I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?
  #2   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 188
Default Copper cable going into the floor, cannot be pulled out

On Tuesday, February 26, 2013 7:54:06 PM UTC-6, Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two

compressors and whatever else you find in the building, including

wiring, for $500".



The building, a former car body shop, is to be demolished next week.



Today we took out a lot of wiring, including one inch copper mains

cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.



Pulled a lot of cable from the walls also. The cables pull, once we

released their "other ends" in their respective panels.



But here's a problem: one of the cables, I am guessing 2-0 gauge, four

conductors, is going into the conduit in the floor concrete.



We cannot find the panel that they are going to and we cannot pull

them out, as they are attached on their other ends. I am beginning to

think that perhaps they are extremely long and valuable.



Is there some low-tech way to trace where that conduit is going?


Where was the outside transformer?
On a pole, or on a cement pad?
  #3   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 1,705
Default Copper cable going into the floor, cannot be pulled out

Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.

--
Steve W.
  #4   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 12,924
Default Copper cable going into the floor, cannot be pulled out


"Steve W." wrote:

Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.



Wire that heavy was likely pulled in with a tractor or forklift. If
you think the wire is that valuable and the building is coming down use
a jack hammer to bust the concrete.
  #5   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 4
Default Copper cable going into the floor, cannot be pulled out

On 2013-02-27, Steve W. wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.


My thinking goes in a little bit different direction. This building
has a huge parking lot. Maybe it goes to that parking lot.

The problem is that I cannot find any other panel that takes similar
cables going in.

i


  #6   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 4
Default Copper cable going into the floor, cannot be pulled out

On 2013-02-27, Michael A. Terrell wrote:

"Steve W." wrote:

Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.



Wire that heavy was likely pulled in with a tractor or forklift. If
you think the wire is that valuable and the building is coming down use
a jack hammer to bust the concrete.


I may do this just to see where it is going, to find the direction..

i
  #7   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 440
Default Copper cable going into the floor, cannot be pulled out


"Ignoramus5974" wrote in message
...
On 2013-02-27, Steve W. wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.


My thinking goes in a little bit different direction. This building
has a huge parking lot. Maybe it goes to that parking lot.

The problem is that I cannot find any other panel that takes similar
cables going in.

i


Could this possibly be the ground wire for the electrical panel? This could
go to a grounding plate, grounding rod, rebar in the slab, structural steel
post, copper wire in the slab, etc.

  #8   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 440
Default Copper cable going into the floor, cannot be pulled out


"anorton" wrote in message
m...

"Ignoramus5974" wrote in message
...
On 2013-02-27, Steve W. wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?

Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.


My thinking goes in a little bit different direction. This building
has a huge parking lot. Maybe it goes to that parking lot.

The problem is that I cannot find any other panel that takes similar
cables going in.

i


Could this possibly be the ground wire for the electrical panel? This
could go to a grounding plate, grounding rod, rebar in the slab,
structural steel post, copper wire in the slab, etc.


Never mind. Just noticed you said 4 conductors, so this would not be a
ground wire.

  #9   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 4
Default Copper cable going into the floor, cannot be pulled out

On 2013-02-27, anorton wrote:

"Ignoramus5974" wrote in message
...
On 2013-02-27, Steve W. wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?

Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.


My thinking goes in a little bit different direction. This building
has a huge parking lot. Maybe it goes to that parking lot.

The problem is that I cannot find any other panel that takes similar
cables going in.

i


Could this possibly be the ground wire for the electrical panel? This could
go to a grounding plate, grounding rod, rebar in the slab, structural steel
post, copper wire in the slab, etc.


No, there are four separate conductors.

i
  #10   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 5
Default Copper cable going into the floor, cannot be pulled out

Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


How about hooking up a compressor and listen for the air escaping the
other end?


  #11   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 52
Default Copper cable going into the floor, cannot be pulled out

On Tue, 26 Feb 2013 19:54:06 -0600, Ignoramus5974
wrote:

I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Could they be the feed from the power company pole to the meter? The
power company may have disconnected the power at the pole.
  #12   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 577
Default Copper cable going into the floor, cannot be pulled out


"Ignoramus5974" wrote in message
...
On 2013-02-27, anorton wrote:

"Ignoramus5974" wrote in message
...
On 2013-02-27, Steve W. wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?

Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12
volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.


My thinking goes in a little bit different direction. This building
has a huge parking lot. Maybe it goes to that parking lot.

