#1
|
|||
|
|||
RCD Keeps tripping on new installation
Hi all.
New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q £55 ones.. at customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. |
#2
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
reeveer wrote:
Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q �55 ones.. at customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. Were the IR tests in spec when you tested the circuit? Did the RCD test as being in normal parameters in particular did it hold in on the x1 test? What happens if you disconnect the fixed appliances? -- Tim Watts |
#3
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In message , Tim Watts
writes reeveer wrote: Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q 0 customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. Were the IR tests in spec when you tested the circuit? Did the RCD test as being in normal parameters in particular did it hold in on the x1 test? What happens if you disconnect the fixed appliances? Could it be that one of the appliances has the neutral linked to its earth? -- hugh |
#4
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Fri, 21 Sep 2012 22:02:09 +0100, hugh wrote:
I am a qualified, registered electrician .... But doesn't understand that a N-E short will trip and RCD. Oh and on that parasitic diybanter "forum". Could it be that one of the appliances has the neutral linked to its earth? Or chippie has stuck a nail through a cable. -- Cheers Dave. |
#5
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article ,
reeveer wrote: When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I'd guess at an earth to neutral short somewhere. I'd disconnect a socket somewhere in the middle of the ring including the wiring, and disconnect one earth at the CU in turn. That should isolate which half of the ring is the problem. Then go through the sockets in that half one by one. -- *He who laughs last, thinks slowest. Dave Plowman London SW To e-mail, change noise into sound. |
#6
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Fri, 21 Sep 2012 19:56:59 +0000, reeveer
wrote: Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q £55 ones.. at customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. -- Graham. %Profound_observation% |
#7
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
reeveer wrote:
Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q £55 ones.. at customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. earth neutral short somewhere -- Ineptocracy (in-ep-toc-ra-cy) €“ a system of government where the least capable to lead are elected by the least capable of producing, and where the members of society least likely to sustain themselves or succeed, are rewarded with goods and services paid for by the confiscated wealth of a diminishing number of producers. |
#8
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
Graham. wrote:
On Fri, 21 Sep 2012 19:56:59 +0000, reeveer wrote: Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q £55 ones.. at customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. There is nothing wrong with them at all. I often fit them - well not from B&Q but from my wholesalers (I pay £54 and I get to choose the MCBs I want.) They are sturdy, hi-integrity and the RCBOs are only £20 a go (at Screwfix). Screwfix are doing a 13 way with 10 MCBs for £59.99 if you need a larger unit. -- Adam |
#9
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
Owain wrote:
On Sep 21, 9:03 pm, reeveer wrote: I am a qualified, registered electrician So you did follow recommended testing procedure and test for insulation resistance etc before energising the installation? Because failure to do so would be a breach of the Electricity At Work Regulations. You don't need to worry about that if there is RCD protection:-) -- Adam |
#10
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Friday, September 21, 2012 9:03:02 PM UTC+1, reeveer wrote:
Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q £55 ones.. at customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. -- reeveer |
#11
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Friday, September 21, 2012 9:03:02 PM UTC+1, reeveer wrote:
Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q £55 ones.. at customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. Seems obvious its a neutral to earth connection somewhere. RM? NT |
#12
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
|
#13
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On 22/09/2012 00:49, wrote:
On Friday, September 21, 2012 9:03:02 PM UTC+1, reeveer wrote: Hi all. Seems obvious its a neutral to earth connection somewhere. RM? "Ring Main" perhaps? -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#14
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Saturday, September 22, 2012 2:41:04 AM UTC+1, John Rumm wrote:
On 22/09/2012 00:49, meow2222 wrote: On Friday, September 21, 2012 9:03:02 PM UTC+1, reeveer wrote: Hi all. Seems obvious its a neutral to earth connection somewhere. RM? "Ring Main" perhaps? Thank god I diy. NT |
#15
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
wrote:
On Saturday, September 22, 2012 2:41:04 AM UTC+1, John Rumm wrote: On 22/09/2012 00:49, meow2222 wrote: On Friday, September 21, 2012 9:03:02 PM UTC+1, reeveer wrote: Hi all. Seems obvious its a neutral to earth connection somewhere. RM? "Ring Main" perhaps? Thank god I diy. Yes, that's his problem, he's got an 11,000v ring main in his flat. -- To reply by e-mail, change the ' + ' to 'plus'. |
#16
