On Sat, 23 Jan 2016 02:03:06 -0500, Micky
wrote: On Fri, 22 Jan 2016 14:25:43 -0000 (UTC), "E. Robinson" wrote: On Fri, 22 Jan 2016 08:28:00 -0500, Micky wrote: I don't think he can do that. He has empty spots where a new breaker could be placed, but it clearly says "Do not remove this twistout". I think he's stuck. I noticed the same thing. It seems to be full. I was kidding. I thought it meant don't remove them until you need to. But you all have convinced me it means something else. Yes, there are half-wide breakers, if you have no more empty spaces. But you have to buy two. Looks like he is replacing half-wide already |
#162
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
wrote in message
... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. But, I think that any water that is INSIDE a conduit will continue to flow inside that conduit down into the drip loop then back up and then down again to the lowest point in the conduit down below. If it were water inside a hose, as new water flowed into the hose at the top of the hose the water inside the hose would continue flowing down to the lowest point further down at the end of the hose. This would be similar to a sink drain and trap -- where the trap is in effect a "drip loop". Similarly, water on the outside of the sink drain would drip off at the bottom of the trap. But water inside the drain line would continue to flow down to the end of the drain line and would continue past the "drip loop"/trap. In the scenario that I had where water was getting inside the conduit and going into the panel, if the conduit had a drip loop in it, I could have cut a small slit in the conduit wrap at the bottom of the drip loop to let the water inside the conduit drip out there rather than continue down into the panel inside the house in the basement. Of course, that would only have been a temporary fix until I corrected the problem of water getting inside the conduct from the meter box. In my case, there was no such drip loop in that part of the conduit (from the bottom of the meter to the panel below inside the house in the basement). |
#163
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Sat, 23 Jan 2016 10:54:21 -0500, "TomR"
wrote: wrote in message .. . On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. The water is not IN the conduit. It gets into the meter box, and with no drip loop the water runs down the cable into the conduit (which goes out the back of the meter box), With the loop, it runs down the wire to the bottom of the loop and drips off - then runs out drainage hole at the bottom of the meter box But, I think that any water that is INSIDE a conduit will continue to flow inside that conduit down into the drip loop then back up and then down again to the lowest point in the conduit down below. If it were water inside a hose, as new water flowed into the hose at the top of the hose the water inside the hose would continue flowing down to the lowest point further down at the end of the hose. This would be similar to a sink drain and trap -- where the trap is in effect a "drip loop". Similarly, water on the outside of the sink drain would drip off at the bottom of the trap. But water inside the drain line would continue to flow down to the end of the drain line and would continue past the "drip loop"/trap. The secret is to keep water OUT of the conduit. In the scenario that I had where water was getting inside the conduit and going into the panel, if the conduit had a drip loop in it, I could have cut a small slit in the conduit wrap at the bottom of the drip loop to let the water inside the conduit drip out there rather than continue down into the panel inside the house in the basement. Of course, that would only have been a temporary fix until I corrected the problem of water getting inside the conduct from the meter box. In my case, there was no such drip loop in that part of the conduit (from the bottom of the meter to the panel below inside the house in the basement). There is NEVER a "drip loop" in conduit. |
#164
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Saturday, January 23, 2016 at 10:54:23 AM UTC-5, TomR wrote:
wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. But, I think that any water that is INSIDE a conduit will continue to flow inside that conduit down into the drip loop then back up and then down again to the lowest point in the conduit down below. If it were water inside a hose, as new water flowed into the hose at the top of the hose the water inside the hose would continue flowing down to the lowest point further down at the end of the hose. This would be similar to a sink drain and trap -- where the trap is in effect a "drip loop". Similarly, water on the outside of the sink drain would drip off at the bottom of the trap. But water inside the drain line would continue to flow down to the end of the drain line and would continue past the "drip loop"/trap. In the scenario that I had where water was getting inside the conduit and going into the panel, if the conduit had a drip loop in it, I could have cut a small slit in the conduit wrap at the bottom of the drip loop to let the water inside the conduit