In my early 1950s house, I decided to upgrade the bathroom
outlet fixture to a GFCI, 20-amp circuit.

When removing the old, metal outlet box, I found that the
ground wire to the outlet was connected to a screw in the
back of the box. The separate bare wire coming down from
the attic, was "connected" to the box by a couple of turns
around one of the nails holding the box to the stud!

This surely wouldn't meet any code in the USA today (I don't
think), but it was obviously not a modification.

So either it met code at construction-time, or it was not
properly inspected during construction.

I'm curios as to which situation was true.

--
croy
  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Past Wiring Codes

On 11/11/2012 3:23 PM, croy wrote:
....

So either it met code at construction-time, or it was not
properly inspected during construction.

I'm curios as to which situation was true.


Neither--it of course would never be Code-compliant; it probably never
saw an inspector specifically.

--
  #3   Report Post  
Posted to alt.home.repair
.-. .-. is offline
external usenet poster
 
Posts: 24
Default Past Wiring Codes


"croy" wrote in message
...
In my early 1950s house, I decided to upgrade the bathroom
outlet fixture to a GFCI, 20-amp circuit.

When removing the old, metal outlet box, I found that the
ground wire to the outlet was connected to a screw in the
back of the box. The separate bare wire coming down from
the attic, was "connected" to the box by a couple of turns
around one of the nails holding the box to the stud!

This surely wouldn't meet any code in the USA today (I don't
think), but it was obviously not a modification.

So either it met code at construction-time, or it was not
properly inspected during construction.

I'm curios as to which situation was true.

--
croy


One thing the electrical codes have always required is an "approved"
connection whether soldered, clamped, twisted (via a wire nut) or screw.
Wrapping a wire around a steel nail, which could rust, would never have made
it. The intent, of course, is to have a reliable connection from the box to
ground.

Tomsic


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Past Wiring Codes

On 11/11/2012 06:06 PM, .-. wrote:

"croy" wrote in message
...
In my early 1950s house, I decided to upgrade the bathroom
outlet fixture to a GFCI, 20-amp circuit.

When removing the old, metal outlet box, I found that the
ground wire to the outlet was connected to a screw in the
back of the box. The separate bare wire coming down from
the attic, was "connected" to the box by a couple of turns
around one of the nails holding the box to the stud!

This surely wouldn't meet any code in the USA today (I don't
think), but it was obviously not a modification.

So either it met code at construction-time, or it was not
properly inspected during construction.

I'm curios as to which situation was true.

--
croy


One thing the electrical codes have always required is an "approved"
connection whether soldered, clamped, twisted (via a wire nut) or screw.
Wrapping a wire around a steel nail, which could rust, would never have made
it. The intent, of course, is to have a reliable connection from the box to
ground.

Tomsic



When was the requirement for the boxes to be grounded actually
introduced? I'm just curious - my data point, house built in 1947 or 48
did not have any grounded boxes other than those provided by connection
to BX (house was a mix of exposed BX and concealed "rag" wiring.)
Clearly if an "early 1950s" house had grounds, it was somewhere in that
time frame that it was introduced.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #5   Report Post  
Posted to alt.home.repair
.-. .-. is offline
external usenet poster
 
Posts: 24
Default Past Wiring Codes


"Nate Nagel" wrote in message
...
On 11/11/2012 06:06 PM, .-. wrote:

"croy" wrote in message
...
In my early 1950s house, I decided to upgrade the bathroom
outlet fixture to a GFCI, 20-amp circuit.

When removing the old, metal outlet box, I found that the
ground wire to the outlet was connected to a screw in the
back of the box. The separate bare wire coming down from
the attic, was "connected" to the box by a couple of turns
around one of the nails holding the box to the stud!

This surely wouldn't meet any code in the USA today (I don't
think), but it was obviously not a modification.

So either it met code at construction-time, or it was not
properly inspected during construction.

I'm curios as to which situation was true.

--
croy


One thing the electrical codes have always required is an "approved"
connection whether soldered, clamped, twisted (via a wire nut) or screw.
Wrapping a wire around a steel nail, which could rust, would never have
made
it. The intent, of course, is to have a reliable connection from the box
to
ground.