The problem is that I cannot find any other panel that takes similar
cables going in.

i


Could this possibly be the ground wire for the electrical panel? This
could
go to a grounding plate, grounding rod, rebar in the slab, structural
steel
post, copper wire in the slab, etc.


No, there are four separate conductors.


?????? ????? ??? ????????? ??????? ????????????? ??????? ??????? ???????? ??
???????????????, ??????? ??????????? ?? ????????? ????? ?????, ???????
????????? ? a13kv + promary /

Jerk ??????, numbnutz ... ????????, killfiling ???? ????? ????? ????,
??????? ?? ??????? ?? ??? ???? ?????, ?????? ???????? ?? probaby ?????.

???? ?????.


  #13   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 1,584
Default Copper cable going into the floor, cannot be pulled out

On 2/26/2013 10:47 PM, Ignoramus5974 wrote:
On 2013-02-27, wrote:

lid wrote in message
...
On 2013-02-27, Steve wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?

Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.


My thinking goes in a little bit different direction. This building
has a huge parking lot. Maybe it goes to that parking lot.

The problem is that I cannot find any other panel that takes similar
cables going in.

i


Could this possibly be the ground wire for the electrical panel? This could
go to a grounding plate, grounding rod, rebar in the slab, structural steel
post, copper wire in the slab, etc.


No, there are four separate conductors.

i



3 phase + ground?
  #14   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 1,346
Default Copper cable going into the floor, cannot be pulled out

On Tue, 26 Feb 2013 19:54:06 -0600, Ignoramus5974
wrote:

I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?



The basic kit is all you need. Just a toner and a receiver

http://www.wisecomponents.com/storec.../cableloc.html

http://www.ebay.com/sch/i.html?_trks...nkw=wire+toner


They are all over Ebay for $30 or so . Got a electronics supply house
close by? Go snag one and hook the toner to one end of your wire..and
start hitting ever box, terminal and conductor you can find with the
wand. When you hear the noise...you can start narrowing your search.

Also check outside. There may..may be a vault outside with a
transformer in it that it goes to.

Gunner

The methodology of the left has always been:

1. Lie
2. Repeat the lie as many times as possible
3. Have as many people repeat the lie as often as possible
4. Eventually, the uninformed believe the lie
5. The lie will then be made into some form oflaw
6. Then everyone must conform to the lie
  #15   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 1,346
Default Copper cable going into the floor, cannot be pulled out

On Tue, 26 Feb 2013 21:38:33 -0600, Ignoramus5974
wrote:

On 2013-02-27, Steve W. wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.

Another method would be a signal injector and it's tracking receiver.


My thinking goes in a little bit different direction. This building
has a huge parking lot. Maybe it goes to that parking lot.

The problem is that I cannot find any other panel that takes similar
cables going in.

i


It may be part of the original wiring and at one time it was
abandoned. That happens a lot with difficult to pull wiring.


The methodology of the left has always been:

1. Lie
2. Repeat the lie as many times as possible
3. Have as many people repeat the lie as often as possible
4. Eventually, the uninformed believe the lie
5. The lie will then be made into some form oflaw
6. Then everyone must conform to the lie


  #16   Report Post  
Posted to rec.crafts.metalworking
Doc Doc is offline
external usenet poster
 
Posts: 1
Default Copper cable going into the floor, cannot be pulled out

Ignoramus5974 wrote in news:X_-
:

I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.


Snippage


We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


The air compressor is a good one or even playing sound through a speaker
can work really well. If the building is that old, be careful of jack
hammering conduits. There are several cases (inluding one on a Navy
base) of unlabled LIVE cable runs under floors to other buildings. So if
the building was built after those around it or if the transformer vault
is located (or ever has been) in the interior of the building, you could
have a live feed sitting in a condiut under the slab. I had the
experience of opening a single phase panel in a three phase system and
having two conductors almost hit me in the face. They were the original
single phase feeders and when the building had the service upgraded,
they never bothered to pull the feeders out. The only problem.. they
were still live.

So, be careful of old building wiring as you cannot depend on people to
have followed reasonable procedures in making changes.



  #18   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 265
Default Copper cable going into the floor, cannot be pulled out

Four conductor ground? Not likely.

Christopher A. Young
Learn more about Jesus
www.lds.org
..

"anorton" wrote in message
m...

"Ignoramus5974" wrote in message
...
But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.


Could this possibly be the ground wire for the electrical panel? This could
go to a grounding plate, grounding rod, rebar in the slab, structural steel
post, copper wire in the slab, etc.



