Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Will someone please explain the difference between the grounding
wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. |
#2
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Herb and Eneva wrote:
Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. The white wire is a neutral, not a ground. You and your wife go to the same movie; are you identical? |
#3
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Herb and Eneva wrote:
Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. When everything is working as intended, the white wire carries current and the green-cooper does not. The only time the white is not carrying current is when nothing on the pair of circuits is on or when there is identical load on both legs of the circuit. In short the without a fault the white can kill you the green can't. If the green fails it can damage equipment on that circuit as it may suddenly get 240V rather than the expected 120V. You can't safely eliminate either one as they both perform critical duties and can not be shared legally or safely. -- Joseph Meehan Dia 's Muire duit |
#4
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Joseph Meehan wrote:
If the green fails it can damage equipment on that circuit as it may suddenly get 240V rather than the expected 120V. Don't you mean white here? Chris |
#5
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Joseph Meehan wrote:
Herb and Eneva wrote: Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. When everything is working as intended, the white wire carries current and the green-cooper does not. Correct The only time the white is not carrying current is when nothing on the pair of circuits is on or when there is identical load on both legs of the circuit. Wrong. When all is off, the white wire sits at ground potential. When all is on, it still sits at ground potential + any tiny voltages created by the resistance of the wire and depending on the length of the wire. In short the without a fault the white can kill you the green can't. Wrong. When all is OK, the white wire has zero or very nearly zero volts potential. If the green fails it can damage equipment on that circuit as it may suddenly get 240V rather than the expected 120V. Only if it were damaged at or outside the main panel. You can't safely eliminate either one as they both perform critical duties and can not be shared legally or safely. True, but your reasoning is all Phhhttt! Please return to studying. Pop` |
#6
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Herb and Eneva wrote:
Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. Lots of reasons; it -can- get complicated to explain, but here's one situation: Any exposed metal in what's called Class 1 equipment (Stove, fridge, etc) must be grounded. The green ground wire is used for that ground. Its sole purpose for existance is safety. In addition, the blk/wh wires are NOT connected to the exposed metal; doors, cabinet, legs, etc etc. in equipment in today's equipment; it was different "yesterday". The reasoning here has to do with "polarity" of the hot/neutral. Should it be reversed, then the exposed metal would become "hot". So, if a miswire or fault occurs, which would/could place the exposed metal at 120V, the green ground wire connection would keep the exposed metal at ground poetntial instead of letting it go to 120V. In a properly wired ckt, it would also pop the fuse/breaker. In a miswired ckt the breaker would still pop since whatever is providing the 120V has to be coming from a fuse/breaker. Without the ground wire, touch the exposed metal and any other grounded point, such as faucets, nearby equipment, cement floor, lamp housing, etc., and you might well be electrocuted. I would recommend some online research for further info; there's a lot of it available. Also, ignore the other advice here so far; those people are gussing and goind a bad job of it at that. HTH, Pop` |
#7
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
If the green fails it can damage equipment on that circuit as it may
suddenly get 240V rather than the expected 120V. Exactly how would that work? Even if you misspoke and meant white instead of green, it still couldn't. Yes, there might be a floating neutral and some items could get over 120v, but they couldn't get 240v. |
#8
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Herb and Eneva wrote:
Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. Description is backward. The groundING wire is green (commonly called a ground wire). The groundED wire is white (commonly called a neutral wire). Use of these terms in the National Electrical Code is very confusing. The white wire is groundED at the service. This has 2 parts: Connection to the earth keeps the hot and white wire voltage to earth at a safe level. Connection to the groundING wires provides a path back to the transformer for fault current to trip a breaker. The green wire is for groundING exposed metal. Connection to earth at the service keeps exposed metal at approximate earth potential. If there is a fault to exposed metal, the groundING wire will conduct current back to the service, through the bond to the supply wire that was groundED, and back to the transfromer to trip a breaker. As others have noted, the groundED wire normally caries circuit current. The groundING wire is for safety and normally does not. -- bud-- |
