What size breaker and wire for a 5200W wall oven?
What size breaker and wire do I need to use for a new installation (not new
oven) of a 5200W wall oven. 2 lines of text for electrical. 120/240 VAC. 60HZ. 5.2KW. 3 WIRE 120/208 VAC. 60HZ. 3.95KW. 3 WIRE Current wires coming out of the oven are 3 at 12 AWG black, red, green, and a 16 AWG white. I am not sure if they are original to the oven or not. I couldn't find the manual online. I acquired this oven used. -- for full context, visit http://www.homeownershub.com/mainten...en-903979-.htm |
#2
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
30a based on a 21.66a load (5200/240) but the real answer is in the
installation manual. My new GE oven calls for a 20. It may not have the same power elements in it tho. On Tue, 20 Sep 2016 16:14:01 +0000, Brent m wrote: What size breaker and wire do I need to use for a new installation (not new oven) of a 5200W wall oven. 2 lines of text for electrical. 120/240 VAC. 60HZ. 5.2KW. 3 WIRE 120/208 VAC. 60HZ. 3.95KW. 3 WIRE Current wires coming out of the oven are 3 at 12 AWG black, red, green, and a 16 AWG white. I am not sure if they are original to the oven or not. I couldn't find the manual online. I acquired this oven used. |
#3
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
Brent m writes:
What size breaker and wire do I need to use for a new installation (not new oven) of a 5200W wall oven. 2 lines of text for electrical. 120/240 VAC. 60HZ. 5.2KW. 3 WIRE 120/208 VAC. 60HZ. 3.95KW. 3 WIRE Current wires coming out of the oven are 3 at 12 AWG black, red, green, and a 16 AWG white. I am not sure if they are original to the oven or not. I couldn't find the manual online. I acquired this oven used. P = VA A = V/P 12AWG is insufficient at 208 or 240VAC. |
#4
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
In article .com,
Brent m wrote: What size breaker and wire do I need to use for a new installation (not new oven) of a 5200W wall oven. 2 lines of text for electrical. 120/240 VAC. 60HZ. 5.2KW. 3 WIRE 120/208 VAC. 60HZ. 3.95KW. 3 WIRE Current wires coming out of the oven are 3 at 12 AWG black, red, green, and a 16 AWG white. I am not sure if they are original to the oven or not. I couldn't find the manual online. I acquired this oven used. Brent- Red and Black wires should go to each side of 240 VAC, White should go to Neutral or Common, and Green should go to the metal frame. But you need to verify how the wires are connected inside the oven, or you could have a serious problem. Your oven would draw 21.7 Amperes for 5200 Watts. A dual 25 Amp breaker should be OK unless there is a 120 VAC outlet. In that case, I'd go for a bigger breaker. I'm not familiar with the codes that specify required wire size. 12 AWG might be OK for 30 Amps, but I would prefer 10 AWG. Fred |
#5
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
replying to Brent, Brent wrote:
I did just finally find an Amana document with my model number that adds 40amp to the end of the electrical lines of text on model plate. So would that mean I need a 40A breaker and 10 gauge wire? In the manual it says: "Line Voltage Requirements Line voltage must not exceed rated voltage. Line voltage less than rated voltage will result in slow heating. Wiring system must conform to U.L. Standards and National Electrical Code. Installation must conform to all local, municipal and state building codes, and local utility regulations. Oven must be connected only to a supplied circuit as specified on rating plate. This oven requires 3 wires, 115/230-120/240 volts, 60 Hertz A.C. Unit is equipped with a No. 10 ground wire in conduit. Oven should be fused separately from other appliances. Verify electric power is off from fuse box to junction box until oven is installed and ready to operate." Maybe I need to open it up where the flex conduit enters the oven and see what else I can find... -- for full context, visit http://www.homeownershub.com/mainten...en-903979-.htm |
#6
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
replying to Brent, Brent wrote:
here are the from the spec sheet I was able to locate Electrical Requirements 120/240 VAC, 60 Hz, 5.2 Kw, 3-wire, 40 Amp 120/208 VAC, 60 Hz, 3.95 Kw, 3-wire, 40 Amp Oven Wattage @ 240V Bake 2,000 Broil, Insta-BroilTM 3,000 -- for full context, visit http://www.homeownershub.com/mainten...en-903979-.htm |
#7
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
Fred McKenzie wrote in -
75-242-165.myvzw.com: I'm not familiar with the codes that specify required wire size. Then you probably shouldn't be trying to offer wiring advice. |
#8
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
replying to Brent, Tony944 wrote:
As you stated your oven have two settings one is for bake and other to Broil. I am sure you can use one or the other but "NOT" both at the same time! At the broil rough estimate of current would be 13-14 Amps. On the bake again rough estimate current will be 9-10 Amps. This is base on 220 power source, number 12 wire would be sufficient enough. Likewise the breaker 20-25 Amps ok. Two poles!! Your white wire is for lights and possible outlet if it has one€¦ -- for full context, visit http://www.homeownershub.com/mainten...en-903979-.htm |
#9
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Tuesday, September 20, 2016 at 3:14:06 PM UTC-4, Brent wrote:
replying to Brent, Brent wrote: I did just finally find an Amana document with my model number that adds 40amp to the end of the electrical lines of text on model plate. So would that mean I need a 40A breaker and 10 gauge wire? We don't know because we can't see what you're reading, don't know how you're interpreting it, don't know what exactly is on the eqpt plate, in the manual, etc. But if it needs 40A, then you need 8g wire. How you get to 40A, IDK, because all I see is 22A at 240V = 5200 watts But a typical oven could by 40A. |
#10
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Tue, 20 Sep 2016 23:03:25 +0100, Doug Miller wrote:
Fred McKenzie wrote in - 75-242-165.myvzw.com: I'm not familiar with the codes that specify required wire size. Then you probably shouldn't be trying to offer wiring advice. Some people prefer physics to regulations. -- Can you grow birds by planting birdseed? |
#11
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Tuesday, September 20, 2016 at 6:14:06 PM UTC-4, Tony944 wrote:
replying to Brent, Tony944 wrote: As you stated your oven have two settings one is for bake and other to Broil. I am sure you can use one or the other but "NOT" both at the same time! At the broil rough estimate of current would be 13-14 Amps. On the bake again rough estimate current will be 9-10 Amps. Very odd then that it says 5200W at 240V. It would also be odd for a new oven to use just 14 amps. They don't typically wire them up with 40A circuits for nothing. It would take a very long time to wait for your dinner. Do you like to wait? This is base on 220 power source, number 12 wire would be sufficient enough. I've never seen a 220V power source, only 240V. Maybe it exists somewhere in the USA, but AFAIK, it's not common. Apparently Amana thinks so too, they spec the oven at 240V. Likewise the breaker 20-25 Amps ok. Two poles!! Your white wire is for lights and possible outlet if it has one€¦ -- for full context, visit http://www.homeownershub.com/mainten...en-903979-.htm |
#12
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Tue, 20 Sep 2016 17:14:01 +0100, Brent m wrote:
What size breaker and wire do I need to use for a new installation (not new oven) of a 5200W wall oven. 2 lines of text for electrical. 120/240 VAC. 60HZ. 5.2KW. 3 WIRE 120/208 VAC. 60HZ. 3.95KW. 3 WIRE Current wires coming out of the oven are 3 at 12 AWG black, red, green, and a 16 AWG white. I am not sure if they are original to the oven or not. I couldn't find the manual online. I acquired this oven used. What a farce. In the UK, ovens (and everything else) only takes 240 volts. No messing about with extra wires and dual breakers. -- ADULT: A person who has stopped growing at both ends and is now growing in the middle. |
#13
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
trader_4
Tue, 20 Sep 2016 23:29:11 GMT in alt.home.repair, wrote: I've never seen a 220V power source, only 240V. Maybe it exists somewhere in the USA, but AFAIK, it's not common. Apparently Amana thinks so too, they spec the oven at 240V. http://preview.tinyurl.com/59bf3j How long have you been an electrician? Just curious, mind you. -- MID: Hmmm. I most certainly don't understand how I can access a copy of a zip file but then not be able to unzip it so I can watch it. That seems VERY clever! http://al.howardknight.net/msgid.cgi?ID=145716711400 |
#14
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Tue, 20 Sep 2016 16:29:11 -0700 (PDT), trader_4
wrote: Very odd then that it says 5200W at 240V. It would also be odd for a new oven to use just 14 amps. They don't typically wire them up with 40A circuits for nothing. It would take a very long time to wait for your dinner. Do you like to wait? I just bought a wall oven and the ones I looked at were listed for a 20a circuit. I ended up with a GE 27" convection oven that spec's out at 3.4kw. I think you will find the 40a circuits are for ranges tho. Wall ovens and cooktops are 20a or 30a. |
#15
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Tuesday, September 20, 2016 at 9:38:15 PM UTC-4, Diesel wrote:
trader_4 Tue, 20 Sep 2016 23:29:11 GMT in alt.home.repair, wrote: I've never seen a 220V power source, only 240V. Maybe it exists somewhere in the USA, but AFAIK, it's not common. Apparently Amana thinks so too, they spec the oven at 240V. http://preview.tinyurl.com/59bf3j What exactly is that ridiculous link supposed to prove? It starts off with: Dear Cecil: "How come the U.S. is practically the only country in the world where household electricity is 110 volts instead of 220 volts?" Obviously they are very confused because the common residential voltages here are 120/240, not 110. Again, 110/220 may exist somewhere in the US today, but I've never seen it. Have you? Where? |
#16
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Wednesday, September 21, 2016 at 2:05:38 AM UTC-4, wrote:
On Tue, 20 Sep 2016 16:29:11 -0700 (PDT), trader_4 wrote: Very odd then that it says 5200W at 240V. It would also be odd for a new oven to use just 14 amps. They don't typically wire them up with 40A circuits for nothing. It would take a very long time to wait for your dinner. Do you like to wait? I just bought a wall oven and the ones I looked at were listed for a 20a circuit. I ended up with a GE 27" convection oven that spec's out at 3.4kw. I think you will find the 40a circuits are for ranges tho. Wall ovens and cooktops are 20a or 30a. I was thinking from what I have hear. The house originally had a Jenn-Air combo oven and microwave wall unit. I recently replaced it with a Kitchenaid double 30" unit. Both of those were 40A, which was fortunate so I didn't have to rewire. I can see a single oven would use less, IDK what the OP has, but he is saying that in the manual it says a 40A circuit, while those other numbers he posted would seem to show 22A, so IDK. |
#17
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
replying to trader_4, Tony944 wrote:
Well I am not surprise that you never seen 220, however there are many places that power is must likely to be around 208 instead of 240 or 220. in most metropolitan area you are lucky to have even 208 I have been in places with power was low as 195 and customer complain why equipment is not working right "surprise". -- for full context, visit http://www.homeownershub.com/mainten...en-903979-.htm |
#18
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thu, 22 Sep 2016 04:14:01 +0000, Tony944
wrote: Well I am not surprise that you never seen 220, however there are many places that power is must likely to be around 208 instead of 240 or 220. in most metropolitan area you are lucky to have even 208 I have been in places with power was low as 195 and customer complain why equipment is not working right "surprise". "In metropolitan areas" (apartments etc) you may actually be looking at 2 legs of a 120/208 3p service If you have less than 216v (240 minus 10%) at your meter on a 120/240 1p service you should be calling the Public Utilities Commission or whomever regulates your PoCo. (if the power company will not do anything about it when you tell them) |
#19
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
trader_4
Wed, 21 Sep 2016 23:53:14 GMT in alt.home.repair, wrote: On Tuesday, September 20, 2016 at 9:38:15 PM UTC-4, Diesel wrote: trader_4 Tue, 20 Sep 2016 23:29:11 GMT in alt.home.repair, wrote: I've never seen a 220V power source, only 240V. Maybe it exists somewhere in the USA, but AFAIK, it's not common. Apparently Amana thinks so too, they spec the oven at 240V. http://preview.tinyurl.com/59bf3j What exactly is that ridiculous link supposed to prove? It starts off with: It doesn't prove anything. Only that 120volt wasn't always the norm. Long before my time on this planet, though. You shouldn't take everything I write so personally... -- MID: Hmmm. I most certainly don't understand how I can access a copy of a zip file but then not be able to unzip it so I can watch it. That seems VERY clever! http://al.howardknight.net/msgid.cgi?ID=145716711400 |
#21
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thursday, September 22, 2016 at 5:45:02 AM UTC-4, Diesel wrote:
trader_4 Wed, 21 Sep 2016 23:53:14 GMT in alt.home.repair, wrote: On Tuesday, September 20, 2016 at 9:38:15 PM UTC-4, Diesel wrote: trader_4 Tue, 20 Sep 2016 23:29:11 GMT in alt.home.repair, wrote: I've never seen a 220V power source, only 240V. Maybe it exists somewhere in the USA, but AFAIK, it's not common. Apparently Amana thinks so too, they spec the oven at 240V. http://preview.tinyurl.com/59bf3j What exactly is that ridiculous link supposed to prove? It starts off with: It doesn't prove anything. Only that 120volt wasn't always the norm. Who said it was? We aren't talking about history here, only what's in use today with the OP's oven. Long before my time on this planet, though. You shouldn't take everything I write so personally... I guess you think it's better to let people imply that 220V is a standard today in the USA, throw that into the mix of this oven, etc. Nothing personal, just that I think facts matter. |
#22
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
You can call it 110 or 120 interchangeably.
