Replacing a single light fixture that's controlled with two switches.
The light box has a standard black/white/ground supply wire. While
installing I found that the white wire was actually hot (and marked
with black tape) and the black was neutral. The only issue was the
only way I could read 120V from the hot wire was to ground the
circuit. This seems odd to me as none of the three way wiring
diagrams I've seen seem to require the neutral being grounded at the
fixture. The reading from hot to neutral was 60V - not sure if this
means anything or not.

Is this OK or is there something I need to look into here?

Thanks
Doug
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default 3-way grounded neutral?

On Sun, 10 Feb 2008 07:42:42 -0800 (PST), Doug
wrote:

Replacing a single light fixture that's controlled with two switches.
The light box has a standard black/white/ground supply wire. While
installing I found that the white wire was actually hot (and marked
with black tape) and the black was neutral. The only issue was the
only way I could read 120V from the hot wire was to ground the
circuit. This seems odd to me as none of the three way wiring
diagrams I've seen seem to require the neutral being grounded at the
fixture. The reading from hot to neutral was 60V - not sure if this
means anything or not.

Is this OK or is there something I need to look into here?

Thanks
Doug


It is legal. Romex comes with one black wire and a white wire. You
assumed the white wire is neutral. It isn't. It is one of the two
wires needed for the switch. The black tape is to tell you that the
wire is the return from the switch and not a neutral.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default 3-way grounded neutral?


"Doug" wrote in message
...
Replacing a single light fixture that's controlled with two switches.
The light box has a standard black/white/ground supply wire. While
installing I found that the white wire was actually hot (and marked
with black tape) and the black was neutral. The only issue was the
only way I could read 120V from the hot wire was to ground the
circuit. This seems odd to me as none of the three way wiring
diagrams I've seen seem to require the neutral being grounded at the
fixture. The reading from hot to neutral was 60V - not sure if this
means anything or not.

Is this OK or is there something I need to look into here?



It doesn't sound okay to me. It sounds as though you have no neutral at the
light fixture. The feed for the light fixture should come from one of the
switches. Open them up and see if you have a neutral in there. The feed
for the circuit should also come into one of the switches. It could be the
same switch as the one that contains the light feed or the other switch.
Check to see if you have juice between the white and the black circuit feed.
I suggest using a pigtail light socket with a light bulb instead of a
digital meter.

Another possibility is that this set-up is wired using only two wires
instead of three between switches. In that type of operation the neutral
and hot rotate getting turned off depending on the positions of the wall
switches. Try flipping the switches and see if the polarity changes and you
get 120 volts. This is not the proper way for three-way switches to work as
the hot is off only 50% of the time and the neutral is off the other 50%.

Did the old light fixture work before you replaced it? If so how was it
wired?

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default 3-way grounded neutral?

On Feb 10, 7:42 am, Doug wrote:
Replacing a single light fixture that's controlled with two switches.
The light box has a standard black/white/ground supply wire. While
installing I found that the white wire was actually hot (and marked
with black tape) and the black was neutral. The only issue was the
only way I could read 120V from the hot wire was to ground the
circuit. This seems odd to me as none of the three way wiring
diagrams I've seen seem to require the neutral being grounded at the
fixture. The reading from hot to neutral was 60V - not sure if this
means anything or not.

Is this OK or is there something I need to look into here?

Thanks
Doug


Doug-

IMO you need to look into this a little.


The wring to the first switch box should be an un-switched hot
(black), an un-switched neutral (white) & a ground wire to the switch
& the box (if metal) .

The wiring from the first switch box to the second switch box should
be two switched hots (black & red or re-indentifed white), an un-
switched neutral (white) & a ground wire to the switch & the box (if
metal) .

So one needs 4 conductors (including the ground) between the two
switch boxes....here's where some people either get confused or
cheat. Ideally you use a three wire romex (black, red, white,
ground) or a double run of 2 wire Romex.

From the second switch box to the fixture box you should have a
switched hot (black), an un-switched neutral (white) & a ground wire
to the switch & the box (if metal) .

The setup you describe (if I'm understanding it) seems a little
off.

Is the circuit wired with Romex or single conductors (knob & tube OR
wire in conduit)?

Maybe the circuit existed as a single switch & the three way part was
added later.

