope of Section 753 has been extended to apply to embedded electric heating systems for surface heating. They also apply to electric heating systems for de-icing or frost prevention or similar applications, and cover both indoor and outdoor systems. Heating systems for industrial and commercial applications complying with TEC 60519, IEC 62395 and IEC 60079 are not covered. Part 8 Energy efficiency This is a completely new Part. The worldwide need to reduce the consumption of energy means that we have to consider how electrical installations can provide the required level of service and safety for the lowest electrical consumption. Part 8 enables a client to specify the level of energy efficiency measures applied to an electrical installation. Installations can also be awarded points for energy efficiency performance levels. The new Part covers several energy efficient areas, such as lighting, metering, cable losses, transformer losses, power- factor correction, and harmonics. The follow main changes have been made within the appendices: Appendix 1 British Standards to which reference is made in the Regulations includes minor changes. Appendix 3 Time/current characteristics of overcurrent protective devices and RCDs The contents of Appendix 14 concerning earth fault loop impedance have been moved into Appendix 3. Appendix 6 Model forms for certification and reporting This Appendix includes minor changes to the certificates, changes to the inspections (for new installation work only) for domestic and similar premises with up to 100 A supply, examples of items requiring inspection for an electrical installation condition report. Appendix 7 (informative) Harmonized cable core colours This Appendix includes only minor changes. Appendix 8 Current carrying capacity- and voltage drop This Appendix includes changes regarding rating factors for current-carrying capacity. Appendix 14 Determination of prospective fault current The contents of Appendix 14 concerning earth fault loop impedance have been moved into Appendix 3. Appendix 14 now contains information on determination of prospective fault current. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#3
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/17 12:38, John Rumm wrote:
Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? |
#4
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/17 13:02, Huge wrote:
On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. |
#5
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 12:57, Tim Watts wrote:
On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. -- Robin reply-to address is (intended to be) valid |
#6
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 13:54, Robin wrote:
But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. Bugger: the second TN-S should be TN-C-S -- Stupid old bugger reply-to address is (intended to be) valid |
#7
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 13:54, Robin wrote:
On 08/06/2017 12:57, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. It says: "542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3 , as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2 . ***Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to***" (My emphasis) Which suggests it applies all earthing types - even TT! -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#8
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Thursday, 8 June 2017 13:17:47 UTC+1, Tim Watts wrote:
On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Is operating a 1st edition install legal? NT |
#9
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 14:27, John Rumm wrote:
On 08/06/2017 13:54, Robin wrote: On 08/06/2017 12:57, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. It says: "542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3 , as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2 . ***Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to***" (My emphasis) Which suggests it applies all earthing types - even TT! Ah, right, thanks. And this being the BS7671 lot I don't suppose they have published their impact assessment for this - you know the kind of thing, with figures for costs and benefits and the like. Sheesh, if it were real legislation (instead of just "tertiary legislation" 'cos in practice it has to be followed) they'd never get away with it. -- Robin reply-to address is (intended to be) valid |
#10
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 15:02, Robin wrote:
On 08/06/2017 14:27, John Rumm wrote: On 08/06/2017 13:54, Robin wrote: On 08/06/2017 12:57, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. It says: "542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3 , as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2 . ***Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to***" (My emphasis) Which suggests it applies all earthing types - even TT! Ah, right, thanks. And this being the BS7671 lot I don't suppose they have published their impact assessment for this - you know the kind of thing, with figures for costs and benefits and the like. I would guess if that comes (*if*) it would be after this consultation exercise... Sheesh, if it were real legislation (instead of just "tertiary legislation" 'cos in practice it has to be followed) they'd never get away with it. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#12
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 16:55, John Rumm wrote:
I would guess if that comes (*if*) it would be after this consultation exercise... Yerrbut...they have form on not publishing their workings (eg on metal CUs). And as you'll know, given the data and the assumptions behind a proposed change people can comment on those as well as the change itself (as with the original Part P where people pointed out the impact assessment scored deaths by electrocution from appliances). If they only publish them after consultation then it's too late to affect decisions. As it is, I have no idea if the driving force is the safety of consumers, let alone the cost per quality adjusted life year or whatever. It might for all I know be DNOs wanting to avoid paying compensation for damage to property. And they might be very happy for consumers to pay £m25 a year to save them £m5 a year. Sorry. Here endeth my rant. -- Robin reply-to address is (intended to be) valid |