  #19   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 2,473
Default Copper cable going into the floor, cannot be pulled out

On 2/26/2013 9:49 PM, Steve W. wrote:

Well you might get lucky. Take an ohm meter and check for continuity
between any of the conductors and ground or each other. If you find a
good path grab a compass and connect up a low voltage DC source (12 volt
battery works well for this) to the conductive path with a self
resetting breaker. Now with the breaker tripping follow the compass
which will be going crazy with the magnetic field around the copper.
This is the same way the "short finder" kits for auto wiring works.


The problem with that is that the cable is in conduit, which acts as a
magnetic shield

Another method would be a signal injector and it's tracking receiver.


Same problem.

Bob

  #20   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 2,473
Default Copper cable going into the floor, cannot be pulled out

On 2/27/2013 12:13 AM, StephenB wrote:

How about hooking up a compressor and listen for the air escaping the
other end?


Oh ... I like that! Good thinking-outside-the-box.

Going with that idea and if you are positively, absolutely,
unequivocally certain that there is no power anywhe use water (stick
a hose in the conduit).

Bob



  #21   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 934
Default Copper cable going into the floor, cannot be pulled out

"Ignoramus5974" wrote in message
...
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Butt another Free Bidniss Consult toward the bottom line of Ig's Bidniss:

RF ringers, a dime a dozen, in Radio Shack iffin you want ot overpay.

Ig, when are you going to at least TIP RCM??
--
EA



  #22   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 265
Default Copper cable going into the floor, cannot be pulled out

The cable has to come up some where... and that some where should have a
cable tone that is detectable.

OP can mix up some orange Tang, and pump that into the conduit. Go around
and look for the orange stain.

Christopher A. Young
Learn more about Jesus
www.lds.org
..

"Bob Engelhardt" wrote in message
...

The problem with that is that the cable is in conduit, which acts as a
magnetic shield

Another method would be a signal injector and it's tracking receiver.


Same problem.

Bob



  #23   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 669
Default Copper cable going into the floor, cannot be pulled out


If it is not the power feed, I vote for the air compressor idea.

I have used toner/tracers for years, and they are SHORT range
even when not in conduit. If you have a friend with Miss
Utility, they will have 38 Khz gear more suited, but....

The air will either announce itself or if it's no-flow, you can
guess the destination is buried and forgotten.

Chisel up enough floor to see the direction is another thought.


--
A host is a host from coast to
& no one will talk to a host that's close........[v].(301) 56-LINUX
Unless the host (that isn't close).........................pob 1433
is busy, hung or dead....................................20915-1433
  #24   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 12,924
Default Copper cable going into the floor, cannot be pulled out


David Lesher wrote:

If it is not the power feed, I vote for the air compressor idea.

I have used toner/tracers for years, and they are SHORT range
even when not in conduit. If you have a friend with Miss
Utility, they will have 38 Khz gear more suited, but....

The air will either announce itself or if it's no-flow, you can
guess the destination is buried and forgotten.

Chisel up enough floor to see the direction is another thought.



That was why I suggested a jackhammer.
  #25   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 141
Default Copper cable going into the floor, cannot be pulled out

On Feb 27, 12:13*am, StephenB wrote:
Ignoramus5974 wrote:
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".


The building, a former car body shop, is to be demolished next week.


Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.


Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.


But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.


We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.


Is there some low-tech way to trace where that conduit is going?


How about hooking up a compressor and listen for the air

escaping the
other end ?


Well, those are un-necessary costs. Just be there with the demo guy or
give him your number.
(especially if no one has a copy of the original prints - which most
counties are supposed to).


  #26   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 141
Default Copper cable going into the floor, cannot be pulled out

On Feb 27, 12:13*am, StephenB wrote:

How about hooking up a compressor and listen for the air escaping the
other end *?


I mean, in demo, I've heard of filling the conduit up with red dyle
and water, and blowing it out of what panel it leads to, but yeah. If
the compressor is yours for a day, anyway. But #2 wire probably won't
pay for the operation, like that 500 would.
(gimping 500 wire is where you really start to put your money on)
  #27   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 1,346
Default Copper cable going into the floor, cannot be pulled out

On Wed, 27 Feb 2013 18:13:14 +0000 (UTC), David Lesher
wrote:


If it is not the power feed, I vote for the air compressor idea.

I have used toner/tracers for years, and they are SHORT range


Ive used them up to 300 feet with no issues.

even when not in conduit. If you have a friend with Miss
Utility, they will have 38 Khz gear more suited, but....