Be careful, because of the limitations of 2 wire Romex systems, some
people take shortcuts on rewiring or additions that can leave you with
less than safe situations.

per John's comments a light bulb is often better than a meter

The 60v reading might be a result of a poor connection somewhere or a
digital meter giving a false reading reading.


cheers
Bob

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,447
Default 3-way grounded neutral?

On Feb 10, 9:40*pm, BobK207 wrote:
On Feb 10, 7:42 am, Doug wrote:

Replacing a single light fixture that's controlled with two switches.
The light box has a standard black/white/ground supply wire. *While
installing I found that the white wire was actually hot (and marked
with black tape) and the black was neutral. *The only issue was the
only way I could read 120V from the hot wire was to ground the
circuit. *This seems odd to me as none of the three way wiring
diagrams I've seen seem to require the neutral being grounded at the
fixture. *The reading from hot to neutral was 60V - not sure if this
means anything or not.


Is this OK or is there something I need to look into here?


Thanks
Doug


Doug-

IMO you need to look into this a little.

The wring to the first switch box should be an un-switched hot
(black), *an un-switched neutral (white) & a ground wire to the switch
& the box (if metal) .

The wiring from the first switch box to the second switch box should
be two *switched hots (black & red or re-indentifed white), *an un-
switched neutral (white) & a ground wire to the switch & the box (if
metal) .

So one needs 4 conductors (including the ground) between the two
switch boxes....here's where some people either get confused or
cheat. * Ideally you use a three wire romex (black, red, white,
ground) or a double run of 2 wire Romex.

From the second switch box to the fixture box you should have a
switched hot (black), an un-switched neutral (white) & a ground wire
to the switch & the box (if metal) .

The setup you describe (if I'm understanding it) *seems a little
off.

Is the circuit wired with Romex or single conductors (knob & tube *OR
wire in conduit)?

Maybe the circuit existed as a single switch & the three way part was
added later.

Be careful, because of the limitations of 2 wire Romex systems, some
people take shortcuts on rewiring or additions that can leave you with
less than safe situations.

per John's comments a light bulb is often better than a meter

The 60v reading might be a result of a poor connection somewhere or a
digital meter giving a false reading reading.

cheers
Bob


Bob that info 'could' be misleading?

What it sound like, as mentioned in one of the replies is that black
and white wires go from the ceiling box down to the switch. One of the
wires is the 'live' feed in and the other is the 'switched live'.

Consequently when the switch is 'on' electricity flows down to the
switch through the switch and back up to the 'hot' side of the light
fixture; and the light goes on.

Reading 60 volts may be meaningless; even cheap modern digital meters
can pick up voltages due to capacitance between wires etc. A much
better way to test is to use a regular bulb.

Nothing should be wired to the ground except metal parts of wiring
boxes, ceiling boxes, metal roses etc. the ground is a safety wire.

The ground can, but only 'momentarily' be used for testing; for
example put the test bulb between a wire and ground; if it comes on
all the time (with circuit breaker for that circuit on) it is a 'non-
switched live'. If it goes on and off as you operate the switch it is
a 'switched live'.

Then turn off the circuit breaker and wire the switched live to the
light fixture (or fixtures. Cos some rooms have two or more lights
controlled by the one switch!) Turn breaker back on (or reinsert
fuse) and test.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default 3-way grounded neutral?

Thanks for all the replies. Looks like a previous post of mine got
lost. Anyway...

I am going to pull out each switch and examine to see if I can
determine exactly what's going on. I will take pictures if I can't
figure it out and post back.

One followup question -

If I am to understand what might be happening is depending on which
switch is switched on, either the white or black wire could be the hot
wire. Is this accurate?

I doubt it was ever a single switch. It's a kitchen light and (with
the exception of the bedrooms) EVERY light in our house is on a 3-way
circuit, including two four ways. As far as how the circuit is wired
(BobK207's comments), everything is wired with standard wiring. I'm
not sure what Romex is. The supply wires in our house are black/white/
bare ground 12 gauge copper covered in what appears to be metallic
sheath (it's silver in color).
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default 3-way grounded neutral?


"Doug" wrote in message
...
Thanks for all the replies. Looks like a previous post of mine got
lost. Anyway...

I am going to pull out each switch and examine to see if I can
determine exactly what's going on. I will take pictures if I can't
figure it out and post back.

One followup question -

If I am to understand what might be happening is depending on which
switch is switched on, either the white or black wire could be the hot
wire. Is this accurate?


