My 1986 Lennox AC compressor unit just stopped running, the fan isnt
running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. |
#2
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 22, 9:06*pm, ransley wrote:
My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. When this happened to my 1991 Lennox, it was the timing board. That particular board delayed turning the thing on for 5 minutes once it was told to by the thermostat. This was to make sure the old mercury therms had time to settle and prevented on-off-on-off. The tech said it was pretty obvious that the board burned out. One possibility? |
#3
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/22/2010 9:06 PM, ransley wrote:
My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD |
#4
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 22, 10:06*pm, ransley wrote:
My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. Is there some specific reason you want to keep fiddling with a unit that is 24 years old and now using a substitute refrigerant for what it was originally charged with ? After fixing a leak the unit stops working completely ? I would say you got your 24 years out of the unit and its time to update your installation... Not only will a newer unit of the same size use less energy, they also have better control systems for them now... ~~ Evan |
#5
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 5:04*am, Evan wrote:
On Aug 22, 10:06*pm, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. Is there some specific reason you want to keep fiddling with a unit that is 24 years old and now using a substitute refrigerant for what it was originally charged with ? After fixing a leak the unit stops working completely ? I would say you got your 24 years out of the unit and its time to update your installation... *Not only will a newer unit of the same size use less energy, they also have better control systems for them now... ~~ Evan My mistake its a 96, only the second time it broke, its 13 seer and I could not get a new one this year, so its fix it or get a window unit for the room I sleep in. |
#6
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 22, 10:01*pm, The Daring Dufas the-daring-
wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something. |
#7
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 22, 10:01*pm, The Daring Dufas the-daring-
wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD Wouldnt the fan run even with a bad capacitor |
#8
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 22, 9:33*pm, Bryan Scholtes wrote:
On Aug 22, 9:06*pm, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. When this happened to my 1991 Lennox, it was the timing board. That particular board delayed turning the thing on for 5 minutes once it was told to by the thermostat. This was to make sure the old mercury therms had time to settle and prevented on-off-on-off. The tech said it was pretty obvious that the board burned out. One possibility? That sounds logical |
#9
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 6:40*am, ransley wrote:
On Aug 23, 5:04*am, Evan wrote: On Aug 22, 10:06*pm, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. Is there some specific reason you want to keep fiddling with a unit that is 24 years old and now using a substitute refrigerant for what it was originally charged with ? After fixing a leak the unit stops working completely ? I would say you got your 24 years out of the unit and its time to update your installation... *Not only will a newer unit of the same size use less energy, they also have better control systems for them now... ~~ Evan My mistake its a 96, only the second time it broke, its 13 seer and I could not get a new one this year, so its fix it or get a window unit for the room I sleep in.- Hide quoted text - - Show quoted text - I'd start by seeing if you have 240v coming into the outside condenser unit. It comes into a relay that gets closed to turn on the compressor. If so, then see if the relay closes and you get 240v on the other side going to the compressor when the system is turned on |
#10
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
ransley wrote:
If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something. It's the only (usually) relay-looking-gizmo in the outside unit. It supplies power to both the fan (120) and the compressor (240). If both are not working, the obvious culprit is the only thing they have in common - the relay. That said, it could be the relay itself is broken (fried, etc.) or the voltage that activates the relay (24V) is missing. If the relay, they're not TOO expensive and, if your hand fits a screwdriver, you should be able to replace it. Label the wires - taking several pictures is better - and take the old one to Graingers. Say "gimme one like this". Remember to wear eye and ear protection when working around electricity and, um, er... one other saftey precaution, but I forget... |