Tomsic



When was the requirement for the boxes to be grounded actually introduced?
I'm just curious - my data point, house built in 1947 or 48 did not have
any grounded boxes other than those provided by connection to BX (house
was a mix of exposed BX and concealed "rag" wiring.) Clearly if an "early
1950s" house had grounds, it was somewhere in that time frame that it was
introduced.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel


Your "1950s" date sounds right, Nate. I don't have copies of the National
Electrical Code that go back that far, but that's when I remember 3-prong
outlets appearing. It took a while to change practice however. I had a
house that was built in 1958 that was wired with knob and tube - no ground
wires in that.

Tomsic




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 294
Default Past Wiring Codes

On Sun, 11 Nov 2012 22:24:00 -0500, ".-." wrote:


Your "1950s" date sounds right, Nate. I don't have copies of the National
Electrical Code that go back that far, but that's when I remember 3-prong
outlets appearing. It took a while to change practice however. I had a
house that was built in 1958 that was wired with knob and tube - no ground
wires in that.

Tomsic


My parents house that I was raised in, was built in 1951. It had NO
grounded outlets anywhere. The wiring was BX in the walls, and metal
EMT conduit in the basement. In the early 60's an electrician added
some circuits and put in grounded outlets on the new additional outlets,
and more when when a garage was built. When I was in my late teens, I
replaced the outlets in the basement by the workbench with grounded
ones, because I got sick of using ground adaptors on every power tool.
My father would not touch electrical stuff, so he asked me to also
change the one by the washer and dryer, and the ones by the kitchen
counter. Eventually I changed more of them in the house.

This says that it was *after* 1951 that grounded outlets became code.

  #7   Report Post  
Posted to alt.home.repair
Bob Bob is offline
external usenet poster
 
Posts: 99
Default Past Wiring Codes

On 11/12/2012 01:29, wrote:

This says that it was *after* 1951 that grounded outlets became code.


The 1962 NEC was the first to require all outlets to be grounded.


  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 294
Default Past Wiring Codes

On Sun, 11 Nov 2012 13:23:05 -0800, croy wrote:

In my early 1950s house, I decided to upgrade the bathroom
outlet fixture to a GFCI, 20-amp circuit.

When removing the old, metal outlet box, I found that the
ground wire to the outlet was connected to a screw in the
back of the box. The separate bare wire coming down from
the attic, was "connected" to the box by a couple of turns
around one of the nails holding the box to the stud!

This surely wouldn't meet any code in the USA today (I don't
think), but it was obviously not a modification.

So either it met code at construction-time, or it was not
properly inspected during construction.

I'm curios as to which situation was true.


A lot of the older metal boxes did not have threaded holes for ground
screws. So, using a nail was all that was possible, unril they came out
with the clamps that snap over the edge if the box. If the nail is
tight, it's likely a good ground, but not allowed by code. In the past,
if I've had to work on old wiring and boxes without ground screw holes,
I opted to use a screw in place of a nail, and put a washer under the
screw head. Then wrap the wire under that washer. Again, it's not
allowed by code, but it works.

I dont know what was allowed by code in the old days, but there are
probably millions of boxes grounded just on a nail. Remember, the old
wiring did not use grounds, so it's not always easy to upgrade without
ripping out walls and stuff.

The correct way would be to drill a hole in the box, thread it, and
insert a ground screw.

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Past Wiring Codes

On 11/11/2012 07:48 PM, wrote:
On Sun, 11 Nov 2012 13:23:05 -0800, croy wrote:

In my early 1950s house, I decided to upgrade the bathroom
outlet fixture to a GFCI, 20-amp circuit.

When removing the old, metal outlet box, I found that the
ground wire to the outlet was connected to a screw in the
back of the box. The separate bare wire coming down from
the attic, was "connected" to the box by a couple of turns
around one of the nails holding the box to the stud!

This surely wouldn't meet any code in the USA today (I don't
think), but it was obviously not a modification.

So either it met code at construction-time, or it was not
properly inspected during construction.

I'm curios as to which situation was true.


