Past Wiring Codes
In my early 1950s house, I decided to upgrade the bathroom
outlet fixture to a GFCI, 20-amp circuit. When removing the old, metal outlet box, I found that the ground wire to the outlet was connected to a screw in the back of the box. The separate bare wire coming down from the attic, was "connected" to the box by a couple of turns around one of the nails holding the box to the stud! This surely wouldn't meet any code in the USA today (I don't think), but it was obviously not a modification. So either it met code at construction-time, or it was not properly inspected during construction. I'm curios as to which situation was true. -- croy |
#2
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On 11/11/2012 3:23 PM, croy wrote:
.... So either it met code at construction-time, or it was not properly inspected during construction. I'm curios as to which situation was true. Neither--it of course would never be Code-compliant; it probably never saw an inspector specifically. -- |
#3
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
"croy" wrote in message ... In my early 1950s house, I decided to upgrade the bathroom outlet fixture to a GFCI, 20-amp circuit. When removing the old, metal outlet box, I found that the ground wire to the outlet was connected to a screw in the back of the box. The separate bare wire coming down from the attic, was "connected" to the box by a couple of turns around one of the nails holding the box to the stud! This surely wouldn't meet any code in the USA today (I don't think), but it was obviously not a modification. So either it met code at construction-time, or it was not properly inspected during construction. I'm curios as to which situation was true. -- croy One thing the electrical codes have always required is an "approved" connection whether soldered, clamped, twisted (via a wire nut) or screw. Wrapping a wire around a steel nail, which could rust, would never have made it. The intent, of course, is to have a reliable connection from the box to ground. Tomsic |
#4
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Sun, 11 Nov 2012 13:23:05 -0800, croy wrote:
In my early 1950s house, I decided to upgrade the bathroom outlet fixture to a GFCI, 20-amp circuit. When removing the old, metal outlet box, I found that the ground wire to the outlet was connected to a screw in the back of the box. The separate bare wire coming down from the attic, was "connected" to the box by a couple of turns around one of the nails holding the box to the stud! This surely wouldn't meet any code in the USA today (I don't think), but it was obviously not a modification. So either it met code at construction-time, or it was not properly inspected during construction. I'm curios as to which situation was true. A lot of the older metal boxes did not have threaded holes for ground screws. So, using a nail was all that was possible, unril they came out with the clamps that snap over the edge if the box. If the nail is tight, it's likely a good ground, but not allowed by code. In the past, if I've had to work on old wiring and boxes without ground screw holes, I opted to use a screw in place of a nail, and put a washer under the screw head. Then wrap the wire under that washer. Again, it's not allowed by code, but it works. I dont know what was allowed by code in the old days, but there are probably millions of boxes grounded just on a nail. Remember, the old wiring did not use grounds, so it's not always easy to upgrade without ripping out walls and stuff. The correct way would be to drill a hole in the box, thread it, and insert a ground screw. |
#5
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On 11/11/2012 06:06 PM, .-. wrote:
"croy" wrote in message ... In my early 1950s house, I decided to upgrade the bathroom outlet fixture to a GFCI, 20-amp circuit. When removing the old, metal outlet box, I found that the ground wire to the outlet was connected to a screw in the back of the box. The separate bare wire coming down from the attic, was "connected" to the box by a couple of turns around one of the nails holding the box to the stud! This surely wouldn't meet any code in the USA today (I don't think), but it was obviously not a modification. So either it met code at construction-time, or it was not properly inspected during construction. I'm curios as to which situation was true. -- croy One thing the electrical codes have always required is an "approved" connection whether soldered, clamped, twisted (via a wire nut) or screw. Wrapping a wire around a steel nail, which could rust, would never have made it. The intent, of course, is to have a reliable connection from the box to ground. Tomsic When was the requirement for the boxes to be grounded actually introduced? I'm just curious - my data point, house built in 1947 or 48 did not have any grounded boxes other than those provided by connection to BX (house was a mix of exposed BX and concealed "rag" wiring.) Clearly if an "early 1950s" house had grounds, it was somewhere in that time frame that it was introduced. nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#7
