Peter Wells
 
Posts: n/a
Default Gas furnace starts with a boom!

It seems the pilot in our gas furnace doesn't reliably ignite the main
burner. The upshot is that sometimes, say 1 in 4, the furnace will start
with a real boom. The furnace is regularly serviced and works fine apart
from the starting issue, I explain the problem to the tech's and they take
the burner out, look at it but don't seem to fix it. Any suggestions.

Thanks,

Peter


  #2   Report Post  
Paul Franklin
 
Posts: n/a
Default

On Wed, 19 Jan 2005 01:37:03 GMT, "Peter Wells"
wrote:

It seems the pilot in our gas furnace doesn't reliably ignite the main
burner. The upshot is that sometimes, say 1 in 4, the furnace will start
with a real boom. The furnace is regularly serviced and works fine apart
from the starting issue, I explain the problem to the tech's and they take
the burner out, look at it but don't seem to fix it. Any suggestions.

Thanks,

Peter

As Greg said, try a different service tech.

You are getting a build up of gas before the pilot ignites the main
flame, and there are several possible causes.

I assume you have a standing (always-on) pilot? If not, you may have
a problem with your flame safety.

In any case, the tech should look for clogged burner holes in the area
of the pilot, misadjusted pilot, mispositioned pilot, and excessive
draft. In addition to cleaning the burner and orifices, they should
remove and clean the pilot assembly, since a partially clogged pilot
can reduce the pilot flame size enough to also cause this.

But get it fixed, those little explosions are hard on the furnace.

HTH,

Paul

  #3   Report Post  
TURTLE
 
Posts: n/a
Default


"NoSpamFANatic" wrote in message
. ..
Appears to be the heat exchanger sending warning signs of failure...next is
asphyxiation!!!


This is Turtle.

No Spam , Booming furnaces does not say bad heat exchanger. A Boomer say bad
ignition problem.

TURTLE


  #4   Report Post  
Bubba
 
Posts: n/a
Default

On Wed, 19 Jan 2005 01:37:03 GMT, "Peter Wells"
wrote:

It seems the pilot in our gas furnace doesn't reliably ignite the main
burner. The upshot is that sometimes, say 1 in 4, the furnace will start
with a real boom. The furnace is regularly serviced and works fine apart
from the starting issue, I explain the problem to the tech's and they take
the burner out, look at it but don't seem to fix it. Any suggestions.

Thanks,

Peter


Just let it go a while longer. You wont have to worry about you, your
family, your home or your lives. Pretty clever way to not pay for
proper service.
Regularly serviced by who?
Bubba
  #5   Report Post  
xrongor
 
Posts: n/a
Default


"Bubba" wrote in message
...
On Wed, 19 Jan 2005 01:37:03 GMT, "Peter Wells"
wrote:

It seems the pilot in our gas furnace doesn't reliably ignite the main
burner. The upshot is that sometimes, say 1 in 4, the furnace will start
with a real boom. The furnace is regularly serviced and works fine apart
from the starting issue, I explain the problem to the tech's and they take
the burner out, look at it but don't seem to fix it. Any suggestions.

Thanks,

Peter


Just let it go a while longer. You wont have to worry about you, your
family, your home or your lives. Pretty clever way to not pay for
proper service.
Regularly serviced by who?
Bubba


if you have nothing useful to say, at least have something funny to say...

randy




  #6   Report Post  
Pop
 
Posts: n/a
Default

Bubba wrote:
On Wed, 19 Jan 2005 01:37:03 GMT, "Peter Wells"

wrote:

It seems the pilot in our gas furnace doesn't reliably ignite
the
main burner. The upshot is that sometimes, say 1 in 4, the
furnace
will start with a real boom. The furnace is regularly
serviced and
works fine apart from the starting issue, I explain the
problem to
the tech's and they take the burner out, look at it but don't
seem
to fix it. Any suggestions.

Thanks,

Peter


Just let it go a while longer. You wont have to worry about
you, your
family, your home or your lives. Pretty clever way to not pay
for
proper service.
Regularly serviced by who?
Bubba


Yeah, sounds like YOU tried to fix it!