A lot of the older metal boxes did not have threaded holes for ground
screws. So, using a nail was all that was possible, unril they came out
with the clamps that snap over the edge if the box. If the nail is
tight, it's likely a good ground, but not allowed by code. In the past,
if I've had to work on old wiring and boxes without ground screw holes,
I opted to use a screw in place of a nail, and put a washer under the
screw head. Then wrap the wire under that washer. Again, it's not
allowed by code, but it works.

I dont know what was allowed by code in the old days, but there are
probably millions of boxes grounded just on a nail. Remember, the old
wiring did not use grounds, so it's not always easy to upgrade without
ripping out walls and stuff.

The correct way would be to drill a hole in the box, thread it, and
insert a ground screw.


which is not hard; Klein makes a tap tool with a screwdriver handle for
just this purpose. Have used it quite a few times for just this
application. (trying to use a standard tap with T-handle is difficult
due to the depth of the boxes, but you don't need a whole lot of torque
to thread the steel of a typical electrical box.)

I would, however, splice the ground wires on the cables entering the box
together, along with a long bare pigtail of the proper gauge, with a
wire nut. The pigtail then loops under the box's ground screw and then
is connected to the ground terminal of the device installed in the box.
If both of the ground wires coming from the cables are long enough,
you could loop one under the box's ground screw, the other under the
device's terminal, then splice with wire nut. This way all connections
are good and proper, and you don't have to mess with BS like trying to
shove two short wires under a single screw without a Sta-Kon.

Aside: Why don't spec grade "back wire" devices allow two ground wires
to be inserted under a single screw like the hots and neutrals?

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 294
Default Past Wiring Codes

On Sun, 11 Nov 2012 20:13:39 -0500, Nate Nagel
wrote:

which is not hard; Klein makes a tap tool with a screwdriver handle for
just this purpose. Have used it quite a few times for just this
application. (trying to use a standard tap with T-handle is difficult
due to the depth of the boxes, but you don't need a whole lot of torque
to thread the steel of a typical electrical box.)


That sounds like a handy tool.

I would, however, splice the ground wires on the cables entering the box
together, along with a long bare pigtail of the proper gauge, with a
wire nut. The pigtail then loops under the box's ground screw and then
is connected to the ground terminal of the device installed in the box.
If both of the ground wires coming from the cables are long enough,
you could loop one under the box's ground screw, the other under the
device's terminal, then splice with wire nut. This way all connections
are good and proper, and you don't have to mess with BS like trying to
shove two short wires under a single screw without a Sta-Kon.


The problem with old wiring is that there is often no bare wires. The
wiring is armoured cable (BX), or metal conduit. The conduit is
normally a good ground, but only the BX with the bare metal insert in
the cable is a decent ground. Aside from ripping the whole house apart,
one can only use what exists as a ground.


Aside: Why don't spec grade "back wire" devices allow two ground wires
to be inserted under a single screw like the hots and neutrals?


I fully agree, actually all devices *could* have more than one ground
screw to make wiring easier. At least two screws, since probably hanf
the outlets and switches feed at least 2 cables. (the source wire and
the wire that goes to the next fixture).

When I wire a box, I normally make one cable longer, than take the bare
and wrap it to the box screw near the entry point (box clamp). Then the
end of that bare wire goes to the outlet or device. If there are two or
more wires, that means more wirenuts. Which of course fills the box
faster and makes wiring harder.

nate





  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 9,066
Default Past Wiring Codes

On Nov 12, 9:14*am, wrote:
On Sun, 11 Nov 2012 20:13:39 -0500, Nate Nagel
wrote:

which is not hard; Klein makes a tap tool with a screwdriver handle for
just this purpose. *Have used it quite a few times for just this
application. *(trying to use a standard tap with T-handle is difficult
due to the depth of the boxes, but you don't need a whole lot of torque
to thread the steel of a typical electrical box.)


That sounds like a handy tool.



I would, however, splice the ground wires on the cables entering the box
together, along with a long bare pigtail of the proper gauge, with a
wire nut. *The pigtail then loops under the box's ground screw and then
is connected to the ground terminal of the device installed in the box.
*If both of the ground wires coming from the cables are long enough,
you could loop one under the box's ground screw, the other under the
device's terminal, then splice with wire nut. *This way all connections
are good and proper, and you don't have to mess with BS like trying to
shove two short wires under a single screw without a Sta-Kon.