Anything is possible. At the fixture, you should have an unswitched Neutral
regardless of what color it is. You should be able to determine which wire
because it will give you continuity to the ground conductor or metal box.
Only ungrounded (hot) goes through the switches, then returns to the
fixture. With a light bulb pigtail, test between the hot return wire from
the switch and either ground or neutral, it'll light with the switch "on"

I doubt it was ever a single switch. It's a kitchen light and (with
the exception of the bedrooms) EVERY light in our house is on a 3-way
circuit, including two four ways. As far as how the circuit is wired
(BobK207's comments), everything is wired with standard wiring. I'm
not sure what Romex is. The supply wires in our house are black/white/
bare ground 12 gauge copper covered in what appears to be metallic
sheath (it's silver in color).



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default 3-way grounded neutral?

On Feb 10, 3:17 pm, Doug wrote:
Thanks for all the replies. Looks like a previous post of mine got
lost. Anyway...

I am going to pull out each switch and examine to see if I can
determine exactly what's going on. I will take pictures if I can't
figure it out and post back.

One followup question -

If I am to understand what might be happening is depending on which
switch is switched on, either the white or black wire could be the hot
wire. Is this accurate?

I doubt it was ever a single switch. It's a kitchen light and (with
the exception of the bedrooms) EVERY light in our house is on a 3-way
circuit, including two four ways. As far as how the circuit is wired
(BobK207's comments), everything is wired with standard wiring. I'm
not sure what Romex is. The supply wires in our house are black/white/
bare ground 12 gauge copper covered in what appears to be metallic
sheath (it's silver in color).


Doug-

Sorry about the use of the term "Romex".....now called NM (non-
metallic cable)

Typically a white, a back & a bare conductor in a plastic sheath (now
yellow for 12ga & cream for 14ga)

I'm guessing that your house is a 50's / 60's unit using BX cable?

cheers
Bob

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default 3-way grounded neutral?

On Sun, 10 Feb 2008 18:43:21 -0500, "RBM" wrote:


"Doug" wrote in message
...
Thanks for all the replies. Looks like a previous post of mine got
lost. Anyway...

I am going to pull out each switch and examine to see if I can
determine exactly what's going on. I will take pictures if I can't
figure it out and post back.

One followup question -

If I am to understand what might be happening is depending on which
switch is switched on, either the white or black wire could be the hot
wire. Is this accurate?


Anything is possible. At the fixture, you should have an unswitched Neutral
regardless of what color it is. You should be able to determine which wire
because it will give you continuity to the ground conductor or metal box.
Only ungrounded (hot) goes through the switches, then returns to the
fixture. With a light bulb pigtail, test between the hot return wire from
the switch and either ground or neutral, it'll light with the switch "on"

If the light is controlled by 2 switches, then you should be seeing
some red wire too.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default 3-way grounded neutral?

On Feb 10, 11:17 am, terry wrote:
On Feb 10, 9:40 pm, BobK207 wrote:



On Feb 10, 7:42 am, Doug wrote:


Replacing a single light fixture that's controlled with two switches.
The light box has a standard black/white/ground supply wire. While
installing I found that the white wire was actually hot (and marked
with black tape) and the black was neutral. The only issue was the
only way I could read 120V from the hot wire was to ground the
circuit. This seems odd to me as none of the three way wiring
diagrams I've seen seem to require the neutral being grounded at the
fixture. The reading from hot to neutral was 60V - not sure if this
means anything or not.


Is this OK or is there something I need to look into here?


Thanks
Doug


Doug-


IMO you need to look into this a little.


The wring to the first switch box should be an un-switched hot
(black), an un-switched neutral (white) & a ground wire to the switch
& the box (if metal) .


The wiring from the first switch box to the second switch box should
be two switched hots (black & red or re-indentifed white), an un-
switched neutral (white) & a ground wire to the switch & the box (if
metal) .


So one needs 4 conductors (including the ground) between the two
switch boxes....here's where some people either get confused or
cheat. Ideally you use a three wire romex (black, red, white,
ground) or a double run of 2 wire Romex.


From the second switch box to the fixture box you should have a
switched hot (black), an un-switched neutral (white) & a ground wire
to the switch & the box (if metal) .


The setup you describe (if I'm understanding it) seems a little
off.