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
"Nate Nagel" wrote in message ... On 11/11/2012 06:06 PM, .-. wrote: "croy" wrote in message ... In my early 1950s house, I decided to upgrade the bathroom outlet fixture to a GFCI, 20-amp circuit. When removing the old, metal outlet box, I found that the ground wire to the outlet was connected to a screw in the back of the box. The separate bare wire coming down from the attic, was "connected" to the box by a couple of turns around one of the nails holding the box to the stud! This surely wouldn't meet any code in the USA today (I don't think), but it was obviously not a modification. So either it met code at construction-time, or it was not properly inspected during construction. I'm curios as to which situation was true. -- croy One thing the electrical codes have always required is an "approved" connection whether soldered, clamped, twisted (via a wire nut) or screw. Wrapping a wire around a steel nail, which could rust, would never have made it. The intent, of course, is to have a reliable connection from the box to ground. Tomsic When was the requirement for the boxes to be grounded actually introduced? I'm just curious - my data point, house built in 1947 or 48 did not have any grounded boxes other than those provided by connection to BX (house was a mix of exposed BX and concealed "rag" wiring.) Clearly if an "early 1950s" house had grounds, it was somewhere in that time frame that it was introduced. nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel Your "1950s" date sounds right, Nate. I don't have copies of the National Electrical Code that go back that far, but that's when I remember 3-prong outlets appearing. It took a while to change practice however. I had a house that was built in 1958 that was wired with knob and tube - no ground wires in that. Tomsic |
#8
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Sun, 11 Nov 2012 20:13:39 -0500, Nate Nagel
wrote: which is not hard; Klein makes a tap tool with a screwdriver handle for just this purpose. Have used it quite a few times for just this application. (trying to use a standard tap with T-handle is difficult due to the depth of the boxes, but you don't need a whole lot of torque to thread the steel of a typical electrical box.) That sounds like a handy tool. I would, however, splice the ground wires on the cables entering the box together, along with a long bare pigtail of the proper gauge, with a wire nut. The pigtail then loops under the box's ground screw and then is connected to the ground terminal of the device installed in the box. If both of the ground wires coming from the cables are long enough, you could loop one under the box's ground screw, the other under the device's terminal, then splice with wire nut. This way all connections are good and proper, and you don't have to mess with BS like trying to shove two short wires under a single screw without a Sta-Kon. The problem with old wiring is that there is often no bare wires. The wiring is armoured cable (BX), or metal conduit. The conduit is normally a good ground, but only the BX with the bare metal insert in the cable is a decent ground. Aside from ripping the whole house apart, one can only use what exists as a ground. Aside: Why don't spec grade "back wire" devices allow two ground wires to be inserted under a single screw like the hots and neutrals? I fully agree, actually all devices *could* have more than one ground screw to make wiring easier. At least two screws, since probably hanf the outlets and switches feed at least 2 cables. (the source wire and the wire that goes to the next fixture). When I wire a box, I normally make one cable longer, than take the bare and wrap it to the box screw near the entry point (box clamp). Then the end of that bare wire goes to the outlet or device. If there are two or more wires, that means more wirenuts. Which of course fills the box faster and makes wiring harder. nate |
#9
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Sun, 11 Nov 2012 22:24:00 -0500, ".-." wrote:
Your "1950s" date sounds right, Nate. I don't have copies of the National Electrical Code that go back that far, but that's when I remember 3-prong outlets appearing. It took a while to change practice however. I had a house that was built in 1958 that was wired with knob and tube - no ground wires in that. Tomsic My parents house that I was raised in, was built in 1951. It had NO grounded outlets anywhere. The wiring was BX in the walls, and metal EMT conduit in the basement. In the early 60's an electrician added some circuits and put in grounded outlets on the new additional outlets, and more when when a garage was built. When I was in my late teens, I replaced the outlets in the basement by the workbench with grounded ones, because I got sick of using ground adaptors on every power tool. My father would not touch electrical stuff, so he asked me to also change the one by the washer and dryer, and the ones by the kitchen counter. Eventually I changed more of them in the house. This says that it was *after* 1951 that grounded outlets became code. |
#10