The problem with old wiring is that there is often no bare wires. *The
wiring is armoured cable (BX), or metal conduit. *The conduit is
normally a good ground, but only the BX with the bare metal insert in
the cable is a decent ground. *Aside from ripping the whole house apart,
one can only use what exists as a ground.

Aside: Why don't spec grade "back wire" devices allow two ground wires
to be inserted under a single screw like the hots and neutrals?


I fully agree, actually all devices *could* have more than one ground
screw to make wiring easier. *At least two screws, since probably hanf
the outlets and switches feed at least 2 cables. *(the source wire and
the wire that goes to the next fixture).

When I wire a box, I normally make one cable longer, than take the bare
and wrap it to the box screw near the entry point (box clamp). *Then the
end of that bare wire goes to the outlet or device. *If there are two or
more wires, that means more wirenuts. *Which of course fills the box
faster and makes wiring harder.

My, things are primitive in the USA.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,463
Default Past Wiring Codes

On 11/12/2012 4:00 AM, harry wrote:
On Nov 12, 9:14 am, wrote:
On Sun, 11 Nov 2012 20:13:39 -0500, Nate Nagel
wrote:

which is not hard; Klein makes a tap tool with a screwdriver handle for
just this purpose. Have used it quite a few times for just this
application. (trying to use a standard tap with T-handle is difficult
due to the depth of the boxes, but you don't need a whole lot of torque
to thread the steel of a typical electrical box.)


That sounds like a handy tool.



I would, however, splice the ground wires on the cables entering the box
together, along with a long bare pigtail of the proper gauge, with a
wire nut. The pigtail then loops under the box's ground screw and then
is connected to the ground terminal of the device installed in the box.
If both of the ground wires coming from the cables are long enough,
you could loop one under the box's ground screw, the other under the
device's terminal, then splice with wire nut. This way all connections
are good and proper, and you don't have to mess with BS like trying to
shove two short wires under a single screw without a Sta-Kon.


The problem with old wiring is that there is often no bare wires. The
wiring is armoured cable (BX), or metal conduit. The conduit is
normally a good ground, but only the BX with the bare metal insert in
the cable is a decent ground. Aside from ripping the whole house apart,
one can only use what exists as a ground.

Aside: Why don't spec grade "back wire" devices allow two ground wires
to be inserted under a single screw like the hots and neutrals?


I fully agree, actually all devices *could* have more than one ground
screw to make wiring easier. At least two screws, since probably hanf
the outlets and switches feed at least 2 cables. (the source wire and
the wire that goes to the next fixture).

When I wire a box, I normally make one cable longer, than take the bare
and wrap it to the box screw near the entry point (box clamp). Then the
end of that bare wire goes to the outlet or device. If there are two or
more wires, that means more wirenuts. Which of course fills the box
faster and makes wiring harder.

My, things are primitive in the USA.


Yea, I'm having a heck of a time with this hand cranked computer and
carrier pigeons carrying IP packets back and forth from my service
provider. O_o

TDD
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 354
Default Past Wiring Codes

On Mon, 12 Nov 2012 03:14:11 -0600, wrote:

On Sun, 11 Nov 2012 20:13:39 -0500, Nate Nagel
wrote:

which is not hard; Klein makes a tap tool with a screwdriver handle for
just this purpose. Have used it quite a few times for just this
application. (trying to use a standard tap with T-handle is difficult
due to the depth of the boxes, but you don't need a whole lot of torque
to thread the steel of a typical electrical box.)


That sounds like a handy tool.

I would, however, splice the ground wires on the cables entering the box
together, along with a long bare pigtail of the proper gauge, with a
wire nut. The pigtail then loops under the box's ground screw and then
is connected to the ground terminal of the device installed in the box.
If both of the ground wires coming from the cables are long enough,
you could loop one under the box's ground screw, the other under the
device's terminal, then splice with wire nut. This way all connections
are good and proper, and you don't have to mess with BS like trying to
shove two short wires under a single screw without a Sta-Kon.


