Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Hi all. A simple electrical question (I hope).
I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), but I'm interested in knowing the 'total' amps of the 220 circuit. I'm thinking I could measure the current on one hot, then on the other hot, and add the two values together. What I would like to do is install a permanent meter but now I'm thinking that I need two, one for each hot. If I try to measure the current by passing both hots through the 'clamp', since they are 180 degrees out of phase, won't they cancel each other out (and I would end up with the difference of the two like on the netural)? So my long winded question is this - how can I use a single 'clamp-on' style meter to measure current on a 220vac circuit? Thanks. |
#2
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
kpg wrote:
Hi all. A simple electrical question (I hope). I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), but I'm interested in knowing the 'total' amps of the 220 circuit. I'm thinking I could measure the current on one hot, then on the other hot, and add the two values together. What I would like to do is install a permanent meter but now I'm thinking that I need two, one for each hot. If I try to measure the current by passing both hots through the 'clamp', since they are 180 degrees out of phase, won't they cancel each other out (and I would end up with the difference of the two like on the netural)? So my long winded question is this - how can I use a single 'clamp-on' style meter to measure current on a 220vac circuit? Thanks. Run one through in the opposite direction. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#3
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
CJT wrote:
kpg wrote: Hi all. A simple electrical question (I hope). I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), but I'm interested in knowing the 'total' amps of the 220 circuit. I'm thinking I could measure the current on one hot, then on the other hot, and add the two values together. What I would like to do is install a permanent meter but now I'm thinking that I need two, one for each hot. If I try to measure the current by passing both hots through the 'clamp', since they are 180 degrees out of phase, won't they cancel each other out (and I would end up with the difference of the two like on the netural)? So my long winded question is this - how can I use a single 'clamp-on' style meter to measure current on a 220vac circuit? Thanks. Run one through in the opposite direction. Oh, and divide by two. -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#4
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"kpg" wrote in message oups.com... Hi all. A simple electrical question (I hope). I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), but I'm interested in knowing the 'total' amps of the 220 circuit. I'm thinking I could measure the current on one hot, then on the other hot, and add the two values together. What I would like to do is install a permanent meter but now I'm thinking that I need two, one for each hot. If I try to measure the current by passing both hots through the 'clamp', since they are 180 degrees out of phase, won't they cancel each other out (and I would end up with the difference of the two like on the netural)? So my long winded question is this - how can I use a single 'clamp-on' style meter to measure current on a 220vac circuit? If you created a loop so that you simultaneously measured one hot backwards and one forwards it ought to work. (actually I don't know, but it seems like it should) Why do you want to do this anyhow? The information is pretty useless. |
#5
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
kpg wrote:
Hi all. A simple electrical question (I hope). I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), Actually, no it won't. If you had a pure 240 load the current on the neutral would be *zero.* Since you have 120VAC branch circuits, some will have more load than others, and some will be connected to one phase and some will be connected to the opposite phase. So you will have *some* current on the neutral, but it should be significantly less than the current on either of the "hot" wires. I realize that sounds very, very strange, but google for "Edison circuit" for an explanation - a feeder to a remote subpanel is essentially a really big Edison circuit. but I'm interested in knowing the 'total' amps of the 220 circuit. It's probably slightly unbalanced. Measure one leg, then the other. I'm thinking I could measure the current on one hot, then on the other hot, and add the two values together. What I would like to do is install a permanent meter but now I'm thinking that I need two, one for each hot. If I try to measure the current by passing both hots through the 'clamp', since they are 180 degrees out of phase, won't they cancel each other out (and I would end up with the difference of the two like on the netural)? So my long winded question is this - how can I use a single 'clamp-on' style meter to measure current on a 220vac circuit? Thanks. Current is current. You measure it directly. nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#6
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Why do you want to do this anyhow? The information is pretty useless.- Hide quoted text -