The air will either announce itself or if it's no-flow, you can
guess the destination is buried and forgotten.

Chisel up enough floor to see the direction is another thought.


The methodology of the left has always been:

1. Lie
2. Repeat the lie as many times as possible
3. Have as many people repeat the lie as often as possible
4. Eventually, the uninformed believe the lie
5. The lie will then be made into some form oflaw
6. Then everyone must conform to the lie
  #28   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 567
Default Copper cable going into the floor, cannot be pulled out


"Existential Angst" wrote in message ...
"Ignoramus5974" wrote in message
...
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Butt another Free Bidniss Consult toward the bottom line of Ig's Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on usenet.
  #29   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 669
Default Copper cable going into the floor, cannot be pulled out

Gunner writes:

I have used toner/tracers for years, and they are SHORT range


Ive used them up to 300 feet with no issues.



Not range along the wire; range at right angles to it, when it is 8"
down in conduit.

--
A host is a host from coast to
& no one will talk to a host that's close........[v].(301) 56-LINUX
Unless the host (that isn't close).........................pob 1433
is busy, hung or dead....................................20915-1433
  #30   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 897
Default Copper cable going into the floor, cannot be pulled out

On Wed, 27 Feb 2013 11:57:54 -0800 (PST), Transition Zone
wrote:

On Feb 27, 12:13*am, StephenB wrote:

How about hooking up a compressor and listen for the air escaping the
other end *?


I mean, in demo, I've heard of filling the conduit up with red dyle
and water, and blowing it out of what panel it leads to, but yeah. If
the compressor is yours for a day, anyway. But #2 wire probably won't
pay for the operation, like that 500 would.
(gimping 500 wire is where you really start to put your money on)


He said it was 2/0, four lead cable. Worth in the neighborhood of 4
dollars a foot.

--
Cheers,

John B.


  #31   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 934
Default Copper cable going into the floor, cannot be pulled out

"PrecisionmachinisT" wrote in message
news:BvCdnZhJYukTHLPMnZ2dnUVZ_tGdnZ2d@scnresearch. com...

"Existential Angst" wrote in message
...
"Ignoramus5974" wrote in message
...
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Butt another Free Bidniss Consult toward the bottom line of Ig's Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on
usenet.
================================================== ==

Ahm tellinya, we should be paid.

Did you see the post where, iiuc, he bought at an auction, and was tryna
flip on RCM cuz he didn't want to pick the **** up hisself?? goodgawd.....
I mean, sheeit, iffin yer gonna plague the group with endless Q's
benefitting yer bidniss, you should throw people a bone... he was looking
to triple his money on an auction flip.
--
EA




  #32   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 9
Default Copper cable going into the floor, cannot be pulled out

On 2013-02-28, Existential Angst wrote:
"PrecisionmachinisT" wrote in message
news:BvCdnZhJYukTHLPMnZ2dnUVZ_tGdnZ2d@scnresearch. com...

"Existential Angst" wrote in message
...
"Ignoramus5974" wrote in message
...
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?


Butt another Free Bidniss Consult toward the bottom line of Ig's Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on
usenet.
================================================= ===

Ahm tellinya, we should be paid.

Did you see the post where, iiuc, he bought at an auction, and was tryna
flip on RCM cuz he didn't want to pick the **** up hisself?? goodgawd.....
I mean, sheeit, iffin yer gonna plague the group with endless Q's
benefitting yer bidniss, you should throw people a bone... he was looking
to triple his money on an auction flip.


I picked it up, made five times the money elsewhere, and sold it for
almost twice what I asked here. It was a good deal.

i
  #33   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 934
Default Copper cable going into the floor, cannot be pulled out

"Ignoramus15027" wrote in message
...
On 2013-02-28, Existential Angst wrote:
"PrecisionmachinisT" wrote in message
news:BvCdnZhJYukTHLPMnZ2dnUVZ_tGdnZ2d@scnresearch. com...

"Existential Angst" wrote in message
...
"Ignoramus5974" wrote in message
...
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".

The building, a former car body shop, is to be demolished next week.

Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.

Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.

But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.

We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.

Is there some low-tech way to trace where that conduit is going?

Butt another Free Bidniss Consult toward the bottom line of Ig's
Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on
usenet.
================================================ ====

Ahm tellinya, we should be paid.

