Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
Question: I have installed central air and I no longer need to 220v
window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? Thanks in Advance, as always!! -A |
#2
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
In article .com, Guy Noir wrote:
Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. No bare wire?? With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) That is not correct. Grounding conductors larger than 6AWG are permitted to be re-identified in that manner, but not 6AWG and smaller. [2005 NEC, Article 250.119] So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? No. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#3
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
"Guy Noir" wrote in message oups.com... Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? Yes, you'll be fine. Make sure the green is continuous and no red is visible. Isn't there an equipment grounding conductor in the box now? |
#4
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
On Jul 30, 1:07 pm, "John Grabowski" wrote:
"Guy Noir" wrote in message oups.com... Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? Yes, you'll be fine. Make sure the green is continuous and no red is visible. Isn't there an equipment grounding conductor in the box now? Unfortunately, no there is no bare or green conductor. -A |
#5
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
According to Guy Noir :
On Jul 30, 1:07 pm, "John Grabowski" wrote: "Guy Noir" wrote in message oups.com... Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? Yes, you'll be fine. Make sure the green is continuous and no red is visible. Isn't there an equipment grounding conductor in the box now? Unfortunately, no there is no bare or green conductor. I'm talking from the perspective of absolutely strict code compliance from the perspective of an anal inspector: Legally, you can't use a black or red wire as neutral, but you can use white for hot (with suitable marking). You can't use any of them as ground, nor can you use a bare ground for anything else. In other words, you could make the black hot, white neutral, but you can't use the red as a ground (or neutral). Also, new/revised work has to be grounded (or equivalent). "Or equivalent" is your back door: 1) Abandon both ends of the red conductor (cap or tape it off - someday in the future you might need that red wire again - so don't cut it off.) 2) use a GFCI outlet. 3) use black for hot, white for neutral on the "line" side of the GFCI. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#6
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
I'd be interested in hearing about exactly what Mr. Guy plans
to do at -each- end of the "run" before commenting on color codes. P On Mon, 30 Jul 2007 17:30:13 -0000, Guy Noir wrote: Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? Thanks in Advance, as always!! -A "Mit der Dummheit kaempfen Goetter selbst vergebens!" -Friedrich Schiller |
#7
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
Chris Lewis wrote:
According to Guy Noir : On Jul 30, 1:07 pm, "John Grabowski" wrote: "Guy Noir" wrote in message oups.com... Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? Yes, you'll be fine. Make sure the green is continuous and no red is visible. Isn't there an equipment grounding conductor in the box now? Unfortunately, no there is no bare or green conductor. I'm talking from the perspective of absolutely strict code compliance from the perspective of an anal inspector: Legally, you can't use a black or red wire as neutral, but you can use white for hot (with suitable marking). You can't use any of them as ground, nor can you use a bare ground for anything else. In other words, you could make the black hot, white neutral, but you can't use the red as a ground (or neutral). Also, new/revised work has to be grounded (or equivalent). "Or equivalent" is your back door: 1) Abandon both ends of the red conductor (cap or tape it off - someday in the future you might need that red wire again - so don't cut it off.) 2) use a GFCI outlet. 3) use black for hot, white for neutral on the "line" side of the GFCI. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. I'd recommend the OP check more carefully to see if there is indeed a bare ground conductor in that Romex, perhaps one that was clipped flush with the jacket for some reason by the original installer. If the Romex has a PVC jacket vs. cloth, there should certainly be a ground conductor in it. The print on the PVC jacket should indicate something like 12-3 with ground. If the Romex is old enough to have a cloth jacket then perhaps it really doesn't have a ground, though I've seen a lot of cloth jacketed Romex that has the expected bare ground conductor. Pete C. |
#8
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
Pete C. wrote:
.... I'd recommend the OP check more carefully to see if there is indeed a bare ground conductor in that Romex, perhaps one that was clipped flush with the jacket for some reason by the original installer. If the Romex has a PVC jacket vs. cloth, there should certainly be a ground conductor in it. The print on the PVC jacket should indicate something like 12-3 with ground. If the Romex is old enough to have a cloth jacket then perhaps it really doesn't have a ground, though I've seen a lot of cloth jacketed Romex that has the expected bare ground conductor. And I've seen a lot of plastic-jacketed romex w/o the ground, too. It certainly wouldn't be at all hard for all the wiring except the ends coming out of the handy box and in the panel to be inaccessible to check, but if can be seen, that would tell OP if he can't tell. But, if the original installer cut it off so short he can't even tell there was one there, it really won't help much any way, will it? -- |