Well, I can't argue with you there. For one, I like gadgets. For another, I have a 5hp compressor, some computer equipment, a full time window unit, and a part time window unit, a bunch of fluorescent lights, occasionally a hand drill or table saw. It all runs on a 30 amp branch circuit and at times the breaker gets quite warm to the touch. I thought it would be nice to be able to monitor the load on the system, i.e., the amps flowing through the feeder line. And did I mention I like gadgets? I'll do some experiments with the one backwards divide by two method. |
#7
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
On Aug 13, 11:02 pm, kpg wrote:
Why do you want to do this anyhow? The information is pretty useless.- Hide quoted text - Well, I can't argue with you there. For one, I like gadgets. For another, I have a 5hp compressor, some computer equipment, a full time window unit, and a part time window unit, a bunch of fluorescent lights, occasionally a hand drill or table saw. It all runs on a 30 amp branch circuit and at times the breaker gets quite warm to the touch. I thought it would be nice to be able to monitor the load on the system, i.e., the amps flowing through the feeder line. And did I mention I like gadgets? I'll do some experiments with the one backwards divide by two method. Each item should have a nameplate. The nameplate will give you a rough estimate of how much everything is using. Everything you have listed could be single phase, which means that each item will cause the reading to go up in only one phase of the circuit. If you do have 240V stuff it will cause both phases to go up at the same time. Measure each leg with nothing on and then turn each item on and read again. Unless you are planing to upgrading , try not to use the compressor and the AC unit at the same time. The breaker is constantly monitoring the use. |
#8
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Everything you have listed could be single phase, which means that
each item will cause the reading to go up in only one phase of the circuit. If you do have 240V stuff it will cause both phases to go up at the same time. Yes, all of the equipment is single phase, some on one leg, some on the other. This is the source of my dilemma. So what I really am asking is this: I know its meaningful to measure the current on one leg or the other, but is it meaningful to measure the current on both at the same time? Say I was drawing 8 amps on one leg, and 9 on the other. Am I using 17 amps? That seems right, but does it have any meaning? The 30 amp breaker is 30 amps per leg - So who cares if they both add up to, say, 40? I'm starting to think measuring each leg independently is the most correct solution. |
#9
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
You need a watt meter to gauge the total used wattage. The 30 amp breaker
getting warm and not tripping may mean a loose connection. Turn of the 30 amp breaker, remove from the panel. Check to be sure the pinch plate isn't turning color [getting to hot] and the matching breaker connections are good as well. Check the lugs on the breaker as well. You might fare better by calling an experience electrician to check it out. Zyp "kpg" wrote in message oups.com... Everything you have listed could be single phase, which means that each item will cause the reading to go up in only one phase of the circuit. If you do have 240V stuff it will cause both phases to go up at the same time. Yes, all of the equipment is single phase, some on one leg, some on the other. This is the source of my dilemma. So what I really am asking is this: I know its meaningful to measure the current on one leg or the other, but is it meaningful to measure the current on both at the same time? Say I was drawing 8 amps on one leg, and 9 on the other. Am I using 17 amps? That seems right, but does it have any meaning? The 30 amp breaker is 30 amps per leg - So who cares if they both add up to, say, 40? I'm starting to think measuring each leg independently is the most correct solution. |
#10
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
On Mon, 13 Aug 2007 22:59:25 -0400, Nate Nagel
wrote: kpg wrote: Hi all. A simple electrical question (I hope). I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), Actually, no it won't. If you had a pure 240 load the current on the neutral would be *zero.* Since you have 120VAC branch circuits, some will have more load than others, and some will be connected to one phase and some will be connected to the opposite phase. So you will have *some* current on the neutral, but it should be significantly less than the current on either of the "hot" wires. Isn't this what he said? Not counting the part about stray current lost through the grounding rod, which I don't really understand. It's rare, isn't it, for any current to go back through the ground or a grounding rod? I realize that sounds very, very strange, but google for "Edison circuit" for an explanation - a feeder to a remote subpanel is essentially a really big Edison circuit. |
#11
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
kpg wrote:
Everything you have listed could be single phase, which means that each item will cause the reading to go up in only one phase of the circuit. If you do have 240V stuff it will cause both phases to go up at the same time. Yes, all of the equipment is single phase, some on one leg, some on the other. This is the source of my dilemma. So what I really am asking is this: I know its meaningful to measure the current on one leg or the other, but is it meaningful to measure the current on both at the same time? Say I was drawing 8 amps on one leg, and 9 on the other. Am I using 17 amps? That seems right, but does it have any meaning? The 30 amp breaker is 30 amps per leg - So who cares if they both add up to, say, 40? I'm starting to think measuring each leg independently is the most correct solution. Nobody cares if they add up to 40 amps in your hypothetical example... simplifying a little bit here, but if you have 29 amps on one leg and 11 amps on another, the current on the neutral will actually be 18 amps (it won't actually in real life, but close enough) if you have 20 and 20, it will be zero. nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#12
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"kpg" wrote in message oups.com... Everything you have listed could be single phase, which means that each item will cause the reading to go up in only one phase of the circuit. If you do have 240V stuff it will cause both phases to go up at the same time. Yes, all of the equipment is single phase, some on one leg, some on the other. This is the source of my dilemma. So what I really am asking is this: I know its meaningful to measure the current on one leg or the other, That's how it is done. but is it meaningful to measure the current on both at the same time? You probably won't get a reading. Say I was drawing 8 amps on one leg, and 9 on the other. Am I using 17 amps? Yes. That seems right, but does it have any meaning? It means you are drawing 17 amps and the load is almost perfectly balanced. You can also measure amps on the neutral. I usually check the grounding electrode conductor also. Once in a while I find current on it and then I explain to the customer that there may be a problem somewhere. The 30 amp breaker is 30 amps per leg - So who cares if they both add up to, say, 40? If I was concerned about the load, I would care. I'm starting to think measuring each leg independently is the most correct solution. You are correct. |
#13
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
It's rare, isn't it, for any
current to go back through the ground or a grounding rod? I thought so until I did some research. There are several situations where there can be dangerous current in the ground wire at the ground rod. Obviously, a fault in the neutral will cause current to use the ground wire as a return path, but also if your neighbor has a fault in his neutral his current could be returning to the transformer via your ground rod. Moral: before disconnecting the ground wire to service the ground rod always check for current. Even if the main is off. Thanks for all the replies. |
#14
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
I don't know if any electrician reading this post
he must be laughing his head of what is total amps on 220 whatever you are reading on your amprob dummy do you have any knowledge in Ohms law. and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. and if you take 220 then split the phase of the same source/cable for 110 the neutral will carry double the current of single hot wire! Tony www.cas-environ.com "kpg" wrote in message oups.com... Hi all. A simple electrical question (I hope). I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), but I'm interested in knowing the 'total' amps of the 220 circuit. I'm thinking I could measure the current on one hot, then on the other hot, and add the two values together. What I would like to do is install a permanent meter but now I'm thinking that I need two, one for each hot. If I try to measure the current by passing both hots through the 'clamp', since they are 180 degrees out of phase, won't they cancel each other out (and I would end up with the difference of the two like on the netural)? So my long winded question is this - how can I use a single 'clamp-on' style meter to measure current on a 220vac circuit? Thanks. |
#15
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
You really should learn some punctuation before you call someone
dummy. On Aug 14, 8:36 pm, "Tony" wrote: I don't know if any electrician reading this post he must be laughing his head of what is total amps on 220 whatever you are reading on your amprob dummy do you have any knowledge in Ohms law. and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. and if you take 220 then split the phase of the same source/cable for 110 the neutral will carry double the current of single hot wire! Tonywww.cas-environ.com "kpg" wrote in message oups.com... Hi all. A simple electrical question (I hope). I have a clamp on amp meter and I'm interested in seeing how much current is used at various loads by the feeder line running to my remote garage. The feeder is has 2 hots and 1 neutral going to a sub panel that divides it into several 110 circuits. I know that the current on the neutral will be the difference between the current on the two hots (less any stray current lost to the grounding rod), but I'm interested in knowing the 'total' amps of the 220 circuit. I'm thinking I could measure the current on one hot, then on the other hot, and add the two values together. What I would like to do is install a permanent meter but now I'm thinking that I need two, one for each hot. If I try to measure the current by passing both hots through the 'clamp', since they are 180 degrees out of phase, won't they cancel each other out (and I would end up with the difference of the two like on the netural)? So my long winded question is this - how can I use a single 'clamp-on' style meter to measure current on a 220vac circuit? Thanks |