It hasn't actually varied in my lifetime, other than the normal day to day variation with load. That's an RMS value, the peak is around 170. Similarly when I worked in a factory the voltage was 440, 460, or 480, depending on who was talking, but it was all the same jolts. |
#23
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
TimR expressed precisely :
You can call it 110 or 120 interchangeably. Yes, but one of those would be wrong. It hasn't actually varied in my lifetime, other than the normal day to day variation with load. No "brownouts" then? Of course, we're not really talking about actual voltages here, but the nomenclature instead. That's an RMS value, the peak is around 170. Yes, but it is best to stick to one measure throughout a discussion. Similarly when I worked in a factory the voltage was 440, 460, or 480, depending on who was talking, but it was all the same jolts. As long as everyone understands each other, then there is no harm. When using figures like that in engineering, everyone should use the 'correct' voltage in their computations. |
#24
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On 09/22/2016 10:04 AM, FromTheRafters wrote:
Ralph Mowery laid this down on his screen : In article , says... .... Years ago , around 1950 , many items were listed as operating on 110 or 220 volts. My dad repaired appliances during that era and often said 110 and 220. If I don't watch it,I will say the same thing even though most household items are listed as 120 and 240 volts. At one time near the middle 1950's items were rated for 115 volts. The 'standard' home voltage seems to have gone from 110 to 115 to 120 volts over the last 70 years. https://en.wikipedia.org/wiki/Mains_...tandardisation "Historically 110 V, 115 V and 117 V have been used at different times and places in North America. Mains power is sometimes spoken of as 110 V; however, 120 V is the nominal voltage." .... US spec's are given in ANSI C84.1-2011; you may be surprised to lean that first standardized effort by AIEE occurred as far back as 1898 the first joint meetings were held with the first accepted for publication in June, 1899. Revisions to it occurred in 1902, 1905 and 1911. The AC low voltage ratings at that time were established as 110,220,440 and 550 V. I don't have the full history between then and the initial C84.1 adoption in (I believe) 1956 but as the Wikipedia article notes, there were intermediary periods of voltages between 110 and the current 120. Some history-type papers I've seen had data that by the late 1940s something like 90% of produced light bulbs were rated for 120V. A link to the C84.1 Table 1 --http://www.powerqualityworld.com/2011/04/ansi-c84-1-voltage-ratings-60-hertz.html |
#25
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thursday, September 22, 2016 at 3:33:27 PM UTC-4, TimR wrote:
You can call it 110 or 120 interchangeably. It hasn't actually varied in my lifetime, other than the normal day to day variation with load. That's an RMS value, the peak is around 170. Similarly when I worked in a factory the voltage was 440, 460, or 480, depending on who was talking, but it was all the same jolts. People can call it whatever they want, but that isn't how the power industry operates and it just adds to the confusion. AFAIK, they have a voltage spec that they try to deliver and in all the places I've been around the USA, that's 120V, not 110. Apparently Ammana, the manufacturer of the oven in question agrees, because you'll see that they spec it at 240V, not 220V. Which is why I asked where anyone has seen 110V today as the norm in the USA? |
#26
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thursday, September 22, 2016 at 4:50:44 PM UTC-4, FromTheRafters wrote:
TimR expressed precisely : You can call it 110 or 120 interchangeably. Yes, but one of those would be wrong. It hasn't actually varied in my lifetime, other than the normal day to day variation with load. No "brownouts" then? Of course, we're not really talking about actual voltages here, but the nomenclature instead. Or how about it hasn't varied from what? 110? or 120? Here it's 120V at the panel, with minor variation. |
#27
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On 9/22/2016 6:02 PM, trader_4 wrote:
People can call it whatever they want, but that isn't how the power industry operates and it just adds to the confusion. AFAIK, they have a voltage spec that they try to deliver and in all the places I've been around the USA, that's 120V, not 110. Apparently Ammana, the manufacturer of the oven in question agrees, because you'll see that they spec it at 240V, not 220V. Which is why I asked where anyone has seen 110V today as the norm in the USA? Recently? I recall 110V at our house in Philadelphia, but that was 60 years ago. Going back to Westinghouse and his AC transformers I did read they were 110V output. With voltage drops at distances it could be low and thus, was boosted to a nominal 120V. I am neither an electrical historian or engineer and I'm not going to search for cites. Nominal voltage today is 120 but can be lower with distance. |