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
Surely though that would not make either of them display the effect. I think
I'd try another rcd first in case its very over sensitive. there could easily be some form of interference suppressor in an applience with a thermostat that is causing a momentary blip. Brian -- From the Sofa of Brian Gaff Reply address is active "hugh" ] wrote in message ... In message , Tim Watts writes reeveer wrote: Hi all. New member here. I am a qualified, registered electrician and I have a mojor problem with a new installation and rewiring. I have rewired 6 new flats and fitted brand new cu's (B&Q 0 customer choice!). Anyway, all rewire and fitting of consumer units of 5 flats are fine... however, the last one... did the rewire, fitted the cu, proceeded to test and the rcd for the kitchen/bathroom is tripping, even though none of the switches are on for the mcb's in the kitchen load of the cu. The kitchen load comprises of, 3 double sockets, 1 radiator switched spur (RM with sockets), 1 cooker switch and a bathroom wall heater (RM with sockets). When I remove the earths from the kitchen/bathroom RM, the RCD will stay on, but as soon as I touch either of the RM earth to the earth busbar, it will trip the RCD. Also, I can leave the RM earths in and remove the Neutral RM cables and it will be fine...but as soon as I touch the RM neutral to the busbar, it trips. All connections are fine... to the correct busbars, etc. I am miffed on this one, and any help would be greatl;y appreciated! Thanks. Were the IR tests in spec when you tested the circuit? Did the RCD test as being in normal parameters in particular did it hold in on the x1 test? What happens if you disconnect the fixed appliances? Could it be that one of the appliances has the neutral linked to its earth? -- hugh |
#17
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
Brian Gaff wrote:
Surely though that would not make either of them display the effect. I think I'd try another rcd first in case its very over sensitive. there could easily be some form of interference suppressor in an applience with a thermostat that is causing a momentary blip. Brian IF there is some neutral-earth solid bonding upstream of the RCD then ANY earth neutral short will provide a path for neutral current that bypasses the RCD by using the earth instead: That unbalances the RCD enough to trip it on quiet small current draws. -- Ineptocracy (in-ep-toc-ra-cy) €“ a system of government where the least capable to lead are elected by the least capable of producing, and where the members of society least likely to sustain themselves or succeed, are rewarded with goods and services paid for by the confiscated wealth of a diminishing number of producers. |
#18
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
ARW wrote:
But as the OP has given no usefull info about the setup there is little point in helping him. FFS he spent more time giving info about the 5 flats that did work and and the choice of CU than explaining the problem Or a troll - he's been very quiet. Most people posting a question like that would be on the net in short order looking for replies. A real sparky, even a 4 day wonder[1], would probably have said they'd tested the wiring and RCD (but probably without the appliances) and found nothing wrong hence genuine confusion. [1] On my 4-day-wonder course, the blatantly clueless and dangerous seemed to leave after a couple of days. Everyone left could run the prescribed tests and locate faults blind based on the tests. -- Tim Watts |
#19
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Saturday, September 22, 2012 9:44:08 AM UTC+1, The Natural Philosopher wrote:
Brian Gaff wrote: Surely though that would not make either of them display the effect. I think I'd try another rcd first in case its very over sensitive. there could easily be some form of interference suppressor in an applience with a thermostat that is causing a momentary blip. Brian IF there is some neutral-earth solid bonding upstream of the RCD then ANY earth neutral short will provide a path for neutral current that bypasses the RCD by using the earth instead: That unbalances the RCD enough to trip it on quiet small current draws. I don't see how that can be right. Lots of properties have N&E connected upstream (PME), the RCD only cares about the downstream L/N current balance. NT |
#20
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article ,
Brian Gaff wrote: Surely though that would not make either of them display the effect. I think I'd try another rcd first in case its very over sensitive. there could easily be some form of interference suppressor in an applience with a thermostat that is causing a momentary blip. I'd hope the commissioning and testing of a new installation is done without any 'appliances' plugged in. But even then, decent sockets are double pole switched, so simply having them switched off would do. -- *You can't teach an old mouse new clicks * Dave Plowman London SW To e-mail, change noise into sound. |
#21
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Sat, 22 Sep 2012 09:28:49 +0100, Brian Gaff wrote:
Surely though that would not make either of them display the effect. I think I'd try another rcd first in case its very over sensitive. OP is supposed to be a "qualified, registered electrician", part of the kit he needs to be that would include an RCD tester. there could easily be some form of interference suppressor in an applience with a thermostat that is causing a momentary blip. No the description is such that the trip occurs instantly when ever N or E are connected at the same time, not at some random point with something else switching. This chap is obviously only an "operator" press the button pass/fail, no understanding of what he is doing, how things work and no abilty to fault find. A "technician" should have enough knowledge of how RCDs and wiring works to figure out what the fault must be. An "engineer" would know... -- Cheers Dave. |
