Running service from house to garage
I am running service from my house to a detached garage through 90' of
buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. |
#2
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On Mar 18, 2:54 pm, wrote:
I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. I imagine that lots of people will weigh in on this, here's my opinion: 1) I hate to run romex through conduit. It is usually easier and cheaper to run THHN wires, and they are easier to pull back out and replace. I thought that there was a code issue with running romex through conduit too, but I don't know that for sure. 2) You could have run two hots & a neutral, with wire or romex - so yes, 12/3 would have been OK 3) Because you don't know what the future holds, I would have run at least 10 or even 8 gauge wire out there, and put in a small subpanel. I know that copper prices had spiked, but they have come down now. It's not like we are talking hundreds of dollars. 4) You could use either of the romexes you ran to have a 240v 15A circuit, but I don't know how much good that would be. What would you use it for? Also, too late for you, but I like to run small circuits to garages through IMC. It only needs to be buried 6" deep. JK |
#3
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
A buried conduit is considered a wet location, except possibly in dry areas.
Romex has type thhn conductors in it, which are NOT for use in wet locations. You don't give the size of the conduit, but without installing panels or grounding rods, you can run two 20 amp circuits, which could be accomplished with a 12/3 UF cable or four individual # 12 THWN or similar conductors. This would give you 20 amps 120/240 volts and would be adequate for what you've described wrote in message ups.com... I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. |
#4
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
The conduit is 3/4"
|
#5
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On Mar 18, 2:54 pm, wrote:
I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. You _should_ do it right to begin with rather than "getting by" w/ a substandard installation (that, of course, imo ). You're already talking of upgrading and will undoubtedly want more in the future once you have power at all. As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. |
#6
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On Mar 18, 4:15 pm, "dpb" wrote:
On Mar 18, 2:54 pm, wrote: I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. You _should_ do it right to begin with rather than "getting by" w/ a substandard installation (that, of course, imo ). You're already talking of upgrading and will undoubtedly want more in the future once you have power at all. As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. Please elaborate, why isn't 3/4" conduit big enough. Or rather not big enough for what exactly?? |
#7
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
If it's a decent, fairly straight and clean run, you could pull 3 #8 and
1#10 for the ground,THWN conductors, use a six circuit panel two ground rods connected with #8 and a 40 amp breaker in the main panel wrote in message ups.com... The conduit is 3/4" |
#8
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
3/4 " isn't big enough to pull a 12/3 UF cable
wrote in message oups.com... On Mar 18, 4:15 pm, "dpb" wrote: On Mar 18, 2:54 pm, wrote: I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. You _should_ do it right to begin with rather than "getting by" w/ a substandard installation (that, of course, imo ). You're already talking of upgrading and will undoubtedly want more in the future once you have power at all. As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. Please elaborate, why isn't 3/4" conduit big enough. Or rather not big enough for what exactly?? |
#9
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
wrote in message ups.com... I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. What size is your conduit? |
#10
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On Mar 18, 4:29 pm, "RBM" rbm2(remove wrote:
3/4 " isn't big enough to pull a 12/3 UF cable wrote in message oups.com... On Mar 18, 4:15 pm, "dpb" wrote: On Mar 18, 2:54 pm, wrote: I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. You _should_ do it right to begin with rather than "getting by" w/ a substandard installation (that, of course, imo ). You're already talking of upgrading and will undoubtedly want more in the future once you have power at all. As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. Please elaborate, why isn't 3/4" conduit big enough. Or rather not big enough for what exactly?? As I mentioned the run is about 90' with a total of 4 90°s in it (all pretty tight). At this point it wouldn't be too difficult to dig up two of the 90's and cut the conduit which would give me one straight long run and two short ones each with one 90 where it enters the buildings. I pulled on the existing romex and couldn't budge it so I assume I'll have to shorten the run as mentioned to get these out. If the conduit isn't big enough to pull #12/3 UF through. Is it more likely that I would be able to pull 4 separate #12 THWN conductors through? Are these pulled one at a time or all together? |