#11
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 6:47*am, ransley wrote:
On Aug 22, 10:01*pm, The Daring Dufas the-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. It should be easy to trace to the contactor (a big relay). The contactor is a 24vac activated relay that supplies 240vac to the entire unit. The inside half sends the 24vac. It is possible to manually activate a contactor by pushing it down carefully with something. The compressor and it's fan are both activated by the contactor. If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. Both the compressor and the fan will use run capacitors but they may be combined in a single can. Ther may also be a start capacitor on the compressor. Since nothing is running I doubt it's a capacitor. |
#12
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Yeah, we can't tell him the other safety precaution. It's too
complicated. I think he will find that the condensor fan is also 220 VAC. And has a run cap. -- Christopher A. Young Learn more about Jesus www.lds.org .. "HeyBub" wrote in message ... It's the only (usually) relay-looking-gizmo in the outside unit. It supplies power to both the fan (120) and the compressor (240). If both are not working, the obvious culprit is the only thing they have in common - the relay. That said, it could be the relay itself is broken (fried, etc.) or the voltage that activates the relay (24V) is missing. If the relay, they're not TOO expensive and, if your hand fits a screwdriver, you should be able to replace it. Label the wires - taking several pictures is better - and take the old one to Graingers. Say "gimme one like this". Remember to wear eye and ear protection when working around electricity and, um, er... one other saftey precaution, but I forget... |
#13
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
As others have suggested. You can check to see if the outdoor unit has
220 VAC. You can also check to see if the contactor is getting the 24 VAC signal, and if the contactor is making connection. The fan and compressor have different capacitors. Possible but not likely that they are both bad at the same time. -- Christopher A. Young Learn more about Jesus www.lds.org .. "ransley" wrote in message ... My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. |
#14
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 7:50*am, jamesgangnc wrote:
On Aug 23, 6:47*am, ransley wrote: On Aug 22, 10:01*pm, The Daring Dufas the-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". *The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. *It should be easy to trace to the contactor (a big relay). *The contactor is a 24vac activated relay that supplies 240vac to the entire unit. *The inside half sends the 24vac. *It is possible to manually activate a contactor by pushing it down carefully with something. *The compressor and it's fan are both activated by the contactor. *If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. *Both the compressor and the fan will use run capacitors but they may be combined in a single can. *Ther may also be a start capacitor on the compressor. *Since nothing is running I doubt it's a capacitor.- Hide quoted text - - Show quoted text - I can hear the wires "Rattle" inside the conduit and the breaker on the main panel makes a zip noise when it powers on, I bet it should have been a larger gauge but they had no more room in the conduit. I mentioned it to them on install and they said 'its ok", but I know it would have been rejected by an inspector. I didnt get a permit or an inspection for the install, In 96 I didnt think permits-inspectors were a help. Thats why I wonder is I have any power since nothing works, but im no electrician. |
#15
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 7:06*am, wrote:
On Aug 23, 6:40*am, ransley wrote: On Aug 23, 5:04*am, Evan wrote: On Aug 22, 10:06*pm, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. Is there some specific reason you want to keep fiddling with a unit that is 24 years old and now using a substitute refrigerant for what it was originally charged with ? After fixing a leak the unit stops working completely ? I would say you got your 24 years out of the unit and its time to update your installation... *Not only will a newer unit of the same size use less energy, they also have better control systems for them now... ~~ Evan My mistake its a 96, only the second time it broke, its 13 seer and I could not get a new one this year, so its fix it or get a window unit for the room I sleep in.- Hide quoted text - - Show quoted text - I'd start by seeing if you have 240v coming into the outside condenser unit. * It comes into a relay that gets closed to turn on the compressor. *If so, then see if the relay closes and you get 240v on the other side going to the compressor when the system is turned on- Hide quoted text - - Show quoted text - Yes AC power is where I will start at, I cant even find my meter today, but its only 72 out. |