#13
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]() "Tim Watts" wrote in message ... On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Not when you just replace a failed outlet etc. |
#14
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 14:27, John Rumm wrote:
On 08/06/2017 13:54, Robin wrote: On 08/06/2017 12:57, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. It says: "542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3 , as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2 . ***Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to***" (My emphasis) Which suggests it applies all earthing types - even TT! I would say it discounts the TT as TT has no distributors earthing facility. -- Adam |
#15
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 13:17, Tim Watts wrote:
On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" -- Adam |
#16
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 13:54, Robin wrote:
On 08/06/2017 12:57, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. [rhetorical question and not a dig at you] Do you think a 100 ohm earth rod will help if you lose the distributors earth on a non RCD circuit? BTW I forgot, almost everything must be now RCD protected because it's SO much safer. But don't worry RCDs NEVER fail and they are ALL tested every 3 months with the test button by the occupiers of the house and every 10 years by an electrician doing an EICR. The 19th edition (or maybe the 18th 3rd amendment) will bring back bathroom supplementary bonding. I believe it was John Rumm that once said "a bit of 4mm cable and a couple of earth clamps are almost bullet proof" Cheers -- Adam |
#17
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 19:11, ARW wrote:
On 08/06/2017 13:17, Tim Watts wrote: On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Changing the battery in the customer's vibrator ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#18
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 18:59, Robin wrote:
On 08/06/2017 16:55, John Rumm wrote: I would guess if that comes (*if*) it would be after this consultation exercise... Yerrbut...they have form on not publishing their workings (eg on metal CUs). And as you'll know, given the data and the assumptions behind a proposed change people can comment on those as well as the change itself (as with the original Part P where people pointed out the impact assessment scored deaths by electrocution from appliances). If they only publish them after consultation then it's too late to affect decisions. In the case of part P though, a very different "they". Part P was a government driven thing championed by Precott - not IET lead. As it is, I have no idea if the driving force is the safety of consumers, let alone the cost per quality adjusted life year or whatever. It might for all I know be DNOs wanting to avoid paying compensation for damage to property. And they might be very happy for consumers to pay £m25 a year to save them £m5 a year. Indeed, or just to keep revenue flowing in from sales of the big (insert colour of choice) book! Sorry. Here endeth my rant. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#19
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 19:04, ARW wrote:
On 08/06/2017 14:27, John Rumm wrote: On 08/06/2017 13:54, Robin wrote: On 08/06/2017 12:57, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. It says: "542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3 , as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2 . ***Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to***" (My emphasis) Which suggests it applies all earthing types - even TT! I would say it discounts the TT as TT has no distributors earthing facility. Yup perhaps, its not that well worded since they quote "542.1.2.1 to 3" where 3 is TT... -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#20
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 19:41, John Rumm wrote:
On 08/06/2017 19:11, ARW wrote: On 08/06/2017 13:17, Tim Watts wrote: On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Changing the battery in the customer's vibrator ;-) I don't think that that the ones in Lou's are changeable. It's a sealed unit (dishwasher proof) and the batteries are charged by induction. -- Adam |
#21
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 19:47, John Rumm wrote:
On 08/06/2017 19:04, ARW wrote: On 08/06/2017 14:27, John Rumm wrote: On 08/06/2017 13:54, Robin wrote: On 08/06/2017 12:57, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? I saw comments on that in April on the earlier draft of changes on the lines of "Bound to be a controversial subject!". But I think TN-S is OK; it's about PME (TN-S) where broken neutrals are - allegedly - increasing. It says: "542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3 , as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2 . ***Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to***" (My emphasis) Which suggests it applies all earthing types - even TT! I would say it discounts the TT as TT has no distributors earthing facility. Yup perhaps, its not that well worded since they quote "542.1.2.1 to 3" where 3 is TT... You know they will **** it up -- Adam |
#22
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 20:14, ARW wrote:
On 08/06/2017 19:41, John Rumm wrote: On 08/06/2017 19:11, ARW wrote: On 08/06/2017 13:17, Tim Watts wrote: On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Changing the battery in the customer's vibrator ;-) I don't think that that the ones in Lou's are changeable. It's a sealed unit (dishwasher proof) and the batteries are charged by induction. Someone obviously took that old joke to heart - you know the "Don't bother trying to get it out Doc, just change the batteries" ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#23
