When my furnace wouldn't work, I called the local gas company (Excel
Energy -- Minneapolis) figuring they would come out and look at it for
free, like PG&E did in CA. But no, they wanted $80 for the first 15
minutes just to look at it, and I think it was $80 each half/hour after
that, and so did all the private repair places I called. I fixed it
myself and thought I would pass it on.

The symptom was, when the thermostat went on, I could hear a fan run for
a while, but no heat. Then this would repeat.

My son Joe suggested I take the furnace panels off and look for a
switch, and sure enough, there was a switch operated by vacuum from the
stack, and the short vacuum hose was cracked and letting air in. But
shorting out the switch didn't make the heat go on either, unless I let
the fan run for a while first.

I should mention that the front of the furnace contains a circuit board
with ICs and a bunch of electronics on it, including diagnostic lights.
To make it short, what happens is this, (at least on my Lennox.)

1) When the thermostat goes on, the furnace computer requires that the
vacuum switch be open (no vacuum). If so, then the stack fan is turns on.
2) After the stack fan is on for a few seconds, the computer requires
the vacuum switch be closed. This is to test the switch every time it
goes on. (A faulty switch could be stuck in the closed position, then
if the stack fan also failed, the system would work without it, causing
possible CO problems.)

So only if there is both no vacuum and then vacuum in sequence, the
computer allows the gas to go on. All I had to do was replace the 1/4"
vacuum hose and it worked fine. I spent $2 instead of $80+.

  #2   Report Post  
Dr. Hardcrab
 
Posts: n/a
Default


"slowhands" wrote in message
...
When my furnace wouldn't work, I called the local gas company (Excel
Energy -- Minneapolis) figuring they would come out and look at it for
free, like PG&E did in CA. But no, they wanted $80 for the first 15
minutes just to look at it, and I think it was $80 each half/hour after
that, and so did all the private repair places I called. I fixed it
myself and thought I would pass it on.

The symptom was, when the thermostat went on, I could hear a fan run for a
while, but no heat. Then this would repeat.

My son Joe suggested I take the furnace panels off and look for a switch,
and sure enough, there was a switch operated by vacuum from the stack, and
the short vacuum hose was cracked and letting air in. But shorting out
the switch didn't make the heat go on either, unless I let the fan run for
a while first.

I should mention that the front of the furnace contains a circuit board
with ICs and a bunch of electronics on it, including diagnostic lights.
To make it short, what happens is this, (at least on my Lennox.)

1) When the thermostat goes on, the furnace computer requires that the
vacuum switch be open (no vacuum). If so, then the stack fan is turns on.
2) After the stack fan is on for a few seconds, the computer requires the
vacuum switch be closed. This is to test the switch every time it goes
on. (A faulty switch could be stuck in the closed position, then if the
stack fan also failed, the system would work without it, causing possible
CO problems.)

So only if there is both no vacuum and then vacuum in sequence, the
computer allows the gas to go on. All I had to do was replace the 1/4"
vacuum hose and it worked fine. I spent $2 instead of $80+.


I am happy for you that you fixed your furnace, but I think you got lucky.
There are SO MANY other things that can go wrong. What if your hot surface
igniter was bad? What if the gas valve was faulty? What if the cicuit board
was fried? Sure you can replace it, but WHY did it fry? What if the switch
(that you hooked the rubber hose to) was bad? PLUS, even if you figure out
what IS wrong, where are you going to get the proper part to fix it (if it
NEEDS a part)?? Gas and electricity is nothing to "experiment" with!!!

I agree that a customer should check the simple things in order to save
themselves a service call. But if they don't know what they are doing, they
can burn their house down and/or casue harm or death to their family.

It's not rocket science, but you are better off leaving some things to the
pros.....


  #3   Report Post  
 
Posts: n/a
Default

Good for you and your do it yourself fix.

As always on this newsgroup and others like hvac
some will try to persuade you to not do it yourself. They'll
say that you should "Leave it to the pro's" I say you,
me, and others are just as capable as the pro's and
as long as a newsgroup is available we should use
it to further our knowledge on do it yourself fixes.

Thanks for the info.



  #4   Report Post  
Bubba
 
Posts: n/a
Default

On Wed, 02 Feb 2005 22:59:47 -0600, slowhands
wrote:

When my furnace wouldn't work, I called the local gas company (Excel
Energy -- Minneapolis) figuring they would come out and look at it for
free, like PG&E did in CA. But no, they wanted $80 for the first 15
minutes just to look at it, and I think it was $80 each half/hour after
that, and so did all the private repair places I called. I fixed it
myself and thought I would pass it on.