Is the circuit wired with Romex or single conductors (knob & tube OR
wire in conduit)?


Maybe the circuit existed as a single switch & the three way part was
added later.


Be careful, because of the limitations of 2 wire Romex systems, some
people take shortcuts on rewiring or additions that can leave you with
less than safe situations.


per John's comments a light bulb is often better than a meter


The 60v reading might be a result of a poor connection somewhere or a
digital meter giving a false reading reading.


cheers
Bob


Bob that info 'could' be misleading?

What it sound like, as mentioned in one of the replies is that black
and white wires go from the ceiling box down to the switch. One of the
wires is the 'live' feed in and the other is the 'switched live'.

Consequently when the switch is 'on' electricity flows down to the
switch through the switch and back up to the 'hot' side of the light
fixture; and the light goes on.

Reading 60 volts may be meaningless; even cheap modern digital meters
can pick up voltages due to capacitance between wires etc. A much
better way to test is to use a regular bulb.

Nothing should be wired to the ground except metal parts of wiring
boxes, ceiling boxes, metal roses etc. the ground is a safety wire.

The ground can, but only 'momentarily' be used for testing; for
example put the test bulb between a wire and ground; if it comes on
all the time (with circuit breaker for that circuit on) it is a 'non-
switched live'. If it goes on and off as you operate the switch it is
a 'switched live'.

Then turn off the circuit breaker and wire the switched live to the
light fixture (or fixtures. Cos some rooms have two or more lights
controlled by the one switch!) Turn breaker back on (or reinsert
fuse) and test.


Terry-

I composed a reply to your comments but lost it when my PC froze.

I'm pretty sure from Doug's original post there is only a white
(tagged with black) & a black wire in the fixture box under
consideration.

If Doug's only got two wires in the box & the tagged white is hot (&
switched)
and the black wire is in fact the neutral (0 volts to ground) ...then
he's got some color coding issues.

I'm not sure I'm understanding your comment

What it sound like, as mentioned in one of the replies is that black

and white wires go from the ceiling box down to the switch. One of the
wires is the 'live' feed in and the other is the 'switched live'.

Consequently when the switch is 'on' electricity flows down to the
switch through the switch and back up to the 'hot' side of the light
fixture; and the light goes on.

if he's only got two wires and one goes to the switch & the other
comes back....he's got no hot feed & no neutral. ???

It seems to me for a switch leg to exist he'd need four wires in the
box; hot in, hot to switch, switched hot back from switch & of course
the neutral.

We'll see what Doug discovers & reports back.

cheers
Bob


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default 3-way grounded neutral?



Doug-

Sorry about the use of the term "Romex".....now called NM (non-
metallic cable)

Typically a white, a back & a bare conductor in a plastic sheath (now
yellow for 12ga & cream for 14ga)

I'm guessing that your house is a 50's / 60's unit using BX cable?

cheers
Bob


Hey Bob,

House was built in 1963. Again, not sure what the cable is called,
sorry for the ignorance. Descriptions I found on the internet of BX
cable appear to have a solid metal sheath. This has more a a cloth-
like metallic texture (i know that's a bad description, sorry). I
can't get pictures until tomorrow evening so I will post back then.
Really appreciate everyone's help on this.

Doug
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default 3-way grounded neutral?


"Terry" wrote in message
...
On Sun, 10 Feb 2008 18:43:21 -0500, "RBM" wrote:


"Doug" wrote in message
...
Thanks for all the replies. Looks like a previous post of mine got
lost. Anyway...

I am going to pull out each switch and examine to see if I can
determine exactly what's going on. I will take pictures if I can't
figure it out and post back.

One followup question -

If I am to understand what might be happening is depending on which
switch is switched on, either the white or black wire could be the hot
wire. Is this accurate?


Anything is possible. At the fixture, you should have an unswitched
Neutral
regardless of what color it is. You should be able to determine which wire
because it will give you continuity to the ground conductor or metal box.
Only ungrounded (hot) goes through the switches, then returns to the
fixture. With a light bulb pigtail, test between the hot return wire from
the switch and either ground or neutral, it'll light with the switch "on"

If the light is controlled by 2 switches, then you should be seeing
some red wire too.

Only between the switches. My understanding is that he only has two
conductors and ground at the fixture. No?


  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default 3-way grounded neutral?