#9
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
dpb wrote:
Pete C. wrote: ... I'd recommend the OP check more carefully to see if there is indeed a bare ground conductor in that Romex, perhaps one that was clipped flush with the jacket for some reason by the original installer. If the Romex has a PVC jacket vs. cloth, there should certainly be a ground conductor in it. The print on the PVC jacket should indicate something like 12-3 with ground. If the Romex is old enough to have a cloth jacket then perhaps it really doesn't have a ground, though I've seen a lot of cloth jacketed Romex that has the expected bare ground conductor. And I've seen a lot of plastic-jacketed romex w/o the ground, too. It certainly wouldn't be at all hard for all the wiring except the ends coming out of the handy box and in the panel to be inaccessible to check, but if can be seen, that would tell OP if he can't tell. But, if the original installer cut it off so short he can't even tell there was one there, it really won't help much any way, will it? -- It depends... If it's original construction and it doesn't have a ground he's out of luck. If it's original construction and the ground was clipped short he's out of luck unless he has some ambition for more work. If there is a ground that was clipped short and it's in a remodel box he can pull the box and potentially have enough slack to reterminate the box with the ground. If it really doesn't have a ground, but it was pulled into a remodel box he may be able to use the wire to pull in new appropriate wire. Pete C. |
#10
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
"Chris Lewis" wrote in message ... According to Guy Noir : On Jul 30, 1:07 pm, "John Grabowski" wrote: "Guy Noir" wrote in message oups.com... Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? Yes, you'll be fine. Make sure the green is continuous and no red is visible. Isn't there an equipment grounding conductor in the box now? Unfortunately, no there is no bare or green conductor. I'm talking from the perspective of absolutely strict code compliance from the perspective of an anal inspector: Legally, you can't use a black or red wire as neutral, but you can use white for hot (with suitable marking). You can't use any of them as ground, nor can you use a bare ground for anything else. How exactly could using a red as a ground hurt anything? The absolute worst senerio is that someone in the future will be working on the circuit and find the red isn't hot like he expected, and that the ground is missing. If he isn't bright enough to put the two together (and the green tape has fallen off the red wire) he will have to fall back on your suggestion, but there is no way any harm can result. |
#11
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
In article , "Toller" wrote:
How exactly could using a red as a ground hurt anything? At some other point in the circuit, somebody may someday decide to connect a hot conductor to it, perhaps. The absolute worst senerio is that someone in the future will be working on the circuit and find the red isn't hot like he expected, and that the ground is missing. If he isn't bright enough to put the two together (and the green tape has fallen off the red wire) he will have to fall back on your suggestion, but there is no way any harm can result. I'll agree that it's unlikely, but as they say, never say never. Categorical statements are always false. g In any event, whether harm can result or not is moot. It's specifically prohibited by the NEC. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#12
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
Thanks for all of the suggestions and comments folks. I truly do
appreciate the input. To answer a few questions.... Yes, you'll be fine. Make sure the green is continuous and no red is visible. Isn't there an equipment grounding conductor in the box now? The outlet, and the feed to the outlet at the breaker panel, no. The sub panel is grounded (New sub panel with proper neutral seperation, ground, etc) If there is a ground that was clipped short and it's in a remodel box he can pull the box and potentially have enough slack to reterminate the box with the ground. No, it's a remodel job that was done and AFAIK, the ground was not clipped, it's just not there. If the Romex has a PVC jacket vs. cloth, there should certainly be a ground conductor in it. The print on the PVC jacket should indicate something like 12-3 with ground. If the Romex is old enough to have a cloth jacket then perhaps it really doesn't have a ground, though I've seen a lot of cloth jacketed Romex that has the expected bare ground conductor. The wire appears to be cloth covered, however the conductors appear to be PVC sheathed. How exactly could using a red as a ground hurt anything? The absolute worst senerio is that someone in the future will be working on the circuit and find the red isn't hot like he expected, and that the ground is missing. If he isn't bright enough to put the two together (and the green tape has fallen off the red wire) he will have to fall back on your suggestion, but there is no way any harm can result. The only thing I could see in the future would be if someone were to tap into the line somewhere under the house where there would obviously be no markings. I'm more concerned about a house inspector dinging me on this if I ever go to sell the house. Thanks again -A |
#13
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