drip out there rather than continue down into the panel inside the house in the basement. Of course, that would only have been a temporary fix until I corrected the problem of water getting inside the conduct from the meter box. In my case, there was no such drip loop in that part of the conduit (from the bottom of the meter to the panel below inside the house in the basement). What you describe in your last paragraph is exactly what I did when I had water coming into my panel. There wasn't exactly a "drip loop" but there was a dip in the service cable along its run. When I put a small slit in the outer jacket, water dripped out for a few minutes. I never got water in the panel again. I eventually fixed the root cause of the water getting into the cable and put some silicon adhesive on the slit to seal it up. |
#165
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
wrote in message
... On Sat, 23 Jan 2016 10:54:21 -0500, "TomR" wrote: wrote in message . .. On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. The water is not IN the conduit. It gets into the meter box, and with no drip loop the water runs down the cable into the conduit (which goes out the back of the meter box), With the loop, it runs down the wire to the bottom of the loop and drips off - then runs out drainage hole at the bottom of the meter box. Maybe we are not both talking about the same thing. I am not exactly sure what the term "conduit" means, but in my case I was using the term "conduit" to mean the heavy gauge, gray-wrapped, "service feed" that runs from the bottom of the meter box down into the building and into the top of the electrical panel inside the basement. It is the same kind and gauge of cable as the service drop that comes down along the outside of the building and goes into the top of the meter box. Using my definition of "conduit" to mean that cable that runs from the bottom of meter box down into the building and into the top of the panel, my "conduit" DID have water running INSIDE that conduit and into the panel. The water was not running down the outside of the "conduit", it was INSIDE the gray-wrapped cable and came out of the inside of that gray-wrapped cable and dripped into the panel. But, I think that any water that is INSIDE a conduit will continue to flow inside that conduit down into the drip loop then back up and then down again to the lowest point in the conduit down below. If it were water inside a hose, as new water flowed into the hose at the top of the hose the water inside the hose would continue flowing down to the lowest point further down at the end of the hose. This would be similar to a sink drain and trap -- where the trap is in effect a "drip loop". Similarly, water on the outside of the sink drain would drip off at the bottom of the trap. But water inside the drain line would continue to flow down to the end of the drain line and would continue past the "drip loop"/trap. The secret is to keep water OUT of the conduit. Yes, of course In the scenario that I had where water was getting inside the conduit and going into the panel, if the conduit had a drip loop in it, I could have cut a small slit in the conduit wrap at the bottom of the drip loop to let the water inside the conduit drip out there rather than continue down into the panel inside the house in the basement. Of course, that would only have been a temporary fix until I corrected the problem of water getting inside the conduct from the meter box. In my case, there was no such drip loop in that part of the conduit (from the bottom of the meter to the panel below inside the house in the basement). There is NEVER a "drip loop" in conduit. I thought that you wrote earlier that there must be a drip loop in the conduit that I was describing as part of the code requirements when you wrote, That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. But, maybe we were talking about two different things. |
#166
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
"DerbyDad03" wrote in message
... On Saturday, January 23, 2016 at 10:54:23 AM UTC-5, TomR wrote: wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. But, I think that any water that is INSIDE a conduit will continue to flow inside that conduit down into the drip loop then back up and then down again to the lowest point in the conduit down below. If it were water inside a hose, as new water flowed into the hose at the top of the hose the water inside the hose would continue flowing down to the lowest point further down at the end of the hose. This would be similar to a sink drain and trap -- where the trap is in effect a "drip loop". Similarly, water on the outside of the sink drain would drip off at the bottom of the trap. But water inside the drain line would continue to flow down to the end of the drain line and would continue past the "drip loop"/trap. In the scenario that I had where water was getting inside the conduit and going into the panel, if the conduit had a drip loop in it, I could have cut a small slit in the conduit wrap at the bottom of the drip loop to let the water inside the conduit drip out there rather than continue down into the panel inside