On Feb 10, 9:36 pm, "RBM" wrote:
"Terry" wrote in message


If the light is controlled by 2 switches, then you should be seeing
some red wire too.


Only between the switches. My understanding is that he only has two
conductors and ground at the fixture. No?


Hey RBM

The supply wire to the fixture contains three 12 gauge copper wires in
a single metallic cloth sheath:

1 black wire
1 white wire with a piece of black electrical tape stuck to it
1 bare ground

Like I said I'll have pictures tonight. Thanks for all the help.

Doug
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default 3-way grounded neutral? - followup

Hey everyone,

I've got the boxes open and am trying to sort everything about. I'm
about to get a light rig out to check for current, but thought I'd go
ahead and post this.

Switch 1 - description:

http://www.thegreatpuma.com/switch/switch1.jpg

CHAOS - this is the best way to describe what's going on in the first
box. There are three 3-way switches in this box all powering
different lights. The switch on the far right, off the edge of the
picture powers the fixture in question. There are seven - SEVEN -
cables (all with their own black/white/bare grd coming into the box).
One of the wires coming in goes to the Kitchen light switch's hot/
neutral connections. The third pole on the 3 way switch comes from a
pigtailed collection of 5 black wires, three of which head back out of
the switch, and one of which actually heads to the third pole on a
second 3-way switch (the switch on the far left - which powers the
family room overhead light), and the last of which heads to the switch
in question. As I was pulling the switch out of the box, this wire
broke and now the light won't work.



Switch 2 description:

http://www.thegreatpuma.com/switch/switch2.jpg

2 Black/White/Bare Grd wires into box:
Black and white from right side go to hot/neutral on switch.
Black from left side heads - by itself - out of the left side of the
box, and re-enters (Here I am making an assumption that this is the
same black wire) in the back of the box below where it originally came
in, and connects to nothing (strange, never seen this before). The
white wire is pigtailed (to add length) and connects directly to the
single pole on the switch.


Thanks a lot

Doug
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default 3-way grounded neutral? - followup

On Feb 11, 10:38 pm, Doug wrote:
Hey everyone,

I've got the boxes open and am trying to sort everything about. I'm
about to get a light rig out to check for current, but thought I'd go
ahead and post this.

Switch 1 - description:

http://www.thegreatpuma.com/switch/switch1.jpg

CHAOS - this is the best way to describe what's going on in the first
box. There are three 3-way switches in this box all powering
different lights. The switch on the far right, off the edge of the
picture powers the fixture in question. There are seven - SEVEN -
cables (all with their own black/white/bare grd coming into the box).
One of the wires coming in goes to the Kitchen light switch's hot/
neutral connections. The third pole on the 3 way switch comes from a
pigtailed collection of 5 black wires, three of which head back out of
the switch, and one of which actually heads to the third pole on a
second 3-way switch (the switch on the far left - which powers the
family room overhead light), and the last of which heads to the switch
in question. As I was pulling the switch out of the box, this wire
broke and now the light won't work.

Switch 2 description:

http://www.thegreatpuma.com/switch/switch2.jpg

2 Black/White/Bare Grd wires into box:
Black and white from right side go to hot/neutral on switch.
Black from left side heads - by itself - out of the left side of the
box, and re-enters (Here I am making an assumption that this is the
same black wire) in the back of the box below where it originally came
in, and connects to nothing (strange, never seen this before). The
white wire is pigtailed (to add length) and connects directly to the
single pole on the switch.

Thanks a lot

Doug


After looking into the big switch box I was able to determine that the
middle switch is not connected to the other two switches with the
exception of a pigtailed white wire.

Further, I got a light out and tested the circuits. Huge pigtail of 5
black wires in the first box is hot, regardless of any switch's
position. That means that the third pole on the first three way
switch is always hot. I could not read any current nor light the bulb
since the third pole disconnected from the pigtail in the first box,
nor could I read any current or light the light in the second box.

I'm having trouble picturing in my head how this switch is
functioning. Any ideas?

Thanks
Doug


  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default 3-way grounded neutral? - followup

On Mon, 11 Feb 2008 19:38:16 -0800 (PST), Doug
wrote:

Hey everyone,

I've got the boxes open and am trying to sort everything about. I'm
about to get a light rig out to check for current, but thought I'd go
ahead and post this.