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/17 19:11, ARW wrote:
Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Well - properly worked on, for some definition of "properly". As you're here, would you do the honours ![]() |
#24
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Thursday, 8 June 2017 16:58:50 UTC+1, John Rumm wrote:
On 08/06/2017 14:39, tabbypurr wrote: On Thursday, 8 June 2017 13:17:47 UTC+1, Tim Watts wrote: On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Is operating a 1st edition install legal? Na, just criminally insane... ;-) The point was, if you carry out modifications to a system that was compliant with the 1st edition at the time of installation, then all new work will still need to comply with current legislation, and also, there are aspects of the existing installation that must be brought up to current standards, even if the new work would not directly affect them. Yup. And my point was that existing work meeting some old regs is legal, and to some other regs it's not. 1st edition wiring would definitely not be, 16th would. NT |
#25
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/2017 10:08, wrote:
On Thursday, 8 June 2017 16:58:50 UTC+1, John Rumm wrote: On 08/06/2017 14:39, tabbypurr wrote: On Thursday, 8 June 2017 13:17:47 UTC+1, Tim Watts wrote: On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Is operating a 1st edition install legal? Na, just criminally insane... ;-) The point was, if you carry out modifications to a system that was compliant with the 1st edition at the time of installation, then all new work will still need to comply with current legislation, and also, there are aspects of the existing installation that must be brought up to current standards, even if the new work would not directly affect them. Yup. And my point was that existing work meeting some old regs is legal, and to some other regs it's not. 1st edition wiring would definitely not be, 16th would. Some old regs, and some other regs? - I can't make sense of that sentence! All work done correctly to old standards is "legal". The difficulty comes when you want to modify it now. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#26
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/17 19:04, ARW wrote:
I would say it discounts the TT as TT has no distributors earthing facility. Agree. It does also help with scenarios where one might run temporary from a genny or UPS and the supplier's earth is in doubt during a power failure. But does it say "and you must have 100% RCD protection"? Without that it's pointless. I know the other parts require 100% RCD coverage (if I read it right?) for new installations, but if this part of earthing and bonding is made retrospective on any major works being done (in the same way that verifying main EB and supplementary EB where applicable is), then it would be a bit odd. |
#27
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Friday, 9 June 2017 10:51:17 UTC+1, John Rumm wrote:
On 09/06/2017 10:08, tabbypurr wrote: On Thursday, 8 June 2017 16:58:50 UTC+1, John Rumm wrote: On 08/06/2017 14:39, tabbypurr wrote: On Thursday, 8 June 2017 13:17:47 UTC+1, Tim Watts wrote: On 08/06/17 13:02, Huge wrote: On 2017-06-08, Tim Watts wrote: On 08/06/17 12:38, John Rumm wrote: Chapter 54 Earthing arrangements and protective conductors Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Building Regs are not retrospective. Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Is operating a 1st edition install legal? Na, just criminally insane... ;-) The point was, if you carry out modifications to a system that was compliant with the 1st edition at the time of installation, then all new work will still need to comply with current legislation, and also, there are aspects of the existing installation that must be brought up to current standards, even if the new work would not directly affect them. Yup. And my point was that existing work meeting some old regs is legal, and to some other regs it's not. 1st edition wiring would definitely not be, 16th would. Some old regs, and some other regs? - I can't make sense of that sentence! All work done correctly to old standards is "legal". The difficulty comes when you want to modify it now. Let's try to explain again... An existing installation conforming to 1st edition of the wiring rules is definitely not legal today. Anyone using such may land themselves in prison. An existing installation conforming to 16th edition is perfectly legal. NT |
#28
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 08/06/2017 19:44, John Rumm wrote:
Not another rant (I promise). I have TN-S with the supplied main earth soldered to the lead sheath. If the DNO converts me to PME so the supplier's main earthing terminal is no longer using that, I wonder if I can use the sheath as a supplementary earth within 542.2.2.2 "(vi) Lead sheaths and other metal coverings of cables, where not precluded by Regulation 542.2.5" given 542.2.5 doesn't seem to bar it: "542.2.5 The use, as an earth electrode, of the lead sheath or other metal covering of a cable shall be subject to all of the following conditions: (i) Adequate precautions shall be taken to prevent excessive deterioration by corrosion (ii) The sheath or covering shall be in effective contact with Earth (iii) The consent of the owner of the cable shall be obtained (iv) Arrangements shall exist for the owner of the electrical installation to be warned of any proposed change to the cable which might affect its suitability as an earth electrode." I have a feeling though I'm probably in Baldrick "cunning plan" territory. -- Robin reply-to address is (intended to be) valid |
#29