The problem with old wiring is that there is often no bare wires. The
wiring is armoured cable (BX), or metal conduit. The conduit is
normally a good ground, but only the BX with the bare metal insert in
the cable is a decent ground. Aside from ripping the whole house apart,
one can only use what exists as a ground.


Aside: Why don't spec grade "back wire" devices allow two ground wires
to be inserted under a single screw like the hots and neutrals?


I fully agree, actually all devices *could* have more than one ground
screw to make wiring easier. At least two screws, since probably hanf
the outlets and switches feed at least 2 cables. (the source wire and
the wire that goes to the next fixture).


Grounds are not supposed to be daisy-chained (neither are neutrals).

When I wire a box, I normally make one cable longer, than take the bare
and wrap it to the box screw near the entry point (box clamp). Then the
end of that bare wire goes to the outlet or device. If there are two or
more wires, that means more wirenuts. Which of course fills the box
faster and makes wiring harder.


  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default Past Wiring Codes

On 11/11/2012 7:13 PM, Nate Nagel wrote:

Aside: Why don't spec grade "back wire" devices allow two ground wires
to be inserted under a single screw like the hots and neutrals?


My guess is that if you replace the receptacle while the circuit is live
you break the ground downstream. The same is true of the neutral. You
can have a "hot" neutral or ground downstream. A hot neutral is not
likely to be a problem (except for the person changing the receptacle).
A hot ground, even for a short time, can be fatal.

For multiwire (Edison) circuits you are not allowed to connect the
neutral through the receptacle. It has to be spliced separately, and a
single neutral wire connects to the receptacle. If replace the
receptacle hot, and break the neutral, one downstream leg-to-neutral can
wind up at 240V and the other 0V.


  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 155
Default Past Wiring Codes

On Sun, 11 Nov 2012 18:48:13 -0600,
wrote:


A lot of the older metal boxes did not have threaded holes for ground
screws.


This one did, but was only used to connect the outlet ground
lug to the outlet box.

So, using a nail was all that was possible, unril they came out
with the clamps that snap over the edge if the box. If the nail is
tight, it's likely a good ground, but not allowed by code.


The thought of dissimilar metals seems like a sure miss to
me (for a dependable connection). And the fact that a nail
used to hold the outlet box to the stud is never going to be
dependably tight--the box gets pushed and pulled every time
something is plugged in or unplugged. Especially when the
studs are soft redwood.

When I wired up my garage, I put 2x4s spanning between
studs, and screwed the boxes to those. None of those boxes
are wiggly at all!


In the past,
if I've had to work on old wiring and boxes without ground screw holes,
I opted to use a screw in place of a nail, and put a washer under the
screw head. Then wrap the wire under that washer. Again, it's not
allowed by code, but it works.


It works long enough to get paid for the job, anyway.


I dont know what was allowed by code in the old days, but there are
probably millions of boxes grounded just on a nail. Remember, the old
wiring did not use grounds, so it's not always easy to upgrade without
ripping out walls and stuff.


In this case, the separate, bare ground was wrapped around
the nail used to mount the box to the stud. This couldn't
have been done post-construction, as there is no evidence of
the sheetrock having been disturbed, and the nail is
otherwise innaccessible.


The correct way would be to drill a hole in the box, thread it, and
insert a ground screw.


And have a direct connection from ground to the recepticle,
as opposed to chaining the ground thru the box (says this
untrained homeowner).

Copper to steel still sounds like a questionable technique
to me, even tho I know it is still the most common (only?)
way of grounding steel boxes. The slightest bit of
moisture.... And if you live near the ocean?

--
croy
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
G-codes past RS-274 a waste? Lloyd E. Sponenburgh[_3_] Metalworking 10 December 8th 10 03:41 AM
What wiring codes say about these wires? Joseph Home Repair 31 May 16th 07 03:34 PM
What wiring codes say about these wires? Joseph Home Repair 16 May 15th 07 07:14 AM
1950s German appliance wiring colour codes Tony Polson UK diy 32 October 5th 06 08:10 PM
RGB monitor input wiring color codes Sam Goldwasser Electronics Repair 1 September 29th 04 03:19 AM


All times are GMT +1. The time now is 11:52 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"