Pop

  #7   Report Post  
Roby
 
Posts: n/a
Default

Peter Wells wrote:

It seems the pilot in our gas furnace doesn't reliably ignite the main
burner. The upshot is that sometimes, say 1 in 4, the furnace will start
with a real boom. The furnace is regularly serviced and works fine apart
from the starting issue, I explain the problem to the tech's and they take
the burner out, look at it but don't seem to fix it. Any suggestions.

Thanks,

Peter


My furnace did that after I cleaned it. Boom sometimes blew the furnace
door off. Got my attention immediately!

A metal channel that collected a bit of gas from each burner and led it to
the pilot was installed wrong (reversed end for end). If your problem
began after somebody was into it, you might have a similar problem.

In any case, it needs fixen'.

Roby
  #8   Report Post  
Bubba
 
Posts: n/a
Default

On Tue, 18 Jan 2005 23:55:32 -0700, "xrongor"
wrote:


"Bubba" wrote in message
.. .
On Wed, 19 Jan 2005 01:37:03 GMT, "Peter Wells"
wrote:

It seems the pilot in our gas furnace doesn't reliably ignite the main
burner. The upshot is that sometimes, say 1 in 4, the furnace will start
with a real boom. The furnace is regularly serviced and works fine apart
from the starting issue, I explain the problem to the tech's and they take
the burner out, look at it but don't seem to fix it. Any suggestions.

Thanks,

Peter


Just let it go a while longer. You wont have to worry about you, your
family, your home or your lives. Pretty clever way to not pay for
proper service.
Regularly serviced by who?
Bubba


if you have nothing useful to say, at least have something funny to say...

randy


Im sorry. Are you my mother?
Blow Me randy. There. Now thats funny.
Bubba
  #9   Report Post  
Bubba
 
Posts: n/a
Default

On Wed, 19 Jan 2005 09:24:35 -0500, "Pop" wrote:

Bubba wrote:
On Wed, 19 Jan 2005 01:37:03 GMT, "Peter Wells"

wrote:

It seems the pilot in our gas furnace doesn't reliably ignite
the
main burner. The upshot is that sometimes, say 1 in 4, the
furnace
will start with a real boom. The furnace is regularly
serviced and
works fine apart from the starting issue, I explain the
problem to
the tech's and they take the burner out, look at it but don't
seem
to fix it. Any suggestions.

Thanks,

Peter


Just let it go a while longer. You wont have to worry about
you, your
family, your home or your lives. Pretty clever way to not pay
for
proper service.
Regularly serviced by who?
Bubba


Yeah, sounds like YOU tried to fix it!

Pop


I guess someone squeezed Pop's head and thats all that came out? Nice
comeback Pop. Get in line. You're next to blow me.
Bubba
  #10   Report Post  
Duane Bozarth
 
Posts: n/a
Default

Peter Wells wrote:

Thanks to those who replied constructively, I spoke to a couple of service
companies and found one who seemed to agree with the suggestions given here.
They came out last night, took the burner apart, cleaned everything (there
was a lot of what looked like chips of rust in it) and now it starts without
the boom.


And the lesson to be learned here is...you could have done this and
should do such an inspection and cleaning every fall before you
relight it for the season. If you find something you don't understand
or something doesn't "look" right, then you can call the service folk...


  #11   Report Post  
Peter Wells
 
Posts: n/a
Default

Duane...

Please read the original post, the system HAS been regularly serviced and
other tech's (reputable companies) have come out specifically to address
this problem, the reality is that try as you might it is difficult without
knowledge to assess the abilities of those who do this kind of work.
Gaining some knowledge before calling a service tech, for which I am
grateful to those who gave constructive comments, helps me vet the tech's
before they come - that to my mind is the lesson learned.

Peter
"Duane Bozarth" wrote in message
...
Peter Wells wrote:

Thanks to those who replied constructively, I spoke to a couple of

service
companies and found one who seemed to agree with the suggestions given

here.
They came out last night, took the burner apart, cleaned everything

(there
was a lot of what looked like chips of rust in it) and now it starts

without
the boom.


And the lesson to be learned here is...you could have done this and
should do such an inspection and cleaning every fall before you
relight it for the season. If you find something you don't understand
or something doesn't "look" right, then you can call the service folk...