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Nov 12, 9:14*am, wrote:
On Sun, 11 Nov 2012 20:13:39 -0500, Nate Nagel wrote: which is not hard; Klein makes a tap tool with a screwdriver handle for just this purpose. *Have used it quite a few times for just this application. *(trying to use a standard tap with T-handle is difficult due to the depth of the boxes, but you don't need a whole lot of torque to thread the steel of a typical electrical box.) That sounds like a handy tool. I would, however, splice the ground wires on the cables entering the box together, along with a long bare pigtail of the proper gauge, with a wire nut. *The pigtail then loops under the box's ground screw and then is connected to the ground terminal of the device installed in the box. *If both of the ground wires coming from the cables are long enough, you could loop one under the box's ground screw, the other under the device's terminal, then splice with wire nut. *This way all connections are good and proper, and you don't have to mess with BS like trying to shove two short wires under a single screw without a Sta-Kon. The problem with old wiring is that there is often no bare wires. *The wiring is armoured cable (BX), or metal conduit. *The conduit is normally a good ground, but only the BX with the bare metal insert in the cable is a decent ground. *Aside from ripping the whole house apart, one can only use what exists as a ground. Aside: Why don't spec grade "back wire" devices allow two ground wires to be inserted under a single screw like the hots and neutrals? I fully agree, actually all devices *could* have more than one ground screw to make wiring easier. *At least two screws, since probably hanf the outlets and switches feed at least 2 cables. *(the source wire and the wire that goes to the next fixture). When I wire a box, I normally make one cable longer, than take the bare and wrap it to the box screw near the entry point (box clamp). *Then the end of that bare wire goes to the outlet or device. *If there are two or more wires, that means more wirenuts. *Which of course fills the box faster and makes wiring harder. My, things are primitive in the USA. |
#11
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On 11/12/2012 4:00 AM, harry wrote:
On Nov 12, 9:14 am, wrote: On Sun, 11 Nov 2012 20:13:39 -0500, Nate Nagel wrote: which is not hard; Klein makes a tap tool with a screwdriver handle for just this purpose. Have used it quite a few times for just this application. (trying to use a standard tap with T-handle is difficult due to the depth of the boxes, but you don't need a whole lot of torque to thread the steel of a typical electrical box.) That sounds like a handy tool. I would, however, splice the ground wires on the cables entering the box together, along with a long bare pigtail of the proper gauge, with a wire nut. The pigtail then loops under the box's ground screw and then is connected to the ground terminal of the device installed in the box. If both of the ground wires coming from the cables are long enough, you could loop one under the box's ground screw, the other under the device's terminal, then splice with wire nut. This way all connections are good and proper, and you don't have to mess with BS like trying to shove two short wires under a single screw without a Sta-Kon. The problem with old wiring is that there is often no bare wires. The wiring is armoured cable (BX), or metal conduit. The conduit is normally a good ground, but only the BX with the bare metal insert in the cable is a decent ground. Aside from ripping the whole house apart, one can only use what exists as a ground. Aside: Why don't spec grade "back wire" devices allow two ground wires to be inserted under a single screw like the hots and neutrals? I fully agree, actually all devices *could* have more than one ground screw to make wiring easier. At least two screws, since probably hanf the outlets and switches feed at least 2 cables. (the source wire and the wire that goes to the next fixture). When I wire a box, I normally make one cable longer, than take the bare and wrap it to the box screw near the entry point (box clamp). Then the end of that bare wire goes to the outlet or device. If there are two or more wires, that means more wirenuts. Which of course fills the box faster and makes wiring harder. My, things are primitive in the USA. Yea, I'm having a heck of a time with this hand cranked computer and carrier pigeons carrying IP packets back and forth from my service provider. O_o TDD |
#12
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Mon, 12 Nov 2012 05:52:57 -0600, The Daring Dufas
wrote: My, things are primitive in the USA. Yea, I'm having a heck of a time with this hand cranked computer and carrier pigeons carrying IP packets back and forth from my service provider. O_o TDD I use two metal soup cans and over 20 miles of string between them. I hear my data one byte at a time, write it down, and wait for the next byte. When I get all the bytes, I have to punch them into punch cards and put the card into a punch card reader. After half a day, I get a printed black and white photo of someone. This high technology is real amazing. I hear someday they will run that string across the ocean. I'm not sure why, but I bet it's so we can listen to fish talk to each other. |