the house in the basement. Of course, that would only have been a temporary fix until I corrected the problem of water getting inside the conduct from the meter box. In my case, there was no such drip loop in that part of the conduit (from the bottom of the meter to the panel below inside the house in the basement). What you describe in your last paragraph is exactly what I did when I had water coming into my panel. There wasn't exactly a "drip loop" but there was a dip in the service cable along its run. When I put a small slit in the outer jacket, water dripped out for a few minutes. I never got water in the panel again. I eventually fixed the root cause of the water getting into the cable and put some silicon adhesive on the slit to seal it up. I understand. I wanted to do exactly what you did -- first put a slit in a low point, then later solve the primary problem by keeping the water out of the cable in the first place. But, in my situation there was no horizontal run where I could even bend it a little to create a dip in the service cable where I could cut a slit in the outer jacket. |
#167
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Sat, 23 Jan 2016 19:04:40 -0500, "TomR"
wrote: wrote in message .. . On Sat, 23 Jan 2016 10:54:21 -0500, "TomR" wrote: wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. The water is not IN the conduit. It gets into the meter box, and with no drip loop the water runs down the cable into the conduit (which goes out the back of the meter box), With the loop, it runs down the wire to the bottom of the loop and drips off - then runs out drainage hole at the bottom of the meter box. Maybe we are not both talking about the same thing. I am not exactly sure what the term "conduit" means, but in my case I was using the term "conduit" to mean the heavy gauge, gray-wrapped, "service feed" that runs from the bottom of the meter box down into the building and into the top of the electrical panel inside the basement. It is the same kind and gauge of cable as the service drop that comes down along the outside of the building and goes into the top of the meter box. Using my definition of "conduit" to mean that cable that runs from the bottom of meter box down into the building and into the top of the panel, my "conduit" DID have water running INSIDE that conduit and into the panel. The water was not running down the outside of the "conduit", it was INSIDE the gray-wrapped cable and came out of the inside of that gray-wrapped cable and dripped into the panel. Not what I was talking about at all -- But, I think that any water that is INSIDE a conduit will continue to flow inside that conduit down into the drip loop then back up and then down again to the lowest point in the conduit down below. If it were water inside a hose, as new water flowed into the hose at the top of the hose the water inside the hose would continue flowing down to the lowest point further down at the end of the hose. This would be similar to a sink drain and trap -- where the trap is in effect a "drip loop". Similarly, water on the outside of the sink drain would drip off at the bottom of the trap. But water inside the drain line would continue to flow down to the end of the drain line and would continue past the "drip loop"/trap. The secret is to keep water OUT of the conduit. Yes, of course In the scenario that I had where water was getting inside the conduit and going into the panel, if the conduit had a drip loop in it, I could have cut a small slit in the conduit wrap at the bottom of the drip loop to let the water inside the conduit drip out there rather than continue down into the panel inside the house in the basement. Of course, that would only have been a temporary fix until I corrected the problem of water getting inside the conduct from the meter box. In my case, there was no such drip loop in that part of the conduit (from the bottom of the meter to the panel below inside the house in the basement). There is NEVER a "drip loop" in conduit. I thought that you wrote earlier that there must be a drip loop in the conduit that I was describing as part of the code requirements when you wrote, That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. But, maybe we were talking about two different things. |
#168
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Saturday, January 23, 2016 at 5:40:39 PM UTC-6, DerbyDad03 wrote:
On Saturday, January 23, 2016 at 10:54:23 AM UTC-5, TomR wrote: wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. But, I think that any water that is INSIDE a conduit will continue to flow inside that conduit down into the drip loop then back up and then down again to the lowest point in the conduit down below. If it were water inside a hose, as new water flowed into the hose at the top of the hose the water inside the hose would continue flowing down to the lowest point further down at the end of the hose. This would be similar to a sink drain and trap -- where the trap is in effect a "drip loop". Similarly, water on the outside of the sink drain would drip off at the bottom of the trap. But water inside the drain line would continue to flow down to the end of the drain line and would continue past the "drip loop"/trap. In the scenario that I had where water was getting inside the conduit and going into the panel, if the conduit had a drip loop in it, I could have cut a small slit in the conduit wrap at the bottom of the drip loop to let the water inside the conduit drip out there rather than continue down into the panel inside the house in the basement. Of course, that would only have been a temporary fix until I corrected the problem of water getting inside the conduct from the meter box. In my case, there was no such drip loop in that part of the conduit (from the bottom of the meter to the panel below inside the house in the basement). What you describe in your last paragraph is exactly what I did when I had water coming into my panel. There wasn't exactly a "drip loop" but there was a dip in the service cable along its run. When I put a small slit in the outer jacket, water dripped out for a few minutes. I never got water in the panel again. I eventually fixed the root cause of the water getting into the cable and put some silicon adhesive on the slit to seal it up. I've never had any luck with silicon adhesive, I had to use silicone caulk. snicker ^_^ [8~{} Uncle Sticky Monster |
#169
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On 1/23/2016 7:51 PM, wrote:
On Sat, 23 Jan 2016 19:04:40 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. But, maybe we were talking about two different things. I suspect it is a drip loop, to keep water from rolling down the outside of the cable. Right before the cable goes through the exterior wall. Unlike a drain trap, which works for sewer gasses. -- .. Christopher A. Young learn more about Jesus .. www.lds.org .. .. |
#170
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
|
#171
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Mon, 25 Jan 2016 09:24:56 -0500, "TomR" wrote:
In , typed: On Sat, 23 Jan 2016 19:04:40 -0500, "TomR" wrote: wrote in message ... On Sat, 23 Jan 2016 10:54:21 -0500, "TomR" wrote: wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. The water is not IN the conduit. It gets into the meter box, and with no drip loop the water runs down the cable into the conduit (which goes out the back of the meter box), With the loop, it runs down the wire to the bottom of the loop and drips off - then runs out drainage hole at the bottom of the meter box. Maybe we are not both talking about the same thing. I am not exactly sure what the term "conduit" means, but in my case I was using the term "conduit" to mean the heavy gauge, gray-wrapped, "service feed" that runs from the bottom of the meter box down into the building and into the top of the electrical panel inside the basement. It is the same kind and gauge of cable as the service drop that comes down along the outside of the building and goes into the top of the meter box. Using my definition of "conduit" to mean that cable that runs from the bottom of meter box down into the building and into the top of the panel, my "conduit" DID have water running INSIDE that conduit and into the panel. The water was not running down the outside of the "conduit", it was INSIDE the gray-wrapped cable and came out of the inside of that gray-wrapped cable and dripped into the panel. Not what I was talking about at all -- Sorry to keep dragging this out, and I am not trying to be argumentative, but what WERE you talking about? -- in particular when you used the term "conduit". Thanks. I was talking about inside the meter base - the wires from the meter to inside - which pass through a conduit. The wires MUST droop below the bottom of the conduit inside the meter base before entering the conduit. Frm meter to bottom of meter base and back up to the exit point of the meter base and out through the conduit to the distribution panel/service entrance box. |
#173
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Tuesday, January 26, 2016 at 9:19:32 AM UTC-6, TomR wrote:
To solve my problem, I used clear 100% silicone caulk and I caulked all around the meter box, especially at the top, and around the front cover and anywhere else that water could possibly get in. That fixed the water problem. I have photos somewhere of the meter box, but I can't seem to find them right now. ....but you're not the OP? |
#174
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Tuesday, January 26, 2016 at 10:19:32 AM UTC-5, TomR wrote:
In , typed: On Mon, 25 Jan 2016 09:24:56 -0500, "TomR" wrote: In , typed: On Sat, 23 Jan 2016 19:04:40 -0500, "TomR" wrote: wrote in message ... On Sat, 23 Jan 2016 10:54:21 -0500, "TomR" wrote: wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. The water is not IN the conduit. It gets into the meter box, and with no drip loop the water runs down the cable into the conduit (which goes out the back of the meter box), With the loop, it runs down the wire to the bottom of the loop and drips off - then runs out drainage hole at the bottom of the meter box. Maybe we are not both talking about the same thing. I am not exactly sure what the term "conduit" means, but in my case I was using the term "conduit" to mean the heavy gauge, gray-wrapped, "service feed" that runs from the bottom of the meter box down into the building and into the top of the electrical panel inside the basement. It is the same kind and gauge of cable as the service drop that comes down along the outside of the building and goes into the top of the meter box. Using my definition of "conduit" to mean that cable that runs from the bottom of meter box down into the building and into the top of the panel, my "conduit" DID have water running INSIDE that conduit and into the panel. The water was not running down the outside of the "conduit", it was INSIDE the gray-wrapped cable and came out of the inside of that gray-wrapped cable and dripped into the panel. Not what I was talking about at all -- Sorry to keep dragging this out, and I am not trying to be argumentative, but what WERE you talking about? -- in particular when you used the term "conduit". Thanks. I was talking about inside the meter base - the wires from the meter to inside - which pass through a conduit. The wires MUST droop below the bottom of the conduit inside the meter base before entering the conduit. Frm meter to bottom of meter base and back up to the exit point of the meter base and out through the conduit to the distribution panel/service entrance box. Okay, got it. My electric meter is on the side of the house and has a service line coming down into the top of the meter box, and a service line coming out of the bottom of the meter box and going down the wall and into the house to the electric panel. Water was getting in through the top of the meter box, filling up in the bottom of the meter box, and then running INSIDE the service cable that comes out of the bottom of the meter box. I wasn't able to open the meter box because it requires a special key, and the utility company was unwilling to come out and open it for me. So, I was never able to see if there are any drip loops inside the meter box, but I doubt that there could be since the service line comes out of the bottom of the meter box. I just did a Google Images search of "electric service meters" and I saw lots of images of the inside of the meter boxes with no drip loop inside. To solve my problem, I used clear 100% silicone caulk and I caulked all around the meter box, especially at the top, and around the front cover and anywhere else that water could possibly get in. That fixed the water problem. I have photos somewhere of the meter box, but I can't seem to find them right now. Water in my panel was the main reason that my wife got an $800 bathroom fan. I had just finished installing a new fan/heater unit in her bathroom, complete with a timer switch for the heater and a humidity sensor for the moisture. The fan, the fancy switches, the 12g wire, the 20A breaker, etc. cost me a few hundred bucks. That was fine, she is worth it. ;-) What hurt was when I turned off the main breaker to pull the wires into the panel and then couldn't get the main to reset. I tried about 10 times until I gave up and called an electrician friend. While I was on the phone with him, it decided to finally catch. He said to leave it alone and he'd look at it the next day. After he looked over the panel, we decided that by the time he found a new main breaker for that old box, which was full and a real mess anyway, it was probably time to just replace the panel, get more space, better grounding, etc. When I took the old main breaker apart, all of the interior contacts were covered with rust from the water that had gotten into the panel a few years prior. No wonder I had a hard time resetting it. That's why I like to say that my wife now has an $800 bathroom fan. |
#175
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Tuesday, January 26, 2016 at 12:59:16 PM UTC-5, DerbyDad03 wrote:
When I took the old main breaker apart, all of the interior contacts were covered with rust from the water that had gotten into the panel a few years prior. No wonder I had a hard time resetting it. Just for clarification: Rust? On copper contacts and bus bars? |
#176
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
"DerbyDad03" wrote in message
stuff snipped What hurt was when I turned off the main breaker to pull the wires into the panel and then couldn't get the main to reset. I tried about 10 times until I gave up and called an electrician friend. While I was on the phone with him, it decided to finally catch. He said to leave it alone Pearls of wisdom. and he'd look at it the next day. After he looked over the panel, we decided that by the time he found a new main breaker for that old box, which was full and a real mess anyway, it was probably time to just replace the panel, get more space, better grounding, etc. I am currently in the same position. Was going to do the new panel this last weekend but Mother Nature had other plans. Can't wait to pull the main breaker and Dremel it open. I'll bet it's grim inside the main breaker. When I took the old main breaker apart, all of the interior contacts were covered with rust from the water that had gotten into the panel a few years prior. No wonder I had a hard time resetting it. It's quite a coincidence that both of us are having