According to Toller :
"Chris Lewis" wrote in message ... I'm talking from the perspective of absolutely strict code compliance from the perspective of an anal inspector: Legally, you can't use a black or red wire as neutral, but you can use white for hot (with suitable marking). You can't use any of them as ground, nor can you use a bare ground for anything else. How exactly could using a red as a ground hurt anything? I can't think of any compelling "bad scenarios" with sane individuals, but there must have been a reason for NEC not permitting the marking of a color normally used for hot as ground (or neutral). It could simply be that they wanted _no_ exceptions whatsoever for color codes, except that they decided that permitting the "recolor" of a white wire as hot was essential for certain switch circuits, and it'd cost the industry too much otherwise, whereas needing to allow the reverse was too rare to worry about. The worst case in this scenario might be that someone mucking with the panel notices the red on the ground bus, thinks that it is the cause of the whatever it was that made them look in the panel (mutters "idiot!" under their breath), immediately jumps to the conclusion it's the cause of their problem, and moves it to a breaker. That could have rather unpleasant consequences, the least being that they've case-energized everything on that circuit. There's a reason why I said "absolutely strict code compliance" which such emphasis. -- Chris Lewis, Age and Treachery will Triumph over Youth and Skill It's not just anyone who gets a Starship Cruiser class named after them. |
#14
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
The only thing I could see in the future would be if someone were to tap into the line somewhere under the house where there would obviously be no markings. I'm more concerned about a house inspector dinging me on this if I ever go to sell the house. Geez, I wish I could have found a house inspector that good when I bought my house! They stick the tester in a few outlets, and if the lights look right they are happy. At least that is my experience. |
#16
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
How about making a bare out of the red? You're going to pull the red wire from the sheathing, strip it, and stuff it back in? |
#17
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
It looks like you've got lots of help with your question about wire color.
I presume that the 220v circuit was protected with a 30A breaker, or such? Be sure to replace that with an appropriate-sized breaker for your new outlet. If it's a 20A or 15A receptacle, use a proper breaker of that rating for the re-purposed circuit. Good luck, Sparky |
#18
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
In article , Terry wrote:
How about making a bare out of the red? Nope, that doesn't meet Code either, unless you have some way to strip *all* of the insulation off of it, from beginning to end. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#19
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
In article .net, SparkyGuy wrote:
It looks like you've got lots of help with your question about wire color. I presume that the 220v circuit was protected with a 30A breaker, or such? Be sure to replace that with an appropriate-sized breaker for your new outlet. If it's a 20A or 15A receptacle, use a proper breaker of that rating for the re-purposed circuit. Irrelevant -- if he truly does not have a bare wire, he cannot make a Code-compliant installation with this cable. Period. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#20
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
"Doug Miller" wrote in message et... In article .net, SparkyGuy wrote: It looks like you've got lots of help with your question about wire color. I presume that the 220v circuit was protected with a 30A breaker, or such? Be sure to replace that with an appropriate-sized breaker for your new outlet. If it's a 20A or 15A receptacle, use a proper breaker of that rating for the re-purposed circuit. Irrelevant -- if he truly does not have a bare wire, he cannot make a Code-compliant installation with this cable. Period. Since this post began I have read 250.119 twice. I see no specific limitation on taping the red wire green regardless of the size. In fact 250.119(B) specifically permits it under qualified supervision |
#21
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
In article , "John Grabowski" wrote:
Since this post began I have read 250.119 twice. I see no specific limitation on taping the red wire green regardless of the size. In fact 250.119(B) specifically permits it under qualified supervision "Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered or insulated. Individually covered or insulated equipment grounding conductors shall have a CONTINUOUS outer finish that is either green or green with one or more yellow stripes except as permitted in this section." [2005 NEC, Article 250.119 (emphasis added)] IOW -- if it's insulated at all, the insulation must be green, or green with yellow tracer(s), from beginning to end. A wire with red insulation, either remarked as green at the ends, or stripped bare at the ends, does not qualify because it does not "have a continuous outer finish that is green or ...". 250.119(A) provides an exception for conductors larger than 6AWG, permitting them to be reidentified as equipment grounding conductors at the time of *installation*. The exception in 250.119(B) applies, in the first place, "where the conditions of maintenance and supervision ensure that only qualified persons service the installation." These conditions do not exist in a residential setting. In the second place, that exception, like the one in 250.119(A), applies at the time of installation *only*. In no case does the Code permit remarking of a conductor as an equipment grounding conductor in an *existing* system. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#22