  #12   Report Post  
Duane Bozarth
 
Posts: n/a
Default

Peter Wells wrote:

Duane...

Please read the original post, the system HAS been regularly serviced and
other tech's (reputable companies) have come out specifically to address
this problem, the reality is that try as you might it is difficult without
knowledge to assess the abilities of those who do this kind of work.
Gaining some knowledge before calling a service tech, for which I am
grateful to those who gave constructive comments, helps me vet the tech's
before they come - that to my mind is the lesson learned.


Chill, Peter... I followed the whole thread. I only put in the
$0.02 at the end because the solution was simple and especially now that
you know you can do the check first each fall. If you then have a
question/concern, you can then call the tech knowing you at least took
care of the really obvious.

If it came out (or you interpreted it) as being critical, I didn't
intend that way, simply that such rust and dirt is an inevitable
occurrence w/ any gas furnace from combustion products and condensation
and the burner and pilot orifices should be checked each fall prior to
lighting and the general crud cleaned out. That any service tech
wouldn't do that w/ the information it wasn't lighting reliably is a
real indictment of them.
  #13   Report Post  
Peter Wells
 
Posts: n/a
Default

Duane,

Sorry if I appear a little punchy, too much coffee early in the morning plus
the realization that I've paid multiple companies to get what should be a
basic piece of work done.

Peter
"Duane Bozarth" wrote in message
...
Peter Wells wrote:

Duane...

Please read the original post, the system HAS been regularly serviced

and
other tech's (reputable companies) have come out specifically to address
this problem, the reality is that try as you might it is difficult

without
knowledge to assess the abilities of those who do this kind of work.
Gaining some knowledge before calling a service tech, for which I am
grateful to those who gave constructive comments, helps me vet the

tech's
before they come - that to my mind is the lesson learned.


Chill, Peter... I followed the whole thread. I only put in the
$0.02 at the end because the solution was simple and especially now that
you know you can do the check first each fall. If you then have a
question/concern, you can then call the tech knowing you at least took
care of the really obvious.

If it came out (or you interpreted it) as being critical, I didn't
intend that way, simply that such rust and dirt is an inevitable
occurrence w/ any gas furnace from combustion products and condensation
and the burner and pilot orifices should be checked each fall prior to
lighting and the general crud cleaned out. That any service tech
wouldn't do that w/ the information it wasn't lighting reliably is a
real indictment of them.



  #14   Report Post  
Duane Bozarth
 
Posts: n/a
Default

Peter Wells wrote:

Duane,

Sorry if I appear a little punchy, too much coffee early in the morning plus
the realization that I've paid multiple companies to get what should be a
basic piece of work done.


I'd demand a refund from the first if all the other did was what was
discussed here...that's inexcusable imo.
  #15   Report Post  
Duane Bozarth
 
Posts: n/a
Default

geoman wrote:

Perhaps, but if they didn't even clean a dirty orifice which turned out
to be the problem, I'd raise holy heck about having paid a service
call. Granted, they should have (and I don't recollect from the thread
whether they were or not or whether that inof was provided) been given
the opportunity to make it right, but as noted if the initial call was
as described, he probably got a kid right out of trade school who just
didn't know what he was doing...

If the rudimentary things aren't done first, there's no point in looking
for more complex problems...in this case, the problem was a
dirty/partially plugged pilot orifice...


  #16   Report Post  
geoman
 
Posts: n/a
Default


"Duane Bozarth" wrote in message
...
Peter Wells wrote:

Duane,

Sorry if I appear a little punchy, too much coffee early in the morning
plus
the realization that I've paid multiple companies to get what should be a
basic piece of work done.


I'd demand a refund from the first if all the other did was what was
discussed here...that's inexcusable imo.


I haven't read all the posts, so If I'm out of line here please forgive me,
I erased all the posts off my computer prior to today's.

The last statement may be rash. You can't ask the previous companies to
refund your money unless they deliberately ripped you off or didn't know
what was wrong. Think about it for a moment. A service man/woman comes out
and does their best to solve your problems but just can't do it because this
is something that is out of the norm. Should he/she not be paid for their
time? You can only ask that someone does their best. You took time from
their life, and they proved what WASN'T the problem. Sometimes there are no
clear directives in a repair, its a trial and error situation. If the
customer doesn't like the odds of service then buy a new furnace which makes
your odds 100% winner.