#11
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
You always pull together. The 12/3 UF is a flat oval. If it were round, it
would fit fine. Individual conductors, preferably stranded, will fit fine and pull easily wrote in message oups.com... On Mar 18, 4:29 pm, "RBM" rbm2(remove wrote: 3/4 " isn't big enough to pull a 12/3 UF cable wrote in message oups.com... On Mar 18, 4:15 pm, "dpb" wrote: On Mar 18, 2:54 pm, wrote: I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. You _should_ do it right to begin with rather than "getting by" w/ a substandard installation (that, of course, imo ). You're already talking of upgrading and will undoubtedly want more in the future once you have power at all. As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. Please elaborate, why isn't 3/4" conduit big enough. Or rather not big enough for what exactly?? As I mentioned the run is about 90' with a total of 4 90°s in it (all pretty tight). At this point it wouldn't be too difficult to dig up two of the 90's and cut the conduit which would give me one straight long run and two short ones each with one 90 where it enters the buildings. I pulled on the existing romex and couldn't budge it so I assume I'll have to shorten the run as mentioned to get these out. If the conduit isn't big enough to pull #12/3 UF through. Is it more likely that I would be able to pull 4 separate #12 THWN conductors through? Are these pulled one at a time or all together? |
#12
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
dpb wrote:
As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. You could stuff four #8 THWN-2 wires in there pretty easily, and #8 is easy to work with. That would give you a 40A service with a separate ground. Or run 2 black sixes and a white #8 for a 50A (60A? I don't remember) service and establish a new ground at the garage. Either of these would be legal with 3/4" conduit. Bob |
#13
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
He only needs #10 for the ground conductor for either #8 or #6. I'm not sure
if it's "still" legal to not run a ground with the circuit conductors, but if he does that, nothing conductive can go between the buildings, including catv, telephone, metal water line, etc. "zxcvbob" wrote in message ... dpb wrote: As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. You could stuff four #8 THWN-2 wires in there pretty easily, and #8 is easy to work with. That would give you a 40A service with a separate ground. Or run 2 black sixes and a white #8 for a 50A (60A? I don't remember) service and establish a new ground at the garage. Either of these would be legal with 3/4" conduit. Bob |
#14
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On Mar 18, 5:38 pm, "RBM" rbm2(remove wrote:
He only needs #10 for the ground conductor for either #8 or #6. I'm not sure if it's "still" legal to not run a ground with the circuit conductors, but if he does that, nothing conductive can go between the buildings, including catv, telephone, metal water line, etc. "zxcvbob" wrote in message ... dpb wrote: As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. You could stuff four #8 THWN-2 wires in there pretty easily, and #8 is easy to work with. That would give you a 40A service with a separate ground. Or run 2 black sixes and a white #8 for a 50A (60A? I don't remember) service and establish a new ground at the garage. Either of these would be legal with 3/4" conduit. Bob Your starting to lose me here (noting conductive can go between th buildings...) In the same trench (outside of the conduit) I ran a coax line. Not sure if this impacts things or not. Correct me if I'm wrong but it sounds like it would be acceptable (and simpliest) to pull out the romex and push 4 #12 THWN conductors through (black, red, white, ??). (Is #12 easy to push or will I need to fish it through?) This would give me 2 120V 20 amp supply lines, one common neutral and a common ground. Without adding a subpanel I could splice these into romex in the garage. But as recommended it would be better to push #10 or #8 to increase the amperage and add a subpanel in the garage. |
#15
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
Exactly. If you think you may need a larger feed for future, you could pull