The symptom was, when the thermostat went on, I could hear a fan run for
a while, but no heat. Then this would repeat.

My son Joe suggested I take the furnace panels off and look for a
switch, and sure enough, there was a switch operated by vacuum from the
stack, and the short vacuum hose was cracked and letting air in. But
shorting out the switch didn't make the heat go on either, unless I let
the fan run for a while first.

I should mention that the front of the furnace contains a circuit board
with ICs and a bunch of electronics on it, including diagnostic lights.
To make it short, what happens is this, (at least on my Lennox.)

1) When the thermostat goes on, the furnace computer requires that the
vacuum switch be open (no vacuum). If so, then the stack fan is turns on.
2) After the stack fan is on for a few seconds, the computer requires
the vacuum switch be closed. This is to test the switch every time it
goes on. (A faulty switch could be stuck in the closed position, then
if the stack fan also failed, the system would work without it, causing
possible CO problems.)

So only if there is both no vacuum and then vacuum in sequence, the
computer allows the gas to go on. All I had to do was replace the 1/4"
vacuum hose and it worked fine. I spent $2 instead of $80+.


And your point is?
Bubba
  #5   Report Post  
 
Posts: n/a
Default


So only if there is both no vacuum and then vacuum in sequence, the
computer allows the gas to go on. All I had to do was replace the 1/4"
vacuum hose and it worked fine. I spent $2 instead of $80+.


And your point is?
Bubba


Some people can get the point.............

Others can't...........If you can't, then you're a candidate for
calling a pro.


  #7   Report Post  
 
Posts: n/a
Default


Thanks for the info.


You are just as capable as the pro's?


If I can fix the problem then yes. I have outsmarted the "pro's "
quite a few times in the past. Being a "pro" is not any more of
a guarantee of success than being a willing, smart, experienced
amateur. The only problem is finding out how to access the same
information that a money hungry "pro" is unwilling to divulge.

Get freakin real you idiot. You
could only hope to be 1/1000th of what a pro is even in your worst
nightmare of a wet dream.
Bubba


Then you don't know me.
  #8   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


wrote in message
...

Thanks for the info.


You are just as capable as the pro's?


If I can fix the problem then yes. I have outsmarted the "pro's "
quite a few times in the past. Being a "pro" is not any more of
a guarantee of success than being a willing, smart, experienced
amateur. The only problem is finding out how to access the same
information that a money hungry "pro" is unwilling to divulge.


You got lucky. Period.
IF you knew ahead of time, the proper check procedure, and find the problem,
good for you.
IF you go poking around, and find it this time, great. IF you think that a
vac hose will be the issue every time, as per your posting suggests, then
you are wrong.
Just curious...did you run your camera up into the heat exchangers to see if
they had holes, cracks or other damage?
A pro would....and some even give you the vid tape to prove it if they find
something.



Get freakin real you idiot. You
could only hope to be 1/1000th of what a pro is even in your worst
nightmare of a wet dream.
Bubba


Then you don't know me.


And you dont know us.
Its guys like you that have made the lawyers in our state pass legislation
that makes it illegal for unlicenced persons to work or install units.

If you think that makes it easy on the competent licenced persons like
myself, you are wrong.

And if you think that the units of tomorrow will be as user friendly, you
are also kidding yourself. We have Tranes now that if you dont have the
infrared reader, you WONT fix a thing....period. We have RTUs that if you
dont have the software to read them, you wont even get them to fire up.

  #9   Report Post  
 
Posts: n/a
Default


Just curious...did you run your camera up into the heat exchangers to see if
they had holes, cracks or other damage?


More information divulged. Thank you. Before long I'll gather all the
techniques for working on a furnace.

P.S. You can keep the technique used to pillage the consumer. I don't
use that technique.
  #11   Report Post  
B-Hate-Me
 
Posts: n/a
Default


"slowhands" wrote in message
...
When my furnace wouldn't work, I called the local gas company (Excel
Energy -- Minneapolis) figuring they would come out and look at it for
free, like PG&E did in CA. But no, they wanted $80 for the first 15
minutes just to look at it, and I think it was $80 each half/hour after
that, and so did all the private repair places I called. I fixed it
myself and thought I would pass it on.


