I noticed the circuit that feeds my double oven is split at a junction
box to wire both the oven and a former range top. The wire to the
junction box is SER aluminum with a 50amp breaker.

At the junction box the wire is split to two smaller wires (one to the
oven, one to the old range top with the wires capped). The wire is
brown, solid and unmarked. It looks like 8 gauge.

I'm sure this is not safe. I would like to reduce the breaker size to
match the brown wire and remove the unused brown wire from the junction
box.

The double oven is marked 120/240 - 7000 watts. I believe that
requires a a dbl 40amp.

I just want to verify that I should change the dbl 50amp to a 40amp to
match the wire and that 40amp is correct for 120/240@7000watts. I will
verify the brown wire is 8 gauge.

Here are a few pictures of the junction box with wires:
http://66.232.129.14/o/oven1.jpg
http://66.232.129.14/o/oven2.jpg
http://66.232.129.14/o/oven3.jpg


Thank you,
John

  #2   Report Post  
zxcvbob
 
Posts: n/a
Default

News wrote:
I noticed the circuit that feeds my double oven is split at a junction
box to wire both the oven and a former range top. The wire to the
junction box is SER aluminum with a 50amp breaker.

At the junction box the wire is split to two smaller wires (one to the
oven, one to the old range top with the wires capped). The wire is
brown, solid and unmarked. It looks like 8 gauge.

I'm sure this is not safe. I would like to reduce the breaker size to
match the brown wire and remove the unused brown wire from the junction
box.

The double oven is marked 120/240 - 7000 watts. I believe that
requires a a dbl 40amp.

I just want to verify that I should change the dbl 50amp to a 40amp to
match the wire and that 40amp is correct for 120/240@7000watts. I will
verify the brown wire is 8 gauge.

Here are a few pictures of the junction box with wires:
http://66.232.129.14/o/oven1.jpg
http://66.232.129.14/o/oven2.jpg
http://66.232.129.14/o/oven3.jpg


Thank you,
John



This is very common and allowed by the electric code. I was going to
say it was probably done correctly, but the wirenuts are wrong if the
SER is really aluminum -- but it could be tinned copper. If you have
aluminum and copper wire spliced together, you need to use a AL7CU or
AL9CU rated connector (there's one other rating too, but I don't
remember if it's CO/ALR or what.) The aluminum and copper are supposed
to be separated by a tin-plated divider that's part of the connector.

Bob
  #3   Report Post  
TURTLE
 
Posts: n/a
Default


"News" wrote in message
oups.com...
I noticed the circuit that feeds my double oven is split at a junction
box to wire both the oven and a former range top. The wire to the
junction box is SER aluminum with a 50amp breaker.

At the junction box the wire is split to two smaller wires (one to the
oven, one to the old range top with the wires capped). The wire is
brown, solid and unmarked. It looks like 8 gauge.

I'm sure this is not safe. I would like to reduce the breaker size to
match the brown wire and remove the unused brown wire from the junction
box.

The double oven is marked 120/240 - 7000 watts. I believe that
requires a a dbl 40amp.

I just want to verify that I should change the dbl 50amp to a 40amp to
match the wire and that 40amp is correct for 120/240@7000watts. I will
verify the brown wire is 8 gauge.

Here are a few pictures of the junction box with wires:
http://66.232.129.14/o/oven1.jpg
http://66.232.129.14/o/oven2.jpg
http://66.232.129.14/o/oven3.jpg


Thank you,
John


This is Turtle.

Yes Dropping to a 40 amp breaker on # 8-2 with Nake Ground seems to be good
here.

Now like ZXCVBob said about the Al. wire in the same wire nut with Cu. wire
should have the proper connector to prevent shorts. You might want to do that.

TURTLE


  #4   Report Post  
News
 
Posts: n/a
Default

Thank you for the information. I did not realize that you can reduce
the wire size on a circuit and still stay within code.

One more quick question: If the oven is 7000watts at 240v, then it uses
about 29 amps. Is that 29amp per leg, or 14.5amp per leg?
Thanks again,
John

  #5   Report Post  
zxcvbob
 
Posts: n/a
Default

News wrote:
Thank you for the information. I did not realize that you can reduce
the wire size on a circuit and still stay within code.