the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. If the two 20 amp circuits will suffice, four #12's will get you there. If you can pull out one of the existing romex's, you could tie the new conductors to the other and use it as a snake wrote in message ps.com... On Mar 18, 5:38 pm, "RBM" rbm2(remove wrote: He only needs #10 for the ground conductor for either #8 or #6. I'm not sure if it's "still" legal to not run a ground with the circuit conductors, but if he does that, nothing conductive can go between the buildings, including catv, telephone, metal water line, etc. "zxcvbob" wrote in message ... dpb wrote: As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. You could stuff four #8 THWN-2 wires in there pretty easily, and #8 is easy to work with. That would give you a 40A service with a separate ground. Or run 2 black sixes and a white #8 for a 50A (60A? I don't remember) service and establish a new ground at the garage. Either of these would be legal with 3/4" conduit. Bob Your starting to lose me here (noting conductive can go between th buildings...) In the same trench (outside of the conduit) I ran a coax line. Not sure if this impacts things or not. Correct me if I'm wrong but it sounds like it would be acceptable (and simpliest) to pull out the romex and push 4 #12 THWN conductors through (black, red, white, ??). (Is #12 easy to push or will I need to fish it through?) This would give me 2 120V 20 amp supply lines, one common neutral and a common ground. Without adding a subpanel I could splice these into romex in the garage. But as recommended it would be better to push #10 or #8 to increase the amperage and add a subpanel in the garage. |
#16
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On Mar 18, 7:08 pm, "RBM" rbm2(remove wrote:
Exactly. If you think you may need a larger feed for future, you could pull the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. If the two 20 amp circuits will suffice, four #12's will get you there. If you can pull out one of the existing romex's, you could tie the new conductors to the other and use it as a snake wrote in message ps.com... On Mar 18, 5:38 pm, "RBM" rbm2(remove wrote: He only needs #10 for the ground conductor for either #8 or #6. I'm not sure if it's "still" legal to not run a ground with the circuit conductors, but if he does that, nothing conductive can go between the buildings, including catv, telephone, metal water line, etc. "zxcvbob" wrote in message ... dpb wrote: As others have noted, I'll reiterate the more significant problems here -- first, for underground even in conduit you need wet-location- rated conductor and what you've described isn't -- you need an UF and could dispense w/ the conduit except for protecting it going underground. 3/4" conduit as you noted later isn't really large enough. I strongly recommend going to #10 for the feed and installing a small subpanel. It will be far better in the end to spend a few extra bucks up front. But, in particularl, the interior romex is _NOT_SUITABLE_ for the application. You could stuff four #8 THWN-2 wires in there pretty easily, and #8 is easy to work with. That would give you a 40A service with a separate ground. Or run 2 black sixes and a white #8 for a 50A (60A? I don't remember) service and establish a new ground at the garage. Either of these would be legal with 3/4" conduit. Bob Your starting to lose me here (noting conductive can go between th buildings...) In the same trench (outside of the conduit) I ran a coax line. Not sure if this impacts things or not. Correct me if I'm wrong but it sounds like it would be acceptable (and simpliest) to pull out the romex and push 4 #12 THWN conductors through (black, red, white, ??). (Is #12 easy to push or will I need to fish it through?) This would give me 2 120V 20 amp supply lines, one common neutral and a common ground. Without adding a subpanel I could splice these into romex in the garage. But as recommended it would be better to push #10 or #8 to increase the amperage and add a subpanel in the garage. Thanks a lot for the feedback. Very helpful. |
#17
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On 2007-03-19, RBM wrote:
Exactly. If you think you may need a larger feed for future, you could pull the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. Couldn't he pull the #8's but still wire the garage as two circuits on his existing main panel? Cheers, Wayne |
#18
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
I suppose, if he connected them to 20 amp breakers. Kinda defeats the
purpose for running 40 amp wire though "Wayne Whitney" wrote in message ... On 2007-03-19, RBM wrote: Exactly. If you think you may need a larger feed for future, you could pull the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. Couldn't he pull the #8's but still wire the garage as two circuits on his existing main panel? Cheers, Wayne |
#19
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
Wayne Whitney wrote:
On 2007-03-19, RBM wrote: Exactly. If you think you may need a larger feed for future, you could pull the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. Couldn't he pull the #8's but still wire the garage as two circuits on his existing main panel? Cheers, Wayne No, it won't all fit in the conduit. Bob |
#20
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
|
#21
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