Did you see the post where, iiuc, he bought at an auction, and was tryna
flip on RCM cuz he didn't want to pick the **** up hisself??
goodgawd.....
I mean, sheeit, iffin yer gonna plague the group with endless Q's
benefitting yer bidniss, you should throw people a bone... he was
looking
to triple his money on an auction flip.


I picked it up, made five times the money elsewhere, and sold it for
almost twice what I asked here. It was a good deal.


You are the bizzy li'l merchant. Don't forget to tip RCM.
--
EA



i



  #34   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 4,632
Default Copper cable going into the floor, cannot be pulled out

"Existential Angst" fired this volley in
:

You are the bizzy li'l merchant. Don't forget to tip RCM.


In defense of Ig, he does. When he offers a deal here, it's a deal. Seems
like he's "paying his dues" to the group.

I've bought from him, based on an offer here. Would again.

Lloyd
  #35   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 2,473
Default Copper cable going into the floor, cannot be pulled out

On 2/27/2013 7:24 PM, Existential Angst wrote:
wrote in message
news:BvCdnZhJYukTHLPMnZ2dnUVZ_tGdnZ2d@scnresearch. com...

"Existential wrote in message
...


Butt another Free Bidniss Consult toward the bottom line of Ig's Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on
usenet.
================================================== ==

Ahm tellinya, we should be paid.

Did you see the post where, iiuc, he bought at an auction, and was tryna
flip on RCM cuz he didn't want to pick the **** up hisself?? goodgawd.....
I mean, sheeit, iffin yer gonna plague the group with endless Q's
benefitting yer bidniss, you should throw people a bone... he was looking
to triple his money on an auction flip.


I find Iggy's posts of his adventures in the surplus/auction business
interesting. Certainly much more so than the endless guns and politics
crap. But the guns and politics crap gets ignored (I don't feel that I
would contribute anything by complaining about it). And his posts are
easily read - I don't find his spelling and grammar to be a challenge
(is "bidness" an attempt at humor, mock-redneck style, or just plain
redneck laziness?).

As far as "... endless Q's benefitting [sic] yer [sic] bidniss [sic]
....", no one has to answer, just as no one has to answer endless OT
questions about water heaters.

Bob


  #36   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 3,797
Default Copper cable going into the floor, cannot be pulled out

On Feb 27, 4:24*pm, "Existential Angst" wrote:
"PrecisionmachinisT" wrote in message

news:BvCdnZhJYukTHLPMnZ2dnUVZ_tGdnZ2d@scnresearch. com...

"Existential Angst" wrote in message

...









"Ignoramus5974" wrote in message
...
I entered into a business transaction of the sort "you buy two
compressors and whatever else you find in the building, including
wiring, for $500".


The building, a former car body shop, is to be demolished next week.


Today we took out a lot of wiring, including one inch copper mains
cables, and a 15 HP I-R T30 compressor and a 5 HP quincy compressor.


Pulled a lot of cable from the walls also. The cables pull, once we
released their "other ends" in their respective panels.


But here's a problem: one of the cables, I am guessing 2-0 gauge, four
conductors, is going into the conduit in the floor concrete.


We cannot find the panel that they are going to and we cannot pull
them out, as they are attached on their other ends. I am beginning to
think that perhaps they are extremely long and valuable.


Is there some low-tech way to trace where that conduit is going?


Butt another Free Bidniss Consult toward the bottom line of Ig's Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on
usenet.
================================================== ==

Ahm tellinya, we should be paid.

Did you see the post where, iiuc, he bought at an auction, and was tryna
flip on RCM cuz he didn't want to pick the **** up hisself?? *goodgawd......
I mean, sheeit, iffin yer gonna plague the group with endless Q's
benefitting yer bidniss, you should throw people a bone... *he was looking
to triple his money on an auction flip.
--
EA


Years ago Iggy complained to me in email about the prices I sell high
end tools for. Those would be tools he will never own and he can't
appreciate. Iggy is a worthless **** on a massive ego trip who will
never learn to be a machinist or a decent welder because he won't pay
his dues.



  #37   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 9
Default Copper cable going into the floor, cannot be pulled out

On 2013-02-28, Lloyd E. Sponenburgh lloydspinsidemindspring.com wrote:
"Existential Angst" fired this volley in
:

You are the bizzy li'l merchant. Don't forget to tip RCM.


In defense of Ig, he does. When he offers a deal here, it's a deal. Seems
like he's "paying his dues" to the group.


Yes, no pussy footing around.

I've bought from him, based on an offer here. Would again.