#16
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
It sounds like you're not very experienced with electricity. Do you
have a friend, or relative you can call, who has some electrical experience? Some things are best learned from an experienced teacher, rather than on the internet. This is one such. -- Christopher A. Young Learn more about Jesus www.lds.org .. "ransley" wrote in message ... Yes AC power is where I will start at, I cant even find my meter today, but its only 72 out. |
#17
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Sun, 22 Aug 2010 19:06:51 -0700 (PDT), ransley
wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. My HVAC took a time-out a few weeks back. Nothing would work at all. The fan would not even run, like yours. I presume the fan blower gets its 110V power from a light switch box in the attic. The switch had failed and no power was getting to the blower fan. YMMV |
#18
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 1:35*pm, Oren wrote:
On Sun, 22 Aug 2010 19:06:51 -0700 (PDT), ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. My HVAC took a time-out a few weeks back. *Nothing would work at all. The fan would not even run, like yours. I presume the fan blower gets its 110V power from a light switch box in the attic. *The switch had failed and no power was getting to the blower fan. YMMV If the inside unit is not working then it's likely that the 24 vac transformer is not getting power and that will explain why the outside unit doesn;t work. The op was not very clear about the inside half but I got the impression it was ok. I could easily be mistaken. |
#19
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 9:49*am, ransley wrote:
On Aug 23, 7:50*am, jamesgangnc wrote: On Aug 23, 6:47*am, ransley wrote: On Aug 22, 10:01*pm, The Daring Dufas the-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". *The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. *It should be easy to trace to the contactor (a big relay). *The contactor is a 24vac activated relay that supplies 240vac to the entire unit. *The inside half sends the 24vac. *It is possible to manually activate a contactor by pushing it down carefully with something. *The compressor and it's fan are both activated by the contactor. *If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. *Both the compressor and the fan will use run capacitors but they may be combined in a single can. *Ther may also be a start capacitor on the compressor. *Since nothing is running I doubt it's a capacitor.- Hide quoted text - - Show quoted text - I can hear the wires "Rattle" inside the conduit and the breaker on the main panel makes a zip noise when it powers on, I bet it should have been a larger gauge but they had no more room in the conduit. I mentioned it to them on install and they said 'its ok", but I know it would have been rejected by an inspector. I didnt get a permit or an inspection for the install, In 96 I didnt think permits-inspectors were a help. Thats why I wonder is I have any power since nothing works, but im no electrician.- Hide quoted text - - Show quoted text - Wires will never move due to being energized in this application. They will get hot if they are too small but they won't "rattle". You are hearing something else. |
#20
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() "ransley" wrote in message ... On Aug 23, 12:55 pm, jamesgangnc wrote: On Aug 23, 1:35 pm, Oren wrote: - Show quoted text - The air handler does work, and when I push in the relay on the outside compressor unit it runs, so I guess next I check for 24v to the compressor relay? The only thing controlling the 24 volt system before it gets to the outside unit is thermostat. Are you sure it is good? Find the two wire cable and test for 24V there first. Many of the 1995 and later models have a low pressure switch wired into the 24 volt system inside the condenser unit. This part might also be the problem. Just mentioning these two things BEFORE you run out and buy a non-returnable contactor. Follow the 24V wires and test for current after each part. Entry point, low pressure switch and at the contactor. Actually working that in reverse is the smarter way to do it. I just wanted you to see the path. -- Colbyt Please come visit http://www.househomerepair.com |
#21
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Stormin Mormon wrote:
Yeah, we can't tell him the other safety precaution. It's too complicated. I think he will find that the condensor fan is also 220 VAC. And has a run cap. Ah, right. I forgot. |
#22
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
ransley wrote:
It's the only (usually) relay-looking-gizmo in the outside unit. It supplies power to both the fan (120) and the compressor (240). If both are not working, the obvious culprit is the only thing they have in common - the relay. That said, it could be the relay itself is broken (fried, etc.) or the voltage that activates the relay (24V) is missing. If the relay, they're not TOO expensive and, if your hand fits a screwdriver, you should be able to replace it. Label the wires - taking several pictures is better - and take the old one to Graingers. Say "gimme one like this". Remember to wear eye and ear protection when working around electricity and, um, er... one other saftey precaution, but I forget...- Hide quoted text - - Show quoted text - When I push in the relay it runs, so now I will go back out and see if its getting 24v. Yep. It's either not getting the 24v OR unable to use the voltage cause the relay itself has given up the ghost, taken a dirt nap, singing in the heavenly choir, or passed this way only once to brighten our lives, provide endearing memories, and let us chill. |
#23
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Mon, 23 Aug 2010 07:33:49 -0500, "HeyBub"
wrote: Remember to wear eye and ear protection when working around electricity and, um, er... one other saftey precaution, but I forget... I know... keep one hand in your pocket! What do I win? |
#24
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/23/2010 12:34 PM, ransley wrote:
On Aug 23, 12:55 pm, wrote: On Aug 23, 1:35 pm, wrote: On Sun, 22 Aug 2010 19:06:51 -0700 (PDT), ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. My HVAC took a time-out a few weeks back. Nothing would work at all. The fan would not even run, like yours. I presume the fan blower gets its 110V power from a light switch box in the attic. The switch had failed and no power was getting to the blower fan. YMMV If the inside unit is not working then it's likely that the 24 vac transformer is not getting power and that will explain why the outside unit doesn;t work. The op was not very clear about the inside half but I got the impression it was ok. I could easily be mistaken.- Hide quoted text - - Show quoted text - The air handler does work, and when I push in the relay on the outside compressor unit it runs, so I guess next I check for 24v to the compressor relay? Squirrels and other critters have been known to enjoy a meal of insulation. |
#25
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Happens to the best of us. We all forget something or
-- Christopher A. Young Learn more about Jesus www.lds.org .. "HeyBub" wrote in message m... Stormin Mormon wrote: Yeah, we can't tell him the other safety precaution. It's too complicated. I think he will find that the condensor fan is also 220 VAC. And has a run cap. Ah, right. I forgot. |
#26
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/23/2010 1:32 PM, ransley wrote:
On Aug 23, 7:33 am, wrote: ransley wrote: If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something. It's the only (usually) relay-looking-gizmo in the outside unit. It supplies power to both the fan (120) and the compressor (240). If both are not working, the obvious culprit is the only thing they have in common - the relay. That said, it could be the relay itself is broken (fried, etc.) or the voltage that activates the relay (24V) is missing. If the relay, they're not TOO expensive and, if your hand fits a screwdriver, you should be able to replace it. Label the wires - taking several pictures is better - and take the old one to Graingers. Say "gimme one like this". Remember to wear eye and ear protection when working around electricity and, um, er... one other saftey precaution, but I forget...- Hide quoted text - - Show quoted text - When I push in the relay it runs, so now I will go back out and see if its getting 24v. The low voltage wires going to the contactor coil are usually yellow in color, sometimes one is blue which is the common. TDD |
#27
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/23/2010 7:50 AM, jamesgangnc wrote:
On Aug 23, 6:47 am, wrote: On Aug 22, 10:01 pm, The Daring Dufasthe-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. It should be easy to trace to the contactor (a big relay). The contactor is a 24vac activated relay that supplies 240vac to the entire unit. The inside half sends the 24vac. It is possible to manually activate a contactor by pushing it down carefully with something. The compressor and it's fan are both activated by the contactor. If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. Both the compressor and the fan will use run capacitors but they may be combined in a single can. Ther may also be a start capacitor on the compressor. Since nothing is running I doubt it's a capacitor. It's not unusual for wires to move or rattle inside a conduit even if the wire is properly sized for the load. The starting current of an AC compressor can easily be several time the run current of the whole unit. Wires can and will dance under the right set of circumstances. TDD |