What do you do for a living?

How much do you make?


  #12   Report Post  
Matt
 
Posts: n/a
Default

When my furnace wouldn't work, I called the local gas company (Excel
Energy -- Minneapolis) figuring they would come out and look at it for
free, like PG&E did in CA. But no, they wanted $80 for the first 15
minutes just to look at it, and I think it was $80 each half/hour after

that, and so did all the private repair places I called. I fixed it
myself and thought I would pass it on.


You learned your first lesson!

1. California is a socialist pink commie fag community. Minnesota is in
the running, but they havn't yet advanced to the point where gov't
subsidises home heating costs.

YET.

  #14   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


wrote in message
...

Just curious...did you run your camera up into the heat exchangers to see

if
they had holes, cracks or other damage?


More information divulged. Thank you. Before long I'll gather all the
techniques for working on a furnace.


Nope...you wont. Not even close..
There is more to it than just running the cam up..LOL...



PS...there is NO technique we use to "pillage" you assuming ****.
I have news for you, that cam cost over $2500 and I have YET to charge a
customer to use it.

Sucks when you assume that just because I own an HVAC company, that I run it
like half the other guys do...

Just curious...when was the last time, you went to work, took over $2400.00
worth of parts they needed, and GAVE it to the boss?
Well...we do it often....matter of fact, I just installed a unit for a lady
last week, and got news this morning, she had died due to her
cancer...now....care to guess what her final bill had on it? CAre to guess
how much she paid for all that work to be done?
I want to see you put your foot in your mouth again....cause ya aint got a
clue.


Its either broke, or it aint.


P.S. You can keep the technique used to pillage the consumer. I don't
use that technique.


  #15   Report Post  
 
Posts: n/a
Default


Sucks when you assume that just because I own an HVAC company, that I run it
like half the other guys do...


Thank you for making my point. I'd rather attempt to fix it myself
than take a 50/50 chance of being robbed.



  #16   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


wrote in message
...

Sucks when you assume that just because I own an HVAC company, that I run

it
like half the other guys do...


Thank you for making my point. I'd rather attempt to fix it myself
than take a 50/50 chance of being robbed.


LOL...ok...

You have a unit not working.
You call a company and they come and fix it correctly.
You have heat, and a bill. How are you robbed?

You get "robbed" every time you pay your electric bill, your water bill, or
your mortgage. Do you own a new car? Have you ever bought one?
If you have, did you talk the dealer down to a price YOU liked? You walked
away thinking you took the dealer for a ride and the dealer was laughing at
you after you left saying, "What a putz", or..."and he THOUGHT he took us
for a ride".

I think the point you are missing, is that there are laws in place to
prevent the uneducated from working on their own units in many areas and for
good reason.You sit here and state that you feel as if you are getting
robbed when you call a professional out, yet that professional has many
years of training, sees more in one day than you will see in a lifetime, has
spent the money on the tools that are required to properly repair and
diagnose problems, knows the proper procedure to remove and replace things,
knows how to properly set up and adjust items that you dont have information
on unless you are in the trade, and knows how to set things up so that you
and your family can go to bed at night and still wake up in the morning.

God help if you have to ever change out a gas valve. The tools alone to
PROPERLY set the unit up after you have installed your new $100 valve cost
over $1000, and you must use them to do the job right. Lets see....a pro
would charge prob no more than say...$200 for the work on a simple
replacement, and thats taking into consideration of the valve, the time to
get the valve if its not a stock item, the insurance that covers you in case
he screws up, his licence, his fuel, his overhead, his tools that you dont
have to buy his labor, his supplies used in the process of changing it out,
his advertising etc.
yea...you got robbed....raped even with no KY...

I live in DIY country. We even have been known to go by and offer advice on
small things to people that call...but one thing I have noticed is that
arrogant DIY folks normally THINK they have it right, and fail to realize
that while its WORKING, it might not be working properly.
Educated DIY folks realize there are limits to what one can do with a basic
tool set they got at Wal Mart for $50 and dont mind for someone to do the
job right.

You might be able to do anything you set your mind to....and more power to
you.
But your posts insinuate that you really dont have a clue and anyone that
takes you seriously could endanger themselves or someone else at some point
thinking that you are right and all professionals are crooks......