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
"Doug Miller" wrote in message . net... In article , "John Grabowski" wrote: Since this post began I have read 250.119 twice. I see no specific limitation on taping the red wire green regardless of the size. In fact 250.119(B) specifically permits it under qualified supervision "Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered or insulated. Individually covered or insulated equipment grounding conductors shall have a CONTINUOUS outer finish that is either green or green with one or more yellow stripes except as permitted in this section." [2005 NEC, Article 250.119 (emphasis added)] IOW -- if it's insulated at all, the insulation must be green, or green with yellow tracer(s), from beginning to end. A wire with red insulation, either remarked as green at the ends, or stripped bare at the ends, does not qualify because it does not "have a continuous outer finish that is green or ...". 250.119(A) provides an exception for conductors larger than 6AWG, permitting them to be reidentified as equipment grounding conductors at the time of *installation*. The exception in 250.119(B) applies, in the first place, "where the conditions of maintenance and supervision ensure that only qualified persons service the installation." These conditions do not exist in a residential setting. In the second place, that exception, like the one in 250.119(A), applies at the time of installation *only*. In no case does the Code permit remarking of a conductor as an equipment grounding conductor in an *existing* system. I'd do it anyway because I think the inspectors would find it acceptable. I remember back in the eighties many companies were specifying isolated ground receptacles. The contractors were installing 3 wire BX and Romex with the r ed wire re-identified with green tape and they passed inspection. At that time the wire marking code references were less liberal than they are now. Now of course hospital BX and MC cable are readily available with insulated grounding conductors. |
#23
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
Doug Miller wrote:
In article .com, Guy Noir wrote: Question: I have installed central air and I no longer need to 220v window AC outlets. They are wired with romax and the colors of the conductor insulation are Black, Red, and White. No bare wire?? With the current cost of copper, I hate to replace these runs. Standard color codes are of course black, white, copper/gnd. If I rewire this for 110v what colors should I put where? I read somewhere in the code that you can re-identify a cable with colored tape (green for instance for the wire used for ground) That is not correct. Grounding conductors larger than 6AWG are permitted to be re-identified in that manner, but not 6AWG and smaller. [2005 NEC, Article 250.119] So, should I use black-hot white-neutral and red-green taped at each end for ground? Does this meet NEC code or at least come close?? No. Doesn't meet letter of the code, but I'd not hesitate to do so, myself. If certainly meets everything but the color and the electrons don't know the difference. The marking needs to be substantial enough so as to be relied upon for staying there. My personal opinion on it is that it is old work, not new and there's no inspector I've ever seen who wouldn't make reasonable allowance for that... Others opinions/choices/etc., may differ of course... -- |
#24
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
In article , "John Grabowski" wrote:
I'd do it anyway because I think the inspectors would find it acceptable. I think I'd check with the inspector before making assumptions about what he would or would not find acceptable. g -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
#25
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
Doug Miller wrote:
In article , "John Grabowski" wrote: I'd do it anyway because I think the inspectors would find it acceptable. I think I'd check with the inspector before making assumptions about what he would or would not find acceptable. g What have you lost? 5 minutes and a couple pieces of green tape or a dab of paint. As noted, w/ old work and done in a workmanlike way, I've not run across an inspector who would require pulling a new cable simply for the sake of running new cable... -- |
#26
Posted to alt.home.repair
|
|||
|
|||
Rewire 220v to 110v Color question
"dpb" wrote in message ... Doug Miller wrote: In article , "John Grabowski" wrote: I'd do it anyway because I think the inspectors would find it acceptable. I think I'd check with the inspector before making assumptions about what he would or would not find acceptable. g What have you lost? 5 minutes and a couple pieces of green tape or a dab of paint. As noted, w/ old work and done in a workmanlike way, I've not run across an inspector who would require pulling a new cable simply for the sake of running new cable... Considering that the conductor we are talking about is non-current carrying it seems practical. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
220v Well Pump on 110v? | Home Repair | |||
Question on adding 220V and 110V circuits to garage | Home Repair | |||
220V for 110V cooktop? | Home Repair | |||
110v vs. 220v for welder | Metalworking | |||
Fwd: Dangerous way of getting 220V from 110V outlets | Metalworking |