#28
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/23/2010 5:48 AM, ransley wrote:
On Aug 22, 10:01 pm, The Daring Dufasthe-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD Wouldnt the fan run even with a bad capacitor It may turn slowly while making an unhappy whirring sound or just hum angrily. HVAC equipment can get emotional at times. 8-) TDD |
#29
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/23/2010 8:00 AM, Stormin Mormon wrote:
As others have suggested. You can check to see if the outdoor unit has 220 VAC. You can also check to see if the contactor is getting the 24 VAC signal, and if the contactor is making connection. The fan and compressor have different capacitors. Possible but not likely that they are both bad at the same time. If it's a combo capacitor with 3 terminals, the top will pop up when it fails, killing both the fan and compressor. TDD |
#30
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/23/2010 1:34 PM, ransley wrote:
On Aug 23, 12:55 pm, wrote: On Aug 23, 1:35 pm, wrote: On Sun, 22 Aug 2010 19:06:51 -0700 (PDT), ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. My HVAC took a time-out a few weeks back. Nothing would work at all. The fan would not even run, like yours. I presume the fan blower gets its 110V power from a light switch box in the attic. The switch had failed and no power was getting to the blower fan. YMMV If the inside unit is not working then it's likely that the 24 vac transformer is not getting power and that will explain why the outside unit doesn;t work. The op was not very clear about the inside half but I got the impression it was ok. I could easily be mistaken.- Hide quoted text - - Show quoted text - The air handler does work, and when I push in the relay on the outside compressor unit it runs, so I guess next I check for 24v to the compressor relay? Did you happen to run a weed eater around the condensing unit? I see that activity cut the control wire to the condenser quite often. TDD |
#31
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/23/2010 2:18 PM, Colbyt wrote:
wrote in message ... On Aug 23, 12:55 pm, wrote: On Aug 23, 1:35 pm, wrote: - Show quoted text - The air handler does work, and when I push in the relay on the outside compressor unit it runs, so I guess next I check for 24v to the compressor relay? The only thing controlling the 24 volt system before it gets to the outside unit is thermostat. Are you sure it is good? Find the two wire cable and test for 24V there first. Many of the 1995 and later models have a low pressure switch wired into the 24 volt system inside the condenser unit. This part might also be the problem. Just mentioning these two things BEFORE you run out and buy a non-returnable contactor. Follow the 24V wires and test for current after each part. Entry point, low pressure switch and at the contactor. Actually working that in reverse is the smarter way to do it. I just wanted you to see the path. He did mention that it's a 13 SEER unit and it may very well have a low pressure cutout switch. The builder grade units, even the newest of them don't have a factory installed low or high pressure cutout. TDD |
#32
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Aug 23, 9:36*pm, The Daring Dufas
wrote: On 8/23/2010 7:50 AM, jamesgangnc wrote: On Aug 23, 6:47 am, *wrote: On Aug 22, 10:01 pm, The Daring Dufasthe-daring- *wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling.. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". *The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. *It should be easy to trace to the contactor (a big relay). *The contactor is a 24vac activated relay that supplies 240vac to the entire unit. *The inside half sends the 24vac. *It is possible to manually activate a contactor by pushing it down carefully with something. *The compressor and it's fan are both activated by the contactor. *If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. *Both the compressor and the fan will use run capacitors but they may be combined in a single can. *Ther may also be a start capacitor on the compressor. *Since nothing is running I doubt it's a capacitor. It's not unusual for wires to move or rattle inside a conduit even if the wire is properly sized for the load. The starting current of an AC compressor can easily be several time the run current of the whole unit. Wires can and will dance under the right set of circumstances. TDD- Hide quoted text - - Show quoted text - You're an idiot. Wires do not move in this example. |
#33
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/24/2010 7:18 AM, jamesgangnc wrote:
On Aug 23, 9:36 pm, The Daring wrote: On 8/23/2010 7:50 AM, jamesgangnc wrote: On Aug 23, 6:47 am, wrote: On Aug 22, 10:01 pm, The Daring Dufasthe-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. It should be easy to trace to the contactor (a big relay). The contactor is a 24vac activated relay that supplies 240vac to the entire unit. The inside half sends the 24vac. It is possible to manually activate a contactor by pushing it down carefully with something. The compressor and it's fan are both activated by the contactor. If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. Both the compressor and the fan will use run capacitors but they may be combined in a single can. Ther may also be a start capacitor on the compressor. Since nothing is running I doubt it's a capacitor. It's not unusual for wires to move or rattle inside a conduit even if the wire is properly sized for the load. The starting current of an AC compressor can easily be several time the run current of the whole unit. Wires can and will dance under the right set of circumstances. TDD- Hide quoted text - - Show quoted text - You're an idiot. Wires do not move in this example. I only have four decades experience in the field and I see it all the time. In an industrial environment I've come across it a lot where there are a numerous high current starting loads for motors. The wire can actually change length under heavy load. I've seen insulation rubbed of a wire because of this movement. The OP can hear the #10 wires jump inside the conduit when his AC unit stars. When you get your PhD in know-it-allogy, come back and call me names. TDD |
#34
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
I'm reminded of a joke, I'm about to make up. Bill Gates, a pollack,
an engineer, and a meterologist are sitting in a room. The one of them asks if it's raining. Bill Gates whips out a PDA, connects to the internet, and looks at a radar map. Says it's not raining. The engineer takes a large piece of plastic. Builds a frame, balance point, and connects the other end of the support to a reverse reading mass scale. He extends this out the window. The liner acceleration of gravitational impulses of descending precipitation are negligible. So, he concludes it is not raining. The meterologist calls the NOAA phone number, listens through the recorded message. And concludes it is not raining. The pollack opens the door, steps outside, and comes back in wet. He brings back in the engineer's device (which was under the eaves). Reports that it is raining. The other three gang up and pound the stuffing out of the pollack, while calling him a liar. Yeah, I'm sure the wires wiggle. Heck, it only makes sense. -- Christopher A. Young Learn more about Jesus www.lds.org .. "The Daring Dufas" wrote in message ... On 8/24/2010 7:18 AM, jamesgangnc wrote: You're an idiot. Wires do not move in this example. I only have four decades experience in the field and I see it all the time. In an industrial environment I've come across it a lot where there are a numerous high current starting loads for motors. The wire can actually change length under heavy load. I've seen insulation rubbed of a wire because of this movement. The OP can hear the #10 wires jump inside the conduit when his AC unit stars. When you get your PhD in know-it-allogy, come back and call me names. TDD |
#35
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
The stormin MORON.. had this to say.
I'm reminded of a joke, I'm about to make up. Bill Gates, a pollack, an engineer, and a meterologist are sitting in a room. Did you mean? Polock? Which is a racist word for our fine Polish countrymen... You.....! My friend, are a pure bred racist How do you get off calling yourself a MORMON? HUH? Do all Mormons use racial epitaphs, like you? |
#36
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/24/2010 12:07 PM, jamesgangnc wrote:
On Aug 24, 2:46 pm, wrote: On 8/24/2010 10:50 AM, jamesgangnc wrote: On Aug 24, 12:31 pm, The Daring Dufasthe-daring- wrote: On 8/24/2010 7:18 AM, jamesgangnc wrote: On Aug 23, 9:36 pm, The Daring wrote: On 8/23/2010 7:50 AM, jamesgangnc wrote: On Aug 23, 6:47 am, wrote: On Aug 22, 10:01 pm, The Daring Dufasthe-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. It should be easy to trace to the contactor (a big relay). The contactor is a 24vac activated relay that supplies 240vac to the entire unit. The inside half sends the 24vac. It is possible to manually activate a contactor by pushing it down carefully with something. The compressor and it's fan are both activated by the contactor. If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. Both the compressor and the fan will use run capacitors but they may be combined in a single can. Ther may also be a start capacitor on the compressor. Since nothing is running I doubt it's a capacitor. It's not unusual for wires to move or rattle inside a conduit even if the wire is properly sized for the load. The starting current of