#16
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"Tony" wrote in news:tUrwi.4051$%55.3250@trnddc04:
I don't know if any electrician reading this post he must be laughing his head of what is total amps on 220 whatever you are reading on your amprob dummy Well, I'm not an electrician, this is why I asked the question. Dummy. do you have any knowledge in Ohms law. I have an Ohm meter. Does that count? and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. and if you take 220 then split the phase of the same source/cable for 110 the neutral will carry double the current of single hot wire! Um, the neutral will carry the difference between the two hot wires. The total current must be the same coming and going - do you have any knowledge in Kirchhoff's Law? |
#17
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. Not true. The two hots in a 240V circuit are 180 degrees out of phase. Only the difference between the loads on the two sides flows through the neutral. Thus, if you have equal 120V loads on each side, the neutral will have zero current flowing in it. and if you take 220 then split the phase of the same source/cable for 110 the neutral will carry double the current of single hot wire! If the neutral carried double the current it would have to be oversized compared to the hots. In reality, it is often *undersized*. The only way this can make sense is if your statement is false. This is why split-wire (aka "edison") circuits need to have the two hots on opposite legs. If they were on the same leg the neutral *would* carry the sum of the two legs, which could cause overheating. Chris |
#18
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"kpg*" wrote in message 20... "Tony" wrote in news:tUrwi.4051$%55.3250@trnddc04: I don't know if any electrician reading this post he must be laughing his head of what is total amps on 220 whatever you are reading on your amprob dummy Sorry I did not mean it as it sound Well, I'm not an electrician, this is why I asked the question. Dummy. do you have any knowledge in Ohms law. I have an Ohm meter. Does that count? NO I have few of them and I do not see myself an engineer or expert by any standard and please don't go there because I am anticipating that would be your next step and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. and if you take 220 then split the phase of the same source/cable for 110 the neutral will carry double the current of single hot wire! Um, the neutral will carry the difference between the two hot wires. The total current must be the same coming and going - do you have any knowledge in Kirchhoff's Law? It is been so long since I stody the basics of Kirechhoffs Law, That I would not atempt to go there Tony |
#19
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"Chris Friesen" wrote in message ... Tony wrote: and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. Not true. The two hots in a 240V circuit are 180 degrees out of phase. Only the difference between the loads on the two sides flows through the neutral. Thus, if you have equal 120V loads on each side, the neutral will have zero current flowing in it. I would like wet one of hand and put it on the ground ant other to the neutral to see if is carrying current in close loop circuit and use something small to close loop like 100 watt bulb that should do it yes why don't try that and let us know because what you saying 0 potential 0 current that should be perfectly safe and if you take 220 then split the phase of the same source/cable for 110 the neutral will carry double the current of single hot wire! If the neutral carried double the current it would have to be oversized compared to the hots. In reality, it is often *undersized*. The only way this can make sense is if your statement is false. This is why split-wire (aka "edison") circuits need to have the two hots on opposite legs. If they were on the same leg the neutral *would* carry the sum of the two legs, which could cause overheating. Chris |
#20
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
plonk
|
#21
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"Tony" wrote in message news:xfHwi.7146$xc5.2631@trnddc06... "Chris Friesen" wrote in message ... Tony wrote: and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. Not true. The two hots in a 240V circuit are 180 degrees out of phase. Only the difference between the loads on the two sides flows through the neutral. Thus, if you have equal 120V loads on each side, the neutral will have zero current flowing in it. I would like wet one of "YOU" hand put it on the ground ant other to the neutral to see if is carrying current in close loop circuit and use something small to close loop like 100 watt bulb that should do it yes why don't try that and let us know because what you saying 0 potential 0 current that should be perfectly safe and if you take 220 then split the phase of the same source/cable for 110 the neutral will carry double the current of single hot wire! If the neutral carried double the current it would have to be oversized compared to the hots. In reality, it is often *undersized*. The only way this can make sense is if your statement is false. This is why split-wire (aka "edison") circuits need to have the two hots on opposite legs. If they were on the same leg the neutral *would* carry the sum of the two legs, which could cause overheating. Chris |
