Just got new drop in electric stove which has 4 wire 10 gage hookup.
Old stove has 3 wire 6 gage cable per my inspection of breaker box.
Do I have to replace with 4 wire cable or can I run a single 6 gage
wire to box to for forth wire.
Stan
  #3   Report Post  
toller
 
Posts: n/a
Default

The stove doesn't give installation instructions for 3wire? Then reply to
Mr. Horne.

(Is the #6 copper or aluminum? My stove is aluminum 3wire #6 and I plan on
replacing it; when the time comes.)


  #5   Report Post  
The Real Tom
 
Posts: n/a
Default

On Thu, 19 May 2005 03:51:14 -0400, " uriah wrote:

Just got new drop in electric stove which has 4 wire 10 gage hookup.
Old stove has 3 wire 6 gage cable per my inspection of breaker box.
Do I have to replace with 4 wire cable or can I run a single 6 gage
wire to box to for forth wire.
Stan



No. Sorry that I don't have the specific article in the NEC that says
it, but I recall, all wires in a circuit must be housed in a cabled
sheath, jacket or raceway. The forth wire would be independent of the
original 3 conductor cable, therefore it would violate this
requirement.

I'm guessing from what you wrote the forth wire would be a dedicated
equipement grounding conductor(since years ago 120/240volt applances
were grounded via the neutral wire), so even thought it isn't normally
carrying current of the circuit, it's part of the system.

Please, working from memory, so referr to the actual codes(even local)
for performing any electrical work.

hth,

tom @ www.WorkAtHomePlans.com





  #6   Report Post  
zxcvbob
 
Posts: n/a
Default

The Real Tom wrote:
On Thu, 19 May 2005 03:51:14 -0400, " uriah wrote:


Just got new drop in electric stove which has 4 wire 10 gage hookup.
Old stove has 3 wire 6 gage cable per my inspection of breaker box.
Do I have to replace with 4 wire cable or can I run a single 6 gage
wire to box to for forth wire.
Stan




No. Sorry that I don't have the specific article in the NEC that says
it, but I recall, all wires in a circuit must be housed in a cabled
sheath, jacket or raceway. The forth wire would be independent of the
original 3 conductor cable, therefore it would violate this
requirement.

I'm guessing from what you wrote the forth wire would be a dedicated
equipement grounding conductor(since years ago 120/240volt applances
were grounded via the neutral wire), so even thought it isn't normally
carrying current of the circuit, it's part of the system.

Please, working from memory, so referr to the actual codes(even local)
for performing any electrical work.

hth,

tom @ www.WorkAtHomePlans.com



Last time I checked, the NEC allows an equipment grounding conductor to
be run seperate from the current-carrying conductors when you are
updating old work. If I'm right, and if the original wiring has a red,
black, and white wire (or 3 black wires since it's #6), OP could run a
separate green or bare wire and bring the existing circuit up-to-date.

My guess is that the old cable is type SE, and he can't add a seperate
4th wire EGC because the cable's grounded conductor is not insulated
except by the outer jacket -- it could short out to the EGC at the metal
J-box -- and it's not white, nor black with white tape on the ends.

I don't know if that makes sense or not; I'm having trouble describing
it. My point is the EGC does *not* always have to run with the other
circuit wires, but that's unlikely to help in this situation.

Bob
  #7   Report Post  
 
Posts: n/a
Default

My apologies to folks who answered my prior post. Stove is new unit
and I have not pulled old unit yet as replacement is for cosmetic
purposes prior to house sale. I found install manual inside of
covered drip pan and have hook up directions. Gives both 3 & 4 wire
methods. Wires are in metal sheathing coming out of stove, & labeled
as 10 gage and are copper.

Seems like for current code (?) I will have to run 4-wire cable unless
I can get along with a separate appliance ground wire. Length of run
will be 30-35 feet so can I use 8 gage wire if separate run is not
allowed?



On Thu, 19 May 2005 03:51:14 -0400, " uriah wrote:

Just got new drop in electric stove which has 4 wire 10 gage hookup.
Old stove has 3 wire 6 gage cable per my inspection of breaker box.
Do I have to replace with 4 wire cable or can I run a single 6 gage
wire to box to for forth wire.
Stan


  #9   Report Post  
 
Posts: n/a
Default

Thank you for your advice Bob.
Stan

On Fri, 20 May 2005 08:31:12 -0500, zxcvbob
wrote:


You never said what the amps requirement is for the new stove; probably
40A. My code book is at work, but I think (if you really want to run a
new cable) you can use #8 copper cable if it is rated 75°C, or you could
use #6 aluminum SER. Eight gauge wire is a lot easier to work with than
#6 because #8 is much more flexible (it has small strands.)

I would just install the new stove on the old 3-wire circuit and be done
with it. You're trying to make this more difficult than it is. :-)

Best regards,
Bob


  #10   Report Post  
The Real Tom
 
Posts: n/a
Default

On Thu, 19 May 2005 21:29:31 -0500, zxcvbob
wrote:

The Real Tom wrote:
On Thu, 19 May 2005 03:51:14 -0400, " uriah wrote:


Just got new drop in electric stove which has 4 wire 10 gage hookup.
Old stove has 3 wire 6 gage cable per my inspection of breaker box.
Do I have to replace with 4 wire cable or can I run a single 6 gage
wire to box to for forth wire.
Stan




No. Sorry that I don't have the specific article in the NEC that says
it, but I recall, all wires in a circuit must be housed in a cabled
sheath, jacket or raceway. The forth wire would be independent of the
original 3 conductor cable, therefore it would violate this
requirement.