Hope you never have to go to a doctor in that case...I guess you will be
taking on open heart surgery at home next.

  #17   Report Post  
 
Posts: n/a
Default

On Sat, 5 Feb 2005 09:39:46 -0500, "Steve@carolinabreezehvac"
wrote:


wrote in message
.. .

Sucks when you assume that just because I own an HVAC company, that I run

it
like half the other guys do...


Thank you for making my point. I'd rather attempt to fix it myself
than take a 50/50 chance of being robbed.


LOL...ok...

You have a unit not working.
You call a company and they come and fix it correctly.
You have heat, and a bill. How are you robbed?


I could get robbed by at least three ways.

1. I would rob myself of learning how the darn thing works if I didn't
at least attempt to investigate the problem.

2. I would rob from my bank account if I paid someone else to
unnecessarily fix a problem that I am capable of fixing myself.

3. I would get robbed if I happened to chose the 50% of pro's that
have no problem in inflating the cost of the job.


I think the point you are missing, is that there are laws in place to
prevent the uneducated from working on their own units in many areas and for
good reason.


This may be true but there are no laws that can guarantee that you
won't get robbed by a pro, and there are no laws that say a pro must
be smarter than you.



























  #18   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


wrote in message
...
On Sat, 5 Feb 2005 09:39:46 -0500, "Steve@carolinabreezehvac"
wrote:


wrote in message
.. .

Sucks when you assume that just because I own an HVAC company, that I

run
it
like half the other guys do...

Thank you for making my point. I'd rather attempt to fix it myself
than take a 50/50 chance of being robbed.


LOL...ok...

You have a unit not working.
You call a company and they come and fix it correctly.
You have heat, and a bill. How are you robbed?


I could get robbed by at least three ways.

1. I would rob myself of learning how the darn thing works if I didn't
at least attempt to investigate the problem.


That would be called 4 years of a tech school....that is required to work on
any gas burning furnace, or electric furnace, or oil burning furnace in most
jurisdictions.
I will not hire a tech unless hes got at LEAST 2 under his belt, and can be
verified.


2. I would rob from my bank account if I paid someone else to
unnecessarily fix a problem that I am capable of fixing myself.


Thats called paying a bill, in a free enerprise system, not getting robbed.


3. I would get robbed if I happened to chose the 50% of pro's that
have no problem in inflating the cost of the job.


The other 50% that I was talking about, simply have higher overhead. The
customer pays for everything, everywhere...you do know that right?



I think the point you are missing, is that there are laws in place to
prevent the uneducated from working on their own units in many areas and

for
good reason.


This may be true but there are no laws that can guarantee that you
won't get robbed by a pro, and there are no laws that say a pro must
be smarter than you.


Ok....first of all, if a consumer calls say, 4 different companies, and lets
just say for arguements sake, there are only 4 in their state....
they get prices of $4500, $5500, $6500, and $7500 for the same size
unit....installed.
The 4500 quote is for a system, alone, 10SEER
The 5500 is for the same
the 6500 one is for a 12 SEER unit, with a digital stat,
and the 7500 one is for a 12SEER unit with a digital programmable stat,
longer warranty, labor warranty, and humidifier with humidistat.
Who is trying to rob the customer?






























  #19   Report Post  
Bubba
 
Posts: n/a
Default

On Sat, 5 Feb 2005 16:40:22 -0500, "Steve@carolinabreezehvac"
wrote:


wrote in message
.. .
On Sat, 5 Feb 2005 09:39:46 -0500, "Steve@carolinabreezehvac"
wrote:


wrote in message
.. .

Sucks when you assume that just because I own an HVAC company, that I

run
it
like half the other guys do...

Thank you for making my point. I'd rather attempt to fix it myself
than take a 50/50 chance of being robbed.


LOL...ok...

You have a unit not working.
You call a company and they come and fix it correctly.
You have heat, and a bill. How are you robbed?


I could get robbed by at least three ways.

1. I would rob myself of learning how the darn thing works if I didn't
at least attempt to investigate the problem.


That would be called 4 years of a tech school....that is required to work on
any gas burning furnace, or electric furnace, or oil burning furnace in most
jurisdictions.
I will not hire a tech unless hes got at LEAST 2 under his belt, and can be
verified.


2. I would rob from my bank account if I paid someone else to
unnecessarily fix a problem that I am capable of fixing myself.


Thats called paying a bill, in a free enerprise system, not getting robbed.