#22
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
According to Tony :
"Tony" wrote in message news:xfHwi.7146$xc5.2631@trnddc06... "Chris Friesen" wrote in message ... Tony wrote: and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. Not true. The two hots in a 240V circuit are 180 degrees out of phase. Only the difference between the loads on the two sides flows through the neutral. Thus, if you have equal 120V loads on each side, the neutral will have zero current flowing in it. I would like wet one of "YOU" hand put it on the ground ant other to the neutral to see if is carrying current in close loop circuit and use something small to close loop like 100 watt bulb that should do it yes why don't try that and let us know because what you saying 0 potential 0 current that should be perfectly safe Even after spelling and gramatical corrections, that's linguistically and technically wrong, not to mention just plain silly. Even if the neutral was carrying current, you're not going to get a shock between the neutral and ground because the voltage difference between the neutral and ground is at most a volt or two[+]. This is true even in a 120V circuit pulling 15A. Remember, the neutral and ground are connected together in the panel. They're never going to be more than a volt or two different. Unless something goes very wrong. The neutral in a 3 wire 240V/120V circuit only carries the difference current between the two hots. If it wasn't and currents added on the neutral, then 3 wire 240V/120V circuits would be illegal. I assure you, they're not. In fact, up until a few years ago, they were _mandatory_ in the Canadian electrical code for kitchen counter outlets (and used to be fairly common practise in the US). This has only changed in Canada because of new requirements for GFCIs on kitchen counter outlets, and GFCI'ing split duplex receptacles requires expensive dual GFCI breakers. If the hots are equal current, the current in the neutral wire is _zero_. Not only that, but the voltage between neutral and ground will also be _zero_[+]. [+] presuming of course that the neutral and ground are properly connected to where they're supposed to be - connected together at the main panel. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#23
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"Chris Lewis" wrote in message ... According to Tony : "Tony" wrote in message news:xfHwi.7146$xc5.2631@trnddc06... "Chris Friesen" wrote in message ... Tony wrote: and neutral at properly design and grounded system IS carrying current it is not at zero ever unless on your screwed up system ground is carrying current which is not suppose to ever. Not true. The two hots in a 240V circuit are 180 degrees out of phase. Only the difference between the loads on the two sides flows through the neutral. Thus, if you have equal 120V loads on each side, the neutral will have zero current flowing in it. I would like wet one of "YOU" hand put it on the ground ant other to the neutral to see if is carrying current in close loop circuit and use something small to close loop like 100 watt bulb that should do it yes why don't try that and let us know because what you saying 0 potential 0 current that should be perfectly safe Even after spelling and gramatical corrections, that's linguistically and technically wrong, not to mention just plain silly. Even if the neutral was carrying current, you're not going to get a shock between the neutral and ground because the voltage difference between the neutral and ground is at most a volt or two[+]. This is true even in a 120V circuit pulling 15A. Sorry Chris for me it is kind hard to explain because of language barrier I should have said that you open neutral from the source/panel in other words you body would be in series with neutral leg/line That is tied to the load in this case light bulb. look easiest way to solve mystery is hook up one light bulb and measure the current on both wires and you will find that both weirs have same current flow, that's easy enough, Remember, the neutral and ground are connected together in the panel. They're never going to be more than a volt or two different. Unless something goes very wrong. The neutral in a 3 wire 240V/120V circuit only carries the difference current between the two hots. If it wasn't and currents added on the neutral, then 3 wire 240V/120V circuits would be illegal. I assure you, they're not. In fact, up until a few years ago, they were _mandatory_ in the Canadian electrical code for kitchen counter outlets (and used to be fairly common practise in the US). This has only changed in Canada because of new requirements for GFCIs on kitchen counter outlets, and GFCI'ing split duplex receptacles requires expensive dual GFCI breakers. If the hots are equal current, the current in the neutral wire is _zero_. Not only that, but the voltage between neutral and ground will also be _zero_[+]. [+] presuming of course that the neutral and ground are properly connected to where they're supposed to be - connected together at the main panel. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#24
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