#9
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Chris Friesen wrote:
Joseph Meehan wrote: If the green fails it can damage equipment on that circuit as it may suddenly get 240V rather than the expected 120V. Don't you mean white here? Chris Sure did. Good catch. -- Joseph Meehan Dia 's Muire duit |
#10
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Pop` wrote:
... True, but your reasoning is all Phhhttt! Please return to studying. Pop` Actually if you read what I wrote, I believe you will find it all correct with the exception of the green/white miss-type. -- Joseph Meehan Dia 's Muire duit |
#11
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
On Feb 20, 9:42 am, "Pop`" wrote:
Joseph Meehan wrote: Herb and Eneva wrote: Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. When everything is working as intended, the white wire carries current and the green-cooper does not. Correct The only time the white is not carrying current is when nothing on the pair of circuits is on or when there is identical load on both legs of the circuit. Wrong. When all is off, the white wire sits at ground potential. When all is on, it still sits at ground potential + any tiny voltages created by the resistance of the wire and depending on the length of the wire. In short the without a fault the white can kill you the green can't. Wrong. When all is OK, the white wire has zero or very nearly zero volts potential. If the green fails it can damage equipment on that circuit as it may suddenly get 240V rather than the expected 120V. Only if it were damaged at or outside the main panel. You can't safely eliminate either one as they both perform critical duties and can not be shared legally or safely. True, but your reasoning is all Phhhttt! Please return to studying. Pop` Are you saying that if I grab a white wire in a household circuit and stick my feet in a bathtub of water , that I will be perfectly fine because both the wire and my feet are at the same potential ??? Maybe I misunderstood you ? |
#12
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Are you saying that if I grab a white wire in a household circuit and stick my feet in a bathtub of water , that I will be perfectly fine because both the wire and my feet are at the same potential ??? That's the truth! Of course with today's plastic pipes, you might even get away with grabbing the BLACK (hot) wire. IF a circuit is fully loaded (but not overloaded) then there might be 1 or 2 (or 3) volts difference between the WHITE and GREEN wires. Maybe I misunderstood you ? |
#13
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
|
#14
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Joseph, sorry, but hang on. I've been doing this stuff my whole life
and what you say just isn't practical or worth mentioning in a forum like this, it's dangerous.. Here's the deal: 1. The white wire is a current carrying conductor, the green wire is not, under normal conditions, that's the simple answer to the question, along with number 2 below. 2. The green wire is as has been stated, the wire that will carry any current imposed on parts of an appliance or other metal surface, so that a breaker will trip in a shorted circuit. 3. NEVER THINK THAT A WHITE WIRE WON'T SHOCK YOU, YOU WILL DIE. White wires carry the same amount of current as black wires. When working on a circuit, always kill power to it first. Discussion about balanced circuits in this thread or in this group should be left alone because balanced circuits rarely occur and in the context of this thread, a single branch circuit, ie, 1 hot, 1neutral and 1 ground, the neutral will carry current equal to the hot wire, and it can kill you. If a circuit is energized and you break the neutral connection and hold on to it while your body is grounded, you won't like what happens, believe me. This has nothing to do with properly connected ground/ green wires, the white wires still have current on them or stated another way, they are looking for a ground and if you become that ground, like you say, you will be sorry, if you live to tell about it. 4. In new construction, the white wire and green wire terminate on separate busses. So no more terminating on the same bus. |
#15
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
"Pop`" wrote in message news:7PECh.962$CG5.186@trnddc03... Herb and Eneva wrote: Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. Lots of reasons; it -can- get complicated to explain, but here's one situation: Any exposed metal in what's called Class 1 equipment (Stove, fridge, etc) must be grounded. The green ground wire is used for that ground. Its sole purpose for existance is safety. In addition, the blk/wh wires are NOT connected to the exposed metal; doors, cabinet, legs, etc etc. in equipment in today's equipment; it was different "yesterday". The reasoning here has to do with "polarity" of the hot/neutral. Should it be reversed, then the exposed metal would become "hot". Using the "neutral" as a ground was generally used in two specific cases: 1) "High Current" 220/240 volt appliances which means stoves and electric dryers. Generally speaking, the neutral normally carried a tiny fraction of the total current. In "modern" stoves, that's just the oven lamp and the clock/electronics. In the dryer, the motor is still often 120. The GROUND/NEUTRAL connection was quite solid. The users definitely had contact with the neutral but in practice it just didn't cause problems. 2) The old style "AC/DC" radios and TVs. It was routine for the chassis to be connected to the neutral. That's why plugs are "polarized." BUT these things were insulated and the users didn't actually have contact with the neutral wire or metal parts that were connected. Now, things are "double insulated." |