Switch 1 - description:

http://www.thegreatpuma.com/switch/switch1.jpg

CHAOS - this is the best way to describe what's going on in the first
box. There are three 3-way switches in this box all powering
different lights. The switch on the far right, off the edge of the
picture powers the fixture in question. There are seven - SEVEN -
cables (all with their own black/white/bare grd coming into the box).
One of the wires coming in goes to the Kitchen light switch's hot/
neutral connections. The third pole on the 3 way switch comes from a
pigtailed collection of 5 black wires, three of which head back out of
the switch, and one of which actually heads to the third pole on a
second 3-way switch (the switch on the far left - which powers the
family room overhead light), and the last of which heads to the switch
in question. As I was pulling the switch out of the box, this wire
broke and now the light won't work.



Switch 2 description:

http://www.thegreatpuma.com/switch/switch2.jpg

2 Black/White/Bare Grd wires into box:
Black and white from right side go to hot/neutral on switch.
Black from left side heads - by itself - out of the left side of the
box, and re-enters (Here I am making an assumption that this is the
same black wire) in the back of the box below where it originally came
in, and connects to nothing (strange, never seen this before). The
white wire is pigtailed (to add length) and connects directly to the
single pole on the switch.


Thanks a lot

Doug


Try something like this: Maybe someone has a better suggestion


b1 goes to s1(black)
w1 to w2

b2 goes to s1(silver)
w2 goes to s1(silver)


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default 3-way grounded neutral? - followup

On Feb 11, 11:13 pm, Doug wrote:
On Feb 11, 10:38 pm, Doug wrote:



Hey everyone,


I've got the boxes open and am trying to sort everything about. I'm
about to get a light rig out to check for current, but thought I'd go
ahead and post this.


Switch 1 - description:


http://www.thegreatpuma.com/switch/switch1.jpg


CHAOS - this is the best way to describe what's going on in the first
box. There are three 3-way switches in this box all powering
different lights. The switch on the far right, off the edge of the
picture powers the fixture in question. There are seven - SEVEN -
cables (all with their own black/white/bare grd coming into the box).
One of the wires coming in goes to the Kitchen light switch's hot/
neutral connections. The third pole on the 3 way switch comes from a
pigtailed collection of 5 black wires, three of which head back out of
the switch, and one of which actually heads to the third pole on a
second 3-way switch (the switch on the far left - which powers the
family room overhead light), and the last of which heads to the switch
in question. As I was pulling the switch out of the box, this wire
broke and now the light won't work.


Switch 2 description:


http://www.thegreatpuma.com/switch/switch2.jpg


2 Black/White/Bare Grd wires into box:
Black and white from right side go to hot/neutral on switch.
Black from left side heads - by itself - out of the left side of the
box, and re-enters (Here I am making an assumption that this is the
same black wire) in the back of the box below where it originally came
in, and connects to nothing (strange, never seen this before). The
white wire is pigtailed (to add length) and connects directly to the
single pole on the switch.


Thanks a lot


Doug


After looking into the big switch box I was able to determine that the
middle switch is not connected to the other two switches with the
exception of a pigtailed white wire.

Further, I got a light out and tested the circuits. Huge pigtail of 5
black wires in the first box is hot, regardless of any switch's
position. That means that the third pole on the first three way
switch is always hot. I could not read any current nor light the bulb
since the third pole disconnected from the pigtail in the first box,
nor could I read any current or light the light in the second box.

I'm having trouble picturing in my head how this switch is
functioning. Any ideas?

Thanks
Doug


One more update before I goto bed - got the broken wire fixed. When
the light fixture is off I read current across both the hot/neutral
combo on switch one, third pole/neutral combo on switch one AND black/
neutral combo on switch two. third pole/neutral combo on switch 2
does not read when the light is off, nor does the unconnected black to
ground or neutral in switch 2.

Doug
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default 3-way grounded neutral? - followup

When you started this project, you were replacing a fixture. Was the
existing fixture and all this switching working properly at the time? You
clearly have a mess there as it appears that three sets of three way
switches were wired all illegally using multiples of two wire cables. Any
suggestions I could give would be wags without knowing where each conductor
comes from and goes to. I would, at this point get an electrician on the job
to do this.



"Doug" wrote in message
...
On Feb 11, 11:13 pm, Doug wrote:
On Feb 11, 10:38 pm, Doug wrote:



Hey everyone,


I've got the boxes open and am trying to sort everything about. I'm
about to get a light rig out to check for current, but thought I'd go
ahead and post this.