look easiest way to solve mystery is hook up one light bulb and measure the current on both wires and you will find that both weirs have same current flow, that's easy enough, In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. In essence, the current flows up one hot, through the bulb, through the other bulb, and back down the other hot. (It's like one hot is positive, the other is negative, and the neutral is zero.) The neutral is only needed for the case where the load on each of the hot legs is not equal. Chris |
#25
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"Chris Friesen" wrote in message ... Tony wrote: look easiest way to solve mystery is hook up one light bulb and measure the current on both wires and you will find that both weirs have same current flow, that's easy enough, In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony In essence, the current flows up one hot, through the bulb, through the other bulb, and back down the other hot. (It's like one hot is positive, the other is negative, and the neutral is zero.) The neutral is only needed for the case where the load on each of the hot legs is not equal. Chris |
#26
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
"Chris Friesen" wrote in message ... Tony wrote: look easiest way to solve mystery is hook up one light bulb and measure the current on both wires and you will find that both weirs have same current flow, that's easy enough, In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony In essence, the current flows up one hot, through the bulb, through the other bulb, and back down the other hot. (It's like one hot is positive, the other is negative, and the neutral is zero.) The neutral is only needed for the case where the load on each of the hot legs is not equal. Chris And here I thought the 3-wire line from the pole was a center tap 220 volt transformer with the load carrying neatrul being the center tap [110 volts.]. Learn something new each day. -- Zyp |
#27
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Zyp wrote:
And here I thought the 3-wire line from the pole was a center tap 220 volt transformer with the load carrying neatrul being the center tap [110 volts.]. Learn something new each day. Just to clarify...it is a center-tap 220V (or 240V) transformer. However, the center tap is tied to ground. The two hots alternate positive and negative, but exactly opposite from each other. Chris |
#28
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
"Chris Friesen" wrote In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony I honestly can't tell if you're a troll or not. If the neutral could carry twice the current of the hots in normal use, then it would have to be a larger conductor than the hots. In reality, the neutral in a feeder line is often *undersized* relative to the hots. This is because it only carries the difference between the two hots, and if you have balanced loads or 240V loads there is no current in the neutral. If that isn't enough of an explanation, I give up. This thread has gone long enough. Please don't do your own wiring. Chris |
#29
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Chris we are not going any way so I am not going to comment
however? there is no such thing in AC circuit as positive and negative the on three phase system or single phase, the phases are out of phase by 90 degree that is it! no positive or negative just about 6-7 months ago I had job replacing 25 hp Refrigeration compressor that runs on 480 three phase and guess what one phase was neutral, amazing isn't and you telling me neutral is not carrying current I afraid you will need eat few more Winnies by have nice day Tony "Chris Friesen" wrote in message ... Tony wrote: "Chris Friesen" wrote In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony I honestly can't tell if you're a troll or not. If the neutral could carry twice the current of the hots in normal use, then it would have to be a larger conductor than the hots. In reality, the neutral in a feeder line is often *undersized* relative to the hots. This is because it only carries the difference between the two hots, and if you have balanced loads or 240V loads there is no current in the neutral. If that isn't enough of an explanation, I give up. This thread has gone long enough. Please don't do your own wiring. Chris |
#30
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
"Chris Friesen" wrote in message ... Tony wrote: look easiest way to solve mystery is hook up one light bulb and measure the current on both wires and you will find that both weirs have same current flow, that's easy enough, In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony Have YOU tried that experiment? In essence, the current flows up one hot, through the bulb, through the other bulb, and back down the other hot. (It's like one hot is positive, the other is negative, and the neutral is zero.) The neutral is only needed for the case where the load on each of the hot legs is not equal. Chris -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#31
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