3. I would get robbed if I happened to chose the 50% of pro's that
have no problem in inflating the cost of the job.


The other 50% that I was talking about, simply have higher overhead. The
customer pays for everything, everywhere...you do know that right?



I think the point you are missing, is that there are laws in place to
prevent the uneducated from working on their own units in many areas and

for
good reason.


This may be true but there are no laws that can guarantee that you
won't get robbed by a pro, and there are no laws that say a pro must
be smarter than you.


Ok....first of all, if a consumer calls say, 4 different companies, and lets
just say for arguements sake, there are only 4 in their state....
they get prices of $4500, $5500, $6500, and $7500 for the same size
unit....installed.
The 4500 quote is for a system, alone, 10SEER
The 5500 is for the same
the 6500 one is for a 12 SEER unit, with a digital stat,
and the 7500 one is for a 12SEER unit with a digital programmable stat,
longer warranty, labor warranty, and humidifier with humidistat.
Who is trying to rob the customer?


Steve,
Im suprised at you. You are arguing with one of the dumbest idiots yet
to date. He thinks he is a "fixit man". You know and I know that he
has probably wasted more time and more money on all his "jury rigged"
**** in his home. Now he is wasting bandwidth.
Im goina need a new keyboard soon if you keep this up. :-)
Bubba
  #20   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


"Bubba" wrote in message
...


Steve,
Im suprised at you. You are arguing with one of the dumbest idiots yet
to date. He thinks he is a "fixit man". You know and I know that he
has probably wasted more time and more money on all his "jury rigged"
**** in his home. Now he is wasting bandwidth.
Im goina need a new keyboard soon if you keep this up. :-)
Bubba


Bubba:

Sorry man. Been a while since I posted in here on a regular basis and
thought that with the bull**** in the other group it would be a nice change
of pace...it has been.
I even found someone dumber than Stormin Moron, or DaveHackinNunits.

I also know, that educated consumers dont do stupid **** like he is talking
about. Now...if he wants to be a HVAC guy, properly, I have some used
equipment, less than a year old, on a used Ford, also less than a year old
(1 ton if anyones interested) that I can set him up with for about $75,000.
While it wont cover the expenses of a new unit, fully stocked, it will give
me a reason to go buy a new Sprinter.

What I wanna see him do is answer that question properly. You know the
answer, I know the answer, and so do several other people in here.

I wanna know if he knows the right answer since he knows so much about
crooks.

the only crook I have seen so far is the handyman wannabe.



  #21   Report Post  
Tekkie
 
Posts: n/a
Default

Steve@carolinabreezehvac posted for all of us....


"Bubba" wrote in message
...


Steve,
Im suprised at you. You are arguing with one of the dumbest idiots yet
to date. He thinks he is a "fixit man". You know and I know that he
has probably wasted more time and more money on all his "jury rigged"
**** in his home. Now he is wasting bandwidth.
Im goina need a new keyboard soon if you keep this up. :-)
Bubba


Bubba:

Sorry man. Been a while since I posted in here on a regular basis and
thought that with the bull**** in the other group it would be a nice change
of pace...it has been.
I even found someone dumber than Stormin Moron, or DaveHackinNunits.

I also know, that educated consumers dont do stupid **** like he is talking
about. Now...if he wants to be a HVAC guy, properly, I have some used
equipment, less than a year old, on a used Ford, also less than a year old
(1 ton if anyones interested) that I can set him up with for about $75,000.
While it wont cover the expenses of a new unit, fully stocked, it will give
me a reason to go buy a new Sprinter.


Those Sprinters are getting popular around here. I guess they are more of a
heavy duty vehicle... Can't wait till the carpet people get them so the
roll of new carpet isn't sticking out in the weather and the door duct taped
/ bungee corded around it... lol

What I wanna see him do is answer that question properly. You know the
answer, I know the answer, and so do several other people in here.

I wanna know if he knows the right answer since he knows so much about
crooks.

the only crook I have seen so far is the handyman wannabe.



--
Tekkie
  #22   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


"Tekkie" wrote in message
...
Steve@carolinabreezehvac posted for all of us....


"Bubba" wrote in message
...