Switch 1 - description:


http://www.thegreatpuma.com/switch/switch1.jpg


CHAOS - this is the best way to describe what's going on in the first
box. There are three 3-way switches in this box all powering
different lights. The switch on the far right, off the edge of the
picture powers the fixture in question. There are seven - SEVEN -
cables (all with their own black/white/bare grd coming into the box).
One of the wires coming in goes to the Kitchen light switch's hot/
neutral connections. The third pole on the 3 way switch comes from a
pigtailed collection of 5 black wires, three of which head back out of
the switch, and one of which actually heads to the third pole on a
second 3-way switch (the switch on the far left - which powers the
family room overhead light), and the last of which heads to the switch
in question. As I was pulling the switch out of the box, this wire
broke and now the light won't work.


Switch 2 description:


http://www.thegreatpuma.com/switch/switch2.jpg


2 Black/White/Bare Grd wires into box:
Black and white from right side go to hot/neutral on switch.
Black from left side heads - by itself - out of the left side of the
box, and re-enters (Here I am making an assumption that this is the
same black wire) in the back of the box below where it originally came
in, and connects to nothing (strange, never seen this before). The
white wire is pigtailed (to add length) and connects directly to the
single pole on the switch.


Thanks a lot


Doug


After looking into the big switch box I was able to determine that the
middle switch is not connected to the other two switches with the
exception of a pigtailed white wire.

Further, I got a light out and tested the circuits. Huge pigtail of 5
black wires in the first box is hot, regardless of any switch's
position. That means that the third pole on the first three way
switch is always hot. I could not read any current nor light the bulb
since the third pole disconnected from the pigtail in the first box,
nor could I read any current or light the light in the second box.

I'm having trouble picturing in my head how this switch is
functioning. Any ideas?

Thanks
Doug


One more update before I goto bed - got the broken wire fixed. When
the light fixture is off I read current across both the hot/neutral
combo on switch one, third pole/neutral combo on switch one AND black/
neutral combo on switch two. third pole/neutral combo on switch 2
does not read when the light is off, nor does the unconnected black to
ground or neutral in switch 2.

Doug



  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 12
Default 3-way grounded neutral? - followup

On Feb 12, 7:38*am, "RBM" wrote:
When you started this project, you were replacing a fixture. Was the
existing fixture and all this switching working properly at the time? You
clearly have a mess there as it appears that three sets of three way
switches were wired all illegally using multiples of two wire cables. Any
suggestions I could give would be wags without knowing where each conductor
comes from and goes to. I would, at this point get an electrician on the job
to do this.

"Doug" wrote in message


Thanks RBM, and I already called one when I noted there were no
responses to this message when I woke up this morning.

"Working properly" can mean many different things. Yes, everything
was "working" and it still is. The question I was seeking an answer
for - I guess - is why I needed to ground the fixture out to make it
work (and whether or not such practice causes a safety hazard). I
still don't know why I need to ground the fixture out. I can't quite
figure out how the switch is working with two hot wires leading into
one three way switch. Hopefully the electrician can "shed some light"
on it.

Again, thanks for everyone's help on this.

Doug
  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default 3-way grounded neutral? - followup


"Doug" wrote in message
...
On Feb 12, 7:38 am, "RBM" wrote:
When you started this project, you were replacing a fixture. Was the
existing fixture and all this switching working properly at the time? You
clearly have a mess there as it appears that three sets of three way
switches were wired all illegally using multiples of two wire cables. Any
suggestions I could give would be wags without knowing where each
conductor
comes from and goes to. I would, at this point get an electrician on the
job
to do this.

"Doug" wrote in message


Thanks RBM, and I already called one when I noted there were no
responses to this message when I woke up this morning.

"Working properly" can mean many different things. Yes, everything
was "working" and it still is. The question I was seeking an answer
for - I guess - is why I needed to ground the fixture out to make it
work (and whether or not such practice causes a safety hazard). I
still don't know why I need to ground the fixture out. I can't quite
figure out how the switch is working with two hot wires leading into
one three way switch. Hopefully the electrician can "shed some light"
on it.
The fixture should work connected to a hot and a neutral. The neutral and
the ground are connected together at the service panel, so they are
essentially the same, except that the ground is only used as a safety to
carry fault current. Your actual problem is that the neutral conductor to
the light is open(dead). It's dificult to diagnose a problem like this when
the wiring was done in such an unorthodox fashion. With a meter, the
electrician will be able to ring out each wire, and figure out where the
open circuit is, and correct it. This is more easily done, leaving
everything connected and as is.