The welder works well?

i
  #38   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 4,632
Default Copper cable going into the floor, cannot be pulled out

Ignoramus15027 fired this volley in
:

The welder works well?


In all modes. It's better at welding than I am, but now that I have a
good welder, I'm becoming a better weldor... day by day.

Despite what some faggots spout about tools and skills they've never had
and never will have, real hardware getting used by real people is good.

Good, sound hardware, no matter (usually) how old, should never be
relegated to scrap; it should be re-sold to someone who needs it.

Queer bankers should be scrapped; but they'll die of AIDS soon enough, so
why waste even one breath doing what they're doing to themselves?

LLoyd
  #39   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 934
Default Copper cable going into the floor, cannot be pulled out

"Bob Engelhardt" wrote in message
...
On 2/27/2013 7:24 PM, Existential Angst wrote:
wrote in message
news:BvCdnZhJYukTHLPMnZ2dnUVZ_tGdnZ2d@scnresearch. com...

"Existential wrote in message
...


Butt another Free Bidniss Consult toward the bottom line of Ig's
Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on
usenet.
================================================== ==

Ahm tellinya, we should be paid.

Did you see the post where, iiuc, he bought at an auction, and was tryna
flip on RCM cuz he didn't want to pick the **** up hisself??
goodgawd.....
I mean, sheeit, iffin yer gonna plague the group with endless Q's
benefitting yer bidniss, you should throw people a bone... he was
looking
to triple his money on an auction flip.


I find Iggy's posts of his adventures in the surplus/auction business
interesting. Certainly much more so than the endless guns and politics
crap. But the guns and politics crap gets ignored (I don't feel that I
would contribute anything by complaining about it). And his posts are
easily read - I don't find his spelling and grammar to be a challenge (is
"bidness" an attempt at humor, mock-redneck style, or just plain redneck
laziness?).


I see that it taxes your reading comprehension.....


As far as "... endless Q's benefitting [sic] yer [sic] bidniss [sic] ...",
no one has to answer, just as no one has to answer endless OT questions
about water heaters.


I take it you lernt nothing about water heaters in that thread, including
the notion of anodic protection of metals, electronic anodic protection,
pressure relief, etc? .

Y'all need to start wearing panties that don't bunch up so tight -- methinks
it's cutting off circulation....
--
EA



Bob



  #40   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 9
Default Copper cable going into the floor, cannot be pulled out

On 2013-02-28, Bob Engelhardt wrote:
On 2/27/2013 7:24 PM, Existential Angst wrote:
wrote in message
news:BvCdnZhJYukTHLPMnZ2dnUVZ_tGdnZ2d@scnresearch. com...

"Existential wrote in message
...


Butt another Free Bidniss Consult toward the bottom line of Ig's Bidniss:


He can't tie his shoe laces without asking a bunch of silly questions on
usenet.
================================================== ==

Ahm tellinya, we should be paid.

Did you see the post where, iiuc, he bought at an auction, and was tryna
flip on RCM cuz he didn't want to pick the **** up hisself?? goodgawd.....
I mean, sheeit, iffin yer gonna plague the group with endless Q's
benefitting yer bidniss, you should throw people a bone... he was looking
to triple his money on an auction flip.


I find Iggy's posts of his adventures in the surplus/auction business
interesting. Certainly much more so than the endless guns and politics
crap. But the guns and politics crap gets ignored (I don't feel that I
would contribute anything by complaining about it). And his posts are
easily read - I don't find his spelling and grammar to be a challenge
(is "bidness" an attempt at humor, mock-redneck style, or just plain
redneck laziness?).

As far as "... endless Q's benefitting [sic] yer [sic] bidniss [sic]
...", no one has to answer, just as no one has to answer endless OT
questions about water heaters.


Thanks. And, sadly and most importantly, this is still the kind of
line of work where one has to actually work for money, money does not
magically flow into the hands.

i
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mineral Insulated Copper-Sheathed Cable Graham UK diy 5 October 13th 06 11:52 PM
Resistance per Meter for copper cable (R1+R2) [email protected] UK diy 10 November 1st 05 01:39 AM
FS: 4/0 Copper Cable / Wire Jess Metalworking 0 July 26th 05 01:33 AM
Aluminum clad MC cable in a chase with copper pipe Paul Home Repair 1 March 10th 05 06:24 PM
Shower cable in a copper pipe ?? Wanderer UK diy 19 September 8th 03 11:28 AM


All times are GMT +1. The time now is 02:54 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"