#16
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
dreamchaser wrote:
Joseph, sorry, but hang on. I've been doing this stuff my whole life and what you say just isn't practical or worth mentioning in a forum like this, it's dangerous.. Here's the deal: Please read my messages. I know it is dangerous. See quotes from my messages: " Doing the same with a _properly connected_ copper ground wires would be safe." " All the above assumes everything is working as it should and Murphy is not applying his law to you at that time." "You can't safely eliminate either one as they both perform critical duties and can not be shared legally or safely." -- Joseph Meehan Dia 's Muire duit |
#17
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
|
#18
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
|
#19
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
|
#21
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
IF a circuit is fully loaded (but not overloaded) then there might be 1 or 2 (or 3) volts difference between the WHITE and GREEN wires. That doesn't matter. There's no current in the green (or bare) wire. There *is* current in the white wire. Using one's own body to provide a secondary path to ground for that current isn't very smart. Don't be silly. A few volts will not harm you. It doesn't matter whether the wires are carrying no current or are carrying many amps. |
#22
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Doug Miller wrote:
In article , says... No, in an ideal world that would be true, the problem is we don't live in an ideal world. The difference would be that if you cut the white wires and held one in each hand in an unbalanced load situation you would have current flowing thought you. You don't have to cut the white wire to get yourself in trouble. Touching an exposed part of an *intact* neutral creates a parallel path to ground through your body. Depending on how the resistance of that path is, you could be in serious trouble. True. -- Joseph Meehan Dia 's Muire duit |
#23
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
On Thu, 22 Feb 2007 19:02:36 -0500, "John Gilmer"
wrote: IF a circuit is fully loaded (but not overloaded) then there might be 1 or 2 (or 3) volts difference between the WHITE and GREEN wires. That doesn't matter. There's no current in the green (or bare) wire. There *is* current in the white wire. Using one's own body to provide a secondary path to ground for that current isn't very smart. Don't be silly. A few volts will not harm you. It doesn't matter whether the wires are carrying no current or are carrying many amps. Even if those many amps are flowing THROUGH you? |
#24
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
On Thu, 22 Feb 2007 19:02:36 -0500, "John Gilmer"
wrote: IF a circuit is fully loaded (but not overloaded) then there might be 1 or 2 (or 3) volts difference between the WHITE and GREEN wires. That doesn't matter. There's no current in the green (or bare) wire. There *is* current in the white wire. Using one's own body to provide a secondary path to ground for that current isn't very smart. Don't be silly. A few volts will not harm you. It doesn't matter whether the wires are carrying no current or are carrying many amps. They could. How many are using you as a conductor? BTW, was that you crossposting that unexplained "072" file? -- Mark Lloyd http://notstupid.laughingsquid.com "Unlike biological evolution. 'intelligent design' is not a genuine scientific theory and, therefore, has no place in the curriculum of our nation's public school classes." -- Ted Kennedy |
#25
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
Don't be silly. A few volts will not harm you. It doesn't matter whether the wires are carrying no current or are carrying many amps. This is incorrect!! It is the amount of amps that kills you........not volts!! |
#26
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
You know it's funny. On paper that may be true, and I've always heard that
statement. BUT I've never heard of someone being killed by a 12 volt battery, and when you do hear about someone being killed by electricity, it's always some higher voltage. -- Steve Barker "avid_hiker" wrote in message ups.com... Don't be silly. A few volts will not harm you. It doesn't matter whether the wires are carrying no current or are carrying many amps. This is incorrect!! It is the amount of amps that kills you........not volts!! |
#27
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