#22
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
Graham. wrote:
What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. |
#23
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On 22/09/2012 13:23, Doctor Drivel wrote:
Graham. wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? |
#24
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
Fredxx wrote:
On 22/09/2012 13:23, Doctor Drivel wrote: Graham. wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? Nothing says it must be split. |
#25
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
Doctor Drivel wrote:
Fredxx wrote: On 22/09/2012 13:23, Doctor Drivel wrote: Graham. wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? Nothing says it must be split. Not even reg 314? -- Adam |
#26
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article ,
Doctor Drivel wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. Gawd save us. He's claiming to know about electrics now. -- *The early bird gets the worm, but the second mouse gets the cheese * Dave Plowman London SW To e-mail, change noise into sound. |
#27
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article ,
Fredxx wrote: An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? Dribble wouldn't know 'edition' if it bit him in the leg. It's one thing him talking ****e about electric cars on here - but another when he ventures into areas where he could do harm. -- *When did my wild oats turn to prunes and all bran? Dave Plowman London SW To e-mail, change noise into sound. |
#28
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
"ARW" wrote in message ... Doctor Drivel wrote: Fredxx wrote: On 22/09/2012 13:23, Doctor Drivel wrote: Graham. wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? Nothing says it must be split. Not even reg 314? No |
#29
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
"Dave Plowman (News)" wrote in message ... In article , Fredxx wrote: An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? D This man is senile....and an insane Jocko. |
#30
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
"Dave Plowman (News)" wrote in message ... In article , Doctor Drivel wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. Gawd This man is an idiot. |
#31
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article ,
Doctor Drivel wrote: "ARW" wrote in message ... Doctor Drivel wrote: Fredxx wrote: On 22/09/2012 13:23, Doctor Drivel wrote: Graham. wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? Nothing says it must be split. Not even reg 314? No how about reading 314 before you make such pronouncements -- From KT24 Using a RISC OS computer running v5.18 |
#32
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
"charles" wrote in message ... In article , Doctor Drivel wrote: "ARW" wrote in message ... Doctor Drivel wrote: Fredxx wrote: On 22/09/2012 13:23, Doctor Drivel wrote: Graham. wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? Nothing says it must be split. Not even reg 314? No how about reading 314 before you make such pronouncements I have!!!! Mandatory and advisory are not the same thing. ........ 314.1 Every installation shall be divided into circuits, as necessary, to: (i) avoid hazards and minimize inconvenience in the event of a fault .... (iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit..... ....... To comply with 17th edition, circuits must be RCD protected if wiring is concealed less than 50mm from the surface. Having one RCD on all the system complies. Nothing in the regs says that a CU must have two RCDs, or split load. There is no specific Reg stating that you can't fit a consumer unit with only one main RCD, 314 only "implies" that one should not have all final circuits run off one RCD. 314 talks about spliting circuits such as lighting (upstairs and downstairs). |
#33
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article , Doctor Drivel
wrote: [Snip] I have!!!! Mandatory and advisory are not the same thing. ....... 314.1 Every installation shall be divided into circuits, as necessary, to: (i) avoid hazards and minimize inconvenience in the event of a fault ... That, I believe, to be the key point. If there is only one RCD hazards will be created. 314.2 goes on to say "separate circuits shall be provided .... in such a way that those circuits are not affected by the failure of other circuits." A single RCD covering all circuits would not comply with this. but then, I'm only a Chartered Electrical Engineer. (iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit..... ...... To comply with 17th edition, circuits must be RCD protected if wiring is concealed less than 50mm from the surface. Having one RCD on all the system complies. Nothing in the regs says that a CU must have two RCDs, or split load. There is no specific Reg stating that you can't fit a consumer unit with only one main RCD, 314 only "implies" that one should not have all final circuits run off one RCD. 314 talks about spliting circuits such as lighting (upstairs and downstairs). not in my copy. -- From KT24 Using a RISC OS computer running v5.18 |
#34
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
charles wrote:
In article , Doctor Drivel wrote: [Snip] I have!!!! Mandatory and advisory are not the same thing. ....... 314.1 Every installation shall be divided into circuits, as necessary, to: (i) avoid hazards and minimize inconvenience in the event of a fault ... That, I believe, to be the key point. If there is only one RCD hazards will be created. Hazards? One RCD creates a hazard? My oh my. 314.2 goes on to say "separate circuits shall be provided .... in such a way that those circuits are not affected by the failure of other circuits." A single RCD covering all circuits would not comply with this. Tripe. A circuit may fail and the mcb trips and the RCD does not. It means splitting lights, sockets, etc, into separate circuits. I have the integrated microwave on a separate circuit (could have been on a ring), as was the cooker, fridge, washing machine, etc. All split. If one drops out on an mcb the rest are OK - well I put in RCBOs which is besides the point. but then, I'm only a Chartered Electrical Engineer. I wouldn't hire you. I bet you think BS's are the regs as well. |
#35
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article ,
Doctor Drivel wrote: charles wrote: In article , Doctor Drivel wrote: [Snip] I have!!!! Mandatory and advisory are not the same thing. ....... 314.1 Every installation shall be divided into circuits, as necessary, to: (i) avoid hazards and minimize inconvenience in the event of a fault ... That, I believe, to be the key point. If there is only one RCD hazards will be created. Hazards? One RCD creates a hazard? My oh my. yes, if something on one circuit takes out the single RCD, then all the lights go out. If it's dark that IS the hazard. 314.2 goes on to say "separate circuits shall be provided .... in such a way that those circuits are not affected by the failure of other circuits." A single RCD covering all circuits would not comply with this. Tripe. A circuit may fail and the mcb trips and the RCD does not. But if the RCD does trip? I wouldn't hire you. I bet you think BS's are the regs as well. How about BS7671:2008? -- From KT24 Using a RISC OS computer running v5.18 |
#36
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
charles wrote:
In article , Doctor Drivel wrote: [Snip] I have!!!! Mandatory and advisory are not the same thing. ....... 314.1 Every installation shall be divided into circuits, as necessary, to: (i) avoid hazards and minimize inconvenience in the event of a fault ... That, I believe, to be the key point. If there is only one RCD hazards will be created. I think two RCDs is better than one. DP RCBOs on all circuits is by far the best. But the point is the regs do not state two RCDs are needed or a CU split into two: one part with an RCD and one part unprotected. NOTHING there states that. Look at words like shall, should , would, ect. You think they all mean shall. Legrand single RCD CU for sale: http://www.screwfix.com/p/6-module-c...s-switch/60136 Note: not split. |
#37
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On 22/09/2012 16:58, Doctor Drivel wrote:
"Dave Plowman (News)" wrote in message ... In article , Fredxx wrote: An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? D This man is senile....and an insane Jocko. He may be senile, as indeed I might be as well. But we, and a few others here, don't have our head in the sand and seemingly fail so badly to appear knowledgeable. Have you ever tried sitting the C&G 2382-12 exam? I have and I passed, as indeed some others here will have done who question your "facts". |
#38
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On 22/09/2012 13:31, Fredxx wrote:
On 22/09/2012 13:23, Doctor Drivel wrote: Graham. wrote: What's wrong with those cheap BG CUs from B&Q? I'm tempted to replace the CU here with one. Get a Wylex CU, the difference is apparent. And use RCBOs on each circuit. Far more expensive but well worth it. Far better. I believe Weygand have double pole RCBOs which is better gain. But you may need a commercial CU with the RCBOs run vertical. This is the best. An RCD that controls a bank of mcb's is a waste of time. A problem on one circuit can have the whole house switched - a daft idea. Whole house? Which edition are you working to? The price is on the cover[1] in pounds shillings and pence... [1] Ladybird book of house electrics probably... -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#39
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
In article ,
Doctor Drivel wrote: Tripe. A circuit may fail and the mcb trips and the RCD does not. It means splitting lights, sockets, etc, into separate circuits. I have the integrated microwave on a separate circuit (could have been on a ring), as was the cooker, fridge, washing machine, etc. All split. If one drops out on an mcb the rest are OK - well I put in RCBOs which is besides the point. If anyone was ever in any doubt about dribble being mad, here's the proof. -- *OK, who stopped payment on my reality check? Dave Plowman London SW To e-mail, change noise into sound. |
#40
Posted to uk.d-i-y
|
|||
|
|||
RCD Keeps tripping on new installation
On Saturday, September 22, 2012 6:45:12 AM UTC+1, A.Lee wrote:
meow2222 wrote: On Saturday, September 22, 2012 2:41:04 AM UTC+1, John Rumm wrote: On 22/09/2012 00:49, meow2222 wrote: On Friday, September 21, 2012 9:03:02 PM UTC+1, reeveer wrote: Hi all. Seems obvious its a neutral to earth connection somewhere. RM? "Ring Main" perhaps? Thank god I diy. Yes, that's his problem, he's got an 11,000v ring main in his flat. Might explain why the bulbs don't last very long. NT |