Since it's a sub panel, you'll need 4 wires. Go get you a length of 10/3
with ground and do it up right. You'll not need any bigger. Then you can put in a 6 spot subpanel, use two for your 220 outlet, and have 4 for 110v outlets or lighting. -- Steve Barker YOU should be the one controlling YOUR car. Check out: www.lightsout.org wrote in message ups.com... I am running service from my house to a detached garage through 90' of buried conduit. I will be operating flourescent lights on one circuit and outlets on another. The outlets will power a fridge, an occasionally a battery charger, small tools, space heater, etc... Initially my plan was not to install a sub panel in the garage, but rather run two separate circuits from the service panel in the house to the garage. In the future I'd like to have the option to expand my voltage in the garage to 240V but at the current time this is not needed. I think I may have made an early mistake that is not to late to fix. So far I have run 2 lines of 14/2 romex through the conduit. I understand that this is only 15 amps on each circuit and I was thinking I should use 20 amp circuits (I know I should have used 12/2 wire). Howver, I purchased the 14/2 and don't have any 12 guage to use. If I leave the 14/2 in will this be enough to power the garage effectively? Also, does this give me the option to create a 240V circuit in the future? If I did decide to switch to 12 guage wire would it make sense to use a single 12/3 wire hooked to 2 separate 20 amp breakers at the main service in the house and split these in the garage to the two 20 amp circuits through 12/2 wire? Both circuits in the garage will be protected with GCFI outlets. |
#22
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
zxcvbob wrote:
Wayne Whitney wrote: On 2007-03-19, RBM wrote: Exactly. If you think you may need a larger feed for future, you could pull the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. Couldn't he pull the #8's but still wire the garage as two circuits on his existing main panel? Cheers, Wayne No, it won't all fit in the conduit. Bob Wait, I thought you meant pull #8's and leave the #12 Romex in the conduit too. Yes he could run #8 wires and feed them with a 20A 2-pole breaker. Then put the subpanel in later (increasing the breaker to 40A.) Bob |
#23
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
On Mar 18, 9:31 pm, zxcvbob wrote:
zxcvbob wrote: Wayne Whitney wrote: On 2007-03-19, RBM wrote: Exactly. If you think you may need a larger feed for future, you could pull the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. Couldn't he pull the #8's but still wire the garage as two circuits on his existing main panel? Cheers, Wayne No, it won't all fit in the conduit. Bob Wait, I thought you meant pull #8's and leave the #12 Romex in the conduit too. Yes he could run #8 wires and feed them with a 20A 2-pole breaker. Then put the subpanel in later (increasing the breaker to 40A.) Bob Because of the coax, running 3 wires for a 240V service is not an option. You need 3 wires for a 120V service or 4 wires for 240V. I don't understand the impact of the coax. Could someone please explain this to me. |
#24
Posted to alt.home.repair
|
|||
|
|||
Running service from house to garage
To run an electrical service to detached building, you didn't necessarily
have to pull a ground conductor with the feeder, you could establish a new ground at the detached building by driving ground rods, which now is a requirement for any service larger than two 20 amp circuits. The down side of establishing an independent grounding system at the detached building is that you can't run anything between the buildings that could become a ground path wrote in message oups.com... On Mar 18, 9:31 pm, zxcvbob wrote: zxcvbob wrote: Wayne Whitney wrote: On 2007-03-19, RBM wrote: Exactly. If you think you may need a larger feed for future, you could pull the number 8's as I describe, which will give you 40 amps, but you'd need a panel and the ground rods. Couldn't he pull the #8's but still wire the garage as two circuits on his existing main panel? Cheers, Wayne No, it won't all fit in the conduit. Bob Wait, I thought you meant pull #8's and leave the #12 Romex in the conduit too. Yes he could run #8 wires and feed them with a 20A 2-pole breaker. Then put the subpanel in later (increasing the breaker to 40A.) Bob Because of the coax, running 3 wires for a 240V service is not an option. You need 3 wires for a 120V service or 4 wires for 240V. I don't understand the impact of the coax. Could someone please explain this to me. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Running wire to detached garage | Home Repair | |||
Garage door stop running when light went off | Home Repair | |||
Running my house from a Generator, can I do this?.... | Home Repair | |||
wiring a detached garage - bringing it into the house/service panel | Home Repair | |||
Running a 220 receptacle to garage | Woodworking |