On Feb 23, 9:32 am, "Steve Barker"
wrote: You know it's funny. On paper that may be true, and I've always heard that statement. BUT I've never heard of someone being killed by a 12 volt battery, and when you do hear about someone being killed by electricity, it's always some higher voltage. -- Steve Barker "avid_hiker" wrote in message ups.com... Don't be silly. A few volts will not harm you. It doesn't matter whether the wires are carrying no current or are carrying many amps. This is incorrect!! It is the amount of amps that kills you........not volts!!- Hide quoted text - - Show quoted text - DC vs. AC current - Alternating current ( 60hz), if passing through your heart, will basically make your heart ( depending on the amount of current) beat at 60 beats/second or 3600 times a minute, therefore fibrillating your heart. The more current the more dangerous to one self. A lowvoltage ( 12vdc) line can not possibly produce as much current as a 120vac or dc line...... E ( voltage )= I (current) times R ( resistance ). Your body, depending on where this current is passing through, has a certain amount of resistance. A DC line, referring to current passing through your heart, will still kill you...........dont get me wrong.........which wont fibrillate your heart, but will completely stop your heart from beating if enough current is present.( Note -that your heart beats by electrical signals.) But yes.......your correct in a way.........that the more voltage is more dangerous........but using the formula.........the more voltage- the more current :-) Dean |
#28
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
|
#29
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
On Wed, 21 Feb 2007 04:44:12 -0500, "John Gilmer"
wrote: "Pop`" wrote in message news:7PECh.962$CG5.186@trnddc03... Herb and Eneva wrote: Will someone please explain the difference between the grounding wire---white, and the grounded wire---green, in a circut? They both go to the same busbar. Lots of reasons; it -can- get complicated to explain, but here's one situation: Any exposed metal in what's called Class 1 equipment (Stove, fridge, etc) must be grounded. The green ground wire is used for that ground. Its sole purpose for existance is safety. In addition, the blk/wh wires are NOT connected to the exposed metal; doors, cabinet, legs, etc etc. in equipment in today's equipment; it was different "yesterday". The reasoning here has to do with "polarity" of the hot/neutral. Should it be reversed, then the exposed metal would become "hot". Using the "neutral" as a ground was generally used in two specific cases: 1) "High Current" 220/240 volt appliances which means stoves and electric dryers. Generally speaking, the neutral normally carried a tiny fraction of the total current. In "modern" stoves, that's just the oven lamp and the clock/electronics. In the dryer, the motor is still often 120. The GROUND/NEUTRAL connection was quite solid. The users definitely had contact with the neutral but in practice it just didn't cause problems. Maybe I'm confused but why is this not using the neutral as a neutral? For the 110v portion of the appliance, a hot and a neutral are required. Why is this not what is here. 2) The old style "AC/DC" radios and TVs. It was routine for the chassis to be connected to the neutral. That's why plugs are "polarized." BUT Plugs are polarized now, but you refer to "old style". Again, maybe I'm confused but I thought there had been AC/DC radiosd all my life and more when I was younger when nothing had a polarized plug. these things were insulated and the users didn't actually have contact with the neutral wire or metal parts that were connected. Now, things are In one case, the case only covered the top and 4 sides, and the rear had a chip in it so that the chassis sometimes rested on a metal table we had. If I then touched that table and the stainless steel trim around the front of the Formica counter in the kitchen, I got a small buzz feeling. I still have the radio, but I've never fixed it. ;( "double insulated." |
#30
Posted to alt.home.repair
|
|||
|
|||
Grounding--ground wire
"Doug Miller" wrote in message .net... In article , says... No, in an ideal world that would be true, the problem is we don't live in an ideal world. The difference would be that if you cut the white wires and held one in each hand in an unbalanced load situation you would have current flowing thought you. As anybody who works much with electricity will tell you you can and will get bit off an intact neutral in any number of situations. It is part of the circuit and if current is flowing anywhere in the circuit it can flow through there too. It usually happens when somebody turns off a switch and not the breaker and starts grabbing wires. Seen it lots of times. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Bonded ground wires vs. earth ground wire | Home Repair | |||
ground wire extension (anti-static ground) | Electronics Repair | |||
Grounding Of Ground Wires In An Electrical Gang Box (how to handle the green ground wires) | Home Repair | |||
[Fwd: Self-grounding outlets vs. grounding wire] | Home Repair | |||
Self-grounding outlets vs. grounding wire | Home Repair |