main breaker troubles. Mine's well over 30 years old so I suppose it was time. I found what was alleged to be NOS (new, old stock) replacement on Ebay but I've been burned by what I call NODS (new old DEAD stock) before. My main breaker seems to be similarly corroded and I wonder if it was water getting it or just condensation damage over the years or or perhaps just inherent vice. Won't know until next week. That's why I like to say that my wife now has an $800 bathroom fan. Did you do the new panel yourself? Sounds like it from the price. I was considering doing it myself but now with the new electronic meters Pepco can tell pretty quickly when you've pulled the meter and they send a crew out to investigate so it's time to do it all nice and legal like. At least now I can install AFCIs on the bedroom and kitchen circuits easily now (weren't enough neutral connections in the old panel). I was thinking of getting a smart panel but their prices really smart. I've been trying to keep the panel load as low as possible until the panel is replaced. Not sure what happens if the main breaker fails but I hope any fireworks are contained inside the circuit box. -- Bobby G. |
#177
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Tue, 26 Jan 2016 09:59:12 -0800 (PST), DerbyDad03
wrote: On Tuesday, January 26, 2016 at 10:19:32 AM UTC-5, TomR wrote: In , typed: On Mon, 25 Jan 2016 09:24:56 -0500, "TomR" wrote: In , typed: On Sat, 23 Jan 2016 19:04:40 -0500, "TomR" wrote: wrote in message ... On Sat, 23 Jan 2016 10:54:21 -0500, "TomR" wrote: wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. The water is not IN the conduit. It gets into the meter box, and with no drip loop the water runs down the cable into the conduit (which goes out the back of the meter box), With the loop, it runs down the wire to the bottom of the loop and drips off - then runs out drainage hole at the bottom of the meter box. Maybe we are not both talking about the same thing. I am not exactly sure what the term "conduit" means, but in my case I was using the term "conduit" to mean the heavy gauge, gray-wrapped, "service feed" that runs from the bottom of the meter box down into the building and into the top of the electrical panel inside the basement. It is the same kind and gauge of cable as the service drop that comes down along the outside of the building and goes into the top of the meter box. Using my definition of "conduit" to mean that cable that runs from the bottom of meter box down into the building and into the top of the panel, my "conduit" DID have water running INSIDE that conduit and into the panel. The water was not running down the outside of the "conduit", it was INSIDE the gray-wrapped cable and came out of the inside of that gray-wrapped cable and dripped into the panel. Not what I was talking about at all -- Sorry to keep dragging this out, and I am not trying to be argumentative, but what WERE you talking about? -- in particular when you used the term "conduit". Thanks. I was talking about inside the meter base - the wires from the meter to inside - which pass through a conduit. The wires MUST droop below the bottom of the conduit inside the meter base before entering the conduit. Frm meter to bottom of meter base and back up to the exit point of the meter base and out through the conduit to the distribution panel/service entrance box. Okay, got it. My electric meter is on the side of the house and has a service line coming down into the top of the meter box, and a service line coming out of the bottom of the meter box and going down the wall and into the house to the electric panel. Water was getting in through the top of the meter box, filling up in the bottom of the meter box, and then running INSIDE the service cable that comes out of the bottom of the meter box. I wasn't able to open the meter box because it requires a special key, and the utility company was unwilling to come out and open it for me. So, I was never able to see if there are any drip loops inside the meter box, but I doubt that there could be since the service line comes out of the bottom of the meter box. I just did a Google Images search of "electric service meters" and I saw lots of images of the inside of the meter boxes with no drip loop inside. To solve my problem, I used clear 100% silicone caulk and I caulked all around the meter box, especially at the top, and around the front cover and anywhere else that water could possibly get in. That fixed the water problem. I have photos somewhere of the meter box, but I can't seem to find them right now. Water in my panel was the main reason that my wife got an $800 bathroom fan. I had just finished installing a new fan/heater unit in her bathroom, complete with a timer switch for the heater and a humidity sensor for the moisture. The fan, the fancy switches, the 12g wire, the 20A breaker, etc. cost me a few hundred bucks. That was fine, she is worth it. ;-) What hurt was when I turned off the main breaker to pull the wires into the panel and then couldn't get the main to reset. I tried about 10 times until I gave up and called an electrician friend. While I was on the phone with him, it decided