#28
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thursday, September 22, 2016 at 7:05:18 PM UTC-4, Ed Pawlowski wrote:
On 9/22/2016 6:02 PM, trader_4 wrote: People can call it whatever they want, but that isn't how the power industry operates and it just adds to the confusion. AFAIK, they have a voltage spec that they try to deliver and in all the places I've been around the USA, that's 120V, not 110. Apparently Ammana, the manufacturer of the oven in question agrees, because you'll see that they spec it at 240V, not 220V. Which is why I asked where anyone has seen 110V today as the norm in the USA? Recently? I recall 110V at our house in Philadelphia, but that was 60 years ago. Going back to Westinghouse and his AC transformers I did read they were 110V output. With voltage drops at distances it could be low and thus, was boosted to a nominal 120V. I am neither an electrical historian or engineer and I'm not going to search for cites. Nominal voltage today is 120 but can be lower with distance. That's all we're talking about, nominal voltage that the power company supplies today for the OP's oven and similar. Which again is why I asked if anyone has seen 110V in the USA and that's today, not in 1942. In my world it's 120/240V. And it does make a difference. If I saw 110V at my panel, I'd know something isn't right. |
#29
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thursday, September 22, 2016 at 7:05:18 PM UTC-4, Ed Pawlowski wrote:
On 9/22/2016 6:02 PM, trader_4 wrote: People can call it whatever they want, but that isn't how the power industry operates and it just adds to the confusion. AFAIK, they have a voltage spec that they try to deliver and in all the places I've been around the USA, that's 120V, not 110. Apparently Ammana, the manufacturer of the oven in question agrees, because you'll see that they spec it at 240V, not 220V. Which is why I asked where anyone has seen 110V today as the norm in the USA? Recently? I recall 110V at our house in Philadelphia, but that was 60 years ago. Going back to Westinghouse and his AC transformers I did read they were 110V output. With voltage drops at distances it could be low and thus, was boosted to a nominal 120V. I am neither an electrical historian or engineer and I'm not going to search for cites. Nominal voltage today is 120 but can be lower with distance. Or to put it another way, if we went to the panel in the homes of the people who are talking about 110/220, would we measure close to that or would we really see 120/240? I'm guessing the latter. |
#30
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
dpb presented the following explanation :
On 09/22/2016 10:04 AM, FromTheRafters wrote: Ralph Mowery laid this down on his screen : In article , says... ... Years ago , around 1950 , many items were listed as operating on 110 or 220 volts. My dad repaired appliances during that era and often said 110 and 220. If I don't watch it,I will say the same thing even though most household items are listed as 120 and 240 volts. At one time near the middle 1950's items were rated for 115 volts. The 'standard' home voltage seems to have gone from 110 to 115 to 120 volts over the last 70 years. https://en.wikipedia.org/wiki/Mains_...tandardisation "Historically 110 V, 115 V and 117 V have been used at different times and places in North America. Mains power is sometimes spoken of as 110 V; however, 120 V is the nominal voltage." ... US spec's are given in ANSI C84.1-2011; you may be surprised to lean that first standardized effort by AIEE occurred as far back as 1898 the first joint meetings were held with the first accepted for publication in June, 1899. Revisions to it occurred in 1902, 1905 and 1911. The AC low voltage ratings at that time were established as 110,220,440 and 550 V. I showed an old phonograph motor to my Electricity & Electronics instructor back in 1970. It had a clear plastic strap around it with 110VAC in black stamped on it. He told me it was about twenty years old because back in 1950 or so 110 volts was the norm. I don't have the full history between then and the initial C84.1 adoption in (I believe) 1956 but as the Wikipedia article notes, there were intermediary periods of voltages between 110 and the current 120. Some history-type papers I've seen had data that by the late 1940s something like 90% of produced light bulbs were rated for 120V. That sounds about right. A link to the C84.1 Table 1 --http://www.powerqualityworld.com/2011/04/ansi-c84-1-voltage-ratings-60-hertz.html |