an AC compressor can easily be several time the run current of the whole unit. Wires can and will dance under the right set of circumstances. TDD- Hide quoted text - - Show quoted text - You're an idiot. Wires do not move in this example. I only have four decades experience in the field and I see it all the time. In an industrial environment I've come across it a lot where there are a numerous high current starting loads for motors. The wire can actually change length under heavy load. I've seen insulation rubbed of a wire because of this movement. The OP can hear the #10 wires jump inside the conduit when his AC unit stars. When you get your PhD in know-it-allogy, come back and call me names. TDD- Hide quoted text - - Show quoted text - Go ahead give us the science behind it then? High current -- wires heat -- heat causes expansion -- expansion causes movement (not exactly "rattle" perhaps, but insulation sliding against insulation could probably approximate a squeak) Am I missing something? What's so hard to understand?- Hide quoted text - - Show quoted text - A piece of 10 guage wire is not going to heat up fast enough to move at a rate you could observe with the naked eye at these currents. First, you haven't quantified the surge current. Second, he didn't see it, he heard it. Things that appear still can make noise -- consider a piezo speaker. Third, the other poster has offered an alternative explanation. |
#37
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() |
#38
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/24/2010 1:21 PM, jamesgangnc wrote:
On Aug 24, 1:48 pm, The Daring wrote: On 8/24/2010 11:50 AM, jamesgangnc wrote: On Aug 24, 12:31 pm, The Daring Dufasthe-daring- wrote: On 8/24/2010 7:18 AM, jamesgangnc wrote: On Aug 23, 9:36 pm, The Daring wrote: On 8/23/2010 7:50 AM, jamesgangnc wrote: On Aug 23, 6:47 am, wrote: On Aug 22, 10:01 pm, The Daring Dufasthe-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. It should be easy to trace to the contactor (a big relay). The contactor is a 24vac activated relay that supplies 240vac to the entire unit. The inside half sends the 24vac. It is possible to manually activate a contactor by pushing it down carefully with something. The compressor and it's fan are both activated by the contactor. If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. Both the compressor and the fan will use run capacitors but they may be combined in a single can. Ther may also be a start capacitor on the compressor. Since nothing is running I doubt it's a capacitor. It's not unusual for wires to move or rattle inside a conduit even if the wire is properly sized for the load. The starting current of an AC compressor can easily be several time the run current of the whole unit. Wires can and will dance under the right set of circumstances. TDD- Hide quoted text - - Show quoted text - You're an idiot. Wires do not move in this example. I only have four decades experience in the field and I see it all the time. In an industrial environment I've come across it a lot where there are a numerous high current starting loads for motors. The wire can actually change length under heavy load. I've seen insulation rubbed of a wire because of this movement. The OP can hear the #10 wires jump inside the conduit when his AC unit stars. When you get your PhD in know-it-allogy, come back and call me names. TDD- Hide quoted text - - Show quoted text - Go ahead give us the science behind it then? You don't know how to use a library? I don't need to give you the science, I have directly observed the phenomenon. Direct observation makes up most science. I did find a document online that has some equations if that will help you understand but if you know anything about electricity, you can visualize that a length of wire has a magnetic field when energized. Take a look at page 3 of the PDF: http://www.pppl.gov/eshis/ESHD_MANUAL/safety/es7.0.pdf TDD- Hide quoted text - - Show quoted text - I know something about electricity. I know it takes a great very deal of current to make a strong magnetic field in a straight wire. Possible in a commercial setting with high pulsed current, yes. In a home ac compressor, I doubt it. Go ahead, hold your ferrous screwdriver blade near the 10 guage wire with the compressor running. Feel any pull? You obviously didn't understand, the wire movement happens when the compressor starts, not continuously. The compressor starts, you can hear the breaker buzz and the wires in a conduit jump, rattle for a split second, not during normal run operation. GEEZ! TDD |
#39
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/24/2010 1:46 PM, cjt wrote:
On 8/24/2010 10:50 AM, jamesgangnc wrote: On Aug 24, 12:31 pm, The Daring Dufasthe-daring- wrote: On 8/24/2010 7:18 AM, jamesgangnc wrote: On Aug 23, 9:36 pm, The Daring wrote: On 8/23/2010 7:50 AM, jamesgangnc wrote: On Aug 23, 6:47 am, wrote: On Aug 22, 10:01 pm, The Daring Dufasthe-daring- wrote: On 8/22/2010 9:06 PM, ransley wrote: My 1986 Lennox AC compressor unit just stopped running, the fan isnt running and no noise comes from the unit, I reset the breakers and the thermostat is the old round analog Honywell, its calling for cooling. Ive never worked on this but is there anything I can test with a V meter before I call a pro. 3 weeks ago I lost all freon from a big leak and had it fixed, all has been fine until today. I would think at least the fan would run. If there was a thunderstorm, a voltage spike could have blown the run capacitor. If your air handler fan doesn't run, it's a power problem there because the 24 volt control voltage comes from the furnace/air handler. Without the 24 volts AC, the condensing unit where the compressor is will not come on. If you can push in the insulated contact carrier on the condenser contactor and the fan and compressor run, you'll know it's not getting control voltage from the furnace/air handler. TDD What does the condensor contactor look like where do I find it, I wonder if the tech left a wire loose since it seems like it just has no power. I do know I dont think it was installed with proper gauge wiring , Its about a 60 ft run of 2 pieces of 10 ga and it rattles in the pipe and at the breaker on turn on. All these years of rattling could have loosened something.- Hide quoted text - - Show quoted text - I've never heard of a wire or a breaker "rattling". The freon lines on some units can be noisy and that might be what you hear. You can check for 240vac at the unit. It should be easy to trace to the contactor (a big relay). The contactor is a 24vac activated relay that supplies 240vac to the entire unit. The inside half sends the 24vac. It is possible to manually activate a contactor by pushing it down carefully with something. The compressor and it's fan are both activated by the contactor. If there are any additional controls such as the startup delay board they will most likely be on the 24vac side. Both the compressor and the fan will use run capacitors but they may be combined in a single can. Ther may also be a start capacitor on the compressor. Since nothing is running I doubt it's a capacitor. It's not unusual for wires to move or rattle inside a conduit even if the wire is properly sized for the load. The starting current of an AC compressor can easily be several time the run current of the whole unit. Wires can and will dance under the right set of circumstances. TDD- Hide quoted text - - Show quoted text - You're an idiot. Wires do not move in this example. I only have four decades experience in the field and I see it all the time. In an industrial environment I've come across it a lot where there are a numerous high current starting loads for motors. The wire can actually change length under heavy load. I've seen insulation rubbed of a wire because of this movement. The OP can hear the #10 wires jump inside the conduit when his AC unit stars. When you get your PhD in know-it-allogy, come back and call me names. TDD- Hide quoted text - - Show quoted text - Go ahead give us the science behind it then? High current -- wires heat -- heat causes expansion -- expansion causes movement (not exactly "rattle" perhaps, but insulation sliding against insulation could probably approximate a squeak) Am I missing something? What's so hard to understand? The inductive kick of a high current motor/compressor start can cause wire inside a metal conduit to make noise. I've heard the telltale racket a million times in many different settings. It sounds a lot like somebody shaking a metal fish tape inside an empty conduit. TDD |
#40
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 8/24/2010 3:36 PM, Stormin Mormon wrote:
I'm reminded of a joke, I'm about to make up. Bill Gates, a pollack, an engineer, and a meterologist are sitting in a room. The one of them asks if it's raining. Bill Gates whips out a PDA, connects to the internet, and looks at a radar map. Says it's not raining. The engineer takes a large piece of plastic. Builds a frame, balance point, and connects the other end of the support to a reverse reading mass scale. He extends this out the window. The liner acceleration of gravitational impulses of descending precipitation are negligible. So, he concludes it is not raining. The meterologist calls the NOAA phone number, listens through the recorded message. And concludes it is not raining. The pollack opens the door, steps outside, and comes back in wet. He brings back in the engineer's device (which was under the eaves). Reports that it is raining. The other three gang up and pound the stuffing out of the pollack, while calling him a liar. Yeah, I'm sure the wires wiggle. Heck, it only makes sense. A walking, talking fish is too valuable to beat up. TDD |