to finally catch. He said to leave it alone and he'd look at it the next day. After he looked over the panel, we decided that by the time he found a new main breaker for that old box, which was full and a real mess anyway, it was probably time to just replace the panel, get more space, better grounding, etc. When I took the old main breaker apart, all of the interior contacts were covered with rust from the water that had gotten into the panel a few years prior. No wonder I had a hard time resetting it. That's why I like to say that my wife now has an $800 bathroom fan. You got off cheap. My panel replacement, including permits and inspections, came to just over $3000. I went with a Square D QO 32 slot 125 amp panel plus 1 arc fault and 2 2 pole GFIs - and it was all aluminum wiring - which had to be inspected throughout. |
#178
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
On Tuesday, January 26, 2016 at 9:19:32 AM UTC-6, TomR wrote:
In , typed: On Mon, 25 Jan 2016 09:24:56 -0500, "TomR" wrote: In , typed: On Sat, 23 Jan 2016 19:04:40 -0500, "TomR" wrote: wrote in message ... On Sat, 23 Jan 2016 10:54:21 -0500, "TomR" wrote: wrote in message ... On Fri, 22 Jan 2016 23:35:44 -0500, "TomR" wrote: That's what the "drip loop" is there for. Around here if the inspector doesn't find that "drip loop" he is very likely to give you a deficiency report. On the property where I had the water-inside-panel problem, there is a drip loop up at the top of what I think maybe is called the mast head (or something like that), where the power line from the pole meets the service drop that goes down into the top of the meter box. Where it comes out of the bottom of the meter box, there is no drip loop. It just runs down into the building and into the top of the electric panel. I don't know that I have ever seen a drip loop on that part of the service line coming into a building (below the meter), but I never really looked carefully to see if there is a drip loop there. Since the water was coming from inside the meter box (getting in through the top of the meter box), and was running INSIDE the wire going from there to the panel, I don't know if a drip loop in that line would have prevented the problem of water getting into the panel inside the house. If the wire from the meter droops below the conduit exiting the meter box to the inside of the building, water cannot follow the wire into the building and into the panel. I may be wrong about this, but I think the purpose of a drip loop is to have water that is on the outside of the wire drip off at the low point of the loop rather than running down on the outside of the wire into a structure etc. The water is not IN the conduit. It gets into the meter box, and with no drip loop the water runs down the cable into the conduit (which goes out the back of the meter box), With the loop, it runs down the wire to the bottom of the loop and drips off - then runs out drainage hole at the bottom of the meter box. Maybe we are not both talking about the same thing. I am not exactly sure what the term "conduit" means, but in my case I was using the term "conduit" to mean the heavy gauge, gray-wrapped, "service feed" that runs from the bottom of the meter box down into the building and into the top of the electrical panel inside the basement. It is the same kind and gauge of cable as the service drop that comes down along the outside of the building and goes into the top of the meter box. Using my definition of "conduit" to mean that cable that runs from the bottom of meter box down into the building and into the top of the panel, my "conduit" DID have water running INSIDE that conduit and into the panel. The water was not running down the outside of the "conduit", it was INSIDE the gray-wrapped cable and came out of the inside of that gray-wrapped cable and dripped into the panel. Not what I was talking about at all -- Sorry to keep dragging this out, and I am not trying to be argumentative, but what WERE you talking about? -- in particular when you used the term "conduit". Thanks. I was talking about inside the meter base - the wires from the meter to inside - which pass through a conduit. The wires MUST droop below the bottom of the conduit inside the meter base before entering the conduit. Frm meter to bottom of meter base and back up to the exit point of the meter base and out through the conduit to the distribution panel/service entrance box. Okay, got it. My electric meter is on the side of the house and has a service line coming down into the top of the meter box, and a service line coming out of the bottom of the meter box and going down the wall and into the house to the electric panel. Water was getting in through the top of the meter box, filling up in the bottom of the meter box, and then running INSIDE the service cable that comes out of the bottom of the meter box. I wasn't able to open the meter box because it requires a special key, and the utility company was unwilling to come out and open it for me. So, I was never able to see if there are any drip loops inside the meter box, but I doubt that there could be since the service line comes out of the bottom of