Steve,
Im suprised at you. You are arguing with one of the dumbest idiots yet
to date. He thinks he is a "fixit man". You know and I know that he
has probably wasted more time and more money on all his "jury rigged"
**** in his home. Now he is wasting bandwidth.
Im goina need a new keyboard soon if you keep this up. :-)
Bubba


Bubba:

Sorry man. Been a while since I posted in here on a regular basis and
thought that with the bull**** in the other group it would be a nice

change
of pace...it has been.
I even found someone dumber than Stormin Moron, or DaveHackinNunits.

I also know, that educated consumers dont do stupid **** like he is

talking
about. Now...if he wants to be a HVAC guy, properly, I have some used
equipment, less than a year old, on a used Ford, also less than a year

old
(1 ton if anyones interested) that I can set him up with for about

$75,000.
While it wont cover the expenses of a new unit, fully stocked, it will

give
me a reason to go buy a new Sprinter.


Those Sprinters are getting popular around here. I guess they are more of

a
heavy duty vehicle... Can't wait till the carpet people get them so the
roll of new carpet isn't sticking out in the weather and the door duct

taped
/ bungee corded around it... lol



Well hell, they ought to be....a rebadged Mercedes with a Dodge, or
Frieghtliner tag on em for under $45,000....
Plus what sucks is that I finally bought a new Dodge 2500 Maxi Van, got it
for a steal since the killed the line like idiots, and now, if you want one
that actually works, gets 20MPG and you can stand in, you HAVE to get one.

I am not fully sold on them YET. Have you looked at the hogshead on a 3500
dually? Tiny....I mean, TINY.


What I wanna see him do is answer that question properly. You know the
answer, I know the answer, and so do several other people in here.

I wanna know if he knows the right answer since he knows so much about
crooks.

the only crook I have seen so far is the handyman wannabe.



--
Tekkie


  #23   Report Post  
 
Posts: n/a
Default

:

I also know, that educated consumers dont do stupid **** like he is talking
about. Now..


If you are talking about me what did I say that I did? Be specific

.if he wants to be a HVAC guy,


Why bother. It doesn't pay enough.

properly, I have some used
equipment, less than a year old, on a used Ford, also less than a year old
(1 ton if anyones interested) that I can set him up with for about $75,000.
While it wont cover the expenses of a new unit, fully stocked, it will give
me a reason to go buy a new Sprinter.

What I wanna see him do is answer that question properly. You know the
answer, I know the answer, and so do several other people in here.


It's hard to answer a question when you haven't asked a question.

I wanna know if he knows the right answer since he knows so much about
crooks.

the only crook I have seen so far is the handyman wannabe.


A bit defensive aren't you? You're not feeling guilty are you?

  #24   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


wrote in message
...
:

I also know, that educated consumers dont do stupid **** like he is

talking
about. Now..


If you are talking about me what did I say that I did? Be specific

.if he wants to be a HVAC guy,


Why bother. It doesn't pay enough.


LOL..
OK.
So you are a brain surgeon...or a lawyer right

For a guy what wants to make the world think that hes in the Forbes list,
you dont read much do ya?


properly, I have some used
equipment, less than a year old, on a used Ford, also less than a year

old
(1 ton if anyones interested) that I can set him up with for about

$75,000.
While it wont cover the expenses of a new unit, fully stocked, it will

give
me a reason to go buy a new Sprinter.

What I wanna see him do is answer that question properly. You know the
answer, I know the answer, and so do several other people in here.


It's hard to answer a question when you haven't asked a question.


Oh..I did, like I said, you cant read well can you?


I wanna know if he knows the right answer since he knows so much about
crooks.

the only crook I have seen so far is the handyman wannabe.


A bit defensive aren't you? You're not feeling guilty are you?


Not a bit there fella...anyone who knows me I have nothing to feel guilty
for.
Of course, when a real pro puts you to the test, its obvious how you
reply...lol..




  #25   Report Post  
 
Posts: n/a
Default

Still waiting. Be specific.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. Furnace improperly installed? Chuck Home Repair 11 November 2nd 04 02:26 AM
Clueless Inspector Faults Furnace Install Hell Toupee Home Repair 3 October 8th 04 06:47 PM
Furnace problems - repair, replace or ???? Paul Home Repair 11 March 24th 04 12:59 AM
Furnace runs but have to manually restart J. Jorgensen Home Repair 19 January 29th 04 04:18 AM
Furnace Problem...HELP! torque Home Repair 5 January 6th 04 01:24 AM


All times are GMT +1. The time now is 03:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"