Again, thanks for everyone's help on this.

Doug




  #21   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 929
Default 3-way grounded neutral? - followup

On Feb 12, 4:38 am, "RBM" wrote:
When you started this project, you were replacing a fixture. Was the
existing fixture and all this switching working properly at the time? You
clearly have a mess there as it appears that three sets of three way
switches were wired all illegally using multiples of two wire cables. Any
suggestions I could give would be wags without knowing where each conductor
comes from and goes to. I would, at this point get an electrician on the job
to do this.

"Doug" wrote in message

...

On Feb 11, 11:13 pm, Doug wrote:
On Feb 11, 10:38 pm, Doug wrote:


Hey everyone,


I've got the boxes open and am trying to sort everything about. I'm
about to get a light rig out to check for current, but thought I'd go
ahead and post this.


Switch 1 - description:


http://www.thegreatpuma.com/switch/switch1.jpg


CHAOS - this is the best way to describe what's going on in the first
box. There are three 3-way switches in this box all powering
different lights. The switch on the far right, off the edge of the
picture powers the fixture in question. There are seven - SEVEN -
cables (all with their own black/white/bare grd coming into the box).
One of the wires coming in goes to the Kitchen light switch's hot/
neutral connections. The third pole on the 3 way switch comes from a
pigtailed collection of 5 black wires, three of which head back out of
the switch, and one of which actually heads to the third pole on a
second 3-way switch (the switch on the far left - which powers the
family room overhead light), and the last of which heads to the switch
in question. As I was pulling the switch out of the box, this wire
broke and now the light won't work.


Switch 2 description:


http://www.thegreatpuma.com/switch/switch2.jpg


2 Black/White/Bare Grd wires into box:
Black and white from right side go to hot/neutral on switch.
Black from left side heads - by itself - out of the left side of the
box, and re-enters (Here I am making an assumption that this is the
same black wire) in the back of the box below where it originally came
in, and connects to nothing (strange, never seen this before). The
white wire is pigtailed (to add length) and connects directly to the
single pole on the switch.


Thanks a lot


Doug


After looking into the big switch box I was able to determine that the
middle switch is not connected to the other two switches with the
exception of a pigtailed white wire.


Further, I got a light out and tested the circuits. Huge pigtail of 5
black wires in the first box is hot, regardless of any switch's
position. That means that the third pole on the first three way
switch is always hot. I could not read any current nor light the bulb
since the third pole disconnected from the pigtail in the first box,
nor could I read any current or light the light in the second box.


I'm having trouble picturing in my head how this switch is
functioning. Any ideas?


Thanks
Doug


One more update before I goto bed - got the broken wire fixed. When
the light fixture is off I read current across both the hot/neutral
combo on switch one, third pole/neutral combo on switch one AND black/
neutral combo on switch two. third pole/neutral combo on switch 2
does not read when the light is off, nor does the unconnected black to
ground or neutral in switch 2.


Doug




RBM-

Thanks for injecting some common sense / reality check into this
thread.

I agree with you, from the keyboard any suggestion is just a WAG.



Doug-

if you feel comfortable doing it....you COULD label each conductor &
determine its path / connection. More easily with a helper.

per RBM's comment three ways need a continuous neutral & a couple of
travelers.....I'm not sure what you've got & its pretty close to
impossible to unscramble it from here.

cheers
Bob

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Should My Washer Be Grounded? John Ross Home Repair 13 May 28th 07 12:37 AM
Grounded switch tap Den Murray Home Repair 9 October 18th 06 05:52 AM
4 gauge neutral wire doesn't fit in my neutral bus panel? sparty Home Repair 8 July 22nd 06 01:50 AM
Grounded (neutral) conductor two sizes smaller, why??? _firstname_@lr_dot_los-gatos_dot_ca.us Home Ownership 2 April 20th 04 02:53 AM
outlet box "grounded" to neutral 1940's ? SkyBlue Home Repair 2 August 25th 03 12:07 AM


All times are GMT +1. The time now is 11:27 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"