the meter box. I just did a Google Images search of "electric service meters" and I saw lots of images of the inside of the meter boxes with no drip loop inside. To solve my problem, I used clear 100% silicone caulk and I caulked all around the meter box, especially at the top, and around the front cover and anywhere else that water could possibly get in. That fixed the water problem. I have photos somewhere of the meter box, but I can't seem to find them right now. Standard practice around here is to use gray duct seal which is like modeling clay in texture to build a cone around the SE cable where it enters the connector at the top of the meter box. This keeps any water from seeping between the SE cable and the rubber grommet in the compression connector. Inside the meter box, there are small drain holes in the back corners of the bottom of the meter box usually from the factory that should be kept open. If there were no holes, I'd drill a 1/8" hole in those locations. Those weep holes can become plugged if calk is run across the bottom of the meter box.. I always ran a bead of calk across the top and sides of the meter box but not across the bottom so that no water could get trapped between the box and the wall. ^_^ [8~{} Uncle Meter Monster |
#179
Posted to alt.home.repair
|
|||
|
|||
SOLVED! Circuit breaker keeps tripping
In ,
Uncle Monster typed: On Tuesday, January 26, 2016 at 9:19:32 AM UTC-6, TomR wrote: Water was getting in through the top of the meter box, filling up in the bottom of the meter box, and then running INSIDE the service cable that comes out of the bottom of the meter box. I wasn't able to open the meter box because it requires a special key, and the utility company was unwilling to come out and open it for me. So, I was never able to see if there are any drip loops inside the meter box, but I doubt that there could be since the service line comes out of the bottom of the meter box. I just did a Google Images search of "electric service meters" and I saw lots of images of the inside of the meter boxes with no drip loop inside. To solve my problem, I used clear 100% silicone caulk and I caulked all around the meter box, especially at the top, and around the front cover and anywhere else that water could possibly get in. That fixed the water problem. I have photos somewhere of the meter box, but I can't seem to find them right now. Standard practice around here is to use gray duct seal which is like modeling clay in texture to build a cone around the SE cable where it enters the connector at the top of the meter box. This keeps any water from seeping between the SE cable and the rubber grommet in the compression connector. Inside the meter box, there are small drain holes in the back corners of the bottom of the meter box usually from the factory that should be kept open. If there were no holes, I'd drill a 1/8" hole in those locations. Those weep holes can become plugged if calk is run across the bottom of the meter box. I always ran a bead of calk across the top and sides of the meter box but not across the bottom so that no water could get trapped between the box and the wall. ^_^ Thanks. I did do the gray duct seal routine back then and, in addition, I did the clear 100% silicone caulk routine. Yesterday, I was able to find the old thread that I started here regarding that problem back in 2013. The topic of the thread was "Unlocking electric meter box -- water problem", and it was started by me (TomR) on 6/8/2013 at 3:16 PM Eastern Time. Looking back, I now remember that the water that was getting into the box was not getting into the wire coming out of the bottom due to the box filling with water at the bottom (as I wrote above). I know that because in re-reading the thread I realize that I did put a drain hole in the bottom of the box and that didn't correct the problem of water gett into the electric panel. The problem that I had at the time was that I could not open the meter box to look inside and see what was going on. The box cover had a special locking mechanism on it that I couldn't unlock. Either the utility company or an electrician with a special tool could have unlocked the front box cover. The utility company refused to do that for me, and I didn't want to hire an electrican just to open the box and look inside. So, the solution that I was left with was to first just try sealing and caulking the box completely from the outside, and that worked. I assume that the water that was previously getting into the box was somehow running down the wires and into the INSIDE of the cable that comes out of the bottom of the box. But, since I couldn't open the box, I could not verify exactly what was going on inside the box. I just know that my sealing and caulking routine on th eoutside of the box solved the problem. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Dryer keeps tripping the circuit breaker | Home Repair | |||
Circuit Breaker Tripping | Home Repair | |||
A/C Unit Keeps Tripping Circuit Breaker - How to test breaker before calling repair man? | Home Repair | |||
DC tripping circuit breaker | Woodworking | |||
a/c tripping circuit breaker | Electronics Repair |