#13
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On 11/11/2012 7:13 PM, Nate Nagel wrote:
Aside: Why don't spec grade "back wire" devices allow two ground wires to be inserted under a single screw like the hots and neutrals? My guess is that if you replace the receptacle while the circuit is live you break the ground downstream. The same is true of the neutral. You can have a "hot" neutral or ground downstream. A hot neutral is not likely to be a problem (except for the person changing the receptacle). A hot ground, even for a short time, can be fatal. For multiwire (Edison) circuits you are not allowed to connect the neutral through the receptacle. It has to be spliced separately, and a single neutral wire connects to the receptacle. If replace the receptacle hot, and break the neutral, one downstream leg-to-neutral can wind up at 240V and the other 0V. |
#14
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
|
#16
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
|
#17
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Mon, 12 Nov 2012 18:47:48 -0800, Bob wrote:
On 11/12/2012 01:29, wrote: This says that it was *after* 1951 that grounded outlets became code. The 1962 NEC was the first to require all outlets to be grounded. Thank you. I didn't think it was till around 1960. |
#18
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Monday, November 12, 2012 6:47:43 PM UTC-8, Bob wrote:
On 11/12/2012 01:29, wrote: This says that it was *after* 1951 that grounded outlets became code. The 1962 NEC was the first to require all outlets to be grounded. So why then aren't all plugs required to be 3-prong? Unless you have a 3-prong plug, it doesn't really matter whether you have a grounded outlet or not. My 1957 rental came with wierd triple outlet with obviously no ground. They are polorized, though. |
#19
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
|
#20
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Tue, 13 Nov 2012 05:58:31 -0800 (PST), wrote:
On Monday, November 12, 2012 6:47:43 PM UTC-8, Bob wrote: On 11/12/2012 01:29, wrote: This says that it was *after* 1951 that grounded outlets became code. The 1962 NEC was the first to require all outlets to be grounded. So why then aren't all plugs required to be 3-prong? You're going to ground a plastic clock? (Yes, I know one "safety inspector" who required it) You've never heard of "double insulated"? Unless you have a 3-prong plug, it doesn't really matter whether you have a grounded outlet or not. You have *no* 3-prong plugs? My 1957 rental came with wierd triple outlet with obviously no ground. Outlets replaced somewhere along the line? They are polorized, though. So are modern two-pronged plugs and three-pronged outlets (without using the ground pin). |
#21
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
|
#22
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Sun, 18 Nov 2012 12:36:57 -0500, wrote:
On Sun, 18 Nov 2012 12:14:40 -0500, z wrote: Grounds are not supposed to be daisy-chained (neither are neutrals). You can chain a neutral through a device unless it is a multiwire circuit. There is no rule at all about grounding conductors beyond "Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems." If the device manufacturer provides 2 screws, you can chain through that device. It is common to see the ground looped through the single screw and continuing on to the next one. I didn't say that it wasn't to code. OTOH, it's terrible practice. An inspector I had would have failed me for using both neutral screws. He probably would have condemned the place had I daisy-chained grounds. |
#23
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
So why then aren't all plugs required to be 3-prong? You're going to ground a plastic clock? (Yes, I know one "safety inspector" who required it) Should have been clearer--I meant extension cord plugs. |
#24
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Nov 19, 3:49*pm, wrote:
So why then aren't all plugs required to be 3-prong? You're going to ground a plastic clock? *(Yes, I know one "safety inspector" who required it) Should have been clearer--I meant extension cord plugs. So you can use it with your plastic clock. |
#25
Posted to alt.home.repair
|
|||
|
|||
Past Wiring Codes
On Mon, 19 Nov 2012 12:49:57 -0800 (PST), wrote:
So why then aren't all plugs required to be 3-prong? You're going to ground a plastic clock? (Yes, I know one "safety inspector" who required it) Should have been clearer--I meant extension cord plugs. OK, let me change the answer to "because it's not necessary". |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
G-codes past RS-274 a waste? | Metalworking | |||
What wiring codes say about these wires? | Home Repair | |||
What wiring codes say about these wires? | Home Repair | |||
1950s German appliance wiring colour codes | UK diy | |||
RGB monitor input wiring color codes | Electronics Repair |