Chris we are not going any way so I am not going to comment however? there is no such thing in AC circuit as positive and negative the on three phase system or single phase, the phases are out of phase by 90 degree that is it! no positive or negative just about 6-7 months ago I had job replacing 25 hp Refrigeration compressor that runs on 480 three phase and guess what one phase was neutral, amazing isn't and you telling me neutral is not carrying current I afraid you will need eat few more Winnies by have nice day Tony May I suggest you read this: ? http://en.wikipedia.org/wiki/Split_phase "Chris Friesen" wrote in message ... Tony wrote: "Chris Friesen" wrote In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony I honestly can't tell if you're a troll or not. If the neutral could carry twice the current of the hots in normal use, then it would have to be a larger conductor than the hots. In reality, the neutral in a feeder line is often *undersized* relative to the hots. This is because it only carries the difference between the two hots, and if you have balanced loads or 240V loads there is no current in the neutral. If that isn't enough of an explanation, I give up. This thread has gone long enough. Please don't do your own wiring. Chris -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#32
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"Tony" wrote in message news:2Ymxi.18$A57.15@trnddc04... Chris we are not going any way so I am not going to comment however? there is no such thing in AC circuit as positive and negative the on three phase system or single phase, the phases are out of phase by 90 degree that is it! no positive or negative just about 6-7 months ago I had job replacing 25 hp Refrigeration compressor that runs on 480 three phase and guess what one phase was neutral, amazing isn't and you telling me neutral is not carrying current I afraid you will need eat few more Winnies by have nice day Tony sounds like a "b" phase ground a and c phase to ground 480v b phase 0v In 3 phase panels you can also have a high phase between a and b b and c a and c all 240v a and c to neutral 120v b to neutral 240v problem is Chris is still right |
#33
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
Chris we are not going any way so I am not going to comment however? there is no such thing in AC circuit as positive and negative the on three phase system or single phase, the phases are out of phase by 90 degree that is it! no positive or negative just about 6-7 months ago I had job replacing 25 hp Refrigeration compressor that runs on 480 three phase and guess what one phase was neutral, amazing isn't and you telling me neutral is not carrying current I afraid you will need eat few more Winnies by have nice day Tony He is simply trying to give you a simplified analogy. The legs on a three phase system are 120 degrees out of phase with each other. On a single phase system the legs are 180 degrees out of phase with each other. |
#34
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"George" wrote in message . .. .. On a single phase system the legs are 180 degrees out of phase with each other. When you say this you need to add ", referenced to ground (neutral)" |
#35
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
On Aug 17, 8:04 pm, George wrote:
Tony wrote: Chris we are not going any way so I am not going to comment however? there is no such thing in AC circuit as positive and negative the on three phase system or single phase, the phases are out of phase by 90 degree that is it! no positive or negative just about 6-7 months ago I had job replacing 25 hp Refrigeration compressor that runs on 480 three phase and guess what one phase was neutral, amazing isn't and you telling me neutral is not carrying current I afraid you will need eat few more Winnies by have nice day Tony He is simply trying to give you a simplified analogy. The legs on a three phase system are 120 degrees out of phase with each other. On a single phase system the legs are 180 degrees out of phase with each other. I can't believe you guys have taken this crazy discussion with Tony to 3 phases. He obviously doesn't even understand 2 phases. When he said: "It is been so long since I stody the basics of Kirechhoffs Law, That I would not atempt to go there Tony " it became obvious he's totally unqualified to be giving advice or opinions on current flowing in a shared neutral. Kirchoff's Law is quite simple and elementary: The sum of all currents at any node must be zero. Which is to say, current can't pile up, it has to go somewhere. In the case of a 240V shared neutral settup, that means whatever current goes up one hot must either go back on the other hot, which is out of phase or back via the neutral. And to go back to the example Chris gave earlier, on a shared neutral, if you put a 100W light bulb from one hot to neutral and another 100W light bulb on the other hot to neutral, you will have zero amps flowing in the neutral because the load is balanced. The current flows from one hot, through the first bulb, through the second and back via the other hot. Now connect another light bulb from one hot to neutral, then you will have current flow in the neutral. Very basic. |
#36
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
In article , "SRN" wrote:
"George" wrote in message ... .. On a single phase system the legs are 180 degrees out of phase with each other. When you say this you need to add ", referenced to ground (neutral)" No, you don't. The statement refers solely to the phase difference between the two hot legs, which has absolutely nothing to do with either's potential difference from neutral. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#37
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Chris Friesen wrote:
Zyp wrote: And here I thought the 3-wire line from the pole was a center tap 220 volt transformer with the load carrying neatrul being the center tap [110 volts.]. Learn something new each day. Just to clarify...it is a center-tap 220V (or 240V) transformer. However, the center tap is tied to ground. The two hots alternate positive and negative, but exactly opposite from each other. Chris Hmmm... you're sort of right, they do "alternate" but 60 times a second. What's the frequency of the AC current got to do with it? -- Zyp |
#38
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
|
#39
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
Tony wrote:
"Chris Friesen" wrote in message ... Tony wrote: look easiest way to solve mystery is hook up one light bulb and measure the current on both wires and you will find that both weirs have same current flow, that's easy enough, In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony In essence, the current flows up one hot, through the bulb, through the other bulb, and back down the other hot. (It's like one hot is positive, the other is negative, and the neutral is zero.) The neutral is only needed for the case where the load on each of the hot legs is not equal. Chris Tony You are off your soundings there bud. In case your not nautically inclined that means you are out of your depth. If you wire two sixty watt bulbs in series across a two forty volt circuit they will burn just fine. Now connect a neutral to the connection that is between the two bulbs and if the bulbs are truly identical then no current will flow on the neutral. Here's a little experiment for you to try. You can build an Edison circuit from two twelve volt batteries and two twelve volt lamps. Wire them all in series. The two twelve volt lights will light just fine. connect a volt meter across the connection between the lights and the connection between the batteries. It will measure six volts. Now change the leads and settings on your multimeter from voltage to current and measure across the same two points. Applying the ammeter as a neutral conductor will not change the current significantly. The only current flowing will be caused by the slight differences in manufacture between the two lights and the two batteries. -- Tom Horne |
#40
Posted to alt.home.repair
|
|||
|
|||
measuring current in a 220 ac circuit
"Chris Friesen" wrote
In a 3-wire circuit you have two hots and a neutral. If you put a light bulb between each of the hots and the neutral, there will be no current flow in the neutral. O yes it will and twice the hot legs, as I siad try and do little expirement on your onw and find out for your self Tony "Chris Friesen" wrote in message ... I honestly can't tell if you're a troll or not. If the neutral could carry twice the current of the hots in normal use, then it would have to be a larger conductor than the hots. In reality, the neutral in a feeder line is often *undersized* relative to the hots. This is because it only carries the difference between the two hots, and if you have balanced loads or 240V loads there is no current in the neutral. If that isn't enough of an explanation, I give up. This thread has gone long enough. Please don't do your own wiring. Chris Tony wrote: Chris we are not going any way so I am not going to comment however? there is no such thing in AC circuit as positive and negative the on three phase system or single phase, the phases are out of phase by 90 degree that is it! no positive or negative just about 6-7 months ago I had job replacing 25 hp Refrigeration compressor that runs on 480 three phase and guess what one phase was neutral, amazing isn't and you telling me neutral is not carrying current I afraid you will need eat few more Winnies by have nice day Tony Tony If you think all grounded current carrying conductors are neutrals then you are inadequately trained. A corner grounded Delta transformer set, such as the one that probably supplied your refrigeration compressor, cannot supply a neutral. The only time phases will be ninety degrees out of phase is in a Scot T transformer arrangement. The two hundred and forty volt, single phase, transformers that are used to supply homes in North American practice are supplied from a single phase on the primary side. How can a transformer with only two windings produce a phase difference across it's output winding? If you have worked with buck boost transformers you know that a single phase transformer can be tapped on it's secondary side to supply several different voltages and although it is rarely done those different voltages can be from the same transformer secondary. I could ground any one of the taps as long as I ground only one without effecting the voltage output available from each portion of the secondary winding. If it produces several voltages on it's output does that make it multi phase? Voltage is usually measured to ground because it is that voltage the insulation must successfully withstand. If you measure the outputs against each other using an oscilloscope you will find that the wave forms are identical in the horizontal or time domain and that they differ only in their amplitude as an expression of their voltage. -- Tom Horne |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Measuring load on a circuit breaker. | Home Repair | |||
Measuring load on a circuit breaker. | Home Repair | |||
Measuring Load Capacitance In-Circuit | Electronics Repair | |||
Layers in circuit board and current. | Electronics Repair | |||
Layers in circuit board and current. | Electronics Repair |