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/2017 08:05, Tim Watts wrote:
On 08/06/17 19:11, ARW wrote: Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Well - properly worked on, for some definition of "properly". As you're here, would you do the honours ![]() Anything that requires an installation certificate (say a new circuit adding) would require the main bonding to be brought up to spec. Minor works such as swapping a light fitting would not. However I would not swap0 a shower for a like for like if there was no RCD protection and the main bonding was poor (others might) -- Adam |
#30
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/2017 14:28, Robin wrote:
On 08/06/2017 19:44, John Rumm wrote: Not another rant (I promise). I have TN-S with the supplied main earth soldered to the lead sheath. If the DNO converts me to PME so the supplier's main earthing terminal is no longer using that, I wonder if I can use the sheath as a supplementary earth within 542.2.2.2 "(vi) Lead sheaths and other metal coverings of cables, where not precluded by Regulation 542.2.5" In theory it sounds like it would be ok. The only difficulty I suppose is ensuring it stays that way. All the time the DNO is supplying your earth via that route you know they will maintain it. Once they convert you to PME, you have no guarantee that they will, and they would be unlikely to feel the need to tell you if they re-cabled a great lump of the supply without the lead sheath. I suppose if you periodically tested as one ought with a TT earth, then you could argue its ok. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#31
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/17 18:42, ARW wrote:
On 09/06/2017 08:05, Tim Watts wrote: On 08/06/17 19:11, ARW wrote: Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Well - properly worked on, for some definition of "properly". As you're here, would you do the honours ![]() Anything that requires an installation certificate (say a new circuit adding) would require the main bonding to be brought up to spec. Minor works such as swapping a light fitting would not. However I would not swap0 a shower for a like for like if there was no RCD protection and the main bonding was poor (others might) Thanks for that Adam. I knew it lay somewhere with more major works but I could not put my finger on it... |
#32
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/17 18:42, ARW wrote:
On 09/06/2017 08:05, Tim Watts wrote: On 08/06/17 19:11, ARW wrote: Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Well - properly worked on, for some definition of "properly". As you're here, would you do the honours ![]() Anything that requires an installation certificate (say a new circuit adding) would require the main bonding to be brought up to spec. Minor works such as swapping a light fitting would not. However I would not swap0 a shower for a like for like if there was no RCD protection and the main bonding was poor (others might) On a related note, I have one more job to do under an open building control job, which is to add lighting to a new shower room and supplementary bonding. Could you help me please with the paperwork? I'm fine with the work and the testing, but I am not sure how to do the certification, given I've already signed an EIC and handed in, plus I hired a sparky to lay in the lighting in the rest of the place to save time and his bit is directly notified. Is this a MWC or an EIC - and if an EIC, do you just record the one circuit affected or do you record all circuits - and if the latter are you expected to retest all of them? Cheers, Tim |
#33
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/2017 19:33, Tim Watts wrote:
On 09/06/17 18:42, ARW wrote: On 09/06/2017 08:05, Tim Watts wrote: On 08/06/17 19:11, ARW wrote: Some IET Regs are - eg bonding and earthing must be brought up to spec when anything electrical is worked on. Define "anything electrical is worked on" Well - properly worked on, for some definition of "properly". As you're here, would you do the honours ![]() Anything that requires an installation certificate (say a new circuit adding) would require the main bonding to be brought up to spec. Minor works such as swapping a light fitting would not. However I would not swap0 a shower for a like for like if there was no RCD protection and the main bonding was poor (others might) On a related note, I have one more job to do under an open building control job, which is to add lighting to a new shower room and supplementary bonding. Could you help me please with the paperwork? I'm fine with the work and the testing, but I am not sure how to do the certification, given I've already signed an EIC and handed in, plus I hired a sparky to lay in the lighting in the rest of the place to save time and his bit is directly notified. Is this a MWC or an EIC - and if an EIC, do you just record the one circuit affected or do you record all circuits - and if the latter are you expected to retest all of them? There is no need to retest all of the circuits MWC or EIC, just the ones you worked on. If the work you are doing is under the 16th edition then you can still carry on under the 16th edition. However if you have handed in a certificate saying all the electrical work was complete then you may have to do the new work under the 17th edition. This one is probably down to your BCOs judgement as to if the EIC you handed in was a final document or not. If he knew there was extra electrical work to be done then you should be able to carry on with the 16th. All the best mate but this one is down to your BCO unless you think I have missed something in my reply. -- Adam |
#34
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/17 20:02, ARW wrote:
This one is probably down to your BCOs judgement as to if the EIC you handed in was a final document or not. If he knew there was extra electrical work to be done then you should be able to carry on with the 16th. All the best mate but this one is down to your BCO unless you think I have missed something in my reply. Cheers mate, I've been working to the 17th the whole way - it was just the procedure of certification that I'm not sure of: Is this an MWC or an EIC for additions in a special location to an existing circuit? Never been sure what a MWC is actually for... Unsurprisingly a 4 day Part P course does not cover such nuances! BTW - I'd designed to not have supp. bonding. But after reading your views on the matter, I'm putting SB on the shower room and probably retro fitting to the main bathroom - albeit it will be externally applied as allowed by the regs, rather than the more conventional approach. Your theory makes sense - nothing much to go wrong with simple SB, but the other approach both relies on RCDs working AND plumbers not coming along later and inserting insulating sections in the pipework ruining the continuity. Having spoken to a GasSafe fitter who will be doing my boiler, apparently the GasSafe certifications don't cover much to do with bonding, which seems a bit weak... |
#35
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 09/06/2017 23:15, Tim Watts wrote:
On 09/06/17 20:02, ARW wrote: This one is probably down to your BCOs judgement as to if the EIC you handed in was a final document or not. If he knew there was extra electrical work to be done then you should be able to carry on with the 16th. All the best mate but this one is down to your BCO unless you think I have missed something in my reply. Cheers mate, I've been working to the 17th the whole way - it was just the procedure of certification that I'm not sure of: Is this an MWC or an EIC for additions in a special location to an existing circuit? Never been sure what a MWC is actually for... Unsurprisingly a 4 day Part P course does not cover such nuances! No but the NICEIC Testing and Certification book does. And in the check list for MWC the first one on the list is "Additional (non emergency) lighting points (luminaires and switching on a single existing circuit)." And it says a MWC is acceptable. So unless it's a new circuit from the CU you can use a MWC. Actually you could probably hand in your old school reports and no one would notice or care. -- Adam |
#36
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 10/06/17 07:44, ARW wrote:
On 09/06/2017 23:15, Tim Watts wrote: On 09/06/17 20:02, ARW wrote: This one is probably down to your BCOs judgement as to if the EIC you handed in was a final document or not. If he knew there was extra electrical work to be done then you should be able to carry on with the 16th. All the best mate but this one is down to your BCO unless you think I have missed something in my reply. Cheers mate, I've been working to the 17th the whole way - it was just the procedure of certification that I'm not sure of: Is this an MWC or an EIC for additions in a special location to an existing circuit? Never been sure what a MWC is actually for... Unsurprisingly a 4 day Part P course does not cover such nuances! No but the NICEIC Testing and Certification book does. Cheers - I'm off to amazon... And in the check list for MWC the first one on the list is "Additional (non emergency) lighting points (luminaires and switching on a single existing circuit)." And it says a MWC is acceptable. So unless it's a new circuit from the CU you can use a MWC. Thanks Adam. I'll do that then... Actually you could probably hand in your old school reports and no one would notice or care. That's pretty much the case... Literally all I have to do now is plumb in a bog (after tiling) and this lighting and it should be building certificate time. |
#37
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 10/06/2017 10:37, Tim Watts wrote:
On 10/06/17 07:44, ARW wrote: On 09/06/2017 23:15, Tim Watts wrote: On 09/06/17 20:02, ARW wrote: This one is probably down to your BCOs judgement as to if the EIC you handed in was a final document or not. If he knew there was extra electrical work to be done then you should be able to carry on with the 16th. All the best mate but this one is down to your BCO unless you think I have missed something in my reply. Cheers mate, I've been working to the 17th the whole way - it was just the procedure of certification that I'm not sure of: Is this an MWC or an EIC for additions in a special location to an existing circuit? Never been sure what a MWC is actually for... Unsurprisingly a 4 day Part P course does not cover such nuances! No but the NICEIC Testing and Certification book does. Cheers - I'm off to amazon... https://www.tlc-direct.co.uk/Products/BKITCslash3.html Just to make sure you buy the right book -- Adam |
#38
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Thursday, 8 June 2017 12:57:16 UTC+1, Tim Watts wrote:
Regulation 542.1.201 has been modified and now requires an additional earth electrode, supplementing any earthing facility provided by the distributor. Does that mean all TN-S and TN-C-S will require retro-fitting of an earthing rod? Do I have to have my own earthing rod, or can eg 100+ flats in a high-rise block share an earthing rod? Does it differ if the flats' supply is provided by a DNO or a BNO (building network operator)? Owain |
#39
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Thursday, 8 June 2017 12:38:09 UTC+1, John Rumm wrote:
Part 8 Energy efficiency Installations can also be awarded points for energy efficiency performance levels. Woo! Points mean prizes! Appendix 6 Model forms for certification and reporting Manufacturers of NCR pads will be pleased. Owain |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Low voltage lighting in 18th edition? | UK diy | |||
17th Edition Wiring Regulations or BS7671 | UK diy | |||
FOR SALE: Limited Edition Lord of the Rings Anduril Sword with special edition mirror wall mount #1295 of 3000. No original packaging, but in perfect condition. | Metalworking | |||
BS7671 on CD - again | UK diy | |||
Section 607 of BS7671 | UK diy |