A good example is you going to a doctor. You expect him to try to find out
what is wrong with you and perform every test possible and you don't intend
to pay them UNLESS you get cured?

There are times when I give customers a break, but before I change an
expensive part I ask them first and warn them that it may not be the
problem. Intermediate problems can really be troublesome.

Like I said, I'm not privy to the entire thread so this post may appear to
sound off the wall to the actual topic.

Now, a delayed ignition IS one of the hardest problems to solve for any
technician! You can do all the tests and then have living or atmospheric
conditions change as soon as you leave the site. If the draft is correct,
the gas pressure is good, then it most likely is the ignition system, burner
wear, transfer bar to light the other burners are plugged or rusted and need
replacement, or the exchanger itself has changed somehow with a coating etc
that causes the air not to scrub. A spider web in the orifices can create
these problems along with a small amount of dust in the burners. Like I
said, this is one of the hardest things to fix. I remember working on a
Trane furnace that we put in. We did everything to it and then Trane came
out with a burner replacement a year later that solved the problem. BUT
TRANE NEVER TOLD US or admitted that there was a problem!! How many tech's
out there got THEIR reputation harmed because of the factory?

Rich

Rich


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default Gas furnace starts with a boom!

replying to Paul Franklin, Jim wrote:



pffranklin.nospam wrote:

As Greg said, try a different service tech.
You are getting a build up of gas before the pilot ignites the main
flame, and there are several possible causes.
I assume you have a standing (always-on) pilot? If not, you may have
a problem with your flame safety.
In any case, the tech should look for clogged burner holes in the area
of the pilot, misadjusted pilot, mispositioned pilot, and excessive
draft. In addition to cleaning the burner and orifices, they should
remove and clean the pilot assembly, since a partially clogged pilot
can reduce the pilot flame size enough to also cause this.
But get it fixed, those little explosions are hard on the furnace.
HTH,
Paul



Just Repaired mine. and was this: A misaligned pilot.



--
posted from
http://www.homeownershub.com/mainten...om-586128-.htm
using HomeOwnersHub's Web, RSS and Social Media Interface
to home and garden related groups

  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default Gas furnace starts with a boom!

replying to TURTLE, Sandy wrote:
Will it cause a fire in the home

--
for full context, visit https://www.homeownershub.com/mainte...om-586128-.htm


  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,367
Default Gas furnace starts with a boom!

Sandy posted for all of us...



replying to TURTLE, Sandy wrote:
Will it cause a fire in the home

--
for full context, visit https://www.homeownershub.com/mainte...om-586128-.htm


Turtle crawled into his shell about 20 years ago and never came out...

--
Tekkie
  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 22,192
Default Gas furnace starts with a boom!

On Tue, 2 Jan 2018 17:22:28 -0500, Tekkie® wrote:

Sandy posted for all of us...



replying to TURTLE, Sandy wrote:
Will it cause a fire in the home

--
for full context, visit https://www.homeownershub.com/mainte...om-586128-.htm


Turtle crawled into his shell about 20 years ago and never came out...


Well, the feller at least went out with a boom.


  #21   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8,803
Default Gas furnace starts with a boom!

On 1/2/2018 4:44 AM, Sandy wrote:
replying to TURTLE, Sandy wrote:
Will it cause a fire in the home


Your pilot light jet is partly plugged, or some other problem that
causes it not to light the burner quick enough. Is the pilot a really
small flame?

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lennox Furnace Run-on NewGuy Home Repair 7 November 17th 04 05:58 PM
Help. Furnace improperly installed? Chuck Home Repair 11 November 2nd 04 02:26 AM
Clueless Inspector Faults Furnace Install Hell Toupee Home Repair 3 October 8th 04 06:47 PM
Furnace problems - repair, replace or ???? Paul Home Repair 11 March 24th 04 12:59 AM
Furnace Problem...HELP! torque Home Repair 5 January 6th 04 01:24 AM


All times are GMT +1. The time now is 02:44 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"