I'm guessing from what you wrote the forth wire would be a dedicated
equipement grounding conductor(since years ago 120/240volt applances
were grounded via the neutral wire), so even thought it isn't normally
carrying current of the circuit, it's part of the system.

Please, working from memory, so referr to the actual codes(even local)
for performing any electrical work.

hth,

tom @ www.WorkAtHomePlans.com



Last time I checked, the NEC allows an equipment grounding conductor to
be run seperate from the current-carrying conductors when you are
updating old work. If I'm right, and if the original wiring has a red,
black, and white wire (or 3 black wires since it's #6), OP could run a
separate green or bare wire and bring the existing circuit up-to-date.


Ah you are right, when replacing an ungrounded receptacle it is
allowed in certain 'existing' installations.

In the 2002 NEC (2005 hasn't been adopted yet here):
300.3 - 300.3(B)2 - 250.130(C)

After you do the connect the dots, you can run it seperate.

BTW, still have to check with the local codes, since they might want
proof the existing installation is ok first, or they might force you
to run a new 4 conductor line.

Remember check with codes before engaging in any electrical work.

My guess is that the old cable is type SE, and he can't add a seperate
4th wire EGC because the cable's grounded conductor is not insulated
except by the outer jacket -- it could short out to the EGC at the metal
J-box -- and it's not white, nor black with white tape on the ends.

I don't know if that makes sense or not; I'm having trouble describing
it. My point is the EGC does *not* always have to run with the other
circuit wires, but that's unlikely to help in this situation.

Bob


Would be nice if it's metal raceway(MC, AC, etc) so just changing the
receptale and grounding to a box would suffice.

IMHO,

tom


  #12   Report Post  
Doug Miller
 
Posts: n/a
Default

In article , Jeff Wisnia wrote:

What I'd like to learn is just what kind of faults and accidents drove
the code to require a separate ground conductor for those kind of
dedicated 230 volt appliance circuits, mainly clothes dryers and stoves
I suppose. By "dedicated" I mean that the circuit only serves one
receptical/appliance.


First off, note that clothes dryers and stoves are *not* purely 240V
appliances: the heating elements are 240V, but the control circuits (and, in
the case of a dryer, the motor) are 120V and thus need a neutral.

The neutral in a 120V circuit carries current. When the equipment chassis is
bonded to the neutral conductor, any person touching the chassis becomes a
secondary, parallel path to ground for the return current. Under certain
adverse circumstances (e.g. barefoot on a wet concrete floor) the possibility
exists for hazardous levels of current to flow through that person - even when
there is no fault in the wiring or in the appliance.

Wiring faults (e.g. a high-resistance connection in the neutral) greatly
increase this hazard, again even when there is no fault in the appliance.

These risks are essentially eliminated when the neutral is isolated from the
equipment chassis, and the chassis is bonded to ground.


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #13   Report Post  
Jeff Wisnia
 
Posts: n/a
Default

Doug Miller wrote:
In article , Jeff Wisnia wrote:

What I'd like to learn is just what kind of faults and accidents drove
the code to require a separate ground conductor for those kind of
dedicated 230 volt appliance circuits, mainly clothes dryers and stoves
I suppose. By "dedicated" I mean that the circuit only serves one
receptical/appliance.



First off, note that clothes dryers and stoves are *not* purely 240V
appliances: the heating elements are 240V, but the control circuits (and, in
the case of a dryer, the motor) are 120V and thus need a neutral.

The neutral in a 120V circuit carries current. When the equipment chassis is
bonded to the neutral conductor, any person touching the chassis becomes a
secondary, parallel path to ground for the return current. Under certain
adverse circumstances (e.g. barefoot on a wet concrete floor) the possibility
exists for hazardous levels of current to flow through that person - even when
there is no fault in the wiring or in the appliance.


You're correct of course, I considered that parallel path condition and
asumed a maximum of 10 amps of motor current flowing on the neutral
lead. With 75 feet of No. 10 wire, 10 amps will create only about 0.9
volt of drop in that neutral lead, and I figured that if you could drive
enought current through a human body with that low a voltage, even with
wet skin, I would have heard about people electrocuting themselves with
a single D cell battery by now. G

Wiring faults (e.g. a high-resistance connection in the neutral) greatly
increase this hazard, again even when there is no fault in the appliance.


I can't argue with that either.

These risks are essentially eliminated when the neutral is isolated from the
equipment chassis, and the chassis is bonded to ground.


Yes, as long as the chassis ground doesn't develop a high resistance or
open too.

All that said, I have to agree that the fourth conductor does add
another level of protection.

Jeff


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?



--
Jeffry Wisnia

(W1BSV + Brass Rat '57 EE)

"Truth exists; only falsehood has to be invented."
  #14   Report Post  
Andy Hill
 
Posts: n/a
Default

The key is that if a separate grounding conductor is used, it takes a
double-point failure (the ground has to be open AND a hot lead has to contact
the chassis) in order to create a life-threatening situation. Using neutral
as ground, all it takes is a single-point failure (floating neutral) to produce
a threat to life.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Whirlpool Stove with F-7 Code. TURTLE Home Repair 3 January 25th 05 11:48 AM
Grounding for Computer Equipment - Overreacting? Jim Home Ownership 19 December 12th 04 06:21 PM
Do you have Past Woodpeck Weekly Special Email? Jeremy Woodworking 2 August 8th 04 03:24 AM
Ceiling Light Problem - No Switch Phil Anderson Home Repair 35 January 26th 04 12:36 PM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 04:48 PM


All times are GMT +1. The time now is 02:26 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"