#31
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On 9/22/2016 8:02 PM, trader_4 wrote:
On Thursday, September 22, 2016 at 7:05:18 PM UTC-4, Ed Pawlowski wrote: On 9/22/2016 6:02 PM, trader_4 wrote: People can call it whatever they want, but that isn't how the power industry operates and it just adds to the confusion. AFAIK, they have a voltage spec that they try to deliver and in all the places I've been around the USA, that's 120V, not 110. Apparently Ammana, the manufacturer of the oven in question agrees, because you'll see that they spec it at 240V, not 220V. Which is why I asked where anyone has seen 110V today as the norm in the USA? Recently? I recall 110V at our house in Philadelphia, but that was 60 years ago. Going back to Westinghouse and his AC transformers I did read they were 110V output. With voltage drops at distances it could be low and thus, was boosted to a nominal 120V. I am neither an electrical historian or engineer and I'm not going to search for cites. Nominal voltage today is 120 but can be lower with distance. Or to put it another way, if we went to the panel in the homes of the people who are talking about 110/220, would we measure close to that or would we really see 120/240? I'm guessing the latter. That would be my guess. Of course you may see a minor variation of a volt or two. I've seen 135 at my house but after reporting it, power company corrected it. |
#32
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thu, 22 Sep 2016 17:02:38 -0700 (PDT), trader_4
wrote: Or to put it another way, if we went to the panel in the homes of the people who are talking about 110/220, would we measure close to that or would we really see 120/240? I'm guessing the latter. If you came to my house it would be 123.5 - 123.9 |
#33
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
trader_4
Thu, 22 Sep 2016 14:37:00 GMT in alt.home.repair, wrote: I guess you think it's better to let people imply that 220V is a standard today in the USA, throw that into the mix of this oven, etc. Nothing personal, just that I think facts matter. You shouldn't make broad assumptions like that. -- MID: Hmmm. I most certainly don't understand how I can access a copy of a zip file but then not be able to unzip it so I can watch it. That seems VERY clever! http://al.howardknight.net/msgid.cgi?ID=145716711400 |
#34
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
|
#35
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thursday, September 22, 2016 at 11:14:28 PM UTC-4, Ralph Mowery wrote:
In article , says... On Thursday, September 22, 2016 at 7:05:18 PM UTC-4, Ed Pawlowski wrote: On 9/22/2016 6:02 PM, trader_4 wrote: Recently? I recall 110V at our house in Philadelphia, but that was 60 years ago. Going back to Westinghouse and his AC transformers I did read they were 110V output. With voltage drops at distances it could be low and thus, was boosted to a nominal 120V. I am neither an electrical historian or engineer and I'm not going to search for cites. Nominal voltage today is 120 but can be lower with distance. Or to put it another way, if we went to the panel in the homes of the people who are talking about 110/220, would we measure close to that or would we really see 120/240? I'm guessing the latter. This discussion is almost like trying to call a 2x4 whatever it is now. Over the years the 2x4 has gotten smaller as the time passes by. The voltage has gotten higher. If you were to go to a lumber yard would you ask for a 2x4 or maybe something like a 1 3/4 x 3 1/2 or whatever they are now ? Not even close to the same. 2x4's are called out as that in construction specs, though the actual dimensions are less. That is what they are referred to by standards, by sellers, by buyers, by people in the trade, who call them 2x4s but deliver the spec'd dimensions. You just saw the specs for the oven in this thread. It says 240V, not 220. Same with my oven when I put it in. The applicances one typically buys are spec'd at 120V, not 110V. And 120V is what the power company delivers, again to a spec. In other words the industry is using 240/120, mostly consistently and that is what you get when you measure at the panel, at least here. So, I don't see the need for the 110/220 confusion, it's just wrong. I have a voltmeter on one of the outlets at my house that stays on all the time. It has been calibrated with instruments that were at one time set to the NIST. It has ranged from a low of 118 to a high of 124 at the times I have seen it. Most of the time it is around 121 to 123 volts. Exactly. It's not in the neighborhood of 110V, because it's 120V power. |