A built-in oven and a seperate cooktop on the same circuit is a special
case.

One more quick question: If the oven is 7000watts at 240v, then it uses
about 29 amps. Is that 29amp per leg, or 14.5amp per leg?


It is something like 29A on one leg and 29.5A on the other, and 1/2 amp
on the neutral (for the oven light.)

If you are sure that the SER is aluminum and not tin-plated copper, you
should have the splices redone with proper connectors and deoxidizer
goop. (The black and red wires look like they might be done right
already.) You might need a large junction box; I can't tell.

Leave the breaker alone; it is OK.

Best regards,
Bob



  #6   Report Post  
NJJohn
 
Posts: n/a
Default

Thank you very much for your help.

Regards,
John

  #7   Report Post  
Brad Behm
 
Posts: n/a
Default

Bob stated:

This is very common and allowed by the electric code.


I don't thinks so Bob. Where in the NEC do you find that? The code allows
for oversizing a breaker on a circuit running a motor (momentary start-up
current draw) but not an oven or range-top...at least not that I am aware.
The overcurrent device has to be rated to protect the wire and the
equipment. How is a 50 amp breaker going to protect 40 amp wire (assuming
its copper)?

Brad in Bend OR



  #8   Report Post  
zxcvbob
 
Posts: n/a
Default

Brad Behm wrote:
Bob stated:

This is very common and allowed by the electric code.


I don't thinks so Bob. Where in the NEC do you find that? The code allows
for oversizing a breaker on a circuit running a motor (momentary start-up
current draw) but not an oven or range-top...at least not that I am aware.
The overcurrent device has to be rated to protect the wire and the
equipment. How is a 50 amp breaker going to protect 40 amp wire (assuming
its copper)?

Brad in Bend OR



THere is an exception, I think it is commonly referred to as a "tap
rule", for wired-in-place cooking appliances fed from a common 50A
circuit. (it is very specific.) I'd look it up for you, but I haven't
been able to find my code book since I took it to my father's house last
summer :-(

The tap wires are relatively short and are protected from overload by
the maximum current draw of the appliance. In case of a short, it won't
matter whether you have a 40A or a 50A breaker cuz either will trip.

A quick search on google looks like it might be 210.19(A)(3), exception
#1, but I can't verify that.

Best regards,
Bob
  #9   Report Post  
Brad Behm
 
Posts: n/a
Default



I don't thinks so Bob. Where in the NEC do you find that? The code
allows
for oversizing a breaker on a circuit running a motor (momentary start-up
current draw) but not an oven or range-top...at least not that I am
aware.
The overcurrent device has to be rated to protect the wire and the
equipment. How is a 50 amp breaker going to protect 40 amp wire
(assuming
its copper)?

Brad in Bend OR



THere is an exception, I think it is commonly referred to as a "tap rule",
for wired-in-place cooking appliances fed from a common 50A circuit. (it
is very specific.) I'd look it up for you, but I haven't been able to
find my code book since I took it to my father's house last summer :-(

The tap wires are relatively short and are protected from overload by the
maximum current draw of the appliance. In case of a short, it won't
matter whether you have a 40A or a 50A breaker cuz either will trip.

A quick search on google looks like it might be 210.19(A)(3), exception
#1, but I can't verify that.

Best regards,
Bob


Well Bob,
Hats off to you! The NEC 210.19(A)(3) exception No. 1 says you are
absolutely correct! I stand corrected. Thanks I learned something new!

Brad in Bend OR.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Circuit Breaker Size? - 25HP, 200V, 3-Phase, 70A (Full Load) Avestruz Metalworking 2 January 11th 05 09:45 PM
Home made heat treating oven kiln: how to & Merry Xmas ! rashid111 Metalworking 8 January 1st 05 08:23 PM
Breaker and wire size? Tony Woodworking 15 March 5th 04 01:20 AM
Oven wiring size? Fred Leiter Home Repair 8 March 2nd 04 12:22 PM
Strange not-quite-240 high-voltage smoke problem... short? circuit breaker? Kent Monroe Home Repair 10 February 22nd 04 02:42 AM


All times are GMT +1. The time now is 04:39 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"