#36
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On Thursday, September 22, 2016 at 8:56:34 PM UTC-4, Diesel wrote:
trader_4 Thu, 22 Sep 2016 14:37:00 GMT in alt.home.repair, wrote: I guess you think it's better to let people imply that 220V is a standard today in the USA, throw that into the mix of this oven, etc. Nothing personal, just that I think facts matter. You shouldn't make broad assumptions like that. Well what should one assume, when it's a 240V oven being connected to a 240V service and you start talking about 220V? Why confuse people who don't even know how to hook up their oven, by using a voltage convention that is wrong and does not exist? |
#37
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On 09/22/2016 02:33 PM, TimR wrote:
You can call it 110 or 120 interchangeably. It hasn't actually varied in my lifetime, other than the normal day to day variation with load. That's an RMS value, the peak is around 170. IIRC, converting RMS to peak, you multiply by the square root of 2 (I don't know why it's THAT). 120 * SQR(2) = 169.7056275, which most people would call 170. I needed to know that recently when selecting a diode (1N4003) for making a light half brightness. Similarly when I worked in a factory the voltage was 440, 460, or 480, depending on who was talking, but it was all the same jolts. I recently was talking to an older friend who was talking about a submersible well pump that uses 220. I've always said 240 for that. Also, I have measured the voltage here, and have almost exactly 120 and 240. BTW, when doing the above math I remember by first class in trigonometry. Most of the time, the teacher was walking around showing people what buttons to press on their calculators. Then they would be asked for something like "the SIN of 80" and some student would read all 8 or more digits of the answer. There was almost nothing said about what trigonometry IS or what it could be used for. -- 93 days until the winter celebration (Sunday December 25, 2016 12:00:00 AM for 1 day). Mark Lloyd http://notstupid.us/ "Most of it is crap, but in every pile of crap is a gem of stupidity that will have you on the floor in laughter." (Preacher)] |
#38
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
|
#39
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
On 09/23/2016 1:01 PM, trader_4 wrote:
.... ... So, I don't see the need for the 110/220 confusion, it's just wrong. Like many things, it (110V referral, that is) hangs around because at one time it _was_ the standard and not all the people who grew up with it died off at the time it was changed and, besides, they had kids and those kids learned to call it what their folks did, and that continues to this day...what the actual is isn't really the issue or the cause either one; it's simply historical precedent. |
#40
Posted to alt.home.repair
|
|||
|
|||
What size breaker and wire for a 5200W wall oven?
Mark Lloyd was thinking very hard :
On 09/22/2016 02:33 PM, TimR wrote: You can call it 110 or 120 interchangeably. It hasn't actually varied in my lifetime, other than the normal day to day variation with load. That's an RMS value, the peak is around 170. IIRC, converting RMS to peak, you multiply by the square root of 2 (I don't know why it's THAT). 120 * SQR(2) = 169.7056275, which most people would call 170. I needed to know that recently when selecting a diode (1N4003) for making a light half brightness. Similarly when I worked in a factory the voltage was 440, 460, or 480, depending on who was talking, but it was all the same jolts. I recently was talking to an older friend who was talking about a submersible well pump that uses 220. I've always said 240 for that. Also, I have measured the voltage here, and have almost exactly 120 and 240. BTW, when doing the above math I remember by first class in trigonometry. Most of the time, the teacher was walking around showing people what buttons to press on their calculators. Then they would be asked for something like "the SIN of 80" and some student would read all 8 or more digits of the answer. There was almost nothing said about what trigonometry IS or what it could be used for. That is a major problem with the way mathematics is taught. Not only does it lead to incomplete understanding of it, it hides the usefulness of it. When I was in school we weren't allowed to use calculators. One teacher I had would allow us to use a slide-rule if we knew how to work one. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Oven Connection and Breaker Size | UK diy | |||
Three wire electric oven, four wire wall? | Home Repair | |||
Breaker size for oven | Home Repair | |||
Oven Breaker Size | Home Repair | |||
Breaker and wire size? | Woodworking |